1.1 ONE-DIMENSIONAL ASSEMBLY U-FACTOR CALCULATION
The assembly U-factor for a building envelope assembly determines the rate of steady-state heat conduction through the assembly. One-dimensional heat flow through building envelope assemblies is the starting point for determining whole-building heat transmittance.
Example 1.
Calculate the system R-value RSystem, assembly total resistance (RAssembly), and UAssembly-factor of the sandwich panel assembly shown in Figure 1; assume winter conditions when selecting values for air films from Table 3 in Chapter 26.
Solution: Determine indoor and outdoor air film resistances from Table 3 in Chapter 26, and thermal resistance of all components from Table 1 in that chapter. If any elements are described by conductivity (independent of thickness) rather than thermal resistance (thickness-dependent), then calculate the resistance.
The conductivity k of expanded polystyrene is 0.035 W/(m · K). For 150 mm thickness,
To calculate the system’s R-value in the example, sum the R-values of the system components only, disregarding indoor and outdoor air films.
The assembly R-value (RAssembly) consists of the system’s R-value plus the thermal resistance of the interior and exterior air films.
Example 2.
Find the U-factor of the commercial roof assembly shown in Figure 2; assume summer conditions when selecting values for air films from Table 3 in Chapter 26.
Solution: The calculation procedure is similar to that shown in Example 1. Note the U-factor of nonvertical assemblies depends on the direction of heat flow [i.e., whether the calculation is for winter (heat flow up) or summer (heat flow down)], because the resistances of indoor air films and plane air spaces in ceilings differ, based on the heat flow direction (see Table 3 in Chapter 26). The effects of mechanical fasteners are not addressed in this example.
Using UAssembly = 1/RAssembly, the UAssembly-factor is 0.17 W/(m2 · K).
During sunny periods, unconditioned attics may be hotter than outdoor air. Peak attic temperatures on a hot, sunny day may be 10 to 45 K above outdoor air temperature, depending on factors such as shingle color, roof framing type, air exchange rate through vents, and use of radiant barriers. Therefore, simple one-dimensional solutions cannot be offered for attics. Energy efficiency estimates can be obtained using models such as Wilkes (1991).
Basement Walls and Floors
Heat transfer through basement walls and floors to the ground depends on the following factors: (1) the difference between the air temperature in the room and that of the ground and outside air, (2) the material of the walls or floor, and (3) the thermal conductivity of surrounding earth. The latter varies with local conditions and is usually unknown. Because of the great thermal inertia of surrounding soil, ground temperature varies with depth, and there is a substantial time lag between changes in outdoor air temperatures and corresponding changes in ground temperatures. As a result, ground-coupled heat transfer is less amenable to steady-state representation than above-grade building elements. However, there are several simplified procedures for estimating ground-coupled heat transfer. These fall into two main categories: (1) those that reduce the ground heat transfer problem to a closed-form solution, and (2) those that use simple regression equations developed from statistically reduced multidimensional transient analyses.
Closed-form solutions, including Latta and Boileau’s (1969) procedure discussed in Chapter 17, generally reduce the problem to one-dimensional, steady-state heat transfer. These procedures use simple, “effective” U-factors or ground temperatures or both. Methods differ in the various parameters averaged or manipulated to obtain these effective values. Closed-form solutions provide acceptable results in climates that have a single dominant season, because the dominant season persists long enough to allow a reasonable approximation of steady-state conditions at shallow depths. The large errors (percentage) that are likely during transition seasons should not seriously affect building design decisions, because these heat flows are relatively insignificant compared to those of the principal season.
The ASHRAE arc-length procedure (Latta and Boileau 1969) is a reliable method for wall heat losses in cold winter climates. Chapter 17 discusses a slab-on-grade floor model developed by one study. Although both procedures give results comparable to transient computer solutions for cold climates, their results for warmer U.S. climates differ substantially.
Research conducted by Dill et al. (1945) and Hougten et al. (1942) indicates a heat flow of approximately 6.3 W/m2 through an uninsulated concrete basement floor with a temperature difference of 11 K between the basement floor and the air 150 mm above it. A U-factor of 5.7 W/(m2 · K) is sometimes used for concrete basement floors on the ground. For basement walls below grade, the temperature difference for winter design conditions is greater than for the floor. Test results indicate that, at the mid-height of the below-grade portion of the basement wall, the unit area heat loss is approximately twice that of the floor.
