6. COMMON DATA AND
PROCEDURES
The following guidelines, data requirements, and procedures apply to all load calculation approaches,
whether heating or cooling, hand-tractable or computerized.
Design for Typical Building Use. In general, residential
systems should be designed to meet representative maximum-load conditions, not extreme conditions.
Normal occupancy should be assumed, not the maximum that might occur during an occasional social
function. Intermittently operated ventilation fans should be assumed to be off. These considerations
are especially important for cooling-system sizing.
Building Codes and Standards. This chapter presentation is
necessarily general. Codes and regulations take precedence; consult local authorities to determine
applicable requirements.
Designer Judgment. Designer experience with local
conditions, building practices, and prior projects should be considered when applying the procedures
in this chapter. For equipment-replacement projects, occupant knowledge concerning performance of
the existing system can often provide useful guidance for achieving a successful design.
Verification. Postconstruction commissioning and
verification are important steps in achieving design performance. Designers should encourage
pressurization testing and other procedures that allow identification and repair of construction
shortcomings.
Uncertainty and Safety Allowances. Residential load
calculations are inherently approximate. Many building characteristics are estimated during design
and ultimately determined by construction quality and occupant behavior. These uncertainties apply
to all calculation methods, including first-principles procedures such as RHB. It is therefore
tempting to include safety allowances for each aspect of a calculation. However, this practice has a
compounding effect and often produces oversized results. Typical conditions should be assumed;
safety allowances, if applied at all, should be added to the final calculated loads rather than to
intermediate components. In addition, temperature swing provides a built-in safety factor for
sensible cooling: a 20% capacity shortfall typically results in a temperature excursion of at most
about one or two degrees.
Common air-conditioning processes involve transferring heat via air transport or leakage. The
sensible, latent, and total heat conveyed by air on a volumetric basis is
where
| qs, ql, qt = sensible, latent,
total heat transfer rates, Btu/h |
| Cs = air sensible heat factor,
Btu/h · °F · cfm
(1.1 at sea level)
|
| Cl = air latent heat factor,
Btu/h · cfm (4840 at sea level)
|
| Ct = air total heat factor,
Btu/h · cfm per Btu/lb enthalpy h (4.5 at sea level)
|
| Q = air volumetric flow rate, cfm |
| Δt = air temperature difference across process,
°F
|
| ΔW = air humidity ratio difference across process,
lbw/lbda
|
| Δh = air enthalpy difference across process,
Btu/lb
|
The heat factors Cs, Cl, and Ct are elevation
dependent. The sea level values in the preceding definitions are appropriate for elevations up to
about 1000 ft. Procedures are provided in Chapter
18 for calculating adjusted values for higher elevations.
The initial step in the load calculation is selecting indoor and outdoor design conditions.
Indoor Conditions. Indoor conditions assumed for design
purposes depend on building use, type of occupancy, and/or code requirements. Chapter 9
and ASHRAE Standard 55 define the relationship between indoor conditions
and comfort.
Typical practice for cooling is to design for indoor conditions of 75°F db and a
maximum of 50 to 65% rh. For heating, 68°F db and 30% rh are common design values.
These conditions are the default values used throughout this chapter.
Outdoor Conditions. Outdoor design conditions for load
calculations should be selected from location-specific climate data in Chapter 14, or according to local
code requirements as applicable following the general guidance below. For demanding situations, the
designer should consider the impacts of extreme conditions as discussed in Section 1.3 of Chapter
18.
Cooling. The 1% design dry-bulb temperature and mean coincident wet bulb
temperature from Chapter 14 climate data are
generally appropriate. As previously emphasized, oversized cooling equipment results in poor system
performance. Extremely hot events are necessarily of short duration (conditions always moderate each
night); therefore, sacrificing comfort under typical conditions to meet occasional extremes is not
recommended.
Load calculations also require the hottest-month dry-bulb temperature daily range, and wind speed.
These values can also be found in Chapter 14, although wind speed is
commonly assumed to be 7.5 mph.
Typical buildings in middle latitudes generally experience maximum cooling requirements in midsummer
(July in the northern hemisphere and January in the southern hemisphere). For this reason, the RLF
method is based on midsummer solar gains. However, this pattern does not always hold. Buildings at
low latitudes or with significant south-facing glazing (north-facing in the southern hemisphere)
should be analyzed at several times of the year using the RHB method. Local experience can provide
guidance as to when maximum cooling is probable. For example, it is common for south-facing
buildings in mild northern-hemisphere climates to have peak cooling loads in the fall because of low
sun angles. Chapter 14 provides monthly
temperature data to support calculations for any time of year.
Heating. General practice is to use the 99% design dry-bulb temperature
from Chapter 14. Heating load
calculations ignore solar and internal gains, providing a built-in safety factor. However, the
designer should consider two additional factors:
-
Many locations experience protracted (several-day) cold periods during which the outdoor
temperature remains below the 99% value.
-
Wind is a major determinant of infiltration. Residences with significant leakage (e.g.,
older houses) may have peak heating demand under conditions other than extreme cold,
depending on site wind patterns.
Depending on the application and system type, the designer should consider using the 99.6% value or
the mean minimum extreme as the heating design temperature. Alternatively, the heating load can be
calculated at the 99% condition and a safety factor applied when equipment is selected. This
additional capacity can also serve to meet pickup loads under nonextreme conditions.
Adjacent Buffer Spaces. Residential buildings often
include unconditioned buffer spaces such as garages, attics, crawlspaces, basements, or enclosed
porches. Accurate load calculations require the adjacent air temperature.
