The main characteristic of an air barrier system is reduced air permeance. To create that performance, the barrier must
-
Meet material permeability requirements.
-
Be continuous when installed (i.e., tight joints in air barrier assembly; effective bonds in air barrier materials at intersections such as wall/roof, wall/foundation, and wall/windows; tightly sealed penetrations).
-
Accommodate dimensional changes caused by temperature or shrinkage without damaging joints or air barrier material.
-
Be strong enough to support stresses applied to air barrier material or assembly. The air barrier must not be ruptured or excessively deformed by wind and stack effect. Where an adhesive is used to complete a joint, the assembly must be designed to withstand forces that might gradually peel away the air barrier material. Where the material is not strong enough to withstand anticipated wind and other loads, it must be supported on both sides to account for positive and negative wind gust pressures.
In addition, the following properties can be important, depending on the application:
-
Elasticity
-
Thermal stability
-
Fire and flammability resistance
-
Inertness to deteriorating elements
-
Ease of fabrication, application, and joint sealing
Air barriers may control both vapor and airflow (i.e., they may act as an air/vapor retarder), depending on the characteristics of the materials used. Many designs are based on this idea, with measures taken to ensure that the layer with vapor-retarding properties is continuous to control airflow. Some designs treat airflow and vapor retarders as separate entities, but an airflow retarder should not be where it can cause moisture to condense if it also has vapor-retarding properties. For example, a vapor-retarding air barrier placed on the cold side of a building envelope may cause condensation, particularly if the vapor retarder at the other side of the building is ineffective. Instead, a carefully installed, sealed cold-side air retarder that has sufficient thermal resistance may lower the potential for condensation by raising the temperature at its inside surface during the cold season (Ojanen et al. 1994).
Air leakage characteristics can be determined with the ASTM Standard E1186 test method for air barriers on the interior side of the building envelope, and described according to ASTM Standard E1677. Specific air leakage criteria for air barriers in cold heating climates are found in Di Lenardo et al. (1995). These specifications provide classes for air leakage rates of 0.05, 0.10, 0.15, and 0.20 L/(s · m2) when measured with an air pressure difference of 75 Pa, depending on the water vapor permeance of the outermost layer of the building envelope. The highest leakage rate applies if the permeance of the outermost layer is greater than 600 ng/(Pa · s · m2); the lowest rate applies if the permeance is less than 60 ng/(Pa · s · m2). Intermediate values are also provided. The recommendations apply only to heating climates.
The required air permeance of an air barrier material has been set by some building codes at 0.02 L/(s · m2) at a pressure difference of 75 Pa. A 2008 addendum to ASHRAE Standard 90.1 also references this value. ASTM Standard E1677 provides an alternative minimum air barrier test and criteria specifically suitable for framed walls of low-rise buildings.
Air leakage characteristics of an air barrier assembly can be determined with the ASTM Standard E2357 test method, which measures the air leakage of three wall specimens: (1) with the air barrier material installed using air barrier accessories alone, (2) with the air barrier material installed and connected to air barrier components (window, doors, and other premanufactured elements) using air barrier accessories, and (3) with an air barrier wall assembly connected to a foundation assembly and roof assembly using air barrier accessories. The test method reports the air leakage rate at a reference pressure difference of 75 Pa, not because it is necessarily representative of in-service conditions, but because it provides a more accurate measurement that can then be adjusted for actual conditions.
Building assemblies are constructed and the various air barrier assemblies are connected to form an air barrier system for the whole building. The building’s air leakage characteristics can be determined with the ASTM Standard E779 test method. A 2008 addendum to ASHRAE Standard 90.1 requires 2.0 L/(s · m2) at 75 Pa pressure difference.
The effectiveness of an air barrier is greatly reduced by openings and penetrations, even small ones. These openings can be caused by poor design, poor workmanship during application, insufficient coating thickness, improper caulking and flashing, uncompensated thermal expansion, mechanical forces, aging, and other forms of degradation. Faults or leaks typically occur at electrical boxes, plumbing penetrations, telephone and television wiring, and other unsealed openings in the structure. This is especially true if telephone, television, or other services are installed after the envelope has been inspected and/or tested. A ceiling air barrier should be continuous at chases for plumbing, ducts, flues, and electrical wiring. In flat roofing, mechanical fasteners are sometimes used to adhere the system to the deck, and often penetrate the air barrier. In heating climates, the resulting holes may allow air exfiltration and accompanying water vapor leakage into the roof. ASTM Standard E1186 describes several techniques for locating air leakage sites in building envelopes and air barrier systems.