For small concrete slab floors (equal in area to a 7.5 by 7.5 m house) in contact with the ground at grade level, tests indicate that heat loss can be calculated as proportional to the length of exposed edge rather than total area. This amounts to 1.4 W per linear metre of exposed edge per degree temperature difference between indoor air and the average outdoor air temperature. This value can be reduced appreciably by installing insulation under the ground slab and along the edge between the floor and abutting walls. In most calculations, if the perimeter loss is calculated accurately, no other floor losses need to be considered. Chapters 17 and 18 contain heat transfer and load calculation guidance for floors on grade and at different depths below grade.
The second category of simplified procedures uses transient two-dimensional computer models to generate ground heat transfer data, which are then reduced to compact form by regression analysis (Mitalas 1982, 1983; Shipp 1983). These are the most accurate procedures available, but the database is very expensive to generate. In addition, these methods are limited to the range of climates and constructions specifically examined. Extrapolating beyond the outer bounds of the regression surfaces can produce significant errors.
Guide details and recommendations related to application of concepts for basements are provided in Chapter 44 of the 2019 ASHRAE Handbook—HVAC Applications. Detailed analysis of heat transfer through foundation insulation may also be found in the Building Foundation Design Handbook (Labs et al. 1988).
1.2 TWO-DIMENSIONAL ASSEMBLY U-FACTOR CALCULATION
The following examples show three methods of two-dimensional, steady-state conductive heat transfer analysis through wall assemblies. They offer approximations to overall rates of heat transfer (U-factor) when assemblies contain a layer composed of dissimilar materials. The methods are described in Chapter 25. The parallel-path method is used when the thermal conductivity of the dissimilar materials in the layer are rather close in value (within the same order of magnitude), as with wood-frame walls. The isothermal-planes method is appropriate for materials with conductivities moderately different from those of adjacent materials (e.g., masonry). The zone method and the modified zone method are appropriate for materials with a very high difference in conductivity (two orders of magnitude or more), such as with assemblies containing metal.
Two-dimensional, steady-state heat transfer analysis is often conducted using computer-based finite difference methods. If the resolution of the analysis is sufficiently fine, computer methods provide better simulations than any of the methods described here, and the results typically show better agreement with measured values.
The methods described here do not take into account heat storage in the materials, nor do they account for varying material properties (e.g., when thermal conductivity is affected by moisture content or temperature). Transient analysis is often used in such cases.
The assembly R-values and U-factors of wood-frame walls can be calculated by assuming either parallel heat flow paths through areas with different thermal resistances or by assuming isothermal planes. Equation (15) in Chapter 25 provides the basis for the two methods.
The framing factor expresses the fraction of the total building component (wall or roof) area that is framing. The value depends on the specific type of construction, and may vary based on local construction practices, even for the same type of construction. For stud walls 400 mm on center (OC), the fraction of insulated cavity may be as low as 0.75, where the fraction of studs, plates, and sills is 0.21 and the fraction of headers is 0.04. For studs 600 mm OC, the respective values are 0.78, 0.18, and 0.04. These fractions contain an allowance for multiple studs, plates, sills, extra framing around windows, headers, and band joists. These assumed framing fractions are used in Example 3, to illustrate the importance of including the effect of framing in determining a building’s overall thermal conductance. The actual framing fraction should be calculated for each specific construction.
Example 3.
Calculate the UAssembly-factor of the 38 by 90 mm stud wall shown in Figure 3. The studs are at 400 mm OC. There is 90 mm mineral fiber batt insulation (R-2.3) in the stud space. The inside finish is 13 mm gypsum wallboard, and the outside is finished with rigid foam insulating sheathing (R-0.7) and vinyl siding. The insulated cavity occupies approximately 75% of the transmission area; the studs, plates, and sills occupy 21%; and the headers occupy 4%.
Solution: If the R-values of building elements are not already specified, obtain the R-values from Tables 1 and 3 of Chapter 26. Assume R = 7.0 (m2 · K)/W for the wood framing . Also, assume the headers are solid wood, and group them with the studs, plates, and sills.
Two simple methods may be used to determine the U-factor of wood frame walls: parallel path and isothermal planes. For highly conductive framing members such as metal studs, the modified zone method must be used.
Parallel-Path Method:
Individual U-factors are reciprocals of the R-value, so U1 = 0.301 and U2 = 0.553 W/(m2 · K). If the wood framing is accounted for using the parallel-path flow method, the wall’s U-factor is determined using Equation (15) from Chapter 25. The fractional area of insulated cavity is 0.75 and the fractional area of framing members is 0.25.
