1. FENESTRATION COMPONENTS
Fenestration components include glazing material, either glass or plastic; framing, insulation, mullions, muntin bars, dividers, and opaque door slabs; and indoor and outdoor shading devices such as louvered blinds, drapes, roller shades, lightshelves, metal grills, and awnings. In this chapter, fenestration and fenestration systems refer to the basic assemblies and components of window, skylight, and door systems that are part of the building envelope.
Most fenestration currently manufactured using glass contains a glazing system that is packaged in the form of a glazing unit. A glazing unit consists of two or more glazing layers that are held apart by an edge seal. Figure 1 shows the construction of a typical double-glazing unit.
The most common glazing material is glass, although polymer (plastic) is sometimes used, either in the form of intermediate films bonded to glass, or as stand-alone glazing material popular in some skylight products. Both may be clear, tinted, coated, laminated, tempered, patterned, or obscured, and polymer types can be easily shaped, textured, and profiled using several processing options. Clear glazing material transmits more than 75% of the incident solar radiation and more than 85% of the visible light. Body-tinted glass containing a pigment is available in many colors, all of which differ in the amount of solar radiation and visible light they transmit and absorb. Some coated glazing materials are highly reflective (e.g., mirrors), whereas others have very low reflectance. Some spectrally selective glazing products include coatings that have a visible light transmittance more than double their solar transmittance; these are desirable for good daylighting while minimizing cooling loads. Coatings that reduce radiant heat exchange are called low-emissivity (low-e) coatings. Laminated glass is made of two panes of glass adhered together. The interlayer between the two panes of glass is typically plastic and may be clear, tinted, or coated. Tempered glass is designed for safety and shatters into pebble-sized pieces when broken. Patterned glass is a durable ceramic frit applied to a glass surface in a decorative pattern. Obscured glass is translucent and is typically used in privacy applications.
Low-e coated glass is energy efficient, improves daylighting potential, and enhances occupant comfort. Thus, it is now used in the vast majority of fenestration products. Low-e coatings are typically applied to one of the protected internal surfaces of the glazing unit (surface #2 or #3 in Figure 1), but some manufacturers now offer double- or triple-glazed products with an additional low-e coating on the exposed room-side surface (surface #4 in Figure 1, or what would be #6 in triple glazing). Low-e coatings can also be applied to thin plastic films for use either as one of the middle layers in glazing units with three or more layers (stretched and held in place by a spacer system), or surface-applied film, where the exposed low-e coating is protected by a very thin, thermal-IR (TIR) transparent protective layer.
A wide variety of low-e coatings are used today. Physically, they can be divided into either soft- or hard-coat types. Soft-coat low-e is fabricated using a sputtering process in a vacuum chamber. This is done as a post-processing phase after glass has been produced, cut, and stored. The resulting coating is very fragile, especially to the effects of moisture, so these coatings are normally protected inside the sealed glazing unit. Hard coatings are created using chemical vapor deposition and are applied to the glass while it is still being floated in its final phases of production. This creates a durable low-e coating that can be exposed to moisture and elements.
From a performance standpoint, categories include (1) high versus low solar gain, (2) spectrally selective, (3) reflective, (4) absorptive, and (5) high light-to-solar-gain (LSG) ratio. Some of these categories are related and causal. As a rule of thumb, soft coats are often low solar gain, whereas hard coats are usually high solar gain.
High-solar-gain coatings, which are more transparent to the whole solar spectrum, are used primarily on south facades in northern heating climates in the northern hemisphere (and, conversely, on north facades in southern heating climates in the southern hemisphere), so solar heat gain during the day can offset thermal heat loss during long, cold winter nights. When this coating is applied to indoor-facing glazing lites (although still facing the glazing cavity), it further increases the solar heat gain coefficient (SHGC), because a higher portion of absorbed solar radiation is transferred to the room (inward-flowing fraction). Their low emissivity helps reduce thermal IR radiation, resulting in increased thermal insulation.
Low-solar-gain coatings, which are usually spectrally selective [blocking admission of the near infrared portion of the solar spectrum, also known as near IR (NIR) or solar IR], are typically applied in hot, cooling-dominated regions to reduce solar heat gains, or in buildings where solar heat gains are not desirable (e.g., commercial buildings with large fenestration areas or high internal heat gains). Such coatings are normally applied to the outdoor-facing glazing lite to reduce the inward-flowing fraction of SHGC. The glass surface’s low emissivity also reduces thermal IR radiation heat transfer and therefore increases thermal resistance of the fenestration product. Although the majority of low-e coatings are applied to the glazing surface facing the glazing cavity, increasing numbers of durable coatings are being applied to the room-facing glazing surface. This further improves thermal performance (U-factor) by substantially reducing thermal IR radiation heat transfer on the room side of the window. However, in building spaces with higher indoor humidity levels in cold climates, this approach may significantly increase the risk of moisture condensation on glass surfaces. A new class of low-e surface-applied films may be applied as a retrofit measure to the indoor-facing glass surface; these films can perform similarly to low-e coated glass, so their use is more likely to be as an easy retrofit measure, removing the need to replace glass or sash.
In addition to low-e, fill gases such as argon, krypton, and xenon are used in lieu of air in the gap between glass panes. These fill gases reduce convective heat transfer across the glazing cavity. Krypton and xenon also reduce gap width, because their optimal gap widths are nearly half that of air.
The main requirements of the edge seal are to exclude moisture, provide a desiccant for the sealed space, and retain the glazing unit’s structural integrity. Further, the edge seal isolates the cavity between the glazing materials, thereby reducing the number of surfaces to be cleaned, and creating an enclosure suitable for nondurable low-e coatings and/or fill gases. The edge seal is composed of a spacer, single- or multilevel sealant, and desiccant.
The spacer separates glazing layers and provides a surface for primary and secondary sealant adhesion. Several types of spacers are used, each of which provides different heat transfer properties, depending on spacer material and geometry.
Heat transfer at the edge of the glazing unit is greater than at its center because of (1) heat flow through the spacer system and (2) convective flow, which creates an area of higher convective heat transfer as the gas turns from one glazing to the other. To minimize this heat flow, warm-edge spacers have been developed that reduce edge heat transfer by using materials (e.g., stainless steel, galvanized steel, tin-plated steel, polymers, foamed silicone) of lower thermal conductivity than the typical aluminum alloy from which spacers have often been made. Fusing or bending the corners of the spacer minimizes moisture and hydrocarbon vapor transmission from the gap space.
Several different sealant configurations are used in glazing unit construction. In dual-seal construction, a primary seal minimizes moisture transmission and gas escape. A secondary seal provides structural integrity between the lites of the glazing unit, and ensures long-term adhesion and greater resistance to solvents, oils, and short-term water immersion. In typical dual-seal construction, the primary seal is made of compressed polyisobutylene (PIB), and the secondary seal is made of silicone, polysulfide, or polyurethane. Single-seal construction depends on a single sealant to adhere the glazing to the spacer and to minimize moisture transmission and gas escape. Single-seal construction is generally more cost effective than dual-seal systems. Dual-seal-equivalent (DSE) materials take advantage of advanced cross-linking polymers that provide low moisture transmission and structural properties equivalent to dual-seal systems.
Desiccants are used to absorb moisture trapped in the glazing unit during assembly or that gradually diffuses through seals after construction. Typical desiccants include molecular sieve, silica gel, or a matrix of both materials.
The three main categories of fenestration framing materials are wood, metal, and polymers. Wood has good structural integrity and insulating value but low resistance to weather, moisture, warpage, and organic degradation (from mold and insects). Metal is durable and has excellent structural characteristics, but it has very poor thermal performance. The metal of choice in fenestration is almost exclusively aluminum alloy, because of its ease of manufacture, low cost, and low mass, but aluminum alloy has a thermal conductivity roughly 1000 times that of wood or polymers. Steel is sometimes used. Although lower in its thermal conductivity, the overall U-factor of a steel frame is similar to that of an aluminum frame of the same geometry. The poor thermal performance of metal-frame fenestration can be improved with a thermal break (a nonmetal component that separates the metal frame exposed to the outdoors from the surfaces exposed to the indoors). However, to be most effective, there must be thermal breaks in all operable sashes as well as in the frame. Polymer frames are made of extruded vinyl [unplasticized PVC (uPVC)] or pultruded fiberglass (glass-reinforced polyester). Their thermal and structural performance is similar to that of wood. Vinyl frames for large fenestration must be reinforced, which degrades their thermal performance slightly and substantially increases their weight. Polymer frames are generally hollow and thus can also be filled with polyurethane insulation, which reduces convective and radiative heat transfer, thereby achieving a better thermal performance than wood.
Manufacturers sometimes combine these materials as clad units (e.g., vinyl-clad aluminum, aluminum-clad wood, vinyl-clad wood) to increase durability, improve thermal performance, or improve aesthetics. In addition, curtain wall systems for commercial buildings may be structurally glazed, and the outdoor “framing” is simply rubber gaskets or silicone.
Generally, the framing system categorizes residential fenestration, as shown by the examples of traditional basic types in Figure 2. The glazing system can be mounted either directly in the frame (a direct-glazed or direct-set fenestration, which is not operable) or in a sash that moves in the frame (for an operating fenestration). In operable fenestration, a weather-sealing system between the frame and sash reduces air and water leakage.
Shading devices are available in a wide range of products that differ greatly in their appearance and energy performance. They include louvered shades (e.g., venetian blinds, vertical blinds, louvered shutters), roller shades, solar screens, cellular shades, awnings, roller shutters, draperies (curtains), roman shades, perforated panels, etc. Shades can be positioned as indoor, outdoor, or between-glazing products. When shades are applied after the fenestration unit was installed, a popular retrofit measure, these products are called fenestration attachments. When a fenestration unit is sold with matched shading as a complete assembly, the shade is called integral. Materials used include metal, wood, polymer, woven, and nonwoven fabrics.
The ability of shading devices to control solar gains depends mainly on the location of the device. Shades on the outdoor side of the glazing can effectively reduce solar heat gains, but need more frequent maintenance and are often difficult to adjust. Conversely, indoor devices are ubiquitous and easier to maintain and operate, but may not be as effective in providing significant solar heat gain control, depending on the glazing type, shade properties, and control (Barnaby et al. 2009; Lee and Selkowitz 1995; Moeseke et al. 2007; Shen and Tzempelikos 2012; Tzempelikos and Athienitis 2007; Wright et al. 2009a). Shading devices often do not produce any significant improvement in a fenestration system’s U-factor (Barnaby et al. 2009; Wright et al. 2009b). However, several classes of insulating shades (e.g., roller shutters, cellular shades, window quilts) can provide substantial insulating value and be used as an effective retrofit option to improve thermal resistance, especially if they are sealed tightly around the perimeter, and are not porous to air.
Shading devices are well suited to deal with daylighting, privacy, views, glare, and thermal comfort issues. Some products, such as properly adjusted venetian blinds, are quite versatile in this respect. Motorized shading devices can be adjusted under changing outdoor conditions to reduce glare, maximize daylight, reduce internal temperatures (Newsham 1994; Reinhart 2004), or improve thermal comfort to building occupants (Bessoudo et al. 2010) while also providing increased hours of view to the outdoor (Rao and Tzempelikos 2012).
Shading of vertical fenestration is not confined to the use of shading devices. Building elements such as window reveals, side fins, and overhangs can also offer effective shading. Metal grilles with fixed louvers mounted horizontally at the top of a fenestration can block solar gain while still letting some light through, thereby avoiding the negative impacts of solid structural overhangs that act as thermal bridges in the building envelope and reduce daylight. Light shelves can provide shading and also redirect sunlight deeper into the room to provide a more even spatial distribution of daylight in a space. Metal perforated panels are a suitable compromise between completely cutting out views and alleviating glare and overillumination issues. Outdoor vegetative shading is particularly effective in reducing solar heat gain while enhancing the outdoor scene, but may be hard to maintain and also not be persistent over multiple years.
3. U-FACTOR (THERMAL TRANSMITTANCE)
In the absence of sunlight, air infiltration, and moisture condensation, the first term on the right side of Equation (1) represents the heat transfer rate through a fenestration system. Most fenestration systems consist of transparent multipane glazing units and opaque elements comprising the sash and frame (hereafter called frame). The glazing unit’s heat transfer paths are subdivided into center-of-glass, edge-of-glass, and frame contributions (denoted by subscripts cg, eg, and f, respectively). Consequently, the total rate of heat transfer through a fenestration system can be calculated knowing the separate contributions of these three paths. (When present, glazing dividers, such as decorative grilles and muntin bars, also affect heat transfer, and their contribution must be considered.) The overall U-factor is estimated using area-weighted U-factors for each contribution by
Note that a product frame normally consists of several different areas, and that, for example, UfAf is really ΣUfiAfi, where i represents each frame region (e.g., sill, jamb, head, meeting rail). Likewise, each “edge of glazing” region is adjacent to a different frame region, so UegAeg is really ΣUegiAegi. Equation (2a) is used in North America [e.g., for fenestration ratings by the National Fenestration Rating Council (NFRC)], Australia [by the Australian Fenestration Rating Council (AFRC; www.afrc.org.au)], India, and other countries. This approach is described as one of the two options in ISO Standard 15099:2003 and is the basis of the calculation used by the Lawrence Berkeley National Lab WINDOW program (LBNL 2016), a widely used software tool for modeling fenestration products’ solar-optical and thermal performance. ASHRAE-derived environmental conditions, as used by the NFRC, are applied when Equation (2a) is used. These environmental conditions are detailed in Table 2.
