5. RESIDENTIAL INFILTRATION
Historically, residential building envelopes were considered sufficiently leaky such that infiltration
alone would provide adequate ventilation air flow rates, supplemented by occupant use of windows and
exhaust fans when needed. Possible difficulties with this approach included variability in occupant use
of windows and exhaust fans, low infiltration when natural forces (stack and wind) are weak; unnecessary
energy consumption when these forces are strong; drafts in cold climates; lack of control of ventilation
rates to meet changing needs; poor humidity control; potential for interstitial condensation from
exfiltration in cold climates or infiltration in hot humid climates; and lack of opportunity to recover
energy used to condition ventilation air. The solution to these concerns was to have a tight building
envelope and a properly designed and operated mechanical ventilation system with automatic control. To
that end, ASHRAE Standard 62.2, U.S. building codes, and the National Building Code of Canada (NRCC 2020) encourage tighter envelope
construction, coupled with increased requirements for mechanical ventilation for newly constructed
residential buildings.
This section summarizes typical infiltration rates from recent measurement studies in single-family homes
and MFBs, common leakage pathways, and strategies for controlling air leakage in new and existing
residential buildings. It also describes several calculation procedures, ranging from simple estimation
techniques to more physical models, for estimating residential building infiltration rates. Orme (1999)
provides a more thorough review of simplified models.
For energy modeling or code compliance, a particular building’s air change rate cannot be reliably
deduced from the building’s construction or age or from a simple visual inspection. Some
measurements are necessary, such as a fan pressurization test of envelope airtightness or a detailed
quantification of the leakage sites and their magnitude. The air change rate of a building may be
calculated given (1) the location and leakage function for every opening in the building envelope and
between major building zones, (2) the wind pressure coefficients over the building envelope, and (3) any
mechanical ventilation airflow rates. These data are generally unavailable for all except very simple
structures or extremely well studied buildings. Therefore, their values must be assumed. The
appropriateness of these assumptions influences the accuracy of predictions of air change rates.
It is much easier and more cost effective to build a tight building than to tighten an existing
building. Elmroth and Levin (1983), Eyre and Jennings (1983), Marbek Resource Consultants (1984),
and Nelson et al. (1985) provide information and construction details on airtight building design
for houses. BC Housing (2017) and RDH (2013) have both published an airtightness design guide for
MFBs.
Most building codes require a continuous air barrier (CAB)
for new residential buildings. Table 2 lists
prescriptive and performance-based air leakage targets from Canadian and American building codes and
standards, for both single-family and multi-family dwellings. Prescriptive requirements are
typically assigned to air barrier materials and assemblies. Performance-based targets apply to the
whole building, or whole dwelling unit in the case of MFBs. Performance-based targets typically
require field verification via fan pressurization testing. Several building codes and standards also
specify maximum allowable air leakage rates for window and door assemblies. Depending on the
authority having jurisdiction, additional prescriptive and/or performance-based airtightness targets
may apply. Always check local building codes and standards for region-specific airtightness
requirements.
Air barrier continuity is critical for performance. Take particular care to ensure continuity at all
wall, floor, and ceiling joints; at window and door frames; and at all penetrations of the air
barrier such as electrical boxes, plumbing connections, and utility service penetrations. If using a
sheet air barrier, joints must be lapped and sealed. In cold climates, the barrier can be installed
either on the inside of the wall framing, in which case it usually functions as a vapor retarder as
well, or on the outside of the wall framing, in which case it should have a permeance rating high
enough to allow diffusion of water vapor from the wall. For a discussion of moisture transfer in
building envelopes, see Chapters
25 and 26.
In MFBs, maintaining continuous air barriers (CABs) between interior zones is important for
controlling interzonal airflow and contaminant transport. The gypsum wall board (or other wall
finishing material) typically acts as the plane of airtightness between zones, with fire stopping
and/or acoustic sealant installed around penetrations and assembly interfaces, to meet fire and
acoustic separation requirements. The EnergyStar Multi-Family High Rise Program explicitly requires
that the bid documents clearly illustrate the continuous plane of airtightness for the building
envelope and all dwelling units, with air barrier materials and accessories identified in section,
plan, and detail form (EnergyStar 2015). Controlling air leakage around interior doors is also
important. The use of weatherstripping and/or door sweeps at interior doors can greatly reduce door
assembly air leakage rates (Tian et al. 2020).
Air leakage paths must first be located before the envelope of an existing building can be tightened.
Air leakage into and out of buildings is caused by not only windows and doors but also a wide range
of unexpected and unobvious construction defects (refer to Leakage
Distributions for more detail). Many important leakage routes can be very difficult to
find. A variety of techniques developed to locate leakage paths are described in ASTM Standard E1186-2022a and Charlesworth (1988).
Once leakages are located (and assuming they are accessible), they can be repaired with materials and
techniques appropriate to the size and location of the leak. Diamond et al. (1982), Energy Resource
Center (1982), Harrje et al. (1979), and many websites and online videos include information on
airtightening or “weatherization” in existing residential buildings with caulking,
sealing, weatherstripping, and use of door sweeps, for example. With these procedures, air leakage
of residential buildings can be reduced dramatically: anywhere from 5% to more than 50%, depending
on the extent of the tightening effort and the experience of those doing the work (Blomsterberg and
Harrje 1979; Giesbrecht and Proskiw 1986; Harrje and Mills 1980; Jacobson et al. 1986; Verschoor and
Collins 1986). Much less information is available for airtightening MFBs, but the same general
principles apply. The few studies that have documented unit-level air-tightening efforts in existing
MFBs reported reductions in dwelling unit air leakage rates between 10 and 70% (Bohac et al. 2007),
and 39 and 89% (Bohac et al. 2016). Both studies noted that airtightening efficacy was greatly
dependent on the accessibility of the leakage pathways and the air sealing materials.
Single-Family Home Building Air
Leakage Data
Typical air leakage rates in single-family housing can vary widely. Chan et al. (2005) analyzed
over 70,000 air leakage measurements from single-family homes in the United States,
with building air leakage characterized using NL. The geometric mean for the entire sample was 0.54,
with a geometric standard deviation of 2.0. More recently, Khemet and Richman (2018) and
Mélois et al. (2019) leveraged national airtightness databases, in Canada and France
respectively, to characterize national airtightness trends in single-family homes. Based on a sample
of 916,600 fan pressurization tests in existing single-family homes, Khemet and Richman
(2018) reported a geometric mean of 5.7 h–1 at 0.20 in. of water (0.67
NL), with measurements ranging from 0.5 to 30 h–1 at 0.20 in. of water
(0.1 to 5.0 NL). Mélois et al. (2019) reported a median air leakage rate of 0.02
cfm/ft2 at a test pressure of 0.016 in. of water (range =
0.002 to 0.02 cfm/ft2), based on 170,028 measurements in
single-family homes constructed between 2010 and 2016. Assuming n =
0.65, these results roughly translate to a median of 0.11 cfm/ft2 at a test
pressure of 0.20 in. of water (range = 0.008 to 0.26 cfm/ft2).
Smaller studies of newly-constructed single-family homes in Europe have reported mean air leakage
rates of 0.40 cfm/ft2 (Pan 2010) and 0.09 to 0.32
cfm/ft2 (Vinha et al., 2015) at test pressures of 0.20 in. of
water.
Khemet and Richman (2018) and Chan et al. (2005) both found that residential building air leakage
rates tended to increase with building age. Construction type has also been shown to affect building
airtightness, with wood-frame structures generally being less airtight than concrete or masonry
structures (Mélois et al. 2019; Pan 2010; Vinha et al. 2015). Although building airtightness
is generally improving, in part due to increased awareness about the role of airtightness in
building energy efficiency, as well as increasingly stringent code requirements, there is still a
large range in measured air leakage rates.
Dickerhoff et al. (1982) and Harrje and Born (1982) studied air leakage of individual building
components and systems. The following points summarize the percentages of whole-building air leakage
area that they found associated with various components and systems. Values in parentheses include
the range determined for each component and the mean of the range. Colliver et al. (1994) also
compiled a list of effective leakage areas for typical building envelope components.
Note that most building codes and standards have moved towards whole-building fan pressurization
testing to characterize the effective building envelope airtightness, in lieu of component air
leakage measurements. Except for window and door assemblies, recent measurement studies have
typically not measured component air leakage rates. The following percentages do not necessarily
represent current construction and air sealing practices; however, these findings are still useful
in identifying typical leakage pathways, which will require diligent air sealing during
construction.
Walls (18 to 50%; 35%). Both interior and exterior walls
contribute to the leakage of the structure. Leakage can occur between the sill plate and the floor
or foundation; through cracks below the bottom of the gypsum wallboard, around and through
electrical boxes, and through plumbing penetrations; and into the attic at the top plates of walls.
Holes drilled through the top plates into the attic for passage of wiring are often unsealed.
Ceiling Details (3 to 30%; 18%). Leakage across the top
ceiling of the heated space is particularly insidious because it reduces the effectiveness of
insulation on the attic floor and contributes to infiltration heat loss. Ceiling leakage also
reduces the effectiveness of ceiling insulation in buildings without attics. Recessed lighting,
plumbing, and other penetrations leading to the attic are some particular areas of concern, as are
intentional openings such as access hatches or for whole-house fans.
Forced-Air Heating and/or Cooling Systems (3 to 28%; 18%).
The location of the heating or cooling equipment, air handler, or ductwork in conditioned or
unconditioned spaces; the venting arrangement of a fuel-burning device; and the existence and
location of a combustion air supply all affect air leakage. Modera et al. (1991) and Robison and
Lambert (1989), among others, found that the variability of leakage in ducts passing through
unconditioned spaces is high, the coefficient of variation being about 50%. Field studies also
showed that in situ repairs can eliminate one-quarter to two-thirds of the observed leakage
(Cummings and Tooley 1989; Cummings et al. 1990; Jump et al. 1996; Robison and Lambert 1989). The
18% contribution of ducts to total leakage significantly underestimates their effect because, during
system operation, pressure differentials across duct leaks are approximately ten times higher than
typical pressure differences across envelope leaks (Modera 1989; Modera et al. 1991) and result in
large (factors of two to three), changes in ventilation rate (Cummings et al. 1990; Walker 1999;
Walker et al. 1999).
Windows and Doors (6 to 22%; 15%). More variation in
window leakage is seen among window types (e.g., casement versus double-hung) than among new windows
of the same type from different manufacturers (Weidt et al. 1979). Windows that seal by compressing
the weather strip (casements, awnings) often show significantly lower leakage than windows with
sliding seals. Leakage around the frames of windows also can be significant if not properly sealed,
typically with controlled-expansion foam, during their installation. The door between a residence
and an attached garage, or an enclosed hallway in MFBs, also needs gasketing to reduce air leakage
as well as smoke and other contaminants’ movement.
Fireplaces (0 to 30%; 12%). When a fireplace is not in
use, poorly fitting dampers allow indoor air to escape. Glass doors may not seal the fireplace
structure more tightly than a closed damper does. Chimney caps or fireplace plugs (with signs that
warn they are in place) effectively reduce leakage through a cold fireplace but may not be allowed
by fire code. The gap between a metal fireplace insert and the surrounding wall, tiles, or brick is
often another leakage path if not properly sealed.
