CHAPTER 21. DUCT DESIGN

 

Commercial, industrial, and residential air duct system design must consider (1) space availability, (2) noise levels, (3) air leakage, (4) balancing, (5) fire and smoke control, (6) initial investment cost, and (7) system operating cost.

Deficiencies in duct design can result in systems that operate incorrectly or are expensive (increased energy) to own and operate. Poor design or lack of system sealing can produce inadequate airflow rates at the terminals, leading to discomfort, loss of productivity, and even adverse health effects. Lack of sound attenuation may lead to objectionable noise levels. Proper duct insulation eliminates excessive heat gain or loss.

In this chapter, system design and calculation of a system’s frictional and dynamic resistance (total pressure) to airflow are considered. Chapter 19 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment examines duct construction and presents construction standards for residential, commercial, and industrial HVAC and exhaust systems. For design guidance specific to residential systems, refer to Manual D by ACCA (2014).

1. BERNOULLI EQUATION

The Bernoulli equation can be developed by equating the forces on an element of a stream tube in a frictionless fluid flow to the rate of momentum change. On integrating this relationship for steady flow, the following expression (Osborne 1966) results:

(1)

where

v = streamline (local) velocity, m/s
p = absolute pressure, Pa (N/m2)
ρ = density, kg/m3
g = acceleration caused by gravity, m/s2
z = elevation, m

Assuming constant fluid density in the system, Equation (1) reduces to

(2)

Although Equation (2) was derived for steady, ideal frictionless flow along a stream tube, it can be extended to analyze flow through ducts in real systems. In terms of pressure, the relationship for fluid resistance between two sections is

(3)

where

V = average duct velocity, m/s
Δpt,1–2 = total pressure loss caused by friction and dynamic losses between sections 1 and 2, Pa

In Equation (3), V (section average velocity) replaces v (streamline velocity) because experimentally determined loss coefficients allow for errors in calculatingv2/2 (velocity pressure) across streamlines.

On the left side of Equation (3), add and subtract pz1; on the right side, add and subtract pz2, where pz1 and pz2 are the values of atmospheric air at heights z1 and z2. Thus,

(4)

Atmospheric pressure at any elevation (pz1 and pz2) expressed in terms of the atmospheric pressure pa at the same datum elevation is given by

(5)

(6)

Substituting Equations (5) and (6) into Equation (4) and simplifying yields the total pressure change between sections 1 and 2. Assume no temperature change between sections 1 and 2 (no heat exchanger within the section); therefore, ρ1 = ρ2. When a heat exchanger is located in the section, the average of the inlet and outlet temperatures is generally used. Let ρ = ρ1 = ρ2, and (p1 – pz1) and (p2 – pz2) are gage pressures at elevations z1 and z2.

(7a)

(7b)

Rearranging Equation (7b) yields

(7c)

where

ps, 1 = static pressure, gage at elevation z1, Pa
ps, 2 = static pressure, gage at elevation z2, Pa
V1 = average velocity at section 1, m/s
V2 = average velocity at section 2, m/s
ρa = density of ambient air, kg/m3
ρ = density of air or gas in duct, kg/m3
Δpse = thermal gravity effect, Pa
Δpt = total pressure change between sections 1 and 2, Pa
Δpt,1–2 = total pressure loss caused by friction and dynamic losses between sections 1 and 2, Pa

1.1  HEAD AND PRESSURE

The terms head and pressure are often used interchangeably; however, head is the height of a fluid column supported by fluid flow, whereas pressure is the normal force per unit area. For liquids, it is convenient to measure head in terms of the flowing fluid. With a gas or air, however, it is customary to measure pressure exerted by the gas on a column of liquid.

 Static Pressure

The term p/ρg is static head; p is static pressure.

 Velocity Pressure

The term V2/2g refers to velocity head, and ρV2/2gc refers to velocity pressure. Although velocity head is independent of fluid density, velocity pressure [Equation (8)] is not.

(8)

where

pv = velocity pressure, Pa
V = fluid mean velocity, m/s

For air at standard conditions (1.204 kg/m3), Equation (8) becomes

(9)

Velocity is calculated by

(10)

where

Q = airflow rate, L/s
A = cross-sectional area of duct, m2

 Total Pressure

Total pressure is the sum of static pressure and velocity pressure:

(11)

or

(12)

where

pt = total pressure, Pa
ps = static pressure, Pa

 Pressure Measurement

The range, precision, and limitations of instruments for measuring pressure and velocity are discussed in Chapter 36. The manometer is a simple and useful means for measuring partial vacuum and low pressure. Static, velocity, and total pressures in a duct system relative to ambient space pressure can be measured with a pitot tube connected to a manometer. Pitot tube construction and locations for traversing round and rectangular ducts are presented in Chapter 37.

2. SYSTEM ANALYSIS

The total pressure change caused by friction, fittings, equipment, and net thermal gravity effect for each section of a duct system is calculated by the following equation:

(13)

where

Δpti = net total pressure change for i sections, Pa
Δpfi = pressure loss caused by friction for i sections, Pa
Δpij = total pressure loss caused by j fittings, including fan system effect (FSE), for i sections, Pa
Δpik = pressure loss caused by k equipment for i sections, Pa
Δpseir = thermal gravity effect caused by r stacks for i sections, Pa
m = number of fittings within i sections
n = number of equipment within i sections
λ = number of stacks within i sections
nup = number of duct sections upstream of fan (exhaust/return air subsystems)
ndn = number of duct sections downstream of fan (supply air subsystems)

From Equation (7), the thermal gravity effect for each nonhorizontal duct with a density other than that of ambient air is determined by the following equation:

(14)

where

Δpse = thermal gravity effect, Pa
z1 and z2 = elevation from datum in direction of airflow (Figure 1), m
ρa = density of ambient air, kg/m3
ρ = density of air or gas within duct, kg/m3
g = 9.81 = gravitational acceleration, m/s2

Example 1.

For Figure 1, calculate the thermal gravity effect for two cases: (a) air cooled to −34°C, and (b) air heated to 540°C. Density of air at −34°C is 1.477 kg/m3 and at 540°C is 0.434 kg/m3. Density of ambient air is 1.204 kg/m3. Stack height is 15 m.

Solution:

(a) For ρ > ρa (Figure 1A),

(b) For ρ < ρa (Figure 1B),


Example 2.

Calculate the thermal gravity effect for the two-stack system shown in Figure 2, where the air is 120°C and stack heights are 15 and 30 m. Density of 120°C air is 0.898 kg/m3; ambient air is 1.204 kg/m3.

Solution:


For the system shown in Figure 3, the direction of air movement created by the thermal gravity effect depends on the initiating force (e.g., fans, wind, opening and closing doors, turning equipment on and off). If for any reason air starts to enter the left stack (Figure 3A), it creates a buoyancy effect in the right stack. On the other hand, if flow starts to enter the right stack (Figure 3B), it creates a buoyancy effect in the left stack. In both cases, the produced thermal gravity effect is stable and depends on stack height and magnitude of heating. The starting direction of flow is important when using natural convection for ventilation.

To determine the fan total pressure requirement for a system, use the following equation:

(15)

where

Fup and Fdn = sets of duct sections upstream and downstream of fan
Pt = fan total pressure, Pa
ε = symbol that ties duct sections into system paths from exhaust/return air terminals to supply terminals

Figure 4 shows the use of Equation (15). This system has three supply and two return terminals consisting of nine sections connected in six paths: 1-3-4-9-7-5, 1-3-4-9-7-6, 1-3-4-9-8, 2-4-9-7-5, 2-4-9-7-6, and 2-4-9-8. Sections 1 and 3 are unequal area; thus, they are assigned separate numbers in accordance with the rules for identifying sections (see step 5 in the section on HVAC Duct Design Procedures). To determine the fan pressure requirement, apply the following six equations, derived from Equation (15). These equations must be satisfied to attain pressure balancing for design airflow. Relying entirely on dampers is not economical and may create objectionable flow-generated noise.

(16)

Thermal Gravity Effect for Example 1

Figure 1. Thermal Gravity Effect for Example 1


Multiple Stacks for Example 2

Figure 2. Multiple Stacks for Example 2


Example 3.

For Figures 5A and 5C, calculate the thermal gravity effect and fan total pressure required when the air is cooled to −34°C. The heat exchanger and ductwork (section 1 to 2) total pressure losses are 170 and 70 Pa respectively. The density of −34°C air is 1.477 kg/m3; ambient air is 1.204 kg/m3. Elevations are 21 and 3 m.

Solution:

(a) For Figure 5A (downward flow),

(b) For Figure 5C (upward flow),


Multiple Stack Analysis

Figure 3. Multiple Stack Analysis


Illustrative 6-Path, 9-Section System

Figure 4. Illustrative 6-Path, 9-Section System


Single Stack with Fan for Examples 3 and 4

Figure 5. Single Stack with Fan for Examples 3 and 4


Example 4.

For Figures 5B and 5D, calculate the thermal gravity effect and fan total pressure required when air is heated to 120°C. Heat exchanger and ductwork (section 1 to 2) total pressure losses are 170 and 70 Pa, respectively. Density of 120°C air is 0.898 kg/m3; ambient air is 1.204 kg/m3. Elevations are 21 and 3 m.

Solution:

(a) For Figure 5B (downward flow),

(b) For Figure 5D (upward flow),

Example 5.

Calculate the thermal gravity effect for each section of the system shown in Figure 6 and the systems’ net thermal gravity effect. Density of ambient air is 1.204 kg/m3, and the lengths are as follows: z1 = 15 m, z2 = 27 m, z4 = 30 m, z5 = 8 m, and z9 = 60 m. Pressure required at section 3 is −25 Pa. Write the equation to determine the fan total pressure requirement.

Solution: The following table summarizes the thermal gravity effect for each section of the system as calculated by Equation (14). The net thermal gravity effect for the system is 118 Pa. To select a fan, use the following equation:

Triple Stack System for Example 5

Figure 6. Triple Stack System for Example 5


Pressure Changes During Flow in Ducts

Figure 7. Pressure Changes During Flow in Ducts


Path (x–x′)

Temp., °C

ρ, kg/m3

Δz (zx′ – zx), m

Δρ (ρa – ρx–x′), kg/m3

Δpse, Pa [Eq. (14)]

1–2

815

0.324

(27 – 15)

+0.880

+104

3–4

540

0.434

0

+0.770

0

4–5

540

0.434

(8 – 30)

+0.770

−166

6–7

120

0.898

0

+0.306

0

8–9

120

0.898

(60 – 0)

+0.306

+180

Net Thermal Gravity Effect

118


2.1 PRESSURE CHANGES IN SYSTEM

Figure 7 shows total and static pressure changes in a fan/duct system consisting of a fan with both supply and return air ductwork. Also shown are total and static pressure gradients referenced to atmospheric pressure.