As noted previously, air barrier assemblies must withstand pressures exerted by stack effects, wind, or both during construction and over the building’s life. The magnitude of pressure varies, depending on building type and sequence of construction. At one extreme, single-family dwellings may be built with exterior cladding partly or entirely installed and insulation in place before the air barrier is added. Chimney effects in these buildings are small, even in cold weather, so stresses on the air barrier during construction are small. At the other extreme, wind and chimney effect forces in tall buildings are much greater. A fragile, unprotected sheet material should not be used as an air barrier because it will probably be torn by wind before construction is completed.
Calculations of water vapor flow, interstitial condensation, and related moisture accumulation using only water vapor resistances are useless when airflow is involved. More information on air leakage in buildings may be found in Chapter 16.
The main characteristic of a water vapor retarder is low vapor permeance. The following properties are also important, depending on the application:
Thermal stability
-
Fire and flammability resistance
-
Resistance to other deteriorating elements [e.g., chemicals, ultraviolet (UV) radiation]
-
Ease of fabrication, application, and joint sealing
Although a flow of dry air may accelerate drying of a wet building component (Karagiozis and Salonvaara 1999a, 1999b), vapor retarders are completely ineffective without effective airflow control, A single layer may serve both purposes, of course: the designer must assess the needs for control of water vapor and air movement in a building envelope, and devise a system that guarantees the required vapor retarder and air barrier properties.
Water vapor retarders demand consideration in every building design. The need for and type of system depend on the climate zone, construction type, building usage, and moisture sources other than indoor water vapor to be considered. Water vapor retarders were originally designed to protect building elements from water vapor diffusing through building materials and condensing against and in layers at the cold side of the thermal insulation. It is now recognized that it is just as important to allow a building assembly to dry as it is to keep the building assembly from getting wet by vapor diffusion. In some cases, to allow the building assembly to dry, a water vapor retarder may not be needed, or should be semipermeable. In other cases, the environmental conditions, building construction, and building usage may dictate that a material with very low water vapor permeance should be installed to protect building components. A balanced design approach is required: a vapor retarder can reduce the potential for an assembly to dry, but can also reduce the potential for the assembly getting wet. ASHRAE Standard 160 should be followed to determine the need for and placement of a vapor retarder.
The 2007 supplement to the International Codes (ICC 2007) lists three water vapor retarder classes:
-
Class I: 5.7 ng/(Pa · s · m2) or less
-
Class II: more than 5.7 ng/(Pa · s · m2) but less than or equal to 57 ng/(Pa · s · m2)
-
Class III: more than 57 ng/(Pa · s · m2) but less than or equal to 570 ng/(Pa · s · m2)
The designer should determine the type of water vapor retarder needed and its location in the envelope assembly, based on climatic conditions, other materials used in the assembly, additional sources of humidity, and the building’s use (e.g., intended relative humidity).
A vapor retarder typically slows the rate of water vapor diffusion, but does not totally prevent it. In most cases, requirements for vapor retarders in envelope assemblies are not extremely stringent: because conditions on the inside and outside of buildings vary continually, air movement and ventilation can provide wetting as well as drying at various times, and water vapor entering one side of an envelope assembly can be stored temporarily as hygroscopic moisture and released later. A vapor barrier is often used to try to stop water vapor transport when the real problem is transport of water vapor by air transport. This causes confusion between the use and function of vapor barriers/retarders and those of air barriers. However, if conditions are conducive to excessive humidification, water vapor retarders help to (1) keep the thermal insulation dry; (2) prevent structural damage from rot, corrosion, freeze/thaw, and other environmental actions; and (3) reduce paint problems on exterior walls (although rain absorption through cracks in the paint may be a more probable cause of paint problems) (ASTM Standard C755). Judicious placement of a vapor retarder may also help an assembly to dry out. Another way to look at a vapor retarder is that it is the most vapor-resistant layer in the assembly; a capable designer knows where this layer is and ensures that it does not promote excessive moisture accumulation or prevent the assembly from drying. Therefore, all building envelope assemblies should be assessed to ensure that an unintentional water vapor retarder does not create problems.