With the isothermal-planes method, the fractional areas are applied only to the building layer that contains the studs and cavity-fill insulation. The average R-value for this layer (Ravs) is added to the R-values of the other components for a total R for the assembly.
Isothermal-Planes Method:
The average R-value Ravs of the stud cavity is calculated using the fractional area of stud and insulation using Equation (15) from Chapter 25.
If the wood framing is included using the isothermal-planes method, the U-factor of the wall is determined using Equations (10) and (11) from Chapter 25 as follows:
For a frame wall with a 600 mm OC stud space, the assembly R-value is 2.76 (m2 · K)/W. Similar calculation procedures may be used to evaluate other wall designs, except those with thermal bridges.
The average overall R-values of masonry walls can be estimated by assuming a combination of layers in series, one or more of which provides parallel paths. This method is used because heat flows laterally through block face shells so that transverse isothermal planes result. Average total resistance RAssembly is the sum of the resistances of the layers between such planes, each layer calculated as shown in Example 4.
Example 4.
Calculate the overall thermal resistance and average U-factor of the 194 mm thick insulated concrete block wall shown in Figure 4. The two-core block has an average web thickness of 25 mm and a face shell thickness of 32 mm. Overall block dimensions are 194 by 194 by 395 mm. Measured thermal resistances of 1700 kg/m3 concrete and 110 kg/m3 expanded perlite insulation are 0.70 and 20 (m2 · K)/W, respectively. (Note: This type of insulation is no longer commonly used with concrete block walls. This historical example has been retained because it is a simplified case with supporting experimental data.)
Solution: The equation used to determine the overall thermal resistance of the insulated concrete block wall is derived from Equations (7) and (15) from Chapter 25 and is given below:
where
| RT(av) | = | overall thermal resistance based on assumption of isothermal planes |
| Ri | = | thermal resistance of inside air surface film (still air) |
| Ro | = | thermal resistance of outside air surface film (6.7 m/s wind) |
| Rf | = | total thermal resistance of face shells |
| Rc | = | thermal resistance of cores between face shells |
| Rw | = | thermal resistance of webs between face shells |
| aw | = | fraction of total area transverse to heat flow represented by webs of blocks |
| ac | = | fraction of total area transverse to heat flow represented by cores of blocks |
From the information given and the data in Tables 1 and 3 in Chapter 26, determine the values needed to compute the overall thermal resistance.
| Ri | = | 0.12 |
| Ro | = | 0.03 |
| Rf | = | 2 × 0.032 × 0.70 = 0.045 |
| Rc | = | (0.194 – 2 × 0.032) × 20 = 2.60 |
| Rw | = | (0.194 – 2 × 0.032) × 0.70 = 0.091 |
| aw | = | 3 × 25/395 = 0.190 |
| ac | = | 1 – 0.190 = 0.810 |
Using the equation given, the overall thermal resistance and average U-factor are calculated as follows:
Based on guarded hot-box tests of this wall without mortar joints, Tye and Spinney (1980) measured the assembly R-value for this insulated concrete block wall as 0.551 (m2 · K)/W.
Assuming parallel heat flow only, the calculated resistance is higher than that calculated on the assumption of isothermal planes. The actual resistance generally is some value between the two calculated values. In the absence of test values, examination of the construction usually reveals whether a value closer to the higher or lower calculated R-value should be used. Generally, if the construction contains a layer in which lateral conduction is high compared with transmittance through the construction, the calculation with isothermal planes should be used. If the construction has no layer of high lateral conductance, the parallel heat flow calculation should be used.
Hot-box tests of insulated and uninsulated masonry walls constructed with block of conventional configuration show that thermal resistances calculated using the isothermal planes heat flow method agree well with measured values (Shu et al. 1979; Valore 1980; Van Geem 1985). Neglecting horizontal mortar joints in conventional block can result in thermal transmittance values up to 16% lower than actual, depending on the masonry’s density and thermal properties, and 1 to 6% lower, depending on the core insulation material (McIntyre 1984; Van Geem 1985). For aerated concrete block walls, other solid masonry, and multicore block walls with full mortar joints, neglecting mortar joints can cause errors in R-values up to 40% (Valore 1988). Horizontal mortar joints, usually found in concrete block wall construction, are neglected in Example 4.