Exhaust Vents from Conditioned Spaces (2 to 12%; 5%).
Exhaust ducts going from conditioned spaces to the outdoors frequently have either no dampers or
dampers that do not close properly. The gap between the duct and the wall or roof penetration often
needs sealing, as well.
Diffusion Through Walls and Ceilings (<1%). Compared to infiltration through holes and other
openings in the structure, diffusion through well-constructed walls and ceilings is not an important
flow mechanism. Proper installation of an air barrier can help minimize this air leakage path. The
National Building Code of Canada requires the installation of a continuous air barrier with a
maximum air permeance of 0.01 to 0.10 cfm/ft2 at 0.30 in. of water,
depending on the performance class (NRCC 2020). At 0.02 in. of water, the permeability
of building materials produces an air change rate of less than 0.01 h–1 by wall
diffusion in a typical house.
Multi-Family Building (MFB) Air
Leakage Data
Air leakage rates in MFBs are measured at either the dwelling level or at the building level,
depending on the jurisdiction and the applicable codes and standards. As mentioned previously, LEED,
ASHRAE Standard 62.2, IECC, and EnergyStar include requirements for
dwelling unit air leakage testing, to assess unit-level compartmentalization. Depending on the
standard, these targets range from 0.20 to 0.30 cfm/ft2 or 3.0 to 5.0
h–1, at a test pressure of 0.20 in. of water. Most measurement studies
reporting air leakage rates in MFBs report dwelling unit air leakage.
Table
3 summarizes results from several recent studies measuring dwelling unit air leakage rates
in newly constructed buildings. Consistent with single-family homes, there is a wide range in
reported values, even in new construction. Dwelling unit air leakage rates are generally higher in
wood-frame MFBs (Bohac et al. 2020; Mélois et al. 2019; Pan 2010; Vinha et al. 2015) compared
to concrete and masonry buildings (Lozinsky and Touchie 2021; Mélois et al. 2019; Pan 2010;
Shin and Jo 2013). There are a few studies that have published whole building test data for MFBs. In
general, whole building air leakage rates are in the same order of magnitude as dwelling units.
Bohac et al. (2020) measured whole-building air leakage rates between 0.05 and 0.47
cfm/ft2, at a test pressure of 0.20 in. of water, in low-rise
wood-framed MFBs. Other studies have reported whole-building values ranging from 0.14 to 0.50
cfm/ft2 (Jones et al., 2014) and 0.05 to 0.55 cfm/ft2
(Jones, 2022), at a test pressure of 0.30 in. of water.
Several studies have measured partition-level air leakage rates in MFBs using guarded fan
pressurization methods. All studies have noted considerable variation in air leakage rates at the
partition level (Bohac et al. 2020; Finch 2007; Lozinsky and Touchie 2023a; Ricketts 2014; Shin and
Jo 2013). Floor/ceiling assemblies and unit-to-unit interior walls were typically the most airtight.
In studies that separated unit-to-corridor wall air leakage, unit-to-corridor walls were on average
two to nine times leakier than unit-to-unit interior walls, when normalized by surface area. Studies
in older buildings have estimated that interior air leakage accounted for 12 to 68% of total
dwelling unit air leakage (Diamond et al. 1986; Finch 2007; Gulay et al. 1993; Levin 1988; Modera et
al. 1986; Ricketts 2014). As building envelope airtightness construction practices have improved,
the contribution of interior air leakage to total dwelling unit air leakage has generally increased,
with recent studies reporting interior air leakage fractions of 50 to 95% (Lozinsky and Touchie
2023a; Shin and Jo 2013).
Many of the air leakage pathways described in the previous section also apply to MFBs and dwelling
units. Mélois et al. (2019) also summarized typical air leakage pathways identified as part
of compliance testing in over 54,000 newly constructed multifamily dwellings in France.
The two most common leakage pathways identified in multifamily dwellings were gaps around mechanical
ventilation ductwork and air terminals, and through-wall/through-floor penetrations, including but
not limited to plumbing pipes and electrical conduits, occurring in 57% and 47% of tests,
respectively. Other interior leakage pathways included junctions between walls, or between wall and
floor assemblies, and electrical and/or lighting penetrations.
Interfloor air leakage via stairwell, elevator, and/or garbage chute shafts can negatively impact
building performance, particularly in tall buildings where stack-induced pressure differentials can
be large. Simulation studies have shown that tightening vertical shafts, by installing fully-weather
stripped doors at stairwell access points and implementing elevator vestibules, can reduce
inter-zonal air flow and contaminant transport, and potentially reduce space conditioning loads,
depending on the building’s mechanical ventilation system (Fine et al. 2022; Lozinsky and
Touchie 2024). The benefits of shaft airtightening interventions only work when all shafts are
tightened simultaneously.
Modeling Residential Infiltration
The following sections describe several modelling techniques for estimating infiltration in
single-family residential buildings. While these techniques are typically used for research and
remediation purposes, most small residential buildings are designed and constructed without direct
involvement of ventilation engineers. Contractors, who typically prepare these buildings’
designs, are required to follow mandates in various codes and standards, and they apply
experience-based rules of thumb when determining, for example, exhaust needs. Often, leaky buildings
or air quality problems result. Research and experience have shown that tightening building
envelopes and using mechanical ventilation with heat recovery can improve IAQ and reduce energy
consumption. Retaining the services of a ventilation engineer before construction begins is
advisable in some situations.
Empirical Models. These models of residential infiltration
are based on statistical fits of infiltration rate data for specific houses. They use fan
pressurization test results to account for house airtightness and take the form of simple relations
between infiltration rate, an airtightness rating, and, in most cases, weather conditions. Empirical
models account for envelope infiltration only and do not include intentional ventilation. In one
approach, the calculated air change rate at 0.20 in. of water based on a pressurization
test is simply divided by a constant approximately equal to 20 (Sherman 1987). This technique does
not account for the effect of infiltration-driving mechanisms on air flow. Empirical models that do
account for weather effects have been developed by Kronvall (1980), Reeves et al. (1979), and Shaw
(1981).
The latter two models account for building air leakage using the values of c and n from Equation (32). The only other
data required are wind speed and temperature difference. These empirical models predict long-term
(one-week) infiltration rates very well in the houses from which they were developed; they do not,
however, work as well in other houses because of the building-specific nature of leakage
distribution, wind pressure, and internal partitioning. Persily (1986) and Persily and Linteris
(1983) compared measured and predicted house infiltration rates for these and other models. The
average long-term differences between measurements and predictions are generally about 40%, although
individual predictions can be inaccurate by 100% or more (Persily, 1986; Walker and Wilson, 1998).
Several procedures have been developed to calculate building air change rates that are based on
physical models of the building interior as a single zone. These single-zone models are only
appropriate for buildings with minimal internal resistance to airflow, and are therefore
inappropriate for large, multizone residential buildings. Some models of this type have been
developed by Cole et al. (1980), Sherman and Grimsrud (1980), Walker and Wilson (1998), and Warren
and Webb (1980). The section on Residential Calculation Examples uses both basic and enhanced models
(Bradley 1993; CHBA 1994; Hamlin and Pushka 1994; Palmiter and Bond 1994; Walker and Wilson 1998).
The basic model uses effective air leakage area AL at 0.016 in. of water, which can be obtained
from a whole-building fan pressurization test. The enhanced
model uses pressurization test results to characterize house air leakage
through the leakage coefficient c and pressure exponent n. The enhanced model improves on the basic model by using a power law to
represent envelope leakage, including a flue as a separate leakage path, and having separate wind
effects for houses with crawlspaces or basements instead of slab-on-grade foundations.
For both models, the user must provide the wind speed, the temperature difference, information on the
distribution of leakage over the building envelope, a wind shelter parameter or local shielding for
the basic model, and a terrain coefficient. The predictive accuracy of the enhanced model can be
very good, typically ±10% when parameters are well known for the building in question
(Palmiter and Bond 1994; Sherman and Modera 1986; Walker and Wilson 1998). All models’ results
are sensitive to the user-provided data, and some of these parameters are often quite difficult to
determine.
Superposition of Wind and Stack
Effects
Simplified physical models of infiltration solve the problem of two natural driving forces (wind and
stack) separately and then combine them in a process called superposition. Superposition is necessary because each
physical process can affect internal and external air pressures on the building’s envelope,
and can cause interactions between physical processes that are otherwise independent. An exact
solution is impossible, because (1) detailed properties of all the building leaks are unknown and
(2) leakage is a nonlinear process. Therefore, most modelers have developed a simplified
superposition process to combine stack and wind effects. Sherman (1992b) compared various
superposition procedures and derived a generalized superposition equation involving simple leakage
distribution parameters, and showed that the result is always subadditive. Typically, only 35% of
infiltration from the smaller effect can be added to the larger effect. Depending on the specific
building and conditions, that percentage could go as high as 85% or as low as zero. Walker and
Wilson (1993) compared several superposition techniques to measured data. Sherman, as well as Walker
and Wilson, found quadrature, shown in Equation (40), to be a robust superposition technique:
The following sections discuss how superposition is combined with calculation of wind and stack flows
to determine total flow.
Residential Calculation Examples
Basic Model. The following calculations are based on the
Sherman and Grimsrud (1980) model, which uses the effective air leakage area at 0.016 in. of
water. This leakage area can be obtained from a whole-building pressurization test. Using
effective air leakage area, the airflow rate from infiltration is
where
| Q = airflow rate, cfm |
| AL = effective air leakage area,
in2
|
| Cs = stack coefficient,
cfm2/in4 · °F
|
| ΔT = average indoor-outdoor temperature difference for time
interval of calculation, °F |
| Cw = wind coefficient,
cfm2/in4 · mph2
|
| U = average wind speed measured at local weather station for
time interval of calculation, mph |
| 1000 = unit conversion factor |
Table 4 shows values of Cs for one-, two-, and three-story houses. The value of wind
coefficient Cw depends on the local shelter class of the
building (Table 5) and the building height. Table 6 shows values of Cw for one-, two-, and three-story houses in shelter classes 1
to 5. In calculating values in Tables 4 and 6, the following assumptions were
made:
-
Terrain used for converting meteorological to local wind speeds is that of a rural area
with scattered obstacles
-
R = 0.5 (half the building leakage in the walls)
-
X = 0 (equal amounts of leakage in the floor and ceiling)
-
Heights of one-, two-, and three-story buildings = 8, 16, and 24 ft,
respectively
Example 1.
Estimate the infiltration at winter design conditions for a two-story house in Lincoln,
Nebraska. The house has effective air leakage area of 77 in2 and
volume of 12,000 ft3, and the predominant wind is perpendicular to
the street (shelter class 3). The indoor air temperature is 68°F.
Solution: The 99% design temperature for Lincoln
is –2°F. Assume a design wind speed of 15 mph. From Equation
(34), with Cs = 0.0299 from Table 4 and Cw = 0.0086 from Table 6, the airflow rate
caused by infiltration is
From Equation
(3), air change rate I is equal to Q divided by the building volume:
Example 2.
Predict the average infiltration during a one-week period in January for a one-story house in
Portland, Oregon. During this period, the average indoor/outdoor temperature difference is
30°F, and average wind speed is 6 mph. The house has volume of
9000 ft3 and effective air leakage area of 107
in2, and it is in an area with buildings and trees within 30
ft in most directions (shelter class 4).