The vapor retarder’s effectiveness depends on its vapor permeance, installation, and location in the insulation. The retarder should be at or near the surface exposed to higher water vapor pressure and higher temperature. In heating climates, this is usually the winter-warm side.
Water vapor retarders are classified as rigid, flexible, or coating materials. Rigid retarders include reinforced plastics, aluminum, and stainless steel. These usually are mechanically fastened in place and are vapor-sealed at the joints. Flexible retarders include metal foils, laminated foil and treated papers, coated felts and papers, and plastic films or sheets. They are supplied in roll form or as an integral part of a building material (e.g., insulation). Accessory materials are required for sealing joints. Coating retarders may be semifluid or mastic; paint (called surface coatings); or hot melt, including thermofusible sheet materials. Their basic composition may be asphaltic, resinous, or polymeric, with or without pigments and solvents, as required to meet design conditions. They can be applied by spray, brush, trowel, roller, dip, or mop, or in sheet form, depending on the type of coating and surface to which it is applied. Potentially, each of these materials is an air barrier; however, to meet air barrier specifications, it must satisfy requirements for strength, continuity, and air permeance. A construction of several materials, some perhaps of substantial thickness, can also constitute a vapor retarder system. In fact, designers have many options. For example, airflow and moisture movement might be controlled using an interior finish, such as drywall, to provide strength and stiffness, along with a low-permeability coating, such as a vapor-retarding paint, to provide the required low permeance. Other designs may use more than one component. However, (1) any component that qualifies as a vapor retarder usually also impedes airflow, and is thus subject to air pressure differences that it must resist; and (2) any component that impedes airflow may also retard vapor movement and promote condensation or frost formation if it is at the wrong location in the assembly.
Several studies found a significant increase in apparent permeance as a result of small holes in the vapor retarder. For example, Seiffert (1970) reported a hundredfold increase in the vapor permeance of aluminum foil when it is 0.014% perforated, and a 4000-fold increase when 0.22% of the surface is perforated. In general, penetrations particularly degrade a vapor retarder’s effectiveness if it has very low permeance (e.g., polyethylene or aluminum foil). In addition, perforations may lead to air leakage, which further erodes effectiveness.
“Smart” vapor retarders allow substantial summer drying while functioning as effective vapor retarders during the cold season. One type of smart vapor retarder has low vapor permeance but conducts liquid water, allowing moisture that condenses on the retarder to dry. Korsgaard and Pedersen (1989, 1992) describe such a retarder composed of synthetic fabric sandwiched between staggered strips of plastic film. The fabric wicks liquid water while the plastic film retards vapor flow. Another type of smart vapor retarder provides low vapor permeance at low relative humidities, but much higher permeance at high relative humidity. During the heating season in cold and moderate climates, the indoor humidity usually is below 50% and the smart vapor retarder’s permeance is low. In the summer or on winter days with high solar heat gains, when the temperature gradient is inward, moisture moving from exterior parts of the wall or roof raises the relative humidity at the vapor retarder. This increases vapor permeance and potential for the wall or roof to dry out. One such vapor retarder is described by Kuenzel (1999). Below 50% rh, the film’s permeance is less than 57 ng/(Pa · s · m2), but it increases above 60% rh, reaching 2050 ng/(Pa · s · m2) at 90% rh.
Apparent soil thermal conductivity is difficult to estimate and may change in the same soil at different times because of changed moisture conditions and freezing temperatures.
Figure 6 shows typical apparent soil thermal conductivity as a function of moisture content for different general types of soil. The figure is based on data presented in Salomone and Marlowe (1989) using envelopes of thermal behavior coupled with field moisture content ranges for different soil types. In Figure 6, “well graded” applies to granular soils with good representation of all particle sizes from largest to smallest. “Poorly graded” refers to granular soils with either uniform gradation, in which most particles are about the same size, or skip (or gap) gradation, in which particles of one or more intermediate sizes are not present.
As heat flows through soil, moisture tends to move away from the heat source. This moisture migration provides initial mass transport of heat, but it also dries the soil adjacent to the heat source, thus lowering the apparent thermal conductivity in that zone of soil.