When a fenestration product has glazed surfaces in only one direction, the sum of the areas equals the projected area Apf. Skylights, greenhouse/garden windows, bay/bow windows, etc., because they extend beyond the plane of the wall/roof, have greater surface area for heat loss than fenestration with a similar glazing option and frame material; consequently, U-factors for such products are greater than for the nonprojecting versions. When the slope of a multiglazed fenestration product varies from vertical, the gas in the glazing cavity begins to exhibit vortices that also increase heat flow per unit area. This results in a further U-Factor penalty for products rated at a slope (such as skylights).
In Europe and in some other parts of the world, U-factor is calculated differently: instead of the area-based, edge-of-glass term of Equation (2a), a linear thermal transmittance term Ψg is used to describe heat transfer near the perimeter of the glass area. This length-weighted method follows an alternative standard, ISO Standard 10077-2:2012, and is also described as second option in ISO Standard 15099.
where lg is the perimeter length of the entire vision area, delimited by the sightline. ISO Standards 10077-2 and 10077-1:2006 use simpler algorithms than ISO Standard 15099. In many fenestration systems, this leads to a different apparent U-factor, depending on which standard was followed. In a globalized economy, it is essential that designers and specifiers are aware of this lack of harmonization and that straight conversion between these standards is not possible.
Comparison Between Area-Weighted and Length-Weighted Methods
Glazing units (double- and triple-pane, many with low-e coatings and noble gas fills) were modeled for U-factor and reviewed by Curcija (2005) and van Dijk (2003). The studies showed that ISO 10077 versus NFRC differences in glazing U-factor can be as great as 0.3 W/(m2·K). These discrepancies are larger than the precision with which U-factors are reported for ratings under the European and NFRC systems. Therefore, for some glazing systems a noticeable difference in U-factor will be seen.
In addition to differences between center-of-glass U-factors obtained by the two methods, it is important to note that large differences can occur in frame U-factors; ISO Standard 15099/NFRC frame U-factors can be ~1 W/(m2 · K) greater than their ISO Standard 10077-2 equivalents. Although such differences are diluted when a whole-system, area-weighted calculation is performed, it cannot be assumed that these differences are negligible in all cases. Use ISO Standard 10077-based U-factors with caution and, for code compliance purposes in the United States, Canada, Australia, and some other countries, seek certifications based on NFRC procedures and environmental conditions. Refer to building codes for detailed requirements concerning NFRC compliance.
3.1 DETERMINING FENESTRATION U-FACTORS
For single glazing, U-factors depend strongly on indoor and outdoor film coefficients. The U-factor for single glazing is
where
| ho, hi | = | outdoor and indoor respective glazing surface heat transfer coefficients, W/(m2 · K) |
| L | = | glazing thickness, m |
| k | = | thermal conductivity of glass, W/(m2 · K) |
For other fenestration, values for Ucg at standard indoor and outdoor conditions depend on glazing construction features such as the number of glazing lights, gas space dimensions, orientation relative to vertical, emissivity of each surface, and composition of fill gas. Several computer programs can be used to estimate glazing unit heat transfer for a wide range of glazing construction. The National Fenestration Rating Council (NFRC) calls for LBNL WINDOW 7.4 (LBNL 2016) as a standard calculation method for center of glazing.
Heat flow across the central glazed portion of a multipane unit must consider both convective and radiative transfer in the gas space, and may be considered one-dimensional. Convective heat transfer is estimated based on high-aspect-ratio, natural convection correlations for vertical and inclined air layers (El Sherbiny et al. 1982; Shewen 1986; Wright 1996a). Radiative heat transfer (ignoring gas absorption) is quantified using a more fundamental approach. Computational methods solving the combined heat transfer problem have been devised by Hollands and Wright (1982), Rubin (1982a, 1982b), and Rubin et al. (1998).
Figure 3 shows the effect of gas space width on Ucg for vertical double- and triple-paned glazing units. U-factors are plotted for air, argon, and krypton fill gases and for high (uncoated) and low (coated) values of surface emissivity. The optimum gas space width is 13 mm for air and argon, and 8 mm for krypton. Greater widths have no significant effect on Ucg. Greater glazing unit thicknesses decrease Uo because the length of the shortest heat flow path through the frame increases. A low-emissivity coating combined with krypton gas fill offers significant potential for reducing heat transfer in narrow-gap-width glazing units.
The edge-of-glass area is typically taken to be a band 65 mm wide around the sightline. The width of this area is determined from the extent of two-dimensional heat transfer effects in current computer models, which are based on conduction-only analysis. In reality, because of convective and radiative effects, this area may extend beyond 65 mm (Beck et al. 1995; Curcija and Goss 1994; Wright and Sullivan 1995a), and depends on the type of glazing unit and its thickness. The edge region may also extend farther in opaque systems such as spandrel panels. The appropriate edge width to use can be determined using finite-element heat transfer modeling, as described by Curcija and Goss (1994).
In low-conductivity frames, most heat flow at the edge-of-glass and frame area is through the spacer, so the type of spacer has a greater impact on the edge-of-glass and frame U-factor. In metal frames, the edge-of-glass and frame U-factor varies little with the type of spacer (metal or insulating) because there is a significant heat flow through the highly conductive frame near the edge-of-glass area.
Fenestration frame elements consist of all structural members exclusive of glazing units and include sash, jamb, head, and sill members; meeting rails and stiles; mullions; and other glazing dividers. Estimating the rate of heat transfer through the frame is complicated by the (1) variety of fenestration products and frame configurations, (2) different combinations of materials used for frames, (3) different sizes available, and, to a lesser extent, (4) glazing unit width and spacer type. Internal dividers or grilles have little effect on the fenestration U-factor, provided there is at least a 3 mm gap between the divider and each glazing.
Computer simulations show that frame heat loss in most fenestration is controlled by a single component or controlling resistance, and only changes in this component significantly affect frame heat loss (EEL 1990). For example, the frame U-factor for thermally broken aluminum fenestration products is largely controlled by the depth of the thermal break material in the heat flow direction. For aluminum frames without a thermal break, the indoor film coefficient provides most of the resistance to heat flow. For vinyl- and wood-framed fenestrations, the controlling resistance is the shortest distance between the indoor and outdoor surfaces, which usually depends on the thickness of the sealed glazing unit.
Carpenter and McGowan (1993) experimentally validated frame U-factors for a variety of fixed and operable fenestration product types, sizes, and materials using computer modeling techniques. Table 1 lists frame U-factors for a variety of frame and spacer materials and glazing unit thicknesses. Frame and edge U-factors are normally determined by two-dimensional, finite-element computer simulation.
Curtain Wall Construction
A curtain wall is an exterior building wall that carries no roof or floor loads and consists entirely or principally of glass and other surfacing materials supported by a framework. A curtain wall typically has a metal frame. To improve the thermal performance of standard metal frames, manufacturers provide both traditional thermal breaks as well as thermally improved products. The traditional thermal break is poured and debridged (i.e., urethane is poured into a metal U-channel in the frame and then the bottom of the channel is removed by machine). For this system to work well, there must be a thermal break between indoors and outdoors for all frame components, including those in any operable sash. Skip debridging (incomplete pour and debridging used for increased structural strength) can significantly degrade the U-factor. Bolts that penetrate the thermal break also degrade performance, but to a lesser degree. Griffith et al. (1998) showed that stainless steel bolts spaced 300 mm on center increased the frame U-factor by 18%. The paper also concluded that, in general, the isothermal planes method referenced in Chapter 27 provides a conservative approach to determining U-factors.
Thermally improved metal curtain wall products are now being used more widely. In these products, most of the metal frame tends to be located on the indoor side with only a metal cap exposed on the outdoor side. Plastic spacers isolate the glazing assembly from both the outdoor metal cap and the indoor metal frame. These products can have significantly better thermal performance than standard metal frames, but it is important to minimize the number and area of the bolts that penetrate from outdoor to indoor. Curtain wall systems using structural silicone glazing (SSG) can also provide better thermal performance than dry-glazed bolted systems. Silicone sealants, with a typical thermal conductivity of 0.35 W/(m · K) and a dimension of 6 mm between the glass and aluminum are considered thermal breaks per NFRC Technical Document 100 (NFRC 2014a). Work by Carbary et al. (2009) demonstrates that SSG systems have lower U-factors than comparable nonbroken or thermally improved dry-glazed systems, resulting in frame temperatures closer to interior ambient conditions.
A more recent development is the use of fiberglass as the framing material for curtain walls. Fiberglass provides the strength needed for taller buildings while having a U-factor equal to or lower than that of other nonmetal materials (e.g., wood, vinyl).
An important consideration in any curtain wall system is durability. Sealants or gaskets that degrade or fail over time allow additional air infiltration, which negatively affects energy consumption. A durable system minimizes air infiltration and thereby energy consumption.
3.2 SURFACE AND CAVITY HEAT TRANSFER COEFFICIENTS
Part of the overall thermal resistance of a fenestration system derives from convective and radiative heat transfer between the exposed surfaces and the environment, and in the cavity between glazings. Surface heat transfer coefficients ho, hi , and hc at the outer and inner glazing surfaces, and in the cavity, respectively, combine the effects of radiation and convection.
Wind speed and building orientation are important in determining ho. This relationship has long been studied, and many correlations have been proposed for ho as a function of wind speed. However, no universal relationship has been accepted, and limited field measurements at low wind speeds by Klems (1989) differ significantly from values used by others.
Convective heat transfer coefficients are usually determined at standard temperature and air velocity conditions on each side. Wind speed can vary from less than 0.2 m/s for calm weather, free convection conditions, to over 29 m/s for storm conditions. A nominal value of 26 W/(m2 · K) corresponding to a 5.5 m/s wind is often used to represent winter design conditions. At low wind speeds, ho varies with outdoor air and surface temperature, orientation to vertical, and air moisture content. The overall surface heat transfer coefficient can be as low as 6.8 W/(m2 · K) (Yazdanian and Klems 1993).
For natural convection and radiation at the indoor surface of a vertical fenestration product, surface coefficient hi depends on the indoor air and glazing surface temperatures and on the emissivity of the glazing surface. Table 2 shows the variation of hi for winter (ti = 21°C) and summer (ti = 24°C) design conditions, for a range of glazing system types and heights. Designers often use hi = 8.3 W/(m2 · K), which corresponds to ti = 21°C, a glazing temperature of –9.4°C, and emissivity of eg = 0.84 (uncoated glass). For summer conditions, the same value [hi = 8.3 W/(m2 · K)] is normally used, and corresponds approximately to a glazing temperature of 35°C, ti = 24°C, and eg = 0.84. For winter conditions, this most closely approximates single glazing with clear glass that is 600 mm tall, but it overestimates the value as the glazing unit conductance decreases and height increases. For summer conditions, this value approximates all types of glass that are 600 mm tall but, again, is less accurate as glass height increases. If the indoor surface of the glass has a low-e coating, hi values are about halved at both winter and summer conditions.
Heat transfer between the glazing surface and its environment is driven not only by local air temperatures but also by radiant temperatures to which the surface is exposed. The radiant temperature of the indoor environment is generally assumed to be equal to the indoor air temperature. This is a safe assumption where a small fenestration is exposed to a large room with surface temperatures equal to the air temperature, but it is not valid in rooms where the fenestration is exposed to other large areas of glazing surfaces (e.g., greenhouse, atrium) or to other cooled or heated surfaces (Parmelee and Huebscher 1947).
The radiant temperature of the outdoor environment is frequently assumed to be equal to the outdoor air temperature. This assumption may be in error, because additional radiative heat loss occurs between a fenestration and the clear sky (Berdahl and Martin 1984). Therefore, for clear-sky conditions, some effective outdoor temperature to,e should replace to in Equation (1). For methods of determining to,e, see, for example, work by AGSL (1992). Note that a fully cloudy sky is assumed in ASHRAE design conditions.
The air space in a glazing unit constructed using glass with no reflective coating on the air space surfaces has a coefficient hs of 7.4 W/(m2 · K). When a reflective coating is applied to an air space surface, hs can be selected from Table 3 by first calculating the effective air space emissivity es,e by Equation (4):
where eo and ei are the hemispherical emissivities of the two air space surfaces. Hemispherical emissivity of ordinary uncoated glass is 0.84 over a wavelength range of 0.4 to 40 μm.
Table 4 lists computed U-factors, using winter design conditions, for a variety of generic fenestration products, based on ASHRAE-sponsored research involving laboratory testing and computer simulations. In the past, test data were used to provide more accurate results for specific products (Hogan 1988). Computer simulations (with validation by testing) are now accepted as the standard method for accurate product-specific U-factor determination. The simulation methodologies are specified in NFRC Technical Document 100 (NFRC 2014a) and are based on algorithms published in ISO Standard 15099. The International Energy Conservation Code and various state energy codes in the United States, the National Energy Code in Canada, and ASHRAE Standards 90.1 and 90.2 all reference these standards. Fenestration must be rated in accordance with the NFRC standards for code compliance. Use of Table 4 should be limited to that of an estimating tool for the early phases of design.
Values in Table 4 are for vertical installation and for skylights and other sloped installations with glazing surfaces sloped 20° from the horizontal. Data are based on center-of-glass and edge-of-glass component U-factors and assume that there are no dividers. However, they apply only to the specific design conditions described in the table’s footnotes, and are typically used only to determine peak load conditions for sizing heating equipment. Although these U-factors have been determined for winter conditions, they can also be used to estimate heat gain during peak cooling conditions, because conductive gain, which is one of several variables, is usually a small portion of the total heat gain for fenestration in direct sunlight. Glazing designs and framing materials may be compared in choosing a fenestration system that needs a specific winter design U-factor.