In many cases, a simple, conservative estimate is adequate, especially for heating calculations. For
example, it is generally reasonable to assume that, under heating design conditions, adjacent
uninsulated garages, porches, and attics are at outdoor temperature. Another reasonable assumption
is that the temperature in an adjacent, unheated, insulated room is the
mean of the indoor and outdoor temperatures.
In cases where a temperature estimate is required, a steady-state heat balance analysis yields the
following:
where
| tb = buffer space temperature, °F
|
| Q = buffer space infiltration/ventilation flow rate,
cfm
|
| to = outdoor air temperature, °F
|
| Ax = area of xth buffer
space surface, ft2 |
| Ux = U-factor of xth
buffer space surface,
Btu/h · ft2 · °F
|
| tx = air temperature at outside of xth buffer space surface, °F (typically, outdoor
air temperature for exterior surfaces, conditioned space temperature for surfaces between
buffer space and house, or ground temperature for below-grade surfaces) |
| q = additional buffer space heat gains, Btu/h
(e.g., solar gains or distribution system losses) |
Component Areas. To perform load calculations efficiently
and reliably, standard methods must be used for determining building surface areas. For
fenestration, the definition of component area must be consistent with associated ratings.
Gross area. It is both efficient and conservative to derive gross surface
areas from outer building dimensions, ignoring wall and floor thicknesses. Thus, floor areas should
be measured to the outside of adjacent exterior walls or to the centerline of adjacent partitions.
When apportioning to rooms, façade area should be divided at partition centerlines. Wall
height should be taken as floor-to-floor.
Using outer dimensions avoids separate accounting of floor edge and wall corner conditions. Further,
it is standard practice in residential construction to define floor area in terms of outer
dimensions, so outer-dimension takeoffs yield areas that can be readily checked against building
plans (e.g., the sum of room areas should equal the plan floor area). Although outer-dimension
procedures are recommended as expedient for load calculations, they are not consistent with rigorous
definitions used in building-related standards (e.g., ASTM Standard
E631). However, the inconsistencies are not significant in the load calculation context.
Fenestration area. Fenestration includes exterior windows, skylights, and
doors. Fenestration U-factor and SHGC ratings (see Table 2) are based on the
entire product area, including frames. Thus, for load calculations, fenestration area is the area of
the rough opening in the wall or roof, less installation clearances (projected product area Apf). Installation clearances can be neglected; it is
acceptable to use the rough opening as an approximation of Apf.
Net area. Net surface area is the gross surface area less fenestration
area (rough opening or Apf) contained within the surface.
Volume. Building volume is expediently calculated by
multiplying floor area by floor-to-floor height. This produces a conservative estimate of enclosed
air volume, because wall and floor volumes are included in the total. More precise calculations are
possible but are generally not justified in this context.
Construction Characteristics.
U-factors. Except for fenestration, construction U-factors should be
calculated using procedures in Chapter
27, or taken from manufacturer’s data, if available. U-factors should be evaluated
under heating (winter) conditions.
Fenestration. Fenestration is characterized by U-factor and solar heat
gain coefficient (SHGC), which apply to the entire assembly (including frames). If available, rated
values should be used, determined according to procedures set forth by National Fenestration Rating
Council (NFRC), Canadian Standards Association (CSA), or other specifying body (see Chapter 15).
Ratings can be obtained from product literature, product label, or online listings (NFRC 2024). For
unrated products (e.g., in existing construction), the U-factor and SHGC can be estimated using Table 2 or tables in Chapter 15. Note that fenestration U-factors are
evaluated under heating (winter) design conditions but are used in this chapter for both heating and
cooling calculations.
Relatively few types of glazing are encountered in residential applications. Single-glazed clear,
double-glazed clear, and double-glazed low-emissivity (“low-e”) glass predominate.
Single-glazed is now rare in new construction but common in older homes. Triple-glazing, reflective
glass, and heat-absorbing glass are encountered occasionally. Acrylic or glass skylights are common.
Multipane low-e insulated glazing is available in high- and low-solar-gain variants, as discussed in
Chapter 15. Low-solar is now the more common for
new construction in all parts of the United States.
Properties of windows equipped with storm windows should be estimated from data for a similar
configuration with an additional pane. For example, data for clear, double-glazed should be used for
a clear single-glazed window with a storm window.
Fenestration interior and exterior shading must be included in cooling load calculations, as
discussed in the Cooling Load section.
Table 2 shows representative
window U-factor and SHGC values for common glazing and frame combinations. Consult Chapter 15
for skylight characteristics.
Below-Grade Surfaces. For cooling calculations, heat flow
into the ground is usually ignored because it is difficult to quantify. Surfaces adjacent to the
ground are modeled as if well insulated on the outside, so there is no overall heat transfer, but
diurnal heat storage effects are included. Heating calculations must include loss via slabs and
basement walls and floors, as discussed in the Heating Load section.
Infiltration. Infiltration is generally a significant component of both cooling
and heating loads. Refer to Chapter 16 for a detailed
discussion of residential air leakage. The simplified residential models found in that chapter can
be used to calculate infiltration rates for load calculations. Infiltration should be evaluated for
the entire building, not individual rooms or zones.
Natural infiltration leakage rates are modified by mechanical pressurization caused by unbalanced
ventilation or duct leakage. These effects are discussed in the section on Combined Ventilation and
Infiltration Airflow.