Solution: From Equation (41), the
airflow rate caused by infiltration is
The air change rate is therefore
Example 3.
Estimate the average infiltration over the heating season in a two-story house with volume of
11,000 ft3 and leakage area of 131 in2. The
house is located on a lot with several large trees but no other close buildings (shelter
class 3). Average wind speed during the heating season is 7 mph, and the
average indoor/outdoor temperature difference is 36°F.
Solution: From Equation (41), the
airflow rate from infiltration is
The average air change rate is therefore
Enhanced Model. This section presents a simple,
single-zone approach to calculating air infiltration rates in houses based on the Walker and Wilson
(1998) model. The airflow rate from stack and wind infiltration is
where
| Qs = stack airflow rate, cfm |
| Qw = wind airflow rate, cfm |
| c = flow coefficient, cfm/(in. of water)n |
| Cs = stack coefficient, (in. of
water/°F)n |
| Cw = wind coefficient, (in. of
water/mph2)n |
| s = shelter factor |
| ΔT = indoor – outdoor temperature difference,
°F
|
| n = pressure exponent, dimensionless |
In calculating tabulated values of Cs, Cw, and s, the assumptions were
-
Each story is 8 ft high.
-
The flue is 6 in. in diameter and reaches 6 ft above the upper
ceiling.
-
The flue is unsheltered.
-
Half of envelope leakage (not including the flue) is in the walls and one-quarter each is
at the floor and ceiling, respectively.
-
n = 0.67
The following examples use typical values for terrain factors, house height, and wind speed
measurement height, wind speed multiplier G given in Table 7, and use a
relationship based on equations found in Chapter 24.
Example 4.
Estimate the infiltration at winter design conditions for a two-story slab-on-grade house
with a flue in Lincoln, Nebraska. The house has a flow coefficient of c = 4370 cfm/(in. of water)n and a pressure
exponent of n = 0.67 (corresponding to effective leakage area of
77 in2 at 0.016 in. of water). The building volume is
12,000 ft3. The 97.5% design temperature is
–2°F, and design wind speed is 15 mph.
Solution: For a slab-on-grade two-story house with
a flue, Table 8 gives
Cs = 0.001478 (in. of water/°F)n and Cw = 0.001313 (in. of water/mph2)n. The house is
maintained at 68°F indoors. The building wind speed is determined by taking
the design wind speed Umet and applying by the wind
speed multiplier G from Table 7:
From Table 5, the shelter class for a
typical urban house is 4. Table 9 gives the shelter
factor for a two-story house with a flue and shelter class 4 as s = 0.64. The stack flow is calculated using Equation (42):
The wind flow is calculated using Equation (43):
Substituting Qs and Qw into Equation (40) gives
Q = 126 cfm = 7560 ft3/h. From Equation (3),
air change rate I is equal to Q
divided by the building volume:
Example 5.
Estimate the average infiltration over a one-week cold-weather period for a single-story
house with a crawlspace in Redmond, Washington. The house has a flow coefficient of c = 6890 cfm/(in. of water)n and a pressure exponent of n = 0.6 (corresponding to effective leakage area of 107
in2 at 0.016 in. of water). The building volume is
9000 ft3. During this period, the average indoor-to-outdoor
temperature difference is 29°F, and wind speed is 6 mph. The
house is electrically heated and has no flue.
Solution: For a single-story house with no flue,
Cs = 0.000891 (in. of water/°F)n. For a crawlspace, Cw = 0.001074 (in. of water/mph2)n. From Table 7, for a
one-story house, G = 0.48.
Table 9 gives shelter
factor s = 0.50 for a house with no flue and shelter class 4.
Stack flow is calculated using Equation (36):
Wind flow is calculated using Equation (37):
Substituting Qs and Qw into Equation (34) gives
Q = 48 cfm = 2880 ft3/h. From Equation (3),
air change rate I is equal to Q
divided by the building volume:
Example 6.
Estimate the infiltration for a three-story house in San Francisco, California. The house has
a flow coefficient of c = 8740 cfm/(in. of water)n and a pressure exponent of n = 0.67 (corresponding to effective leakage area of 155
in2 at 0.016 in. of water). The building volume is
14,200 ft3. The indoor/outdoor temperature difference is
9°F and wind speed is 10 mph. The house has a flue and a
crawlspace.
Solution: For a three-story house with a flue,
Cs = 0.001791 (in. of water/°F)n. For a crawlspace, Cw = 0.001295 (in. of water/mph2)n. From Table 7, for a
three-story house, G = 0.67.
The prevailing wind blows along the row of houses parallel to the street, so the house has a
shelter class of 5. Table 7 gives the
shelter factor for a three-story house with a flue and shelter class 5 as s = 0.43.
Substituting Qs and Qw in Equation (34) gives
Q = 83 cfm = 4960 ft3/h. The air changes
per hour are
Combining Residential Infiltration and
Mechanical Ventilation
Significant infiltration and mechanical ventilation often occur simultaneously in residences. The
pressure difference from Equation (17) can be used for each building leak, and the flow network
(including mechanical ventilation) for the building can be solved to find the airflow through all
the leaks while accounting for the effect of the mechanical ventilation. However, for simplified
models, natural infiltration and mechanical ventilation are usually determined separately and
require a superposition method to combine the flow rates.
Sherman (1992b) compared various procedures and derived a generalized superposition equation that
involves simple leakage distribution parameters. The result is always sub-additive. For small,
unbalanced fans, typically only half the mechanically introduced outdoor airflow contributes to the
total, but this fraction can be anywhere between 0 and 100%, depending on leakage distribution. When
the makeup air fan’s flow rate is large, infiltration may be ignored, because the building
becomes either neutrally or positively pressurized.
In special cases when the leakage distribution is known and highly skewed, it may be necessary to
work through the superposition method in more detail. For example, in a wind-dominated situation, a
makeup air fan has a much bigger effect than an exhaust fan on changing the total ventilation rate;
the same is true for houses with high NPLs in cold climates. For the general case, when details are
not known or can be assumed to be broad and typical, the following superposition gives good results:
Multicell models of airflow in buildings treat buildings as a series of interconnected zones and
assume that air within each zone can be characterized by a single temperature and contaminant
concentration, with the pressure only dependent on air density. Several such models have been
developed by Allard and Herrlin (1989), Dols and Polidoro (2020), Etheridge and Alexander (1980),
Feustel and Raynor-Hoosen (1990), Herrlin (1985), Liddament and Allen (1983), and Walton (1984,
1989). They are all based on a mass balance for each zone of the building. These mass balances are
used to solve for interior static pressures in the building by requiring that inflows and outflows
for each zone balance to zero. The user must provide information describing building envelope
leakage, values to account for wind pressure on the building envelope, temperatures for each zone,
and any mechanical ventilation airflow rates. Wind pressure coefficient data in the literature, air
leakage measurement results from the building or its components, and air leakage data from research
can be used as estimates. These models not only solve for whole-building and individual zone air
change rates, but also determine airflow rates and pressure differences between zones. These
interzone airflow rates are useful for predicting contaminant transport within buildings with well
mixed zones. Chapter 13 has more details on
multizone airflow and IAQ modeling.
ASHRAE members can access ASHRAE Journal articles and ASHRAE research project
final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase
by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.
ANSI. 2019. Standard for testing airtightness of
building, dwelling unit, and sleeping unit enclosures; airtightness of heating and cooling air
distribution systems; and airflow of mechanical ventilation systems. ANSI/RESNET/ICC Standard 380-2019.
ASHRAE. 2023. Control of infectious aerosols. Standard 241-2023.
ASHRAE. 2002. Measuring air-change effectiveness.
ANSI/ASHRAE Standard 129-97 (RA 2002).
ASHRAE. 2003. Risk management guidance for health,
safety and environmental security under extraordinary incidents. Report, Presidential Ad Hoc Committee for Building Health and Safety
Under Extraordinary Incidents.
ASHRAE. 2004. Air leakage performance for detached
single-family residential building. ANSI/ASHRAE Standard 119-1988
(RA 2004) (withdrawn).
ASHRAE. 2015. Ventilation and IAQ in low-rise
residential buildings. ASHRAE Guideline 24-2015.
ASHRAE. 2017. Ventilation of health care facilities.
ANSI/ASHRAE/ASHE Standard 170-2017.
ASHRAE. 2018. Energy-efficient design of low-rise
residential buildings. ANSI/ASHRAE/IES Standard 90.2-2018.
ASHRAE. 2019a. Standard 62.1-2019
user’s manual.
ASHRAE. 2019b. Standard 62.2-2019
user’s manual.
ASHRAE. 2021. Design guide for
natural ventilation.
ASHRAE. 2022a. Ventilation for acceptable indoor air
quality. ANSI/ASHRAE Standard 62.1-2022.
ASHRAE. 2022b. Ventilation and acceptable indoor air
quality in residential buildings. ANSI/ASHRAE Standard
62.2-2022.
ASHRAE. 2022c. Energy standard for buildings except
low-rise residential buildings. ANSI/ASHRAE Standard
90.1-2022.
ASHRAE. 2022d. ASHRAE design guide
for dedicated outdoor air systems, 2nd ed.
ASHRAE. 2023a. Thermal environmental conditions for
human occupancy. ASHRAE Standard 55-2023.
ASHRAE. 2023b. Standard for the design of
high-performance green buildings. ANSI/ASHRAE/IES/USGBC Standard
189.1-2023.
ASHRAE. 2023c. Control of infectious aerosols. ASHRAE
Standard 241-2023.
ACGIH. 2016. Industrial
ventilation: A manual of recommended practice, 29th ed. American Conference of
Governmental Industrial Hygienists, Cincinnati, OH.
Ackerman, M.Y., J.D. Dale, and D.J. Wilson. 2006.
Infiltration heat recovery, part 1: Field studies in an instrumented test building (RP-1169).
ASHRAE Transactions 112(2):597-608. Paper QC-06-056.
Allard, F., and M. Herrlin. 1989. Wind-induced
ventilation. ASHRAE Transactions 95(2):722-728. Paper VA-89-10-2.
Anis, W. 2001. The impact of airtightness on system
design. ASHRAE Journal 43(12):31-35.
Anis, W., and T. Brennan. 2014. Measuring airtightness
of mid and high-rise non-residential buildings. ASHRAE Research Project RP-1478, Final Report.
ASCE. 2022. Minimum design loads and associated criteria
for buildings and other structures. ASCE/SEI Standard 7-22.
Ask, A. 2003. Ventilation and air leakage. ASHRAE Journal 45(11):28-36.
ASTM. 2017a. Test method for determining air change in a
single zone by means of a tracer gas dilution. Standard
E741-11(2017). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2017b. Test methods for determining airtightness
of buildings using an orifice blower door. Standard E1827-11(2017).
American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2018a. Guide for assessing
depressurization-induced backdrafting and spillage from vented combustion appliances. Standard E1998-11(2018). American Society for Testing and Materials,
West Conshohocken, PA.
ASTM. 2018b. Standard test method for measuring the air
leakage rate of a large or multizone building. Standard E3158-2018.
American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2018c. Test method for field measurement of air
leakage through installed exterior windows and doors. Standard
E783-02(2018). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2019a. Test method for determining air leakage
rate by fan pressurization. Standard E779-19. American Society for
Testing and Materials, West Conshohocken, PA.