Table 4 lists 48 glazing types, with multiple glazing categories appropriate for sealed glazing units and the addition of storm sash to other glazing units. No distinction is made between flat and domed units such as skylights. For acrylic domes, use an average gas-space width to determine the U-factor. Note that garden window and sloped/pyramid/barrel vault skylight U-factors are approximately twice those of other similar products. Although this is partially because of the difference in slope in the case of sloped/pyramid/barrel vault skylights, it is largely because these products project out from the surface of the wall or roof. For instance, the skylight surface area, which includes the curb, can vary from 13 to 240% greater than the rough opening area, depending on the size and mounting method. Unless otherwise noted, all multiple-glazed units are filled with dry air. Argon units are assumed to be filled with 90% argon (Elmahdy and Yusuf 1995). U-factors for CO2-filled units are similar to argon fills. For spaces up to 13 mm, argon/SF6 (sulfur hexafluoride) mixtures up to 70% SF6 are generally the same as argon fills. Use of krypton gas can provide U-factors lower than those for argon for glazing spaces less than 13 mm.
Table 4 provides data for six values of hemispherical emissivity and for 6 and 13 mm gas space widths. Emissivity of various low-e glasses varies considerably between manufacturers and processes. When emissivity is between the listed values, interpolation may be used. When manufacturers’ data are not available for low-e glass, assume that glass with a pyrolytic (hard) coating has a maximum emissivity of 0.20 and that glass with a sputtered (soft) coating has a maximum emissivity of 0.10. Tinted glass does not change the winter U-factor. Also, some surface-coated reflective glass may have an emissivity less than 0.84. Values listed are for glass units using aluminum edge spacers. If an insulated or nonmetallic spacer is used, the U-factors are approximately 0.17 W/(m2 · K) lower.
Fenestration product types are subdivided first by vertical versus sloped installation and then into two general categories: manufactured and site assembled. Manufactured products are delivered as complete units to the site. These products are typically installed in low-rise residential and small commercial/institutional/industrial buildings. Use the operable category for vertical sliders, horizontal sliders, casement, awning, pivoted, and dual-action windows, and for sliding and swinging glass doors. For picture windows, use the fixed category. For products that project out from the surface of the wall, use the garden window category. For skylights, use the sloped skylight category.
Site-assembled products have frame extrusions that are assembled on site, and then glazing is added. These products are typically installed in high-rise residential and larger commercial/institutional/industrial buildings. Curtain walls are typically made up of vision (transparent) and spandrel (opaque) panels. Table 4 contains representative U-factors for the vision panel (including mullions) for these assemblies. The spandrel portion of curtain walls usually consists of a metal pan filled with insulation and covered with a sheet of glass or other weatherproof covering. Although the U-factor in the center of the spandrel panel can be quite low, the metal pan is a thermal bridge, significantly increasing the U-factor of the assembly. Two-dimensional simulation, validated by testing of a curtain wall having an aluminum frame with a thermal break, found that the U-factor for the edge of the spandrel panel (the 65 mm band around the perimeter adjacent to the frame) was 40% of the way toward the U-factor of the frame. The U-factor was 0.34 W/(m2· K) for the center of the spandrel, 2.56 for the edge of the spandrel, and 6.02 for the frame (Carpenter and Elmahdy 1994). Two-dimensional heat transfer analysis or physical testing is recommended to determine the U-factor of spandrel panels. Use the sloped/overhead glazing category for sloped glazing panels comparable to curtain walls.
Physical testing of double-glazed units showed U-factors of 5.74 W/(m2· K) for a thermally broken aluminum pyramidal skylight and 7.4 W/(m2· K) for an aluminum-frame half-round barrel vault (both normalized to a rough opening of 2.4 by 2.4 m). Until more conclusive results are available, U-factors for these systems can be estimated by multiplying the site-assembled sloped/overhead glazing values in Table 4 by the ratio of total product surface area (including curbs) to rough opening area. These ratios range from 1.2 to 2.0 for low-slope skylights, 1.4 to 2.1 for pyramid assemblies sloped at 45°, and 1.7 to 2.9 for semicircular barrel vault assemblies.
U-factors in Table 4 are based on definitions of the six product types, frame sizes, and proportion of frame to glass area shown in Figure 4. Four of the products are manufactured type. Sizes are as defined in NFRC Technical Document 100 (2014a): operable and fixed (nonoperable) glazing units are 1.8 m2 in area, and the overall size corresponds to a 1200 by 1500 mm fenestration product. The garden window category is 1.8 m2 in projected area (3.24 m2 in surface area) and 1500 mm wide by 1200 mm high by 380 mm deep. The manufactured skylight category is a nominal 1.44 m2 in area, corresponding to a 1200 by 1200 mm skylight. The nominal dimensions of a roof-mounted skylight correspond to centerline spacing of roof framing members; consequently, the rough opening dimensions are 1180 by 1180 mm. The curtain wall and sloped/overhead glazing categories are a nominal 4 m2 in area, representing repeating 2000 by 2000 mm panels. The nominal dimensions correspond to centerline spacing of the head and sill and vertical mullions.
Six frame types are listed (although not all for any one category) in order of improving thermal performance. The most conservative assumption is to use the frame category of aluminum frame without a thermal break (although there are products on the market that have higher U-factors). The aluminum frame with a thermal break is for frames having at least a 10 mm thermal break between the indoors and outdoors for all members including both the frame and the operable sash, if applicable. Some products are available with significantly wider thermal breaks, which achieve considerable improvement. The aluminum-clad wood/reinforced vinyl category represents vinyl-frame products, such as sliding glass doors or large windows that have extensive metal reinforcing within the frame and wood products with extensive metal, usually on the outdoor surface of the frame. Both of these factors provide short circuits, which degrade the thermal performance of the frame material. The wood/vinyl frame category represents the improved thermal performance that is possible if the thermal short circuits from the previous frame category do not exist. Insulated fiberglass/vinyl represents fiberglass or vinyl frames that do not have metal reinforcing and whose frame cavities are filled with insulation. For several site-assembled product types, there is a structural glazing frame category that represents products where sheets of glass are butt-glazed to each other using a sealant only, and framing members are not exposed to the exterior. For glazing with a steel frame, use aluminum frame values. For aluminum fenestration with wood trim or vinyl cladding, use the values for aluminum. Frame type refers to the primary unit; therefore, when storm sash is added over another fenestration product, use values given for the nonstorm product.
To estimate the overall U-factor of a fenestration product that differs significantly from the assumptions given in Table 4 and/or Figure 4, first determine the area that is frame/sash, center-of-glass, and edge-of-glass (based on a 63.5 mm band around the perimeter of each glazing unit). Next, determine the appropriate component U-factors. These can be taken either from the standard values listed in italics in Table 4 for glass, from the values in Table 1 for frames, or from some other source such as test data or computed factors. Finally, multiply the area and the component U-factors, sum these products, and then divide by the rough opening in the building envelope where this product will fit to obtain the overall U-factor Uo.
Table 5 provides approximate data to convert the overall U-factor at one wind condition to a U-factor at another.
Example 1.
Estimate the design U-factor for a manufactured fixed fenestration product with a reinforced vinyl frame and double-glazing with a sputter-type low-e coating (e = 0.10). The gap is 13 mm wide and argon-filled, and the spacer is metal. The outdoor wind speed is 12 km/h.
Solution: Locate the glazing system type in the first column of Table 4 (ID = 23), then find the appropriate product type (fixed) and frame type (reinforced vinyl). The U-factor listed (in the tenth column of U-factors) is 1.86 W/(m2 · K). This U-factor is for 24 km/h outdoor wind speed.
From Table 5, interpolate 1.86 in the 24 km/h column to the corresponding value in the 12 km/h column.
Example 2.
Estimate a representative U-factor for a wood-framed, 970 by 2080 mm swinging French door with eight 280 by 400 mm panes (true divided panels), each consisting of clear double-glazing with a 6.5 mm air space and a metal spacer.
Solution: Without more detailed information, assume that the dividers have the same U-factor as the frame and that the divider edge has the same U-factor as the edge-of-glass. Calculate center-of-glass, edge-of-glass, and frame areas:
Select center-of-glass, edge-of-glass, and frame U-factors. These component U-factors are 3.12 and 3.63 W/(m2 · K) (from Table 4, glazing ID = 4, U-factor columns 1 and 2) and 2.90 W/(m2 · K) (from Table 1, wood frame, metal spacer, operable, double-glazing), respectively. From Equation (2),
Example 3.
Estimate the overall average U-factor for a multifloor curtain wall assembly that is part vision glass and part opaque spandrel. The typical floor-to-floor height is 3.6 m, and the building module is 1.2 m as reflected in the spacing of the mullions both horizontally and vertically. For a representative section 1.2 m wide and 3.6 m tall, one of the modules is glazed and the other two are opaque. The mullions are aluminum frame with a thermal break 80 mm wide and centered on the module. The glazing unit is double glazing with a pyrolytic low-e coating (e = 0.40) and has a 13 mm gap filled with air and a metal spacer. The spandrel panel has a metal pan backed by R = 3.5 (m2 · K)/W insulation and no intermediate reinforcing members.
Solution: It is necessary to calculate the U-factor for the glazed module and for the opaque spandrel modules, and then to do an area-weighted average to determine the average U-factor for the overall curtain wall assembly.
First, calculate the overall U-factor for the glazed module. Calculate center-of-glass, edge-of-glass, and frame areas. The glazed area is 1120 by 1120 mm (1200 mm module, 38 mm of mullions on each edge).
Select center-of-glass, edge-of-glass, and frame U-factors. These component U-factors are 2.27 and 3.04 W/(m2 · K) (from Table 4, ID = 13, columns 1 and 2) and 9.94 W/(m2 · K) (from Table 1, aluminum frame with a thermal break, metal spacer, curtain wall, double glazing), respectively. From Equation (2),
Then, calculate the overall U-factor for the two opaque spandrel modules. The center-of-spandrel, edge-of spandrel, and frame areas are the same as the glazed module. The frame U-factor is the same. Calculate the center-of-spandrel U-factor. In this particular case, the R-value of the insulation does not need to be rated, because there are no intermediate framing members penetrating it and providing thermal short circuits. When the resistance of the insulation [3.5 (m2 · K)/W] is added to the exterior air film resistance of 0.03 (m2 · K)/W and the interior air film resistance of 0.12 (m2 · K)/W (from Table 1, Chapter 26), the total resistance is 3.65 (m2 · K)/W, and the U-factor is 1/3.65 = 0.274 W/(m2 · K). The edge-of-spandrel U-factor is 40% of the way to the frame U-factor, which is 0.274 + [0.40(9.94 – 0.274)] = 4.14 W/(m2 · K).
Finally, calculate the overall average U-factor for the curtain wall assembly, including the one module of vision glass and the two modules of opaque spandrel.
Note that even with double glazing having a low-e coating and with R = 3.5 (m2 · K)/W in the opaque areas, this curtain wall with metal pans only has an overall R-value of approximately 0.38 (m2 · K)/W.
Example 4.
Estimate the U-factor for a semicircular barrel vault that is 6 m wide, 3 m tall, and 10 m long mounted on a 150 mm curb. The barrel vault has an aluminum frame without a thermal break. The glazing is double with a 13 mm gap width filled with air and a low-e coating (e = 0.20).
Solution: An approximation can be made by multiplying the U-factor for a site-assembled sloped/overhead glazing product having the same frame and glazing features by the ratio of the surface area (including the curb) of the barrel vault to the rough opening area in the roof that the barrel vault fits over. First, determine the surface area (including the curb) of the barrel vault:
Area of the curved portion of the barrel vault
|
| |
Area of the two ends of the barrel vault
|
| |
Area of the curb
|
| |
Total surface area of the barrel vault
|
| |
Second, determine the rough opening area in the roof that the barrel vault fits over:
|
| |
Third, determine the ratio of the surface area to the rough opening area:
|
| |
| Fourth, determine the U-factor from Table 4 of a site-assembled sloped/overhead glazing product having the same frame and glazing features. The U-factor is 3.51 W/(m2 · K) (ID = 17, 12th column on the second page of Table 4). |
| |
Fifth, determine the estimated U-factor of the barrel vault.
|
3.3 REPRESENTATIVE U-FACTORS FOR DOORS
Doors are often an overlooked component in the thermal integrity of the building envelope. Although entry doors (swinging, revolving, etc.) represent a small portion of the building envelope of residential, commercial, and institutional buildings, their U-factor is usually many times higher than that of the walls or ceilings. In some commercial and industrial buildings, vehicular access doors (upward-acting doors) represent a significant area of heat loss. Table 6 contains representative U-factors for swinging doors determined through computer simulation (Carpenter and Hogan 1996). These are generic values, and product-specific values determined in accordance with standards should be used whenever available. NFRC Technical Document 100 (NFRC 2014a) gives procedures for evaluating the performance of entry and vehicular access doors. Tables 7 to 9 contain representative U-factors for revolving, emergency exit, garage, and aircraft hangar doors determined through testing (McGowan et al. 2006).