Leakage rate. Air leakage rates are specified either as airflow rate
Qi, or air exchanges per hour (ACH), related as follows:
where
| Qi = infiltration airflow rate, cfm |
| ACH = air exchange rate, changes/h |
| V = building volume, ft3 |
Infiltration airflow rate depends on two factors:
-
Building effective leakage area (envelope leaks plus other air leakage paths, notably
flues) and its distribution among ceilings, walls, floors, and flues.
-
Driving pressure caused by buoyancy (stack effect) and wind.
Using the simplifying assumptions presented in Chapter 16, these factors can be
evaluated separately and combined using Equation (8).
where
| AL = building effective leakage area (including flue)
at reference pressure difference = 0.016 in. of water, assuming discharge
coefficient CD = 1, in2 |
| IDF = infiltration driving force, cfm/in2 |
The following sections provide procedures for determining AL
and IDF.
Leakage area. As discussed in Chapter 16, there are several
interconvertible ways to characterize building leakage, depending on reference pressure differences
and assumed discharge coefficient. This formulation uses the effective leakage area at 0.016
in. of water, assuming CD = 1, designated AL (Sherman and Grimsrud 1980).
The only accurate procedure for determining AL is by
measurement using a pressurization test (commonly called a blower door test). Numerous field studies
have shown that visual inspection is not adequate for obtaining even a crude estimate of leakage.
For buildings in design, a pressurization test is not possible and leakage area must be assumed for
design purposes. Leakage can be estimated using tabulated component leakage areas found in Chapter 16. A simpler approach is
based on an assumed average leakage per unit of building surface area:
where
| Aes = building exposed surface area,
ft2
|
| Aul = unit leakage area,
in2/ft2 (from Table
3)
|
Aul is the leakage area per unit surface area; suitable design
values are found in Table 3. Field experience indicates that the
level of care applied to reducing leakage often depends on winter conditions, because cold-air
leakage is readily detected. Thus, lower Aul values are
expected in colder climates. Note that the Aul value doubles
at each reduced construction quality step in Table 3; very high infiltration loads are
typical in older houses.
In Equation (9), Aes is the total building surface area at the envelope pressure
boundary, defined as all above-grade surface area that separates the outdoors from conditioned or
semiconditioned space. Table 4 provides guidance for
evaluating Aes.
IDF. To determine IDF, use the Chapter 16 methods cited
previously. As a further simplification, Barnaby and Spitler (2005) derived the following
relationship that yields results approximately equal to the AIM-2 model (Walker and Wilson 1990,
1998; Chapter 16’s enhanced
model) at design conditions:
where
| I0, I1, I2 = coefficients, as follows: |
| H = building average stack height, ft (typically
8 to 10 ft per story)
|
| Δt = difference between indoor and outdoor temperatures,
°F
|
| AL,flue = flue effective leakage area at reference
pressure difference = 0.016 in. of water, assuming CD = 1, in2 (total for flues
serving furnaces, domestic water heaters, fireplaces, or other vented equipment, evaluated
assuming associated equipment is not operating and with dampers in closed position; see Chapter 16) |
Building stack height H is the average height difference between the
ceiling and floor (or grade, if the floor is below grade). Thus, for buildings with vented
crawlspaces, the crawlspace height is not included. For basement or slab-on-grade construction,
H is the average height of the ceiling above grade. Generally, there is
significant leakage between basements and spaces above, so above-grade basement height should be
included whether or not the basement is fully conditioned. With suitable adjustments for grade
level, H can also be estimated as V/Acf (conditioned floor area).
Equation (10) is
valid for typical suburban residential wind sheltering, AL,flue <AL/2, and at
any elevation. Table 5 shows IDF values derived with
Equation (10),
assuming AL,flue = 0.
Verification of leakage. A postconstruction pressurization test is
strongly recommended to verify that design leakage assumptions are actually achieved. Excess leaks
should be located and repaired.
Allocation of infiltration to rooms. Total building infiltration should
typically be allocated to rooms according to room volume; that is, it should be assumed that each
room has the same air exchange rate as the whole building. In reality, leakage varies by room and
over time, depending on outdoor temperature and wind conditions. These effects can either increase
or decrease room leakage. In addition, system air mixing tends to redistribute localized leakage to
all rooms. Thus, in most cases, there is no reasonable way to assign more or less leakage to
specific rooms.
An exception is leaky, multistory houses. The preferable and cost-effective response is mitigation of
the leakage. If repair is not possible, then for heating load calculation purposes, some leakage can
be differentially assigned to lower story and/or windward rooms in proportion to exposed surface
area (i.e., adjustment using an “exposure factor”).
Multifamily buildings. Usually, the simplified methods in Chapter 16 and this section do
not apply to multifamily residences. However, they can be used for row houses that are full building
height and have more than one exposed façade. For apartment units subdivided within a former
detached residence, the entire building should be analyzed and the resulting exchange rate applied
to the apartment volume. In other multifamily structures, infiltration is determined by many
factors, including overall building height and degree of sealing between apartments. For low-rise
construction, an upper bound for the infiltration rate can be found by evaluating the entire
building. As building height increases, leakage problems can be magnified, as discussed in Chapter 16. Estimating leakage
rates may require advice from a high-rise infiltration specialist.
Ventilation.
Whole-building ventilation. Because of energy efficiency concerns, residential construction has
become significantly tighter over the last several decades. Natural leakage rates are often
insufficient to maintain acceptable indoor air quality. ASHRAE Standard
62.2 specifies the required minimum whole-building ventilation rate as
where
| Qv = required ventilation flow rate, cfm
|
| Acf = building conditioned floor area,
ft2
|
| Nbr = number of bedrooms (not less than 1) |
Certain mild climates are exempted from this standard; local building authorities ultimately dictate
actual requirements. In addition, Standard 62.2 specifies alternative
methods for determining ventilation requirements that may result in smaller Qv values. Whole-building ventilation is expected to become
more common because of a combination of regulation and consumer demand. The load effect of Qv must be included in both cooling and heating calculations.
