CHAPTER 1. PSYCHROMETRICS

 

Psychrometrics uses thermodynamic and transport prop erties to analyze conditions and processes involving moist air. This chapter discusses perfect gas relations and their use in common heating, cooling, and humidity control problems. Formulas developed by Herrmann et al. (2009) may be used where greater precision is required.

Herrmann et al. (2009), Hyland and Wexler (1983a, 1983b), and Nelson and Sauer (2002) developed formulas for thermodynamic properties of moist air and water modeled as real gases. However, perfect gas relations can be substituted in most air-conditioning problems. Kuehn et al. (1998) showed that errors are less than 0.7% in calculating humidity ratio, enthalpy, and specific volume of saturated air at standard atmospheric pressure for a temperature range of –60 to 120°F. Furthermore, these errors decrease with decreasing pressure.

Herrmann et al. (2020) prepared formulas for transport properties of moist air.

1. COMPOSITION OF DRY AND MOIST AIR

Atmospheric air contains many gaseous components as well as water vapor and miscellaneous contaminants (e.g., smoke, pollen, and gaseous pollutants not normally present in free air far from pollution sources).

Dry air is atmospheric air with all water vapor and contaminants removed. Its composition is relatively constant, but small variations in the amounts of individual components occur with time, geographic location, and altitude. Harrison (1965) lists the approximate percentage composition of dry air by volume as: nitrogen, 78.084; oxygen, 20.9476; argon, 0.934; neon, 0.001818; helium, 0.000524; methane, 0.00015; sulfur dioxide, 0 to 0.0001; hydrogen, 0.00005; and minor components such as krypton, xenon, and ozone, 0.0002. Harrison (1965) and Hyland and Wexler (1983a) used a value 0.0314 (circa 1955) for carbon dioxide. Carbon dioxide reached 0.0379 in 2005, is currently increasing by 0.00019 percent per year and is projected to reach 0.0438 in 2036 (Gatley et al. 2008; Keeling and Whorf 2005a, 2005b). Increases in carbon dioxide are offset by decreases in oxygen; consequently, the oxygen percentage in 2036 is projected to be 20.9352. Using the projected changes, the mole mass for dry air for at least the first half of the 21st century is 28.966 lbda/kmol, based on the carbon-12 scale. The gas constant for dry air using the Mohr and Taylor (2005) value for the universal gas constant is

(1)

Moist air is a binary (two-component) mixture of dry air and water vapor. The amount of water vapor varies from zero (dry air) to a maximum that depends on temperature and pressure. Saturation is a state of neutral equilibrium between moist air and the condensed water phase (liquid or solid); unless otherwise stated, it assumes a flat interface surface between moist air and the condensed phase. Saturation conditions change when the interface radius is very small (e.g., with ultrafine water droplets). According to the Industrial Formulation IAPWS-IF97 (R7-97 2012), the mole mass of water is 18.015257 lbw/kmol. The gas constant for water is

(2)

2. U.S. STANDARD ATMOSPHERE

The temperature and barometric pressure of atmospheric air vary considerably with altitude as well as with local geographic and weather conditions. The standard atmosphere gives a standard of reference for estimating properties at various altitudes. At sea level, standard temperature is 59°F; standard barometric pressure is 14.696 psia or 29.921 in. Hg. Temperature is assumed to decrease linearly with increasing altitude throughout the troposphere (lower atmosphere), and to be constant in the lower reaches of the stratosphere. The lower atmosphere is assumed to consist of dry air that behaves as a perfect gas. Gravity is also assumed constant at the standard value, 32.1740 ft/s2. Table 1 summarizes property data for altitudes to 30,000 ft.

Pressure values in Table 1 may be calculated from

(3)

The equation for temperature as a function of altitude is

Table 1 Standard Atmospheric Data for Altitudes to 30,000 ft

Altitude, ft

 

Temperature, °F

 

Pressure, psia

–1,000

 

62.6

 

15.23

–500

 

60.8

 

14.96

0

 

59.0

 

14.70

500

 

57.2

 

14.43

1,000

 

55.4

 

14.17

2,000

 

51.9

 

13.66

3,000

 

48.3

 

13.73

4,000

 

44.7

 

12.69

5,000

 

41.2

 

12.23

6,000

 

37.6

 

11.78

7,000

 

34.0

 

11.34

8,000

 

30.5

 

10.92

9,000

 

26.9

 

10.50

10,000

 

23.3

 

10.11

15,000

 

5.5

 

8.29

20,000

 

–12.3

 

6.76

30,000

 

–48.0

 

4.36

Source: Adapted from NASA (1976).

(4)

where

Z = altitude, ft
p = barometric pressure, psia
t = temperature, °F


Equations (3) and (4) are accurate from –16,500 ft to 36,000 ft. For higher altitudes, comprehensive tables of barometric pressure and other physical properties of the standard atmosphere, in both SI and I-P units, can be found in NASA (1976).

3. THERMODYNAMIC PROPERTIES OF MOIST AIR

Table 2, calculated using ASHRAE’s (2023) LibHuAirProp software (based on ASHRAE RP-1485; Herrmann et al. 2009, 2020), shows values of thermodynamic properties of saturated moist air and dry air at 14.696 psia and temperatures from –80 to 200°F.

The following properties are shown in Table 2:

t = Fahrenheit temperature, °F, based on the ITS-90 and expressed relative to absolute temperature T in Rankine by the following relation:

Ws = humidity ratio at saturation, lbw/lbda; gaseous phase (moist air) exists in equilibrium with condensed phase (liquid or solid) at given temperature and pressure (standard atmospheric pressure). At given values of temperature and pressure, humidity ratio W can have any value from zero to Ws.
vda = specific volume of dry air, ft3/lbda.
vs = specific volume of moist air at saturation, ft3/lbda.
hda = specific enthalpy of dry air, Btu/lbda. In Table 2, hda is assigned a value of 0 at 0°F and standard atmospheric pressure.
hs = specific enthalpy of moist air at saturation, Btu/lbda.
cp,da = specific heat capacity of dry air, Btu/lb·°R
cp,s = specific heat capacity of moist air at saturation, Btu/lb·°R
sda = specific entropy of dry air, Btu/lbda · °R. In Table 2, sda is assigned a value of 0 at 0°F and standard atmospheric pressure.
ss = specific entropy of moist air at saturation, Btu/lbda · °R.

Table 2 Thermodynamic Properties of Saturated Moist and Dry Air at Standard Atmospheric Pressure, 14.696 psia