Swinging doors can be divided into two categories: slab and stile-and-rail. A stile-and-rail door is a swinging door with a full-glass insert supported by horizontal rails and vertical stiles. The stiles and rails are typically either solid wood members or extruded aluminum or vinyl, as shown in Figure 5. Most residential doors are slab type with solid wood, steel, or a fiberglass skin over foam insulation in a wood frame with aluminum sill. The edges of the steel skin door are normally wood to provide a thermal break. In commercial construction, doors are either steel skin over foam insulation in a steel frame (i.e., utility doors) or a full glass door made up of aluminum stiles, rails, and frame (i.e., entrance doors). The most important factors affecting door U-factor are material construction, glass size, and glass type. Frame depth, slab width, and number of panels have a minor effect on door performance. Side lites and double doors have U-factors similar to a single door of the same construction. For wood slab doors in a wood frame, the glazing area has little effect on the U-factor. For an insulated steel slab in a wood frame, however, glazing area strongly affects U-factor. Typical commercial insulated slab doors have a U-factor approximately twice that of residential insulated doors, the prime reason being thermal bridging of the slab edge and the steel frame. Stile-and-rail doors, even if thermally broken, have U-factors 50% higher than a full-glass commercial steel slab door.
There are three generic types of upward-acting doors:
Rolling (also called roll-up) doors consist of small metal slats of approximately 65 mm in height that travel in vertical guides and roll up around a metal barrel to open.
Sectional (also called garage) doors consist of a series of approximately 460 to 815 mm high sections that travel in vertical tracks to open.
Folding (also called biparting) doors, commonly used in aircraft hangars, have two large sections that also travel in vertical tracks to open, but fold together when the door is fully open.
There is a wide range in the design of insulated upward-acting doors. Factors affecting heat transfer include insulation thickness, section/slat design, and section/slat interface design (which may include a thermal break). For noninsulated upward-acting doors, there is very little difference between the center value and the total value: the value is essentially equal to that of single glazing. The center of an insulated door has a relatively low U-factor, but thermal bridging at the door frame and section interfaces can affect the door assembly U-factor. Center-of-door U-factors for vehicular access doors may be used in thermal calculations for buildings only if the door design or door size indicates little difference with respect to the total door assembly U-factor.
Many commercial buildings use revolving entrance doors. Most of these doors are of similar design: single glazing in an aluminum frame without thermal break. The door, however, can be in two positions: closed (X-shaped as viewed from above) or open (+-shaped as viewed from above). At nighttime, these doors are locked in the X position, effectively creating a double-glazed system. During the daytime, the door revolves and is often left positioned so that there is only one glazing between the indoors and outdoors (+ position). U-factors are given in Table 7 for both positions.
9. SELECTING FENESTRATION
Because fenestration systems provide so many functions, and because environmental conditions and user needs vary widely, it is difficult to make a completely optimal selection of a fenestration system. Considering aesthetics and cost, visual and comfort performance, annual energy costs, peak-load consequences, and acoustic characteristics, the choice is seldom optimal. The HVAC system designer, fortunately, has a more restricted range of interests, mainly dealing with the energy consequences of a particular fenestration selection. This section therefore focuses on fenestration energy performance determination.
9.1 ANNUAL ENERGY PERFORMANCE
Instantaneous energy performance indices (e.g., U-factor, solar heat gain coefficient, visible transmittance, air leakage) are typically used to compare fenestration systems under a fixed set of conditions. However, the absolute and relative effect of these indices on a building’s heating and cooling load can fluctuate as environmental conditions change. Further, internal loads from electric lighting fluctuate as automatic controls dim or turn off electric lighting in response to available daylight. As a result, these indices alone are not good indicators of the annual energy performance attributable to the fenestration. Such energy performance is difficult to quantify in and of itself because of numerous dynamic responses between the fenestration system and the total environment in which it is installed. The four basic mechanisms of fenestration energy performance (thermal transfer, solar heat gains, air leakage, and daylighting) should all be taken into account but are not independent of many other parameters that influence performance. As a result, the annual energy performance of fenestration systems can be accurately determined only when many variables are considered. Building type and orientation, climate (weather, temperature, wind speed), microclimate (shading from adjacent buildings, trees, terrain), occupant usage patterns, and certain HVAC parameters can significantly affect the annual energy effects of fenestration systems.
For these reasons, the most effective means of establishing fenestration annual energy performance is through detailed, dynamic, hourly computer simulations for the specific building and climate of interest. Because instantaneous performance of fenestration often varies by differing magnitudes as climatic conditions change, the most accurate simulation results are obtained when these variances are accounted for in a building energy simulation computer program. After constructing the simulation model following the procedures defined in Chapters 17 and 18 (for residential and commercial construction, respectively), specific changes to the fenestration system can be modeled, and the annual energy performance changes attributable to fenestration can be quantified. These analytical techniques do not consider issues of performance durability for the various instantaneous indices and should only be used as an initial annual energy performance indicator (Mathis and Garries 1995).
Simplified Techniques for Rough Estimates of Fenestration Annual Energy Performance
Although dynamic hourly modeling is certainly the most accurate technique for determining fenestration annual energy performance, and software for hourly modeling now runs on most desktop and laptop computers, it is not always available to decision makers and end users of fenestration products, simply because users may not want to make the necessary inputs to run the analysis. Under these circumstances, it may be useful to assess the relative importance of, or balance the trade-off between, the known instantaneous performance indices of U-factor, SHGC, Tv, and air leakage, for any given fenestration system when considering heating, cooling, and lighting loads for many different building types and climates. Huang et al. (1999) and Mitchell et al. (1999, 2012) describe personal computer programs to run this simplified analysis for residential windows.
Broad generalizations can be made for some classifications of building types and climates. For instance, with large commercial buildings, which require substantial cooling energy use during daytime occupied hours because of high internal loads, significant thermal mass, or high orientation dependency, low SHGC is important to reduce the cooling load. Also, an evaluation of commercial fenestration annual energy use can take into account the trade-off between electric lighting and the natural daylighting benefits associated with a particular fenestration system. However, low U-factor is also important because commercial buildings have bimodal operation: they can have significant heating energy consumption during morning warm-up, which occurs during unoccupied predawn hours, before people arrive and lights and equipment are turned on, and before any passive solar gain. In low-rise, detached residential buildings, electric lighting loads are typically very small in comparison to the heating and cooling loads because of high envelope-dependent energy use, egress requirements, and occupant usage patterns. The slight energy benefits of daylighting may be neglected altogether when using light-emitting diode (LED) lighting, which reduces residential light loads substantially. Despite these generalizations, the problem still exists of balancing and assessing the effect of each of the remaining parameters to establish seasonal or annual energy performance for cases in which detailed computer modeling is not performed. Furthermore, in all building types, the fact that energy savings afforded by daylighting are small does not negate the desirability of well-controlled natural light: daylighting without glare or excessive contrast is an important amenity.
Developing simplified annual energy performance indices for fenestration typically involves using instantaneous fenestration performance indices to quantify building- and climate-independent scalars of annual or seasonal energy performance for rating purposes. Many of these performance indices can be relatively independent of building type, climate, distribution of products, orientation, and other items needed for hourly dynamic building energy analyses. These normalized, scalar-based approaches are also limited in accuracy for the same reasons. A further limitation of the simplified techniques is that they do not have broad applicability to varied building types (e.g., commercial versus residential buildings). The usefulness of these scalar-based approaches can be increased when limiting the comparison to a single building type. Currently, simplified techniques for characterizing fenestration annual energy performance are applicable only to fenestration systems for detached residential buildings and are not appropriate for use with multifamily residential or commercial building fenestration systems.
Where a building function requires controlling outdoor air through a door opening, evaluation of the fenestration annual energy performance involving the resulting air exchange cannot be based on instantaneous indices, but must be based on an annualized process. Evaluate an automated door product designed to limit door-opening, door-open, and door-closing times for its air exchange, air leakage, and thermal transmittance properties, and compare its performance to that of a conventionally operating automated insulated sectional door complying with U-factor and air leakage requirements. Because a door product limiting air exchange is specified in terms of the number of opening and closing cycles per day averaged over a one-year period, not only can its annual energy performance be assessed, but its heating and cooling savings can also be estimated with respect to the sectional door, assuming the same number of average cycles per day and a similar door-open time.
Simplified Residential Annual Energy Performance Ratings
Annual energy performance (AEP) ratings can provide a simple means of product comparisons for consumers. These ratings have been derived with many assumptions, usually to suit local climatic conditions.
The Canadian Standards Association (CSA Standard A440.2) developed a simplified energy rating applicable to residential heating in the Canadian climate, which was adopted in the 1995 National Energy Code for Houses. The standard also provides for specific energy ratings to compare products by orientation and climate.
In the United States, where heating and cooling are both significant, NFRC is developing a rating system that includes both effects (Arasteh et al. 2000; Crooks et al. 1995). NFRC’s (2014i) Technical Document 901 provides guidance on how fenestration affects heating and cooling energy consumption in single-family residences.
In Australia, the Window Energy Rating Scheme (WERS; www.wers.net) publishes simplified, consumer-friendly AEP ratings for heating and cooling performance of residential windows. It displays regression-based AEP rankings as stars, on a scale of 0 to 10; one rating is for cooling performance, and another for heating. Ten stars for either heating and cooling corresponds to the “perfect” window for that purpose. As inputs, WERS uses U-factor and SHGC, determined using procedures licensed from the NFRC and the Australian Fenestration Rating Council (AFRC; www.afrc.org.au).
9.2 CONDENSATION RESISTANCE
Water vapor condenses in a film on fenestration surfaces that are at temperatures below the dew-point temperature of the indoor air. If the surface temperature is below freezing, frost forms. Sometimes, condensation occurs first, and ice from the condensed water forms when temperatures drop below freezing. Condensation frequently occurs on single glazing and on aluminum frames without a thermal break. The edge seal creates a thermal bridge at the perimeter of the glazing unit.
Circulation of fill gas caused by temperature differences in the glazing unit cavity contributes to the condensation problem at the bottom of the indoor glazing (Curcija and Goss 1994, 1995; Wright 1996b; Wright and Sullivan 1995a, 1995b). In winter, fill gas near the indoor glazing is warmed and flows up, while gas near the outdoor glazing is cooled and flows down. The descending gas becomes progressively colder until it reaches the bottom of the cavity. There, the gas turns and flows to the indoor glazing, resulting in higher heat transfer rates at the bottom. Thus, the bottom edge of the indoor glazing is cooled both by edge-seal conduction and by fill-gas convection. The combined effect of these two heat transfer mechanisms is shown in Figure 30. The surface isotherms show a wider band of cold glazing at the bottom of the window. Typical condensation patterns match these isotherms. The vertical indoor surface temperature profile also shows the effect of edge-seal conduction and that the minimum indoor surface temperature is near the bottom edge of the glazing.
Condensation on fenestration and surrounding structures can cause extensive structural, aesthetic, and health problems. Specific examples include peeling of paint, rotting of wood, saturation of insulation, and mold growth. Ice can render doors and windows inoperable and prevent egress during an emergency.
Energy-efficient housing has been accompanied by reduced ventilation. The resulting increase in indoor humidity has contributed to the condensation problem. However, the solution does not lie in the reduction of humidity levels to a minimum. Relative humidity below 20% and above 70% can increase health risks and reduce comfort. Generally, a minimum of 30% rh should be maintained, and 40% to 50% is more desirable (Sterling et al. 1985). Consequently, a better solution is to improve the fenestration product so interior surface temperatures are warmer and condensation does not occur or is minimized.
Minimum indoor surface temperatures can be quantified in a variety of ways. De Abreu et al. (1996), Elmahdy (1996), Griffith et al. (1996), Sullivan et al. (1996), and Zhao et al. (1996) demonstrated good agreement between detailed two-dimensional numerical simulation and surface temperature measurements using thermographs. Curcija et al. (1996) and Wright and Sullivan (1995c) developed simplified simulation models to predict condensation resistance. Center-glass and bottom-edge surface temperatures that can be expected for two different glazing systems exposed to a range of outdoor temperature are shown in Figure 31. Both glazing systems include insulating foam edge seals. High-performance glazing systems (e.g., low-e/argon and insulated spacers) allow significantly higher indoor humidity levels.
Current measures of condensation resistance of a fenestration system are the condensation resistance (CR) as defined by NFRC 500 (2014j) and its user guide (2014h), the condensation resistance factor (CRF) as defined by AAMA (1988), or the temperature index (I), as defined in CSA Standards A440 and A440.1.
Note that the temperature index method in CSA Standard A440 stipulates that the test is performed on the fenestration with all the cracks not sealed. This represents a major difference between the CSA Standard A440 method and the AAMA and NFRC methods. There are some merits of leaving cracks unsealed during testing for condensation resistance. In particular, any inherent deficiencies in fenestration design may result in uncontrolled air leakage through the fenestration. This air leakage could not be detected or dealt with in the simulation models, and can only be seen in the results of the determined temperature index. On the other hand, there is some financial benefit to the window manufacturer in testing the fenestration for condensation resistance with cracks sealed, because one test can determine R-value and condensation resistance.
Research shows that air leakage does affect the temperature index (measure of condensation resistance as determined by CSA Standard A440). Elmahdy (2001, 2003) showed that sealing cracks during testing artificially improves the temperature index, compared to the results of the same window tested with cracks unsealed.
Condensation resistance is a measure of condensation potential, based on both area and temperature weighting and expressed as a minimum of center-of-glazing, edge-of-glazing, and frame CRs. The novelty of this index is that it is determined using computer simulation tools unless the overall thermal performance cannot be validated with testing. If thermal performance cannot be validated, a testing option for determining CR is used.
The other two standards define the values by a single dimensionless number as
where th and tc are the warm- and cold-side temperatures, respectively. Figure 32 can be used to determine the acceptable range of CRF/I for a specific climatic zone.