Typically, when other factors are held constant, k increases with moisture content and with dry density of a soil, but decreases with increasing organic content of a soil and for uniform gradations and rounded soil grains (because grain-to-grain contacts are reduced). The k of a frozen soil may be higher or lower than that of the same unfrozen soil (because the conductivity of ice is higher than that of water but lower than that of typical soil grains). Differences in k below moisture contents of 7 to 8% are quite small. At approximately 15% moisture content, k may vary up to 30% from unfrozen values.
Although thermal conductivity varies greatly over the complete range of possible moisture contents, this range can be narrowed if it is assumed that the moisture contents of most field soils lie between the wilting point of the soil (i.e., the moisture content of a soil below which a plant cannot alleviate its wilting symptoms) and the field capacity of the soil (i.e., the moisture content of a soil that has been thoroughly wetted and then drained until the drainage rate has become negligibly small). After a prolonged dry spell, moisture is near the wilting point, and after a rainy period, soil has moisture content near its field capacity. Moisture contents at these limits have been studied by many agricultural researchers, and data for different types of soil are given by Kersten (1949) and Salomone and Marlowe (1989). Shaded areas in Figure 6 approximate (1) the full range of moisture contents for different soil types and (2) a range between average values of each limit.
Table 8 summarizes design values for thermal conductivities of the basic soil classes. Table 9 gives ranges of thermal conductivity for some basic classes of rock. The value chosen depends on whether heat transfer is calculated for minimum heat loss through the soil, as in a ground heat exchange system, or a maximum value, as in peak winter heat loss calculations for a basement. Hence, high and low values are given for each soil class.
When calculating annual energy use, choose values that represent typical mean site conditions. In climates where ground freezing is significant, accurate heat transfer simulations should include the effect of the latent heat of fusion of water. Energy released during this phase change significantly retards the progress of the frost front in moist soils.
For further information, see Chapter 17, which includes a method for estimating heat loss through foundations.
ASHRAE. 2010. Energy standard for buildings except low-rise residential buildings. ANSI/ASHRAE/IES Standard 90.1-2010.
ASTM. 2010. Standard terminology relating to thermal insulation. Standard C168-10. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2010. Standard test method for steady-state heat flux measurements and thermal transmission properties by means of the guarded-hot-plate apparatus. Standard C177-10. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2010. Standard test method for steady-state heat transfer properties of pipe insulation. Standard C335/C335M-10e1. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2010. Standard test method for steady-state thermal transmission properties by means of the heat flow meter apparatus. Standard C518-10. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2015. Standard practice for selection of water vapor retarders for thermal insulation. Standard C755-10 (R2015). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2005. Standard classification of potential health and safety concerns associated with thermal insulation materials and accessories. Standard C930-05. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2013. Standard practice for calculating thermal transmission properties under steady-state conditions. Standard C1045-07 (R2013). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2011. Standard test method for thermal performance of building materials and envelope assemblies by means of a hot box apparatus. Standard C1363-11. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2016. Standard specification for insulated vinyl siding. Standard D7793-16. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2010. Standard test methods for water vapor transmission of materials. Standard E96/E96M-10. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2009. Standard practices for air leakage site detection in building envelopes and air barrier systems. Standard E1186-03 (2009). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2011. Standard specification for air barrier (AB) material or system for low-rise framed building walls. Standard E1677-11. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2011. Standard test method for determining air leakage of air barrier assemblies. Standard E2357-11. American Society for Testing and Materials, West Conshohocken, PA.
CAN/ULC. 2003. Standard for determination of log-term thermal resistance of closed-cell thermal insulating foams. CAN/ULC Standard S770-2003. Standards Council of Canada, Ottawa, ON, and Underwriters Laboratories Canada, Toronto, ON.
VDI. 1999. Environmental meteorology—Interactions between atmosphere and surfaces—Calculation of short-wave and long-wave radiation. Standard 3789 Part 2. Verein Deutscher Ingenieure (Association of German Engineers), Dusseldorf.
ASHRAE members can access ASHRAE Journal articles and ASHRAE research project final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.
Adams, L. 1971. Supporting cryogenic equipment with wood. Chemical Engineering (May):156-158.
ASHRAE. 1998. Standard method for determining and expressing the heat transfer and total optical properties of fenestration products. SPC 142.