Temp. t, °F

Humidity Ratio Ws, lbw/lbda

Specific Volume, ft3/lbda

Specific Enthalpy, Btu/lbda

Specific Heat Capacity, Btu/lb·°F

Specific Entropy, Btu/lbda·°F

vda

vs

hda

hs

cp,da

cp,s

sda

ss

–80

0.0000049

9.553

9.553

–19.218

–19.213

0.2403

0.2404

–0.04593

–0.04592

–79

0.0000053

9.578

9.578

–18.977

–18.972

0.2403

0.2403

–0.04530

–0.04529

–78

0.0000057

9.603

9.604

–18.737

–18.731

0.2403

0.2403

–0.04467

–0.04465

–77

0.0000062

9.629

9.629

–18.497

–18.490

0.2403

0.2403

–0.04404

–0.04402

–76

0.0000067

9.654

9.654

–18.256

–18.250

0.2403

0.2403

–0.04341

–0.04339

–75

0.0000072

9.680

9.680

–18.016

–18.009

0.2403

0.2403

–0.04279

–0.04277

–74

0.0000078

9.705

9.705

–17.776

–17.768

0.2403

0.2403

–0.04216

–0.04214

–73

0.0000084

9.730

9.730

–17.535

–17.527

0.2403

0.2403

–0.04154

–0.04152

–72

0.0000090

9.756

9.756

–17.295

–17.286

0.2403

0.2403

–0.04092

–0.04090

–71

0.0000097

9.781

9.781

–17.055

–17.045

0.2403

0.2403

–0.04030

–0.04027

–70

0.0000104

9.806

9.806

–16.814

–16.804

0.2403

0.2403

–0.03968

–0.03966

–69

0.0000112

9.832

9.832

–16.574

–16.563

0.2403

0.2403

–0.03907

–0.03904

–68

0.0000120

9.857

9.857

–16.334

–16.321

0.2403

0.2403

–0.03845

–0.03842

–67

0.0000129

9.882

9.882

–16.094

–16.080

0.2403

0.2403

–0.03784

–0.03781

–66

0.0000139

9.908

9.908

–15.853

–15.839

0.2403

0.2403

–0.03723

–0.03719

–65

0.0000149

9.933

9.933

–15.613

–15.598

0.2403

0.2403

–0.03662

–0.03658

–64

0.0000160

9.958

9.959

–15.373

–15.356

0.2403

0.2403

–0.03601

–0.03597

–63

0.0000172

9.984

9.984

–15.132

–15.115

0.2403

0.2403

–0.03541

–0.03536

–62

0.0000184

10.009

10.009

–14.892

–14.873

0.2403

0.2403

–0.03480

–0.03475

–61

0.0000198

10.034

10.035

–14.652

–14.632

0.2403

0.2403

–0.03420

–0.03414

–60

0.0000212

10.060

10.060

–14.412

–14.390

0.2403

0.2403

–0.03360

–0.03354

–59

0.0000227

10.085

10.085

–14.171

–14.148

0.2403

0.2403

–0.03300

–0.03293

–58

0.0000243

10.110

10.111

–13.931

–13.906

0.2403

0.2403

–0.03240

–0.03233

–57

0.0000260

10.136

10.136

–13.691

–13.664

0.2403

0.2403

–0.03180

–0.03173

–56

0.0000279

10.161

10.161

–13.451

–13.422

0.2402

0.2403

–0.03120

–0.03113

–55

0.0000298

10.186

10.187

–13.210

–13.179

0.2402

0.2403

–0.03061

–0.03053

–54

0.0000319

10.212

10.212

–12.970

–12.937

0.2402

0.2402

–0.03002

–0.02993

–53

0.0000341

10.237

10.237

–12.730

–12.695

0.2402

0.2402

–0.02942

–0.02933

–52

0.0000365

10.262

10.263

–12.490

–12.452

0.2402

0.2402

–0.02883

–0.02874

–51

0.0000390

10.288

10.288

–12.249

–12.209

0.2402

0.2402

–0.02825

–0.02814

–50

0.0000416

10.313

10.314

–12.009

–11.966

0.2402

0.2402

–0.02766

–0.02755

–49

0.0000445

10.338

10.339

–11.769

–11.723

0.2402

0.2402

–0.02707

–0.02695

–48

0.0000475

10.364

10.364

–11.529

–11.479

0.2402

0.2402

–0.02649

–0.02636

–47

0.0000507

10.389

10.390

–11.289

–11.236

0.2402

0.2402

–0.02591

–0.02577

–46

0.0000541

10.414

10.415

–11.048

–10.992

0.2402

0.2402

–0.02532

–0.02518

–45

0.0000577

10.439

10.440

–10.808

–10.748

0.2402

0.2402

–0.02474

–0.02459

–44

0.0000615

10.465

10.466

–10.568

–10.504

0.2402

0.2402

–0.02417

–0.02400

–43

0.0000656

10.490

10.491

–10.328

–10.259

0.2402

0.2402

–0.02359

–0.02341

–42

0.0000699

10.515

10.517

–10.087

–10.015

0.2402

0.2402

–0.02301

–0.02283

–41

0.0000744

10.541

10.542

–9.847

–9.770

0.2402

0.2402

–0.02244

–0.02224

–40

0.0000793

10.566

10.567

–9.607

–9.524

0.2402

0.2402

–0.02187

–0.02166

–39

0.0000844

10.591

10.593

–9.367

–9.279

0.2402

0.2402

–0.02129

–0.02107

–38

0.0000898

10.617

10.618

–9.127

–9.033

0.2402

0.2402

–0.02072

–0.02049

–37

0.0000956

10.642

10.644

–8.886

–8.787

0.2402

0.2402

–0.02015

–0.01990

–36

0.0001017

10.667

10.669

–8.646

–8.540

0.2402

0.2402

–0.01959

–0.01932

–35

0.0001081

10.693

10.695

–8.406

–8.293

0.2402

0.2402

–0.01902

–0.01874

–34

0.0001150

10.718

10.720

–8.166

–8.046

0.2402

0.2402

–0.01846

–0.01816

–33

0.0001222

10.743

10.745

–7.926

–7.798

0.2402

0.2402

–0.01789

–0.01757

–32

0.0001298

10.769

10.771

–7.685

–7.550

0.2402

0.2402

–0.01733

–0.01699

–31

0.0001379

10.794

10.796

–7.445

–7.301

0.2402

0.2402

–0.01677

–0.01641

–30

0.0001465

10.819

10.822

–7.205

–7.052

0.2402

0.2402

–0.01621

–0.01583

–29

0.0001555

10.845

10.847

–6.965

–6.802

0.2402

0.2402

–0.01565

–0.01525

–28

0.0001650

10.870

10.873

–6.725

–6.552

0.2402

0.2402

–0.01509

–0.01467

–27

0.0001751

10.895

10.898

–6.485

–6.301

0.2402

0.2402

–0.01454

–0.01409

–26

0.0001857

10.920

10.924

–6.244

–6.050

0.2402

0.2402

–0.01398

–0.01351

–25

0.0001970

10.946

10.949

–6.004

–5.797

0.2402

0.2402

–0.01343

–0.01293

–24

0.0002088

10.971

10.975

–5.764

–5.545

0.2402

0.2402

–0.01288

–0.01234

–23

0.0002213

10.996

11.000

–5.524

–5.291

0.2402

0.2402

–0.01233

–0.01176

–22

0.0002345

11.022

11.026

–5.284

–5.037

0.2402

0.2402

–0.01178

–0.01118

–21

0.0002485

11.047

11.051

–5.043

–4.782

0.2402

0.2402

–0.01123

–0.01060

–20

0.0002632

11.072

11.077

–4.803

–4.527

0.2402

0.2402

–0.01068

–0.01002

–19

0.0002786

11.098

11.103

–4.563

–4.270

0.2402

0.2402

–0.01014

–0.00943

–18

0.0002949

11.123

11.128

–4.323

–4.013

0.2402

0.2402

–0.00959

–0.00885

–17

0.0003121

11.148

11.154

–4.083

–3.754

0.2402

0.2402

–0.00905

–0.00826

–16

0.0003302

11.174

11.179

–3.843

–3.495

0.2402

0.2402

–0.00851

–0.00768

–15

0.0003493

11.199

11.205

–3.602

–3.234

0.2402

0.2402

–0.00797

–0.00709

–14

0.0003694

11.224

11.231

–3.362

–2.973

0.2402

0.2402

–0.00743

–0.00650

–13

0.0003905

11.249

11.257

–3.122

–2.710

0.2402

0.2402

–0.00689

–0.00591

–12

0.0004127

11.275

11.282

–2.882

–2.446

0.2402

0.2403

–0.00635

–0.00532

–11

0.0004361

11.300

11.308

–2.642

–2.181

0.2402

0.2403

–0.00582

–0.00473

–10

0.0004607

11.325

11.334

–2.402

–1.915

0.2402

0.2403

–0.00528

–0.00414

–9

0.0004866

11.351

11.360

–2.161

–1.647

0.2402

0.2403

–0.00475

–0.00354

–8

0.0005138

11.376

11.385

–1.921

–1.378

0.2402

0.2403

–0.00422

–0.00294

–7

0.0005425

11.401

11.411

–1.681

–1.108

0.2402

0.2403

–0.00369

–0.00234

–6

0.0005725

11.427

11.437

–1.441

–0.835

0.2402

0.2403

–0.00316

–0.00174

–5

0.0006041

11.452

11.463

–1.201

–0.561

0.2402

0.2403

–0.00263

–0.00114

–4

0.0006373

11.477

11.489

–0.961

–0.286

0.2402

0.2403

–0.00210

–0.00053

–3

0.0006721

11.502

11.515

–0.720

–0.009

0.2402

0.2403

–0.00157

0.00008

–2

0.0007087

11.528

11.541

–0.480

0.271

0.2402

0.2403

–0.00105

0.00069

–1

0.0007471

11.553

11.567

–0.240

0.552

0.2402

0.2403

–0.00052

0.00130

0

0.0007875

11.578

11.593

0.000

0.835

0.2402

0.2403

0.00000

0.00192

1

0.0008298

11.604

11.619

0.240

1.121

0.2402

0.2403

0.00052

0.00254

2

0.0008741

11.629

11.645

0.480

1.408

0.2402

0.2403

0.00104

0.00317

3

0.0009207

11.654

11.671

0.720

1.698

0.2402

0.2404

0.00156

0.00379

4

0.0009695

11.680

11.698

0.961

1.991

0.2402

0.2404

0.00208

0.00443

5

0.0010207

11.705

11.724

1.201

2.286

0.2402

0.2404

0.00260

0.00506

6

0.0010743

11.730

11.750

1.441

2.583

0.2402

0.2404

0.00311

0.00570

7

0.0011306

11.755

11.777

1.681

2.884

0.2402

0.2404

0.00363

0.00635

8

0.0011895

11.781

11.803

1.921

3.187

0.2402

0.2404

0.00414

0.00700

9

0.0012512

11.806

11.830

2.161

3.493

0.2402

0.2404

0.00466

0.00765

10

0.0013158

11.831

11.856

2.402

3.803

0.2402

0.2404

0.00517

0.00832

11

0.0013835

11.857

11.883

2.642

4.116

0.2402

0.2405

0.00568

0.00898

12

0.0014544

11.882

11.910

2.882

4.432

0.2402

0.2405

0.00619

0.00965

13

0.0015286

11.907

11.936

3.122

4.752

0.2402

0.2405

0.00670

0.01033

14

0.0016062

11.933

11.963

3.362

5.076

0.2402

0.2405

0.00721

0.01102

15

0.0016874

11.958

11.990

3.603

5.403

0.2402

0.2405

0.00771

0.01171

16

0.0017724

11.983

12.017

3.843

5.735

0.2402

0.2405

0.00822

0.01241

17

0.0018613

12.008

12.044

4.083

6.071

0.2402

0.2406

0.00872

0.01311

18

0.0019543

12.034

12.071

4.323

6.411

0.2402

0.2406

0.00922

0.01383

19

0.0020515

12.059

12.099

4.563

6.756

0.2402

0.2406

0.00973

0.01455

20

0.0021531

12.084

12.126

4.803

7.106

0.2402

0.2406

0.01023

0.01528

21

0.0022593

12.110

12.153

5.044

7.461

0.2402

0.2406

0.01073

0.01602

22

0.0023703

12.135

12.181

5.284

7.821

0.2402

0.2407

0.01123

0.01677

23

0.0024863

12.160

12.209

5.524

8.186

0.2402

0.2407

0.01173

0.01753

24

0.0026075

12.185

12.236

5.764

8.557

0.2402

0.2407

0.01222

0.01830

25

0.0027340

12.211

12.264

6.004

8.934

0.2402

0.2408

0.01272

0.01908

26

0.0028662

12.236

12.292

6.244

9.317

0.2402

0.2408

0.01321

0.01987

27

0.0030042

12.261

12.320

6.485

9.707

0.2402

0.2408

0.01371

0.02067

28

0.0031482

12.287

12.349

6.725

10.103

0.2402

0.2408

0.01420

0.02148

29

0.0032986

12.312

12.377

6.965

10.506

0.2402

0.2409

0.01469

0.02231

30

0.0034555

12.337

12.405

7.205

10.916

0.2402

0.2409

0.01518

0.02315

31

0.0036192

12.362

12.434

7.445

11.334

0.2402

0.2409

0.01567

0.02400

32

0.0037900

12.388

12.463

7.6857

11.759

0.2402

0.2410

0.01616

0.02486

33

0.0039468

12.413

12.492

7.9259

12.169

0.2402

0.2410

0.01665

0.02570

34

0.0041093

12.438

12.520

8.1661

12.586

0.2402

0.2411

0.01714

0.02654

35

0.0042778

12.464

12.549

8.4063

13.009

0.2402

0.2411

0.01762

0.02740

36

0.0044524

12.489

12.578

8.6465

13.439

0.2402

0.2411

0.01811

0.02827

37

0.0046333

12.514

12.607

8.8867

13.876

0.2402

0.2412

0.01859

0.02915

38

0.0048208

12.539

12.636

9.1269

14.321

0.2402

0.2412

0.01908

0.03004

39

0.0050151

12.565

12.666

9.3671

14.772

0.2402

0.2413

0.01956

0.03095

40

0.0052163

12.590

12.695

9.6073

15.232

0.2402

0.2413

0.02004

0.03187

41

0.0054247

12.615

12.725

9.8475

15.699

0.2402

0.2413

0.02052

0.03280

42

0.0056404

12.641

12.755

10.088

16.175

0.2402

0.2414

0.02100

0.03375

43

0.0058639

12.666

12.785

10.328

16.658

0.2402

0.2414

0.02148

0.03472

44

0.0060952

12.691

12.815

10.568

17.151

0.2402

0.2415

0.02196

0.03569

45

0.0063346

12.716

12.845

10.808

17.653

0.2402

0.2416

0.02243

0.03669

46

0.0065824

12.742

12.876

11.049

18.163

0.2402

0.2416

0.02291

0.03770

47

0.0068389

12.767

12.907

11.289

18.684

0.2402

0.2417

0.02338

0.03873

48

0.0071042

12.792

12.938

11.529

19.214

0.2402

0.2417

0.02386

0.03978

49

0.0073787

12.817

12.969

11.769

19.755

0.2402

0.2418

0.02433

0.04084

50

0.0076627

12.843

13.001

12.010

20.305

0.2402

0.2418

0.02480

0.04192

51

0.0079563

12.868

13.032

12.250

20.867

0.2402

0.2419

0.02527

0.04302

52

0.0082601

12.893

13.064

12.490

21.440

0.2403

0.2420

0.02574

0.04414

53

0.0085741

12.919

13.096

12.730

22.024

0.2403

0.2420

0.02621

0.04528

54

0.0088989

12.944

13.129

12.971

22.620

0.2403

0.2421

0.02668

0.04645

55

0.0092345

12.969

13.161

13.211

23.229

0.2403

0.2422

0.02715

0.04763

56

0.0095815

12.994

13.194

13.451

23.850

0.2403

0.2423

0.02761

0.04883

57

0.0099402

13.020

13.227

13.691

24.483

0.2403

0.2423

0.02808

0.05006

58

0.010311

13.045

13.261

13.932

25.131

0.2403

0.2424

0.02854

0.05131

59

0.010694

13.070

13.294

14.172

25.792

0.2403

0.2425

0.02901

0.05259

60

0.011089

13.096

13.328

14.412

26.467

0.2403

0.2426

0.02947

0.05389

61

0.011498

13.121

13.363

14.653

27.156

0.2403

0.2427

0.02993

0.05522

62

0.011921

13.146

13.397

14.893

27.861

0.2403

0.2428

0.03039

0.05657

63

0.012357

13.171

13.432

15.133

28.581

0.2403

0.2429

0.03085

0.05795

64

0.012807

13.197

13.468

15.373

29.317

0.2403

0.2430

0.03131

0.05936

65

0.013272

13.222

13.503

15.614

30.070

0.2403

0.2431

0.03177

0.06080

66

0.013753

13.247

13.539

15.854

30.839

0.2403

0.2432

0.03223

0.06226

67

0.014249

13.272

13.576

16.094

31.626

0.2403

0.2433

0.03268

0.06376

68

0.014761

13.298

13.612

16.335

32.431

0.2403

0.2434

0.03314

0.06529

69

0.015289

13.323

13.649

16.575

33.254

0.2403

0.2435

0.03360

0.06685

70

0.015835

13.348

13.687

16.815

34.097

0.2403

0.2436

0.03405

0.06844

71

0.016398

13.374

13.725

17.056

34.959

0.2403

0.2438

0.03450

0.07007

72

0.016979

13.399

13.763

17.296

35.841

0.2403

0.2439

0.03495

0.07173

73

0.017578

13.424

13.802

17.536

36.744

0.2403

0.2440

0.03541

0.07343

74

0.018197

13.449

13.842

17.777

37.668

0.2403

0.2441

0.03586

0.07516

75

0.018835

13.475

13.881

18.017

38.614

0.2403

0.2443

0.03631

0.07694

76

0.019494

13.500

13.922

18.257

39.583

0.2403

0.2444

0.03676

0.07875

77

0.020173

13.525

13.962

18.498

40.576

0.2403

0.2446

0.03720

0.08060

78

0.020874

13.550

14.004

18.738

41.592

0.2404

0.2447

0.03765

0.08250

79

0.021597

13.576

14.046

18.978

42.634

0.2404

0.2449

0.03810

0.08444

80

0.022343

13.601

14.088

19.219

43.700

0.2404

0.2450

0.03854

0.08642

81

0.023112

13.626

14.131

19.459

44.793

0.2404

0.2452

0.03899

0.08844

82

0.023905

13.651

14.174

19.699

45.914

0.2404

0.2454

0.03943

0.09052

83

0.024723

13.677

14.219

19.940

47.062

0.2404

0.2456

0.03988

0.09264

84

0.025566

13.702

14.263

20.180

48.238

0.2404

0.2457

0.04032

0.09481

85

0.026436

13.727

14.309

20.420

49.445

0.2404

0.2459

0.04076

0.09703

86

0.027333

13.753

14.355

20.661

50.681

0.2404

0.2461

0.04120

0.09930

87

0.028257

13.778

14.402

20.901

51.949

0.2404

0.2463

0.04164

0.1016

88

0.029211

13.803

14.449

21.142

53.250

0.2404

0.2465

0.04208

0.1040

89

0.030193

13.828

14.497

21.382

54.583

0.2404

0.2467

0.04252

0.1064

90

0.031206

13.854

14.546

21.622

55.951

0.2404

0.2469

0.04296

0.1089

91

0.032251

13.879

14.596

21.863

57.354

0.2404

0.2472

0.04339

0.1115

92

0.033327

13.904

14.646

22.103

58.794

0.2404

0.2474

0.04383

0.1141

93

0.034437

13.929

14.698

22.344

60.271

0.2404

0.2476

0.04427

0.1168

94

0.035581

13.955

14.750

22.584

61.787

0.2404

0.2479

0.04470

0.1196

95

0.036760

13.980

14.803

22.825

63.342

0.2404

0.2481

0.04514

0.1224

96

0.037976

14.005

14.857

23.065

64.938

0.2404

0.2484

0.04557

0.1252

97

0.039228

14.031

14.912

23.305

66.577

0.2405

0.2486

0.04600

0.1282

98

0.040520

14.056

14.968

23.546

68.259

0.2405

0.2489

0.04643

0.1312

99

0.041851

14.081

15.025

23.786

69.987

0.2405

0.2492

0.04686

0.1343

100

0.043222

14.106

15.083

24.027

71.760

0.2405

0.2495

0.04729

0.1375

101

0.044636

14.132

15.142

24.267

73.581

0.2405

0.2498

0.04772

0.1408

102

0.046094

14.157

15.202

24.508

75.452

0.2405

0.2501

0.04815

0.1441

103

0.047596

14.182

15.263

24.748

77.373

0.2405

0.2504

0.04858

0.1476

104

0.049145

14.207

15.325

24.989

79.347

0.2405

0.2507

0.04901

0.1511

105

0.050741

14.233

15.389

25.229

81.374

0.2405

0.2510

0.04943

0.1547

106

0.052386

14.258

15.454

25.470

83.458

0.2405

0.2514

0.04986

0.1584

107

0.054082

14.283

15.520

25.710

85.598

0.2405

0.2517

0.05028

0.1622

108

0.055830

14.308

15.587

25.951

87.799

0.2405

0.2521

0.05071

0.1661

109

0.057632

14.334

15.656

26.191

90.060

0.2405

0.2525

0.05113

0.1701

110

0.059490

14.359

15.726

26.432

92.385

0.2405

0.2528

0.05155

0.1742

111

0.061405

14.384

15.798

26.672

94.775

0.2405

0.2532

0.05197

0.1784

112

0.063380

14.409

15.871

26.913

97.233

0.2405

0.2536

0.05240

0.1827

113

0.065416

14.435

15.946

27.154

99.761

0.2406

0.2541

0.05282

0.1872

114

0.067516

14.460

16.022

27.394

102.36

0.2406

0.2545

0.05324

0.1917

115

0.069680

14.485

16.100

27.635

105.03

0.2406

0.2549

0.05365

0.1964

116

0.071913

14.511

16.180

27.875

107.79

0.2406

0.2554

0.05407

0.2012

117

0.074215

14.536

16.262

28.116

110.62

0.2406

0.2558

0.05449

0.2061

118

0.076590

14.561

16.345

28.356

113.53

0.2406

0.2563

0.05491

0.2112

119

0.079040

14.586

16.431

28.597

116.53

0.2406

0.2568

0.05532

0.2164

120

0.081566

14.612

16.518

28.838

119.61

0.2406

0.2573

0.05574

0.2218

121

0.084173

14.637

16.607

29.078

122.79

0.2406

0.2578

0.05615

0.2273

122

0.086863

14.662

16.699

29.319

126.06

0.2406

0.2584

0.05657

0.2330

123

0.089638

14.687

16.793

29.559

129.43

0.2406

0.2589

0.05698

0.2388

124

0.092503

14.713

16.889

29.800

132.90

0.2406

0.2595

0.05739

0.2448

125

0.095459

14.738

16.988

30.041

136.48

0.2406

0.2600

0.05781

0.2510

126

0.098510

14.763

17.089

30.281

140.16

0.2406

0.2606

0.05822

0.2573

127

0.10166

14.788

17.192

30.522

143.96

0.2407

0.2612

0.05863

0.2638

128

0.10491

14.814

17.298

30.763

147.88

0.2407

0.2619

0.05904

0.2705

129

0.10827

14.839

17.407

31.003

151.91

0.2407

0.2625

0.05945

0.2774

130

0.11174

14.864

17.519

31.244

156.07

0.2407

0.2632

0.05985

0.2846

131

0.11533

14.889

17.634

31.485

160.37

0.2407

0.2639

0.06026

0.2919

132

0.11903

14.915

17.752

31.725

164.80

0.2407

0.2646

0.06067

0.2994

133

0.12286

14.940

17.873

31.966

169.37

0.2407

0.2653

0.06108

0.3072

134

0.12681

14.965

17.998

32.207

174.08

0.2407

0.2660

0.06148

0.3152

135

0.13090

14.990

18.126

32.447

178.95

0.2407

0.2668

0.06189

0.3235

136

0.13513

15.016

18.258

32.688

183.98

0.2407

0.2676

0.06229

0.3320

137

0.13950

15.041

18.393

32.929

189.18

0.2407

0.2684

0.06269

0.3408

138

0.14402

15.066

18.533

33.170

194.55

0.2407

0.2692

0.06310

0.3499

139

0.14870

15.091

18.677

33.410

200.09

0.2407

0.2700

0.06350

0.3592

140

0.15354

15.117

18.825

33.651

205.83

0.2408

0.2709

0.06390

0.3689

141

0.15856

15.142

18.977

33.892

211.75

0.2408

0.2718

0.06430

0.3789

142

0.16375

15.167

19.134

34.133

217.89

0.2408

0.2727

0.06470

0.3892

143

0.16913

15.192

19.296

34.373

224.23

0.2408

0.2737

0.06510

0.3998

144

0.17470

15.218

19.463

34.614

230.80

0.2408

0.2746

0.06550

0.4108

145

0.18047

15.243

19.636

34.855

237.60

0.2408

0.2756

0.06590

0.4222

146

0.18646

15.268

19.814

35.096

244.64

0.2408

0.2767

0.06630

0.4339

147

0.19267

15.294

19.998

35.337

251.94

0.2408

0.2777

0.06670

0.4461

148

0.19911

15.319

20.188

35.577

259.51

0.2408

0.2788

0.06709

0.4587

149

0.20579

15.344

20.384

35.818

267.35

0.2408

0.2799

0.06749

0.4717

150

0.21273

15.369

20.588

36.059

275.49

0.2408

0.2811

0.06788

0.4852

151

0.21994

15.395

20.798

36.300

283.93

0.2409

0.2822

0.06828

0.4992

152

0.22743

15.420

21.016

36.541

292.70

0.2409

0.2835

0.06867

0.5138

153

0.23522

15.445

21.242

36.782

301.81

0.2409

0.2847

0.06907

0.5288

154

0.24332

15.470

21.476

37.023

311.27

0.2409

0.2860

0.06946

0.5444

155

0.25174

15.496

21.719

37.263

321.12

0.2409

0.2873

0.06985

0.5606

156

0.26051

15.521

21.971

37.504

331.35

0.2409

0.2887

0.07024

0.5775

157

0.26965

15.546

22.232

37.745

342.01

0.2409

0.2901

0.07063

0.5950

158

0.27917

15.571

22.504

37.986

353.11

0.2409

0.2915

0.07103

0.6132

159

0.28909

15.597

22.787

38.227

364.67

0.2409

0.2930

0.07141

0.6322

160

0.29945

15.622

23.081

38.468

376.73

0.2409

0.2945

0.07180

0.6519

161

0.31026

15.647

23.387

38.709

389.31

0.2409

0.2960

0.07219

0.6724

162

0.32156

15.672

23.706

38.950

402.45

0.2410

0.2976

0.07258

0.6939

163

0.33336

15.698

24.039

39.191

416.17

0.2410

0.2993

0.07297

0.7162

164

0.34571

15.723

24.386

39.432

430.52

0.2410

0.3010

0.07335

0.7396

165

0.35865

15.748

24.749

39.673

445.54

0.2410

0.3027

0.07374

0.7640

166

0.37219

15.773

25.128

39.914

461.26

0.2410

0.3046

0.07413

0.7895

167

0.38640

15.799

25.525

40.155

477.74

0.2410

0.3064

0.07451

0.8162

168

0.40131

15.824

25.941

40.396

495.03

0.2410

0.3083

0.07490

0.8442

169

0.41697

15.849

26.376

40.637

513.18

0.2410

0.3103

0.07528

0.8735

170

0.43344

15.874

26.833

40.878

532.26

0.2410

0.3123

0.07566

0.9043

171

0.45077

15.900

27.314

41.119

552.33

0.2410

0.3144

0.07604

0.9366

172

0.46903

15.925

27.819

41.360

573.48

0.2411

0.3165

0.07643

0.9706

173

0.48829

15.950

28.351

41.601

595.77

0.2411

0.3187

0.07681

1.0065

174

0.50864

15.975

28.911

41.842

619.30

0.2411

0.3210

0.07719

1.0442

175

0.53015

16.001

29.503

42.083

644.18

0.2411

0.3234

0.07757

1.0841

176

0.55293

16.026

30.129

42.324

670.51

0.2411

0.3258

0.07795

1.1262

177

0.57708

16.051

30.792

42.565

698.43

0.2411

0.3283

0.07833

1.1708

178

0.60273

16.076

31.495

42.807

728.06

0.2411

0.3308

0.07871

1.2181

179

0.63000

16.102

32.241

43.048

759.57

0.2411

0.3335

0.07908

1.2684

180

0.65907

16.127

33.035

43.289

793.13

0.2411

0.3362

0.07946

1.3218

181

0.69009

16.152

33.881

43.530

828.94

0.2412

0.3390

0.07984

1.3787

182

0.72326

16.177

34.786

43.771

867.23

0.2412

0.3419

0.08021

1.4395

183

0.75882

16.203

35.753

44.012

908.25

0.2412

0.3449

0.08059

1.5045

184

0.79700

16.228

36.791

44.253

952.30

0.2412

0.3480

0.08096

1.5743

185

0.83811

16.253

37.908

44.495

999.71

0.2412

0.3512

0.08134

1.6493

186

0.88247

16.278

39.112

44.736

1050.9

0.2412

0.3545

0.08171

1.7300

187

0.93050

16.304

40.414

44.977

1106.2

0.2412

0.3579

0.08209

1.8174

188

0.98263

16.329

41.825

45.218

1166.3

0.2412

0.3614

0.08246

1.9120

189

1.0394

16.354

43.362

45.460

1231.8

0.2412

0.3650

0.08283

2.0149

190

1.1015

16.379

45.040

45.701

1303.3

0.2413

0.3688

0.08320

2.1273

191

1.1696

16.405

46.880

45.942

1381.7

0.2413

0.3726

0.08357

2.2504

192

1.2446

16.430

48.906

46.183

1468.2

0.2413

0.3766

0.08394

2.3859

193

1.3277

16.455

51.147

46.425

1563.9

0.2413

0.3807

0.08431

2.5356

194

1.4202

16.480

53.640

46.666

1670.4

0.2413

0.3850

0.08468

2.7021

195

1.5238

16.506

56.430

46.907

1789.6

0.2413

0.3894

0.08505

2.8882

196

1.6405

16.531

59.571

47.149

1924.0

0.2413

0.3940

0.08542

3.0976

197

1.7729

16.556

63.135

47.390

2076.4

0.2413

0.3988

0.08579

3.3349

198

1.9245

16.581

67.212

47.631

2250.9

0.2413

0.4037

0.08616

3.6062

199

2.0997

16.607

71.921

47.873

2452.5

0.2414

0.4087

0.08652

3.9193

200

2.3044

16.632

77.421

48.114

2688.1

0.2414

0.4140

0.08689

4.2847


4. THERMODYNAMIC PROPERTIES OF WATER AT SATURATION

Table 3 shows thermodynamic properties of water at saturation for temperatures from –80 to 300°F, calculated using ASHRAE’s (2023) LibHuAirProp software of Herrmann et al. (2009, 2020), based on IAPWS formulations described in IAPWS R7-97 (2012), R10-06 (2009), and R14-08 (2011). The internal energy and entropy of saturated liquid water are both assigned the value zero at the triple point, 32.018°F. Between the triple-point and critical-point temperatures of water, both saturated liquid and saturated vapor may coexist in equilibrium; below the triple-point temperature, both saturated ice and saturated vapor may coexist in equilibrium.

The following properties are shown in Table 3:

t = Fahrenheit temperature, °F, based on ITS-90 and expressed relative to absolute temperature T in Rankine by the following relation:

pws = saturation pressure of water (solid, liquid, or vapor), psia
vi = specific volume of saturated solid (ice), ft3/lb
vf = specific volume of saturated liquid (water), ft3/lb
vg = specific volume of saturated vapor (steam), ft3/lb
hi = specific enthalpy of saturated solid (ice), Btu/lb
hf = specific enthalpy of saturated liquid (water), Btu/lb
hg = specific enthalpy of saturated vapor (steam), Btu/lb
cp,i = specific heat capacity of saturated solid (ice), Btu/lb·°R
cp,f = specific heat capacity of saturated liquid (water), Btu/lb·°R
cp,g = specific heat capacity of saturated vapor (steam), Btu/lb·°R
si = specific entropy of saturated solid (ice), Btu/lb·°R
sf = specific entropy of saturated liquid (water), Btu/lb·°R
sg = specific entropy of saturated vapor (steam), Btu/lb·°R

The saturation pressure over liquid water for the temperature range of 32°F ≤ t < 705.103°F (critical temperature) is given by the IAPWS Industrial Formulation IAPWS-IF97 (R7-97, 2012):

(5)

where

A = θ2 + n1θ + n2
B = n3θ2 + n4θ + n5
C = n6θ2 + n7θ + n8

with

and the coefficients

n1 = 0.116 705 214 527 67 E+04
n2 = –0.724 213 167 032 06 E+06
n3 = –0.170 738 469 400 92 E+02
n4 = 0.120 208 247 024 70 E+05
n5 = –0.323 255 503 223 33 E+07
n6 = 0.149 151 086 135 30 E+02
n7 = –0.482 326 573 615 91 E+04
n8 = 0.405 113 405 420 57 E+06
n9 = –0.238 555 575 678 49 E+00
n10 = 0.650 175 348 447 98 E+03
n11 = 0.555 555 555 555 56

Equation (5) fits exactly to Equation (39).

The saturation (sublimation) pressure over ice for the temperature range of –369.67°F ≤ t <32°F is given by IAPWS 2008 Formulation (R14-08, 2011):

(6)

where

θ = T/491.688°R

with the coefficients and exponents

a1 = –0.212 144 006 E+02
a2 = 0.273 203 819 E+02
a3 = –0.610 598 130 E+01
b1 =0.333 333 333 E–02
b2 =0.120 666 667 E+01
b3 = 0.170 333 333 E+01

In both Equations (5) and (6),

pws = saturation pressure, psia
T = absolute temperature, T = (t / °F + 459.67)°R

The vapor pressure ps of water in saturated moist air at total pressures, which approximately correspond to the barometric pressure, differs negligibly from the saturation vapor pressure pws of pure water at the same temperature (e.g., 0.5% at 15 psia and 0.8% at 30 psia total pressures) . Consequently, ps can be used in place of pws at atmospheric pressure p:

where xws is the mole fraction of water vapor in saturated moist air at temperature t and pressure p, and p is the total barometric pressure of moist air.

5. HUMIDITY PARAMETERS

 Basic Parameters

Humidity ratio W (or mixing ratio) of a given moist air sample is defined as the ratio of the mass of water vapor to the mass of dry air in the sample:

(7)

W equals the mole fraction ratio xw/xda multiplied by the ratio of mole masses (18.015 257/28.966 = 0.621 945):

(8)

Specific humidity γ is the ratio of the mass of water vapor to total mass of the moist air sample:

(9a)

In terms of the humidity ratio,

(9b)

Absolute humidity (alternatively, water vapor density) dv is the ratio of the mass of water vapor to total volume of the sample:

(10)

Density ρ of a moist air mixture is the ratio of total mass to total volume:

(11)

where v is the moist air specific volume, ft3/lbda, as defined by Equation (25).

