Mass Transfer Coefficient
Convective mass transfer is analogous to convective heat transfer where geometry and boundary conditions are similar. The analogy holds for both laminar and turbulent flows and applies to both external and internal flow problems.
Mass Transfer Coefficients for External Flows. Most external convective mass transfer problems can be solved with an appropriate formulation that relates the mass transfer flux (to or from an interfacial surface) to the concentration difference across the boundary layer illustrated in Figure 5. This formulation gives rise to the convective mass transfer coefficient, defined as
where
| hM = local external mass transfer coefficient, m/s |
= mass flux of gas B from surface, kg/(m2 · s) |
| ρBi = density of gas B at interface (saturation density), kg/m3 |
| ρB∞ = density of component B outside boundary layer, kg/m3 |
If ρBi and ρB∞ are constant over the entire interfacial surface, the mass transfer rate from the surface can be expressed as
where
is the average mass transfer coefficient, defined as
Mass Transfer Coefficients for Internal Flows. Most internal convective mass transfer problems, such as those that occur in channels or in the cores of dehumidification coils, can be solved if an appropriate expression is available to relate the mass transfer flux (to or from the interfacial surface) to the difference between the concentration at the surface and the bulk concentration in the channel, as shown in Figure 6. This formulation leads to the definition of the mass transfer coefficient for internal flows:
where
| hM = internal mass transfer coefficient, m/s |
= mass flux of gas B at interfacial surface, kg/(m2 · s) |
| ρBi = density of gas B at interfacial surface, kg/m3 |
ρBb ≡ = bulk density of gas B at location x |
= average velocity of gas B at location x, m/s |
| Acs = cross-sectional area of channel at station x, m2 |
| uB = velocity of component B in x direction, m/s |
| ρB = density distribution of component B at station x, kg/m3 |
Often, it is easier to obtain the bulk density of gas B from
where
= mass flow rate of component B at station x = 0, kg/s |
| A = interfacial area of channel between station x = 0 and station x = x, m2 |
Equation (28) can be derived from the preceding definitions. The major problem is determining
. If, however, analysis is restricted to cases where B is dilute and concentration gradients of B in the x direction are negligibly small,
. Component B is swept along in the x direction with an average velocity equal to the average velocity of the dilute mixture.
Simplified Equations for Evaporation of Water into Air
Shah (1992, 2014, 2018, 2022, 2023) has suggested equations for evaporation from horizontal water surfaces during natural and forced convection. The equation for natural convection was first given in Shah (1992); the equation for forced convection was first given in Shah (2018) and improved on in later papers. The physical model on which these are based is as follows (Shah 2022): a thin layer of air at the water surface gets quickly saturated due to molecular movement at the air/water interface. If this layer is not removed, it will keep getting thicker and further evaporation will be only by molecular diffusion, which is a very slow process. Rapid evaporation is possible only if the thin layer of saturated air at the air/water interface continues being removed and replaced by drier air. This air movement can occur by the following mechanisms.
-
Air currents caused by natural convection (buoyancy effect). Air close to the water’s surface picks up moisture and its relative humidity rises, thus becoming lighter than the surrounding air. This lighter air moves up while the heavier surrounding air moves down, causing air circulation, which continuously removes the saturated film at the air/water interface.
-
Air movement due to currents caused by building ventilation system or infiltration/exfiltration in indoor pools, forced airflow over pool surface in some indoor pools, and wind in outdoor pools. Air movement by any of these causes is considered forced convection.
The equation for natural convection is
The equation for forced convection is
where
| E = evaporation rate, kg/(m2·s) |
| p = vapor pressure of moisture in air, Pa |
| C = 0.0097 |
| B = 1.39 × 10–8 |
| u∞ = air velocity above pool, m/s |
| utr = air velocity at transition point, 0.12 m/s |
| W = humidity ratio |
For u∞ < utr, use u∞ = utr.
Evaporation rate E is the larger of those given by Equations (35) and (36). This method was verified with data from 29 sources. The range of these data is listed in Table 3.
Equation (35) was derived from the analogy between heat and mass transfer by Shah (1992) as follows. Evaporation is given by
where subscript ∞ indicates air distant from water surface, and s indicates air saturated at water temperature.