ASTM. 1985a. Guarded hot plate and heat flow meter methodology. Special Technical Publication STP 879. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 1985b. Building applications of heat flux transducers. Special Technical Publication STP 885. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 1988. Thermal insulation: Material and systems. Special Technical Publication STP 922. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 1990. Insulation materials: Testing and applications. Special Technical Publication STP 1030. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 1991. Insulation materials: Testing and applications, 2nd vol. Special Technical Publication STP 1116. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. Annual. Annual book of ASTM standards, vol. 04.06, Thermal insulation; building and environmental acoustics. American Society for Testing and Materials, West Conshohocken, PA.
Bassett, M.R., and H.A. Trethowen. 1984. Effect of condensation on emittance of reflective insulation. Journal of Thermal Insulation 8(October):127.
Binder, A., D. Zirkelbach, and H.M. Künzel. 2010. Test method to quantify the wicking properties of insulation materials designed to prevent interstitial condensation. Proceedings of Buildings XI Conference, ASHRAE.
Bomberg, M.T., and M.K. Kumaran. 1986. A test method to determine air flow resistance of exterior membranes and sheathings. Journal of Thermal Insulation 9:224-235.
Brandreth, D.A., ed. 1986. Advances in foam aging—A topic in energy conservation series. Caissa Editions, Yorklyn, DE.
Brown, W.C., M.T. Bomberg, J. Rasmussen, and J. Ullett. 1993. Measured thermal resistance of frame walls with defects in the installation of mineral fibre insulation. Journal of Thermal Insulation and Building Envelopes 16(April):318-339.
Burch, D.M., and A.O. Desjarlais. 1995. Water vapor measurements of low-slope roofing materials. Report NISTIR 5681. National Institute of Standards and Technology, Gaithersburg, MD.
Burch, D.M., W.C. Thomas, and A.H. Fanney. 1992. Water vapor permeability measurements of common building materials. ASHRAE Transactions 98(2).
CIBSE. 2006. Thermal properties of building structures. Chapter 3 in CIBSE Guide A: Environmental Design. The Chartered Institution of Building Services Engineers, London, U.K.
Construction Specifications Canada. 1990. Tek-AID on air barrier systems. Toronto.
Di Lenardo, B., W.C. Brown, W.A. Dalgleish, K. Kumaran, and G.F. Poirier. 1995. Technical guide for air barrier systems for exterior walls of low-rise buildings. Canadian Construction Materials Centre, National Research Council Canada, Ottawa, Ontario.
Donnelly, R.G., V.J. Tennery, D.L. McElroy, T.G. Godfrey, and J.O. Kolb. 1976. Industrial thermal insulation: An assessment. Oak Ridge National Laboratory Reports TM-5283, TM-5515, and TID-27120.
Glaser, P.E., I.A. Black, R.S. Lindstrom, F.E. Ruccia, and A.E. Wechsler. 1967. Thermal insulation systems—A survey. NASA Report SP5027.
Goss, W.P., and R.G. Miller. 1989. Literature review of measurement and prediction of reflective building insulation system performance: 1900-1989. ASHRAE Transactions 95(2).
Hedlin, C.P. 1985. Effect of insulation joints on heat loss through flat roofs. ASHRAE Transactions 91(2B):608-622.
Hooper, F.C., and W.J. Moroz. 1952. The impact of aging factors on the emissivity of reflective insulations. ASTM Bulletin (May):92-95.
ICC. 2007. 2007 supplement to the International Codes. International Code Council, Washington, D.C.
ISO. 2003. Thermal performance of windows, doors, and shading devices—Detailed calculations. Standard 15099. International Organization for Standardization, Geneva.
Karagiozis, A.N., and H.M. Salonvaara. 1999a. Hygrothermal performance of EIFS-clad walls: Effect of vapor diffusion and air leakage on the drying of construction moisture. Special Technical Publication STP 1352, pp. 32-51. American Society for Testing and Materials, West Conshohocken, PA.
Karagiozis, A.N., and H.M. Salonvaara. 1999b. Whole building hygrothermal performance: Proceedings of the 5th Symposium on Building Physics in the Nordic Countries, Goteborg, vol. 2, pp. 745-753. C.E. Hagentoft and P.I. Sandberg, eds.