ASTM. 2019b. Test method for determining rate of air
leakage through exterior windows, curtain walls, and doors under specified pressure differences
across the specimen. Standard E283-19. American Society for Testing
and Materials, West Conshohocken, PA.
ASTM. 2022a. Practices for air leakage site detection in
building envelopes and air barrier systems. Standard E1186-2022.
American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2022b. Standard Test Method for Capture and
Containment Performance of Commercial Kitchen Exhaust Ventilation Systems. Standard F1704-12(2022). American Society for Testing and Materials,
West Conshohocken, PA.
Axley, J.W. 2001a. Application of
natural ventilation for U.S. commercial buildings—Climate suitability, design
strategies and methods, modeling studies. GCR-01-820, National Institute of Standards
and Technology, Gaithersburg, MD.
Axley, J.W. 2001b. Residential passive ventilation
systems: Evaluation and design. Technical Note 54. International
Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Bankvall, C.G. 1987. Air movements and thermal
performance of the building envelope. In Thermal insulation: Materials and
systems, pp. 124-131. F.J. Powell and S.L. Mathews, eds. American Society for Testing
and Materials, West Conshohocken, PA.
Batterman, S. 2017. Review and extension of
CO2-based methods to determine ventilation rates with application to school
classrooms. International Journal of Environmental Research and Public
Health 14(2):145.
Batterman, S., G. Hatzivasilis, and C. Jia. 2006.
Concentrations and emissions of gasoline and other vapors from residential vehicle garages.
Atmospheric Environment 40:1828-1844.
Berg-Munch, B., G. Clausen, and P.O. Fanger. 1986.
Ventilation requirements for the control of body odor in spaces occupied by women. Environmental International 12(1-4):195.
Berlad, A.L., N. Tutu, Y. Yeh, R. Jaung, R. Krajewski,
R. Hoppe and F. Salzano. 1978. Air intrusion effects on the performance of permeable insulation
systems. In Thermal insulation performance, STP 718, pp. 181-194. D.
McElroy and R. Tye, eds. American Society for Testing and Materials, West Conshohocken,
PA.
Berquist, J. and Banister, C., 2020. Feasibility of
Low-Cost CO2 Sensors for demand-controlled ventilation—Laboratory chamber
testing. ASHRAE Transactions 126(2).
Berquist, J., A. Wills, I. Macdonald, C. Banister, M.
Bartko, and M. Vuotari. 2020. The effects of leakage location on building air change rate in a
pressurized building. ASHRAE Transactions 126:409-418.
Berquist, J., N. Cassidy, M.F. Touchie, W.
O’Brien, and J.P. Fine. 2022. High-rise residential building ventilation in cold climates:
A review of ventilation system types and their impact on measured building performance. Indoor Air 32(11):e13158.
Berquist, J., Z. Xiong, B. Gunay, and M. Vuotari. 2023.
Investigation of the accuracy of BAS-grade CO2 sensors for measuring infiltration
rates. Journal of Building Engineering 80:108064.
Blomsterberg, A.K., and D.T. Harrje. 1979. Approaches to
evaluation of air infiltration energy losses in buildings. ASHRAE
Transactions 85(1):797. Paper PH-79-10-1.
Bohac, D.L., D.T. Harrje, and L.K. Norford. 1985.
Constant concentration infiltration measurement technique: An analysis of its accuracy and field
measurements, 176. Proceedings of the ASHRAE/DOE/BTECC Conference on the
Thermal Performance of the Exterior Envelopes of Buildings III, Clearwater Beach,
FL.
Bohac, D.L., D.T. Harrje, and G.S. Horner. 1987. Field
study comparisons of constant concentration and PFT infiltration measurements. Proceedings of the 8th IEA Conference of the Air Infiltration and Ventilation
Centre, Überlingen, Germany, pp. 47-62.
Bohac, D. L., M.J. Hewett, J. Fitzgerald, and D.
Grimsrud. 2007. Measured change in multifamily unit air leakage and airflow due to air sealing
and ventilation treatments. Buildings X: Thermal Performance of the
Exterior Envelopes of Whole Buildings, 1-13.
Bohac, D. L., M.J. Hewett, S.K. Hammond, and D.
Grimsrud. 2011. Secondhard smoke transfer and reductions by air sealing and ventilation in
multiunit buildings: PFT and nicotine verification. Indoor Air,
21:36-44.
Bohac, D.L.B. Schoenbauer, J. Fitzgerald, C. Harrington,
J. Garcia, and M. Modera. 2016. Using an aerosol sealant to reduce multifamily envelope leakage.
ACEEE Summer Study on Energy Efficiency in Buildings,
1–16.
Bohac, D.L., L. Sweeney, R. Davis, C. Olson, and G.
Nelson. 2020. Energy code field studies: Low-rise multifamily air leakage
testing. Centre for Energy and Environment.
Bradley, B. 1993. Implementation of the AIM-2
infiltration model in HOT-2000. Report, for Natural Resources
Canada.
Buchanan, C.R., and M.H. Sherman. 2000. A mathematical
model for infiltration heat recovery. Proceedings of the 21st IEA
Conference of the Air Infiltration and Ventilation Centre, The Hague, Netherlands.
Report LBNL-44294. Lawrence Berkeley National Laboratory, Berkeley,
CA.
Cain, W.S., B. Leaderer, R. Isseroff, L. Berglund, R.
Huey, and E. Lipsitt. 1983. Ventilation requirements in buildings—I. Control of occupancy
odor and tobacco smoke odor. Atmospheric Environment
17(6):1183-1197.
CDC. 2020. Evidence on the use of indoor air filtration
as an intervention for wildfire smoke pollutant exposure: a summary for health
departments.
CGSB. 2005. Depressurization test. CAN/CGSB Standard 51.71-2005. Canadian General Standards Board, Ottawa,
ON.
CGSB. 1996. Determination of the overall envelope
airtightness of buildings by the fan pressurization method using the building’s air
handling systems. Standard 149.15-96. Canadian General Standards
Board, Ottawa, ON.
CGSB. 2019. Determination of the airtightness of
building envelopes by the fan depressurization method. Standard
149.10-M86(2019). Canadian General Standards Board, Ottawa, ON.
Chan, W.R., W.W. Nazaroff. P.N. Price, M.D. Sohn, and
A.J. Gadgil. 2005. Analyzing a database of residential air leakage in the United States. Atmospheric Environment 39(19):3445-3455.
Charlesworth, P.S. 1988. Measurement of air exchange
rates. Chapter 2 in Air exchange rate and airtightness measurement
techniques—An applications guide. International Energy Agency Air Infiltration
and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Chastain, J.P. 1987. Pressure
gradients and the location of the neutral pressure axis for low-rise structures under pure
stack conditions. Unpublished M.S. thesis. University of Kentucky, Lexington.
Chastain, J.P., and D.G. Colliver. 1989. Influence of
temperature stratification on pressure differences resulting from the infiltration stack effect.
ASHRAE Transactions 95(1):256-268. Paper
3230.
Chastain, J.P., D.G. Colliver, and P.W. Winner, Jr.
1987. Computation of discharge coefficients for laminar flow in rectangular and circular
openings. ASHRAE Transactions 93(2):2259-2283. Paper NT-87-27-1.
CHBA. 1994. HOT2000 technical
manual. Canadian Home Builders Association, Ottawa, ON.
CIBSE. 2000. Testing buildings for air leakage. Standard TM-23. Chartered Institution of Building Services Engineers,
London.
CIBSE. 2005. Natural ventilation in
non-domestic buildings. Chartered Institution of Building Services Engineers,
London.
Claridge, D.E., and S. Bhattacharyya. 1990. The measured
impact of infiltration in a test cell. ASME Journal of Solar Energy
Engineering 112: 123-126.
Claridge, D.E., M. Krarti, and S. Bhattacharyya. 1988.
Preliminary measurements of the energy impact of infiltration in a test cell. Proceedings of the Fifth Annual Symposium on Improving Building Energy
Efficiency in Hot and Humid Climates, pp. 308-317.
Clark, J., B. Less, S. Dutton, I.Walker, and M. Sherman.
2019. Efficacy of occupancy-based smart ventilation control in residences in California and the
United States. Building and Environment (156):253-267.
Clark, J., I. Walker, and G. Rojas. 2018a. Measured
pollutant removal performance of range-integrated downdraft exhaust kitchen ventilation device.
Proceedings of Indoor Air 2018, Philadelphia, PA. International
Society for IAQ.
Clark, J., G. Rojas, and I. Walker. 2018b. Towards the
development of a standardized testing protocol for overhead island kitchen exhaust devices:
Procedures, measurements and paths forward. Building and Environment
142:301-311.
Claude-Alain, R., and F. Foradini. 2002. Simple and
cheap air change rate measurement using CO2 concentration decays. International Journal of Ventilation 1(1):39-44.
Cole, J.T., T.S. Zawacki, R.H. Elkins, J.W. Zimmer, and
R.A. Macriss. 1980. Application of a generalized model of air infiltration to existing homes.
ASHRAE Transactions 86(2):765. Paper
DV-80-09-2.
Collet, P.F. 1981. Continuous measurements of air
infiltration in occupied dwellings. Proceedings of the 2nd IEA Conference
of the Air Infiltration Centre, Stockholm, p. 147.
Colliver, D., W. Murphy, and W. Sun. 1994. Development
of a building component air leakage data base. ASHRAE RP-438. ASHRAE
Transactions (100):292-305.
CSA. 2023. Residential mechanical ventilation systems.
CAN/CSA-F326-M91 (R2023). Canadian Standards Association, Toronto.
Cummings, J.B., and J.J. Tooley, Jr. 1989. Infiltration
and pressure differences induced by forced air systems in Florida residences. ASHRAE Transactions 96(20):551-560. Paper
VA-89-05-4.
Cummings, J.B., J.J. Tooley, Jr., and R. Dunsmore. 1990.
Impacts of duct leakage on infiltration rates, space conditioning energy use and peak electrical
demand in Florida homes. Proceedings of the ACEEE Summer Study,
Pacific Grove, CA. American Council for an Energy-Efficient Economy, Washington, D.C.
Cutter. 1987. Air-to-air heat exchangers. In Energy design update. Cutter Information Corporation, Arlington,
MA.
Daish, N.C., G.Carrilho da Graca, P.F. Linden, and D.
Banks. 2016. Impact of aperture separation on wind-driven single-sided natural ventilation.
Building and Environment 108:122-134.
Delp, W.W. and B.C. Singer. 2012. Performance of U.S.
cooking exhaust hoods. Environmental Science and Technology
46(11):6167-6176.
Diamond, R.C., J.B. Dickinson, R.D. Lipschutz, B.
O’Regan, and B. Shohl. 1982. The house doctor’s manual. Report PUB-3017. Lawrence Berkeley National Laboratory, Berkeley,
CA.
Diamond, R.C., M.P. Modera, and H.E. Feustel. 1986.
Ventilation and occupant behaviour in two apartment buildings. Proceedings
of the 7th IEA Conference of the Air Infiltration and Ventilation Centre,
Stratford-upon-Avon, U.K. Report LBL-21862. Lawrence Berkeley
National Laboratory, Berkeley, CA.
Dickerhoff, D.J., D.T. Grimsrud, and R.D. Lipschutz.