Table 3 Thermodynamic Properties of Water at Saturation

Temp. t, °F

Absolute Pressure pws, psia

Specific Volume, ft3/lb

Specific Enthalpy, Btu/lb

Specific Heat Capacity, Btu/lb·°R

Specific Entropy, Btu/lb·°R

Sat. Solid/Liquid vi/vf

Sat. Vapor vg

Sat. Solid/Liquid hi/hf

Sat. Vapor hg

Sat. Solid/Liquid cp,i/cp,f

Sat. Vapor cp,g

Sat. Solid/Liquid si/sf

Sat. Vapor sg

–80

0.000116

0.01732

1953807

–193.38

1025.8

0.3930

0.4423

–0.4064

2.8048

–79

0.000125

0.01732

1814635

–192.98

1026.3

0.3940

0.4424

–0.4054

2.7975

–78

0.000135

0.01732

1686036

–192.59

1026.7

0.3949

0.4424

–0.4043

2.7903

–77

0.000145

0.01732

1567159

–192.19

1027.1

0.3958

0.4424

–0.4033

2.7831

–76

0.000157

0.01732

1457224

–191.80

1027.6

0.3968

0.4424

–0.4023

2.7759

–75

0.000169

0.01733

1355519

–191.40

1028.0

0.3977

0.4424

–0.4012

2.7688

–74

0.000182

0.01733

1261390

–191.00

1028.5

0.3987

0.4424

–0.4002

2.7617

–73

0.000196

0.01733

1174239

–190.60

1028.9

0.3996

0.4424

–0.3992

2.7547

–72

0.000211

0.01733

1093518

–190.20

1029.3

0.4006

0.4424

–0.3981

2.7477

–71

0.000227

0.01733

1018724

–189.80

1029.8

0.4015

0.4425

–0.3971

2.7408

–70

0.000244

0.01733

949394

–189.40

1030.2

0.4024

0.4425

–0.3961

2.7338

–69

0.000263

0.01733

885105

–189.00

1030.7

0.4034

0.4425

–0.3950

2.7270

–68

0.000283

0.01733

825469

–188.59

1031.1

0.4043

0.4425

–0.3940

2.7201

–67

0.000304

0.01733

770128

–188.19

1031.6

0.4053

0.4425

–0.3930

2.7133

–66

0.000326

0.01734

718753

–187.78

1032.0

0.4062

0.4425

–0.3919

2.7065

–65

0.000350

0.01734

671043

–187.38

1032.4

0.4072

0.4425

–0.3909

2.6998

–64

0.000376

0.01734

626720

–186.97

1032.9

0.4081

0.4426

–0.3899

2.6931

–63

0.000404

0.01734

585529

–186.56

1033.3

0.4091

0.4426

–0.3888

2.6865

–62

0.000433

0.01734

547234

–186.15

1033.8

0.4100

0.4426

–0.3878

2.6799

–61

0.000464

0.01734

511620

–185.74

1034.2

0.4110

0.4426

–0.3868

2.6733

–60

0.000498

0.01734

478487

–185.33

1034.7

0.4119

0.4426

–0.3858

2.6667

–59

0.000533

0.01734

447651

–184.92

1035.1

0.4129

0.4426

–0.3847

2.6602

–58

0.000571

0.01735

418943

–184.50

1035.5

0.4138

0.4427

–0.3837

2.6537

–57

0.000612

0.01735

392207

–184.09

1036.0

0.4148

0.4427

–0.3827

2.6473

–56

0.000655

0.01735

367299

–183.67

1036.4

0.4157

0.4427

–0.3816

2.6409

–55

0.000701

0.01735

344086

–183.26

1036.9

0.4167

0.4427

–0.3806

2.6345

–54

0.000749

0.01735

322445

–182.84

1037.3

0.4176

0.4427

–0.3796

2.6282

–53

0.000801

0.01735

302263

–182.42

1037.7

0.4186

0.4428

–0.3785

2.6219

–52

0.000857

0.01735

283436

–182.00

1038.2

0.4195

0.4428

–0.3775

2.6156

–51

0.000916

0.01736

265866

–181.58

1038.6

0.4205

0.4428

–0.3765

2.6093

–50

0.000978

0.01736

249464

–181.16

1039.1

0.4214

0.4428

–0.3755

2.6031

–49

0.001045

0.01736

234148

–180.74

1039.5

0.4224

0.4429

–0.3744

2.5970

–48

0.001115

0.01736

219841

–180.32

1040.0

0.4234

0.4429

–0.3734

2.5908

–47

0.001191

0.01736

206472

–179.89

1040.4

0.4243

0.4429

–0.3724

2.5847

–46

0.001270

0.01736

193976

–179.47

1040.8

0.4253

0.4429

–0.3713

2.5786

–45

0.001355

0.01736

182292

–179.04

1041.3

0.4262

0.4430

–0.3703

2.5726

–44

0.001445

0.01736

171363

–178.62

1041.7

0.4272

0.4430

–0.3693

2.5666

–43

0.001540

0.01737

161139

–178.19

1042.2

0.4281

0.4430

–0.3683

2.5606

–42

0.001641

0.01737

151570

–177.76

1042.6

0.4291

0.4430

–0.3672

2.5546

–41

0.001749

0.01737

142611

–177.33

1043.1

0.4300

0.4431

–0.3662

2.5487

–40

0.001862

0.01737

134222

–176.90

1043.5

0.4310

0.4431

–0.3652

2.5428

–39

0.001983

0.01737

126363

–176.47

1043.9

0.4320

0.4431

–0.3642

2.5370

–38

0.002111

0.01737

118999

–176.04

1044.4

0.4329

0.4432

–0.3631

2.5311

–37

0.002246

0.01737

112096

–175.60

1044.8

0.4339

0.4432

–0.3621

2.5253

–36

0.002389

0.01738

105625

–175.17

1045.3

0.4348

0.4432

–0.3611

2.5196

–35

0.002541

0.01738

99555

–174.73

1045.7

0.4358

0.4433

–0.3600

2.5138

–34

0.002701

0.01738

93860

–174.30

1046.1

0.4368

0.4433

–0.3590

2.5081

–33

0.002871

0.01738

88516

–173.86

1046.6

0.4377

0.4434

–0.3580

2.5024

–32

0.003051

0.01738

83500

–173.42

1047.0

0.4387

0.4434

–0.3570

2.4968

–31

0.003241

0.01738

78790

–172.98

1047.5

0.4396

0.4434

–0.3559

2.4911

–30

0.003442

0.01738

74366

–172.54

1047.9

0.4406

0.4435

–0.3549

2.4855

–29

0.003654

0.01738

70209

–172.10

1048.4

0.4416

0.4435

–0.3539

2.4800

–28

0.003878

0.01739

66303

–171.66

1048.8

0.4425

0.4436

–0.3529

2.4744

–27

0.004115

0.01739

62631

–171.22

1049.2

0.4435

0.4436

–0.3518

2.4689

–26

0.004365

0.01739

59179

–170.77

1049.7

0.4445

0.4437

–0.3508

2.4634

–25

0.004629

0.01739

55931

–170.33

1050.1

0.4454

0.4437

–0.3498

2.4580

–24

0.004908

0.01739

52876

–169.88

1050.6

0.4464

0.4437

–0.3488

2.4525

–23

0.005202

0.01739

50001

–169.43

1051.0

0.4473

0.4438

–0.3477

2.4471

–22

0.005512

0.01739

47294

–168.99

1051.4

0.4483

0.4439

–0.3467

2.4418

–21

0.005839

0.01740

44745

–168.54

1051.9

0.4493

0.4439

–0.3457

2.4364

–20

0.006184

0.01740

42345

–168.09

1052.3

0.4502

0.4440

–0.3447

2.4311

–19

0.006548

0.01740

40084

–167.64

1052.8

0.4512

0.4440

–0.3436

2.4258

–18

0.006932

0.01740

37953

–167.19

1053.2

0.4522

0.4441

–0.3426

2.4205

–17

0.007335

0.01740

35944

–166.73

1053.7

0.4531

0.4441

–0.3416

2.4153

–16

0.007761

0.01740

34050

–166.28

1054.1

0.4541

0.4442

–0.3406

2.4101

–15

0.008209

0.01740

32264

–165.82

1054.5

0.4551

0.4443

–0.3396

2.4049

–14

0.008681

0.01741

30580

–165.37

1055.0

0.4560

0.4443

–0.3385

2.3997

–13

0.009177

0.01741

28990

–164.91

1055.4

0.4570

0.4444

–0.3375

2.3946

–12

0.009700

0.01741

27490

–164.46

1055.9

0.4580

0.4445

–0.3365

2.3895

–11

0.010249

0.01741

26073

–164.00

1056.3

0.4589

0.4445

–0.3355

2.3844

–10

0.010827

0.01741

24736

–163.54

1056.7

0.4599

0.4446

–0.3344

2.3793

–9

0.011435

0.01741

23473

–163.08

1057.2

0.4609

0.4447

–0.3334

2.3743

–8

0.012075

0.01741

22279

–162.62

1057.6

0.4618

0.4448

–0.3324

2.3692

–7

0.012747

0.01742

21152

–162.15

1058.1

0.4628

0.4448

–0.3314

2.3642

–6

0.013453

0.01742

20086

–161.69

1058.5

0.4638

0.4449

–0.3303

2.3593

–5

0.014194

0.01742

19078

–161.23

1058.9

0.4647

0.4450

–0.3293

2.3543

–4

0.014974

0.01742

18125

–160.76

1059.4

0.4657

0.4451

–0.3283

2.3494

–3

0.015792

0.01742

17223

–160.29

1059.8

0.4667

0.4452

–0.3273

2.3445

–2

0.016651

0.01742

16370

–159.83

1060.3

0.4677

0.4453

–0.3263

2.3396

–1

0.017553

0.01742

15563

–159.36

1060.7

0.4686

0.4454

–0.3252

2.3348

0

0.018499

0.01743

14799

–158.89

1061.2

0.4696

0.4455

–0.3242

2.3300

1

0.019492

0.01743

14076

–158.42

1061.6

0.4706

0.4456

–0.3232

2.3251

2

0.020533

0.01743

13391

–157.95

1062.0

0.4715

0.4457

–0.3222

2.3204

3

0.021625

0.01743

12742

–157.48

1062.5

0.4725

0.4458

–0.3212

2.3156

4

0.022770

0.01743

12127

–157.00

1062.9

0.4735

0.4459

–0.3201

2.3109

5

0.023971

0.01743

11545

–156.53

1063.4

0.4745

0.4460

–0.3191

2.3062

6

0.025229

0.01743

10992

–156.05

1063.8

0.4754

0.4461

–0.3181

2.3015

7

0.026547

0.01744

10469

–155.58

1064.2

0.4764

0.4462

–0.3171

2.2968

8

0.027929

0.01744

9972.3

–155.10

1064.7

0.4774

0.4463

–0.3160

2.2921

9

0.029375

0.01744

9501.4

–154.62

1065.1

0.4783

0.4464

–0.3150

2.2875

10

0.030890

0.01744

9054.6

–154.15

1065.6

0.4793

0.4466

–0.3140

2.2829

11

0.032476

0.01744

8630.7

–153.67

1066.0

0.4803

0.4467

–0.3130

2.2783

12

0.034136

0.01744

8228.3

–153.18

1066.4

0.4813

0.4468

–0.3120

2.2738

13

0.035874

0.01744

7846.3

–152.70

1066.9

0.4822

0.4470

–0.3109

2.2692

14

0.037692

0.01745

7483.6

–152.22

1067.3

0.4832

0.4471

–0.3099

2.2647

15

0.039593

0.01745

7139.1

–151.74

1067.7

0.4842

0.4472

–0.3089

2.2602

16

0.041582

0.01745

6811.9

–151.25

1068.2

0.4852

0.4474

–0.3079

2.2557

17

0.043662

0.01745

6501.0

–150.77

1068.6

0.4861

0.4475

–0.3069

2.2513

18

0.045837

0.01745

6205.5

–150.28

1069.1

0.4871

0.4477

–0.3058

2.2468

19

0.048109

0.01745

5924.6

–149.79

1069.5

0.4881

0.4478

–0.3048

2.2424

20

0.050485

0.01746

5657.6

–149.30

1069.9

0.4891

0.4480

–0.3038

2.2380

21

0.052967

0.01746

5403.6

–148.81

1070.4

0.4900

0.4481

–0.3028

2.2337

22

0.055560

0.01746

5162.1

–148.32

1070.8

0.4910

0.4483

–0.3018

2.2293

23

0.058268

0.01746

4932.3

–147.83

1071.3

0.4920

0.4484

–0.3007

2.2250

24

0.061096

0.01746

4713.7

–147.34

1071.7

0.4930

0.4486

–0.2997

2.2207

25

0.064048

0.01746

4505.6

–146.85

1072.1

0.4939

0.4488

–0.2987

2.2164

26

0.067130

0.01746

4307.6

–146.35

1072.6

0.4949

0.4489

–0.2977

2.2121

27

0.070347

0.01747

4119.0

–145.86

1073.0

0.4959

0.4492

–0.2967

2.2078

28

0.073704

0.01747

3939.4

–145.36

1073.4

0.4969

0.4495

–0.2957

2.2036

29

0.077206

0.01747

3768.4

–144.86

1073.9

0.4979

0.4499

–0.2946

2.1994

30

0.080858

0.01747

3605.5

–144.36

1074.3

0.4988

0.4503

–0.2936

2.1952

31

0.084668

0.01747

3450.2

–143.86

1074.8

0.4998

0.4506

–0.2926

2.1910

32

0.088649

0.01602

3302.0

–0.01788

1075.2

1.0079

0.4510

0.0000

2.1868

33

0.092293

0.01602

3178.1

0.98981

1075.6

1.0074

0.4511

0.0020

2.1833

34

0.096069

0.01602

3059.3

1.9970

1076.1

1.0070

0.4512

0.0041

2.1797

35

0.099981

0.01602

2945.5

3.0039

1076.5

1.0066

0.4513

0.0061

2.1762

36

0.10403

0.01602

2836.5

4.0102

1076.9

1.0062

0.4513

0.0081

2.1727

37

0.10823

0.01602

2731.9

5.0163

1077.4

1.0058

0.4514

0.0102

2.1693

38

0.11258

0.01602

2631.7

6.0219

1077.8

1.0054

0.4515

0.0122

2.1658

39

0.11708

0.01602

2535.6

7.0272

1078.3

1.0051

0.4516

0.0142

2.1624

40

0.12173

0.01602

2443.4

8.0321

1078.7

1.0048

0.4517

0.0162

2.1590

41

0.12656

0.01602

2355.0

9.0367

1079.1

1.0044

0.4518

0.0182

2.1556

42

0.13155

0.01602

2270.1

10.041

1079.6

1.0041

0.4519

0.0202

2.1522

43

0.13671

0.01602

2188.7

11.045

1080.0

1.0038

0.4520

0.0222

2.1488

44

0.14205

0.01602

2110.6

12.049

1080.5

1.0036

0.4521

0.0242

2.1454

45

0.14757

0.01602

2035.6

13.052

1080.9

1.0033

0.4522

0.0262

2.1421

46

0.15328

0.01602

1963.6

14.055

1081.3

1.0031

0.4523

0.0282

2.1388

47

0.15919

0.01602

1894.4

15.058

1081.8

1.0028

0.4524

0.0302

2.1355

48

0.16530

0.01602

1828.0

16.061

1082.2

1.0026

0.4526

0.0321

2.1322

49

0.17161

0.01602

1764.2

17.064

1082.6

1.0024

0.4527

0.0341

2.1289

50

0.17813

0.01602

1702.9

18.066

1083.1

1.0022

0.4528

0.0361

2.1257

51

0.18487

0.01602

1644.0

19.068

1083.5

1.0020

0.4529

0.0381

2.1225

52

0.19184

0.01603

1587.4

20.070

1083.9

1.0018

0.4530

0.0400

2.1192

53

0.19903

0.01603

1533.0

21.071

1084.4

1.0016

0.4531

0.0420

2.1160

54

0.20646

0.01603

1480.6

22.073

1084.8

1.0014

0.4533

0.0439

2.1129

55

0.21414

0.01603

1430.3

23.074

1085.3

1.0012

0.4534

0.0459

2.1097

56

0.22206

0.01603

1381.9

24.075

1085.7

1.0011

0.4535

0.0478

2.1065

57

0.23024

0.01603

1335.4

25.077

1086.1

1.0009

0.4536

0.0497

2.1034

58

0.23868

0.01603

1290.6

26.077

1086.6

1.0008

0.4538

0.0517

2.1003

59

0.24740

0.01603

1247.5

27.078

1087.0

1.0006

0.4539

0.0536

2.0972

60

0.25639

0.01603

1206.1

28.079

1087.4

1.0005

0.4540

0.0555

2.0941

61

0.26567

0.01604

1166.2

29.079

1087.9

1.0004

0.4542

0.0575

2.0910

62

0.27524

0.01604

1127.7

30.079

1088.3

1.0002

0.4543

0.0594

2.0879

63

0.28511

0.01604

1090.7

31.080

1088.7

1.0001

0.4545

0.0613

2.0849

64

0.29529

0.01604

1055.1

32.080

1089.2

1.0000

0.4546

0.0632

2.0818

65

0.30579

0.01604

1020.8

33.080

1089.6

0.9999

0.4547

0.0651

2.0788

66

0.31662

0.01604

987.77

34.080

1090.0

0.9998

0.4549

0.0670

2.0758

67

0.32777

0.01605

955.93

35.079

1090.5

0.9997

0.4550

0.0689

2.0728

68

0.33927

0.01605

925.25

36.079

1090.9

0.9996

0.4552

0.0708

2.0699

69

0.35113

0.01605

895.68

37.079

1091.3

0.9995

0.4553

0.0727

2.0669

70

0.36334

0.01605

867.19

38.078

1091.8

0.9994

0.4555

0.0746

2.0640

71

0.37592

0.01605

839.72

39.078

1092.2

0.9993

0.4556

0.0765

2.0610

72

0.38889

0.01606

813.23

40.077

1092.7

0.9992

0.4558

0.0784

2.0581

73

0.40224

0.01606

787.69

41.076

1093.1

0.9992

0.4559

0.0802

2.0552

74

0.41599

0.01606

763.06

42.075

1093.5

0.9991

0.4561

0.0821

2.0523

75

0.43015

0.01606

739.30

43.074

1094.0

0.9990

0.4563

0.0840

2.0495

76

0.44473

0.01606

716.38

44.073

1094.4

0.9990

0.4564

0.0859

2.0466

77

0.45973

0.01607

694.26

45.072

1094.8

0.9989

0.4566

0.0877

2.0438

78

0.47518

0.01607

672.92

46.071

1095.2

0.9988

0.4567

0.0896

2.0409

79

0.49108

0.01607

652.32

47.070

1095.7

0.9988

0.4569

0.0914

2.0381

80

0.50744

0.01607

632.44

48.069

1096.1

0.9987

0.4571

0.0933

2.0353

81

0.52427

0.01608

613.25

49.068

1096.5

0.9987

0.4572

0.0951

2.0325

82

0.54159

0.01608

594.72

50.066

1097.0

0.9986

0.4574

0.0970

2.0297

83

0.55940

0.01608

576.82

51.065

1097.4

0.9986

0.4576

0.0988

2.0270

84

0.57772

0.01608

559.54

52.064

1097.8

0.9985

0.4578

0.1007

2.0242

85

0.59656

0.01609

542.84

53.062

1098.3

0.9985

0.4579

0.1025

2.0215

86

0.61593

0.01609

526.71

54.061

1098.7

0.9984

0.4581

0.1043

2.0188

87

0.63585

0.01609

511.13

55.059

1099.1

0.9984

0.4583

0.1062

2.0160

88

0.65632

0.01609

496.07

56.058

1099.6

0.9984

0.4585

0.1080

2.0133

89

0.67736

0.01610

481.51

57.056

1100.0

0.9983

0.4586

0.1098

2.0107

90

0.69899

0.01610

467.45

58.054

1100.4

0.9983

0.4588

0.1116

2.0080

91

0.72122

0.01610

453.85

59.053

1100.9

0.9983

0.4590

0.1134

2.0053

92

0.74405

0.01611

440.70

60.051

1101.3

0.9983

0.4592

0.1152

2.0027

93

0.76751

0.01611

427.98

61.049

1101.7

0.9982

0.4594

0.1171

2.0000

94

0.79161

0.01611

415.68

62.048

1102.1

0.9982

0.4596

0.1189

1.9974

95

0.81636

0.01612

403.79

63.046

1102.6

0.9982

0.4598

0.1207

1.9948

96

0.84178

0.01612

392.28

64.044

1103.0

0.9982

0.4599

0.1225

1.9922

97

0.86788

0.01612

381.15

65.042

1103.4

0.9981

0.4601

0.1242

1.9896

98

0.89468

0.01612

370.38

66.041

1103.9

0.9981

0.4603

0.1260

1.9870

99

0.92220

0.01613

359.96

67.039

1104.3

0.9981

0.4605

0.1278

1.9845

100

0.95044

0.01613

349.87

68.037

1104.7

0.9981

0.4607

0.1296

1.9819

101

0.97943

0.01613

340.10

69.035

1105.1

0.9981

0.4609

0.1314

1.9794

102

1.0092

0.01614

330.65

70.033

1105.6

0.9981

0.4611

0.1332

1.9769

103

1.0397

0.01614

321.50

71.032

1106.0

0.9981

0.4613

0.1350

1.9743

104

1.0710

0.01614

312.63

72.030

1106.4

0.9981

0.4615

0.1367

1.9718

105

1.1032

0.01615

304.05

73.028

1106.9

0.9981

0.4617

0.1385

1.9693

106

1.1361

0.01615

295.73

74.026

1107.3

0.9981

0.4619

0.1403

1.9669

107

1.1699

0.01616

287.68

75.024

1107.7

0.9981

0.4621

0.1420

1.9644

108

1.2046

0.01616

279.88

76.022

1108.1

0.9981

0.4623

0.1438

1.9619

109

1.2401

0.01616

272.32

77.021

1108.6

0.9981

0.4625

0.1455

1.9595

110

1.2766

0.01617

264.99

78.019

1109.0

0.9981

0.4627

0.1473

1.9570

111

1.3140

0.01617

257.89

79.017

1109.4

0.9981

0.4629

0.1490

1.9546

112

1.3523

0.01617

251.01

80.015

1109.8

0.9981

0.4632

0.1508

1.9522

113

1.3915

0.01618

244.34

81.013

1110.3

0.9981

0.4634

0.1525

1.9498

114

1.4318

0.01618

237.87

82.012

1110.7

0.9981

0.4636

0.1543

1.9474

115

1.4730

0.01618

231.60

83.010

1111.1

0.9982

0.4638

0.1560

1.9450

116

1.5153

0.01619

225.51

84.008

1111.5

0.9982

0.4640

0.1577

1.9427

117

1.5586

0.01619

219.62

85.006

1112.0

0.9982

0.4642

0.1595

1.9403

118

1.6030

0.01620

213.90

86.005

1112.4

0.9982

0.4644

0.1612

1.9380

119

1.6484

0.01620

208.35

87.003

1112.8

0.9982

0.4647

0.1629

1.9356

120

1.6949

0.01620

202.96

88.002

1113.2

0.9983

0.4649

0.1647

1.9333

121

1.7426

0.01621

197.74

89.000

1113.6

0.9983

0.4651

0.1664

1.9310

122

1.7914

0.01621

192.67

89.998

1114.1

0.9983

0.4653

0.1681

1.9287

123

1.8414

0.01622

187.75

90.997

1114.5

0.9983

0.4656

0.1698

1.9264

124

1.8925

0.01622

182.97

91.995

1114.9

0.9984

0.4658

0.1715

1.9241

125

1.9449

0.01623

178.34

92.994

1115.3

0.9984

0.4660

0.1732

1.9218

126

1.9985

0.01623

173.84

93.992

1115.7

0.9984

0.4662

0.1749

1.9195

127

2.0534

0.01623

169.47

94.991

1116.2

0.9985

0.4665

0.1766

1.9173

128

2.1096

0.01624

165.22

95.990

1116.6

0.9985

0.4667

0.1783

1.9150

129

2.1670

0.01624

161.10

96.988

1117.0

0.9986

0.4669

0.1800

1.9128

130

2.2258

0.01625

157.10

97.987

1117.4

0.9986

0.4672

0.1817

1.9106

131

2.2860

0.01625

153.22

98.986

1117.8

0.9986

0.4674

0.1834

1.9084

132

2.3475

0.01626

149.44

99.985

1118.3

0.9987

0.4677

0.1851

1.9061

133

2.4105

0.01626

145.77

100.98

1118.7

0.9987

0.4679

0.1868

1.9039

134

2.4749

0.01626

142.21

101.98

1119.1

0.9988

0.4682

0.1885

1.9018

135

2.5407

0.01627

138.74

102.98

1119.5

0.9988

0.4684

0.1902

1.8996

136

2.6081

0.01627

135.38

103.98

1119.9

0.9989

0.4686

0.1918

1.8974

137

2.6769

0.01628

132.10

104.98

1120.4

0.9989

0.4689

0.1935

1.8953

138

2.7473

0.01628

128.92

105.98

1120.8

0.9990

0.4691

0.1952

1.8931

139

2.8193

0.01629

125.83

106.98

1121.2

0.9990

0.4694

0.1969

1.8910

140

2.8929

0.01629

122.82

107.98

1121.6

0.9991

0.4697

0.1985

1.8888

141

2.9681

0.01630

119.90

108.98

1122.0

0.9991

0.4699

0.2002

1.8867

142

3.0450

0.01630

117.06

109.98

1122.4

0.9992

0.4702

0.2019

1.8846

143

3.1235

0.01631

114.29

110.98

1122.8

0.9993

0.4704

0.2035

1.8825

144

3.2038

0.01631

111.60

111.97

1123.3

0.9993

0.4707

0.2052

1.8804

145

3.2858

0.01632

108.99

112.97

1123.7

0.9994

0.4710

0.2068

1.8783

146

3.3696

0.01632

106.44

113.97

1124.1

0.9994

0.4712

0.2085

1.8762

147

3.4552

0.01633

103.97

114.97

1124.5

0.9995

0.4715

0.2101

1.8742

148

3.5426

0.01633

101.56

115.97

1124.9

0.9996

0.4718

0.2118

1.8721

149

3.6319

0.01634

99.216

116.97

1125.3

0.9997

0.4721

0.2134

1.8701

150

3.7231

0.01634

96.934

117.97

1125.7

0.9997

0.4723

0.2151

1.8680

151

3.8163

0.01635

94.714

118.97

1126.2

0.9998

0.4726

0.2167

1.8660

152

3.9114

0.01635

92.552

119.97

1126.6

0.9999

0.4729

0.2183

1.8640

153

4.0085

0.01636

90.448

120.97

1127.0

0.9999

0.4732

0.2200

1.8620

154

4.1076

0.01636

88.399

121.97

1127.4

1.0000

0.4735

0.2216

1.8599

155

4.2089

0.01637

86.405

122.97

1127.8

1.0001

0.4738

0.2232

1.8580

156

4.3122

0.01637

84.463

123.97

1128.2

1.0002

0.4741

0.2249

1.8560

157

4.4176

0.01638

82.571

124.97

1128.6

1.0003

0.4743

0.2265

1.8540

158

4.5253

0.01638

80.729

125.98

1129.0

1.0003

0.4746

0.2281

1.8520

159

4.6351

0.01639

78.934

126.98

1129.4

1.0004

0.4749

0.2297

1.8500

160

4.7472

0.01639

77.186

127.98

1129.8

1.0005

0.4753

0.2313

1.8481

161

4.8616

0.01640

75.483

128.98

1130.2

1.0006

0.4756

0.2329

1.8461

162

4.9783

0.01640

73.824

129.98

1130.6

1.0007

0.4759

0.2346

1.8442

163

5.0973

0.01641

72.207

130.98

1131.1

1.0008

0.4762

0.2362

1.8423

164

5.2187

0.01642

70.632

131.98

1131.5

1.0009

0.4765

0.2378

1.8403

165

5.3426

0.01642

69.097

132.98

1131.9

1.0010

0.4768

0.2394

1.8384

166

5.4689

0.01643

67.600

133.98

1132.3

1.0011

0.4771

0.2410

1.8365

167

5.5978

0.01643

66.141

134.98

1132.7

1.0012

0.4775

0.2426

1.8346

168

5.7292

0.01644

64.720

135.99

1133.1

1.0013

0.4778

0.2442

1.8327

169

5.8632

0.01644

63.333

136.99

1133.5

1.0014

0.4781

0.2458

1.8308

170

5.9998

0.01645

61.982

137.99

1133.9

1.0015

0.4785

0.2474

1.8290

171

6.1390

0.01645

60.664

138.99

1134.3

1.0016

0.4788

0.2489

1.8271

172

6.2810

0.01646

59.379

139.99

1134.7

1.0017

0.4791

0.2505

1.8252

173

6.4258

0.01647

58.125

141.00

1135.1

1.0018

0.4795

0.2521

1.8234

174

6.5733

0.01647

56.903

142.00

1135.5

1.0019

0.4798

0.2537

1.8215

175

6.7237

0.01648

55.710

143.00

1135.9

1.0020

0.4802

0.2553

1.8197

176

6.8769

0.01648

54.547

144.00

1136.3

1.0021

0.4805

0.2569

1.8179

177

7.0331

0.01649

53.412

145.00

1136.7

1.0022

0.4809

0.2584

1.8160

178

7.1922

0.01650

52.305

146.01

1137.1

1.0023

0.4813

0.2600

1.8142

179

7.3544

0.01650

51.225

147.01

1137.5

1.0025

0.4816

0.2616

1.8124

180

7.5196

0.01651

50.171

148.01

1137.9

1.0026

0.4820

0.2631

1.8106

181

7.6879

0.01651

49.142

149.02

1138.3

1.0027

0.4824

0.2647

1.8088

182

7.8593

0.01652

48.138

150.02

1138.7

1.0028

0.4828

0.2663

1.8070

183

8.0339

0.01653

47.158

151.02

1139.1

1.0029

0.4831

0.2678

1.8052

184

8.2118

0.01653

46.201

152.03

1139.5

1.0031

0.4835

0.2694

1.8035

185

8.3930

0.01654

45.267

153.03

1139.9

1.0032

0.4839

0.2709

1.8017

186

8.5775

0.01654

44.355

154.03

1140.3

1.0033

0.4843

0.2725

1.7999

187

8.7653

0.01655

43.465

155.04

1140.7

1.0034

0.4847

0.2741

1.7982

188

8.9566

0.01656

42.596

156.04

1141.0

1.0036

0.4851

0.2756

1.7964

189

9.1514

0.01656

41.747

157.04

1141.4

1.0037

0.4855

0.2772

1.7947

190

9.3497

0.01657

40.918

158.05

1141.8

1.0038

0.4859

0.2787

1.7930

191

9.5515

0.01658

40.108

159.05

1142.2

1.0040

0.4863

0.2802

1.7912

192

9.7570

0.01658

39.317

160.06

1142.6

1.0041

0.4868

0.2818

1.7895

193

9.9662

0.01659

38.545

161.06

1143.0

1.0042

0.4872

0.2833

1.7878

194

10.179

0.01659

37.790

162.07

1143.4

1.0044

0.4876

0.2849

1.7861

195

10.396

0.01660

37.053

163.07

1143.8

1.0045

0.4880

0.2864

1.7844

196

10.616

0.01661

36.332

164.08

1144.2

1.0047

0.4885

0.2879

1.7827

197

10.841

0.01661

35.628

165.08

1144.6

1.0048

0.4889

0.2895

1.7810

198

11.069

0.01662

34.940

166.09

1144.9

1.0049

0.4894

0.2910

1.7793

199

11.301

0.01663

34.268

167.09

1145.3

1.0051

0.4898

0.2925

1.7777

200

11.538

0.01663

33.611

168.10

1145.7

1.0052

0.4903

0.2940

1.7760

201

11.778

0.01664

32.968

169.10

1146.1

1.0054

0.4908

0.2956

1.7743

202

12.023

0.01665

32.341

170.11

1146.5

1.0055

0.4912

0.2971

1.7727

203

12.271

0.01665

31.727

171.12

1146.9

1.0057

0.4917

0.2986

1.7710

204

12.525

0.01666

31.127

172.12

1147.3

1.0058

0.4922

0.3001

1.7694

205

12.782

0.01667

30.540

173.13

1147.6