Considering the water surface as a heated plate facing upwards, analogy between heat and mass transfer gives
where GrM is the Grashof number for mass transfer given by
Combining Equations (38) to (40) and expanding Sc and Sh, the following equation is obtained:
where L is the length of the pool. Substituting hM from Equation (41) into Equation (37),
The value of Dv2/3μ–1/3 does not vary much over the typical range of room air conditions. Inserting a mean value in Equation (42), Equation (35) is obtained.
Shah (2013) gives a model for calculating evaporation from occupied swimming pools. It is a modification of Equation (35) to take into account the effect of pool occupants.
Table 4 gives the deviations of this model with test data in natural and forced convection. Excellent agreement with data is seen in both regimes. It is interesting to see that Equation (35), which is the simplified version of Equation (42), has lower deviations than Equation (42), which was derived directly form the analogy between heat and mass transfer. Figure 9 compares the predictions of Equation (35) with some of the data for evaporation under natural convection. Figure 10 compares Equation (36)’s predictions with some of the data for evaporation under forced convection. Close agreement is seen in both cases.
The kind of similarity between heat and mass transfer that results in Equations (31) to (34) can also be shown to exist between heat and momentum transfer. Chilton and Colburn (1934) used this similarity to relate Nusselt number to friction factor by the analogy
where n = 2/3, St = Nu/(Re Pr) is the Stanton number, and jH is the Chilton-Colburn j-factor for heat transfer. Substituting Sh for Nu and Sc for Pr in Equations (33) and (34) gives the Chilton-Colburn j-factor for mass transfer, jD:
where Stm = ShPAm/(Re Sc) is the Stanton number for mass transfer. Equations (43) and (44) are called the Chilton-Colburn j-factor analogy.
The power of the Chilton-Colburn j-factor analogy is represented in Figures 10 to 13. Figure 10 plots various experimental values of jD from a flat plate with flow parallel to the plate surface. The solid line, which represents the data to near perfection, is actually f/2 from Blasius’ solution of laminar flow on a flat plate (left-hand portion of the solid line) and Goldstein’s solution for a turbulent boundary layer (right-hand portion). The right-hand part also represents McAdams’ (1954) correlation of turbulent flow heat transfer coefficient for a flat plate.
A wetted-wall column is a vertical tube in which a thin liquid film adheres to the tube surface and exchanges mass by evaporation or absorption with a gas flowing through the tube. Figure 11 illustrates typical data on vaporization in wetted-wall columns, plotted as jD versus Re. The point spread with variation in μ/ρDv results from Gilliland’s finding of an exponent of 0.56, not 2/3, representing the effect of the Schmidt number. Gilliland’s equation can be written as follows:
Similarly, McAdams’ (1954) equation for heat transfer in pipes can be expressed as
This is represented by the dash-dot curve in Figure 11, which falls below the mass transfer data. The curve f/2, representing friction in smooth tubes, is the upper, solid curve.
Data for liquid evaporation from single cylinders into gas streams flowing transversely to the cylinders’ axes are shown in Figure 12. Although the dash-dot line in Figure 12 represents the data, it is actually taken from McAdams (1954) as representative of a large collection of data on heat transfer to single cylinders placed transverse to airstreams. To compare these data with friction, it is necessary to distinguish between total drag and skin friction. Because the analogies are based on skin friction, normal pressure drag must be subtracted from the measured total drag. At Re = 1000, skin friction is 12.6% of the total drag; at Re = 31 600, it is only 1.9%. Consequently, values of f/2 at a high Reynolds number, obtained by the difference, are subject to considerable error.
In Figure 13, data on evaporation of water into air for single spheres are presented. The solid line, which best represents these data, agrees with the dashed line representing McAdams’ correlation for heat transfer to spheres. These results cannot be compared with friction or momentum transfer because total drag has not been allocated to skin friction and normal pressure drag. Application of these data to air/water-contacting devices such as air washers and spray cooling towers is well substantiated.
When the temperature of the heat exchanger surface in contact with moist air is below the air’s dew-point temperature, vapor condensation occurs. Typically, air dry-bulb temperature and humidity ratio both decrease as air flows through the exchanger. Therefore, sensible and latent heat transfer occur simultaneously. This process is similar to one that occurs in a spray dehumidifier and can be analyzed using the same procedure; however, this is not generally done.