Heat recovery. Heat recovery devices should be considered part of
mechanical ventilation systems. These appliances are variously called heat recovery ventilators
(HRVs) or energy recovery ventilators (ERVs) and integrate with residential distribution systems, as
described in Chapter 26 of the 2024 ASHRAE Handbook—HVAC Systems and
Equipment. Either sensible heat or total heat (enthalpy) can be exchanged between
the
exhaust and intake airstreams. ERV/HRV units are characterized by their sensible and total
effectiveness.
Local mechanical exhaust. Kitchen and bathroom exhaust fans are required
by Standard 62.2 and are typically present. Exhaust fans that operate
intermittently by manual control are generally not included in load calculations. Continuously
operating ventilation should be included. Note that exhaust fans induce load only through enhanced
infiltration because of building depressurization (see the section on Combined Ventilation and
Infiltration Airflow for further discussion).
Combustion Air. Fuel-fired boilers, furnaces, and domestic
water heaters require combustion air. If the combustion air source is within the building envelope
(including in semiconditioned basements), additional infiltration and heating load are induced.
Locating the equipment outside of conditioned space (e.g., in a garage or vented mechanical closet)
or using sealed-combustion equipment eliminates this load.
Combustion air requirements for new forced-draft equipment can be estimated at 0.25 cfm per
1000 Btu/h or about 25 cfm for a 100,000 Btu/h heating
appliance. The requirements for existing natural draft equipment should be estimated at twice that
amount. In many cases, these quantities are relatively small and can be neglected.
For cooling load calculations, heating equipment is assumed to be not operating, leaving only any
domestic water heaters, for which the combustion air requirements are generally neglected.
Combined Ventilation and Infiltration Airflow. Mechanical
pressurization modifies the infiltration leakage rate. To assess this effect, overall supply and
exhaust flow rates must be determined and then divided into “balanced” and
“unbalanced” components.
where
| Qbal = balanced airflow rate, cfm |
| Qsup = total ventilation supply airflow rate,
cfm
|
| Qexh = total ventilation exhaust airflow rate
(including any combustion air requirements), cfm |
| Qunbal = unbalanced airflow rate, cfm
|
Note that unbalanced duct leakage can produce additional pressurization or depressurization. This
effect is discussed in the section on Distribution Losses.
Airflow components can be combined with infiltration leakage as follows (Palmiter and Bond 1991;
Sherman 1992):
where
| Qvi = combined infiltration/ventilation flow rate
(not including balanced component), cfm |
| Qi = infiltration leakage rate assuming no mechanical
pressurization, cfm |
Ventilation/infiltration load. The cooling or heating load from
ventilation and infiltration is calculated as follows:
where
| qvi,s = sensible ventilation/infiltration load,
Btu/h
|
| εs = HRV/ERV sensible effectiveness |
| Qbal,hr = balanced ventilation flow rate via HRV/ERV
equipment, cfm |
| Qbal,oth = other balanced ventilation supply airflow
rate, cfm |
| Δt = indoor/outdoor temperature difference,
°F
|
| ΔW = indoor/outdoor humidity ratio difference |
| qvi,t = total ventilation/infiltration load,
Btu/h
|
| εt = HRV/ERV total effectiveness |
| Δh = indoor/outdoor enthalpy difference,
Btu/lb
|
| qvi,l = latent ventilation/infiltration load,
Btu/h
|
Distribution Losses. Air leakage and heat losses from duct
systems frequently impose substantial equipment loads in excess of building requirements. The
magnitude of losses depends on the location of duct runs, their surface areas, surrounding
temperatures, duct wall insulation, and duct airtightness. These values are usually difficult to
accurately determine at the time of preconstruction load calculations, and must be estimated using
assumed values, so that selected equipment capacity is sufficient.
Good design and workmanship both reduce duct losses. Locating duct runs within the conditioned
envelope (above dropped hallway ceilings, for example) substantially eliminates duct losses.
Specific recommendations are found in Chapter 10
of the 2024 ASHRAE
Handbook—HVAC Systems and Equipment. Good workmanship and correct materials
are
essential to achieve low leakage. Many common sealing techniques, notably duct tape, have been shown
to fail in a few years. Well-constructed duct systems show leakage rates of 5% of fan flow from
supply and return runs, whereas 11% or more on each side is more typical. Because of the potentially
large load impact of duct leakage, postconstruction verification of airtightness is strongly
recommended.
Duct losses can be estimated using models specified in ASHRAE Standard
152, Francisco and Palmiter (1999), and Palmiter and Francisco (1997). The allowance for
distribution losses is calculated as follows:
where
| qd = distribution loss, Btu/h |
| Fdl = duct loss/gain factor, from Table 6 or ASHRAE Standard 152 design
efficiencies or a detailed model |
| qbl = total building load, Btu/h |
Table 6 shows typical duct
loss/gain factors calculated for the conditions indicated. These values can provide guidance for
hand estimates and illustrate the need for achieving low duct leakage. To the extent conditions
differ from those shown, specific calculations should be made using a method cited previously. Note
also that Table 6 cooling factors represent
sensible gain only. Duct leakage may also introduce significant latent gain; see ASHRAE Standard 152.
A cooling load calculation determines total sensible cooling load from heat gain (1) through opaque
surfaces (walls, floors, ceilings, and doors), (2) through transparent fenestration surfaces (windows,
skylights, and glazed doors), (3) caused by infiltration and ventilation, and (4) because of occupancy.