1.0060

0.4927

0.3016

1.7678

206

13.044

0.01667

29.967

174.14

1148.0

1.0062

0.4931

0.3031

1.7661

207

13.310

0.01668

29.406

175.14

1148.4

1.0063

0.4936

0.3047

1.7645

208

13.581

0.01669

28.857

176.15

1148.8

1.0065

0.4941

0.3062

1.7629

209

13.856

0.01669

28.321

177.16

1149.2

1.0066

0.4947

0.3077

1.7613

210

14.136

0.01670

27.796

178.17

1149.5

1.0068

0.4952

0.3092

1.7597

212

14.709

0.01671

26.781

180.18

1150.3

1.0071

0.4962

0.3122

1.7565

214

15.302

0.01673

25.809

182.20

1151.0

1.0075

0.4973

0.3152

1.7533

216

15.915

0.01674

24.879

184.21

1151.8

1.0078

0.4983

0.3182

1.7502

218

16.548

0.01676

23.988

186.23

1152.5

1.0082

0.4995

0.3211

1.7471

220

17.201

0.01677

23.135

188.25

1153.3

1.0085

0.5006

0.3241

1.7440

222

17.875

0.01679

22.317

190.27

1154.0

1.0089

0.5017

0.3271

1.7409

224

18.571

0.01680

21.534

192.29

1154.8

1.0093

0.5029

0.3300

1.7378

226

19.290

0.01681

20.783

194.31

1155.5

1.0096

0.5041

0.3330

1.7348

228

20.031

0.01683

20.063

196.33

1156.2

1.0100

0.5054

0.3359

1.7318

230

20.795

0.01684

19.373

198.35

1157.0

1.0104

0.5066

0.3388

1.7288

232

21.583

0.01686

18.710

200.37

1157.7

1.0108

0.5079

0.3418

1.7258

234

22.395

0.01687

18.074

202.40

1158.4

1.0112

0.5092

0.3447

1.7229

236

23.233

0.01689

17.464

204.42

1159.1

1.0116

0.5106

0.3476

1.7199

238

24.096

0.01691

16.878

206.45

1159.8

1.0120

0.5120

0.3505

1.7170

240

24.985

0.01692

16.316

208.47

1160.5

1.0125

0.5134

0.3534

1.7141

242

25.901

0.01694

15.775

210.50

1161.2

1.0129

0.5148

0.3563

1.7113

244

26.844

0.01695

15.256

212.53

1161.9

1.0133

0.5162

0.3592

1.7084

246

27.815

0.01697

14.757

214.56

1162.6

1.0138

0.5177

0.3620

1.7056

248

28.814

0.01698

14.277

216.59

1163.3

1.0142

0.5193

0.3649

1.7028

250

29.843

0.01700

13.816

218.62

1164.0

1.0147

0.5208

0.3678

1.7000

252

30.901

0.01702

13.373

220.65

1164.7

1.0152

0.5224

0.3706

1.6972

254

31.990

0.01703

12.946

222.68

1165.4

1.0156

0.5240

0.3735

1.6944

256

33.110

0.01705

12.535

224.72

1166.1

1.0161

0.5256

0.3763

1.6917

258

34.261

0.01707

12.140

226.75

1166.8

1.0166

0.5273

0.3792

1.6890

260

35.445

0.01708

11.760

228.79

1167.4

1.0171

0.5290

0.3820

1.6862

262

36.662

0.01710

11.394

230.83

1168.1

1.0176

0.5307

0.3848

1.6836

264

37.913

0.01712

11.041

232.87

1168.8

1.0181

0.5325

0.3876

1.6809

266

39.198

0.01714

10.702

234.90

1169.4

1.0186

0.5343

0.3904

1.6782

268

40.518

0.01715

10.374

236.94

1170.1

1.0192

0.5361

0.3932

1.6756

270

41.874

0.01717

10.059

238.99

1170.7

1.0197

0.5380

0.3960

1.6730

272

43.267

0.01719

9.7552

241.03

1171.4

1.0203

0.5399

0.3988

1.6704

274

44.697

0.01721

9.4621

243.07

1172.0

1.0208

0.5418

0.4016

1.6678

276

46.165

0.01722

9.1796

245.12

1172.7

1.0214

0.5438

0.4044

1.6652

278

47.671

0.01724

8.9070

247.16

1173.3

1.0219

0.5458

0.4071

1.6626

280

49.218

0.01726

8.6442

249.21

1173.9

1.0225

0.5478

0.4099

1.6601

282

50.804

0.01728

8.3905

251.26

1174.5

1.0231

0.5499

0.4127

1.6575

284

52.431

0.01730

8.1457

253.31

1175.2

1.0237

0.5520

0.4154

1.6550

286

54.100

0.01731

7.9094

255.36

1175.8

1.0243

0.5541

0.4182

1.6525

288

55.812

0.01733

7.6813

257.41

1176.4

1.0249

0.5562

0.4209

1.6500

290

57.567

0.01735

7.4610

259.47

1177.0

1.0255

0.5584

0.4236

1.6476

292

59.366

0.01737

7.2482

261.52

1177.6

1.0262

0.5606

0.4264

1.6451

294

61.210

0.01739

7.0426

263.58

1178.2

1.0268

0.5629

0.4291

1.6427

296

63.100

0.01741

6.8441

265.64

1178.8

1.0275

0.5652

0.4318

1.6402

298

65.037

0.01743

6.6521

267.70

1179.4

1.0281

0.5675

0.4345

1.6378

300

67.021

0.01745

6.4666

269.76

1180.0

.1.0288

0.5699

0.4372

1.6354


 Humidity Parameters Involving Saturation

The following definitions of humidity parameters involve the concept of moist air saturation:

Saturation humidity ratio Ws(t, p) is the humidity ratio of moist air saturated with respect to water (or ice) at the same temperature t and pressure p.

Saturated water vapor pressure enhancement factor was introduced by Goff and Gratch in 1943, significantly broadened by Wexler and Hyland in 1983, and recently updated by Herrmann et. al. in 2009. The enhancement factor is a function of temperature and total pressure. It represents the increase of the actual water vapor saturation pressure in moist air from the saturation pressure of pure water with no air present at specified temperature and elevated pressure.

(12)

where f is the water vapor pressure enhancement factor, ps is the corrected saturation water vapor pressure, and pws is the saturation vapor pressure of pure water.

This factor accounts for the nonideal behavior of the water vapor-air mixture in the saturated state. The nonideal behavior arises from: (a) the increase in vapor pressure because of the interaction between different molecular species in the gaseous phase of the mixture (the major contribution); (b) the increase in vapor pressure because of the superimposed pressure of the air on the condensed phase (the Poynting effect); and (c) the decrease in vapor pressure due to the solution of air in the water condensed phase with which the gas mixture is in equilibrium (the Raoult or Henry’s law effect). (This is a negligible decrease.). Figure 1 illustrates the effects of both pressure and temperature on the enhancement factor.

Enhancement Factor f of Real Moist Air for Constant Total Pressures p over Temperature t

Figure 1. Enhancement Factor f of Real Moist Air for Constant Total Pressures p over Temperature t


Relative humidity ϕ is the ratio of the actual water vapor partial pressure pw in moist air at the total pressure p and dew-point temperature td to the saturation water vapor partial pressure at the total pressure p and dry-bulb temperature t:

(13)

Note that Equations (13) and (23) have been revised so that they cover both the normal range of relative humidity where pws(t) < p and the extended range (e.g., atmospheric pressure drying kilns) where pws(t) ≥ p. The definitions in earlier editions applied only to the normal range.

Dew-point temperature td is the temperature of moist air saturated at pressure p, with the same humidity ratio W as that of the given sample of moist air. It is defined as the solution td(p, W) of the following equation:

(14)

Thermodynamic wet-bulb temperature t* is the temperature at which water (liquid or solid), by evaporating into moist air at dry-bulb temperature t and humidity ratio W, can bring air to saturation adiabatically at the same temperature t* while total pressure p is constant. This parameter is considered separately in the section on Thermodynamic Wet-Bulb and Dew-Point Temperature.

6. PERFECT GAS RELATIONSHIPS FOR DRY AND MOIST AIR

When moist air is considered a mixture of independent perfect gases (i.e., dry air and water vapor), each is assumed to obey the perfect gas equation of state as follows:

(15)

(16)

where

pda = partial pressure of dry air
pw = partial pressure of water vapor
V = total mixture volume
nda = number of moles of dry air
nw = number of moles of water vapor
R = universal gas constant, 1545.349 ft · lbf/lb mol · °R
T = absolute temperature, °R

The mixture also obeys the perfect gas equation:

(17)

or

(18)

where p = pda + pw is the total mixture pressure and n = nda + nw is the total number of moles in the mixture. From Equations (15) to (18), the mole fractions of dry air and water vapor are, respectively,

(19)

and

(20)

From Equations (8), (19), and (20), the humidity ratio W is

(21)

The saturation humidity ratio Ws is

(22)

The term pws represents the saturation pressure of water vapor in the absence of air at the given temperature t. This pressure pws is a function only of temperature and differs slightly from the vapor pressure of water in saturated moist air.

The relative humidity ϕ is defined in Equation (13). Using the second equality and eliminating the enhancement factors, which are not applicable using the perfect gas assumption, gives

(23)

Substituting Equation (22) for Ws into Equation (14),

(24)

where μ is degree of saturation W/Ws, dimensionless.

Both ϕ and μ are zero for dry air and unity for saturated moist air. At intermediate states, their values differ, substantially at higher temperatures.

The specific volume v of a moist air mixture is expressed in terms of a unit mass of dry air:

(25)

where V is the total volume of the mixture, mda is the mass of dry air, nda is the number of moles of dry air, and the value 28.966 lbda/kmol is the molar mass of dry air. By Equations (15) and (25), with the relation p = pda + pw,

(26)

Using Equations (8) and (19) with the relation 1 = xda + xw,

(27)

In Equations (26) and (27), v is specific volume, R is the universal molar gas constant, Rda is the specific gas constant of dry air, T is absolute temperature, p is total pressure, pw is partial pressure of water vapor, and W is humidity ratio.

In specific units, Equation (27) may be expressed as

(28)

where

v = specific volume, ft3/lbda
t = dry-bulb temperature, °F
W = humidity ratio, lbw/lbda
p = total pressure, psia

The enthalpy of a mixture of perfect gases equals the sum of the individual partial enthalpies of the components. Therefore, the specific enthalpy of moist air can be written as follows:

(29)

where hda is the specific enthalpy for dry air in Btu/lbda and hg is the specific enthalpy for saturated water vapor in Btu/lbw at the mixture’s temperature. As an approximation,

(30)

(31)

where t is the dry-bulb temperature in °F. The moist air specific enthalpy in Btu/lbda then becomes

(32)

7. THERMODYNAMIC WET-BULB AND DEW-POINT TEMPERATURE

For any state of moist air, a temperature t* exists at which liquid (or solid) water evaporates into the air to bring it to saturation at exactly this same temperature and total pressure (Harrison 1965). During adiabatic saturation, saturated air is expelled at a temperature equal to that of the injected water. In this constant-pressure process,

  • Humidity ratio increases from initial value W to Ws*, corresponding to saturation at temperature t*

  • Enthalpy increases from initial value h to hs*, corresponding to saturation at temperature t*

  • Mass of water added per unit mass of dry air is (Ws* – W), which adds energy to the moist air of amount (Ws* – W)hw*, where hw* denotes specific enthalpy in Btu/lbw of water added at temperature t*

Therefore, if the process is strictly adiabatic, conservation of enthalpy at constant total pressure requires that

(33)

Ws*, hw*, and hs* are functions only of temperature t* for a fixed value of pressure. The value of t* that satisfies Equation (33) for given values of h, W, and p is the thermodynamic wet-bulb temperature.

A psychrometer consists of two thermometers; one thermometer’s bulb is covered by a wick that has been thoroughly wetted with water. When the wet bulb is placed in an airstream, water evaporates from the wick, eventually reaching an equilibrium temperature called the wet-bulb temperature. This process is not one of adiabatic saturation, which defines the thermodynamic wet-bulb temperature, but one of simultaneous heat and mass transfer from the wet bulb. The fundamental mechanism of this process is described by the Lewis relation [Equation (40) in Chapter 6]. The thermodynamic wet-bulb temperature can be approximated by the measured wet-bulb temperature. Refer to ANSI/ASHRAE Standard 41.6-2014 for information on measurement of wet-bulb temperature. Measured wet-bulb temperature is not exactly equal to the adiabatic saturation temperature (or, thermodynamic wet-bulb temperature) according to ASHRAE RP-1460 (Brenner et al. 2010) because:

  • Radiative heat exchange occurs between wick (psychrometer) and environment.

  • Temperature of water being added to wick is not equal to the thermodynamic wet-bulb temperature of air.

  • Velocity of air flowing over the wick may not be sufficiently fast enough to prevent moisture in that airstream affecting the process of water evaporating from the wick into the airstream.

For more information see Greenspan and Wexler (1968) and Simões-Moreira (1999).

As defined, thermodynamic wet-bulb temperature is a unique property of a given moist air sample independent of measurement techniques.

Equation (33) is exact because it defines the thermodynamic wet-bulb temperature t*. Substituting the approximate perfect gas relation [Equation (32)] for h, the corresponding expression for hs*, and the approximate relation for saturated liquid water

(34)

into Equation (33), and solving for the humidity ratio,

(35)

where t and t* are in °F. Below freezing, the corresponding equations are

(36)

(37)

A wet/ice-bulb thermometer is imprecise when determining moisture content at 32°F.

The dew-point temperature td of moist air with humidity ratio W and pressure p was defined as the solution td(p, W) of Ws(p, td). For perfect gases, this reduces to

(38)

where pw is the water vapor partial pressure for the moist air sample and pws(td) is the saturation vapor pressure at temperature td. The saturation vapor pressure is obtained from Table 3 or by using Equation (5) or (6).

The dew-point temperature above and equal 32°F can be calculated from the water vapor partial pressure by the IAPWS-IF97 saturation temperature equation:

(39)

where

with

where

and the coefficients:

n1 = 0.116 705 214 527 67 E+04
n2 = –0.724 213 167 032 06 E+06
n3 = –0.170 738 469 400 92 E+02
n4 = 0.120 208 247 024 70 E+05
n5 = –0.323 255 503 223 33 E+07
n6 = 0.149 151 086 135 30 E+02
n7 = –0.482 326 573 615 91 E+04
n8 = 0.405 113 405 420 57 E+06
n9 = –0.238 555 575 678 49 E+00
n10 = 0.650 175 348 447 98 E+03

Equation (39) is valid for the water vapor partial pressures 0.08865 ≤ pw < 145.038 psia. It fits exactly to Equation (5). The dew-point temperature td of moist air at total pressures that approximately correspond to the barometric pressure differs negligibly from the saturation temperature of pure water at the same pressure pw (e.g., 0.03% at 15 psia and 0.05% at 30 psia total pressures).

The dew-point temperature below 32°F is obtained from Table 3 or iteratively by using the Equation (6). Alternatively, it can be calculated directly from the equation:

(40)

where

with the coefficients and exponents:

d0 = 0.212 573 393 068 044 4 E+03
d1 = –0.111 182 915 832 924 7 E+02
d2 = 0.101 399 557 485 811 1E+00
d3 = 0.212 958 716 178 593 0 E–05
e0 = 0.1 E+01
e1 = –0.868 954 548 461 757 7 E–01
e2 =0.229 516 184 515 270 4 E–02
e3 = –0.174 889 589 777 246 0 E–04

Equation (40) is valid for the water vapor partial pressures 2.81·10–44 ≤ pw ≤ 0.08865 psia.

In both Equations (39) and (40),

pw = water vapor partial pressure, psia
Td = absolute dew-point temperature, Td = (td/°F + 459.67)°R

8. NUMERICAL CALCULATION OF MOIST AIR PROPERTIES

The following are outlines, citing equations and tables already presented, for calculating moist air properties using perfect gas relations. These relations are accurate enough for most engineering calculations in air-conditioning practice, and are readily adapted to either hand or computer calculating methods. For more details, refer to Tables 15 through 18 in Chapter 1 of Olivieri (1996). Graphical procedures are discussed in the section on Psychrometric Charts.

SITUATION 1.

Given: Dry-bulb temperature t, Wet-bulb temperature t*, Pressure p

To Obtain

Use

Comments

pws(t*)

Table 3 or Equation (5) or (6)

Sat. press. for temp. t*

Ws*

Equation (21)

Using pws(t*)

W

Equation (33) or (35)

 

pws(t)

Table 3 or Equation (5) or (6)

Sat. press. for temp. t

Ws

Equation (21)

Using pws(t)

ϕ

Equation (23)

Using pws(t)

v

Equation (26)

 

h

Equation (30)

 

pw

Equation (36)

 

td

Table 3 with Equation (36), (37), or (38)


SITUATION 2.

Given: Dry-bulb temperature t, Dew-point temperature td, Pressure p

To Obtain

Use

Comments

pw = pws(td)

Table 3 or Equation (5) or (6)

Sat. press. for temp. td

W

Equation (20)

 

pws(t)

Table 3 or Equation (5) or (6)

Sat. press. for temp. t

Ws

Equation (21)

Using pws(t)

ϕ

Equation (23)

Using pws(t)

v

Equation (26)

 

h

Equation (30)

 

t*

Equation (21) and (33) or (35) with Table 3 or with Equation (5) or (6)

Requires trial-and-error or numerical solution method


SITUATION 3.

Given: Dry-bulb temperature t, Relative humidity ϕ, Pressure p

To Obtain

Use

Comments

pws(t)

Table 3 or Equation (5) or (6)

Sat. press. for temp. t

pw

Equation (22)

 

W

Equation (20)

 

Ws

Equation (21)

Using pws(t)

v

Equation (26)

 

h

Equation (30)

 

td

Table 3 with Equation (36), (37), or (38)

 

t*

Equation (21) and (33) or (35) with Table 3 or with Equation (5) or (6)

Requires trial-and-error or numerical solution method


 Moist Air Property Tables for Standard Pressure

Table 2 shows thermodynamic properties for standard atmospheric pressure at temperatures from –80 to 200°F calculated using the ASHRAE RP-1485 (Herrmann et al. 2009) research project numerical model. Properties of intermediate moist air states can be calculated using the degree of saturation μ:

(41)

(42)

These equations are accurate to about 662°F. At higher temperatures, errors can be significant.

9. PSYCHROMETRIC CHARTS

A psychrometric chart graphically represents the thermodynamic properties of moist air.

The choice of coordinates for a psychrometric chart is arbitrary. A chart with coordinates of enthalpy and humidity ratio provides convenient graphical solutions of many moist air problems with a minimum of thermodynamic approximations. ASHRAE developed five such psychrometric charts. Chart 1 is shown as Figure 2; the others may be obtained through ASHRAE.

Charts 1, 2, and 3 are for sea-level pressure, Chart 4 is for 5000 ft altitude (24.89 in. Hg), and Chart 5 is for 7500 ft altitude (22.65 in. Hg). All charts use oblique-angle coordinates of enthalpy and humidity ratio, and are consistent with the data of Table 2 and the properties computation methods of Hyland and Wexler (1983a) and ASHRAE research project RP-1485. Palmatier (1963) describes the geometry of chart construction applying specifically to Charts 1 and 4.

The dry-bulb temperature ranges covered by the charts are

Charts 1, 4, 5

Normal temperature

32 to 120°F

Chart 2

Low temperature

–40 to 50°F

Chart 3

High temperature

60 to 250°F

Psychrometric properties or charts for other barometric pressures can be derived by interpolation. Sufficiently exact values for most purposes can be derived by methods described in the section on Perfect Gas Relationships for Dry and Moist Air. Constructing charts for altitude conditions has been discussed by Haines (1961), Karig (1946), and Rohsenow (1946).

Comparison of charts 1 and 4 by overlay reveals the following:

  • The dry-bulb (db) lines coincide.

  • Wet-bulb (wb) lines for a given temperature originate at the intersections of the corresponding dry-bulb line and the two saturation curves, and they have the same slope.

  • Humidity ratio W and enthalpy h for a given dry- and wet-bulb temperature increase with altitude, but there is little change in relative humidity (rh).

  • Volume v changes rapidly; for a given dry-bulb temperature and humidity ratio, it is practically inversely proportional to barometric pressure.

The following table compares properties at sea level (chart 1) and 5000 ft (chart 4):

Chart No.

db

wb

h

W

rh

v

1

100

81

44.6

0.0186

45

14.5

4

100

81

49.8

0.0234

46

17.6

Figure 2 shows humidity ratio lines (horizontal) for the range from 0 (dry air) to 0.03 lbw/lbda. Enthalpy lines are oblique lines across the chart precisely parallel to each other.


Dry-bulb temperature lines are straight, not precisely parallel to each other, and inclined slightly from the vertical position. Thermodynamic wet-bulb temperature lines are oblique and in a slightly different direction from enthalpy lines. They are straight but are not precisely parallel to each other.

Relative humidity lines are shown in intervals of 10%. The saturation curve is the line of 100% rh, whereas the horizontal line for W = 0 (dry air) is the line for 0% rh.

Specific volume lines are straight but are not precisely parallel to each other.

A narrow region above the saturation curve has been developed for fog conditions of moist air. This two-phase region represents a mechanical mixture of saturated moist air and liquid water, with the two components in thermal equilibrium. Isothermal lines in the fog region coincide with extensions of thermodynamic wet-bulb temperature lines. If required, the fog region can be further expanded by extending humidity ratio, enthalpy, and thermodynamic wet-bulb temperature lines.

The protractor to the left of the chart shows two scales: one for sensible/total heat ratio, and one for the ratio of enthalpy difference to humidity ratio difference. The protractor is used to establish the direction of a condition line on the psychrometric chart.

Example 1 shows use of the ASHRAE psychrometric chart to determine moist air properties.

ASHRAE Psychrometric Chart No. 1

Figure 2. ASHRAE Psychrometric Chart No. 1

Example 1.

Moist air exists at 100°F dry-bulb temperature, 65°F thermodynamic wet-bulb temperature, and 14.696 psia (29.921 in. Hg) pressure. Determine the humidity ratio, enthalpy, dew-point temperature, relative humidity, and specific volume.

Solution: Locate state point on chart 1 (Figure 2) at the intersection of 100°F dry-bulb temperature and 65°F thermodynamic wet-bulb temperature lines. Read humidity ratio W = 0.00523 lbw/lbda.

The enthalpy can be found by using two triangles to draw a line parallel to the nearest enthalpy line (30 Btu/lbda) through the state point to the nearest edge scale. Read h = 29.80 Btu/lbda.

Dew-point temperature can be read at the intersection of W = 0.00523 lbw/lbda with the saturation curve. Thus, td = 40°F.

Relative humidity ϕ can be estimated directly. Thus, ϕ = 13%.

Specific volume can be found by linear interpolation between the volume lines for 14.0 and 14.5 ft3/lbda. Thus, v = 14.22 ft3/lbda.


10. TYPICAL AIR-CONDITIONING PROCESSES

The ASHRAE psychrometric chart can be used to solve numerous process problems with moist air. Its use is best explained through illustrative examples. In each of the following examples, the process takes place at a constant total pressure of 14.696 psia.

 Moist Air Sensible Heating or Cooling

Adding heat alone to or removing heat alone from moist air is represented by a horizontal line on the ASHRAE chart, because the humidity ratio remains unchanged.

Figure 3 shows a device that adds heat to a stream of moist air. For steady-flow conditions, the required rate of heat addition is

(43)

Example 2.