Cooling coil analysis and design are complicated by the problem of determining transport coefficients h, hM, and f. It would be convenient if heat transfer and friction data for dry heating coils could be used with the Colburn analogy to obtain the mass transfer coefficients, but this approach is not always reliable, and Guillory and McQuiston (1973) and Helmer (1974) show that the analogy is not consistently true. Figure 14 shows j-factors for a simple parallel-plate exchanger for different surface conditions with sensible heat transfer. Mass transfer j-factors and friction factors exhibit the same behavior. Dry-surface j-factors fall below those obtained under dehumidifying conditions with the surface wet. At low Reynolds numbers, the boundary layer grows quickly; the droplets are soon covered and have little effect on the flow field. As the Reynolds number increases, the boundary layer becomes thin and more of the total flow field is exposed to the droplets. Roughness caused by the droplets induces mixing and larger j-factors.
The data in Figure 14 cannot be applied to all surfaces, because the length of the flow channel is also an important variable. However, water collecting on the surface is mainly responsible for breakdown of the j-factor analogy. The j-factor analogy is approximately true when surface conditions are identical. Under some conditions, it is possible to obtain a film of condensate on the surface instead of droplets. Guillory and McQuiston (1973) and Helmer (1974) related dry sensible j- and f-factors to those for wetted dehumidifying surfaces.
The equality of jH, jD, and f/2 for certain streamlined shapes at low mass transfer rates has experimental verification. For flow past bluff objects, jH and jD are much smaller than f/2, based on total pressure drag. The heat and mass transfer, however, still relate in a useful way by equating jH and jD.
Example 6.
Using solid cylinders of volatile solids (e.g., naphthalene, camphor, dichlorobenzene) with airflow normal to these cylinders, Bedingfield and Drew (1950) found that the ratio between the heat and mass transfer coefficients could be closely correlated by the following relation:
For completely dry air at 21°C flowing at a velocity of 9.5 m/s over a wet-bulb thermometer of diameter d = 7.5 mm, determine the heat and mass transfer coefficients from Figure 12 and compare their ratio with the Bedingfield-Drew relation.
Solution: For dry air at 21°C and standard pressure, ρ = 1.198 kg/m3, μ = 1.82 × 10–5 kg/(s · m), k = 0.02581 W/(m · K), and cp = 1.006 kJ/(kg · K). From Equation (10), Dv = 25.13 mm2/s. Therefore,
From Figure 12 at Reda = 4700, read jH = 0.0089, and jD = 0.010. From Equations (43) and (44),
From the Bedingfield-Drew relation,
Equations (44) and (45) are called the Reynolds analogy when Pr = Sc = 1. This suggests that h/ρhM = cp = 1006 J/(kg · K). This close agreement is because the ratio Sc/Pr is 0.605/0.709 or 0.85, so that the exponent of these numbers has little effect on the ratio of the transfer coefficients.
The extensive developments for calculating heat transfer coefficients can be applied to calculate mass transfer coefficients under similar geometrical and flow conditions using the j-factor analogy. For example, Table 8 of Chapter 4 lists equations for calculating heat transfer coefficients for flow inside and normal to pipes. Each equation can be used for mass transfer coefficient calculations by equating jH and jD and imposing the same restriction to each stated in Table 8 of Chapter 4. Similarly, mass transfer experiments often replace corresponding heat transfer experiments with complex geometries where exact boundary conditions are difficult to model (Sparrow and Ohadi 1987a, 1987b).
The j-factor analogy is useful only at low mass transfer rates. As the rate increases, the movement of matter normal to the transfer surface increases the convective velocity. For example, if a gas is blown from many small holes in a flat plate placed parallel to an airstream, the boundary layer thickens, and resistance to both mass and heat transfer increases with increasing blowing rate. Heat transfer data are usually collected at zero or, at least, insignificant mass transfer rates. Therefore, if such data are to be valid for a mass transfer process, the mass transfer rate (i.e., the blowing) must be low.
The j-factor relationship jH = jD can still be valid at high mass transfer rates, but neither jH nor jD can be represented by data at zero mass transfer conditions. Chapter 24 of Bird et al. (1960) and Eckert and Drake (1972) have detailed information on high mass transfer rates.