The latent portion of the cooling load is evaluated separately. Although the entire structure may be
considered a single zone, equipment selection and system design should be based on room-by-room
calculations. For proper design of the distribution system, the conditioned airflow required by each
room must be known.
To select a properly sized cooling unit, the peak or maximum load (block load) for each zone must be
computed. The block load for a single-family detached house with one central system is the sum of
all the room loads. If the house has a separate system for each zone, each zone block load is
required. When a house is zoned with one central cooling system, the system size is based on the
entire house block load, whereas zone components, such as distribution ducts, are sized using zone
block loads.
In multifamily structures, each living unit has a zone load that equals the sum of the room loads.
For apartments with separate systems, the block load for each unit establishes the system size.
Apartment buildings having a central cooling system with fan-coils in each apartment require a block
load calculation for the complete structure to size the central system; each unit load establishes
the size of the fan-coil and air distribution system for each apartment. One of the methods for
nonresidential buildings discussed in Chapter
18 may be used to calculate the block load.
Heat gain through walls, floors, ceilings, and doors is caused by (1) the air temperature difference
across such surfaces and (2) solar gains incident on the surfaces. The heat capacity of typical
construction moderates and delays building heat gain. This effect is modeled in detail in the
computerized RHB method, resulting in accurate simultaneous load estimates.
The RLF method uses the following to estimate cooling load:
where
| qopq = opaque surface cooling load,
Btu/h
|
| A = net surface area, ft2 |
| CF = surface cooling factor, Btu/h · ft2 |
| U = construction U-factor,
Btu/h · ft2 · °F
|
| Δt = cooling design temperature difference,
°F
|
| OFt,OFb,OFr =
opaque-surface cooling factors (see Table 7) |
| DR = cooling daily range, °F |
OF factors, found in Table 7, represent
construction-specific physical characteristics. OFt values
less than 1 capture the buffering effect of attics and crawlspaces, OFb represents incident solar gain, and OFr captures heat storage effects by reducing the effective
temperature difference. Note also that CF can be viewed as CF = U
× CLTD, the formulation used in prior residential and nonresidential methods.
Table 7 factors for
walls are simplified in two ways. First, the values do not depend on wall orientation. This has
minimal effect on total load, because residences typically have a mix of exposures. Second, only
wood frame construction is included. The wood frame values can be used for heavier construction
(e.g., masonry), but this overpredicts the wall’s contribution to cooling load and is thus
conservative.
Slab floors produce a slight reduction in cooling load, as follows:
where
| A = area of slab, ft2 |
| CFslab = slab cooling factor,
Btu/h · ft2
|
| hsrf = effective surface conductance, including
resistance of slab covering material such as carpet =1/(Rcvr + 0.68),
Btu/h · ft2 · °F.
Representative Rcvr values are found in Chapter 6 of
the 2024 ASHRAE Handbook—HVAC Systems and
Equipment. |
| 0.59 = constant, Btu/h · ft2 |
| 2.5 = factor, °F |
Surfaces Adjacent to Buffer Space
Heat gain from adjacent unconditioned or semiconditioned spaces can be calculated based on the
partition U-factor and temperature difference. Buffer space air temperature tb can be estimated using procedures discussed in the section
on Adjacent Buffer Spaces. Generally, simple approximations are sufficient. If the partition surface
is large and/or poorly insulated, buffer temperature should be calculated with more care.
Transparent Fenestration Surfaces
Cooling load associated with nondoor fenestration is calculated as follows:
where
| qfen = fenestration cooling load, Btu/h
|
| A = fenestration area (including frame),
ft2
|
| CFfen = surface cooling factor,
Btu/h · ft2
|
| U = fenestration NFRC heating
U-factor,
Btu/h · ft2 · °F
|
| Δt = cooling design temperature difference,
°F
|
| PXI = peak exterior irradiance, including shading modifications,
Btu/h · ft2 [see Equations (26) or (27)]
|
| SHGC = fenestration rated or estimated NFRC solar heat gain coefficient |
| IAC = interior shading attenuation coefficient, Equation (29) |
| FFs = fenestration solar load factor, Table 13 |
Peak Exterior Irradiance (PXI). Although solar gain occurs throughout the day, RP-1199 regression
studies (Barnaby et al. 2004) showed that the cooling load contribution of fenestration correlates
well with the peak-hour irradiance incident on the fenestration exterior. PXI is calculated as
follows:
where
| PXI = peak exterior irradiance, Btu/h · ft2
|
| Et, Ed, ED = peak total,
diffuse, and direct irradiance (Table 9 or 10),
Btu/h · ft2
|
| Tx = transmission of exterior attachment (insect
screen or shade screen) |
| Fshd = fraction of fenestration shaded by permanent
overhangs, fins, or environmental obstacles |
For horizontal or vertical surfaces, peak irradiance values can be obtained from Table 10 for
primary exposures, or from Table 9 equations for any exposure.
Skylights with slope less than 30° from horizontal should be treated as horizontal. Steeper,
nonvertical slopes are not supported by the RLF method.
Exterior Attachments. Common window coverings can
significantly reduce fenestration solar gain. Table 11 shows transmission
values for typical attachments.