The two standards differ in the methods used to determine temperature. The CSA test procedure is based on thermocouple measurements at the coldest location on the frame plus three locations on the glazing, each 10 mm above the bottom sightline. The AAMA procedure specifies two separate factors: one for the frame (CRFF), which uses weighted frame temperature obtained from surface temperature measurements at predetermined and roving locations on the frame, and one for the glazing unit (CRFG), which uses the average of six temperatures measured at predetermined locations near the top, middle, and bottom of the glazed area.
Indoor details can significantly alter the potential for condensation on fenestration surfaces. Items such as venetian blinds, roll blinds, insect screens, and drapes increase thermal resistance between the indoor space and fenestration and lower the temperature of the fenestration surfaces. These fenestration treatments do not prevent migration of moisture, so they can cause increased condensation. Figure 33 shows different situations that affect the potential for condensation. Note that window reveal plays an important role. If the window is placed near the outside of the wall, the increase in the outdoor film coefficient and decrease in the indoor film coefficient cause colder window surfaces. This effect is more pronounced near the corners of the recess where the indoor film coefficient is locally suppressed because air movement is restricted. Also, blinds should be placed at least 100 mm from the plane of the wall to allow some natural convection between the window and the blind.
Air leakage, especially in operable sections of fenestration, is another important cause of low surface temperature. Leakage near edge-of-glass sections can further increase the potential for condensation. However, the drier outdoor air decreases relative humidity near leakage sites and, in some cases, offsets the undesirable effect of lower surface temperatures. The net effect of air leakage cannot readily be determined experimentally or with simulation.
9.3 OCCUPANT COMFORT AND ACCEPTANCE
Human thermal comfort is an immediate sensation that reflects building occupants’ perceived response to many physical factors. Unlike much building design that is based primarily on long-term energy and economic considerations, comfort-related design focuses on, and must take heed of, short-term responses of the body’s physiology to its surroundings.
Fenestration influences thermal comfort through a combination of three mechanisms: long-wave radiation exchange, absorption of solar radiation, and convective draft effects (Figure 34). An understanding of these phenomena is important to help designers evaluate the benefits of improved fenestration and create comfortable buildings. Although it is well understood that high-performance fenestration can reduce building energy consumption, a better understanding of their effect on comfort might lead to further savings. For example, Hawthorne and Reilly (2000) suggest that significant energy consumption is caused by the standard practice of using perimeter duct distribution in houses to mitigate potential discomfort caused by fenestration. They found that perimeter heating is often not necessary when high-performance fenestration is installed and that heating energy savings of 10 to 15% could result from installing a simpler, less expensive duct system. Better windows can allow thermostat settings to be lowered with no loss of comfort. Another simulation study (Lyons et al. 2000) examined the relative magnitudes of a residential window’s physical influences under a wide variety of winter and summer climates, glazing parameters, and clothing levels. They found that
Long-wave, thermal radiation influences of the window dominate unless direct sun strikes the occupant
Direct solar load has a major influence on perceptions of comfort
For most residential-size windows, draft effects are generally small
With all but highly insulating fenestration, the indoor surface temperature of the fenestration is heavily influenced by outdoor conditions, and this temperature can significantly affect radiant heat exchange between an occupant and the environment. If this heat exchange moves outside the acceptable range, discomfort results. Mean radiant temperature (MRT) is commonly used to simplify the characterization of the radiant environment. On a cold day, the indoor surface temperature can easily drop below –9°C for a clear single-pane window and below 4°C for a clear, double-pane window. If the occupant is sitting sufficiently near the window, MRT could drop to 13°C for the single-pane case and 17°C for the double-pane case. Based on ASHRAE Standard 55, even use of the clear double-pane window could result in discomfort. [This example assumes an outdoor air temperature of –18°C, indoor air temperature of 22°C, nonwindow surface temperatures of 22°C, occupant/window view factor of 0.3, 0.9 clo (standard winter indoor clothing), and activity level of 1 met.] In addition to the MRT effect, a cold indoor glazing surface can induce a downward draft that increases air movement, contributing to further discomfort. If direct solar radiation strikes the glazing or occupant, the situation is much more complex. Conversely, for a double-pane window with a low-e coating and a triple-pane window with two low-e coatings, the net results would be MRTs of 19°C and 21°C, respectively. Both of these would satisfy the ASHRAE Standard 55 criteria for comfort.
In winter, the warming effect of sunlight on skin and clothing is often welcome, depending on the compounding effect of other factors such as air temperature. Fenestration also absorbs and transmits a significant amount of solar radiation. Because of such absorption, solar-heated fenestration may improve MRT for a nearby person. The premise of passive solar design is that occupants will welcome, or at least tolerate, solar gain in exchange for savings on heating energy. However, it is desirable that the onset of discomfort be able to be predicted; otherwise, the energy-saving design may be defeated if occupants draw shades to prevent overheating.
In summer, solar-heated glazing may become uncomfortably hot and, in commercial premises, actually devalue rented space near windows. The indoor surface of body-tinted, heat-absorbing glass can routinely reach temperatures above 50°C in summer conditions, raising MRT by as much as 8 K. This can be ameliorated by adding a second glazing on the indoors. Transmitted radiation often causes discomfort if it falls directly on the occupant. A person sitting near a window in direct solar radiation can experience heat gain equivalent to a 11 K rise in MRT (Arens et al. 1986). Similarly, in residential applications, the perceived need for solar control is affected both by the contribution of window surfaces to MRT and by overheating from direct solar load.
Advances in fenestration technology, especially high-performance glazings, mean that the designer has a choice of potential glazing systems. On the basis of annual energy performance for heating, cooling, and lighting, these alternatives may give similar outcomes. However, because they represent different combinations of U-factor, SHGC, and indoor glazing surface temperature, their comfort outcomes may differ considerably. Research continues to develop tools to help designers evaluate such difficult trade-offs. In the meantime, several general rules of thumb may be followed:
In heating-dominated climates, fenestration with the lowest U-factor tends to give the best comfort outcomes. However, there is likely to be a trade-off between the twin goals of maximizing instantaneous comfort and minimizing annual energy consumption.
In cooling-dominated climates or for orientations where cooling loads are of concern, fenestration with the lowest rise in surface temperature for a given SHGC tends to give the best comfort outcomes.
Proper acoustical treatment of outdoor walls can decrease noise levels in certain areas. The airtightness of a wall is the primary factor to consider in reducing sound transmission from outdoors. Once walls and fenestration products are tight, the choice of glazing and draperies becomes important. Draperies do not prevent sound from coming through the fenestration; they act as an absorber for sound that does penetrate. Table 17 lists average sound transmission losses for various types of glass. These averages apply for the frequency range of 125 to 4000 Hz and were determined by tests based on ASTM Standard E90.
In addition to its thermal, visual, and aesthetic functions, glazing for building exteriors must also perform well structurally. Wind loads are specified in most building codes, and these requirements may be adequate for many structures. However, detailed wind tunnel tests should be run for tall or unusually shaped buildings and for buildings where the surroundings create unusual wind patterns. The strength of annealed, heat-strengthened, tempered, laminated, and insulated glass is given in ASTM Standard E1300.
Thermal expansion and contraction can break ordinary annealed glass. This expansion and contraction can be caused by solar radiation onto partly shaded glazing, by heat traps from drop ceilings and tight-fitting drapes, or by HVAC ducts incorrectly directed toward the glazing. High-performance tinted and reflective glasses with low-e coatings are usually more vulnerable to thermal stress breakage than clear glass. Heat treating (heat strengthening or fully tempering) the glass resists thermal stress breakage. Heat-strengthened glass, although not a safety glass, is usually preferred to tempered (safety) glass because it typically has less distortion and is much less likely to have spontaneous breakage, which can occur on very rare occasions in tempered glass. Consult the glass manufacturer or fabricator for information on thermal stress performance.
Building codes may require glass in certain positions to perform with certain breakage characteristics, which can be satisfied by tempered, laminated, or wired glass. In this case, glass should meet Code of Federal Regulations 16CFR1201 or other appropriate breakage performance requirements.
Alternative building shells should be compared to ensure satisfactory energy use and total energy budget compliance, if required. ASHRAE Standards 90.1 and 90.2 should be used as a starting point. A life-cycle cost model should be developed for each system considered. See Chapter 37 of the 2019 ASHRAE Handbook—HVAC Applications.
Service life and long-term performance of fenestration systems depend on the durability of all the system’s components. Representative samples of glazing units are usually tested (for seal durability) according to test methods to ensure the integrity of the seal. Failure of glazing units is usually indicated by loss of adhesion of sealant to the glazing; as a result, fogging occurs inside the glazing cavity.
For argon-filled units, seal failure means a loss of argon and, hence, degradation in the unit’s thermal characteristics. Extensive study of the durability of glazing units filled with argon gas (Elmahdy and Yusuf 1995) indicated that, under normal conditions, argon loss by diffusion through the sealant is very small. However, when cracks or pinholes exist in the sealant, most of the argon gas escapes, which implies that stringent quality control procedures are essential for production of durable glazing units.
Degradation of organic materials and other chemical components in glazing units as a result of exposure to ultraviolet radiation is also a factor affecting durability and service life of fenestration systems. Low-e coatings on glass tend to enhance the appearance of chemical deposits on the glass surface. Also, inserting muntin bars in glazing cavities may result in excessive rates of unit failure during ultraviolet volatile (fogging) tests unless strict quality assurance processes are implemented. Current ASTM (United States) and CGSB (Canada) durability standards are being reviewed to reflect the emergence of new technologies in the fenestration industry.
A 15-year correlation study of insulating glazing units products by the Insulating Glass Manufacturers Association (IGMA) found that long-term performance and durability of glazing units correlated well with the test level to which the unit’s construction had been manufactured under ASTM Standard E2190’s specification for sealed glazing units. Units showing the highest percentage of resistance to seal failure were those tested in conformance with the ASTM Standard E2190 class CBA standard. Units that did not qualify to the A level showed a definite correlation to a higher percentage of failure. Field correlation studies found that units glazed in compliance with IGMA recommendations perform for longer periods than units not constructed properly, having deficiencies in the glazing system, or not meeting ASTM requirements.
Durability of fenestration systems also depends on durability of other system components, such as weatherstripping, gaskets, glazing tapes, air seals, and hardware. Wear of these elements with time and use may result in excessive air and water leakage, which affects overall performance and service life of the system. Excessive water leakage may cause damage to the fenestration product, especially the edge seal, as well as the wall section where the product is mounted. Excessive air leakage may lead to frost build-up and condensation on fenestration surfaces.
Studies conducted at the National Research Council of Canada (Elmahdy 1995) and elsewhere (Patenaude 1995) showed that, when windows are tested at high pressure and temperature differentials, they experience air leakage rates exceeding those determined at 75 Pa and zero temperature differential (conditions used in rating window air leakage in U.S. and Canadian standards). In other studies (CANMET 1991, 1993), pressure and motion cycling on windows resulted in excessive degradation in almost all performance factors, particularly condensation resistance, ease of operation, and air and water leakage.
To predict long-term performance, unit construction for glazing units should be tested and certified in accordance with ASTM Standard E2190 class CBA level and the requirements of IGMA or equivalent.
Durability may also affect long-term energy performance. Consequently, NFRC now requires third-party certification for sealed-glass units.
9.5 SUPPLY AND EXHAUST AIRFLOW WINDOWS
Airflow windows allow air to flow between glass panes of multilayered glazing units, to improve the window assembly’s thermal performance.
Exhaust air windows allow indoor air to flow between the inner two panes of a triple-glazed window. In the cooling season, this airflow helps reduce the cooling load by transferring heat to the flowing air and discharging it to the outdoors. During the heating season, heat loss through the outer pane of the window comes mostly from exhaust airflow, which helps reduce thermal transmission loss through the window. In addition, exhaust airflow helps maintain the inner pane surface temperature close to the indoor air temperature, thus improving the thermal comfort of occupants (Haddad and Elmahdy 1998, 1999).
The supply air window allows outdoor air to flow between the outer two panes of a triple-glazed window and into the building. The airflow helps reduce the heating load when heat picked up by the flowing air finds its way back into the indoor space. In the cooling season, the supply air window may increase the cooling load when heat is picked up from the outer glass pane and delivered into the indoor space.
Haddad and Elmahdy (1998, 1999) provide results of computer models comparing thermal performance of supply and exhaust airflow windows with conventional windows in various locations in North America.
National Fenestration Rating Council (NFRC)
The National Fenestration Rating Council (NFRC) was formed in 1989 to respond to a need for fair, accurate, and credible ratings for fenestration products. NFRC has developed rating procedures for U-factor [NFRC (2014a) Technical Document 100], solar heat gain coefficient and visible transmittance [NFRC (2014d) Technical Document 200], optical properties [NFRC (2014c) Technical Document 300], air leakage [NFRC (2014f) Technical Document 400], and condensation resistance [NFRC (2014j) Technical Document 500]. To provide certified ratings, manufacturers follow the requirements in the NFRC Product Certification Program (PCP), which involves working with laboratories accredited to the NFRC Laboratory Accreditation Program (LAP), and independent certification and inspection agencies accredited through the NFRC Certification Agency Program (CAP).
NFRC (2014a) Technical Document 100 was the first NFRC rating procedure approved and thus the first NFRC procedure adopted into energy codes in the United States. It requires using a combination of state-of-the-art computer simulations and improved thermal testing to determine U-factors for the whole product. The next step is product certification. NFRC has a series of checks and balances to ensure that the rating system is accurately and uniformly used. Products and their ratings are authorized for certification by an NFRC-licensed independent certification and inspection agency (IA). Finally, two labels are required: the temporary label, which contains the product ratings, and a permanent label, which allows tracking back to the IA and information in the NFRC Product Directory. In addition to informing the buyer, the temporary label provides the building inspector with information necessary to verify energy code compliance. The permanent label provides access to energy rating information for a future owner, property manager, building inspector, lending agency, or building energy rating organization.