Kersten, M.S. 1949. Thermal properties of soils. University of Minnesota, Engineering Experiment Station Bulletin 28 (June).
Korsgaard, V., and C.R. Pedersen. 1989. Transient moisture distribution in flat roofs with hygro diode vapor retarder. Proceedings of ASHRAE/DOE/BTECC/CIBSE Conference on Thermal Performance of Exterior Envelopes of Buildings IV.
Korsgaard, V., and C.R. Pedersen. 1992. Laboratory and practical experience with a novel water-permeable vapor retarder. Proceedings of ASHRAE/DOE/BTECC/CIBSE Conference on Thermal Performance of Exterior Envelopes of Buildings V, pp. 480-490.
Kuenzel, H.M. 1999. More moisture load tolerance of construction assemblies through the application of a smart vapor retarder. Proceedings of Thermal Performance of the Exterior Envelopes of Buildings VII, pp. 129-132. ASHRAE.
Kumaran, M.K. 1989. Experimental investigation on simultaneous heat and moisture transport through thermal insulation. Proceedings of the Conseil International du Batiment/International Building Council (CIB) 11th International Conference 2:275-284.
Kumaran, M.K. 1996. Heat, air and moisture transport. Final Report, vol. 3, task 3: Material properties. International Energy Agency Annex 24.
Kumaran, M.K. 2002. A thermal and moisture transport database for common building and insulating materials. ASHRAE Research Project RP-1018, Final Report. National Research Council, Canada.
Lander, R.M. 1955. Gas is an important factor in the thermal conductivity of most insulating materials. ASHRAE Transactions 61:151.
Lecompte, J. 1989. The influence of natural convection in an insulated cavity on the thermal performance of the wall. Special Technical Publication STP 1000:397-420. American Society for Testing and Materials, West Conshohocken, PA.
Lewis, W.C. 1967. Thermal conductivity of wood-base fiber and particle panel materials. Forest Products Laboratory, Research Paper FPL 77, June.
Lewis, J.E. 1979. Thermal evaluation of the effects of gaps between adjacent roof insulation panels. Journal of Thermal Insulation (October):80-103.
Lotz, W.A. 1964. Vapor barrier design, neglected key to freezer insulation effectiveness. Quick Frozen Foods (November):122.
Lotz, W.A. 1969. Facts about thermal insulation. ASHRAE Journal (June): 83-84.
MacLean, J.D. 1941. Thermal conductivity of wood. ASHVE Transactions 47:323.
McGowan, A.G. 2007. Catalog of material thermal property data (RP-905). ASHRAE Research Project, Final Report.
NIST. 2000. NIST standard reference database 81: NIST heat transmission properties of insulating and building materials. U.S. Department of Commerce, National Institute of Standards and Materials, Gaithersburg, MD. srdata.nist.gov/insulation/.
Nottage, H.B. 1947. Thermal properties of building materials used in heat flow calculations. ASHVE Transactions 53:215-243.
Ojanen, T., R. Kohonen, and M.K Kumaran. 1994. Modeling heat, air, and moisture transport through building materials and components. Chapter 2 in Manual MNL 18, Moisture control in buildings. American Society for Testing and Materials, West Conshohocken, PA.
Ostrogorsky, A.G., and L.R. Glicksman. 1986. Laboratory tests of effectiveness of diffusion barriers. Journal of Cellular Plastics 22:303.
Pelanne, C.M. 1979. Thermal insulation heat flow measurements: Requirements for implementation. ASHRAE Journal 21(3):51.
Rasmussen J., W.C. Brown, M. Bomberg, and J.M. Ullett. 1993. Measured thermal performance of frame walls with defects in the installation of mineral fibre insulation. Proceedings of the 3rd Symposium on Building Physics in the Nordic Countries, pp. 209-217.
Robinson, H.E., F.J. Powlitch, and R.S. Dill. 1954. The thermal insulation value of airspaces. Housing Research Paper 32, Housing and Home Finance Agency.
Robinson, H.E., F.J. Powell, and L.A. Cosgrove. 1957. Thermal resistance of airspaces and fibrous insulations bounded by reflective surfaces. National Bureau of Standards, Building Materials and Structures Report BMS 151.