Permanent Shading. The shaded fraction Fshd can be taken as 1 for any fenestration shaded by adjacent
structures during peak hours. Simple overhang shading can be estimated using the following:
where
| SLF = shade line factor from Table 12 |
| Doh = depth of overhang (from plane of fenestration),
ft
|
| Xoh = vertical distance from top of fenestration to
overhang, ft |
| h = height of fenestration, ft |
The shade line factor (SLF) is the ratio of the vertical distance a shadow falls beneath the edge of
an overhang to the depth of the overhang, so the shade line equals the SLF times the overhang depth.
Table 12 shows SLFs for July 21
averaged over the hours of greatest solar intensity on each exposure.
More complex shading situations should be analyzed with the RHB method.
Fenestration Solar Load Factors. Fenestration solar load
factors FFs depend on fenestration exposure and are found in
Table 13. The values
represent the fraction of transmitted solar gain that contributes to peak cooling load. It is thus
understandable that morning (east) values are lower than afternoon (west) values. Higher values are
included for multifamily buildings with limited exposure.
Interior Shading. Interior shading significantly reduces
solar gain and is ubiquitous in residential buildings. Field studies show that a large fraction of
windows feature some sort of shading; for example, James et al. (1997) studied 368 houses and found
interior shading in 80% of audited windows. Therefore, in all but special circumstances, interior
shading should be assumed when calculating cooling loads. In the RLF method, the interior
attenuation coefficient (IAC) model is used, as described in Chapter 15.
Residential values from that chapter are consolidated in Table 14. IAC values
for many other configurations are found in Chapter 15, Tables
14A to 14G.
In some cases, it is reasonable to assume that a shade is partially open. For example, drapes are
often partially open to admit daylight. IAC values are computed as follows:
where
| IAC = interior attenuation coefficient of fenestration with partially closed shade |
| Fcl = shade fraction closed (0 to 1) |
| IACcl = interior attenuation coefficient of fully
closed configuration (from Table 14 or Chapter 15, Tables
14A to 14G)
|
Infiltration and Ventilation
See the Common Data and Procedures section.
The contributions of occupants, lighting, and appliance gains to peak sensible and latent loads can
be estimated as
where
| qig,s = sensible cooling load from internal gains,
Btu/h
|
| qig,l = latent cooling load from internal gains,
Btu/h
|
| Acf = conditioned floor area of building,
ft2
|
| Noc = number of occupants (if unknown, estimate as
Nbr + 1)
|
Equations (30) and (31) and their
coefficients are derived from Building America (2004) load profiles evaluated at 4:00 pm, as
documented by Barnaby and Spitler (2005). Predicted gains are typical for U.S. homes. Further
allowances should be considered when unusual lighting intensities or other equipment are in
continuous use during peak cooling hours. In critical situations where intermittent high occupant
density or other internal gains are expected, a parallel cooling system should be considered.
For room-by-room calculations, qig,s should be evaluated for
the entire conditioned area, and allocated to kitchen and living spaces.
Air Distribution System: Heat Gain
See the Common Data and Procedures section.
The latent cooling load is the result of three predominant moisture sources: outdoor air
(infiltration and ventilation), occupants, and miscellaneous sources, such as cooking, laundry, and
bathing. These components, discussed in previous sections, combine to yield the total latent load:
where
| ql = total latent load, Btu/h |
| qvi,l = ventilation/infiltration latent gain,
Btu/h, from Equation (16) or (18)
|
| qig,l = internal latent gain, Btu/h,
from Equation
(31) |
Additional latent gains may be introduced through return duct leakage and specific atypical sources.
These may be estimated and included. Lstiburek and Carmody (1993) provide data for household
moisture sources; however, again note that Equation (31) adequately accounts for normal gains.
Because air conditioning systems are usually controlled by a thermostat, latent cooling is a side
effect of equipment operation. During periods of significant latent gain but mild temperatures,
there is little cooling operation, resulting in unacceptable indoor humidity. Multispeed equipment,
combined temperature/humidity control, and dedicated dehumidification should be considered to
address this condition.
Summary of RLF Cooling Load Equations
Table 15 contains a brief
list of equations used in the cooling load calculation procedure described in this chapter.
Calculating a residential heating load involves estimating
the maximum heat loss of each room or space to be heated and the simultaneous maximum (block) heat loss
for the building, while maintaining a selected indoor air temperature during periods of design outdoor
weather conditions. As discussed in the section on Calculation Approach, heating calculations use
conservative assumptions, ignoring solar and internal gains, and building heat storage. This leaves a
simple steady-state heat loss calculation, with the only significant difficulty being surfaces adjacent
to grade.
Exterior Surfaces Above Grade
All above-grade surfaces exposed to outdoor conditions (walls, doors, ceilings, fenestration, and
raised floors) are treated identically, as follows:
where HF is the heating load factor in Btu/h · ft2
Two ceiling configurations are common:
-
For ceiling/roof combinations (e.g., flat roof
or cathedral ceiling), the U-factor should be evaluated for the entire assembly.
-
For well-insulated ceilings (or walls) adjacent to vented
attic space, the U-factor should be that of the insulated
assembly only (the roof is omitted) and the attic temperature assumed to equal the
heating design outdoor temperature. The effect of attic radiant barriers can be
neglected. In cases where the ceiling or wall is not well insulated, the adjacent buffer
space procedure (see the section on Surfaces Adjacent to Buffer Space) can be used.
Below-Grade and On-Grade Surfaces
The Heating Load Calculations section of Chapter
18 includes simplified procedures for estimating heat loss through below-grade walls and
below- and on-grade floors. Those procedures are applicable to residential buildings. In more
detailed work, Bahnfleth and Pedersen (1990) show a significant effect of the area-to-perimeter
ratio. For additional generality and accuracy, see also methods described or cited in
Beausoleil-Morrison and Mitalas (1997), CAN/CSA Standard F280, HRAI
(2018), Krarti and Choi (1996), Kruis and Krarti (2017), and Rock (2005).