For all constant-area sections, total and static pressure losses are equal. At diverging transitions, velocity pressure decreases, absolute total pressure decreases, and absolute static pressure can increase. The static pressure increase at these sections is known as static regain.

At converging transitions, velocity pressure increases in the direction of airflow, and absolute total and absolute static pressures decrease.

At the exit, total pressure loss depends on the shape of the fitting and the flow characteristics. Exit loss coefficients Co can be greater than, less than, or equal to one. Total and static pressure grade lines for the various coefficients are shown in Figure 7. Note that, for a loss coefficient less than one, static pressure upstream of the exit is less than atmospheric pressure (negative). Static pressure just upstream of the discharge fitting can be calculated by subtracting the upstream velocity pressure from the upstream total pressure.

At section 1, total pressure loss depends on the shape of the entry. Total pressure immediately downstream of the entrance equals the difference between the upstream pressure, which is zero (atmospheric pressure), and loss through the fitting. Static pressure of ambient air is zero; several diameters downstream, static pressure is negative, equal to the sum of the total pressure (negative) and the velocity pressure (always positive).

System resistance to airflow is noted by the total pressure grade line in Figure 7. Sections 3 and 4 include fan system effect pressure losses. To obtain the fan static pressure requirement for fan selection where fan total pressure is known, use

(17)

where

Ps = fan static pressure, Pa
Pt = fan total pressure, Pa
pv,o = fan outlet velocity pressure, Pa

3. FLUID RESISTANCE

Duct system losses are the irreversible transformation of mechanical energy into heat. The two types of losses are (1) friction and (2) dynamic.

3.1 FRICTION LOSSES

Friction losses are caused by fluid viscosity and result from momentum exchange between molecules (in laminar flow) or between individual particles of adjacent fluid layers moving at different velocities (in turbulent flow). Friction losses occur along the entire duct length.

 Darcy and Colebrook Equations

For fluid flow in conduits, friction loss can be calculated by the Darcy equation:

(18)

where

Δpf = friction losses in terms of total pressure, Pa
f = friction factor, dimensionless
L = duct length, m
Dh = hydraulic diameter [Equation (24)], mm
V = velocity, m/s
ρ = density, kg/m3

In the region of laminar flow (Reynolds numbers less than 2300), the friction factor is a function of Reynolds number only. For completely turbulent flow (fully rough), the friction factor depends on duct surface roughness and internal protuberances (e.g., joints). Between the bounding limits of hydraulically smooth behavior (laminar flow) and fully rough behavior is a transitional zone where the friction factor depends on both roughness and Reynolds number. In both the transitional and fully rough (see Moody diagram: Figure 13 in Chapter 3) regions, the friction factor f is calculated by Colebrook’s equation (Colebrook 1938–1939). Because Colebrook’s equation cannot be solved explicitly for f, use iterative techniques (Behls 1971).

(19)

where

ε = material absolute roughness factor, mm
Re = Reynolds number

Reynolds number (Re) may be calculated by using the following equation.

(20)

where ν = kinematic viscosity, m2/s.

For standard air and temperature between 4 and 38°C, Re can be calculated by

(21)

 Roughness Factors

Roughness factors listed in Table 1, column 3, are recommended for use with Equation (19). For increased calculation accuracy, use an absolute roughness factor from column 2.

Pressure Loss Correction Factor for Flexible Duct Not Fully Extended

Figure 8. Pressure Loss Correction Factor for Flexible Duct Not Fully Extended


Flexible Duct. For fully stretched and compressed flexible duct, use Equation (22) or Figure 8 (Abushakra et al. 2004; Culp 2011), where the multiplier PDCF is based on flexible duct with an absolute roughness ε = 0.9 mm. The resistance of flexible duct can be calculated using Fitting CD11-2 in the ASHRAE Duct Fitting Database (ASHRAE 2016). Flexible duct should be installed fully extended; its resistance when fully extended is increased approximately 50%. See Example 6 for the increase in resistance of flexible duct fully stretched and compressed relative to rigid spiral duct.

For commercial systems, flexible ducts should be

  • Limited to connections of rigid ducts to diffusers. For diffuser installation suggestions, see Figure 9. The purpose of limiting the offset to D/8 in Figure 9B is to minimize noise generation. Flexible duct should not be installed upstream of variable-air-volume (VAV) boxes.

    Commentary: The loss coefficient or pressure loss for flexible duct elbows, such as those in Figure 9A, can be obtained from the ASHRAE Duct Fitting Database (ASHRAE 2016), Fitting CD3-22 (r/D = 1.0) or CD3-23 (r/D = 1.5). Loss coefficients are for fully stretched elbows.

  • Limited to 2 m maximum, fully stretched.

  • Installed without any radial compression.

Example 6.

Compare the total pressure resistance of 250 mm, 1.8 m installed length, galvanized steel spiral and flexible duct, 0% compressed (fully stretched), 4%, 15%, and 30% compressed. Airflow is 470 L/s, air density is 1.204 kg/m3, and absolute roughnesses ε of spiral round and flexible ducts are 0.12 mm and 0.9 mm. Calculate using the ASHRAE Duct Fitting Database [DFDB; ASHRAE (2016)].

Solution: See Table 2 for results.

(22)

with

(23)

where

PDCF = pressure drop correction factor
Kc = flexible duct compressed, percent
D = flexible duct diameter, mm
L = installed duct length, m
LFE = duct length fully extended, m


Table 1 Duct Roughness Factors

1

2

3

Duct Type/Material

Absolute Roughness ε, mm

Range

Roughness Category

Drawn tubing (Madison and Elliot 1946)

0.00046

Smooth 0.00046

PVC plastic pipe (Swim 1982)

0.009 to 0.046

Medium smooth 0.046

Commercial steel or wrought iron (Moody 1944)

0.046

 

Aluminum, round, longitudinal seams, crimped slip joints, 0.91 m spacing (Hutchinson 1953)

0.037 to 0.061

 

Friction chart:

Galvanized steel, round, longitudinal seams, variable joints (Vanstone, drawband, welded. Primarily beaded coupling), 1.22 m joint spacing (Griggs et al. 1987)

0.049 to 0.098

Average 0.09

Galvanized steel, spiral seams, 3.05 m joint spacing (Jones 1979)

0.061 to 0.12

 

Galvanized steel, spiral seam with 1, 2, and 3 ribs, beaded couplings, 3.66 m joint spacing (Griggs et al. 1987)

0.088 to 0.116

 

Galvanized steel, rectangular, various type joints (Vanstone, drawband, welded. Beaded coupling), 1.22 m spacinga (Griggs and Khodabakhsh-Sharifabad 1992)

0.082 to 0.15

 

Wright Friction Chart:

Galvanized steel, round, longitudinal seams, 0.76 m joint spacing, ε = 0.15 mm

Retained for historical purposes [See Wright (1945) for development of friction chart]

Flexible duct, nonmetallic and wire, fully extended (Abushakra et al. 2004; Culp 2011)

0.09 to 0.9

Medium rough 0.9

Galvanized steel, spiral, corrugated,b Beaded slip couplings, 3.05 m spacing (Kulkarni et al. 2009)

0.54 to 0.91

 

Fibrous glass duct, rigid (tentative)c

—

 

Fibrous glass duct liner, air side with facing material (Swim 1978)

1.52

 

Fibrous glass duct liner, air side spray coated (Swim 1978)

4.57

Rough 3.0

Flexible duct, metallic corrugated, fully extended

1.2 to 2.1

 

Concrete (Moody 1944)

0.30 to 3.0

 

a Griggs and Khodabakhsh-Sharifabad (1992) showed that ε values for rectangular duct construction combine effects of surface condition, joint spacing, joint type, and duct construction (cross breaks, etc.), and that the ε-value range listed is representative.

b Spiral seam spacing was 119 mm with two corrugations between seams. Corrugations were 19 mm wide by 6 mm high (semicircle).

c Subject duct classified “tentatively medium rough” because no data available.


Table 2 Solution for Example 6

Duct

DFDB Fitting

ε, mm

Airflow, L/s

Diameter, mm

Velocity, m/s

Compression, %

PDCF*

Δpt, Pa

% Δpt Increased

Flexible

CD11-2

0.9

470

250

9.6

(fully stretched)

1.0

11.4

48

Flexible

CD11-2

0.9

470

250

9.6

4

1.7

19.5

153

Flexible

CD11-2

0.9

470

250

9.6

15

3.5

40.0

419

Flexible

CD11-2

0.9

470

250

9.6

30

5.9

68.9

795

Galvanized steel, spiral

CD11-1

0.12

470

250

9.6

NA

NA

7.7

Base


Diffuser Installation Suggestions

Figure 9. Diffuser Installation Suggestions


 Friction Chart

The friction chart (Figure 10) is a plot of the Darcy and Colebrook equations [Equations (18) and (19), respectively), where the absolute roughness is 0.09 mm and the air is standard air (density = 1.204 kg/m3)]. Figure 10 can be used for (1) duct construction/materials categorized as “average” in Table 1, (2) temperature variations of ±15 K from 20°C, (3) elevations to 500 m, and (4) duct pressures from –5 to +5 kPa relative to ambient pressure. These individual variations in temperature, elevation, and duct pressure result in duct losses within ±5% of the standard air friction chart.

The friction chart was changed in 1985 from an absolute roughness of 0.15 mm to 0.09 mm based on research by Griggs et al. (1987), who found that the roughness factor is affected by the material surface, joint spacing, and type of joint. The Wright friction chart appeared in the Handbook from 1946 to 1981. This chart was based on an absolute roughness ε = 0.15 mm, primarily because of the 760 mm joint spacing. In 1985 the friction chart was changed to ε = 0.09 mm because joint spacing was increasing. For the relative effect of straight duct resistance between charts, see Figure 11. For a 250 mm diameter duct at 10 m/s (491 L/s), the resistance decreased 5 to 6%.