This process has noteworthy features that make it superior to previous fenestration energy rating systems and correct past problems:
The procedures provide a means for manufacturers to take credit for all the nuances and refinement in their product design and a common basis for others to compare product claims.
Involvement of independent laboratories and the IA provides architects, engineers, designers, contractors, consumers, building officials, and utility representatives with greater confidence that the information is unbiased.
Requiring simulation and testing provides an automatic check on accuracy. This also remedies a shortcoming of previous energy code requirements that relied on testing alone, which allowed manufacturers to perform several tests and then use the best one for code purposes.
The certification process indicates that the manufacturer is consistently producing the product that was rated. This corrects a past concern that manufacturers were able to make an exceptionally high-quality sample and obtain a good rating in a test but not consistently produce that product.
A readily visible temporary label can be used by the building inspector to quickly verify compliance with the energy code.
A permanent label enables future access to energy rating information.
Although the NFRC program is similar for other fenestration characteristics, there are differences worth noting. Solar heat gain coefficient and visible transmittance ratings [NFRC (2014d) Technical Document 200], referenced in several codes, and condensation resistance ratings [NFRC (2014j) Technical Document 500] are based on simulation alone. Optical properties [NFRC (2014c) Technical Document 300] and emissivity [NFRC (2014g) Technical Document 301] are based on measurements by the manufacturer, with independent verification. Air leakage ratings [NFRC (2014h) Technical Document 400] are based on testing alone. For site-assembled fenestration products (e.g., curtain walls, window walls), an NFRC label certificate fulfills the labeling requirements and serves the certification purpose. A separate NFRC label certificate is required for each “individual product” in a particular project.
United States Energy Policy Act (EPAct)
In the United States, the 1992 Energy Policy Act (EPAct) required the development of national fenestration energy rating systems and specified NFRC as the preferred developer. (The U.S. Department of Energy was to establish procedures if NFRC did not.) Although this recognition provided an impetus for NFRC to develop the desired procedures and programs, the EPAct sections on energy codes have been a key factor in their implementation.
EPAct set baselines for state energy codes. The ICC 2015 International Energy Conservation Code® (IECC®) and ASHRAE/IES Standard 90.1-2016, Energy Standard for Buildings Except Low-Rise Residential Buildings, are the current successors to the versions cited in the 1992 legislation. The majority of states have adopted the predecessors to the 2015 IECC (including the 2012, 2009, 2006, 2003, 2000, and 1998 IECC and the CABO 1995 Model Energy Code) and to ASHRAE/IES Standard 90.1-2016 (i.e., ASHRAE/IES Standard 90.1-2013/2010/2007/2004/2001/1999/1989) into their codes either directly or by reference when adopting a building code published by one of the three national code organizations in the United States. The ICC 2015 International Building Code (the U.S. model building code jointly developed by ICBO, BOCA, and SBCCI) references the 2015 IECC.
ICC’s 2015 International Energy Conservation Code
The ICC’s 2015 IECC references NFRC (2014a) Technical Document 100 for U-factor (as did the 2012, 2009, 2006, 2003, 2000, and 1998 IECC and the 1995 Model Energy Code) and NFRC (2014d) Technical Document 200 for solar heat gain coefficient (SHGC) (as did the 2012, 2009, 2006, 2003, 2000, and 1998 IECC). Sections C303.1.1 and R303.1.3, which cover all occupancies, require U-factors and SHGCs and visible transmittances (Tvs) of fenestration products (windows, doors, and skylights) to be determined in accordance with NFRC Technical Documents 100 and 200 by an accredited independent laboratory, and labeled and certified by the manufacturer. The language does not specify NFRC accreditation; however, it requires both the use of the NFRC rating procedure by an independent entity, and labeling and certification. Sections C402.4.3 and R402.4.3 cite NFRC (2014h) Technical Document 400, and others for air leakage testing.
ASHRAE/IES Standard 90.1-2016
In 1999, ASHRAE and IES published a comprehensive update to Standard 90.1-1989 that included fenestration rating, labeling, and certification criteria in Sections 5.2.2 and 5.2.3. U-factors were to be determined in accordance with NFRC (2014a) Technical Document 100, solar heat gain coefficient and visible transmittance in accordance with NFRC (2014d) Technical Document 200, and air leakage in accordance with NFRC (2014h) Technical Document 400.
In 2001, ASHRAE and IES made nominal modifications to Standard 90.1. The most significant changes for the 2004 version were in the lighting section, with fenestration rating, labeling, and certification criteria found in Sections 5.8.2.
The 2007 revision included substantial increases in stringency for the building envelope, including both opaque assemblies and fenestration. The NFRC references remained unchanged.
The 2010 update had limited changes to the fenestration U-factor and SHGC criteria, but called for reduced air leakage. The standard began to address fenestration orientation and daylighting: in the northern hemisphere, vertical fenestration must have more area on the south side than on either the east or west side. Spaces with tall ceilings and under a roof must have a minimum skylight area for daylighting purposes. Exceptions are provided to the SHGC requirements for dynamic glazing.
The 2013 version made significant changes to fenestration U-factor and SHGC criteria. The standard expanded the consideration of daylighting by establishing criteria for a minimum VT/SHGC ratio where there is automatic control of lighting in daylight zones.
The 2016 update further changed the requirements for fenestration U-factors in most climate zones, and for SHGC in a few climate zones. Limited modifications were made to the fenestration orientation criteria.
For further information on U.S. energy codes, the Building Codes Assistance Project (BCAP) publishes a bimonthly summary entitled “Status of State Energy Codes,” which provides information on current codes and pending legislation. For additional information, contact BCAP at www.bcap-energy.org.
ASHRAE/USGBC/IES Standard 189.1-2014
In 2006, ASHRAE, the U.S. Green Building Council (USGBC), and IES embarked on a project to develop a baseline standard for high-performance, green buildings that would apply to all buildings except low-rise residential buildings. Their Standard 189.1-2009 addresses sustainable sites, energy and water efficiency, the building’s effect on the atmosphere, materials and resources, and indoor environmental quality (IEQ). The standard is not a rating system, but it is hoped that it will be integrated into future building rating systems.
Energy-efficiency goals for the first version of Standard 189.1 were to achieve a 30% additional energy savings beyond that in ASHRAE/IES Standard 90.1-2007. Standard 189.1 builds on Standard 90.1, but the prescriptive option in Standard 189.1 substitutes more stringent values in the tables and adds other criteria. For example, the prescriptive option requires that, in the northern hemisphere, vertical fenestration on the west, south, and east be shaded by a device or devices with a 0.50 projection factor (e.g., an overhang that is one-half as wide as the window is tall).
There were subsequent updates in 2011 and 2014.
ICC’s 2015 International Green Construction Code™
The ICC’s 2012 International Green Construction Code™ (IgCC™) is an overlay code to ICC’s 2012 IECC. The fenestration criteria call for a 10% reduction in U-factor and SHGC from the 2012 IECC. The prescriptive option requires that, in the northern hemisphere, vertical fenestration on the west, south, and east be shaded by a device with a 0.25 projection factor (e.g., an overhang that is one-quarter as wide as the window is tall). The IgCC also allows ASHRAE/USGBC/IES Standard 189.1 as a compliance option.
After publication of the 2019 International Green Construction Code, ASHRAE and USGBC began investigating the possibilities for greater alignment between the IgCC and Standard 189.1.
Canadian Standards Association (CSA)
In Canada, the Canadian Standards Association (CSA) promulgates fenestration energy rating standards. CSA Standard A440.2 addresses most fenestration products, and CSA Standard A453 addresses doors. These are companion standards to NFRC (2014a) Technical Document 100. NFRC and CSA established a Thermal Harmonization Task Force to attempt to harmonize their fenestration energy rating standards.
Building Code of Australia/National Construction Code
In Australia, the Australian Building Codes Board maintains the National Construction Code, which includes the Building Code of Australia (BCA). The code is divided into separate volumes for residential and commercial construction. Sections 2 and 3 (residential) and Section J (commercial) set out various compliance paths for building envelope performance. Section J of the National Construction Code covers energy efficiency provisions for nonresidential building stock in Australia. To demonstrate compliance with Section J2 of the National Construction Code, the U-factor and SHGC of fenestration systems are to be rated in accordance to with Australian Fenestration Rating Council (AFRC; www.afrc.org.au), which adopts the same technical procedures as NFRC. Users should note that the energy provisions for fenestration systems are based on an energy-flow approach and do not have an upper limit for fenestration area as a percentage of gross wall area.
Complex Glazings and Window Coverings
In North America, the European Union, and Australia, fenestration rating programs are being extended to include shading devices and other nonspecular, “complex” glazing layers. These rating schemes rely on expanded capabilities of existing modeling software and measurements of basic material properties, supported by a set of industry-consensus assumptions about fitting details. However, such calculations can also be performed in “expert” mode to serve the needs of building energy modelers who require exact, rather than generalized, details.
| a | = | absorptance in a layer, considered as an isolated layer |
| A | = | total projected area of a fenestration product; apparent solar constant |
| A | = | absorptance in a layer or a collection of layers (system or subsystem) |
| e | = | hemispherical emissivity |
| Ed | = | diffuse sky irradiance |
| ED | = | direct irradiance |
| EDN | = | direct normal irradiance |
| Er | = | diffuse ground reflected irradiance |
| Et | = | total irradiance |
| FR | = | radiant fraction |
| h | = | surface heat transfer coefficient |
| k | = | thermal conductivity |
| L | = | glass thickness |
| n | = | refractive index |
| PH | = | horizontal projection depth |
| PV | = | vertical projection depth |
| q | = | instantaneous energy flux |
| Q | = | instantaneous energy flow |
| R | = | reflectance of a layer or collection of layers (system or subsystem) |
| RH | = | height of opaque surface between fenestration product and horizontal projection |
| RW | = | width of opaque surface between fenestration product and vertical projection |
| SH | = | shadow height |
| SW | = | shadow width |
| SHGC | = | solar heat gain coefficient |
| t | = | relative temperature |
| T | = | absolute temperature; transmittance of layer or collection of layers (system or subsystem) |
| U | = | overall coefficient of heat transfer |
| W | = | fenestration product width |
Greek
| α | = | material absorptivity |
| β | = | solar altitude angle |
| γ | = | surface solar azimuth |
| Δ | = | vertical projection profile angle |
| δ | = | declination |
| θ | = | incident angle |
| λ | = | wavelength |
| ξ | = | refractive angle |
| ρg | = | ground reflectivity |
| Σ | = | surface tilt |
| τ | = | transmissivity |
| φ | = | solar azimuth |
| Ω | = | horizontal projection profile angle |
| ϖ̄ | = | solid angle |
ASHRAE members can access ASHRAE Journal articles and ASHRAE research project final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.
AAMA. 1987. Skylight handbook: Design guidelines. American Architectural Manufacturers Association, Schamberg, IL.
AAMA. 1988. Voluntary test method for thermal transmittance and condensation resistance of windows, doors and glazed wall sections. Publication AAMA 1503.1-88. American Architectural Manufacturers Association, Schamberg, IL.
ADOPT. 1996. Angle-dependent optical properties. Commission of the European Communities, Standards, Measurement and Testing Programme, DG XII, Contract SMT4-CT96-2138. Coordinator A. Roos, University of Uppsala, Sweden.
AGSL. 1992. Vision3: Glazing system thermal analysis—User manual. Department of Mechanical Engineering, University of Waterloo, Ontario.
Allen, T. 1997. Conventional and tubular skylights: An evaluation of the daylighting systems at two ACT commercial buildings. Proceedings of the 22nd National Passive Solar Conference, Washington, D.C., pp. 97-129.
Arasteh, D., J. Huang, R. Mitchell, B. Clear, and C. Kohler. 2000. A database of window annual energy use in typical North American single family houses. ASHRAE Transactions 106(1):562-574.
Arasteh, D., C. Kohler, and B. Griffith. 2009. Modeling windows in EnergyPlus with simple performance indices. Report LBNL-2804E. Lawrence Berkeley National Laboratory.
Arens, E.A., R. Gonzalez, and L. Berglund. 1986. Thermal comfort under an extended range of environmental conditions. ASHRAE Transactions 92(1).
ASHRAE. 2013. Thermal environmental conditions for human occupancy. ANSI/ASHRAE Standard 55-2013.
ASHRAE. 2016. Energy standard for buildings except low-rise residential buildings. ANSI/ASHRAE/IES Standard 90.1-2016.
ASHRAE. 2007. Energy-efficient design of low-rise residential buildings. ANSI/ASHRAE Standard 90.2-2007.
ASHRAE. 2014. Standard for the design of high-performance green buildings except low-rise residential buildings. ANSI/ASHRAE/USGBC/IES Standard 189.1-2014.
ASTM. 2009. Recommended practice for laboratory measurements of airborne sound transmission loss of building partitions. Standard E90-09. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2012. Standard test method for determining rate of air leakage through exterior windows, curtain walls, and doors under specified pressure differences across the specimen. Standard E283-04 (2012). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 1992. Tables for terrestrial direct normal solar spectral irradiance tables for air mass 1.5. Standard E891-1989 (1992). Withdrawn 1999. American Society for Testing and Materials, West Conshohockehn, PA.