Moist air, saturated at 35°F, enters a heating coil at a rate of 20,000 cfm. Air leaves the coil at 100°F. Find the required rate of heat addition.

Solution: Figure 4 schematically shows the solution. State 1 is located on the saturation curve at 35°F. Thus, h1 = 13.01 Btu/lbda, W1 = 0.00428 lbw/lbda, and v1 = 12.55 ft3/lbda. State 2 is located at the intersection of t = 100°F and W2 = W1 = 0.00428 lbw/lbda. Thus, h2 = 28.77 Btu/lbda. The mass flow of dry air is

From Equation (43),


 Moist Air Cooling and Dehumidification

Moisture condensation occurs when moist air is cooled to a temperature below its initial dew point. Figure 5 shows a schematic cooling coil where moist air is assumed to be uniformly processed. Although water can be removed at various temperatures ranging from the initial dew point to the final saturation temperature, it is assumed that condensed water is cooled to the final air temperature t2 before it drains from the system.

For the system in Figure 4, the steady-flow energy and material balance equations are

Thus,

(44)

(45)

Example 3.

Moist air at 85°F dry-bulb temperature and 50% rh enters a cooling coil at 10,000 cfm and is processed to a final saturation condition at 50°F. Find the tons of refrigeration required.

Solution: Figure 6 shows the schematic solution. State 1 is located at the intersection of t = 85°F and ϕ = 50%. Thus, h1 = 34.62 Btu/lbda, W1 = 0.01292 lbw/lbda, and v1 = 14.01 ft3/lbda. State 2 is located on the saturation curve at 50°F. Thus, h2 = 20.30 Btu/lbda and W2 = 0.00766 lbw/lbda. From Table 3, hw2 = 18.07 Btu/lbw. The mass flow of dry air is

From Equation (45),


Schematic of Device for Heating Moist Air

Figure 3. Schematic of Device for Heating Moist Air


Schematic Solution for Example 2

Figure 4. Schematic Solution for Example 2


 Adiabatic Mixing of Two Moist Airstreams

A common process in air-conditioning systems is the adiabatic mixing of two moist airstreams. Figure 7 schematically shows the problem. Adiabatic mixing is governed by three equations:

Eliminating gives

(46)

according to which, on the ASHRAE chart, the state point of the resulting mixture lies on the straight line connecting the state points of the two streams being mixed, and divides the line into two segments, in the same ratio as the masses of dry air in the two streams.

Schematic of Device for Cooling Moist Air

Figure 5. Schematic of Device for Cooling Moist Air


Schematic Solution for Example 3

Figure 6. Schematic Solution for Example 3


Example 4.

A stream of 5000 cfm of outdoor air at 40°F dry-bulb temperature and 35°F thermodynamic wet-bulb temperature is adiabatically mixed with 15,000 cfm of recirculated air at 75°F dry-bulb temperature and 50% rh. Find the dry-bulb temperature and thermodynamic wet-bulb temperature of the resulting mixture.

Solution: Figure 8 shows the schematic solution. States 1 and 2 are located on the ASHRAE chart: v1 = 12.65 ft3/lbda, and v2 = 13.68 ft3/lbda. Therefore,

According to Equation (46),

Consequently, the length of line segment 1-3 is 0.735 times the length of entire line 1-2. Using a ruler, state 3 is located, and the values t3 = 65.9°F and t3* = 56.6°F found.


Adiabatic Mixing of Two Moist Airstreams

Figure 7. Adiabatic Mixing of Two Moist Airstreams


Schematic Solution for Example 4

Figure 8. Schematic Solution for Example 4


 Adiabatic Mixing of Water Injected into Moist Air

Steam or liquid water can be injected into a moist airstream to raise its humidity, as shown in Figure 9. If mixing is adiabatic, the following equations apply:

Therefore,

(47)

according to which, on the ASHRAE chart, the final state point of the moist air lies on a straight line in the direction fixed by the specific enthalpy of the injected water, drawn through the initial state point of the moist air.

Schematic Showing Injection of Water into Moist Air

Figure 9. Schematic Showing Injection of Water into Moist Air


Schematic Solution for Example 5

Figure 10. Schematic Solution for Example 5


Example 5.

Moist air at 70°F dry-bulb and 45°F thermodynamic wet-bulb temperature is to be processed to a final dew-point temperature of 55°F by adiabatic injection of saturated steam at 230°F. The rate of dry airflow is 200 lbda/min. Find the final dry-bulb temperature of the moist air and the rate of steam flow required.

Solution: Figure 10 shows the schematic solution. By Table 3, the enthalpy of the steam hg = 1157 Btu/lbw. Therefore, according to Equation (47), the condition line on the ASHRAE chart connecting states 1 and 2 must have a direction:

The condition line can be drawn with the Δh/ΔW protractor. First, establish the reference line on the protractor by connecting the origin with the value Δh/ΔW = 1157 Btu/lbw. Draw a second line parallel to the reference line and through the initial state point of the moist air. This second line is the condition line. State 2 is established at the intersection of the condition line with the horizontal line extended from the saturation curve at 55°F (td2 = 55°F). Thus, t2 = 72.2°F.

Values of W2 and W1 can be read from the chart. The required steam flow is


 Space Heat Absorption and Moist Air Moisture Gains

Air conditioning required for a space is usually determined by (1) the quantity of moist air to be supplied, and (2) the supply air condition necessary to remove given amounts of energy and water from the space at the exhaust condition specified.

Figure 11 shows a space with incident rates of energy and moisture gains. The quantity qs denotes the net sum of all rates of heat gain in the space, arising from transfers through boundaries and from sources within the space. This heat gain involves energy addition alone and does not include energy contributions from water (or water vapor) addition. It is usually called the sensible heat gain. The quantity denotes the net sum of all rates of moisture gain on the space arising from transfers through boundaries and from sources within the space. Each pound of water vapor added to the space adds an amount of energy equal to its specific enthalpy.

Assuming steady-state conditions, governing equations are

or

(48)

(49)

The left side of Equation (48) represents the total rate of energy addition to the space from all sources. By Equations (48) and (49),

according to which, on the ASHRAE chart and for a given state of withdrawn air, all possible states (conditions) for supply air must lie on a straight line drawn through the state point of withdrawn air, with its direction specified by the numerical value of . This line is the condition line for the given problem.

Schematic of Air Conditioned Space

Figure 11. Schematic of Air Conditioned Space


Schematic Solution for Example 6

Figure 12. Schematic Solution for Example 6


Example 6.

Moist air is withdrawn from a room at 80°F dry-bulb temperature and 66°F thermodynamic wet-bulb temperature. The sensible rate of heat gain for the space is 30,000 Btu/h. A rate of moisture gain of 10 lbw/h occurs from the space occupants. This moisture is assumed as saturated water vapor at 90°F. Moist air is introduced into the room at a dry-bulb temperature of 60°F. Find the required thermodynamic wet-bulb temperature and volume flow rate of the supply air.

Solution: Figure 12 shows the schematic solution. State 2 is located on the ASHRAE chart. From Table 3, the specific enthalpy of the added water vapor is hg = 1100.43 Btu/lbw. From Equation (50),

With the Δh/ΔW protractor, establish a reference line of direction Δh/ΔW = 4100 Btu/lbw. Parallel to this reference line, draw a straight line on the chart through state 2. The intersection of this line with the 60°F dry-bulb temperature line is state 1. Thus, t1* = 56.4°F.

An alternative (and approximately correct) procedure in establishing the condition line is to use the protractor’s sensible/total heat ratio scale instead of the Δh/ΔW scale. The quantity ΔHs/ΔHt is the ratio of rate of sensible heat gain for the space to rate of total energy gain for the space. Therefore,

Note that ΔHs/ΔHt = 0.732 on the protractor coincides closely with Δh/ΔW = 4100 Btu/lbw.

The flow of dry air can be calculated from either Equation (48) or (49). From Equation (48),

At state 1, v1 = 13.29 ft3/lbda.

Therefore, supply volume = = 101.5 × 13.29 = 1349 cfm.


11. TRANSPORT PROPERTIES OF MOIST AIR

For certain scientific and experimental work, particularly in the heat transfer field, many other moist air properties are important. Generally classified as transport properties, these include diffusion coefficient, viscosity, thermal conductivity, and thermal diffusion factor.

Table 4 shows diffusion coefficients calculated by Mason and Monchick (1965). Table 5, calculated using ASHRAE LibHuAirProp Software (ASHRAE 2023) based on ASHRAE RP-1767 (Herrmann et al. 2018, 2020), shows values of density, viscosity, kinematic viscosity, thermal conductivity, and Prandtl number of saturated moist air and dry air at the pressure 14.696 psia and temperatures from –80°F to 200°F.

The following properties are shown in Table 5:

t = Fahrenheit temperature, °F, based on the ITS-90 and expressed relative to absolute temperature T in Rankine by the following relation:

Table 4 Calculated Diffusion Coefficients Dwa for Water/Air at 14.696 psia

Temp., °F

 

Dwa, ft2/h

 

Temp., °F

 

Dwa, ft2/h

 

Temp., °F

 

Dwa, ft2/h

–100

 

0.504

 

40

 

0.884

 

140

 

1.205

–50

 

0.600

 

50

 

0.915

 

150

 

1.240

–40

 

0.655

 

60

 

0.942

 

200

 

1.414

–30

 

0.682

 

70

 

0.973

 

250

 

1.600

–20

 

0.709

 

80

 

1.008

 

300

 

1.794

–10

 

0.736

 

90

 

1.042

 

350

 

1.996

0

 

0.767

 

100

 

1.073

 

400

 

2.205

10

 

0.794

 

110

 

1.104

 

450

 

2.422

20

 

0.825

 

120

 

1.139

 

500

 

2.647

30

 

0.853

 

130

 

1.170

       


Viscosity of Moist Air as Function of Temperature with Lines of Constant Humidity Ratio Ranging from W = 0 (dry air) to W = 10 lbw/lbda and Water Vapor (steam) at Standard Atmospheric Pressure of 14.696 psia

Figure 13. Viscosity of Moist Air as Function of Temperature with Lines of Constant Humidity Ratio Ranging from W = 0 (dry air) to W = 10 lbw/lbda and Water Vapor (steam) at Standard Atmospheric Pressure of 14.696 psia


Ws = humidity ratio at saturation, lbw/lbda; gaseous phase (moist air) exists in equilibrium with condensed phase (liquid or solid) at given temperature and pressure (standard atmospheric pressure). At given values of temperature and pressure, humidity ratio W can have any value from zero to Ws
ρda = density of dry air, lb/ft3kg/m3
ρs = density of moist air at saturation, lb/ft3
ηda = viscosity of dry air, lb/(ft·h)
ηs = viscosity of moist air at saturation, lb/(ft·h)
νda = kinematic viscosity of dry air, ft/h
νs = kinematic viscosity of moist air at saturation, ft/h
λda = thermal conductivity of dry air, Btu/(ft·h·°R)
λs = thermal conductivity of moist air at saturation, Btu/(ft·h·°R)
Prda = Prandtl number of dry air
Prs = Prandtl number of moist air at saturation

Table 5 Transport Properties of Saturated Moist Air and Dry Air at Atmospheric Pressure, 14.696 psia

Temp., t °F

Humidity Ratio, Ws lbw/lbda

Density, lb/ft3

Viscosity, lb/(ft·h)

Kinematic Viscosity, ft/h

Thermal Cond., Btu/(ft·h·°R)

Prandtl Number (—)