1982. Component leakage testing in residential buildings. Proceedings of
the American Council for an Energy-Efficient Economy, 1982 Summer Study, Santa Cruz,
CA. Report LBL 14735. Lawrence Berkeley National Laboratory,
Berkeley, CA.
Dietz, R.N., R.W. Goodrich, E.A. Cote, and R.F. Wieser.
1986. Detailed description and performance of a passive perfluorocarbon tracer system for
building ventilation and air exchange measurement. In Measured air leakage
of buildings, STP 904, p. 203. H.R. Trechsel and P.L. Lagus, eds. American Society
for Testing and Materials, West Conshohocken, PA.
Dols, W., and Polidoro, B. 2020. CONTAM User Guide and
Program Documentation Version 3.4, Technical Note (NIST TN), National Institute of Standards and
Technology, Gaithersburg, MD. doi.org/10.6028/NIST .TN.1887r1.
Dols, W. S., L. Wang, S. J. Emmerich, and B. J.
Polidoro. 2014. Development and application of an updated whole-building coupled thermal,
airflow and contaminant transport simulation program (TRNSYS/CONTAM). Journal of Building Performance Simulation: 1-21.
D’Ottavio, T.W., G.I. Senum, and R.N. Dietz. 1988.
Error analysis techniques for perfluorocarbon tracer derived multizone ventilation rates. Building and Environment 23(40).
Elmroth, A., and P. Levin. 1983. Air infiltration control in housing. International Energy Agency Air
Infiltration Centre, Sint-Stevens-Woluwe, Belgium.
Emmerich, S.J. 2006. Simulated performance of natural
and hybrid ventilation systems in an office building. HVAC&R
Research (now Science and Technology for the Built
Environment) 12(4):975-1004.
Emmerich, S.J., and A.K Persily. 2001. State-of-the-art
review of CO2 demand controlled ventilation technology and application. NISTIR Report 6729. National Institute of Standards and Technology,
Washington, D.C.
Emmerich, S.J., J.E. Gorfain, and C. Howard-Reed. 2003.
Air and pollutant transport from attached garages to residential living spaces—Literature
review and field test. International Journal of Ventilation
2(3):265-276.
Emmerich, S.J., and A.K. Persily. 2005. Airtightness of
commercial buildings in the U.S. Proceedings of the 26th IEA Conference of
the Air Infiltration and Ventilation Centre, Brussels, pp 65-70.
Enai, M., C.Y. Shaw, and J.T. Reardon. 1990. On the
multiple tracer gas techniques for measuring interzonal airflows in buildings. Air Infiltration and Ventilation Centre 4(3370).
Energy Resource Center. 1982. How
to house doctor. University of Illinois, Chicago.
Etheridge, D.W. 1977. Crack flow equations and scale
effect. Building and Environment 12:181.
Etheridge, D.W., and D.K. Alexander. 1980. The British
gas multi-cell model for calculating ventilation. ASHRAE
Transactions 86(2):808. Paper DV-80-09-4.
Etheridge, D.W., and J.A. Nolan. 1979. Ventilation
measurements at model scale in a turbulent flow. Building and
Environment 14(1):53.
Eyre, D., and D. Jennings. 1983. Air-vapour barriers—A general perspective and guidelines for
installation. Energy, Mines, and Resources Canada, Ottawa, ON.
Farrington, R., D. Martin, and R. Anderson. 1990. A
comparison of displacement efficiency, decay time constant, and age of air for isothermal flow
in an imperfectly mixed enclosure. Proceedings of the ACEEE 1990 Summer
Study on Energy Efficiency in Buildings, pp. 4.35-4.43. American Council for an
Energy-Efficient Economy, Washington, D.C.
Fennell, H.C., and J. Haehnel. 2005. Setting
airtightness standards. ASHRAE Journal 47(9):26-31.
Feustel, H.E., and A. Raynor-Hoosen, eds. 1990.
Fundamentals of the multizone air flow model—COMIS. Technical
Note 29. International Energy Agency Air Infiltration and Ventilation Centre,
Sint-Stevens-Woluwe, Belgium.
FGI. 2014. Guidelines for design
and construction of hospital and healthcare facilities. American Institute of
Architects, Facilities Guidelines Institute, and U.S. Department of Health and Human Services,
Washington, D.C.
Finch, G. 2007. The performance of
rainscreen walls in coastal British Columbia. M.A.Sc. thesis. University of Waterloo,
Waterloo, ON.
Fine, J.P., C.H. Lozinsky, and M.F. Touchie. 2022.
Reducing indirect inter-suite air flow in high-rise multi-unit residential buildings: A
parametric study using a CONTAM model. ASHRAE 2022 Annual
Conference, Toronto, ON.
Fisk, W.J., R.J. Prill, and O. Steppanen. 1989. A
multi-tracer technique for studying rates of ventilation, air distribution patterns and air
exchange efficiencies. Proceedings of Conference on Building
Systems—Room Air and Air Contaminant Distribution, pp. 237-240. ASHRAE.
Fortmann, R.C., N.L. Nagda, and H.E. Rector. 1990.
Comparison of methods for the measurement of air change rates and interzonal airflows to two
test residences. In Air change rate and airtightness in buildings,
STP 1067, pp. 104-118. M.H. Sherman, ed. American Society of Testing and Materials, West
Conshohocken, PA.
Foster, M.P., and M.J. Down. 1987. Ventilation of
livestock buildings by natural convection. Journal of Agricultural
Engineering Research 37:1.
Fritz, R. L. 1989. A realistic evaluation of kitchen
ventilation hood design. ASHRAE Transactions 95(1).
Fugler, D. 2004. Garage performance testing. CMHC Research Highlights (April). Canada Mortgage and Housing
Corporation, Ottawa, ON.
Giesbrecht, P., and G. Proskiw. 1986. An evaluation of
the effectiveness of air leakage sealing. In Measured air leakage of
buildings, STP 904, p. 312. H.R. Trechsel and P.L. Lagus, eds. American Society for
Testing and Materials, West Conshohocken, PA.
Grieve, P.W. 1989. Measuring
ventilation using tracer-gases. Brüel and Kjær, Denmark.
Grimsrud, D.T., M.H. Sherman, R.C. Diamond, P.E. Condon,
and A.H. Rosenfeld. 1979. Infiltration-pressurization correlations: Detailed measurements in a
California house. ASHRAE Transactions 85(1):851. Paper PH-79-10-5.
Grimsrud, J.E., D.T. Sherman, M.H. Janssen, A.N.
Pearman, and D.T. Harrje. 1979. An intercomparison of tracer gases used for air infiltration
measurements. ASHRAE Transactions 86.
Grot, R.A., and A.K. Persily. 1986. Measured air
infiltration and ventilation rates in eight large office buildings. In Measured air leakage of buildings, STP 904, p. 151. H.R. Trechsel and
P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
GSA. 2021. P100 Facilities
standards for the public buildings service. PBS-P100. U.S. General Services
Administration, Washington, D.C.
Gulay, B.W., C.D. Stewart, and G.J. Foley. 1993. Field
investigation survey of airtightness, air movement and IAQ in high rise apartment buildings
Summary Report. Ottawa, ON.
Guyot, G., I.S. Walker, M.H. Sherman, and J.D. Clark.
2017. Residential smart ventilation: A review. LBNL Report 2001056,
Lawrence Berkeley National Laboratory, Berkeley, CA.
Hamlin, T., and W. Pushka. 1994. Predicted and measured
air change rates in houses with predictions of occupant IAQ comfort. Proceedings of the 15th IEA Air Infiltration and Ventilation Centre
Conference, Buxton, U.K., pp. 771-775.
Harriman, L., B. Stephens, and T. Brennan. 2019. New
Guidance for Residential Air Cleaners. ASHRAE Journal. September
Issue.
Harrje, D.T., and G.J. Born. 1982. Cataloguing air
leakage components in houses. Proceedings of the ACEEE 1982 Summer
Study, Santa Cruz, CA. American Council for an Energy-Efficient Economy, Washington,
D.C.
Harrje, D.T., and T.A. Mills, Jr. 1980. Air infiltration
reduction through retrofitting. In Building air change rate and
infiltration measurements. STP 719, p. 89. C.M. Hunt, J.C. King, and H.R. Trechsel,
eds. American Society for Testing and Materials, West Conshohocken, PA.
Harrje, D.T., G.S. Dutt, and J. Beyea. 1979. Locating
and eliminating obscure but major energy losses in residential housing. ASHRAE Transactions 85(2):521. Paper
DE-79-03-1.
Harrje, D.T., R.A. Grot, and D.T. Grimsrud. 1981. Air
infiltration site measurement techniques. Proceedings of the 2nd IEA
Conference of the Air Infiltration Centre, p. 113. Stockholm, Sweden.
Harrje, D.T., G.S. Dutt, D.L. Bohac, and K.J. Gadsby.
1985. Documenting air movements and infiltration in multicell buildings using various tracer-gas
techniques. ASHRAE Transactions 91(2):2012-2027. Paper HI-85-40-3.
Harrje, D.T., R.N. Dietz, M. Sherman, D.L. Bohac, T.W.
D’Ottavio, and D.J. Dickerhoff. 1990. Tracer gas measurement systems compared in a
multifamily building. In Air change rate and airtightness in
buildings, STP 1067, pp. 5-12. M.H. Sherman, ed. American Society for Testing and
Materials, West Conshohocken, PA.
Heiselberg, P. 2002. Principles of hybrid ventilation.
Final Report, International Energy Agency Energy Conservation in
Buildings and Community Systems, Annex 35. Hybrid Ventilation Centre, Aalborg University,
Denmark.
Herrlin, M.K. 1985. MOVECOMP: A
static-multicell-airflow-model. ASHRAE Transactions 91(2B):1989.
Paper HI-85-40-1.
Hong, T., and W.J. Fisk. 2010. Assessment of energy
savings potential from the use of demand controlled ventilation in general office spaces in
California. Building Simulation 3:117-124.
Honma, H. 1975. Ventilation of
dwellings and its disturbances. Faibo Grafiska, Stockholm, Sweden.
Hopkins, L.P., and B. Hansford. 1974. Air flow through
cracks. Building Service Engineer 42(September):123.
Hunt, C.M. 1980. Air infiltration: A review of some
existing measurement techniques and data. In Building air change rate and
infiltration measurements, STP 719, p. 3. C.M. Hunt, J.C. King, and H.R. Trechsel,
eds. American Society for Testing and Materials, West Conshohocken, PA.
Hutcheon, N.B., and Handegord, G.O.P. 1995. Building science for a cold climate. National Research Council of
Canada.
ICC. 2021. International energy
conservation code® (IECC®). International Code Council, Washington,
D.C.
ICC. 2015. ICC/ASHRAE 700-2015
National Green Building Standard. ANSI, NAHB, ASHRAE, International Code Council,
Washington, D.C.
ISO. 2015. Thermal performance of
buildings—Determination of air permeability of buildings—Fan pressurization method.
Standard 9972-2015. International Organization for Standardization,
Geneva.
Iwashita, G., K. Kimura., et al. 1989. Pilot study on
addition of olf units for perceived air pollution sources. Proceedings of
the SHASE Annual Meeting, pp. 3221-3324. Society of Heating, Air-Conditioning and
Sanitary Engineers of Japan, Tokyo.