Surfaces Adjacent to Buffer Space
Heat loss to adjacent unconditioned or semiconditioned spaces can be calculated using a heating
factor based on the partition temperature difference:
Buffer space air temperature tb can be estimated using
procedures discussed in the section on Adjacent Buffer Spaces. Generally, simple approximations are
sufficient except where the partition surface is poorly insulated.
Crawlspaces and basements
are cases where the partition (the house floor) is often poorly insulated; they also involve heat
transfer to the ground. Most codes require crawlspaces to be adequately vented year-round. However,
work highlighting problems with venting crawlspaces (DeWitt 2003) has led to application of sealed
crawlspaces with insulated perimeter walls. Equation (5) may be applied to basements and crawlspace by including
appropriate ground-related terms in the heat balance formulation. For example, when including
below-grade walls, Ax = Abw, Ux = Uavg,bw, and tx = tgr should be included as applicable in the summations in Equation (5). Losses
from piping or ducting should be included as additional buffer space heat gain. Determining the
ventilation or infiltration rate for crawlspaces and basements is difficult. Latta and Boileau
(1969) estimated the air exchange rate for an uninsulated basement at 0.67 ach under winter
conditions. Field measurements of eight ventilated crawlspaces summarized in Palmiter and Francisco
(1996) yielded a median flow rate of 4.6 ach. Clearly, crawlspace infiltration rates vary widely,
depending on vent configuration and operation.
Ventilation and Infiltration
Infiltration of outdoor air causes both sensible and latent heat loss. The energy
required to raise the temperature of outdoor infiltrating air to indoor air temperature is the
sensible component; energy associated with net loss of moisture from the space is the latent
component. Determining the volumetric flow Q of outdoor air entering the
building is discussed in the Common Data and Procedures section and in Chapter 16. Determining the
resulting sensible and latent loads is discussed in the Ventilation/Infiltration Load subsection.
In many climates, humidification is required to maintain comfortable indoor relative humidity under
heating conditions. The latent ventilation and infiltration load calculated, assuming desired indoor
humidity conditions, equals the sensible heat needed to evaporate water at a rate sufficient to
balance moisture losses from air leakage. Self-contained humidifiers provide this heat from internal
sources. If the heat of evaporation is taken from occupied space or the distribution system, the
heating capacity should be increased accordingly.
For intermittently heated buildings and night thermostat setback, additional heat is required to
raise the temperature of air, building materials, and material contents to the specified
temperature. The rate at which this additional heat must be supplied is the pickup load, which
depends on the structure’s heat capacity, its material contents, and the time in which these
are to be heated.
Because the design outdoor temperature is generally much lower than typical winter temperatures,
under most conditions excess heating capacity is available for pickup. Therefore, many engineers
make no pickup allowance except for demanding situations. If pickup capacity is justified, the
following guidance can be used to estimate the requirement.
Relatively little rigorous information on pickup load exists. Building simulation programs can
predict recovery times and required equipment capacities, but a detailed simulation study is rarely
practical. Armstrong et al. (1992a, 1992b) developed a model for predicting recovery from setback
and validated it for a church and two office buildings. Nelson and MacArthur (1978) studied the
relationship between thermostat setback, furnace capacity, and recovery time. Hedrick et al. (1992)
compared Nelson and MacArthur’s results to tests for two test houses and found that the
furnace oversizing required for a 2 h recovery time ranges from 20 to 120%, depending on size of
setback, building mass, and heating Δt (colder locations require
less oversizing on a percentage basis).
The designer should be aware that there are trade-offs between energy savings from thermostat setback
and energy penalties incurred by oversizing equipment. Koenig (1978) studied a range of locations
and suggested that 30% oversizing allows recovery times less than 4 h for nearly the entire heating
season and is close to optimum from an energy standpoint.
The preceding guidance applies to residential buildings with fuel-fired furnaces. Additional
considerations may be important for other types of heating systems. For air-source heat pumps with
electric resistance auxiliary heat, thermostat setback may be undesirable (Bullock 1978).
Thermostats with optimum-start algorithms, designed to allow both energy savings and timely recovery
to the daytime set point, are becoming routinely available and should be considered in all cases.
Summary of Heating Load Procedures
Table 16 lists
equations used in the heating load calculation procedures described in this chapter.
ASHRAE members can access ASHRAE Journal articles and ASHRAE research project
final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase
by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.
ACCA. 2016. Manual J residential
load calculations, 8th ed., v. 2.5. Air Conditioning Contractors of America,
Arlington, VA.
Armstrong, P.R., C.E. Hancock, and J.R. Seem. 1992a.
Commercial building temperature recovery—Part 1: Design procedure based on a step response
model (RP-491). ASHRAE Transactions 98(1):381-396.
Armstrong, P.R., C.E. Hancock, and J.R. Seem. 1992b.
Commercial building temperature recovery—Part 2: Experiments to verify step response model
(RP-491). ASHRAE Transactions 98(1):397-410.
ASHRAE. 2023. Thermal environmental conditions for human
occupancy. ANSI/ASHRAE Standard 55-2023.
ASHRAE. 2022. Ventilation and acceptable indoor air
quality in low-rise residential buildings. ANSI/ASHRAE Standard
62.2-2022.
ASHRAE. 2014. Method of test for determining the design
and seasonal efficiencies of residential thermal distribution systems. ANSI/ASHRAE Standard 152-2014.