 Noncircular Ducts

A momentum analysis can relate average wall shear stress to pressure drop per unit length for fully developed turbulent flow in a passage of arbitrary shape but uniform longitudinal cross-sectional area. This analysis leads to the definition of hydraulic diameter:

(24)

where

Dh = hydraulic diameter, mm
A = duct area, mm2
P = perimeter of cross section, mm

Although hydraulic diameter is often used to correlate noncircular data, exact solutions for laminar flow in noncircular passages show that this causes some inconsistencies. No exact solutions exist for turbulent flow. Tests over a limited range of turbulent flow indicated that fluid resistance is the same for equal lengths of duct for equal mean velocities of flow if the ducts have the same ratio of cross-sectional area to perimeter. From experiments using round, square, and rectangular ducts having essentially the same hydraulic diameter, Huebscher (1948) found that each, for most purposes, had the same flow resistance at equal mean velocities. Tests by Griggs and Khodabakhsh-Sharifabad (1992) also indicated that experimental rectangular duct data for airflow over the range typical of HVAC systems can be correlated satisfactorily using Equation (19) together with hydraulic diameter, particularly when a realistic experimental uncertainty is accepted. These tests support using hydraulic diameter to correlate noncircular duct data.

Rectangular Ducts. Huebscher (1948) developed the relationship between rectangular and round ducts that is used to determine size equivalency based on equal flow, resistance, and length. This relationship, Equation (25), is the basis for Table 3.

(25)

where

De = circular equivalent of rectangular duct for equal length, fluid resistance, and airflow, mm
a = length one side of duct, mm
b = length adjacent side of duct, mm

To determine equivalent round duct diameter, use Table 3. Equations (18) and (19) must be used to determine pressure loss.

Flat Oval Ducts. To convert round ducts to flat oval sizes, use Table 4, which is based on Equation (26) (Heyt and Diaz 1975), the circular equivalent of a flat oval duct for equal airflow, resistance, and length. Equations (18) and (19) must be used to determine friction loss.

(26)

where AR is the cross-sectional area of flat oval duct defined as

(27)

and the perimeter P is calculated by

(28)

where

P = perimeter of flat oval duct, mm
A = major axis of flat oval duct, mm
a = minor axis of flat oval duct, mm

3.2 DYNAMIC LOSSES

Dynamic losses result from flow disturbances caused by duct-mounted equipment and fittings that change flow direction (elbows), area changes (transitions), and converging/diverging junctions. For a detailed discussion of hydraulic networks, consult Idelchik et al. (1994).

 Local Loss Coefficients

The dimensionless coefficient C is used for fluid resistance because this coefficient has the same value in dynamically similar streams (i.e., streams with geometrically similar stretches, equal Reynolds numbers, and equal values of other criteria necessary for dynamic similarity). The fluid resistance coefficient represents the ratio of total pressure loss to velocity pressure at the referenced cross section:

(29)

where

C = local loss coefficient, dimensionless
Δpt = total pressure loss, Pa
ρ = density, kg/m3
V = velocity, m/s
pv = velocity pressure, Pa

For all fittings, except junctions, total pressure loss is calculated by Equation (30):

(30)

where

Δpt = total pressure loss of fitting, Pa
Co = local loss coefficient of fitting, dimensionless
pv,o = velocity pressure at section o of fitting, Pa

Dynamic loss is based on the actual velocity in the duct, not the velocity in an equivalent circular duct. For the cross section to reference a fitting loss coefficient, see step 5 in the section on HVAC Duct Design Procedures. Where necessary (e.g., unequal-area fittings), convert a loss coefficient from section o to section 1 using Equation (31), where V is the velocity at the respective sections.

(31)

Friction Chart for Round Duct (ρ = 1.20 kg/m3 and ε = 0.0003 ft)

Figure 10. Friction Chart for Round Duct (ρ = 1.20 kg/m3 and ε = 0.0003 ft)


Table 3  Circular Equivalents of Rectangular Duct for Equal Friction and Airflow*

Side Lengths, mm

Length of One Side of Rectangular Duct a, mm

100

150

200

250

300

400

500

600

800

1 000

1 200

Circular Duct Diameter, mm

200

152

189

219

               

250

169

210

244

273

             

300

183

229

266

299

328

           

400

207

260

305

343

378

437

         

500

 

287

337

381

420

488

547

       

600

 

310

365

414

457

533

598

656

     

800

   

414

470

520

609

687

755

875

   

1 000

     

517

574

674

762

840

976

1 093

 

1 200

       

620

731

827

914

1 066

1 196

1 312

1 400

         

781

886

980

1 146

1 289

1 416

1 600

         

827

939

1 041

1 219

1 373

1 511

1 800

           

988

1 096

1 286

1 451

1 598

2 000

           

1 034

1 147

1 348

1 523

1 680

* Table based on Equation (25).


Table 4 Equivalent Flat Oval Duct Dimensions*

Circular Duct Diameter, mm

Minor Axis a, mm

70

100

125

150

175

200

250

275

300

325

350

375

400

450

500

550

600

Major Axis A, mm

125

205

                               

140

265

180

                             

160

360

235

190

                           

180

475

300

235

200

                         

200

 

380

290

245

215

                       

224

 

490

375

305

—

240

                     

250

   

475

385

325

290

                     

280

     

485

410

360

—

285

                 

315

     

635

525

—

—

345

325

               

355

     

840

—

580

460

425

395

375

             

400

     

1 115

—

760

—

530

490

460

435

           

450

     

1 490

—

995

—

675

—

570

535

505

         

500

         

1 275

—

845

—

700

655

615

580

       

560

         

1 680

—

1 085

—

890

820

765

720

       

630

             

1 425

—

1 150

1 050

970

905

810

     

710

                 

1 505

1 370

1 260

1 165

1 025

     

800

                   

1 800

1 645

1 515

1 315

1 170

1 065

 

900

                     

2 165

1 985

1 705

1 500

1 350

 

1 000

                         

2 170

1 895

1 690

 

1 120

                           

2 455

2 170

1 950

1 250

                             

2 795

2 495

* Table based on Equation (26).


Plot Illustrating Relative Resistance of Roughness Categories

Figure 11. Plot Illustrating Relative Resistance of Roughness Categories


For converging and diverging flow junctions, total pressure loss through the straight (main) section is calculated by

(32)

where

Δpt,s = total pressure loss across straight-through section s of junction, Pa
Cs = local loss coefficient referenced to s section of junction, dimensionless
pv,s = velocity pressure at section s, Pa

For total pressure loss through the branch section,

(33)

where

Δpt,b = total pressure loss across branch b section of junction, Pa
Cb = local loss coefficient referenced to b section of junction, dimensionless
pv,b = velocity pressure at section b, Pa

The junction of two parallel streams moving at different velocities is characterized by turbulent mixing of the streams, accompanied by pressure losses. In the course of this mixing, particles moving at different velocities exchange momentum, resulting in equalization of the velocity distributions in the common stream. The jet with higher velocity loses part of its kinetic energy by transmitting it to the slower jet. The loss in total pressure before and after mixing is always large and positive for the higher-velocity jet, and increases with an increase in the amount of energy transmitted to the lower-velocity jet. Consequently, the local loss coefficient [Equation (29)] is always positive. Energy stored in the lower-velocity jet can increase because of mixing. The loss in total pressure and the local loss coefficient can, therefore, also have negative values for the lower-velocity jet (Idelchik et al. 1994).

 Duct Fitting Database

Loss coefficients for more than 220 round, flat oval, and rectangular fittings are available in the ASHRAE Duct Fitting Database [DFDB; ASHRAE (2016)]. Also included are the pressure loss for round duct (CD11-1), flexible duct (CD11-2), rectangular duct (CR11-1), and flat oval (CF11-1) duct, as well as the following design tools:

  • CD11-3, Straight Duct, Round, Velocity Limited

  • CD11-4, Straight Duct, Round, Friction Rate Constant

  • CD11-5, Straight Duct, Round, Minimum Velocity

Table 5 Duct Fitting Codes

Fitting Function

Geometry

Category

Sequential Number

S: Supply

D: round (Diameter)

1. Entries

1, 2, 3... n

   

2. Exits

 

E: Exhaust/Return

R: Rectangular

3. Elbows

 
   

4. Transitions

 

C: Common (supply and return)

F: Flat oval

5. Junctions

 
 

6. Obstructions

 
 

7. Fan and system interactions

 
   

8. Duct-mounted equipment

 
   

9. Dampers

 
   

10. Hoods

 
   

11. Straight duct

 


Table 6 200 mm VAV Box Data

Airflow, L/s

Δps, Pa

Inlet Velocity, m/s

Outlet Velocity, m/s

pv, in, Pa

pv, out, Pa

Δpv, Pa

Δpt, Pa

1

2

3

4

5

6

7

8

165

13.2

5.1

2.1

15.6

2.7

12.9

26.1

236

27.1

7.3

3.0

31.9

5.6

26.3

53.4

330

53.0

10.2

4.3

62.5

11.0

51.5

104.5

425

87.8

13.1

5.5

103.3

18.1

85.1

173.0

Δps = static pressure difference

Δpt = total pressure difference at standard air conditions

pv, in = inlet velocity pressure at standard air conditions

pv, out = outlet velocity pressure at standard air conditions

Δpv = velocity pressure difference at standard air conditions


Commentary: CD11-3 determines the size of a duct knowing airflow such that the design velocity is not exceeded. CD11-4 is for sizing duct systems by the equal friction method, knowing the design (target) friction rate and airflow. CD4-11 determines the duct size for industrial systems that must maintain a minimum velocity to convey particulates.

Example 8 uses CD11-3 in the equal friction and static regain designs, and CD11-4 for the equal friction design.

The fittings are numbered (coded) as shown in Table 5. Entries and converging junctions are only in the exhaust/return portion of systems. Exits and diverging junctions are only in supply systems. Equal-area elbows, obstructions, and duct-mounted equipment are common to both supply and exhaust systems. Transitions and unequal-area elbows can be either supply or exhaust fittings. Fitting ED5-1 is an Exhaust fitting with a round shape (Diameter). The number 5 indicates that the fitting is a junction, and 1 is its sequential number. Fittings SR31 and ER3-1 are Supply and Exhaust fittings, respectively. The R indicates that the fitting is Rectangular, and the 3 identifies the fitting as an elbow. Note that the cross-sectional areas at sections 0 and 1 are not equal. Otherwise, the elbow would be a Common fitting such as CR3-6.

Terminal Unit Loss Coefficients. Manufacturers’ data for terminal units are not useful for duct design because they are given in terms of static pressure resistance and velocity pressure at standard air conditions (1.204 kg/m3). The total pressure loss coefficient for the 200 mm terminal used in Example 7 is calculated from manufacturer’s published data (Table 6: Columns 1, 2, and 7) and plotting Δpv,in versus Δpt (Figure 12). The loss coefficient is 1.67 and is applicable for any elevation (air density). The total pressure loss (Δpt) in Table 6 is only useful for projects at sea level. ASHRAE Standard 130-2016, Section 5.2, covers the laboratory test for total pressure loss and the calculation of the loss coefficient. In the ASHRAE Duct Fitting Database (ASHRAE 2016), the single-duct reheat VAV box is the CD8-series.