Constructions Containing Metal
Curtain and metal stud-wall constructions often include metallic and other thermal bridges, which can significantly reduce the thermal resistance. However, the capacity of the adjacent facing materials to transmit heat transversely to the metal is limited, and some contact resistance between all materials in contact limits the reduction. Contact resistances in building structures are only 0.01 to 0.1 (m2 · K)/W, too small to be of concern in many cases. For these metal stud/wall constructions, the recommended approach is the modified zone method (see Example 7) or two-dimensional analysis software such as THERM.
Thermal characteristics for panels of sandwich construction can be computed by combining the thermal resistances of the layers. R-values for assembled sections should be determined on a representative sample by using a hot-box method. If the sample is a wall section with air cavities on both sides of fibrous insulation, the sample must be of representative height because convective airflow can contribute significantly to heat flow through the test section. Computer modeling can also be useful, but all heat transfer mechanisms must be considered.
The metal studs in Example 5 are 90 mm deep and placed at 400 mm on center. The metal member is only 0.5 mm thick, but it is in contact with adjacent facings over a 32 mm wide area. The steel member is 32 mm deep, has a thermal resistance of approximately 0.0019 (m2 · K)/W, and is virtually isothermal.
For this insulated steel frame wall, Farouk and Larson (1983) measured an assembly R-value of 1.16 (m2 · K)/W. For the same assembly, the recommended modified zone method (see Example 5) gives an assembly R-value of 1.18 (m2 · K)/W. Two-dimensional analysis (THERM) yields Uav = 1.0 or R = 1.00 (m2 · K)/W. ASHRAE/IES Standard 90.1 describes how to determine the thermal resistance of wall assemblies containing metal framing by using insulation/framing adjustment factors in Table A9.2B of the standard. For 38 by 90 mm steel framing, 400 mm OC, Fc = 0.50. Using the correction factor method, an assembly R-value of 1.13 (m2 · K)/W [0.08 + 1.94(0.50) + 0.08] is obtained for the wall described here.
Zone Method of Calculation
For structures with widely spaced metal members of substantial cross-sectional area, the isothermal planes method can give thermal resistance values that are too low. For these constructions, the zone method can be used. This method involves two separate computations: one for a chosen limited portion, zone A, containing the highly conductive element; the other for the remaining portion of simpler construction, zone B. The two computations are then combined using the parallel-flow method, and the average transmittance per unit overall area is calculated. The basic laws of heat transfer are applied by adding the area conductances CA of elements in parallel, and adding area resistances R/A of elements in series. The modified zone method improves on the zone method with better guidance for defining the widths of zones A and B.
Modified Zone Method for Metal Stud Walls with Insulated Cavities
The modified zone method is similar to the parallel-path and zone methods; all three are based on parallel-path calculations. Figure 5 shows the width w of the zone of thermal anomalies around a metal stud. This zone can be assumed to equal the length of the stud flange L (parallel-path method), or can be calculated as a sum of the length of stud flange and a distance double that from wall surface to metal Σdi (zone method). In the modified zone method, the width of the zone depends on three parameters:
Example 5.
Calculate the U-factor of the wall section shown in Figure 5 using the modified zone method.
Solution: The wall cross section is divided into two zones: the zone of thermal anomalies around the metal stud (zone W), and the cavity zone (zone cav). Wall material layers are grouped into exterior and interior surface sections A (sheathing, siding) and B (wallboard), and interstitial sections I and II (cavity insulation, metal stud flange).
Assuming that the wall materials in section A are thicker than those in section B, as shown, they can be described as follows:
where
| n | = | number of material layers (of thickness di) between metal stud flange and wall surface for section A |
| m | = | number of material layers (of thickness dj) for section B |
Then, the width W of zone W can be estimated by
where
| L | = | stud flange size |
| di | = | thickness of material layers in section A |
| zf | = | zone factor, shown in Figure 6 (zf = 2 for zone method) |
Kosny and Christian (1995) developed the modified zone method and verified its accuracy for over 200 simulated cases of metal frame walls with insulated cavities. For all configurations considered, the discrepancy between results were within ±2%. Hot-box-measured R-values for 15 metal stud walls tested by Barbour et al. (1994) were compared with results obtained by Kosny and Christian (1995) and McGowan and Desjarlais (1997). The modified zone method was found to be the most accurate simple method for estimating the clear-wall R-value of light-gage steel stud walls with insulated cavities. However, this analysis does not apply to construction with metal sheathing. Also, ASHRAE Standard 90.1 may require a different method of analysis.