ASTM. 2011. Standard practice for calculation of photometric transmittance and reflectance of materials to solar radiation. Standard E971-11. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2013. Standard test method for solar photometric transmittance of sheet materials using sunlight. Standard E972-92 (2013). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2015. Standard test method for solar transmittance (terrestrial) of sheet materials using sunlight. Standard E1084-86 (2015). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2015. Standard test method for determining solar or photopic reflectance, transmittance, and absorptance of materials using a large diameter integrating sphere. Standard E1175-87 (2015). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2016. Standard practice for determining load resistance of glass in buildings. Standard E1300-16. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2010. Standard specification for insulated glass unit performance and evaluation. Standard E2190-10. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2012. Standard tables for reference solar spectral irradiances: Direct normal and hemispherical on 37° tilted surface. Standard G173-03 (2012). American Society for Testing and Materials, West Conshohocken, PA.
Barnaby, C.S., J.L. Wright, and M.R. Collins. 2009. Improving load calculations for fenestration with shading devices. ASHRAE Transactions 115(2):130-144.
Beck, F.A., B.T. Griffith, D. Turler, and D. Arasteh. 1995. Using infrared thermography for the creation of a window surface temperature database to validate computer heat transfer models. Proceedings of Windows Innovations Conference ’95, Toronto, ON.
Berdahl, P., and M. Martin. 1984. Emissivity of clear skies. Solar Energy 32(5).
Bessoudo, M., A. Tzempelikos, A.K. Athienitis, and R. Zmeureanu. 2010. Indoor thermal environmental conditions near glazed facades with shading devices—Part I: Experiments and building thermal model. Building and Environment 45:2506-2516.
Brandle, K., and R.F. Boehm. 1982. Airflow windows: Performance and applications. Proceedings of Thermal Performance of the Exterior Envelopes of Buildings II, ASHRAE/DOE Conference, ASHRAE Special Project SP-38.
CANMET. 1991. A study of the long term performance of operating and fixed windows subjected to pressure cycling. Catalogue M91-7/214-1993E. Efficiency and Alternative Energy Technology Branch, CANMET, Ottawa, ON.
CANMET. 1993. Long term performance of operating windows subjected to motion cycling. Catalogue M91-7/235-1993E. Efficiency and Alternative Energy Technology Branch, CANMET, Ottawa, ON.
Carbary, L., V. Hayez, A. Wolf, and M. Bhandari. 2009. Comparisons of thermal performance and energy consumptions of facades used in commercial buildings. Proceedings of Glass Performance Days 2009, pp. 89-94.
Carmody, J., S. Selkowitz, E.S. Lee, and D. Arasteh. 2004. Window systems for high-performance buildings. W.W. Norton & Company.
Carpenter, S., and A. Elmahdy. 1994. Thermal performance of complex fenestration systems. ASHRAE Transactions 100(2):1179-1186.
Carpenter, S., and J. Hogan. 1996. Recommended U-factors for swinging, overhead and revolving doors. ASHRAE Transactions 102(1):955-959.
Carpenter, S., and A. McGowan. 1993. Effect of framing systems on the thermal performance of windows. ASHRAE Transactions 99(1):907-914.
Carter, D.J. 2008. Tubular guidance systems for daylight: UK case studies. Building Research & Information 36(5):520-535.
Carter, D.J,. and M. Al-Marwaee. 2009. User attitudes toward tubular daylight guidance systems. Lighting Research and Technology 41:71-88.
CEC. 2010. 2008 Building energy efficiency standards for residential and nonresidential buildings. California Code of Regulations, Title 24, Part 6. California Energy Commission.
Choi, A.S., and R.G. Mistrick. 1999. Analysis of daylight responsive dimming system performance. Building and Environment 34:231-243.
CIE. 2006. Tubular daylight guidance systems, CIE Technical Report 173:2006. Technical Committee TC3-38, International Commission on Illumination, Austria.
Code of Federal Regulations. Annual. Safety standard for architectural glazing materials. 16CFR1201. U.S. Government Printing Office, Washington, D.C.
Collins, M.R., and J.L. Wright. 2006. Calculating center-glass performance indices of windows with a diathermanous layer. ASHRAE Transactions 112(2):22-29.
Collins, M.R., S.H. Tasnim, and J.L. Wright. 2008. Determination of convective heat transfer for glazing systems with between-the-glass louvered shades. International Journal of Heat and Mass Transfer 51:2742-2751.
Collins, M.R., J.L. Wright, and N.A. Kotey. 2011. Measuring off-normal solar optical properties of flat shading materials. Journal of Measurement (45):79-93.
Crooks, B.P., J. Larsen, R. Sullivan, D. Arasteh, and S. Selkowitz. 1995. NFRC efforts to develop a residential fenestration annual energy rating methodology. Proceedings of Windows Innovations Conference ’95, Toronto, ON. Lawrence Berkeley Laboratory Publication 36896.
CSA. 2000. Windows. CAN/CSA Standard A440-00. Canadian Standards Association, Etobicoke, ON.
CSA. 2005. Windows/User selection guide to CSA Standard CAN/CSA-A440-00. CAN/CSA Special Publication A440.1-00 (R2005). Canadian Standards Association, Etobicoke, ON.
CSA. 2014. Fenestration energy performance. CAN/CSA Standard A440.2. Canadian Standards Association, Etobicoke, ON.
CSA. 2000. Energy performance evaluation of swinging doors. CAN/CSA Standard A453-95 (R2000). Canadian Standards Association, Etobicoke, ON.
Curcija, D.C. 2005. Discrepancies between ISO window simulation standards. Technical report to ISO TC 163, Subcommittee 2, Working Group 9. November 23, 2005.
Curcija, D., and W.P. Goss. 1994. Two-dimensional finite-element model of heat transfer in complete fenestration systems. ASHRAE Transactions 100(2):1207-1221.
Curcija, D., and W.P. Goss. 1995. Three-dimensional finite element model of heat transfer in complete fenestration systems. Proceedings of Windows Innovations Conference ’95, Toronto, ON.
Curcija, D., W.P. Goss, J.P. Power, and Y. Zhao. 1996. “Variable-h” model for improved prediction of surface temperatures in fenestration systems. Technical Report, University of Massachusetts at Amherst.
de Abreu, P., R.A. Fraser, H.F. Sullivan, and J.L. Wright. 1996. A study of insulated glazing unit surface temperature profiles using two-dimensional computer simulation. ASHRAE Transactions 102(2):497-507.
EEL. 1990. FRAME/VISION window performance modelling and sensitivity analysis. Institute for Research in Construction, National Research Council of Canada, Ottawa.
Elmahdy, A.H. 1995. Air leakage characteristics of windows subjected to simultaneous temperature and pressure differentials. Proceedings of Windows Innovations Conference ’95, CANMET.
Elmahdy, H. 1996. Surface temperature measurement of insulating glass units using infrared thermography. ASHRAE Transactions 102(2):489-496.
Elmahdy, A.H. 2001. To seal or not to seal? A critical look at the effects of air leakage on the condensation resistance of windows. The Whole-Life Performance of Façades, Bath, U.K.
Elmahdy, A.H. 2003. Quantification of air leakage effects on the condensation resistance of windows. ASHRAE Transactions 109(1):600-606.
Elmahdy, A.H., and S.A. Yusuf. 1995. Determination of argon concentration and assessment of the durability of high-performance insulating glass units filled with argon gas. ASHRAE Transactions 101(2):1026-1037.
El Sherbiny, S.M., K.G.T. Hollands, and G.D. Raithby. 1982. Heat transfer by natural convection across vertical and inclined air layers. Journal of Heat Transfer 104:96-102.
Erhorn, H., and M. Dirksmöller, eds. 2000. Documentation of the software package ADELINE 3. Fraunhofer Institut für Bauphysik, Stuttgart.
Ewing, W.B., and J.I. Yellott. 1976. Energy conservation through the use of exterior shading of fenestration. ASHRAE Transactions 82(1):703-733.
Finlayson, E.U., and D. Arasteh. 1993. WINDOW 4.0: Documentation of calculation procedures. Publication LBL-33943/UC-350, Lawrence Berkeley Laboratory, Energy & Environment Division, Berkeley, CA.
Griffith, B.T., D. Turler, and D. Arasteh. 1996. Surface temperatures of insulated glazing units: Infrared thermography laboratory measurements. ASHRAE Transactions 102(2):479-488.
Griffith, B., E. Finlayson, M. Yazdanian, and D. Arasteh. 1998. The significance of bolts in the thermal performance of curtain-wall frames for glazed facades. ASHRAE Transactions 105(1):1063-1069.
Gueymard, C.A. 2007. Advanced solar irradiance model and procedure for spectral solar heat gain calculation. ASHRAE Transactions 113(1):149-164.
Gueymard, C.A., and W.C. DuPont. 2009. Spectral effects on the transmittance, solar heat gain, and performance rating of glazing systems. Solar Energy 83:940-953.
Gueymard, C.A., and H.D. Kambezidis. 2004. Solar spectral radiation. Ch. 5 in Solar radiation and daylight models, T. Muneer, ed., pp. 221-301. Elsevier Butterworth-Heinemann, Oxford.
Haddad, K.H., and A.H. Elmahdy. 1998. Comparison of the thermal performance of a conventional window and a supply-air window. ASHRAE Transactions 104(1A):1261-1270.
Haddad, K.H., and A.H. Elmahdy. 1999. Comparison of the thermal performance of an exhaust-air window and a supply-air window. ASHRAE Transactions 105(2):918-926.
Hawthorne, W.A., and S. Reilly. 2000. The impact of glazing selection on residential duct design and comfort. ASHRAE Transactions 106(1):553-561.
Heschong, L., D. Mahone, F. Rubinstein, and J. McHugh. 1998. Skylighting guidelines. The Heschong Mahone Group, Sacramento, CA.
Hitchcock, R.J., R. Mitchell, M. Yazdanian, E. Lee, and C. Huigenza. 2008. COMFEN—A commercial fenestration/façade design tool. Proceedings of SimBuild 2008, pp. 246-252.
Hogan, J.F. 1988. A summary of tested glazing U-values and the case for an industry wide testing program. ASHRAE Transactions 94(2).
Hollands, K.G.T. and J.L. Wright. 1982. Heat loss coefficients and effective τα products for flat plate collectors with diathermous covers. Solar Energy 30:211-216.
Huang, J., R. Mitchell, D. Arasteh, and S. Selkowitz. 1999. Residential fenestration performance analysis using RESFEN 3.1. Thermal Performance of the Exterior Envelopes of Buildings VII, ASHRAE.
Huang, N.Y.T., J.L. Wright, and M.R. Collins. 2006. Thermal resistance of a window with an enclosed venetian blind: Guarded heater plate measurements. ASHRAE Transactions 112(2):13-21.
Hutchins, M.G., A.J. Topping, C. Anderson, F. Olive, P.A. van Nijnatten, P. Polato, A. Roos, and M. Rubin. 2001. Angle-dependent optical properties of coated glass products: results of an inter-laboratory comparison of spectral transmittance and reflectance. Thin Solid Films 392(2):269.
ICC. 2015. International building code® (IBC ®). International Code Council, Washington, D.C.
ICC. 2015. International energy conservation code® (IECC ®). International Code Council, Washington, D.C.
ICC. 2015. International green construction code™ (IgCC ™). International Code Council, Washington, D.C.
IEA. 1999. Daylighting simulation: Methods, algorithms, and resources. IEA SHC Task 21/ECBCS Annex 29. LBNL-44296, Lawrence Berkeley National Laboratory. www.iea-shc.org.
IES. 1999. IES recommended practice of daylighting. IES RP-5-99. Illuminating Engineering Society, New York.
ISO. 2015. Solar energy—Reference solar spectral irradiance at the ground at different receiving conditions—Part 1: Direct normal and hemispherical solar irradiance for air mass 1,5. Standard 9845-1992 (2005). International Organization for Standardization, Geneva.
ISO. 2006. Thermal performance of windows, doors and shutters—Calculation of thermal transmittance—Part 1: General. Standard 10077-1. International Organization for Standardization, Geneva.
ISO. 2012. Thermal performance of windows, doors and shutters—Calculation of thermal transmittance—Part 2: Numerical method for frames. Standard 10077-2. International Organization for Standardization, Geneva.
ISO. 2003. Thermal performance of windows, doors and shading devices—Detailed calculations. Standard 15099. International Organization for Standardization, Geneva.
Jennings, J.D., F.M. Rubinstein, D. DiBartolomeo, and S. Blanc. 1999. Comparison of control options in private offices in an advanced lighting controls testbed. LBNL-43096, Lawrence Berkeley National Laboratory, Berkeley, CA.
Karlsson, J., M. Rubin, and A. Roos. 2001. Evaluation of some models for the angle-dependent total solar energy transmittance of glazing materials. Solar Energy 71(1).
Keyes, M.W. 1967. Analysis and rating of drapery materials used for indoor shading. ASHRAE Transactions 73(1):8.4.1.
Klems, J.H. 1989. U-values, solar heat gain, and thermal performance: Recent studies using the MoWiTT. ASHRAE Transactions 95(1):609-617.
Klems, J.H. 1994a. A new method for predicting the solar heat gain of complex fenestration systems: I. Overview and derivation of the matrix layer calculation. ASHRAE Transactions 100(1):1065-1072.
Klems, J.H. 1994b. A new method for predicting the solar heat gain of complex fenestration systems: II. Detailed description of the matrix layer calculation. ASHRAE Transactions 100(1):1073-1086.
Klems, J.H. 2001. Solar heat gain through fenestration systems containing shading: Procedures for estimating performance from minimal data. LBNL-46682. Windows and Daylighting Group, Lawrence Berkeley National Laboratory, Berkeley, CA.