VAV Box Loss Coefficient Plot

Figure 12. VAV Box Loss Coefficient Plot


3.3 DUCTWORK SECTIONAL LOSSES

 Darcy-Weisbach Equation

Total pressure loss in a duct section is calculated by combining Equations (18) and (29) in terms of Δp, where ΣC is the summation of local loss coefficients in the duct section. Each fitting loss coefficient must be referenced to that section’s velocity pressure.

(34)

4. FAN/SYSTEM INTERFACE

 Fan Inlet and Outlet Conditions

Fan performance data measured in the field may show lower performance capacity than manufacturers’ ratings. The most common causes of deficient performance of the fan/system combination are poor outlet connections, nonuniform inlet flow, and swirl at the fan inlet. These conditions alter the fan’s aerodynamic characteristics so that its full flow potential is not realized. One bad connection can reduce fan performance below its rating.

Normally, a fan is tested with open inlets and a section of straight duct attached to the outlet (AMCA Standard 210). This setup results in uniform flow into the fan and efficient static pressure recovery on the fan outlet. If good inlet and outlet conditions are not provided in the design of duct systems, fan performance suffers.

Figure 13 shows deficient fan performance resulting from poor inlet and outlet connections to ductwork. Point 1 is the fan/system operating point without taking into account poor inlet and/or outlet conditions. Point 2 is the system operating point when the apparent resistance of poor connections is included in the calculations. Point 4 is the operating point on the original fan performance curve, taking into consideration the apparent system resistance of poor fan/system connections. Point 3 is the fan operating point on the original system curve when the apparent resistance of poor inlet and/or fan connections is not taken into account. The airflow difference between points 2 and 4 represents the deficiency in airflow from design airflow.

 Fan System Effect Coefficients

The system effect concept was formulated by Farquhar (1973) and Meyer (1973); the magnitudes of the system effect, called system effect factors, were determined experimentally by the Air Movement and Control Association International (AMCA 2011a; Brown 1973; Clarke et al. 1978). The system effect factors, converted to local loss coefficients, are in the ASHRAE Duct Fitting Database (ASHRAE 2016) for both centrifugal and axial fans. Fan system effect coefficients are only an approximation. Fans of different types and even fans of the same type, but supplied by different manufacturers, do not necessarily react to a system in the same way. Therefore, judgment based on experience must be applied to any design.

Deficient System Performance with System Effect Ignored

Figure 13. Deficient System Performance with System Effect Ignored


Fan Outlet Conditions. Fans intended primarily for duct systems are usually tested with an outlet duct in place (AMCA Standard 210). Figure 14 shows the changes in velocity profiles at various distances from the fan outlet. For 100% recovery, the duct, including transition, must meet the requirements for 100% effective duct length [Le (Figure 14)], which is calculated as follows:

For Vo > 13 m/s,

(35)

For Vo ≤ 13 m/s,

(36)

where

Vo = duct velocity, m/s
Le = effective duct length, m
Ao = duct area, mm2

Centrifugal fans should not abruptly discharge to the atmosphere. A diffuser design should be selected from Fitting SR7-2 or SR7-3. Consult the SR7-series fittings of the ASHRAE Duct Fitting Database (ASHRAE 2016) for guidance in the design of fan/ductwork connections.

Fan Inlet Conditions. For rated performance, air must enter the fan uniformly over the inlet area in an axial direction without prerotation. Nonuniform flow into the inlet is the most common cause of reduced fan performance. Such inlet conditions are not equivalent to a simple increase in system resistance; therefore, they cannot be treated as a percentage decrease in the flow and pressure from the fan. A poor inlet condition results in an entirely new fan performance.

Establishment of Uniform Velocity Profile in Straight Fan Outlet Duct (Adapted by permission from AMCA Publication 201)

Figure 14. Establishment of Uniform Velocity Profile in Straight Fan Outlet Duct (Adapted by permission from AMCA Publication 201)


Inlet Duct Connections Causing Inlet Spin (Adapted by permission from AMCA Publication 201)

Figure 15. Inlet Duct Connections Causing Inlet Spin (Adapted by permission from AMCA Publication 201)


Fitting ED7-2 (Fan Inlet, Centrifugal Fan, SISW, with 4-Gore Elbow) [ASHRAE Duct Fitting Database (ASHRAE 2016)]

Figure 16. Fitting ED7-2 (Fan Inlet, Centrifugal Fan, SISW, with 4-Gore Elbow) [ASHRAE Duct Fitting Database (ASHRAE 2016)]


Inlet spin may arise from many different approach conditions, and sometimes the cause is not obvious. Figure 15 shows some common duct connections that cause inlet spin. Inlet spin can be avoided by providing an adequate length of duct between the elbow and the fan inlet, as shown by Figure 16. Two L/Do duct lengths upstream of the fan inlet reduces swirl and pressure loss (loss coefficient) by approximately 45% (Table 7).

Table 7 ED7-2 Loss Coefficients (see Figure 16)

L/Do

L/Do

0

2

5

10

0.5

1.80

1.00

0.53

0.53

0.75

1.40

0.80

0.40

0.40

1.0

1.20

0.67

0.33

0.33

1.5

1.10

0.60

0.33

0.33

2.0

1.00

0.53

0.33

0.33

4.0

0.67

0.40

0.22

0.22


Fans within plenums and cabinets or next to walls should be located so that air may flow unobstructed into the inlets. Fan performance is reduced if the space between the fan inlet and the enclosure is too restrictive. System effect coefficients for fans in an enclosure or adjacent to walls are listed under Fitting ED7-1. How the airstream enters an enclosure in relation to the fan inlets also affects fan performance. Plenum or enclosure inlets or walls that are not symmetrical with the fan inlets cause uneven flow and/or inlet spin.

5. MECHANICAL EQUIPMENT ROOMS

In the initial phase of building design, the design engineer seldom has sufficient information to render the optimum HVAC design for the project, and its space requirements are often based on percentage of total area or other rule of thumb. The final design is usually a compromise between what the engineer recommends and what the architect can accommodate. Total mechanical and electrical space requirements range between 4 and 9% of gross building area, with most buildings in the 6 to 9% range. This range includes space for HVAC, electrical, plumbing, and fire protection equipment, as well as vertical shaft space for mechanical and electrical distribution through the building.

 Outdoor Air Intake and Exhaust Air Discharge Locations

A key factor in the location of mechanical equipment rooms is the source of outdoor air. If the air intake or exhaust system is not well designed, contaminants from nearby outdoor sources (e.g., vehicle exhaust) or from the building itself (e.g., laboratory fume hood exhaust) can enter the building with insufficient dilution. Poorly diluted contaminants may cause odors, health impacts, and reduced indoor air quality. Examples are toxic stack exhausts, automobile and truck traffic, kitchen cooking hoods, evaporative cooling towers, building general exhaust air, trash dumpsters, stagnant water bodies, snow and leaves, rain and fog, plumbing vents, vandalism, and terrorism.

Chapter 45 of the 2019 ASHRAE Handbook—HVAC Applications discusses proper design of exhaust stacks and placement of air intakes to avoid adverse air quality impacts. Experience provides some general guidelines on air intake placement. Unless dispersion modeling analysis is conducted, air intakes should never be located on the roof in the same architectural screen enclosure as exhaust outlets. If exhaust is discharged from several locations on the roof, intakes should be located to minimize contamination. Typically, this means maximizing separation distance. Where all exhausts of concern are emitted from a single, relatively tall stack or tight cluster of stacks, a possible intake location might be close to the base of this tall stack, if this location is not adversely affected by other exhaust locations, or is not influenced by tall adjacent structures creating downwash. Architectural screens placed around rooftop equipment to reduce noise or hide equipment interact with the windflow patterns on the roof and can adversely affect exhaust dilution. Chapter 45 of the 2019 ASHRAE Handbook—HVAC Applications describes a method to account for these screens by modifying the physical stack height.

When wind is perpendicular to the upwind wall, air flows up and down the wall, dividing at about two-thirds up the wall. The downward flow creates ground-level swirl that stirs up dust and debris. To take advantage of the natural separation of wind over the upper and lower halves of a building, toxic or nuisance exhausts should be located on the roof and intakes on the lower one-third of the building, but high enough to avoid wind-blown dust, debris, and vehicle exhaust. If ground-level sources are major sources of contaminants, rooftop intake is desirable.

Buildings over three stories usually require vertical shafts to consolidate mechanical, electrical, and telecommunication distribution through the facility. Vertical shafts should be located in or adjacent to mechanical/fan rooms and as far as possible from noise-sensitive areas. In general, duct shafts with an aspect ratio of 2:1 to 4:1 are easier to develop than large square shafts. The rectangular shaft also facilitates transition from equipment in the fan rooms to the shaft.

Fan rooms in a basement or at street level should be avoided. These locations are a security concern because harmful substances could easily be introduced. Using louvers at these locations is also a concern because debris, leaves, and snow may fill the area, resulting in safety, health, and fan performance concerns. Loading docks and nearby parking areas may also compromise ventilation air quality.

 Equipment Room Locations

Mechanical equipment rooms, including air-handling units, should be centrally located to centralize maintenance and operation. But, for many reasons, not all equipment rooms can be centrally located in the building. In any case, equipment should be kept together whenever possible to minimize space requirement, centralize maintenance and operation, and simplify electrical systems. All HVAC air system equipment rooms should have space for maintaining equipment and the replacement of fans, coils and other key equipment.

High-rise buildings may opt for decentralized fan rooms for each floor, or for more centralized service with one mechanical/fan room serving the lower 10 to 20 floors, one serving the middle floors of the building, and one at the roof serving the top floors.

Decentralized Equipment Rooms. Locate decentralized mechanical equipment rooms as far as possible from noise-sensitive areas, and surround equipment rooms with buffer zones such as toilet and storage rooms, as well as elevator, stair, and duct shafts. Figure 17 shows various core locations from poor to best. The number of decentralized fan rooms required depends largely on total floor area and any fan system power limitation imposed by codes or standards (e.g., ASHRAE Standard 90.1-2016, section 6.5.3.1). When decentralized air systems are located centrally to the spaces served, duct systems are shorter, occupy less volume, use less power, are quieter, and are less expensive. Pointing out these advantages can often help to convince architects to make desirable decentralized locations available.

6. DUCT DESIGN

6.1 DESIGN CONSIDERATIONS

 HVAC System Air Leakage

See Chapter 19 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment for (1) sealant specifications, and (2) the rationale for HVAC system sealing and leakage testing.