ρda

ρs

ηda

ηs

νda

νs

λda

λs

Prda

Prs

–80

0.0000049

0.10468

0.10468

0.03373

0.03373

0.3222

0.3222

0.01122

0.01122

0.7228

0.7228

–79

0.0000053

0.10440

0.10440

0.03381

0.03381

0.3238

0.3238

0.01124

0.01124

0.7227

0.7227

–78

0.0000057

0.10413

0.10413

0.03388

0.03388

0.3254

0.3254

0.01127

0.01127

0.7225

0.7225

–77

0.0000062

0.10385

0.10385

0.03396

0.03396

0.3270

0.3270

0.01130

0.01130

0.7224

0.7224

–76

0.0000067

0.10358

0.10358

0.03403

0.03403

0.3285

0.3285

0.01132

0.01132

0.7223

0.7223

–75

0.0000072

0.10331

0.10331

0.03410

0.03410

0.3301

0.3301

0.01135

0.01135

0.7222

0.7222

–74

0.0000078

0.10304

0.10304

0.03418

0.03418

0.3317

0.3317

0.01138

0.01138

0.7220

0.7220

–73

0.0000084

0.10277

0.10277

0.03425

0.03425

0.3333

0.3333

0.01140

0.01140

0.7219

0.7219

–72

0.0000090

0.10251

0.10251

0.03433

0.03433

0.3349

0.3349

0.01143

0.01143

0.7218

0.7218

–71

0.0000097

0.10224

0.10224

0.03440

0.03440

0.3365

0.3365

0.01146

0.01145

0.7216

0.7216

–70

0.0000104

0.10198

0.10198

0.03447

0.03447

0.3381

0.3381

0.01148

0.01148

0.7215

0.7215

–69

0.0000112

0.10171

0.10171

0.03455

0.03455

0.3397

0.3396

0.01151

0.01151

0.7214

0.7214

–68

0.0000120

0.10145

0.10145

0.03462

0.03462

0.3413

0.3413

0.01153

0.01153

0.7213

0.7213

–67

0.0000129

0.10119

0.10119

0.03469

0.03469

0.3429

0.3429

0.01156

0.01156

0.7211

0.7211

–66

0.0000139

0.10093

0.10093

0.03477

0.03477

0.3445

0.3445

0.01159

0.01159

0.7210

0.7210

–65

0.0000149

0.10068

0.10067

0.03484

0.03484

0.3461

0.3461

0.01161

0.01161

0.7209

0.7209

–64

0.0000160

0.10042

0.10042

0.03491

0.03491

0.3477

0.3477

0.01164

0.01164

0.7208

0.7208

–63

0.0000172

0.10016

0.10016

0.03499

0.03499

0.3493

0.3493

0.01167

0.01167

0.7206

0.7206

–62

0.0000184

0.09991

0.09991

0.03506

0.03506

0.3509

0.3509

0.01169

0.01169

0.7205

0.7205

–61

0.0000198

0.09966

0.09966

0.03513

0.03513

0.3525

0.3525

0.01172

0.01172

0.7204

0.7204

–60

0.0000212

0.09941

0.09941

0.03521

0.03521

0.3542

0.3542

0.01174

0.01174

0.7203

0.7203

–59

0.0000227

0.09916

0.09916

0.03528

0.03528

0.3558

0.3558

0.01177

0.01177

0.7201

0.7202

–58

0.0000243

0.09891

0.09891

0.03535

0.03535

0.3574

0.3574

0.01180

0.01180

0.7200

0.7200

–57

0.0000260

0.09866

0.09866

0.03543

0.03542

0.3591

0.3591

0.01182

0.01182

0.7199

0.7199

–56

0.0000279

0.09842

0.09841

0.03550

0.03550

0.3607

0.3607

0.01185

0.01185

0.7198

0.7198

–55

0.0000298

0.09817

0.09817

0.03557

0.03557

0.3623

0.3623

0.01187

0.01187

0.7197

0.7197

–54

0.0000319

0.09793

0.09793

0.03564

0.03564

0.3640

0.3640

0.01190

0.01190

0.7195

0.7196

–53

0.0000341

0.09769

0.09768

0.03572

0.03572

0.3656

0.3656

0.01193

0.01193

0.7194

0.7194

–52

0.0000365

0.09744

0.09744

0.03579

0.03579

0.3673

0.3673

0.01195

0.01195

0.7193

0.7193

–51

0.0000390

0.09720

0.09720

0.03586

0.03586

0.3689

0.3689

0.01198

0.01198

0.7192

0.7192

–50

0.0000416

0.09697

0.09696

0.03593

0.03593

0.3706

0.3706

0.01200

0.01200

0.7191

0.7191

–49

0.0000445

0.09673

0.09673

0.03601

0.03600

0.3722

0.3722

0.01203

0.01203

0.7190

0.7190

–48

0.0000475

0.09649

0.09649

0.03608

0.03608

0.3739

0.3739

0.01206

0.01206

0.7188

0.7189

–47

0.0000507

0.09626

0.09625

0.03615

0.03615

0.3756

0.3756

0.01208

0.01208

0.7187

0.7188

–46

0.0000541

0.09602

0.09602

0.03622

0.03622

0.3772

0.3772

0.01211

0.01211

0.7186

0.7186

–45

0.0000577

0.09579

0.09579

0.03629

0.03629

0.3789

0.3789

0.01213

0.01213

0.7185

0.7185

–44

0.0000615

0.09556

0.09555

0.03637

0.03636

0.3806

0.3806

0.01216

0.01216

0.7184

0.7184

–43

0.0000656

0.09533

0.09532

0.03644

0.03644

0.3822

0.3822

0.01219

0.01219

0.7183

0.7183

–42

0.0000699

0.09510

0.09509

0.03651

0.03651

0.3839

0.3839

0.01221

0.01221

0.7182

0.7182

–41

0.0000744

0.09487

0.09487

0.03658

0.03658

0.3856

0.3856

0.01224

0.01224

0.7180

0.7181

–40

0.0000793

0.09464

0.09464

0.03665

0.03665

0.3873

0.3873

0.01226

0.01226

0.7179

0.7180

–39

0.0000844

0.09442

0.09441

0.03673

0.03672

0.3890

0.3890

0.01229

0.01229

0.7178

0.7179

–38

0.0000898

0.09419

0.09419

0.03680

0.03679

0.3907

0.3907

0.01232

0.01231

0.7177

0.7178

–37

0.0000956

0.09397

0.09396

0.03687

0.03687

0.3924

0.3923

0.01234

0.01234

0.7176

0.7176

–36

0.0001017

0.09374

0.09374

0.03694

0.03694

0.3940

0.3940

0.01237

0.01237

0.7175

0.7175

–35

0.0001081

0.09352

0.09352

0.03701

0.03701

0.3957

0.3957

0.01239

0.01239

0.7174

0.7174

–34

0.0001150

0.09330

0.09329

0.03708

0.03708

0.3974

0.3974

0.01242

0.01242

0.7173

0.7173

–33

0.0001222

0.09308

0.09307

0.03715

0.03715

0.3992

0.3991

0.01244

0.01244

0.7171

0.7172

–32

0.0001298

0.09286

0.09286

0.03722

0.03722

0.4009

0.4008

0.01247

0.01247

0.7170

0.7171

–31

0.0001379

0.09264

0.09264

0.03730

0.03729

0.4026

0.4026

0.01249

0.01249

0.7169

0.7170

–30

0.0001465

0.09243

0.09242

0.03737

0.03736

0.4043

0.4043

0.01252

0.01252

0.7168

0.7169

–29

0.0001555

0.09221

0.09220

0.03744

0.03743

0.4060

0.4060

0.01255

0.01254

0.7167

0.7168

–28

0.0001650

0.09200

0.09199

0.03751

0.03750

0.4077

0.4077

0.01257

0.01257

0.7166

0.7167

–27

0.0001751

0.09178

0.09177

0.03758

0.03757

0.4094

0.4094

0.01260

0.01260

0.7165

0.7166

–26

0.0001857

0.09157

0.09156

0.03765

0.03764

0.4112

0.4111

0.01262

0.01262

0.7164

0.7165

–25

0.0001970

0.09136

0.09135

0.03772

0.03772

0.4129

0.4129

0.01265

0.01265

0.7163

0.7164

–24

0.0002088

0.09115

0.09114

0.03779

0.03779

0.4146

0.4146

0.01267

0.01267

0.7162

0.7163

–23

0.0002213

0.09094

0.09093

0.03786

0.03786

0.4164

0.4163

0.01270

0.01270

0.7161

0.7162

–22

0.0002345

0.09073

0.09072

0.03793

0.03793

0.4181

0.4181

0.01272

0.01272

0.7160

0.7161

–21

0.0002485

0.09052

0.09051

0.03800

0.03800

0.4198

0.4198

0.01275

0.01275

0.7159

0.7160

–20

0.0002632

0.09032

0.09030

0.03807

0.03807

0.4216

0.4215

0.01278

0.01277

0.7158

0.7159

–19

0.0002786

0.09011

0.09009

0.03814

0.03814

0.4233

0.4233

0.01280

0.01280

0.7157

0.7158

–18

0.0002949

0.08990

0.08989

0.03821

0.03821

0.4251

0.4250

0.01283

0.01282

0.7155

0.7157

–17

0.0003121

0.08970

0.08968

0.03828

0.03828

0.4268

0.4268

0.01285

0.01285

0.7154

0.7156

–16

0.0003302

0.08950

0.08948

0.03835

0.03835

0.4286

0.4285

0.01288

0.01287

0.7153

0.7155

–15

0.0003493

0.08929

0.08928

0.03843

0.03841

0.4303

0.4303

0.01290

0.01290

0.7152

0.7154

–14

0.0003694

0.08909

0.08907

0.03850

0.03848

0.4321

0.4320

0.01293

0.01292

0.7151

0.7153

–13

0.0003905

0.08889

0.08887

0.03857

0.03855

0.4338

0.4338

0.01295

0.01295

0.7150

0.7152

–12

0.0004127

0.08869

0.08867

0.03864

0.03862

0.4356

0.4356

0.01298

0.01298

0.7149

0.7151

–11

0.0004361

0.08850

0.08847

0.03870

0.03869

0.4374

0.4373

0.01300

0.01300

0.7148

0.7151

–10

0.0004607

0.08830

0.08827

0.03877

0.03876

0.4391

0.4391

0.01303

0.01303

0.7147

0.7150

–9

0.0004866

0.08810

0.08807

0.03884

0.03883

0.4409

0.4409

0.01305

0.01305

0.7146

0.7149

–8

0.0005138

0.08790

0.08788

0.03891

0.03890

0.4427

0.4426

0.01308

0.01308

0.7145

0.7148

–7

0.0005425

0.08771

0.08768

0.03898

0.03897

0.4445

0.4444

0.01310

0.01310

0.7144

0.7147

–6

0.0005725

0.08752

0.08749

0.03905

0.03904

0.4462

0.4462

0.01313

0.01313

0.7143

0.7146

–5

0.0006041

0.08732

0.08729

0.03912

0.03910

0.4480

0.4480

0.01316

0.01315

0.7142

0.7145

–4

0.0006373

0.08713

0.08710

0.03919

0.03917

0.4498

0.4498

0.01318

0.01318

0.7141

0.7145

–3

0.0006721

0.08694

0.08690

0.03926

0.03924

0.4516

0.4516

0.01321

0.01320

0.7140

0.7144

–2

0.0007087

0.08675

0.08671

0.03933

0.03931

0.4534

0.4533

0.01323

0.01322

0.7139

0.7143

–1

0.0007471

0.08656

0.08652

0.03940

0.03938

0.4552

0.4551

0.01326

0.01325

0.7138

0.7142

0

0.0007875

0.08637

0.08633

0.03947

0.03945

0.4570

0.4569

0.01328

0.01327

0.7137

0.7141

1

0.0008298

0.08618

0.08614

0.03954

0.03951

0.4588

0.4587

0.01331

0.01330

0.7136

0.7141

2

0.0008741

0.08599

0.08595

0.03961

0.03958

0.4606

0.4605

0.01333

0.01332

0.7136

0.7140

3

0.0009207

0.08581

0.08576

0.03968

0.03965

0.4624

0.4623

0.01336

0.01335

0.7135

0.7139

4

0.0009695

0.08562

0.08557

0.03975

0.03972

0.4642

0.4641

0.01338

0.01337

0.7134

0.7139

5

0.0010207

0.08543

0.08538

0.03981

0.03978

0.4660

0.4659

0.01341

0.01340

0.7133

0.7138

6

0.0010743

0.08525

0.08520

0.03988

0.03985

0.4678

0.4678

0.01343

0.01342

0.7132

0.7137

7

0.0011306

0.08507

0.08501

0.03995

0.03992

0.4697

0.4696

0.01346

0.01345

0.7131

0.7137

8

0.0011895

0.08488

0.08482

0.04002

0.03998

0.4715

0.4714

0.01348

0.01347

0.7130

0.7136

9

0.0012512

0.08470

0.08464

0.04009

0.04005

0.4733

0.4732

0.01351

0.01350

0.7129

0.7135

10

0.0013158

0.08452

0.08445

0.04016

0.04012

0.4751

0.4750

0.01353

0.01352

0.7128

0.7135

11

0.0013835

0.08434

0.08427

0.04023

0.04018

0.4770

0.4768

0.01356

0.01354

0.7127

0.7134

12

0.0014544

0.08416

0.08409

0.04030

0.04025

0.4788

0.4787

0.01358

0.01357

0.7126

0.7133

13

0.0015286

0.08398

0.08391

0.04036

0.04032

0.4806

0.4805

0.01361

0.01359

0.7125

0.7133

14

0.0016062

0.08380

0.08372

0.04043

0.04038

0.4825

0.4823

0.01363

0.01362

0.7124

0.7132

15

0.0016874

0.08363

0.08354

0.04050

0.04045

0.4843

0.4842

0.01366

0.01364

0.7123

0.7132

16

0.0017724

0.08345

0.08336

0.04057

0.04051

0.4861

0.4860

0.01368

0.01367

0.7122

0.7131

17

0.0018613

0.08328

0.08318

0.04064

0.04058

0.4880

0.4878

0.01370

0.01369

0.7121

0.7131

18

0.0019543

0.08310

0.08300

0.04070

0.04064

0.4898

0.4897

0.01373

0.01371

0.7121

0.7130

19

0.0020515

0.08293

0.08282

0.04077

0.04071

0.4917

0.4915

0.01375

0.01374

0.7120

0.7130

20

0.0021531

0.08275

0.08265

0.04084

0.04077

0.4935

0.4934

0.01378

0.01376

0.7119

0.7130

21

0.0022593

0.08258

0.08247

0.04091

0.04084

0.4954

0.4952

0.01380

0.01379

0.7118

0.7129

22

0.0023703

0.08241

0.08229

0.04098

0.04090

0.4972

0.4971

0.01383

0.01381

0.7117

0.7129

23

0.0024863

0.08224

0.08211

0.04104

0.04097

0.4991

0.4989

0.01385

0.01383

0.7116

0.7129

24

0.0026075

0.08207

0.08194

0.04111

0.04103

0.5010

0.5008

0.01388

0.01386

0.7115

0.7128

25

0.0027340

0.08190

0.08176

0.04118

0.04110

0.5028

0.5026

0.01390

0.01388

0.7114

0.7128

26

0.0028662

0.08173

0.08159

0.04125

0.04116

0.5047

0.5045

0.01393

0.01390

0.7113

0.7128

27

0.0030042

0.08156

0.08141

0.04132

0.04122

0.5066

0.5063

0.01395

0.01393

0.7113

0.7128

28

0.0031482

0.08139

0.08124

0.04138

0.04128

0.5085

0.5082

0.01398

0.01395

0.7112

0.7127

29

0.0032986

0.08122

0.08106

0.04145

0.04135

0.5103

0.5101

0.01400

0.01397

0.7111

0.7127

30

0.0034555

0.08106

0.08089

0.04152

0.04141

0.5122

0.5119

0.01403

0.01400

0.7110

0.7127

31

0.0036192

0.08089

0.08071

0.04159

0.04147

0.5141

0.5138

0.01405

0.01402

0.7109

0.7127

32

0.0037900

0.08073

0.08054

0.04165

0.04153

0.5160

0.5157

0.01408

0.01404

0.7108

0.7127

33

0.0039468

0.08056

0.08037

0.04172

0.04162

0.5179

0.5179

0.01410

0.01408

0.7107

0.7124

34

0.0041093

0.08040

0.08020

0.04179

0.04169

0.5198

0.5198

0.01412

0.01411

0.7107

0.7124

35

0.0042778

0.08023

0.08003

0.04185

0.04175

0.5217

0.5217

0.01415

0.01413

0.7106

0.7124

36

0.0044524

0.08007

0.07986

0.04192

0.04181

0.5236

0.5236

0.01417

0.01415

0.7105

0.7124

37

0.0046333

0.07991

0.07969

0.04199

0.04188

0.5255

0.5255

0.01420

0.01418

0.7104

0.7124

38

0.0048208

0.07975

0.07952

0.04206

0.04194

0.5274

0.5274

0.01422

0.01420

0.7103

0.7124

39

0.0050151

0.07959

0.07935

0.04212

0.04200

0.5293

0.5293

0.01425

0.01423

0.7102

0.7124

40

0.0052163

0.07943

0.07918

0.04219

0.04207

0.5312

0.5313

0.01427

0.01425

0.7101

0.7124

41

0.0054247

0.07927

0.07901

0.04226

0.04213

0.5331

0.5332

0.01430

0.01427

0.7101

0.7124

42

0.0056404

0.07911

0.07884

0.04232

0.04219

0.5350

0.5351

0.01432

0.01430

0.7100

0.7124

43

0.0058639

0.07895

0.07868

0.04239

0.04225

0.5369

0.5371

0.01434

0.01432

0.7099

0.7124

44

0.0060952

0.07880

0.07851

0.04246

0.04232

0.5388

0.5390

0.01437

0.01434

0.7098

0.7124

45

0.0063346

0.07864

0.07834

0.04252

0.04238

0.5407

0.5409

0.01439

0.01437

0.7097

0.7124

46

0.0065824

0.07848

0.07817

0.04259

0.04244

0.5427

0.5429

0.01442

0.01439

0.7097

0.7124

47

0.0068389

0.07833

0.07801

0.04266

0.04250

0.5446

0.5448

0.01444

0.01442

0.7096

0.7125

48

0.0071042

0.07817

0.07784

0.04272

0.04256

0.5465

0.5468

0.01447

0.01444

0.7095

0.7125

49

0.0073787

0.07802

0.07768

0.04279

0.04262

0.5485

0.5487

0.01449

0.01446

0.7094

0.7125

50

0.0076627

0.07787

0.07751

0.04286

0.04269

0.5504

0.5507

0.01451

0.01449

0.7093

0.7126

51

0.0079563

0.07771

0.07734

0.04292

0.04275

0.5523

0.5527

0.01454

0.01451

0.7093

0.7126

52

0.0082601

0.07756

0.07718

0.04299

0.04281

0.5543

0.5547

0.01456

0.01453

0.7092

0.7126

53

0.0085741

0.07741

0.07701

0.04305

0.04287

0.5562

0.5566

0.01459

0.01456

0.7091

0.7127

54

0.0088989

0.07726

0.07685

0.04312

0.04293

0.5581

0.5586

0.01461

0.01458

0.7090

0.7127

55

0.0092345

0.07711

0.07668

0.04319

0.04299

0.5601

0.5606

0.01464

0.01461

0.7089

0.7128

56

0.0095815

0.07696

0.07652

0.04325

0.04305

0.5620

0.5626

0.01466

0.01463

0.7089

0.7129

57

0.0099402

0.07681

0.07635

0.04332

0.04311

0.5640

0.5646

0.01468

0.01465

0.7088

0.7129

58

0.010311

0.07666

0.07619

0.04338

0.04317

0.5660

0.5666

0.01471

0.01468

0.7087

0.7130

59

0.010694

0.07651

0.07602

0.04345

0.04323

0.5679

0.5686

0.01473

0.01470

0.7086

0.7131

60

0.011089

0.07636

0.07586

0.04352

0.04329

0.5699

0.5707

0.01476

0.01473

0.7085

0.7132

61

0.011498

0.07621

0.07570

0.04358

0.04335

0.5718

0.5727

0.01478

0.01475

0.7085

0.7133

62

0.011921

0.07607

0.07553

0.04365

0.04341

0.5738

0.5747

0.01481

0.01477

0.7084

0.7134

63

0.012357

0.07592

0.07537

0.04371

0.04347

0.5758

0.5768

0.01483

0.01480

0.7083

0.7135

64

0.012807

0.07578

0.07520

0.04378

0.04353

0.5777

0.5788

0.01485

0.01482

0.7082

0.7136

65

0.013272

0.07563

0.07504

0.04384

0.04359

0.5797

0.5809

0.01488

0.01485

0.7082

0.7137

66

0.013753

0.07549

0.07488

0.04391

0.04365

0.5817

0.5830

0.01490

0.01487

0.7081

0.7138

67

0.014249

0.07534

0.07471

0.04398

0.04371

0.5837

0.5850

0.01493

0.01489

0.7080

0.7139

68

0.014761

0.07520

0.07455

0.04404

0.04377

0.5856

0.5871

0.01495

0.01492

0.7079

0.7140

69

0.015289

0.07506

0.07438

0.04411

0.04383

0.5876

0.5892

0.01497

0.01494

0.7079

0.7142

70

0.015835

0.07492

0.07422

0.04417

0.04389

0.5896

0.5913

0.01500

0.01497

0.7078

0.7143

71

0.016398

0.07477

0.07405

0.04424

0.04395

0.5916

0.5934

0.01502

0.01499

0.7077

0.7145

72

0.016979

0.07463

0.07389

0.04430

0.04400

0.5936

0.5955

0.01505

0.01502

0.7076

0.7146

73

0.017578

0.07449

0.07373

0.04437

0.04406

0.5956

0.5977

0.01507

0.01504

0.7076

0.7148

74

0.018197

0.07435

0.07356

0.04443

0.04412

0.5976

0.5998

0.01509

0.01507

0.7075

0.7149

75

0.018835

0.07421

0.07340

0.04450

0.04418

0.5996

0.6020

0.01512

0.01509

0.7074

0.7151

76

0.019494

0.07407

0.07323

0.04456

0.04424

0.6016

0.6041

0.01514

0.01512

0.7074

0.7153

77

0.020173

0.07394

0.07307

0.04463

0.04430

0.6036

0.6063

0.01517

0.01514

0.7073

0.7155

78

0.020874

0.07380

0.07290

0.04469

0.04436

0.6056

0.6085

0.01519

0.01517

0.7072

0.7157

79

0.021597

0.07366

0.07273

0.04476

0.04442

0.6076

0.6107

0.01521

0.01519

0.7071

0.7159

80

0.022343

0.07352

0.07257

0.04482

0.04448

0.6096

0.6129

0.01524

0.01522

0.7071

0.7161

81

0.023112

0.07339

0.07240

0.04489

0.04454

0.6116

0.6152

0.01526

0.01525

0.7070

0.7163

82

0.023905

0.07325

0.07224

0.04495

0.04460

0.6137

0.6174

0.01528

0.01527

0.7069

0.7166

83

0.024723

0.07312

0.07207

0.04502

0.04466

0.6157

0.6197

0.01531

0.01530

0.7069

0.7168

84

0.025566

0.07298

0.07190

0.04508

0.04472

0.6177

0.6219

0.01533

0.01532

0.7068

0.7171

85

0.026436

0.07285

0.07174

0.04515

0.04478

0.6197

0.6242

0.01536

0.01535

0.7067

0.7173

86

0.027333

0.07271

0.07157

0.04521

0.04484

0.6218

0.6265

0.01538

0.01538

0.7067

0.7176

87

0.028257

0.07258

0.07140

0.04527

0.04490

0.6238

0.6288

0.01540

0.01540

0.7066

0.7179

88

0.029211

0.07245

0.07123

0.04534

0.04496

0.6258

0.6312

0.01543

0.01543

0.7065

0.7182

89

0.030193

0.07232

0.07106

0.04540

0.04502

0.6279

0.6335

0.01545

0.01546

0.7065

0.7185

90

0.031206

0.07218

0.07089

0.04547

0.04508

0.6299

0.6359

0.01547

0.01549

0.7064

0.7188

91

0.032251

0.07205

0.07072

0.04553

0.04514

0.6319

0.6383

0.01550

0.01551

0.7063

0.7191

92

0.033327

0.07192

0.07055

0.04560

0.04520

0.6340

0.6406

0.01552

0.01554

0.7062

0.7194

93

0.034437

0.07179

0.07038

0.04566

0.04526

0.6360

0.6431

0.01555

0.01557

0.7062

0.7198

94

0.035581

0.07166

0.07021

0.04572

0.04532

0.6381

0.6455

0.01557

0.01560

0.7061

0.7201

95

0.036760

0.07153

0.07004

0.04579

0.04538

0.6401

0.6480

0.01559

0.01563

0.7060

0.7205

96

0.037976

0.07140

0.06986

0.04585

0.04544

0.6422

0.6504

0.01562

0.01566

0.7060

0.7209

97

0.039228

0.07127

0.06969

0.04592

0.04550

0.6442

0.6529

0.01564

0.01569

0.7059

0.7213

98

0.040520

0.07115

0.06952

0.04598

0.04556

0.6463

0.6554

0.01566

0.01571

0.7059

0.7217

99

0.041851

0.07102

0.06934

0.04604

0.04562

0.6483

0.6579

0.01569

0.01574

0.7058

0.7221

100

0.043222

0.07089

0.06917

0.04611

0.04568

0.6504

0.6605

0.01571

0.01577

0.7057

0.7225

101

0.044636

0.07076

0.06899

0.04617

0.04574

0.6525

0.6631

0.01573

0.01580

0.7057

0.7230

102

0.046094

0.07064

0.06881

0.04624

0.04581

0.6545

0.6656

0.01576

0.01583

0.7056

0.7235

103

0.047596

0.07051

0.06864

0.04630

0.04587

0.6566

0.6682

0.01578

0.01586

0.7055

0.7240

104

0.049145

0.07039

0.06846

0.04636

0.04593

0.6587

0.6709

0.01581

0.01589

0.7055

0.7245

105

0.050741

0.07026

0.06828

0.04643

0.04599

0.6608

0.6735

0.01583

0.01592

0.7054

0.7250

106

0.052386

0.07014

0.06810

0.04649

0.04605

0.6628

0.6761

0.01585

0.01595

0.7053

0.7255

107

0.054082

0.07001

0.06792

0.04655

0.04610

0.6649

0.6788

0.01588

0.01599

0.7053

0.7261

108

0.055830

0.06989

0.06774

0.04662

0.04616

0.6670

0.6815

0.01590

0.01602

0.7052

0.7266

109

0.057632

0.06977

0.06755

0.04668

0.04622

0.6691

0.6842

0.01592

0.01605

0.7052

0.7272

110

0.059490

0.06964

0.06737

0.04674

0.04628

0.6712

0.6869

0.01595

0.01608

0.7051

0.7278

111

0.061405

0.06952

0.06719

0.04681

0.04634

0.6733

0.6897

0.01597

0.01611

0.7050

0.7285

112

0.063380

0.06940

0.06700

0.04687

0.04639

0.6754

0.6924

0.01599

0.01614

0.7050

0.7291

113

0.065416

0.06928

0.06681

0.04693

0.04645

0.6775

0.6952

0.01602

0.01617

0.7049

0.7298

114

0.067516

0.06916

0.06663

0.04700

0.04650

0.6796

0.6979

0.01604

0.01620

0.7048

0.7305

115

0.069680

0.06904

0.06644

0.04706

0.04655

0.6817

0.7007

0.01606

0.01623

0.7048

0.7312

116

0.071913

0.06892

0.06625

0.04712

0.04661

0.6838

0.7035

0.01609

0.01626

0.7047

0.7319

117

0.074215

0.06880

0.06606

0.04719

0.04666

0.6859

0.7063

0.01611

0.01629

0.7047

0.7327

118

0.076590

0.06868

0.06587

0.04725

0.04671

0.6880

0.7091

0.01613

0.01632

0.7046

0.7335

119

0.079040

0.06856

0.06567

0.04731

0.04675

0.6901

0.7119

0.01616

0.01635

0.7045

0.7343

120

0.081566

0.06844

0.06548

0.04737

0.04680

0.6922

0.7147

0.01618

0.01638

0.7045

0.7352

121

0.084173

0.06832

0.06528

0.04744

0.04684

0.6943

0.7175

0.01620

0.01641

0.7044

0.7360

122

0.086863

0.06820

0.06509

0.04750

0.04688

0.6964

0.7203

0.01623

0.01644

0.7044

0.7370

123

0.089638

0.06809

0.06489

0.04756

0.04692

0.6986

0.7231

0.01625

0.01646

0.7043

0.7379

124

0.092503

0.06797

0.06469

0.04762

0.04696

0.7007

0.7259

0.01627

0.01649

0.7043

0.7389

125

0.095459

0.06785

0.06449

0.04769

0.04699

0.7028

0.7287

0.01630

0.01652

0.7042

0.7399

126

0.098510

0.06774

0.06428

0.04775

0.04702

0.7049

0.7315

0.01632

0.01654

0.7041

0.7409

127

0.10166

0.06762

0.06408

0.04781

0.04705

0.7071

0.7342

0.01634

0.01657

0.7041

0.7420

128

0.10491

0.06751

0.06387

0.04788

0.04707

0.7092

0.7370

0.01637

0.01659

0.7040

0.7431

129

0.10827

0.06739

0.06367

0.04794

0.04709

0.7113

0.7397

0.01639

0.01661

0.7040

0.7442

130

0.11174

0.06728

0.06346

0.04800

0.04711

0.7135

0.7424

0.01641

0.01663

0.7039

0.7454

131

0.11533

0.06716

0.06325

0.04806

0.04712

0.7156

0.7450

0.01643

0.01665

0.7039

0.7466

132

0.11903

0.06705

0.06304

0.04812

0.04713

0.7178

0.7477

0.01646

0.01667

0.7038

0.7479

133

0.12286

0.06693

0.06282

0.04819

0.04713

0.7199

0.7503

0.01648

0.01669

0.7037

0.7492

134

0.12681

0.06682

0.06261

0.04825

0.04713

0.7221

0.7528

0.01650

0.01671

0.7037

0.7505

135

0.13090

0.06671

0.06239

0.04831

0.04713

0.7242

0.7554

0.01653

0.01672

0.7036

0.7519

136

0.13513

0.06660

0.06217

0.04837

0.04712

0.7264

0.7578

0.01655

0.01673

0.7036

0.7533

137

0.13950

0.06649

0.06195

0.04844

0.04710

0.7285

0.7603

0.01657

0.01675

0.7035

0.7548

138

0.14402

0.06637

0.06173

0.04850

0.04708

0.7307

0.7627

0.01660

0.01676

0.7035

0.7563

139

0.14870

0.06626

0.06150

0.04856

0.04705

0.7328

0.7650

0.01662

0.01676

0.7034

0.7578

140

0.15354

0.06615

0.06128

0.04862

0.04702

0.7350

0.7673

0.01664

0.01677

0.7034

0.7594

141

0.15856

0.06604

0.06105

0.04868

0.04698

0.7372

0.7695

0.01667

0.01678

0.7033

0.7611

142

0.16375

0.06593

0.06082

0.04875

0.04693

0.7393

0.7717

0.01669

0.01678

0.7033

0.7628

143

0.16913

0.06582

0.06059

0.04881

0.04688

0.7415

0.7738

0.01671

0.01678

0.7032

0.7646

144

0.17470

0.06571

0.06035

0.04887

0.04682

0.7437

0.7758

0.01673

0.01678

0.7032

0.7664

145

0.18047

0.06560

0.06012

0.04893

0.04676

0.7458

0.7778

0.01676

0.01678

0.7031

0.7682

146

0.18646

0.06550

0.05988

0.04899

0.04669

0.7480

0.7797

0.01678

0.01677

0.7031

0.7701

147

0.19267

0.06539

0.05964

0.04905

0.04661

0.7502

0.7815

0.01680

0.01677

0.7030

0.7721

148

0.19911

0.06528

0.05940

0.04912

0.04653

0.7524

0.7833

0.01683

0.01676

0.7030

0.7741

149

0.20579

0.06517

0.05915

0.04918

0.04644

0.7546

0.7850

0.01685

0.01675

0.7029

0.7762

150

0.21273

0.06506

0.05891

0.04924

0.04634

0.7568

0.7866

0.01687

0.01673

0.7029

0.7783

151

0.21994

0.06496

0.05866

0.04930

0.04623

0.7589

0.7882

0.01690

0.01672

0.7028

0.7804

152

0.22743

0.06485

0.05840

0.04936

0.04612

0.7611

0.7897

0.01692

0.01670

0.7028

0.7827

153

0.23522

0.06475

0.05815

0.04942

0.04600

0.7633

0.7911

0.01694

0.01668

0.7027

0.7850

154

0.24332

0.06464

0.05789

0.04948

0.04588

0.7655

0.7924

0.01696

0.01666

0.7027

0.7873

155

0.25174

0.06453

0.05763

0.04955

0.04575

0.7677

0.7937

0.01699

0.01664

0.7026

0.7897

156

0.26051

0.06443

0.05737

0.04961

0.04561

0.7699

0.7949

0.01701

0.01662

0.7026

0.7922

157

0.26965

0.06432

0.05711

0.04967

0.04546

0.7721

0.7961

0.01703

0.01659

0.7025

0.7947

158

0.27917

0.06422

0.05684

0.04973

0.04531

0.7743

0.7972

0.01706

0.01657

0.7025

0.7972

159

0.28909

0.06412

0.05657

0.04979

0.04516

0.7766

0.7982

0.01708

0.01654

0.7024

0.7999

160

0.29945

0.06401

0.05630

0.04985

0.04500

0.7788

0.7992

0.01710

0.01651

0.7024

0.8025

161

0.31026

0.06391

0.05602

0.04991

0.04483

0.7810

0.8002

0.01712

0.01648

0.7023

0.8053

162

0.32156

0.06381

0.05575

0.04997

0.04466

0.7832

0.8010

0.01715

0.01645

0.7023

0.8081

163

0.33336

0.06370

0.05547

0.05003

0.04448

0.7854

0.8019

0.01717

0.01642

0.7022

0.8109

164

0.34571

0.06360

0.05518

0.05009

0.04429

0.7876

0.8027

0.01719

0.01638

0.7022

0.8139

165

0.35865

0.06350

0.05490

0.05016

0.04410

0.7899

0.8034

0.01721

0.01635

0.7021

0.8168

166

0.37219

0.06340

0.05461

0.05022

0.04391

0.7921

0.8041

0.01724

0.01631

0.7021

0.8199

167

0.38640

0.06330

0.05432

0.05028

0.04371

0.7943

0.8048

0.01726

0.01628

0.7020

0.8230

168

0.40131

0.06320

0.05402

0.05034

0.04351

0.7965

0.8054

0.01728

0.01624

0.7020

0.8261

169

0.41697

0.06310

0.05372

0.05040

0.04330

0.7988

0.8060

0.01731

0.01620

0.7019

0.8293

170

0.43344

0.06299

0.05342

0.05046

0.04309

0.8010

0.8065

0.01733

0.01616

0.7019

0.8326

171

0.45077

0.06289

0.05312

0.05052

0.04287

0.8032

0.8070

0.01735

0.01612

0.7019

0.8359

172

0.46903

0.06279

0.05281

0.05058

0.04264

0.8055

0.8075

0.01737

0.01608

0.7018

0.8393

173

0.48829

0.06270

0.05250

0.05064

0.04241

0.8077

0.8079

0.01740

0.01604

0.7018

0.8428

174

0.50864

0.06260

0.05218

0.05070

0.04217

0.8100

0.8082

0.01742

0.01600

0.7017

0.8463

175

0.53015

0.06250

0.05186

0.05076

0.04193

0.8122

0.8085

0.01744

0.01595

0.7017

0.8499

176

0.55293

0.06240

0.05154

0.05082

0.04168

0.8145

0.8086

0.01746

0.01591

0.7016

0.8535

177

0.57708

0.06230

0.05122

0.05088

0.04142

0.8167

0.8087

0.01749

0.01586

0.7016

0.8572

178

0.60273

0.06220

0.05089

0.05094

0.04115

0.8190

0.8087

0.01751

0.01581

0.7016

0.8610

179

0.63000

0.06211

0.05056

0.05100

0.04087

0.8212

0.8085

0.01753

0.01576

0.7015

0.8648

180

0.65907

0.06201

0.05022

0.05106

0.04059

0.8235

0.8082

0.01755

0.01571

0.7015

0.8687

181

0.69009

0.06191

0.04988

0.05112

0.04029

0.8258

0.8077

0.01758

0.01565

0.7014

0.8726

182

0.72326

0.06181

0.04954

0.05118

0.03998

0.8280

0.8070

0.01760

0.01559

0.7014

0.8766

183

0.75882

0.06172

0.04919

0.05124

0.03966

0.8303

0.8062

0.01762

0.01553

0.7013

0.8806

184

0.79700

0.06162

0.04884

0.05130

0.03932

0.8326

0.8051

0.01764

0.01547

0.7013

0.8847

185

0.83811

0.06153

0.04849

0.05136

0.03898

0.8348

0.8038

0.01767

0.01540

0.7013

0.8888

186

0.88247

0.06143

0.04813

0.05142

0.03861

0.8371

0.8023

0.01769

0.01533

0.7012

0.8930

187

0.93050

0.06134

0.04777

0.05148

0.03824

0.8394

0.8005

0.01771

0.01525

0.7012

0.8972

188

0.98263

0.06124

0.04740

0.05154

0.03785

0.8417

0.7984

0.01773

0.01517

0.7011

0.9014

189

1.0394

0.06115

0.04703

0.05160

0.03744

0.8439

0.7961

0.01776

0.01509

0.7011

0.9056

190

1.1015

0.06105

0.04666

0.05166

0.03702

0.8462

0.7935

0.01778

0.01501

0.7011

0.9098

191

1.1696

0.06096

0.04628

0.05172

0.03659

0.8485

0.7907

0.01780

0.01492

0.7010

0.9141

192

1.2446

0.06086

0.04590

0.05178

0.03616

0.8508

0.7877

0.01782

0.01483

0.7010

0.9183

193

1.3277

0.06077

0.04551

0.05184

0.03571

0.8531

0.7846

0.01785

0.01474

0.7009

0.9226

194

1.4202

0.06068

0.04512

0.05190

0.03526

0.8554

0.7814

0.01787

0.01465

0.7009

0.9268

195

1.5238

0.06059

0.04472

0.05196

0.03480

0.8577

0.7781

0.01789

0.01456

0.7009

0.9310

196

1.6405

0.06049

0.04432

0.05202

0.03435

0.8600

0.7749

0.01791

0.01447

0.7008

0.9353

197

1.7729

0.06040

0.04392

0.05208

0.03390

0.8623

0.7719

0.01794

0.01439

0.7008

0.9395

198

1.9245

0.06031

0.04351

0.05214

0.03347

0.8646

0.7691

0.01796

0.01431

0.7008

0.9437

199

2.0997

0.06022

0.04310

0.05220

0.03305

0.8669

0.7667

0.01798

0.01425

0.7007

0.9480

200

2.3044

0.06013

0.04268

0.05226

0.03265

0.8692

0.7649

0.01800

0.01419

0.7007

0.9523


In addition, Figures 13 and 14 summarize viscosity and thermal conductivity at atmospheric pressure in diagrams.