Kotey, N.A., J.L. Wright, and M.R. Collins. 2008. Proceedings of the 3rd Annual Canadian Solar Buildings Conference, Fredericton, NB. Solar Energy Society of Canada.
Kotey, N.A., M.R. Collins, J.L. Wright, and T. Jiang. 2009a. A simplified method for calculating the effective solar optical properties of a venetian blind layer for building energy simulation. ASME Journal of Solar Energy Engineering 131(2).
Kotey, N.A., J.L. Wright, and M.R. Collins. 2009b. Determination of angle-dependent solar optical properties of drapery fabrics. ASHRAE Transactions 115(2).
Kotey, N.A., J.L. Wright, and M.R. Collins. 2009c. A detailed model to determine the effective solar optical properties of draperies. ASHRAE Transactions 115(1).
Kotey, N.A., J.L. Wright, and M.R. Collins. 2009d. Determination of angle-dependent solar optical properties of roller blind materials. ASHRAE Transactions 115(1).
Kotey, N.A., J.L. Wright, and M.R. Collins. 2009e. Determination of angle-dependent solar optical properties of insect screens. ASHRAE Transactions 115(1).
Kotey, N.A., J.L. Wright, and M.R. Collins. 2011. A method for determining the effective longwave radiative properties of pleated draperies. HVAC&R Research (now Science and Technology for the Built Environment) 17(5):660-669.
Kruis, N. 2016. Representative layer-by-layer descriptions for fenestration systems with specified bulk properties such as U-factor and SHGC. ASHRAE Research Project RP-1588, Report.
Laouadi, A. 2004. Design with SkyVision: A computer tool to predict daylighting performance of skylights. CIB World Building Conference, Toronto, pp. 1-11.
Laouadi, A. 2013. Advanced performance prediction of tubular daylighting devices: New research from the National Research Council of Canada takes an in-depth look inside TDDs. Lighting Design and Application (September):52.
Laouadi, A., A.D. Galasiu, M.R. Atif, and A. Haqqani. 2003. SkyVision: A software tool to calculate the optical characteristics and daylighting performance of skylights. Building Simulation, 8th IBPSA Conference, Eindhoven, Netherlands, pp. 705-712.
Laouadi, A., H.H. Saber, A.D. Galasiu, and C. Arsenault. 2013a. Optical model for tubular hollow light guides (1415-RP). HVAC&R Research (now Science and Technology for the Built Environment) 19(3):324-334.
Laouadi, A., A.D. Galasiu, H.H. Saber, and C. Arsenault. 2013b. Tubular daylighting devices- part I: development of an optical model (1415-RP). HVAC&R Research (now Science and Technology for the Built Environment) 19(5):536-556.
Laouadi, A., C. Arsenault, H.H. Saber, and A.D. Galasiu. 2013c. Tubular daylighting devices- part II: validation of the optical model (1415-RP). HVAC&R Research (now Science and Technology for the Built Environment) 19(5):557-572.
Laouadi, A., H.H. Saber, A.D. Galasiu, and C. Arsenault. 2013d. Tubular daylighting devices—Development and validation of a thermal model (1415-RP). HVAC&R Research (now Science and Technology for the Built Environment) 19(5):513-535.
Lee, E., and S.E. Selkowitz. 1995. The design and evaluation of integrated envelope and lighting control strategies for commercial buildings. ASHRAE Transactions 101(1):326-342.
Lyons, P.R., D.A. Arasteh, and C. Huizenga. 2000. Window performance for human thermal comfort. ASHRAE Transactions 106(1):594-602.
Lyons, P., J. Wong, and M. Bhandari. 2010. A comparison of window modeling methods in Energyplus 4.0. SimBuild 2010, New York.
Mathis, R.C., and R. Garries. 1995. Instant, annual life: A discussion on the current practice and evolution of fenestration energy performance rating. Proceedings of Windows Innovations Conference ’95, Toronto, ON.
McCluney, R. 1990. Awning shading algorithm update. ASHRAE Transactions 96(1):34-38.
McCluney, R. 1993. Sensitivity of optical properties and solar gain of spectrally selective glazing systems to changes in solar spectrum. Solar ’93, 22nd American Solar Energy Society Conference, Washington, D.C.
McCluney, R. 1994a. Angle of incidence and diffuse radiation influences on glazing system solar gain. Proceedings Solar ’94 Conference, American Solar Energy Society, San Jose, CA.
McCluney, R. 1994b. Introduction to radiometry and photometry. Artech House, Boston.
McCluney, R. 1996. Sensitivity of fenestration solar gain to source spectrum and angle of incidence. ASHRAE Transactions 102(2):112-122.
McCluney, R., and P. Jindra. 2001. Industry guide to selecting the best residential window options for the Florida climate. FSEC-PF-358-01. Florida Solar Energy Center, University of Central Florida, Cocoa.
McGowan, A, R. Jutras, G. Riopel, and M. Hanam. 2006. Heat transfer through roll-up doors, revolving doors and opaque non-residential swinging, sliding and rolling doors. ASHRAE Research Project RP-1236, Final Report.
Mitchell, R., J. Huang, D. Arasteh, R. Sullivan, and S. Phillip. 1999. RESFEN 3.1: A PC program for calculating the heating and cooling energy use of windows in residential buildings—Program description. LBNL-40682 Rev. BS-371. Lawrence Berkeley National Laboratory, Berkeley, CA.
Mitchell, R., M. Yazdanian, L. Zhu, D. Arasteh, and J. Huang. 2012. RESFEN6: Program description. LBNL-40682 Rev. Lawrence Berkeley National Laboratory, Berkeley, CA.
Moeseke, G., I. Bruyere, and A.D. Herde. 2007. Impact of control rules on the efficiency of shading devices and free cooling for office buildings. Building and Environment 42:784-793.
Newsham, G.R. 1994. Manual control of window blinds and electric lighting: implications for comfort and energy consumption. Indoor Environment 3, pp. 135-144.
NFRC. 2014a. Procedure for determining fenestration product U-factors. Technical Document 100-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014b. Spectral data library. Available from www.nfrc.org/software.aspx. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014c. Standard test method for determining the solar optical properties of glazing materials and systems. Technical Document 300-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014d. Procedure for determining fenestration product solar heat gain coefficient and visible transmittance at normal incidence. Technical Document 200-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014e. Procedure for interim standard test method for measuring he solar heat gain coefficient of fenestration systems using calorimetry hot box methods. Technical Document 201-2014. National Fenestration Rating Council, Silver Spring, MD.
NRFC. 2014f. Procedure for determining visible transmittance of tubular daylighting devices. Technical Document 203-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014g. Standard test method for emittance of specular surfaces using spectromteric measurements. Technical Document 301-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014h. Procedure for determining fenestration product air leakage. Technical Document 400-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014i. Guidelines to estimate the effects of fenestration on heating and cooling energy consumption in single family residences. Technical Document 901-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014j. Procedure for determining fenestration product condensation resistance values. Technical Document 500-2014. National Fenestration Rating Council, Silver Spring, MD.
NFRC. 2014k. User guide to the procedure for determining fenestration product condensation resistance rating values. Technical Document 501-2014. National Fenestration Rating Council, Silver Spring, MD.
NRCC. 2011. Tubular daylighting devices: An alternative to skylights. Construction Innovation 16(1). National Research Council Canada, Ottawa.
Ochoa, C.E., and I.G. Capeluto. 2009. Advice tool for early design stages of intelligent facades based on energy and visual comfort approach. Energy and Buildings 41(5):480-488.
Parmelee, G.V., and R.G. Huebscher. 1947. Forced convection heat transfer from flat surfaces. ASHVE Transactions, pp. 245-284.
Patenaude, A. 1995. Air infiltration rate of windows under temperature and pressure differentials. Proceedings of Windows Innovations Conference ’95, Toronto, ON.
Pennington, C.W., and G.L. Moore. 1967. Measurement and application of solar properties of drapery shading materials. ASHRAE Transactions 73(1):8.3.1.
Rao, S.R., and A. Tzempelikos. 2012. The impact of a combined dynamic shading system on the thermal performance of building perimeter zones. ASHRAE Transactions 118(1):265-273.
Reinhart, C.F. 2004. Lightswitch-2002: A model for manual and automated control of electric lighting and blinds. Solar Energy 77(2004):15-28.
Robbins, C.L. 1986. Daylighting: Design and analysis. Van Nostrand Reinhold, New York.
Rubin, M. 1982a. Solar optical properties of windows. Energy Research 6: 122-133.
Rubin, M. 1982b. Calculating heat transfer through windows. Energy Research 6:341-349.
Rubin, M. 1985. Optical constants and bulk optical properties of soda lime silica glasses for windows. Solar Energy Materials 12:275-288.
Rubin, M., K. von Rottkay, and R. Powles. 1998. Window optics. Solar Energy 62(3):149-161.
Rubin, M., R. Powles, and K. von Rottkay. 1999. Models for the angle-dependent optical properties of coated glazing materials. Solar Energy 66(4):267-276.
Schutrum, L.F., and N. Ozisik. 1961. Solar heat gains through domed skylights. ASHRAE Journal, pp. 51-60.
Sezgen, O., and J.G. Koomey. 1998. Interactions between lighting and space conditioning energy use in U.S. commercial buildings. LBNL-39795, Lawrence Berkeley National Laboratory, Berkeley, CA. eetd.lbl.gov/sites/all/files/lbnl-39795.pdf.
Shen, H., and A. Tzempelikos. 2012. Daylighting and energy analysis of private offices with automated interior roller shades. Solar Energy 86, pp. 681-704.
Shewen, E.C. 1986. A Peltier-effect technique for natural convection heat flux measurement applied to the rectangular open cavity. Ph.D. dissertation. Department of Mechanical Engineering, University of Waterloo, ON.
Smith, W.A., and C.W. Pennington. 1964. Shading coefficients for glass block panels. ASHRAE Journal 5(12):31.
Sodergren, D., and T. Bostrom. 1971. Ventilating with the exhaust air window. ASHRAE Journal 13(4):51.
Sterling, E.M., A. Arundel, and T.D. Sterling. 1985. Criteria for human exposure in occupied buildings. ASHRAE Transactions 91(1).
Sullivan, H.F., J.L. Wright, and R.A. Fraser. 1996. Overview of a project to determine the surface temperatures of insulated glazing units: Thermographic measurement and two-dimensional simulation. ASHRAE Transactions 102(2):516-522.
Tzempelikos, A., and A.K. Athienitis. 2005. Integrated daylighting and thermal analysis of office buildings. ASHRAE Transactions 111(1):227-238.
Tzempelikos, A., and A.K. Athienitis. 2007. The impact of shading design and control on building cooling and lighting demand. Solar Energy 81(3), 369-382.
van Dijk, D. 2003. Comparison of standards on thermal, solar and/or light properties of windows and window components. TNO Building and Construction Research, Delft, Netherlands. April 8.
Ward, G.W. 1990. Visualization. Lighting Design + Application 20(6):4-20.
Winkelmann, F.C. 1983. Daylighting calculation in DOE-2. LBNL-11353. Lawrence Berkeley National Laboratory, Berkeley, CA.
Wong, J.C.S. 2016. Personal communication.
Wright, J.L. 1995a. VISION4 glazing system thermal analysis: Reference manual. Advanced Glazing System Laboratory, University of Waterloo.
Wright, J.L. 1995b. Summary and comparison of methods to calculate solar heat gain. ASHRAE Transactions 101(1):802-818.
Wright, J.L. 1996a. A correlation to quantify convective heat transfer between window glazings. ASHRAE Transactions 102(1):940-946.
Wright, J.L. 1996b. A simplified numerical method for assessing the condensation resistance of windows. ASHRAE Transactions 104(1):1222-1229.
Wright, J.L. 2008. Calculating centre-glass performance indices of glazing systems with shading devices. ASHRAE Transactions 114(2):199-209.
Wright, J.L., and H.F. Sullivan. 1995a. A two-dimensional numerical model for glazing system thermal analysis. ASHRAE Transactions 101(1):819-831.
Wright, J.L., and H.F. Sullivan. 1995b. A two-dimensional numerical model for natural convection in a vertical, rectangular window cavity. ASHRAE Transactions 100(2):1193-1206.
Wright, J.L., and H.F. Sullivan. 1995c. A simplified method for the numerical condensation resistance analysis of windows. Proceedings of Windows Innovations Conference ’95, Toronto, ON.
Wright, J.L., N.Y.T. Huang, and M.R. Collins. 2008. Thermal resistance of a window with an enclosed venetian blind: A simplified model. ASHRAE Transactions 114(1):471-482.
Wright, J.L., M.R. Collins, and N. Kotey. 2009a. Solar gain through windows with shading devices: Simulations versus measurements. ASHRAE Transactions 115(2):18-30.
Wright, J.L., C. Barnaby, M.R. Collins, and N. Kotey. 2009b. Improving load calculations for fenestrations with shading devices. ASHRAE Research Project RP-1311, Final Report.
Yazdanian, M., and J.H. Klems. 1993. Measurement of the exterior convective film coefficient for windows in low-rise buildings. ASHRAE Transactions 100(1):1087-1096.
Yellott, J.I. 1963. Selective reflectance—A new approach to solar heat control. ASHRAE Transactions 69:418.
Zhang, X., and T. Muneer. 2000. Mathematical model for the performance of lightpipes. Lighting Research and Technology 32(3):141-146.
Zhao, Y., D. Curcija, and W.P. Goss. 1996. Condensation resistance validation project—Detailed computer simulations using finite element methods. ASHRAE Transactions 102(2):508-515.