System Sealing. All ductwork and plenum transverse joints, longitudinal seams, and duct penetrations should be sealed. Openings for rotating shafts should be sealed with bushings or other devices that minimize air leakage but that do not interfere with shaft rotation or prevent thermal expansion. Spiral lock seams need not be sealed. Duct-mounted equipment, such as terminal units, reheat coils, access doors, sound attenuators, balancing dampers, control dampers, and fire dampers, should be specified as low leakage so that the system can meet the air leakage acceptance criteria set by the designer, standards, and codes. Recommended specifications for duct-mounted equipment are provided later in this section.

Comparison of Various Mechanical Equipment Room Locations (Schaffer 2011)

Figure 17. Comparison of Various Mechanical Equipment Room Locations (Schaffer 2011)


Sealing that would void product listings (e.g., for fire/smoke or volume control dampers) is not required. It is, however, recommended that the design engineer specify low-leakage duct-mounted components. For example, some UL-listed and -labeled fire/smoke dampers allow sealing and gasketing of breakaway duct/sleeve connections; all can provide sealed non-breakaway duct/sleeve connections.

Scope. It is recommended that supply air (both upstream and downstream of the VAV box primary air inlet damper when used) and independent exhaust air systems be tested for air leakage after construction at operating conditions using ASHRAE Proposed Standard 215 (under development, and expected to be published in 2018) to verify (1) good workmanship, and (2) the use of low-leakage components as required to achieve the design allowable system air leakage. To ensure that a system passes its air leakage test at operating conditions, sufficient ductwork sections should be leak tested during construction. Leakage of duct-mounted components should be determined by specification and certified leakage data provided with equipment submittals. Leakage of air-handling units should be determined by specification and verification leakage tests

Independent exhaust air system: air discharged from a space to the outdoors by a system not coupled to supply or return air systems.

Acceptance Criteria. To enable proper accounting of leakage-related impacts on fan energy and space conditioning loads, the allowable system air leakage for each fan system should be established by the design engineer as a percentage of fan airflow at the maximum system operating conditions. The recommended maximum system leakage is 5% of design airflow. Exceptions: supply and return ductwork sections that leak directly to/from outdoors and exhaust system ductwork sections that draw in indoor air through leaks should be limited to 2%.

Equation (37) is for use in a leakage test during construction to ensure that ductwork will meet the leakage specification. This equation translates system fractional air leakage to test section leakage class, as specified by ASHRAE Standard 90.1-2016, section 6.4.4.2.2.

(37)

where

CL,section = test section leakage class, L/s per Pa0.65 per square metre of duct surface area
Qfan = maximum fan airflow that would occur during operation, L/s}
Qleak, frac = system leakage fraction corresponding to maximum fan airflow that would occur during operation, %
Asystem = total system duct surface area, m2
Δpsection = test section static pressure difference corresponding to maximum fan airflow that would occur during operation, Pa

Equation (37) shows that leakage class depends on fractional air leakage and normalized fan airflow (Qfan/Asystem), and varies inversely with the pressure difference raised to the 0.65 power. For example, to achieve 3% leakage for ductwork with Qfan/Asystem = 10 L/s per m2 of duct surface area and Δpsection = 750 Pa, the required leakage class is 0.004 L/s per Pa0.65 per square metre of duct surface area. With Δpsection = 125 Pa instead (six times less), the required leakage class is about three times greater (0.13).

The maximum acceptable air leakage for a test section corresponding to the leakage class determined by Equation (37) can be expressed by Equation (38).

(38)

where

Qleak,section = test section air leakage, L/s
Asection = test section duct surface area, m2

Equations (37) and (38) can be combined so that the maximum acceptable air leakage for a test section during construction is simply a function of system fractional leakage, normalized fan airflow (Qfan/Asystem), and section duct surface area:

(39)

Thus, for air leakage tests during construction, the maximum acceptable leakage for a ductwork section is given by Equation (38) or (39). Duct surface area should be calculated in accordance with European Standard EN 14239. The test pressure for each section should be specified by the design engineer based on the maximum static pressure for that section that would occur during operation at maximum fan airflow.

Example 7.

The system depicted by Figure 18 has the characteristics summarized by Table 8. For a maximum acceptable leakage of 3% of the 2360 L/s maximum fan airflow, which is 71 L/s total, what is the maximum allowable ductwork leakage in (1) each section that is to be tested at the pressures noted, and (2) sections 4 and 5 when leak tested together?

Solution: The calculations and maximum allowable leakage are also summarized in Table 8. Note that adjacent sections with the same static pressure can be grouped for leakage testing. In this case, Sections 4 and 5 can be grouped. The allowable leakage for Sections 4 and 5 when tested individually is 4 L/s and 20 L/s respectively. The allowable leakage for Sections 4 and 5 when tested together is 24 L/s.


Table 8 Solution for Example 7

Section

Section Inlet Flow, L/s

Asection, m2

Section Static Pressure, Pa

 

Section Leakage Class, L/s per m2 per Pa0.65

 

Section Allowable Leakage, L/s

Input

Equation (37)

Equation (38) or (39)

1

2 360

46.5

750

 

0.003

 

10

2

944

62.0

250

 

0.006

 

14

3

1 416

69.7

500

 

0.004

 

15

4

472

18.6

250

 

0.006

 

4

5

944

92.9

250

 

0.006

 

20

Total

 

289.6

       

63

4 and 5

1 416

111.5

250

 

0.006

 

24


Duct Layout for Example 7

Figure 18. Duct Layout for Example 7


Recommended Specification for Duct-Mounted Equipment. Duct-mounted component leakage is controlled by specification and certified leakage data provided with equipment submittals. The following are recommended leakage-related specifications for duct-mounted equipment.

  • Terminal Units. Seal longitudinal seams of casings, inlet face of casings, and inlet collars with mastic. Seal damper shaft penetrations of casings. Casing leakage for the basic terminal unit should not exceed 2.1 L/s at 2.49 Pa static pressure differential. Terminal unit leakage with an access door should not exceed 2.2 L/s at 2.49 Pa. Testing should be by an accredited laboratory. Leakage tests should comply with ASHRAE Standard 130.

    Access doors in terminal unit casings should comply with AMCA Standard 500-D, and leakage rates should be certified per AMCA (2013) Publication 511. Access door (frame not included) leakage should not exceed 0.24 L/s at 2.49 kPa static pressure differential.

  • Electric Reheat Coils. Flange-mount electric coils with a gasket. Coil leakage should not exceed 0.24 L/s at 249 Pa static pressure differential. Tests should be by an accredited laboratory. Leakage tests should be in compliance with ASHRAE Standard 126.

  • Hot-Water Reheat Coils. Flange-mount hot-water coils with a gasket in an insulated plenum or casing. Seal all seams and casing penetrations for supply and return water tubes. Coil casing leakage (not counting transverse joints) should not exceed 0.24 L/s at 249 Pa static pressure differential. An accredited laboratory should perform leakage tests in compliance with ASHRAE Standard 126.

  • Access Doors. Access door leakage (excluding the frame) should not exceed 0.24 L/s at 2.49 kPa static pressure differential. Leakage tests should comply with AMCA Standard 500-D, and leakage rates certified per AMCA (2013) Publication 511.

  • Attenuators. Sound attenuator casing seams should be sealed at the factory if used in-line with the ductwork. Attenuators stacked in plenums do not have to be sealed, but plenums should be sealed.

  • Fire/Smoke Dampers. These dampers should be installed in accordance with the manufacturer’s UL installation instructions. Each fire damper should be furnished with a UL-approved sleeve. Sleeve seams should be continuously welded or sealed, and the transverse joint should be a sealed UL-approved flanged duct sleeve connection (break-away or non-break-away).

  • Balancing Dampers. Balancing damper casing seams should be continuously welded or sealed, and the shaft penetrating the casing should have seals.

  • Control Dampers. Control damper shafts penetrating ducts should have seals.

Recommended Specification for Air-Handling Units. Refer to Chapter 19 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment for leakage-related specifications for air-handling units.

Responsibilities. The engineer should

  • Specify HVAC system components, duct-mounted equipment, sealants, and sealing procedures that together will meet the system airtightness design objective.

  • Inspect the system during construction for quality of workmanship and to verify that correct duct-mounted components and air-handling units are installed.

  • Specify the construction-stage ductwork leakage test standard or procedures.

  • Specify the construction-stage test pressures to the nearest 25 Pa expected during operation at design conditions and the maximum allowable air leakage.

  • Review and approve the sheet metal and test contractors’ leakage test reports. If any system has a leakage failure, the engineer should discuss remedies with the sheet metal contractor, vendor, and/or owner’s representative.

The sheet metal contractor should

  • Construct the system using quality workmanship and correct duct-mounted components and air-handling units. If any installed duct-mounted equipment appears to be leakage suspect, the contractor should discuss remedies with the engineer and/or owner’s representative.

  • Conduct ductwork leakage pressurization tests during construction. As a minimum, 25% of the ductwork system (based on duct surface area) should be tested during construction, and another 25% if any of the initial sections fail. If any section of the second 25% fails, the entire ductwork system should be leak tested.

  • Provide connections for test apparatus, and separate test sections from each other as needed so that the test apparatus capacity is not exceeded.

  • Report test results and, where required, take corrective action to seal ductwork and absorb the cost for conducting related additional leak tests.

The test contractor should

  • Conduct the operating system leakage test in compliance with ASHRAE Proposed Standard 215 (expected to publish in 2018).

  • Report test results, including reasons for any failures.

It should be the responsibility of the owner or owner’s representative to provide direction upon request.

 Fire and Smoke Control

Because duct systems can convey smoke, hot gases, and fire from one area to another and can accelerate a fire within the system, fire protection is an essential part of air-conditioning and ventilation system design. Generally, fire safety codes require compliance with the standards of national organizations. NFPA Standard 90A examines fire safety requirements for (1) ducts, connectors, and appurtenances; (2) plenums and corridors; (3) air outlets, air inlets, and fresh air intakes; (4) air filters; (5) fans; (6) electric wiring and equipment; (7) air-cooling and -heating equipment; (8) building construction, including protection of penetrations; and (9) controls, including smoke control.