Jacobson, D.I., G.S. Dutt, and R.H. Socolow. 1986.
Pressurization testing, infiltration reduction, and energy savings. In Measured air leakage of buildings, STP 904, p. 265. H.R. Trechsel and
P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Janu, G.J., J.D. Wegner, and C.G. Nesler. 1995. Outdoor
airflow control for VAV systems. ASHRAE Journal 37(4):62-68.
Jo, J.H., J.H. Lim, S.Y. Song, M.S. Yeo, and K.W. Kim.
2007. Characteristics of pressure distribution and solution to the problems caused by stack
effect in high-rise residential buildings. Building and Environment.
42:263-277.
Jo J.H., H.T. Seok, M.S. Yeo, and K.W. Kim. 2009.
Simplified prediction method of stack-induced pressure distribution in high-rise residential
buildings. Journal of Asian Architecture and Building Engineering.
8(1):283-290.
Johnson, T., and T. Long. 2005. Determining the
frequency of open windows in residences: A pilot study in Durham, North Carolina during varying
temperature conditions. Journal of Exposure Analysis and Environmental
Epidemiology 15(4):329-349.
Jones, D. 2022. Testing tales from the Northwest. ABAA Building Enclosure Conference, Reston, VA, May 10 – 11,
2022.
Jones, D., B. Brown, T. Thompson, and G. Finch. 2014.
Building enclosure airtightness testing in Washington state—Lessons learned about air
barrier systems and large building testing procedures. Presented at ASHRAE Annual
Conference.
Judkoff, R., J.D. Balcomb, C.E. Handcock, G. Barker, and
K. Subbarao. 1997. Side-by-side thermal tests of modular offices: A validation study of the STEM
method. Report. National Renewable Energy Laboratory, Golden,
CO.
Jump, D.A., I.S. Walker, and M.P. Modera. 1996. Field
measurements of efficiency and duct retrofit effectiveness in residential forced air
distribution systems. Proceedings of the 1996 ACEEE Summer Study,
pp. 1.147-1.156. American Council for an Energy-Efficient Economy, Washington, D.C.
Kaschuba-Holtgrave, A., A. Rohr, S. Rolfsmeier, and O.
Solcher. 2018. Individual unit and guard-zone airtightness tests of apartment buildings. Journal of Building Physics 1-37.
Khemet, B. ,and R. Richman. 2018. A univariate and
multiple linear regression analysis on a national fan (de)pressurization testing database to
predict airtightness in houses. Building and Environment
146:88-97.
Kiel, D.E., and D.J. Wilson. 1986. Gravity driven
airflows through open doors, 15.1. Proceedings of the 7th IEA Conference of
the Air Infiltration and Ventilation Centre, Stratford-upon-Avon, U.K.
Klote, J.H., J.A. Milke, P.G. Turnbull, A. Kashef, and
M.J. Ferreira. 2012. Handbook of smoke control engineering.
ASHRAE.
Kohonen, R., T. Ojanen, and M. Virtanen. 1987. Thermal
coupling of leakage flows and heating load of buildings. Proceedings of the
8th IEA Air Infiltration and Ventilation Centre Conference, Überlingen, Germany,
pp. 10.1-10.22.
Kono, J., J. Gieselman, M.K. McNulty, and B. Abramson.
2022. Increasing ventilation in 1980s high-rise commercial office buildings. ASHRAE Journal 64(11).
Kreith, F., and R. Eisenstadt. 1957. Pressure drop and
flow characteristics of short capillary tubes at low Reynolds numbers. ASME
Transactions, pp. 1070-1078.
Kronvall, J. 1980. Correlating
pressurization and infiltration rate data—Tests of an heuristic model. Lund
Institute of Technology, Division of Building Technology, Lund, Sweden.
Kuehn, T.H., J. Ramsey, H. Han, M. Perkovich, and S.
Yuossef. 1989. A study of kitchen range exhaust systems. ASHRAE
Transactions (95)1: 744-752.
Kumar, R., A.D. Ireson, and H.W. Orr. 1979. An automated
air infiltration measuring system using SF6 tracer gas in constant concentration and decay
methods. ASHRAE Transactions 85(2):385. Paper DE-2553.
Lagus, P.L. 1989. Tracer measurement instrumentation
suitable for infiltration, air leakage, and airflow pattern characterization. Proceedings of the Conference on Building Systems—Room Air and Air
Contaminant Distribution, pp. 97-102. ASHRAE.
Lagus, P., and A.K. Persily. 1985. A review of
tracer-gas techniques for measuring airflows in buildings. ASHRAE
Transactions 91(2B):1075. Paper HI-85-2-1.
Lau, J., X. Lin, and G. Yuill. 2014. CO2-based demand controlled ventilation for multiple zone HVAC
systems. ASHRAE RP-1547.
Lecompte, J.G.N. 1987. The influence of natural
convection in an insulated cavity on thermal performance of a wall. In Insulation materials, testing, and applications. American Society for
Testing and Materials, West Conshohocken, PA.
Less, B.D. and I.S. Walker. 2016. Smart ventilation
control of indoor humidity in high performance homes in humid U.S. climates. Proceedings of ASHRAE/DOE/BTECC Thermal Performance of the Exterior Envelopes
of Buildings Conference XIII, Clearwater Beach, FL. ASHRAE, Atlanta, GA. LBNL
1006980.
Less, B., I. S. Walker, and Y. Tang. 2014. Development
of an outdoor temperature-based control algorithm for residential mechanical ventilation
control.
LBNL Report 6936E. Lawrence
Berkeley National Laboratory: Berkeley, CA.
Less, B., S. Dutton, I. Walker, M. Sherman, and J.
Clark. 2019. Energy savings with outdoor temperature-based smart ventilation control strategies
in advanced California homes. Energy and Buildings
194:317-327.
Levin, P. 1988. Air leakage between apartments. 9th AIVC Conference: Air Movement and Ventilation Within Buildings.
pg. 251–263.
Li, Y., and A. Delsante. 1996. Derivation of capture
efficiency of kitchen range hoods in a confined space. Building and
Environment 31(5):461-468.
Li, Y., A. Delsante, and J. Symons. 1997. Residential
kitchen range hoods—Buoyancy-capture principle and capture efficiency revisited. Indoor Air 7(3): 151-157.
Li, Y., and P. Heiselberg. 2003. Analysis methods for
natural and hybrid ventilation—A critical literature review and recent developments. International Journal of Ventilation 1(4):3-20.
Liddament, M.W. 1988. The calculation of wind effect on
ventilation. ASHRAE Transactions 94(2):1645-1660. Paper OT-88-13-1.
Liddament, M., and C. Allen. 1983. The validation and
comparison of mathematical models of air infiltration. Technical
Note 11. International Energy Agency Air Infiltration and Ventilation Centre,
Sint-Stevens-Woluwe, Belgium.
Lim, K., and C. Lee. 2008. A numerical study on the
characteristics of flow field, temperature and concentration distribution according to changing
the shape of separation plate of kitchen hood system. Energy and
Buildings 40(2):175-184.
Liu, M., and D.E. Claridge. 1992a. The measured energy
impact of infiltration under dynamic conditions. Proceedings of the 8th
Symposium on Improving Building Systems in Hot and Humid Climates, Dallas.
Liu, M., and D.E. Claridge. 1992b. The measured energy
impact of infiltration in a test cell. Proceedings of the 8th Symposium on
Improving Building Systems in Hot and Humid Climates, Dallas.
Liu, M., and D.E. Claridge. 1992c. The energy impact of
combined solar radiation/infiltration/conduction effects in walls and attics. Proceedings of the Thermal Performance of Exterior Envelopes of Buildings,
5th ASHRAE/DOE/BTECC Conference, Clearwater Beach, FL.
Liu, M., and D.E. Claridge. 1995. Experimental methods
for identifying infiltration heat recovery in building. Proceedings of the
Thermal Performance of Exterior Envelopes of Buildings, 6th ASHRAE/DOE/BTECC
Conference, Clearwater Beach, FL.
Lo, J., D. Banks, and A. Novoselac. 2013. Combined wind
tunnel and CFD analysis for indoor airflow prediction of wind-driven cross ventilation. Building and Environment 60:12-23.
Love, J.A. 1990. Airtightness survey of row houses in
Calgary, Alberta. In Air Change Rate and Airtightness in Buildings, ASTM
STP 1067, Philadelphia, PA, 194-210.
Lozinsky, C.H. and M.F. Touchie. 2020. Inter-zonal
airflow in multi-unit residential buildings: A review of the magnitude and interaction of
driving forces, measurement techniques and magnitudes, and its impact on building performance.
Indoor Air 30:1083-1108.
Lozinsky, C.H. and M.F. Touchie. 2021. Suite-level air
tightness and compartmentalization in multi-unit residential buildings: How do we achieve our
intended goals? Building and Environment 192:107600.
Lozinsky, C.H., H. Stopps, H., and M.F Touchie. 2023.
In-situ performance of a pressurized corridor ventilation system: a long-term study in a
high-rise multi-unit residential building. Journal of Building
Engineering, 70(1):106320.
Lozinsky, C.H. and M.F. Touchie. 2023a. Quantifying
suite-level airtightness in newly constructed multi-unit residential buildings using guarded
suite-level air leakage testing. Building and Environment.
236:110273.
Lozinsky, C.H. and M.F. Touchie. 2024. Size matters (at
least for interior air flow pathways): the indoor air quality and energy implications of
compartmentalization in multi-unit residential buildings. Building and
Environment. 253:111275.
Madsen, U., N. O. Breum, and P. V. Nielsen. 1994. Local
exhaust ventilation-a numerical and experimental study of capture efficiency. Building and Environment 29(3):319-323.
Marbek Resource Consultants. 1984. Air sealing homes for energy conservation. Energy, Mines and Resources
Canada, Buildings Energy Technology Transfer Program, Ottawa, ON.
Martin, E., D. Parker, and K. Fenaughty. 2018. Energy
savings and comfort enhancement potential of a smart residential ventilation control strategy.
Proceedings of the ACEEE 2018 Summer Study on Energy Efficiency of
Buildings, Pacific Grove, CA.
McDowell, T.P., S. Emmerich, J.W. Thornton, and G.
Walton. 2003. Integration of airflow and energy simulation using CONTAM and TRNSYS. ASHRAE Transactions 109(2):757-770. Paper
KC-03-10-2.
McNulty, M.K., J. Kono, and B. Abramson. 2022. From
guidance to implementation: Applying ASHRAE Epidemic Task Force building readiness strategies in
95 commercial office buildings. ASHRAE Transactions
128(1):393-401.
McWilliams, J., and M. Sherman. 2005. Review of
literature related to residential ventilation requirements. Paper
LBNL-57236. Lawrence Berkeley National Laboratory, Berkeley, CA.
Mélois, A. B., B. Moujalled, G. Guyot, and V.
Leprince. 2019. Improving building envelope knowledge from analysis of 219,000 certified on-site
air leakage measurements in France. Building and Environment.
159:106145.
Merrin, Z., Francisco, P. W., Bohac, D., Quinnell, J.
A., & Olson, C. 2018. An evaluation of strategies to reduce transport of pollutants from
garages to homes. Science and Technology for the Built Environment
24(2):198-208.