12. TRANSPORT PROPERTIES OF WATER AT SATURATION

Table 6 shows transport properties of water at saturation for temperatures from –32 to 200°F, calculated using ASHRAE LibHuAirProp Software (ASHRAE 2021) based on IAPWS formulations described in the releases IAPWS R7-97 2012, R12-08 2008, and R15-11 2011.

Thermal Conductivity of Moist Air as Function of Temperature with Lines of Constant Humidity Ratio Ranging from W = 0 (dry air) to W = 1 lbw/lbda Water Vapor at Standard Atmospheric Pressure of 14.696 psia

Figure 14. Thermal Conductivity of Moist Air as Function of Temperature with Lines of Constant Humidity Ratio Ranging from W = 0 (dry air) to W = 1 lbw/lbda Water Vapor at Standard Atmospheric Pressure of 14.696 psia


The following properties are shown in Table 6:

t = Fahrenheit temperature, °F, based on the ITS-90 and expressed relative to absolute temperature T in Rankine by the following relation:

pws = saturation pressure of water (liquid or vapor), psiakPa
ρf = density of saturated liquid water, lb/ft3
ρg = density of saturated water vapor, lb/ft3
ηf = viscosity of saturated liquid water, lb/(ft·h)
ηg = viscosity of saturated water vapor, lb/(ft·h)
νf = kinematic viscosity of saturated liquid water, ft/h
νg = kinematic viscosity of saturated water vapor, ft/h
λf = thermal conductivity of saturated liquid water, Btu/(ft·h·°R)
λg = thermal conductivity of saturated water vapor, Btu/(ft·h·°R).
Prf = Prandtl number of saturated liquid water.
Prg = Prandtl number of saturated water vapor.

Table 6 Transport Properties of Water at Saturation

Temp. t, °F

Absolute Pressure pws, psia

Density, lb/ft3

Viscosity, lb/ft·h

Kinematic Visc., ft2/h

Thermal Cond., Btu/h·ft·°R

Prandtl Number (—)

Sat. Liq.

Sat. Vap.

Sat. Liq.

Sat. Vap.

Sat. Liq.

Sat. Vap.

Sat. Liq.

Sat. Vap.

Sat. Liq.

Sat. Vap.