Rowley, F.B., and A.B. Algren. 1937. Thermal conductivity of building materials. University of Minnesota Bulletin #12, Minneapolis.
Rowley, F.B., R.C. Jordan, C.E. Lund, and R.M. Lander. 1952. Gas is an important factor in the thermal conductivity of most insulating materials. ASHVE Transactions 58:155.
Sabine, H.J., M.B. Lacher, D.R. Flynn, and T.L. Quindry. 1975. Acoustical and thermal performance of exterior residential walls, doors and windows. NBS Building Science Series 77. National Institute of Standards and Technology, Gaithersburg, MD.
Salomone, L.A., and J.I. Marlowe. 1989. Soil and rock classification according to thermal conductivity: Design of ground-coupled heat pump systems. EPRI CU-6482. Electric Power Research Institute, Palo Alto, CA.
Seiffert, K. 1970. Damp diffusion and buildings. Elsevier, Amsterdam, the Netherlands.
Shu, L.S., A.E. Fiorato, and J.W. Howanski. 1979. Heat transmission coefficients of concrete block walls with core insulation. Proceedings of the ASHRAE/DOE-ORNL Conference on Thermal Performance of the Exterior Envelopes of Buildings, ASHRAE SP 28, pp. 421-435.
Simons, E. 1955. In-place studies of insulated structures. Refrigerating Engineering 63:40, 128.
Touloukian, Y.S., R.W. Powell, C.Y. Ho, and I.G. Clemens. 1970. Thermophysical properties of matter. Thermal conductivity data tables of nonmetallic solids. IFI/Plenum, New York.
Tye, R.P. 1985. Upgrading thermal insulation performance of industrial processes. Chemical Engineering Progress (February):30-34.
Tye, R.P. 1986. Effects of product variability on thermal performance of thermal insulation. Proceedings of the First Asian Thermal Properties Conference, Beijing, People’s Republic of China.
Tye, R.P. 1988. Aging of cellular plastics: A comprehensive bibliography. Journal of Thermal Insulation 11:196-222.
Tye, R.P., and A.O. Desjarlais. 1981. Performance characteristics of foam-in-place urea formaldehyde insulation. ORNL/Sub-78/86993/1. Oak Ridge National Laboratory, Oak Ridge, TN.
Tye, R.P., and A.O. Desjarlais. 1983. Factors influencing the thermal performance of thermal insulations for industrial applications. In Thermal insulation, materials, and systems for energy conservation in the ’80s, F.A. Govan, D.M. Greason, and J.D. McAllister, eds. ASTM STP 789:733-748.
Valore, R.C., 1988. Thermophysical properties of masonry and its constituents, parts I and II. International Masonry Institute, Washington, D.C.
Van Geem, M.G. 1985. Thermal transmittance of concrete block walls with core insulation. ASHRAE Transactions 91(2).
Verschoor, J.D. 1977. Effectiveness of building insulation applications. USN/CEL Report CR78.006—NTIS AD-AO53 452/9ST.
Verschoor, J.D., and P. Greebler. 1952. Heat transfer by gas conductivity and radiation in fibrous insulations. ASME Transactions 74(6):961-968.
Wilkes, K.E. 1979. Thermophysical properties data base activities at Owens-Corning Fiberglas. Proceedings of the ASHRAE/DOE-ORNL Conference on Thermal Performance of the Exterior Envelopes of Buildings, ASHRAE SP 28, pp. 662-677.
Wilkes, K.E., and P.W. Childs. 1992. Thermal performance of fiberglass and cellulose attic insulations. Proceedings of the ASHRAE/DOE/BTECC/CIBSE Conference on Thermal Performance of the Exterior Envelopes of Buildings V, pp. 357-367.
Wilkes, K.E., and J.L. Rucker. 1983. Thermal performance of residential attic insulation. Energy and Buildings 5:263-277.
Yarbrough, D.W. 1983. Assessment of reflective insulations for residential and commercial applications. ORNL/TM-8891. Oak Ridge National Laboratory, Oak Ridge, TN.
Zhao, J., J. Grunewald, U. Ruisinger, and S. Feng. 2017. Evaluation of capillary-active mineral insulation systems for interior retrofit solution. Building and Environment 115:215-227. dx.doi.org/10.1016/j.buildenv.2017.01.004.