 
-
Step 2
Calculate width W of affected zone W:
-
Step 3
Calculate the exterior and interior thermal resistances, using conductivity or thermal resistance values from step 1.
The particular thermal resistances of the zone elements are then calculated.
Zone W is the zone at the web of the metal member. For width W, the thermal conductance C is calculated as the sum of the contributory areas. Because the thickness of the web of the metal member is dI and the length along the flange section is L,
Using resistance rather than conductance, the contributing R-values are calculated as
At the cavity, the sum of the series R-values is
In zone W, the sum of the R-values is
The total conductivity across the length s is proportional to the contributing lengths of zone W and the cavity:
or
In this example, the calculated total R-value for the wall is 2.71 (m2 · K)/W, and the wall’s U-factor is 0.369 W/(m2 · K).
Building enclosure geometry of two- and three-dimensional assemblies may be complex, including corners, terminations of materials, and junctures of different materials. Such assemblies cannot be analyzed effectively with explicit calculations; rather, they require iterative calculations using computers. These calculations have been made for a number of common assemblies (Hershfield 2011), and the results can be applied within a simpler estimation method, as shown in Example 6.
Buildings with thermal mass or other forms of thermal storage require dynamic models to evaluate their performance in the environmental climate of interest.
Figure 7 shows a corner composed of homogeneous material. Surface temperatures can be estimated from the intersections of isotherms and the surface. If, in this figure, the interior were warm with respect to outside, then the line at the corner would be colder than the remainder of the interior surface. This effect may be exacerbated by the air film at the corner, which has a greater effective thickness than on the plane of the wall, and therefore offers greater thermal resistance, further lowering the corner temperature.
Figure 8 shows an insulating material applied to a conductive material. Insulation is placed at the inside, during a period of cold outdoor temperatures. A computer program may be used to trace the isotherms. The interior isotherm is cut where the insulating material is interrupted, indicating lowered temperature at that location (point A). In fact, the temperature at the edge of the interrupted insulation is even lower than that at the surface of the uninsulated wall. Interruptions in insulation can lead to thermal bridges. For this reason, insulating conductive assemblies such as masonry or concrete is often more successful when applied to the outside rather than to the inside of the building.
Example 6.
Comparing Linear Transmittance Method to Area-Weighted Method for Brick Veneer Shelf Angle Anomaly.
Calculate the overall U-value of the steel-stud brick veneer assembly with a slab and shelf angle with exterior insulation R-15 (2.6 RSI) and interior stud cavity insulation R-12 (2.1 RSI) (see Figure 9), using the following information and method:
| Gross wall height | = | 2.7 m |
| Gross wall length | = | 15.2 m |
| Gross wall area | = | 41.0 m |
Area-Weighted Method. The thermal transmittance Ub for the area around the shelf angle is 1.162 W/(m2·K) for the effective lengths L1 = 205 mm, L2 = 619 mm, and Uo = 0.287 W/(m2·K). [Area thermal transmittance depends on the definition of the effective lengths (Hershfield 2011). This calculation is not shown here.]
Calculate area for the thermal anomaly and area for the clear field:
Calculate the overall U-value:
Linear Transmittance Method. From Appendix F of RP-1365, for this brick veneer assembly, Uo = 0.287 W/(m2 · K) and the linear transmittance Ψ of a slab with a shelf angle for this assembly is 0.544 W/(m · K).
Calculate the overall U-value
This example illustrates the simplicity of the linear transmittance method compared to the area-weighted method for thermal anomalies in opaque building envelope assemblies. The amount of information that must be provided is reduced and the calculation is simpler. The weighted average method is further complicated for a whole-building elevation when accounting for 3D intersections. Some [e.g., Kemp (1997)] suggest that the overlapping effects be combined using mitered corners.
Table 4 of Chapter 15 lists U-factors for various fenestration products. For heat transmission coefficients for wood and steel doors, see Table 6 in Chapter 15. All U-factors are approximate, because a significant portion of the resistance of a window or door is contained in the air film resistances, and some parameters that may have important effects are not considered. For example, the listed U-factors assume the surface temperatures of surrounding bodies are equal to the ambient air temperature. However, the indoor surface of a window or door in an actual installation may be exposed to nearby radiating surfaces, such as radiant heating panels, or opposite walls with much higher or lower temperatures than the indoor air. Air movement across the surface of a window or door, such as that caused by nearby heating and cooling outlet grilles or by wind outdoors, increases the U-factor.