Fire safety codes often refer to the testing and labeling practices of nationally recognized laboratories, such as Factory Mutual and Underwriters Laboratories (UL). UL’s annual Building Materials Directory lists fire and smoke dampers that have been tested and meet the requirements of UL Standards 555 and 555S. This directory also summarizes maximum allowable sizes for individual dampers and assemblies of these dampers. Fire dampers are 1.5 h or 3 h fire-rated. Smoke dampers are classified by (1) temperature degradation [ambient air or high temperature (120°C minimum)] and (2) leakage at 250 and 1000 Pa pressure difference (2 and 3 kPa classification optional). Smoke dampers are tested under conditions of maximum airflow. UL’s annual Fire Resistance Directory lists fire resistances of floor/roof and ceiling assemblies with and without ceiling fire dampers.

For a more detailed presentation of fire protection, see the NFPA (2008) Fire Protection Handbook, Chapter 53 of the 2019 ASHRAE Handbook—HVAC Applications, and Klote et al. (2012).

 Duct Insulation

In all new construction (except low-rise residential buildings), air-handling ducts and plenums that are part of an HVAC air distribution system should be thermally insulated in accordance with ASHRAE Standard 90.1. Duct insulation for new low-rise residential buildings should comply with ASHRAE Standard 90.2. Existing buildings should meet requirements of ASHRAE Standard 100. In all cases, thermal insulation should meet local code requirements. Insulation thicknesses in these standards are minimum values; economic and thermal considerations may justify higher insulation levels. Additional insulation, vapor retarders, or both may be required to limit vapor transmission and condensation.

Duct heat gains or losses must be known to calculate supply air quantities, supply air temperatures, and coil loads. To estimate duct heat transfer and entering or leaving air temperatures, refer to Chapters 4 and 23.

 Physical Security

Ducts entering into spaces considered secured or sensitive should contain measures to detect or inhibit forced entry into those spaces through the duct system. Inhibiting measures should be based on a delay or resistance time set by the facility owner or user. The following security measures should be considered:

  • Barrier duct bars: placement should be at locations deemed appropriate by the facility owner and user, or where secured or sensitive area boundaries exist (e.g., duct penetration through the wall of a secured room). Bar diameter, material, and spacing should be established by the facility owner or user. Ensure that barriers do not inhibit proper operation and maintenance of dampers, detectors, sensors, and other devices in the duct system.

  • Welded diffuser and return grilles: grille material and spacing should be established by the facility owner or user.

  • Sensors on access doors: sensors should be connected to a facility security system or panel, and notify security personnel of a duct system breach. Communicating HVAC maintenance schedules to security personnel is necessary to ensure that an intrusive duct system breach is not confused with HVAC system maintenance.

 Louvers

Use Figure 19 for preliminary sizing of air intake and exhaust louvers. For air quantities greater than 3300 L/s per louver, the air intake gross louver openings are based on 2 m/s; for exhaust louvers, 2.5 m/s is used for air quantities of 2400 L/s per louver and greater. For smaller air quantities, see Figure 19. These criteria are presented on a per-louver basis (i.e., each louver in a bank of louvers) to include each louver frame. Representative production-run louvers were used in establishing Figure 19, and all data used were based on AMCA Standard 500-L tests. For louvers larger than 1.5 m2, the free areas are greater than 45%; for louvers less than 1.5 m2, free areas are less than 45%. Unless specific louver data are analyzed, no louver should have a face area less than 0.4 m2. If debris can collect on the screen of an intake louver, or if louvers are located at grade with adjacent pedestrian traffic, louver face velocity should not exceed 0.5 m/s.

Louvers require special treatment because the blade shapes, angles, and spacing cause significant variations in louver-free area and performance (pressure drop and water penetration). Selection and analysis should be based on test data obtained from the manufacturer in accordance with AMCA Standard 500-L, which presents both pressure drop and water penetration test procedures and a uniform method for calculating the free area of a louver. Tests are conducted on a 1220 mm square louver with the frame mounted flush in the wall. For water penetration tests, rainfall is 100 mm/h, no wind, and the water flow down the wall is 0.05 L/s per linear metre of louver width.

AMCA Standard 500-L also includes a method for measuring water rejection performance of louvers. These louvers are subjected to simulated rain and wind pressure and tested at a rainfall of 76 mm/h falling on the louver’s face with a predetermined wind velocity directed at the face of the louver (typically 13 or 20 m/s). Effectiveness ratings are assigned at various airflow rates through the louver.

 Duct Shape Selection

No Space Constraints. Round ductwork is preferable to rectangular or flat oval ductwork when adequate space is available for the following reasons.

  • Mass of round ductwork is less than rectangular. Figure 20 shows the relative weight of rectangular duct to round duct for duct pressures from ±125 to ±2500 Pa when the equivalent diameter of the rectangular duct is the same as the round duct diameter. Equivalent diameter is defined as the diameter of a rectangular duct that has equal resistance to flow for equal flow and length.

  • Perimeter of round ducts is less than rectangular ducts. For rectangular duct aspect ratios from 2 to 4, the increase is approximately 30 to 55%. This increase results in increased insulation, including possible thickness to offset the additional heat transfer. For a comprehensive study of round and rectangular ducts as they affect system performance, consult McGill (1988).

  • Round ducts have an excellent resistance to low-frequency break-out noise (Schaffer 2011).

  • Duct rumble can occur in rectangular duct systems (Paulauskis 2016).

Criteria for Louver Sizing

Figure 19. Criteria for Louver Sizing


Relative Weight of Rectangular Duct to Round Spiral Duct

Figure 20. Relative Weight of Rectangular Duct to Round Spiral Duct


Maximum Airflow of Round, Flat Oval, and Rectangular Ducts as Function of Available Ceiling Space

Figure 21. Maximum Airflow of Round, Flat Oval, and Rectangular Ducts as Function of Available Ceiling Space


Table 9 Maximum Airflow of Round, Flat Oval and Rectangular Ducts as Function of Available Ceiling Space*

A. Design Criterion: 0.65 Pa/m or 12.7 m/s Maximum

Minimum Clearance for Duct, mm

500

600

730

900

1100

Single Round Duct

  Duct diameter, mm.

400

500

630

800

1000

  Airflow, L/s

680

1230

2270

4290

7730

  Velocity, m/s

5.4

6.3

7.3

8.5

9.8

Rectangular Duct with Aspect Ratio = 2

  Rectangular W × H, mm

800 × 400

1000 × 500

1200 × 600

1600 × 800

2000 × 1000

  Airflow, L/s

2100

3780

6150

13 100

23 500

  Velocity, m/s

6.6

7.6

8.5

10.2

11.8

  Equivalent diameter De, mm

609

762

914

1219

1523

Flat Oval Duct with Aspect Ratio = 2

  Flat oval A × a, mm

800 × 400

1000 × 500

1200 × 600

1600 × 800

2000 × 1000

  Airflow, L/s

2000

3600

5850

12 500

22 500

  Velocity, m/s

7.0

8.1

9.1

10.9

12.6

  Equivalent diameter De, mm

591

739

887

1183

1479

Two Round Ducts in Parallel

  Duct diameter, mm

Two 400

Two 500

Two 630

Two 800

Two 1000

  Airflow, L/s

680 each

1230 each

2270 each

4290 each

7730 each

  Velocity, m/s

5.4

6.3

7.3

8.5

9.8

B. Design Criterion: 2 Pa/m or 12.7 m/s Maximum

Minimum clearance for duct, mm

500

600

730

900

1100

Single Round Duct

  Duct diameter, mm

400

500

630

800

1000

  Airflow, L/s

1250

2250

3950

6360

10 000

  Velocity, m/s

9.9

11.5

12.7

12.7

12.7

Rectangular Duct with Aspect Ratio = 2

  Rectangular W × H, mm

800 × 400

1000 × 500

1200 × 600

1600 × 800

2000 × 1000

  Airflow, L/s

3820

6350

9150

16 300

25 400

  Velocity, m/s

11.9

12.7

12.7

12.7

12.7

  Equivalent diameter De, mm

609

762

914

1219

1523

Flat Oval Duct with Aspect Ratio = 2

  Flat oval A × a, mm

800 × 400

1000 × 500

1200 × 600

1600 × 800

2000 × 1000

  Airflow, L/s

3630

5650

8150

14 500

22 600

  Velocity, m/s

12.7

12.7

12.7

12.7

12.7

  Equivalent diameter De, mm

591

739

887

1183

1479

Two Round Ducts in Parallel

  Duct diameter, mm

Two 400

Two 500

Two 630

Two 800

Two 1000

  Airflow, L/s

1250 each

2250 each

3950 each

6360 each

10 000 each

  Velocity, fpm

9.9

11.5

12.7

12.7

12.7

C. Design Criterion: 5 Pa/m or 15.2 m/s Maximum

Minimum clearance for duct, mm

500

600

730

900

1100

Single Round Duct

  Duct diameter mm

400

500

630

800

1000

  Airflow, L/s

1910

2990

4750

7620

11 900

  Velocity, m/s

15.2

15.2

15.2

15.2

15.2

Rectangular Duct with Aspect Ratio = 2

  Rectangular W × H, mm

800 × 400

1000 × 500

1200 × 600

1600 × 800

2000 × 1000

  Airflow, L/s

4850

7600

10 970

19 500

30 400

  Velocity, m/s

15.2

15.2

15.2

15.2

15.2

  Equivalent diameter De, mm

609

762

914

1219

1523

Flat Oval Duct with Aspect Ratio = 2

  Flat oval A × a, mm

800 × 400

1000 × 500

1200 × 600

1600 × 800

2000 × 1000

  Airflow, L/s

4350

6800

9800

17 400

27 200

  Velocity, m/s

15.2

15.2

15.2

15.2

15.2

  Equivalent diameter De, mm

591

739

887

1183

1479

Two Round Ducts in Parallel

  Duct diameter, mm

Two 400

Two 500

Two 630

Two 800

Two 1000

  Airflow, L/s

1910 each

2990 each

4750 each

7620 each

11 900 each

  Velocity, m/s

5.4

6.3

7.3

8.5

9.8


Space Constraints. Space constraints and obstructions, particularly ceiling height, are frequent problems. In these cases, the choice is round, rectangular, or flat oval ducts, depending on the air quantity that needs to be conveyed by the duct. Table 9 and Figure 21 cover three design cases: 0.65, 2, and 5 Pa/m friction rates. Friction rate 2 Pa/m is at the middle range. In Table 9, six ceiling (plenum) heights ranging from 400 to 1100 mm, in approximately 200 mm increments, are covered. Space allocated for insulation and reinforcement is 50 mm all around. The aspect ratio of the rectangular and flat oval ducts is 2:1. Figure 21 shows the maximum airflow as a function of the design friction rates and plenum spaces, as noted. For example, the 900 mm plenum as a design friction rate of 2 Pa/m is 6360 L/s maximum for a 800 mm round duct; 14 500 L/s for a 1600 × 800 mm rectangular duct; and 21,000 cfm16 300 L/s for a 1600 × 800 mm flat oval duct. The airflow capacity of two round 800 mm ducts is 6360 L/s each.