Modera, M.P. 1989. Residential duct system leakage:
Magnitude, impacts, and potential for reduction. ASHRAE Transactions
96(2):561-569. Paper VA-89-05-5.
Modera, M.P., and D.J. Wilson. 1990. The effects of wind
on residential building leakage measurements. In Air change rate and
airtightness in buildings, STP 1067, pp. 132-145. M.H. Sherman, ed. Lawrence Berkeley
National Laboratory, Berkeley, CA. Report LBL-24195.
Modera, M.P., D. Dickerhoff, R. Jansky, and B. Smith.
1991. Improving the energy efficiency of residential air distribution systems in California.
Report LBL-30866. Lawrence Berkeley National Laboratory, Berkeley,
CA.
Mumma, S.A. 2004. Transient occupancy ventilation by
monitoring CO2. ASHRAE IAQ Applications, Winter
2004.
Mumma, S.A., and K.M. Shank. 2001. Achieving dry outside
air in an energy efficient manner. ASHRAE Transactions
107(1):553-561. Paper AT-01-07-2.
Mumma, S.A., and Y.M. Wong. 1990. Analytical evaluation
of outdoor airflow rate variation vs. supply airflow rate variation in VAV systems when the
outside air damper position is fixed. ASHRAE Transactions
90(1):1197-1208.
Murphy, W.E., D.G. Colliver, and L.R. Piercy. 1991.
Repeatability and reproducibility of fan pressurization devices in measuring building air
leakage. ASHRAE Transactions 97(2):885-895. Paper IN-91-12-1.
NRCC. 2020. National Building Code
of Canada. National Research Council of Canada, Ottawa, ON.
Nelson, B.D., D.A. Robinson, and G.D. Nelson. 1985.
Designing the envelope—Guidelines for buildings (SP-49). Proceedings
of the ASHRAE/DOE/BTECC Conference—Thermal Performance of the Exterior Envelopes of
Buildings III, Florida, pp. 1117-1122.
Ng, L.C., A. Musser, A.K. Persily, and S.J. Emmerich.
2012. Airflow and IAQ models of DOE reference commercial buildings. Technical Note 1734. National Institute of Standards and Technology,
Gaithersburg, MD.
Ng, L.C., A.K. Persily, and S.J. Emmerich. 2015.
Improving infiltration modeling in commercial building energy models. Energy and Buildings 88:316-323.
Ng, L.C., N.O. Quiles, W.S. Dols, and S.J. Emmerich,
2018. Weather correlations to calculate infiltration rates for US commercial building energy
models. Building and Environment 127:47-57.
Nylund, P.O. 1980. Infiltration and ventilation. Report D22:1980. Swedish Council for Building Research,
Stockholm.
O’Neill, Z.D., Y. Li, H.C. Cheng, X. Zhou, and
S.T. Taylor. 2020. Energy savings and ventilation performance from CO2-based demand
controlled ventilation: Simulation results from ASHRAE RP-1747. ASHRAE RP-1747, Report.
Orme, M. 1999. Applicable models for air infiltration
and ventilation calculations. Technical Note 51. International
Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Ormerod, R. 1983. Nuclear shelters:
A guide to design. Architectural Press, London.
Palmiter, L., and T. Bond. 1994. Modeled and measured
infiltration II—A detailed case study of three homes. Report
TR 102511. Electric Power Research Institute, Palo Alto, CA.
Palmiter, L., and I. Brown. 1989. The Northwest
residential infiltration survey: Description and summary of results. Proceedings of the ASHRAE/DOE/BTECC/CIBSE Conference—Thermal
Performance of the Exterior Envelopes of Buildings IV, Florida, pp. 445-457.
Pan, W. 2010. Relationships between air-tightness and
its influencing factors of post-2006 new-build dwellings in the UK. Building and Environment. 45:2387–2399.
Parekh, A., K. Ruest, and M. Jacobs. 1991. Comparison of
airtightness, IAQ and power consumption before and after air-sealing of high-rise residential
buildings. Proceedings of the 12th IEA Conference of the Air Infiltration
and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Parker, G.B., M. McSorley, and J. Harris. 1990. The
Northwest residential infiltration survey: A field study of ventilation in new houses in the
Pacific North-west. In Air change rate and airtightness in
buildings, STP 1067, pp. 93-103. M.H. Sherman, ed. American Society for Testing and
Materials, West Conshohocken, PA.
Persily, A.K. 1986. Measurements of air infiltration and
airtightness in passive solar homes. In Measured air leakage of
buildings, STP 904, p. 46. H.R. Trechsel and P.L. Lagus, eds. American Society for
Testing and Materials, West Conshohocken, PA.
Persily, A.K. 1988. Tracer gas techniques for studying
building air exchange. Report NBSIR 88-3708. National Institute of
Standards and Technology, Gaithersburg, MD.
Persily, A.K. 2004. Building ventilation and
pressurization as a security tool. ASHRAE Journal 46
(9):18-24.
Persily, A.K., and J. Axley. 1990. Measuring airflow
rates with pulse tracer techniques. In Air change rate and airtightness in
buildings, pp. 31-51. STP 1067. M.H. Sherman, ed. American Society for Testing and
Materials, West Conshohocken, PA.
Persily, A.K. and L de Jonge. 2017. Carbon dioxide
generation rates for building occupants. Indoor Air
27(5):868-879.
Persily, A.K., and R.A. Grot. 1985a. The airtightness of
office building envelopes. Proceedings of the ASHRAE/DOE/BTECC Conference
on the Thermal Performance of the Exterior Envelopes of Buildings III, Clearwater
Beach, FL, p. 125.
Persily, A.K., and R.A. Grot. 1985b. Accuracy in
pressurization data analysis. ASHRAE Transactions 91(2B):105. Paper HI-85-03-2.
Persily, A.K., and R.A. Grot. 1986. Pressurization
testing of federal buildings. In Measured air leakage of buildings,
STP 904, p. 184. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials,
West Conshohocken, PA.
Persily, A.K., and G.T. Linteris. 1983. A comparison of
measured and predicted infiltration rates. ASHRAE Transactions
89(2):183. Paper DC-83-04-1. Persily, A.K., J. Gorfain, and G.
Brunner. 2005. Ventilation design and performance in U.S. office buildings. ASHRAE Journal 47(4):30-35.
Persily, A.K., R.E. Chapman, S. Emmerich, W.S. Dols, H.
Davis, P. Lavappa, and A. Rushing. 2007. Building retrofits for increased protection against
airborne chemical and biological releases. NISTIR Report 7379.
National Institute of Standards and Technology, Gaithersburg, MD.
Persily, A., and L. de Jonge. 2017. Carbon dioxide
generation rates for building occupants. Indoor Air 27(5):868–79.
Powell, F., M. Krarti, and A. Tuluca. 1989. Air movement
influence on the effective thermal resistance of porous insulations: A literature survey. Journal of Thermal Insulation 12:239-251.
Price, P.N., and M.H. Sherman. 2006. Ventilation
behavior and household characteristics in new California houses. Report LBNL-59620.
Proskiw G., and B. Phillips. 2008. An examination of air
pressure and air movement patterns in multi-unit residential buildings. Building Enclosure Science and Technology (BEST) Conference.
Minneapolis, MN.
RDH. 2013. Air leakage control in
multi-unit residential buildings. Canada Mortgage and Housing Corporation.
Reardon, J.T., and C.Y. Shaw. 1997. Evaluation of five
simple ventilation strategies suitable for houses without forced-air heating. ASHRAE Transactions 103(1):731-744. Paper
PH-97-08-5.
Reeves, G., M.F. McBride, and C.F. Sepsy. 1979. Air
infiltration model for residences. ASHRAE Transactions 85(1):667.
Paper PH-79-07A-1.
Ricketts, L. 2014. A field study of airflow in a
high-rise multi-unit residential building. M.A.Sc. Thesis, University of Waterloo, Waterloo,
ON.
Riley, M. 1990. IAQ and energy conservation: The R-2000
home program experience. Proceedings of Indoor Air ’90: International
Conference on IAQ and Climate, Ottawa, vol. 5, p. 143.
Rim, D. H., A. K. Persily, and L. L. Wallace. 2011.
Reduction of exposure to ultrafine particles by kitchen exhaust fans of varying flow rates.
Presented at 12th International Conference on IAQ and Climate, International Society of IAQ and
Climate, Austin, TX.
Rim, D., L. Wallace, S. Nabinger, and A. Persily. 2012.
Reduction of exposure to ultrafine particles by kitchen exhaust hoods: The effects of exhaust
flow rates, particle size, and burner position. Science of the Total
Environment 432:350-356.
Robison, P.E., and L.A. Lambert. 1989. Field
investigation of residential infiltration and heating duct leakage. ASHRAE
Transactions 95(2):542-550. Paper VA-89-05-3.
Rock, B.A. 1992. Characterization
of transient pollutant transport, dilution, and removal for the study of IAQ. Ph.D.
dissertation, University of Colorado at Boulder. University Microfilms International.
Rock, B.A. 2005. A user-friendly model and coefficients
for slab-on-grade load and energy calculations. ASHRAE Transactions
111(2):122-136. Paper 4795.
Rudd, A.F. 1998. Design/sizing methodology and economic
evaluation of central-fan-integrated supply ventilation systems. ACEEE 1998
Summer Study on Energy Efficiency in Buildings. 23-28 August, Pacific Grove, CA.
American Council for an Energy Efficient Economy, Washington, D.C.
Russell, M., M. Sherman, and A. Rudd. 2005. Review of
residential ventilation technologies. Paper LBNL-576. Lawrence
Berkeley National Laboratory, Berkeley, CA.
Sandberg, M.H. 1981. What is ventilation efficiency?
Building and Environment 16:123-135.
Seppanen, O.A., W.J. Fisk and M.J. Mendell. 1999.
Association of ventilation rates and CO2 concentrations with health and other
responses in commercial and institutional buildings. Indoor Air
9(4):226-252.
Shaw, C.Y. 1980. Methods for conducting small-scale
pressurization tests and air leakage data of multi-storey apartment buildings. ASHRAE Transactions 86(1):241-250.
Shaw, C.Y. 1981. A correlation between air infiltration
and air tightness for a house in a developed residential area. ASHRAE
Transactions 87(2):333. Paper CI-2655.
Shaw, C.Y., and W.C. Brown. 1982. Effect of a gas
furnace chimney on the air leakage characteristic of a two-story detached house. Proceedings of the 3rd IEA Conference of the Air Infiltration Centre,
London.
Shaw, C.Y., R.J. Magee, and J. Rousseau. 1991. Overall
and component airtightness values of a five-story apartment building. ASHRAE Transactions 97(2):347-353.
Sherman, M.H. 1986. Infiltration degree-days: A
statistic for quantifying infiltration-related climate. ASHRAE
Transactions 92(2):161-181. Paper 2986. Sherman, M.H.
1987. Estimation of infiltration from leakage and climate indications. Energy and Buildings 10(1):81.
Sherman, M.H. 1989a. Uncertainty in airflow calculations
using tracer gas measurements. Building and Environment
24(4):347-354.
Sherman, M.H. 1989b. On the estimation of multizone
ventilation rates from tracer gas measurements. Building and
Environment 24(4):355-362. Sherman, M.H. 1990. Tracer gas techniques for measuring
ventilation in a single zone. Building and Environment
25(4):365-374.