ASTM. 2024. Standard terminology of building
constructions. Standard E631-15. American Society for Testing and
Materials, West Conshohocken, PA. www.astm.org.
Bahnfleth, W.P., and C.O. Pedersen 1990. A
three-dimensional numerical study of slab-on-grade heat transfer. ASHRAE
Transactions 96(2):61-72.
Barnaby, C.S., and J.D. Spitler. 2005. Development of
the residential load factor method for heating and cooling load calculations. ASHRAE Transactions 111(1):291-307.
Barnaby, C.S., J.D. Spitler, and D. Xiao. 2004. Updating
the ASHRAE/ACCA residential heating and cooling load calculation procedures and data (RP-1199).
ASHRAE Research Project, Final Report.
Barnaby, C.S., J.D. Spitler, and D. Xiao. 2005. The
residential heat balance method for heating and cooling load calculations (RP-1199). ASHRAE Transactions 111(1):308-319.
Beausoleil-Morrison, I., and G. Mitalas. 1997. BASESIMP:
A residential-foundation heat-loss algorithm for incorporating into whole-building
energy-analysis programs. Proceedings of Building Simulation
’97, Prague.
Bullock, C.E. 1978. Energy savings through thermostat
setback with residential heat pumps. ASHRAE Transactions
84(2):352-363.
CSA Group. 2012. Determining the required capacity of
residential space heating and cooling appliances. CAN/CSA Standard
F280-12. CSA Group, Mississauga, ON, Canada.
DeWitt, C. 2003. Crawlspace myths. ASHRAE Journal 45:20-26.
Francisco, P.W., and L. Palmiter. 1999 (rev. 2003).
Improvements to ASHRAE Standard 152P.
Ecotope, Inc., Seattle, WA.
Hedrick, R.L., M.J. Witte, N.P. Leslie, and W.W.
Bassett. 1992. Furnace sizing criteria for energy-efficient setback strategies. ASHRAE Transactions 98(1):1239-1246.
HRAI. 2018. Residential heat loss
and heat gain calculations. Heating, Refrigerating and Air Conditioning Institute of
Canada. Mississauga, ON.
James, P., J. Cummings, J. Sonne, R. Vieira, and J.
Klongerbo. 1997. The effect of residential equipment capacity on energy use, demand, and
run-time. ASHRAE Transactions 103(2):297-303.
Koenig, K. 1978. Gas furnace sizing requirements for
residential heating using thermostat night setback. ASHRAE
Transactions 84(2):335-351.
Krarti, M., and S. Choi 1996. Simplified method for
foundation heat loss calculation. ASHRAE Transactions
102(1):140-152.
Kruis, N., and M. Krarti. 2017. Three-dimensional
accuracy with two-dimensional computational speed: Using the Kiva™ numerical framework to
improve foundation heat transfer calculations. Journal of Building
Performance Simulation 10(2):161-182. dx.doi.org/10.1080/19401493.2016.1211177.
Latta, J.K., and G.G. Boileau. 1969. Heat losses from
house basements. Canadian Building 19(10):39.
Lstiburek, J.L., and J. Carmody. 1993. Moisture control handbook. Van Nostrand Reinhold, New York.
McQuiston, F.C. 1984. A study and review of existing
data to develop a standard methodology for residential heating and cooling load calculations
(RP-342). ASHRAE Transactions 90(2A):102-136.
Nelson, L.W., and J.W. MacArthur. 1978. Energy savings
through thermostat setback. ASHRAE Transactions
84(2):319-334.
Palmiter, L., and T. Bond. 1991. Interaction of
mechanical systems and natural infiltration. Proceedings of the 12th AIVC
Conference on Air Movement and Ventilation Control Within Buildings. Air Infiltration
and Ventilation Centre, Coventry, U.K.
Palmiter, L., and P. Francisco. 1996. Modeled and
measured infiltration: Phase III. A detailed case study of three homes. Electric Power Research
Institute Report TR-106288. Palo Alto, CA.
Palmiter, L., and P. Francisco. 1997. Development of a
practical method of estimating the thermal efficiency of residential forced-air distribution
systems. Electric Power Research Institute Report TR-107744. Palo
Alto, CA.
Parker, D.S., J.E.R. McIlvaine, S.F. Barkaszi, D.J.
Beal, and M.T. Anello. 2000. Laboratory testing of the reflectance
properties of roofing materials. FSEC-CR670-00. Florida Solar Energy Center,
Cocoa.
Pedersen, C.O., D.E. Fisher, J.D. Spitler, and R.J.
Liesen. 1998. Cooling and heating load calculation principles.
ASHRAE.
Pedersen, C.O., R.J. Liesen, R.K. Strand, D.E. Fisher,
L. Dong, and P.G. Ellis. 2001. Toolkit for building load
calculations. ASHRAE.
Rock, B.A. 2005. A user-friendly model and coefficients
for slab-on-grade load and energy calculations. ASHRAE Transactions
111(2):122-136.
Sherman, M.H. 1992. Superposition in infiltration
modeling. Indoor Air 2: 101-114.
Sherman, M.H., and D.T. Grimsrud. 1980.
Infiltration-pressurization correlation: Simplified physical modeling. ASHRAE Transactions 86(2):778.
Walker, I.S., and D.J. Wilson. 1990. The Alberta air
infiltration model. The University of Alberta, Department of Mechanical Engineering, Technical Report 71.
Walker, I.S., and D.J. Wilson. 1998. Field validation of
equations for stack and wind driven air infiltration calculations. International Journal of HVAC&R Research (now Science and Technology for the Built Environment) 4(2).