When selecting a rectangular or flat oval duct, consider the following:

  • Rectangular duct has the advantage in mass because construction standards for flat oval exist only for +2500 Pa, whereas rectangular has seven pressure classes, starting at 125 Pa. All rectangular pressure classes are ±.

    Note: Negative-pressure flat oval duct systems can be designed by using +2500 Pa sheet gages with the negative-pressure rectangular reinforcement welded to the duct.

  • Low-frequency breakout noise for flat oval is good, fair for rectangular (Schaffer 2011).

  • Duct rumble can occur in rectangular duct systems (Paulauskis 2016).

  • Perimeter. Using rectangular duct instead of flat oval when sized for equivalent diameter increases the perimeter roughly 17 to 7% for aspect ratios ranging from 1 to 4, respectively. This increase results in an increased surface area. Flat oval requires less insulation. For a comprehensive study of flat oval and rectangular ducts as they affect system performance, consult McGill (1995).

  • Duct Lengths. Rectangular duct is available in 1200, 1500, or 1800 mm lengths. Spiral round and flat oval can be provided in longer lengths.

 Testing and Balancing

Each air duct system should be tested, adjusted, and balanced. Guidance and procedures are given in Chapter 38 of the 2019 ASHRAE Handbook—HVAC Applications and in ASHRAE Standard 111. To determine fan total (or static) pressure from field measurements taking into account fan system effect, consult AMCA (2011b) Publication 203, which provides numerous fan/system configurations encountered in the field.

Many VAV noise complaints have been traced to control problems. Although most problems are associated with improper installation, many are caused by poor design. The designer should specify high-quality fans or air handlers within their optimum ranges, not at the edge of their operation ranges, where low system tolerances can lead to inaccurate fan flow capacity control. Also, in-duct static pressure sensors should be placed in duct sections having the lowest possible air turbulence (i.e., at least three equivalent duct diameters from any elbow, takeoff, transition, offset, or damper).

6.2 DESIGN RECOMMENDATIONS

  • Engage the architect and structural engineer early to coordinate shafts for systems.

  • Route ducts as straight as possible to reduce pressure loss, noise, and first costs.

  • Use round spiral ducts whenever round ducts can fit within space constraints.

  • Avoid consecutive fittings and close-coupled fittings because they can significantly increase pressure losses.

  • Use return air plenums when possible because they reduce both energy and first costs. Plenum return requires fire-rated construction.

  • Design air distribution systems to minimize flow resistance and turbulence. High flow resistance increases fan pressure, which results in higher noise being generated by the fan, especially at low frequencies. Turbulence also increases flow noise generated by duct fittings and dampers, especially at low frequencies.

  • Efficient fittings create the least turbulence and noise. Figure 22 provides generalized guidelines for minimizing regenerated noise from takeoffs. Tables 10 and 11 provide specific guidance for tees and wyes.

  • Duct transitions should not exceed an included angle of 15°.

  • To avoid fan system effects, fans should discharge into duct sections that remain straight for as long as possible, up to 10 duct diameters from the fan discharge to allow flow to fully develop (Figure 23). Use the ASHRAE Duct Fitting Database (ASHRAE 2016) to account for fan outlet system effects (SD7 and SR7-series).

  • Design duct connections at the fan inlet for uniform and straight airflow. Both turbulence and flow separation at the fan blades can significantly increase fan-generated noise. To account for fan inlet system effects, use the ASHRAE Duct Fitting Database (ASHRAE 2016) (ED7 and ER7 series).

  • For all except very-noise-sensitive applications, select VAV reheat boxes for a total pressure loss from 125 to 150 Pa; for a fan-powered VAV box, from 150 to 175 Pa. For details, see Taylor and Stein (2004).

  • VAV terminal unit inlet duct should be the same size as the inlet to the box, unless the box is in the critical path or the length exceeds about 4.5 m from the takeoff. Duct upstream of box inlets should be rigid sheet metal duct, 1.2 m minimum. Do not use flexible duct immediately upstream of VAV boxes.

  • See Figure 24 for Schaffer’s (2011) guidelines for the installation of single-duct, dual-duct, and induction terminal units, as well as parallel and series flow fan-powered units.

  • Place fan-powered mixing boxes away from noise-sensitive areas.

  • Use demand-based static pressure set-point reset to reduce fan energy and noise.

  • For constant-volume systems, select the fan to operate as near as possible to its rated peak efficiency. Also, select a fan that generates the lowest possible noise at required design conditions. Using an oversized or undersized fan that does not operate at or near rated peak efficiency can substantially increase noise levels. For VAV applications, see Schaffer (2011).

Commentary. Consult Noise and Vibration Control for HVAC Systems (Schaffer 2011) for the following guidelines related to duct systems:

  • Selection of mechanical room walls

  • Noise control for mechanical rooms

  • Upward noise control for mechanical rooms

  • Duct penetrations through walls

  • Structural support of rooftop equipment for vibration control

Guidelines For Minimizing Regenerated Noise in Takeoff (Schaffer 2011)

Figure 22. Guidelines For Minimizing Regenerated Noise in Takeoff (Schaffer 2011)


Guidelines for Centrifugal Fan Installations (Schaffer 2011)

Figure 23. Guidelines for Centrifugal Fan Installations (Schaffer 2011)


Guidelines for VAV Terminal Unit Installation (Schaffer 2011)

Figure 24. Guidelines for VAV Terminal Unit Installation (Schaffer 2011)


Table 10 Options for Selecting 90° Takeoff

Code

Description

Efficiency

Loss Coefficient

Maina

Branchb

SD5-12

Tee, 45° entry branch

Highest

0.15

0.64

SD5-4

Wye, 45°, Straight body branch with 45° elbow, 90° to main

—

0.15

0.74

SD5-11

Tee, Conical branch

—

0.15

0.87

SD5-10

Tee, Conical branch tapered into body

—

0.15

1.10

SD5-9

Tee

Lowest

0.15

1.80

a Qs/Qc = 0.8; As/Ac = 0.69

b Qb/Qc = 0.2; Ab/Ac = 0.25


Table 11 Options for Selecting 45° Takeoff (Wye)

Code

Description

Efficiency

Loss Coefficient

Main, Csa

Branch, Cbb

SD5-2

Wye, 45°, Conical branch tapered into body

Highest

0.15

0.45

SD5-3

Wye, 45°, Straight body branch with reduction transition

—

0.15

0.50

SD5-1

Wye, 45°

Lowest

0.15

0.70

a Qs/Qc = 0.8; As/Ac = 0.69

b Qb/Qc = 0.2; Ab/Ac = 0.25


6.3 DESIGN METHODS

Equal Friction Method. The equal friction method for sizing duct systems uses a constant friction rate. The target velocity determines the size of the first duct section both downstream and upstream of the fan. From the size determined by the target velocity, the design friction rate is determined to size all remaining duct sections except for connections to VAV and constant-volume (CV) terminal units and diffusers in the critical path, or for sections whose length exceeds around 4.5 m. In these cases, the inlet to terminal units should have at least three diameters of rigid duct and 2 m maximum of rigid or flexible duct (see Figure 9) to diffusers. The section upstream of the rigid duct to terminal units and the section of rigid/flexible duct to diffusers should be sized by the design friction rate, and an appropriate transition placed between sections. Refer to sections 8 and 9 in Figure 26 for an example.

Static Regain Method. The static regain method uses the conservation of momentum principle, which results in an increase in static pressure when the velocity is reduced in an airstream. This method sizes the main and branch ducts after a junction so that the recovery in static pressure caused by the reduced velocity is approximately equal to the total pressure drop caused by the duct and fittings in the subject duct section according to Equation (41). This is done iteratively by selecting a size for a section and checking to see if the section’s static pressure loss is close to zero. The basic steps are to design the first section at the velocity recommended in Table 12. Then each downstream section is subsequently sized using the same duct size as the upstream section as a starting point. If there is no static regain, meaning there is a positive static pressure loss, then the downstream section will be the same size as the upstream section. But, if there is static regain, meaning the change in static pressure is negative, then an opportunity exists to use a smaller duct section. Typically, the next smaller size available that is smaller than the upstream section is selected and the calculations are repeated. Refer to column 12 of Table 15 for examples of static regain.

Table 12 Recommended Maximum Airflow Velocities to Achieve Specified Acoustic Design Criteria*

Duct Location

NC or RC Rating in Adjoining Occupancy

Maximum Airflow Velocity, m/s

Rectangular Duct

Round Duct

1

2

3

4

In shaft or above solid drywall ceiling

45

17.8

25.4

35

12.7

17.8

25 or less

7.6

12.7

Above suspended acoustical ceiling

45

12.7

22.9

35

8.9

15.2

25 or less

5.1

10.2

Duct within occupied space

45

10.2

19.8

35

7.4

13.2

25 or less

4.8

8.6


For connections to VAV and CV terminal units and diffusers in the critical path or the section length with the terminal unit or diffuser exceeds around 4.5 m, the inlet to terminal units should have at least three diameters of rigid duct and 2 m maximum of rigid or flexible duct (see Figure 6) to diffusers. The section upstream of the rigid duct to terminal units and the section of rigid/flexible duct to diffusers should be sized by the static regain method and an appropriate transition placed between sections. Refer to sections 8 and 9 in Figure 26 for an example.

(40)

Rearranging,

(41)

where

pv1 = velocity pressure at section 1, Pa
pv2 = velocity pressure at section 2, Pa
Δpt,1–2 = total pressure loss from section 1 to 2, Pa
Δps,1–2 = static pressure regain (+) or loss (–), Pa

Balancing. When system unbalance is greater than about 30%, it is recommended that balance be improved by changing duct size, and/or fittings from a select few that have comparable efficiency without introducing additional significant turbulence (noise). Tables 10 and 11 are examples.

 Noise Control

Understanding what noise is and how to control it is fundamental to duct design. The underlying principles of sound and vibration are covered in Chapter 8. Chapter 48 of the 2019 ASHRAE Handbook—HVAC Applications contains technical discussions and design examples helpful to the design engineer. AHRI Standard 885 has procedures for estimating sound pressure levels in the occupied zone for the portion of the system downstream of terminal units. For guidance in designing HVAC systems to avoid noise and vibration problems, consult Schaffer (2011). Specifying quiet equipment and designing systems to avoid noise and vibration problems are necessary parts of the design process.