Sherman, M.H. 1991. Single-zone stack-dominated
infiltration modeling. Proceedings of the 12th IEA Conference of the Air
Infiltration and Ventilation Centre, Ottawa, ON, pp. 297-314.
Sherman, M.H. 1992a. A power law formulation of laminar
flow in short pipes. Journal of Fluids Engineering 114:601-605.
Report LBL-29414, Lawrence Berkeley National Laboratory, Berkeley,
CA.
Sherman, M.H. 1992b. Superposition in infiltration
modeling. Indoor Air 2:101-114.
Sherman, M.H., and D. Dickerhoff. 1989. Description of
the LBL multitracer measurement system. Proceedings of the
ASHRAE/DOE/BTECC/CIBSE Conference—Thermal Performance of the Exterior Envelopes of
Buildings IV, pp. 417-432.
Sherman, M.H., and D.T. Grimsrud. 1980.
Infiltration-pressurization correlation: Simplified physical modeling. ASHRAE Transactions 86(2): 778. Paper
DV-80-09-3.
Sherman, M.H., and N. Matson. 1997. Residential
ventilation and energy characteristics. ASHRAE Transactions
103(1):717-730. Paper PH-97-08-4.
Sherman, M.H., and M.P. Modera. 1986. Comparison of
measured and predicted infiltration using the LBL infiltration model. In Measured air leakage of buildings, STP 904, p. 325. H.R. Trechsel and
P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Sherman, M.H., and D.J. Wilson. 1986. Relating actual
and effective ventilation in determining IAQ. Building and
Environment 21(3/4):135.
Sherman, M.H., D.T. Grimsrud, P.E. Condon, and B.V.
Smith. 1980. Air infiltration measurement techniques. Proceedings of the
1st IEA Conference of theAir Infiltration Centre, London. Report LBL-10705. Lawrence Berkeley National Laboratory, Berkeley,
CA.
Sherman, M.H., I.S. Walker, and J.M. Logue. 2011.
Equivalence in ventilation and IAQ. HVAC&R Research (now Science and Technology for the Built Environment)
189(4):760-773.
Shin, H.K., and J.H. Jo. 2013. Air leakage
characteristics and leakage distribution of dwellings in high-rise residential buildings in
Korea. Journal of Asian Architcture and Building Engineering.
12:87–92.
Shin, H.K., K.H. Ji, H. Cho, Y.H. Cho, and J.H. Jo.
2015. Impact of stack-induced infiltration on heating load in the high-rise building. ISHVAC-COBEE 2015: International Conference on Building Energy and
Environment. Tianjin, CN.
Simmonds, P., and D. Phillips. 2021. The influence of
outdoor conditions on the heating and cooling loads of supertall and mega tall buildings. CIBSE 2021 REV 1, Proceedings of the CIBSE Technical Symposium 2021,
Virtual.
Sinden, F.W. 1978. Wind, temperature and natural
ventilation—Theoretical considerations. Energy and Buildings
1(3):275.
Singer, B. C., W. W. Delp, P. N. Price, and M. G. Apte.
2012. Performance of installed cooking exhaust devices. Indoor Air
22(3):224-234.
Sorensen, J.H., and B.M. Vogt. 2001. Will duct tape and
plastic really work? Issues related to expedient sheltering-in-place. Report ORNL/TM-2001/154. Oak Ridge National Laboratory, Oak Ridge,
TN.
SQCAQMD. 2024. South Coast Air Quality Management
District AQ-SPEC Air Quality Sensor Performance Evaluation Center. www.aqmd.gov/aq-spec.
Stathopoulos, T., D. Surry, and A.G. Davenport. 1979.
Internal pressure characteristics of low-rise buildings due to wind action. Wind Engineering 1:451-463.
Stratton, J.C., and B.C. Singer. 2014. Addressing
kitchen contaminants for healthy, low-energy homes. LBNL Report
6547E.
Tamura, G.T., and C.Y. Shaw. 1976a. Studies on exterior
wall air tightness and air infiltration of tall buildings. ASHRAE
Transactions 82(1):122. Paper DA- 2388.
Tamura, G.T., and C.Y. Shaw. 1976b. Air leakage data for
the design of elevator and stair shaft pressurization system. ASHRAE
Transactions 82(2):179. Paper SE-2413.
Tamura, G.T., and A.G. Wilson. 1966. Pressure
differences for a nine-story building as a result of chimney effect and ventilation system
operation. ASHRAE Transactions 72(1):180-189.
Tamura, G.T., and A.G. Wilson. 1967a. Pressure
differences caused by chimney effect in three high buildings. ASHRAE
Transactions 73(2):II.1.1.
Tamura, G.T., and A.G. Wilson. 1967b. Building pressures
caused by chimney action and mechanical ventilation. ASHRAE
Transactions 73(2):II.2.1.
Tian, X., J. Fine, and M.F. Touchie. 2020. Investigating
the impact of sweeps and weather stripping on suite door air tightness in multi-family
buildings. ASHRAE 2020 Winter Conference.
Timusk, J., A.L. Seskus, and K. Linger. 1992. A systems
approach to extend the limit of envelope performance. Proceedings of the
6th ASHRAE/DOE/BTECC Conference—Thermal Performance of Exterior Envelopes of
Buildings, Clearwater Beach, FL.
Turk, B.T., D.T. Grimsrud, J.T. Brown, K.L.
Geisling-Sobotka, J. Harrison, and R.J. Prill. 1989. Commercial building ventilation rates and
particle concentrations. ASHRAE Transactions 95(1):422-433. Paper 3248.
Urquhart, R., R. Richman, and G. Finch. 2015. The effect
of an enclosure retrofit on air leakage rates for a multi-unit residential case-study building.
Energy and Buildings 86:35-44.
USACE. 2013. U.S. Army Corps of
Engineers air leakage test protocol for building envelopes. Air Barrier Association
of America, Walpole, MA, and U.S. Army Corps of Engineers.
Verschoor, J.D., and J.O. Collins. 1986. Demonstration
of air leakage reduction program in navy family housing. In Measured air
leakage of buildings, STP 904, p. 294. H.R. Trechsel and P.L. Lagus, eds. American
Society for Testing and Materials, West Conshohocken, PA.
Vinha, J., E. Manelius, M. Korpi, K. Salminen, J.
Kurnitski, M. Kiviste, and A. Laukkarinen. 2015. Airtightness of residential buildings in
Finland. Building and Environment. 93:128-140.
Walker, I.S. 1999. Distribution system leakage impacts
on apartment building ventilation rates. ASHRAE Transactions
105(1):943-950. Paper CH-99-14-2.
Walker, I.S., and T.W. Forest. 1995. Field measurements
of ventilation rates in attics. Building and Environment
30(3):333-347.
Walker, I.S., and D.J. Wilson. 1993. Evaluating models
for superposition of wind and stack effects in air infiltration. Building
and Environment 28(2):201-210.
Walker, I.S., D.J. Wilson., and M.H. Sherman. 1997. A
comparison of the power law to quadratic formulations for air infiltration calculations. Energy and Buildings 27(3).
Walker, I.S., and D.J. Wilson. 1998. Field validation of
algebraic equations for stack and wind driven air infiltration calculations. International Journal of HVAC&R Research (now Science and Technology for the Built Environment) 4(2):119-140.
Walker, I.S., M. Sherman, J. Siegel, D. Wang, C.
Buchanan, and M. Modera. 1999. Leakage diagnostics, sealant longevity, sizing and technology
transfer in residential thermal distribution systems: Part II. Report LBNL-42691.
Walker, I. S., M. Sherman, and D. Dickerhoff. 2012.
Development of a residential integrated ventilation controller. LBNL Report 5554E. Lawrence Berkeley National Laboratory, Berkeley,
CA.
Walton, G.N. 1984. A computer algorithm for predicting
infiltration and interroom airflows. ASHRAE Transactions 90(1B):601.
Paper AT-84-11-3.
Walton, G.N. 1989. Airflow network models for
element-based building airflow modeling. ASHRAE Transactions
95(2):611-620. Paper VA-89-06-5.
Warren, P.R., and B.C. Webb. 1980. The relationship
between tracer gas and pressurization techniques in dwellings. Proceedings
of the 1st IEA Conference of the Air Infiltration Centre, London.
Weidt, J.L., J. Weidt, and S. Selkowitz. 1979. Field air
leakage of newly installed residential windows. Proceedings of the
ASHRAE/DOE Conference—Thermal Performance of the Exterior Envelopes of
Buildings Orlando, FL, p. 149.
Weschler, C.J. 2000. Ozone in indoor environments:
Concentration and chemistry. Indoor Air 10:269-288.
Weschler, C.J., and W.W. Nazaroff. 2008 Semivolatile
organic compounds in indoor environments. Atmospheric Environment
42(40):9018-9040.
Wilson, D.J., and I.S. Walker. 1992. Feasibility of
passive ventilation by constant area vents to maintain IAQ in houses. Proceedings of IAQ ’92, ASHRAE/ACGIH/AIHA Conference, San
Francisco.
Wilson, D.J., and I.S. Walker. 1993. Infiltration data
from the Alberta Home Heating Research Facility. Technical Note 41.
Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Wolbrink, D. W. and J.R. Sarnosky. 1992. Residential
kitchen ventilation-a guide for the specifying engineer. ASHRAE
Transactions 98(2):1187-1198.
Wolf, S. 1966. A theory of the effects of convective air
flow through fibrous thermal insulation. ASHRAE Transactions
72(1):III 2.1-III 2.9.
Won, D., G. Nong, and S. So. 2021. Development of
formaldehyde flux sampler using a commercial DNPH cartridge. Building and Environment, 196,
107795.
Xiong, Z., J. Berquist, H.B. Gunay, and C.A.
Cruickshank. 2021. An inquiry into the use of indoor CO2 and humidity ratio trend
data with inverse modelling to estimate air infiltration. Building and
Environment 206:108365.
Yaglou, C.P., E.C. Riley, and D.I. Coggins. 1936.
Ventilation requirements. ASHVE Transactions 42:133.
Yuill, G.K. 1986. The variation of the effective natural
ventilation rate with weather conditions. Proceedings of the Solar Energy
Society of Canada Renewable Energy Conference ’86, pp. 70-75.
Yuill, G.K. 1991. The development of a method of
determining air change rates in detached dwellings for assessing IAQ. ASHRAE Transactions 97(2):896-903. Paper
IN-91-12-2.
Yuill, G.K. 1996. Impact of high use automatic doors on
infiltration. ASHRAE Research Project RP-763, Final Report.
Yuill, D.P., G.K. Yuill, and A.H. Coward. 2008.
Measurement and analysis of vitiation of secondary air in air distribution systems (RP-1276).
HVAC&R Research (now Science and Technology
for the Built Environment) 14(3):345-357.
Yuill, D.P., G.K. Yuill, and A.H. Coward. 2012.
Experimental validation of the multiple-zone system ventilation efficiency equation of
ANSI/ASHRAE Standard 62.1 (RP-1276). HVAC&R
Research (now Science and Technology for the Built
Environment) 18(3).
Zhivov, A. 2013. Air tightness in new and retrofitted US
army buildings. Air Barrier Association of America, Walpole, MA.