ρf

ρg

ηf

ηg

νf

νg

λf

λg

Prf

Prg

33

0.092293

62.417

0.0050403

4.252

0.02168

0.06813

68.90

0.3218

0.00970

13.31

1.0077

34

0.096069

62.419

0.0052360

4.172

0.02172

0.06684

66.44

0.3226

0.00972

13.02

1.0075

35

0.099981

62.421

0.0054382

4.094

0.02176

0.06559

64.08

0.3234

0.00975

12.74

1.0074

36

0.10403

62.422

0.0056473

4.019

0.02179

0.06438

61.82

0.3242

0.00977

12.47

1.0072

37

0.10823

62.423

0.0058634

3.946

0.02183

0.06321

59.65

0.3250

0.00979

12.21

1.0071

38

0.11258

62.423

0.0060867

3.874

0.02187

0.06207

57.56

0.3258

0.00981

11.96

1.0069

39

0.11708

62.423

0.0063175

3.805

0.02191

0.06096

55.56

0.3265

0.00983

11.71

1.0068

40

0.12173

62.423

0.0065558

3.738

0.02195

0.05989

53.63

0.3273

0.00985

11.48

1.0067

41

0.12656

62.423

0.0068019

3.673

0.02199

0.05884

51.79

0.3280

0.00987

11.25

1.0066

42

0.13155

62.422

0.0070561

3.609

0.02203

0.05782

50.01

0.3288

0.00989

11.02

1.0065

43

0.13671

62.421

0.0073186

3.548

0.02207

0.05684

48.30

0.3295

0.00991

10.81

1.0064

44

0.14205

62.420

0.0075895

3.488

0.02211

0.05587

46.66

0.3302

0.00993

10.60

1.0063

45

0.14757

62.418

0.0078692

3.429

0.02215

0.05494

45.09

0.3309

0.00995

10.40

1.0062

46

0.15328

62.416

0.0081578

3.372

0.02219

0.05403

43.57

0.3316

0.00998

10.20

1.0061

47

0.15919

62.414

0.0084556

3.317

0.02223

0.05314

42.11

0.3323

0.01000

10.01

1.0060

48

0.16530

62.412

0.0087628

3.263

0.02227

0.05228

40.71

0.3330

0.01002

9.824

1.0060

49

0.17161

62.409

0.0090797

3.211

0.02231

0.05144

39.36

0.3337

0.01004

9.644

1.0059

50

0.17813

62.406

0.0094066

3.159

0.02235

0.05062

38.06

0.3344

0.01006

9.469

1.0058

51

0.18487

62.403

0.0097436

3.109

0.02239

0.04983

36.81

0.3350

0.01008

9.299

1.0058

52

0.19184

62.400

0.010091

3.061

0.02243

0.04905

35.60

0.3357

0.01010

9.134

1.0057

53

0.19903

62.396

0.010449

3.013

0.02247

0.04829

34.45

0.3364

0.01012

8.973

1.0057

54

0.20646

62.392

0.010819

2.967

0.02251

0.04756

33.33

0.3370

0.01015

8.816

1.0056

55

0.21414

62.388

0.011199

2.922

0.02255

0.04684

32.26

0.3377

0.01017

8.664

1.0056

56

0.22206

62.384

0.011591

2.878

0.02259

0.04613

31.22

0.3383

0.01019

8.516

1.0056

57

0.23024

62.379

0.011995

2.835

0.02263

0.04545

30.22

0.3389

0.01021

8.372

1.0055

58

0.23868

62.374

0.012411

2.793

0.02267

0.04478

29.26

0.3395

0.01023

8.232

1.0055

59

0.24740

62.369

0.012840

2.752

0.02271

0.04412

28.34

0.3402

0.01025

8.095

1.0055

60

0.25639

62.364

0.013282

2.712

0.02276

0.04349

27.45

0.3408

0.01028

7.962

1.0055

61

0.26567

62.358

0.013736

2.673

0.02280

0.04286

26.59

0.3414

0.01030

7.832

1.0055

62

0.27524

62.352

0.014204

2.635

0.02284

0.04226

25.76

0.3420

0.01032

7.706

1.0055

63

0.28511

62.346

0.014686

2.597

0.02288

0.04166

24.96

0.3426

0.01034

7.583

1.0055

64

0.29529

62.340

0.015182

2.561

0.02292

0.04108

24.18

0.3432

0.01036

7.463

1.0055

65

0.30579

62.334

0.015692

2.525

0.02296

0.04051

23.44

0.3438

0.01038

7.345

1.0055

66

0.31662

62.327

0.016217

2.490

0.02300

0.03996

22.72

0.3443

0.01041

7.231

1.0056

67

0.32777

62.320

0.016757

2.456

0.02305

0.03942

22.03

0.3449

0.01043

7.119

1.0056

68

0.33927

62.313

0.017313

2.423

0.02309

0.03888

21.36

0.3455

0.01045

7.010

1.0056

69

0.35113

62.306

0.017884

2.390

0.02313

0.03837

20.72

0.3461

0.01047

6.904

1.0056

70

0.36334

62.299

0.018472

2.358

0.02317

0.03786

20.09

0.3466

0.01049

6.800

1.0057

71

0.37592

62.291

0.019076

2.327

0.02321

0.03736

19.49

0.3472

0.01052

6.699

1.0057

72

0.38889

62.283

0.019697

2.297

0.02326

0.03687

18.91

0.3477

0.01054

6.600

1.0058

73

0.40224

62.275

0.020336

2.267

0.02330

0.03640

18.35

0.3483

0.01056

6.503

1.0058

74

0.41599

62.267

0.020992

2.237

0.02334

0.03593

17.81

0.3488

0.01058

6.409

1.0059

75

0.43015

62.258

0.021667

2.209

0.02338

0.03548

17.29

0.3493

0.01061

6.316

1.0059

76

0.44473

62.250

0.022360

2.181

0.02342

0.03503

16.78

0.3499

0.01063

6.226

1.0060

77

0.45973

62.241

0.023073

2.153

0.02347

0.03459

16.29

0.3504

0.01065

6.138

1.0060

78

0.47518

62.232

0.023804

2.126

0.02351

0.03416

15.82

0.3509

0.01067

6.051

1.0061

79

0.49108

62.223

0.024556

2.100

0.02355

0.03374

15.36

0.3514

0.01070

5.967

1.0062

80

0.50744

62.214

0.025328

2.074

0.02360

0.03333

14.92

0.3520

0.01072

5.884

1.0062

81

0.52427

62.204

0.026121

2.048

0.02364

0.03293

14.50

0.3525

0.01074

5.804

1.0063

82

0.54159

62.194

0.026935

2.023

0.02368

0.03253

14.08

0.3530

0.01076

5.725

1.0064

83

0.55940

62.184

0.027770

1.999

0.02372

0.03215

13.68

0.3535

0.01079

5.647

1.0065

84

0.57772

62.174

0.028628

1.975

0.02377

0.03177

13.30

0.3540

0.01081

5.571

1.0066

85

0.59656

62.164

0.029509

1.952

0.02381

0.03139

12.92

0.3545

0.01083

5.497

1.0066

86

0.61593

62.154

0.030412

1.929

0.02385

0.03103

12.56

0.3550

0.01085

5.425

1.0067

87

0.63585

62.143

0.031339

1.906

0.02390

0.03067

12.21

0.3554

0.01088

5.354

1.0068

88

0.65632

62.133

0.032291

1.884

0.02394

0.03032

11.88

0.3559

0.01090

5.284

1.0069

89

0.67736

62.122

0.033267

1.862

0.02398

0.02997

11.55

0.3564

0.01092

5.216

1.0070

90

0.69899

62.111

0.034268

1.841

0.02403

0.02964

11.23

0.3569

0.01095

5.149

1.0071

91

0.72122

62.100

0.035295

1.820

0.02407

0.02930

10.92

0.3573

0.01097

5.084

1.0072

92

0.74405

62.088

0.036348

1.799

0.02411

0.02898

10.63

0.3578

0.01099

5.019

1.0073

93

0.76751

62.077

0.037428

1.779

0.02416

0.02866

10.34

0.3583

0.01101

4.956

1.0074

94

0.79161

62.065

0.038535

1.759

0.02420

0.02834

10.06

0.3587

0.01104

4.895

1.0075

95

0.81636

62.053

0.039670

1.740

0.02424

0.02803

9.789

0.3592

0.01106

4.834

1.0076

96

0.84178

62.041

0.040834

1.720

0.02429

0.02773

9.527

0.3596

0.01108

4.775

1.0078

97

0.86788

62.029

0.042026

1.702

0.02433

0.02743

9.274

0.3601

0.01111

4.717

1.0079

98

0.89468

62.017

0.043249

1.683

0.02437

0.02714

9.028

0.3605

0.01113

4.660

1.0080

99

0.92220

62.004

0.044501

1.665

0.02442

0.02685

8.789

0.3610

0.01115

4.604

1.0081

100

0.95044

61.992

0.045784

1.647

0.02446

0.02657

8.558

0.3614

0.01118

4.549

1.0082

101

0.97943

61.979

0.047099

1.630

0.02451

0.02630

8.335

0.3618

0.01120

4.496

1.0083

102

1.0092

61.966

0.048445

1.613

0.02455

0.02602

8.117

0.3623

0.01123

4.443

1.0085

103

1.0397

61.953

0.049825

1.596

0.02459

0.02576

7.907

0.3627

0.01125

4.391

1.0086

104

1.0710

61.940

0.051237

1.579

0.02464

0.02549

7.703

0.3631

0.01127

4.340

1.0087

105

1.1032

61.927

0.052684

1.563

0.02468

0.02523

7.505

0.3635

0.01130

4.290

1.0088

106

1.1361

61.913

0.054165

1.547

0.02473

0.02498

7.312

0.3639

0.01132

4.241

1.0090

107

1.1699

61.900

0.055681

1.531

0.02477

0.02473

7.126

0.3644

0.01134

4.193

1.0091

108

1.2046

61.886

0.057234

1.515

0.02482

0.02448

6.945

0.3648

0.01137

4.146

1.0092

109

1.2401

61.872

0.058823

1.500

0.02486

0.02424

6.770

0.3652

0.01139

4.100

1.0094

110

1.2766

61.858

0.060449

1.485

0.02490

0.02400

6.599

0.3656

0.01142

4.054

1.0095

111

1.3140

61.844

0.062113

1.470

0.02495

0.02377

6.434

0.3660

0.01144

4.009

1.0096

112

1.3523

61.830

0.063816

1.456

0.02499

0.02354

6.273

0.3664

0.01146

3.965

1.0098

113

1.3915

61.815

0.065559

1.441

0.02504

0.02331

6.118

0.3668

0.01149

3.922

1.0099

114

1.4318

61.801

0.067342

1.427

0.02508

0.02309

5.966

0.3671

0.01151

3.880

1.0101

115

1.4730

61.786

0.069165

1.413

0.02513

0.02287

5.819

0.3675

0.01154

3.838

1.0102

116

1.5153

61.771

0.071031

1.400

0.02517

0.02266

5.676

0.3679

0.01156

3.797

1.0104

117

1.5586

61.756

0.072938

1.386

0.02522

0.02245

5.538

0.3683

0.01158

3.757

1.0105

118

1.6030

61.741

0.074889

1.373

0.02526

0.02224

5.403

0.3687

0.01161

3.717

1.0106

119

1.6484

61.726

0.076884

1.360

0.02531

0.02203

5.272

0.3690

0.01163

3.679

1.0108

120

1.6949

61.710

0.078924

1.347

0.02535

0.02183

5.145

0.3694

0.01166

3.640

1.0109

121

1.7426

61.695

0.081009

1.334

0.02540

0.02163

5.022

0.3698

0.01168

3.603

1.0111

122

1.7914

61.679

0.083140

1.322

0.02544

0.02143

4.902

0.3701

0.01171

3.566

1.0112

123

1.8414

61.664

0.085319

1.310

0.02549

0.02124

4.785

0.3705

0.01173

3.530

1.0114

124

1.8925

61.648

0.087546

1.298

0.02553

0.02105

4.671

0.3708

0.01176

3.494

1.0116

125

1.9449

61.632

0.089821

1.286

0.02558

0.02086

4.561

0.3712

0.01178

3.459

1.0117

126

1.9985

61.616

0.092147

1.274

0.02562

0.02068

4.454

0.3715

0.01181

3.424

1.0119

127

2.0534

61.600

0.094522

1.263

0.02567

0.02050

4.349

0.3719

0.01183

3.390

1.0120

128

2.1096

61.583

0.096950

1.251

0.02571

0.02032

4.248

0.3722

0.01186

3.357

1.0122

129

2.1670

61.567

0.099429

1.240

0.02576

0.02014

4.149

0.3726

0.01188

3.324

1.0123

130

2.2258

61.550

0.10196

1.229

0.02580

0.01997

4.053

0.3729

0.01191

3.291

1.0125

131

2.2860

61.533

0.10455

1.218

0.02585

0.01980

3.960

0.3732

0.01193

3.260

1.0127

132

2.3475

61.517

0.10719

1.208

0.02589

0.01963

3.869

0.3736

0.01196

3.228

1.0128

133

2.4105

61.500

0.10989

1.197

0.02594

0.01946

3.781

0.3739

0.01198

3.197

1.0130

134

2.4749

61.483

0.11264

1.187

0.02598

0.01930

3.695

0.3742

0.01201

3.167

1.0132

135

2.5407

61.465

0.11546

1.176

0.02603

0.01914

3.611

0.3746

0.01203

3.137

1.0133

136

2.6081

61.448

0.11833

1.166

0.02607

0.01898

3.530

0.3749

0.01206

3.108

1.0135

137

2.6769

61.431

0.12126

1.156

0.02612

0.01882

3.450

0.3752

0.01208

3.079

1.0137

138

2.7473

61.413

0.12425

1.147

0.02616

0.01867

3.373

0.3755

0.01211

3.050

1.0139

139

2.8193

61.395

0.12730

1.137

0.02621

0.01852

3.298

0.3758

0.01213

3.022

1.0140

140

2.8929

61.378

0.13042

1.127

0.02626

0.01837

3.225

0.3761

0.01216

2.995

1.0142

141

2.9681

61.360

0.13360

1.118

0.02630

0.01822

3.154

0.3764

0.01218

2.967

1.0144

142

3.0450

61.342

0.13684

1.109

0.02635

0.01807

3.084

0.3767

0.01221

2.940

1.0146

143

3.1235

61.324

0.14015

1.100

0.02639

0.01793

3.017

0.3770

0.01224

2.914

1.0147

144

3.2038

61.305

0.14353

1.091

0.02644

0.01779

2.951

0.3773

0.01226

2.888

1.0149

145

3.2858

61.287

0.14697

1.082

0.02648

0.01765

2.886

0.3776

0.01229

2.862

1.0151

146

3.3696

61.269

0.15049

1.073

0.02653

0.01751

2.824

0.3779

0.01231

2.837

1.0153

147

3.4552

61.250

0.15407

1.064

0.02658

0.01737

2.763

0.3782

0.01234

2.812

1.0155

148

3.5426

61.231

0.15772

1.056

0.02662

0.01724

2.704

0.3785

0.01237

2.788

1.0157

149

3.6319

61.213

0.16145

1.047

0.02667

0.01711

2.646

0.3788

0.01239

2.764

1.0159

150

3.7231

61.194

0.16525

1.039

0.02671

0.01698

2.589

0.3791

0.01242

2.740

1.0161

151

3.8163

61.175

0.16913

1.031

0.02676

0.01685

2.534

0.3793

0.01244

2.717

1.0163

152

3.9114

61.156

0.17307

1.023

0.02681

0.01672

2.481

0.3796

0.01247

2.693

1.0165

153

4.0085

61.137

0.17710

1.015

0.02685

0.01660

2.429

0.3799

0.01250

2.671

1.0167

154

4.1076

61.117

0.18121

1.007

0.02690

0.01647

2.378

0.3801

0.01252

2.648

1.0169

155

4.2089

61.098

0.18539

0.9989

0.02694

0.01635

2.328

0.3804

0.01255

2.626

1.0171

156

4.3122

61.078

0.18965

0.9913

0.02699

0.01623

2.280

0.3807

0.01258

2.604

1.0173

157

4.4176

61.059

0.19400

0.9837

0.02704

0.01611

2.232

0.3809

0.01260

2.583

1.0175

158

4.5253

61.039

0.19842

0.9762

0.02708

0.01599

2.186

0.3812

0.01263

2.562

1.0177

159

4.6351

61.019

0.20293

0.9688

0.02713

0.01588

2.141

0.3814

0.01266

2.541

1.0179

160

4.7472

60.999

0.20753

0.9615

0.02717

0.01576

2.097

0.3817

0.01268

2.520

1.0181

161

4.8616

60.979

0.21221

0.9543

0.02722

0.01565

2.055

0.3819

0.01271

2.500

1.0183

162

4.9783

60.959

0.21698

0.9472

0.02727

0.01554

2.013

0.3822

0.01274

2.480

1.0186

163

5.0973

60.939

0.22184

0.9402

0.02731

0.01543

1.972

0.3824

0.01277

2.460

1.0188

164

5.2187

60.918

0.22679

0.9333

0.02736

0.01532

1.932

0.3827

0.01279

2.441

1.0190

165

5.3426

60.898

0.23183

0.9264

0.02740

0.01521

1.894

0.3829

0.01282

2.422

1.0192

166

5.4689

60.877

0.23696

0.9197

0.02745

0.01511

1.856

0.3832

0.01285

2.403

1.0195

167

5.5978

60.857

0.24218

0.9130

0.02750

0.01500

1.819

0.3834

0.01288

2.384

1.0197

168

5.7292

60.836

0.24751

0.9064

0.02754

0.01490

1.783

0.3836

0.01290

2.366

1.0199

169

5.8632

60.815

0.25292

0.8999

0.02759

0.01480

1.747

0.3838

0.01293

2.348

1.0202

170

5.9998

60.794

0.25844

0.8934

0.02764

0.01470

1.713

0.3841

0.01296

2.330

1.0204

171

6.1390

60.773

0.26405

0.8871

0.02768

0.01460

1.679

0.3843

0.01299

2.312

1.0207

172

6.2810

60.752

0.26977

0.8808

0.02773

0.01450

1.646

0.3845

0.01301

2.295

1.0209

173

6.4258

60.731

0.27559

0.8746

0.02777

0.01440

1.614

0.3847

0.01304

2.277

1.0212

174

6.5733

60.709

0.28151

0.8685

0.02782

0.01431

1.583

0.3850

0.01307

2.260

1.0214

175

6.7237

60.688

0.28753

0.8624

0.02787

0.01421

1.552

0.3852

0.01310

2.244

1.0217

176

6.8769

60.666

0.29366

0.8565

0.02791

0.01412

1.523

0.3854

0.01313

2.227

1.0219

177

7.0331

60.645

0.29990

0.8506

0.02796

0.01403

1.493

0.3856

0.01315

2.211

1.0222

178

7.1922

60.623

0.30625

0.8447

0.02801

0.01393

1.465

0.3858

0.01318

2.195

1.0225

179

7.3544

60.601

0.31271

0.8389

0.02805

0.01384

1.437

0.3860

0.01321

2.179

1.0228

180

7.5196

60.579

0.31928

0.8332

0.02810

0.01375

1.410

0.3862

0.01324

2.163

1.0230

181

7.6879

60.557

0.32596

0.8276

0.02815

0.01367

1.383

0.3864

0.01327

2.148

1.0233

182

7.8593

60.535

0.33276

0.8220

0.02819

0.01358

1.357

0.3866

0.01330

2.132

1.0236

183

8.0339

60.513

0.33968

0.8165

0.02824

0.01349

1.332

0.3868

0.01332

2.117

1.0239

184

8.2118

60.490

0.34671

0.8111

0.02829

0.01341

1.307

0.3870

0.01335

2.102

1.0242

185

8.3930

60.468

0.35387

0.8057

0.02833

0.01332

1.283

0.3872

0.01338

2.088

1.0245

186

8.5775

60.445

0.36114

0.8004

0.02838

0.01324

1.259

0.3873

0.01341

2.073

1.0248

187

8.7653

60.423

0.36854

0.7952

0.02842

0.01316

1.235

0.3875

0.01344

2.059

1.0251

188

8.9566

60.400

0.37606

0.7900

0.02847

0.01308

1.213

0.3877

0.01347

2.045

1.0254

189

9.1514

60.377

0.38370

0.7848

0.02852

0.01300

1.191

0.3879

0.01350

2.031

1.0257

190

9.3497

60.354

0.39148

0.7798

0.02856

0.01292

1.169

0.3881

0.01353

2.017

1.0260

191

9.5515

60.332

0.39938

0.7747

0.02861

0.01284

1.148

0.3882

0.01356

2.003

1.0263

192

9.7570

60.308

0.40742

0.7698

0.02866

0.01276

1.127

0.3884

0.01359

1.990

1.0267

193

9.9662

60.285

0.41558

0.7649

0.02870

0.01269

1.106

0.3886

0.01362

1.977

1.0270

194

10.179

60.262

0.42388

0.7600

0.02875

0.01261

1.086

0.3887

0.01365

1.964

1.0273

195

10.396

60.239

0.43232

0.7552

0.02880

0.01254

1.067

0.3889

0.01368

1.951

1.0277

196

10.616

60.215

0.44089

0.7505

0.02884

0.01246

1.048

0.3891

0.01371

1.938

1.0280

197

10.841

60.192

0.44960

0.7458

0.02889

0.01239

1.029

0.3892

0.01374

1.925

1.0284

198

11.069

60.168

0.45845

0.7411

0.02894

0.01232

1.011

0.3894

0.01377

1.913

1.0287

199

11.301

60.144

0.46745

0.7365

0.02898

0.01225

0.9932

0.3895

0.01380

1.901

1.0291

200

11.538

60.121

0.47659

0.7320

0.02903

0.01218

0.9757

0.3897

0.01383

1.888

1.0295

201

11.778

60.097

0.48587

0.7275

0.02908

0.01211

0.9586

0.3898

0.01386

1.876

1.0298

202

12.023

60.073

0.49530

0.7231

0.02912

0.01204

0.9419

0.3900

0.01389

1.864

1.0302

203

12.271

60.049

0.50489

0.7187

0.02917

0.01197

0.9255

0.3901

0.01392

1.853

1.0306

204

12.525

60.025

0.51462

0.7143

0.02922

0.01190

0.9094

0.3902

0.01395

1.841

1.0310

205

12.782

60.000

0.52450

0.7100

0.02926

0.01183

0.8937

0.3904

0.01398

1.830

1.0314

206

13.044

59.976

0.53454

0.7058

0.02931

0.01177

0.8783

0.3905

0.01401

1.818

1.0318

207

13.310

59.952

0.54474

0.7016

0.02936

0.01170

0.8633

0.3907

0.01404

1.807

1.0322

208

13.581

59.927

0.55509

0.6974

0.02940

0.01164

0.8485

0.3908

0.01407

1.796

1.0326

209

13.856

59.902

0.56561

0.6933

0.02945

0.01157

0.8341

0.3909

0.01410

1.785

1.0330

210

14.136

59.878

0.57629

0.6892

0.02950

0.01151

0.8199

0.3910

0.01413

1.774

1.0334

211

14.420

59.853

0.58713

0.6852

0.02954

0.01145

0.8060

0.3912

0.01417

1.764

1.0338

212

14.709

59.828

0.59814

0.6812

0.02959

0.01139

0.7925

0.3913

0.01420

1.753

1.0343

213

15.003

59.803

0.60931

0.6772

0.02964

0.01132

0.7792

0.3914

0.01423

1.743

1.0347

214

15.302

59.778

0.62066

0.6733

0.02968

0.01126

0.7661

0.3915

0.01426

1.733

1.0352

215

15.606

59.753

0.63217

0.6695

0.02973

0.01120

0.7533

0.3916

0.01429

1.722

1.0356

216

15.915

59.728

0.64386

0.6656

0.02978

0.01114

0.7408

0.3918

0.01432

1.712

1.0361

217

16.229

59.703

0.65573

0.6618

0.02982

0.01109

0.7286

0.3919

0.01435

1.702

1.0365

218

16.548

59.677

0.66777

0.6581

0.02987

0.01103

0.7165

0.3920

0.01439

1.693

1.0370

219

16.872

59.652

0.67999

0.6544

0.02992

0.01097

0.7048

0.3921

0.01442

1.683

1.0375

220

17.201

59.626

0.69240

0.6507

0.02996

0.01091

0.6932

0.3922

0.01445

1.673

1.0380

221

17.535

59.601

0.70498

0.6471

0.03001

0.01086

0.6819

0.3923

0.01448

1.664

1.0384

222

17.875

59.575

0.71776

0.6435

0.03006

0.01080

0.6708

0.3924

0.01452

1.654

1.0389

223

18.221

59.549

0.73072

0.6399

0.03010

0.01075

0.6599

0.3925

0.01455

1.645

1.0395

224

18.571

59.523

0.74387

0.6364

0.03015

0.01069

0.6493

0.3926

0.01458

1.636

1.0400

225

18.928

59.497

0.75721

0.6329

0.03020

0.01064

0.6388

0.3927

0.01461

1.627

1.0405

226

19.290

59.471

0.77074

0.6294

0.03024

0.01058

0.6286

0.3928

0.01465

1.618

1.0410

227

19.657

59.445

0.78447

0.6260

0.03029

0.01053

0.6185

0.3928

0.01468

1.609

1.0415

228

20.031

59.419

0.79840

0.6226

0.03034

0.01048

0.6087

0.3929

0.01471

1.600

1.0421

229

20.410

59.392

0.81253

0.6193

0.03038

0.01043

0.5990

0.3930

0.01475

1.592

1.0426

230

20.795

59.366

0.82686

0.6159

0.03043

0.01038

0.5895

0.3931

0.01478

1.583

1.0432

231

21.186

59.339

0.84140

0.6126

0.03048

0.01032

0.5802

0.3932

0.01481

1.575

1.0437

232

21.583

59.313

0.85614

0.6094

0.03052

0.01027

0.5711

0.3933

0.01485

1.566

1.0443

233

21.986

59.286

0.87109

0.6062

0.03057

0.01022

0.5622

0.3933

0.01488

1.558

1.0449

234

22.395

59.259

0.88626

0.6030

0.03062

0.01017

0.5534

0.3934

0.01491

1.550

1.0455

235

22.811

59.233

0.90163

0.5998

0.03066

0.01013

0.5448

0.3935

0.01495

1.542

1.0461

236

23.233

59.206

0.91722

0.5967

0.03071

0.01008

0.5363

0.3935

0.01498

1.534

1.0467

237

23.661

59.179

0.93303

0.5936

0.03076

0.01003

0.5281

0.3936

0.01502

1.526

1.0473

238

24.096

59.152

0.94906

0.5905

0.03080

0.009983

0.5199

0.3937

0.01505

1.518

1.0479

239

24.537

59.124

0.96531

0.5874

0.03085

0.009936

0.5119

0.3937

0.01508

1.510

1.0485

240

24.985

59.097

0.98179

0.5844

0.03090

0.009889

0.5041

0.3938

0.01512

1.503

1.0491

241

25.439

59.070

0.99849

0.5814

0.03094

0.009843

0.4964

0.3939

0.01515

1.495

1.0498

242

25.901

59.042

1.0154

0.5785

0.03099

0.009798

0.4889

0.3939

0.01519

1.488

1.0504

243

26.369

59.015

1.0326

0.5756

0.03104

0.009753

0.4815

0.3940

0.01522

1.480

1.0511

244

26.844

58.987

1.0500

0.5727

0.03108

0.009708

0.4742

0.3940

0.01526

1.473

1.0517

245

27.326

58.960

1.0676

0.5698

0.03113

0.009664

0.4671

0.3941

0.01529

1.466

1.0524

246

27.815

58.932

1.0855

0.5669

0.03118

0.009620

0.4601

0.3941

0.01533

1.458

1.0531

247

28.311

58.904

1.1036

0.5641

0.03122

0.009577

0.4532

0.3942

0.01536

1.451

1.0537

248

28.814

58.876

1.1220

0.5613

0.03127

0.009534

0.4465

0.3942

0.01540

1.444

1.0544

249

29.325

58.848

1.1406

0.5585

0.03132

0.009491

0.4398

0.3942

0.01543

1.437

1.0551

250

29.843

58.820

1.1594

0.5558

0.03136

0.009449

0.4333

0.3943

0.01547

1.430

1.0558

251

30.368

58.792

1.1785

0.5531

0.03141

0.009407

0.4269

0.3943

0.01551

1.424

1.0565

252

30.901

58.764

1.1979

0.5504

0.03146

0.009366

0.4207

0.3943

0.01554

1.417

1.0573

253

31.441

58.735

1.2175

0.5477

0.03150

0.009325

0.4145

0.3944

0.01558

1.410

1.0580

254

31.990

58.707

1.2373

0.5451

0.03155

0.009285

0.4084

0.3944

0.01561

1.404

1.0587

255

32.546

58.679

1.2575

0.5424

0.03160

0.009244

0.4025

0.3944

0.01565

1.397

1.0595

256

33.110

58.650

1.2779

0.5398

0.03164

0.009205

0.3967

0.3945

0.01569

1.391

1.0602

257

33.681

58.621

1.2985

0.5373

0.03169

0.009165

0.3909

0.3945

0.01572

1.384

1.0610

258

34.261

58.593

1.3194

0.5347

0.03174

0.009126

0.3853

0.3945

0.01576

1.378

1.0618

259

34.849

58.564

1.3406

0.5322

0.03178

0.009087

0.3798

0.3945

0.01580

1.372

1.0626

260

35.445

58.535

1.3621

0.5297

0.03183

0.009049

0.3743

0.3945

0.01583

1.366

1.0633

261

36.049

58.506

1.3839

0.5272

0.03188

0.009011

0.3690

0.3946

0.01587

1.359

1.0641

262

36.662

58.477

1.4059

0.5247

0.03192

0.008974

0.3637

0.3946

0.01591

1.353

1.0649

263

37.283

58.448

1.4282

0.5223

0.03197

0.008936

0.3586

0.3946

0.01595

1.347

1.0658

264

37.913

58.418

1.4508

0.5199

0.03201

0.008899

0.3535

0.3946

0.01598

1.341

1.0666

265

38.551

58.389

1.4736

0.5175

0.03206

0.008863

0.3485

0.3946

0.01602

1.336

1.0674

266

39.198

58.360

1.4968

0.5151

0.03211

0.008827

0.3436

0.3946

0.01606

1.330

1.0682

267

39.854

58.330

1.5203

0.5128

0.03215

0.008791

0.3388

0.3946

0.01610

1.324

1.0691

268

40.518

58.301

1.5440

0.5104

0.03220

0.008755

0.3341

0.3946

0.01614

1.318

1.0699

269

41.192

58.271

1.5681

0.5081

0.03225

0.008720

0.3294

0.3946

0.01617

1.313

1.0708

270

41.874

58.241

1.5924

0.5058

0.03229

0.008685

0.3248

0.3946

0.01621

1.307

1.0717

271

42.566

58.211

1.6171

0.5036

0.03234

0.008650

0.3204

0.3946

0.01625

1.302

1.0725

272

43.267

58.182

1.6420

0.5013

0.03239

0.008616

0.3159

0.3946

0.01629

1.296

1.0734

273

43.977

58.152

1.6673

0.4991

0.03243

0.008582

0.3116

0.3946

0.01633

1.291

1.0743

274

44.697

58.122

1.6929

0.4968

0.03248

0.008548

0.3073

0.3946

0.01637

1.285

1.0752

275

45.426

58.091

1.7188

0.4947

0.03253

0.008515

0.3031

0.3946

0.01641

1.280

1.0761

276

46.165

58.061

1.7450

0.4925

0.03257

0.008482

0.2990

0.3945

0.01645

1.275

1.0770

277

46.913

58.031

1.7715

0.4903

0.03262

0.008449

0.2949

0.3945

0.01648

1.270

1.0779

278

47.671

58.001

1.7984

0.4882

0.03266

0.008417

0.2909

0.3945

0.01652

1.265

1.0789

279

48.439

57.970

1.8256

0.4860

0.03271

0.008384

0.2870

0.3945

0.01656

1.259

1.0798

280

49.218

57.940

1.8531

0.4839

0.03276

0.008353

0.2832

0.3945

0.01660

1.254

1.0807

281

50.006

57.909

1.8809

0.4819

0.03280

0.008321

0.2794

0.3944

0.01664

1.249

1.0817

282

50.804

57.878

1.9091

0.4798

0.03285

0.008290

0.2756

0.3944

0.01668

1.245

1.0826

283

51.612

57.847

1.9376

0.4777

0.03290

0.008258

0.2720

0.3944

0.01672

1.240

1.0836

284

52.431

57.817

1.9665

0.4757

0.03294

0.008228

0.2683

0.3944

0.01676

1.235

1.0846

285

53.261

57.786

1.9957

0.4737

0.03299

0.008197

0.2648

0.3943

0.01681

1.230

1.0856

286

54.100

57.755

2.0252

0.4717

0.03303

0.008167

0.2613

0.3943

0.01685

1.225

1.0865

287

54.951

57.723

2.0551

0.4697

0.03308

0.008137

0.2578

0.3943

0.01689

1.221

1.0875

288

55.812

57.692

2.0854

0.4677

0.03313

0.008107

0.2545

0.3942

0.01693

1.216

1.0885

289

56.684

57.661

2.1160

0.4658

0.03317

0.008078

0.2511

0.3942

0.01697

1.211

1.0895

290

57.567

57.630

2.1470

0.4638

0.03322

0.008048

0.2479

0.3941

0.01701

1.207

1.0905

291

58.461

57.598

2.1783

0.4619

0.03327

0.008019

0.2446

0.3941

0.01705

1.202

1.0916

292

59.366

57.567

2.2100

0.4600

0.03331

0.007991

0.2415

0.3940

0.01709

1.198

1.0926

293

60.283

57.535

2.2421

0.4581

0.03336

0.007962

0.2383

0.3940

0.01714

1.194

1.0936

294

61.210

57.503

2.2745

0.4562

0.03340

0.007934

0.2353

0.3939

0.01718

1.189

1.0947

295

62.150

57.472

2.3073

0.4544

0.03345

0.007906

0.2322

0.3939

0.01722

1.185

1.0957

296

63.100

57.440

2.3405

0.4525

0.03350

0.007878

0.2293

0.3938

0.01726

1.181

1.0967

297

64.063

57.408

2.3741

0.4507

0.03354

0.007851

0.2263

0.3938

0.01730

1.176

1.0978

298

65.037

57.376

2.4080

0.4489

0.03359

0.007823

0.2234

0.3937

0.01735

1.172

1.0989

299

66.023

57.344

2.4424

0.4471

0.03364

0.007796

0.2206

0.3937

0.01739

1.168

1.0999

300

67.021

57.312

2.4771

0.4453

0.03368

0.007770

0.2178

0.3936

0.01743

1.164

1.1010


13. SYMBOLS

a1 to a3 = constants in Equation (6)
b1 to b3 = exponents in Equation (6)
d0 to d3 = constants in Equation (40)
dv = absolute humidity of moist air, mass of water per unit volume of mixture, lbw/ft3
e0 to e3 = exponents in Equation (40)
f = saturated water vapor pressure enhancement factor
h = specific enthalpy of moist air, Btu/lbda
Hs = rate of sensible heat gain for space, Btu/h
hs* = specific enthalpy of saturated moist air at thermodynamic wet-bulb temperature, Btu/lbda
Ht = rate of total energy gain for space, Btu/h
hw* = specific enthalpy of condensed water (liquid or solid) at thermodynamic wet-bulb temperature and a pressure of 14.696 psia, Btu/lbw
mda = mass of dry air in moist air sample, lbda
= mass flow of dry air, per unit time, lbda/min
mw = mass of water vapor in moist air sample, lbw
= mass flow of water (any phase), per unit time, lbw/min
n = nda + nw, total number of moles in moist air sample
n1 to n10 = constants in Equations (5) and (39)
nda = number of moles of dry air
nw = number of moles of water vapor
p = total pressure of moist air, psia
pda = partial pressure of dry air, psia
ps = vapor pressure of water in moist air at saturation, psia. Differs from saturation pressure of pure water pws at elevated total pressures.
pw = partial pressure of water vapor in moist air, psia
pws = pressure of saturated pure water, psia
Pr = Prandtl number
qs = rate of addition (or withdrawal) of sensible heat, Btu/h
R = universal gas constant, 1545.329 ft · lbf/lb · mol·°R
Rda = specific gas constant for dry air, ft · lbf/lbda · °R
Rw = specific gas constant for water, ft · lbf/lbw · °R
s = specific entropy, Btu/lbda · °R or Btu/lbw · °R
T = absolute temperature, °R
t = dry-bulb temperature of moist air, °F
td = dew-point temperature of moist air, °F
t* = thermodynamic wet-bulb temperature of moist air, °F
V = total volume of moist air sample, ft3
v = specific volume, ft3/lbda or ft3/lbw
W = humidity ratio of moist air, lbw/lbda
Ws* = humidity ratio of moist air at saturation at thermodynamic wet-bulb temperature, lbw/lbda
xda = mole fraction of dry air, moles of dry air per mole of mixture
xw = mole fraction of water, moles of water per mole of mixture
xws = mole fraction of water vapor under saturated conditions, moles of vapor per mole of saturated mixture
Z = altitude, ft

Greek

γ = specific humidity of moist air, mass of water per unit mass of mixture
η = viscosity, lb/(ft · h)
λ = thermal conductivity, Btu/(ft · h · °R)
ν = kinematic viscosity, ft/h
ρ = moist air density, b/ft3
ϕ = relative humidity, dimensionless

Subscripts

da = dry air
f = saturated liquid water
g = saturated water vapor
i = saturated ice
s = saturated moist air
t = total
w = water in any phase

REFERENCES

ASHRAE members can access ASHRAE Journal articles and ASHRAE research project final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.

ASHRAE. 2023. Library of Psychrometric, Thermodynamic, and Transport Properties for Real Humid Air, Steam, Water, and Ice (LibHuAirProp), I-P and SI Units. ASHRAE, available from https://www.ashrae.org/technical-resources/bookstore.

Gatley, D.P. 2013. Understanding psychrometrics, 3rd ed. ASHRAE.

Gatley, D.P., S. Herrmann, and H.-J. Kretzschmar. 2008. A twenty-first century molar mass for dry air. HVAC&R Research (now Science and Technology for the Built Environment) 14:655-662.

Greenspan, L., and A. Wexler. 1968. An adiabatic saturation psychrometer. Journal of Research of the National Bureau of Standards, Section C: Engineering and Instrumentation 72C(1):33-47.

Haines, R.W. 1961. How to construct high altitude psychrometric charts. Heating, Piping, and Air Conditioning 33(10):144-146.

Harrison, L.P. 1965. Fundamental concepts and definitions relating to humidity. In Humidity and moisture measurement and control in science and industry, vol. 3. A. Wexler and W.A. Wildhack, eds. Reinhold, New York.

Herrmann, S., H.-J. Kretzschmar, and D.P. Gatley. 2009. Thermodynamic properties of real moist air, dry air, steam, water, and ice. HVAC&R Research (now Science and Technology for the Built Environment) 15(5): 961-986.

Herrmann, S., H.-J. Kretzschmar, V.C. Aute, D.P. Gatley, and E. Vogel. 2021. Transport properties of real moist air, dry air, steam, and water. Science and Technology for the Built Environment 27(4):393-401.

Hyland, R.W., and A. Wexler. 1983a. Formulations for the thermodynamic properties of dry air from 173.15 K to 473.15 K, and of saturated moist air from 173.15 K to 372.15 K, at pressures to 5 MPa. ASHRAE Transactions 89(2A):520-535.

Hyland, R.W., and A. Wexler. 1983b. Formulations for the thermodynamic properties of the saturated phases of H2O from 173.15 K to 473.15 K. ASHRAE Transactions 89(2A):500-519.

IAPWS. 2018. R6-95, Revised release on the IAPWS formulation 1995 for the thermodynamic properties of ordinary water substance for general and scientific use. International Association for the Properties of Water and Steam. (Available at www.iapws.org).

IAPWS. 2012. R7-97, Revised release on the IAPWS industrial formulation 1997 for the thermodynamic properties of water and steam. International Association for the Properties of Water and Steam. (Available at www.iapws.org).

IAPWS. 2009. R10-06, Revised release on the equation of state 2006 for H2O ice Ih. International Association for the Properties of Water and Steam. (Available at www.iapws.org).

IAPWS. 2008. R12-08, Release on the IAPWS Formulation 2008 for the Viscosity of Ordinary Water Substance. International Association for the Properties of Water and Steam. (Available at www.iapws.org).

IAPWS. 2011. R14-08, Revised release on the pressure along the melting and sublimation curves of ordinary water substance. International Association for the Properties of Water and Steam. (Available at www.iapws.org).

IAPWS. 2011. R15-11, Release on the IAPWS Formulation 2011 for the Thermal Conductivity of Ordinary Water Substance. International Association for the Properties of Water and Steam. (Available at www.iapws.org).

Keeling, C.D., and T.P. Whorf. 2005a. Atmospheric carbon dioxide record from Mauna Loa. Scripps Institution of Oceanography—CO2 Research Group. gml.noaa.gov/ccgg/trends/mlo.html.

Keeling, C.D., and T.P. Whorf. 2005b. Atmospheric CO2 records from sites in the SIO air sampling network. In Trends: A compendium of data on global change. Carbon Dioxide Information Analysis Center, Oak Ridge National Laboratory, U.S. Department of Energy.

Kuehn, T.H., J.W. Ramsey, and J.L. Threlkeld. 1998. Thermal environmental engineering, 3rd ed. Prentice-Hall, Upper Saddle River, NJ.

Mason, E.A., and L. Monchick. 1965. Survey of the equation of state and transport properties of moist gases. In Humidity and moisture measurement and control in science and industry, vol. 3. A. Wexler and W.A. Wildhack, eds. Reinhold, New York.

Mohr, P.J., and P.N. Taylor. 2005. CODATA recommended values of the fundamental physical constants: 2002. Reviews of Modern Physics 77:1-107.

NASA. 1976. U.S. Standard atmosphere, 1976. National Oceanic and Atmospheric Administration, National Aeronautics and Space Administration, and the United States Air Force. Available from National Geophysical Data Center, Boulder, CO.

Nelson, H.F., and H.J. Sauer, Jr. 2002. Formulation of high-temperature properties for moist air. International Journal of HVAC&R Research 8(3):311-334.

Olivieri, J. 1996. Psychrometrics—Theory and practice. ASHRAE.

Palmatier, E.P. 1963. Construction of the normal temperature. ASHRAE psychrometric chart. ASHRAE Transactions 69:7-12.

Rohsenow, W.M. 1946. Psychrometric determination of absolute humidity at elevated pressures. Refrigerating Engineering 51(5):423.

Simões-Moreira, J.R. 1999. A thermodynamic formulation of the psychrometer constant. Measurement Science and Technology 10(4):302-311.

BIBLIOGRAPHY

Brenner, J.P., G.F. Nellis, and D.T. Reindl. 2010. Design specifications for wet-bulb aspirator apparatus. ASHRAE Research Project RP-1460, Final Report.

Gatley, D.P. 2016. A proposed full range relative humidity definition. ASHRAE Journal 58(3):24-29.

Herrmann, S., H.-J. Kretzschmar, V.C. Aute, D.P. Gatley, and E. Vogel. 2018. Transport properties of real moist air, dry air, steam, and water. ASHRAE Research Project RP-1767, Final Report.

Herrmann, S., H.-J. Kretzschmar, and D.P. Gatley. 2020. Thermodynamic properties of real moist air, dry air, steam, water, and ice. ASHRAE Research Project RP-1485, Final Report.

Lemmon, E.W., R.T. Jacobsen, S.G. Penoncello, and D.G. Friend. 2000. Thermodynamic properties of air and mixture of nitrogen, argon, and oxygen from 60 to 2000 K at pressures to 2000 MPa. Journal of Physical and Chemical Reference Data 29:331-385.

NIST. 1990. Guidelines for realizing the international temperature scale of 1990 (ITS-90). NIST Technical Note 1265. National Institute of Technology and Standards, Gaithersburg, MD.

Wexler, A., R. Hyland, and R. Stewart. 1983. Thermodynamic properties of dry air, moist air and water and SI psychrometric charts. ASHRAE Research Projects RP-216 and RP-257, Final Report.



The preparation of this chapter is assigned to TC 1.1, Thermodynamics and Psychrometrics.