Noise in system comes from fans and generated noise resulting from air turbulence in ducts, individual fittings, close-coupled fittings, dampers, air modulating equipment and diffusers/grilles. Objectionable self-generated duct noise can be controlled by limiting the duct velocity to the values listed in Table 12.

 Goals

The goal of duct design is an air distribution system without objectionable noise and minimum life-cycle cost (LCC). Noise can be controlled by limiting the duct velocity to the values listed in Table 12. For example, for ductwork above a suspended acoustical ceiling and with a maximum allowable NC or RC of 35 in the adjoining space, the maximum round and rectangular duct airflow velocities are 15.2 and 8.9 m/s, respectively. Use this velocity to size the first duct section either upstream or downstream from the fan for all duct design methods. Lowering duct velocity reduces system operating cost and minimizes noise from sources other than ducts (fittings, close-coupled fittings, and dampers).

Commentary: In 1988, Dr. Robert J. Tsal developed the T-method (Tsal and Adler 1987; Tsal et al. 1988, 1990) to design systems with a minimum LCC. The T-method was technically sound, but the system cost was not sufficiently accurate. As a result, the T-method was removed from the Handbook in 2013.

 Design Method to Use

Supply Duct Sizing.

  • Size fan supply ducts by either the equal friction (EF) or static regain (SR) method. The duct velocity anywhere in the system should not exceed the velocity listed in Table 12.

  • Size ducts downstream of terminal boxes, toilet exhaust ducts, and other low-pressure systems (e.g., in Figure 25C) using the equal friction method with a friction rate in the range from 0.4 to1.6 Pa/m such that the duct velocity in the duct anywhere in the system does not exceed the values in Table 12. Use Table 13 as a guide to select the design friction rate.

  • Terminal unit (VAV box) runouts should be full size with the exception that runouts in the “critical” path or a runout length greater than about 4.5 m should be a minimum 1.5 m of rigid duct full size and the remainder’s size determined by the design method (e.g., Example 8 and Figure 26).

  • Diffuser runouts should be full size, except for runouts in the critical path or a runout length greater than about 4.5 m: these runouts should be at least 2 m of flexible-duct full size, and the remainder’s size determined by the design method.

Table 13 Guide for Selecting Low-Pressure System Friction Rate*

Airflow Q, L/s

0.4 Pa/m

0.8 Pa/m

1.0 Pa/m

1.2 Pa/m

1.6 Pa/m

D, mm

V, m/s

D, mm

V, m/s

D, mm

V, m/s

D, mm

V, m/s

D, mm

V, m/s

240

312

3.1

270

4.2

258

4.6

248

5.0

234

5.6

470

402

3.7

348

4.9

332

5.4

320

5.8

302

6.6

940

520

4.4

452

5.9

432

6.4

416

6.9

394

7.7

1 420

608

4.9

530

6.4

506

7.1

488

7.6

460

8.5

1 890

678

5.2

590

6.9

564

7.6

544

8.1

512

9.2

2 360

738

5.5

642

7.3

614

8.0

592

8.6

558

9.7

4 720

958

6.5

834

8.6

796

9.5

768

10.2

726

11.4

7 080

1118

7.2

972

9.5

930

10.4

896

11.2

846

12.6

9 440

1248

7,7

1086

10.2

1038

11.2

1002

12.0

946

13.4

11 800

1358

8.1

1182

10.8

1130

11.5

1090

12.6

1030

14.2

14 160

1456

8.5

1268

11.2

1212

12.3

1168

13.2

1104

14.8

* Table developed using ASHRAE Duct Fitting Database (ASHRAE 2016): CD11-4 (ε = 0.12 mm; ρ = 1.204 kg/m3).


Return Duct Systems.

  • Sizing ducted returns depend on economizer relief system. For systems with return fans (Figure 25A), the return air ducts are sized using the EF method. The SR method does not work for negative-pressure duct systems.

    If building relief is by relief fans or gravity/motorized dampers, pressure drop should be kept low as shown by the total pressure grade line associated with Figures 25B and 25C.

    Control dampers in the economizer system should be selected (parallel or opposed blade) and sized in compliance with ASHRAE Guideline 16. Louvers should be sized in accordance with the section on Louvers, under Duct Design.

  • Unducted return air shafts are typically sized for low pressure loss using either a fixed friction rate, velocity, or both. Typically, shafts are simply sized based on velocity. Maximum velocities are generally in the 4.1 to 6.1 m/s range through the free area at the top of the shaft (highest airflow rate).

  • Diffuser/grille runouts should be designed by the design method of choice and a transition located at the outlet. For outlets in the critical path, the outlet duct size should be increased. Registers should not be used because of the damper.

Example 8.

For the VAV system shown in Figure 26, design the duct system by both the equal friction (EF) and static regain (SR) methods, and compare the section duct sizes, total pressure required for each path, and the unbalance between paths.

The system is located in Denver (1655 m elevation) and the duct is spiral round, galvanized steel (absolute roughness ε = 0.12 mm). The duct system is located above a suspended acoustical ceiling, and the allowable background sound in the occupied spaces is NC-35. Terminals T1, T2, T3, and T4 (VAV boxes with a one-row hot-water coil) are 380 L/s. VAV box loss coefficients are 1.67.

Solution: Use the ASHRAE Duct Fitting Database (ASHRAE 2016) to determine the air density, which is used to identify the velocity pressure and fitting loss coefficients for fittings. Density is 0.978 kg/m3 (Figure 27). The maximum design duct velocity from Table 12 is 15.2 m/s. The EF and SR calculations are shown by Tables 14 and 15 spread-sheets.

For both the EF and SR designs, the duct size for Section 2 is 375 mm determined using CD11-3 (Figure 28). Sizing the remaining section depends on the design method. For the equal friction design method, the system equal friction (also from CD11-3) is 4.2 Pa/m. Knowing the system design friction rate, the duct sizes are determined by CD11-4. Figure 29 is an example for Section 4. For the static regain method, all sections other than the terminal unit runouts are sized by iterating using Equation (41) (column 12 on the spreadsheet). For example, the results of the iteration for Section 4 are summarized by Table 16. The solution is the diameter that gives the result from Equation (41) that is closest to zero: in this case,

Tables 17 and 18 summarize the results. The SR design is slightly better balanced, 19% compared to 23%, and the SR design requires 9% less energy. In addition, the SR sizes are slightly larger, and thus potentially less noisy. Both methods have static regain, but the SR design uses the regain more efficiently.


Economizer Duct System Shown (ASHRAE Guideline 16)

Figure 25. Economizer Duct System Shown (ASHRAE Guideline 16)


Table 14 Example 8, Equal Friction Design


Table 15 Example 8, Static Regain Design


System Layout for Example 8

Figure 26. System Layout for Example 8


Air Density for Example 8 ASHRAE Duct Fitting Database (ASHRAE 2016)

Figure 27. Air Density for Example 8 ASHRAE Duct Fitting Database (ASHRAE 2016)


Sizing Section 2 for EF and SR Design Examples

Figure 28. Sizing Section 2 for EF and SR Design Examples


6.4 INDUSTRIAL EXHAUST SYSTEMS

Chapter 32 of the 2019 ASHRAE Handbook—HVAC Applications discusses design criteria, including hood design, for industrial exhaust systems. Exhaust systems conveying vapors, gases, and smoke are designed by the equal-friction method. Systems conveying particulates are designed by the constant velocity method at duct velocities adequate to convey particles to the system air cleaner. For contaminant transport velocities, see Table 2 in Chapter 32 of the 2019 ASHRAE Handbook—HVAC Applications.

EF Design: Sizing Sections 4, 6, and 8 Knowing Design Friction Rate (Section 4 Shown)
Note: Diameter rounded up to next 25 mm increment.

Figure 29. EF Design: Sizing Sections 4, 6, and 8 Knowing Design Friction Rate (Section 4 Shown)


Table 16 Static Regain Iteration Process for Section 4

Iteration

Calculation

Duct Size, mm

[pv1 – pv2] – Δpi

Remarks

1

4a

375

19

 

2

4b

350

−7

Solution


Table 17 Summary of System Duct Sizes

Section

Size, mm

Remarks

EF

SR

1

450 × 500

450 × 500

Fan outlet

2

375

375

Initial section

4

350

350

Sections affected by design method

6

300

325

8

226

259

3

200

200

Terminal runout

5

200

200

Terminal runout

7

200

200

Terminal runout

9

200

200

Terminal runout


Table 18 System Unbalance

Path

Equal Friction

Static Regain

Pt, Pa

Unbalance

Pt, Pa

Unbalance

A

0.88

23%

0.88

18%

B

0.95

17%

0.95

11%

C

1.08

6%

1.00

7%

D

1.15

0%

1.07

0%


Two pressure-balancing methods can be considered when designing industrial exhaust systems. One method uses balancing devices (e.g., dampers, blast gates) to obtain design airflow through each hood. The other approach balances systems by adding resistance to ductwork sections (i.e., changing duct size, selecting different fittings, increasing airflow). This self-balancing method is preferred, especially for systems conveying abrasive materials. Where potentially explosive or radioactive materials are conveyed, the prebalanced system is mandatory because contaminants could accumulate at the balancing devices. To balance systems by increasing airflow, use Equation (42), which assumes that all ductwork has the same diameter and that fitting loss coefficients, including main and branch tee coefficients, are constant.

(42)

where

Qc = airflow rate required to increase Pl to Ph, L/s
Qd = total airflow rate through low-resistance duct run, L/s
Ph = absolute value of pressure loss in high-resistance ductwork section(s), Pa
Pl = absolute value of pressure loss in low-resistance ductwork section(s), Pa

For systems conveying particulates, use elbows with a large centerline radius-to-diameter ratio (r/D), greater than 1.5 whenever possible. If r/D is 1.5 or less, abrasion in dust-handling systems can reduce the life of elbows. Elbows are often made of seven or more gores, especially in large diameters. For converging flow fittings, a 30° entry angle is recommended to minimize energy losses and abrasion in dust-handling systems. For the entry loss coefficients of hoods and equipment for specific operations, see Chapter 32 of the 2019 ASHRAE Handbook—HVAC Applications and ACGIH (2016).

Commentary: Fitting CD11-5 of the ASHRAE Duct Fitting Database (ASHRAE 2016) is available for sizing minimum-velocity ducts conveying particulates.

Metalworking Exhaust System for Example 9

Figure 30. Metalworking Exhaust System for Example 9


Example 9.

For the metalworking exhaust system in Figures 30 and 31, size the ductwork and calculate fan static pressure requirement for an industrial exhaust designed to convey granular materials. Pressure-balance the system by changing duct sizes and adjusting airflow rates. Minimum particulate transport velocity for the chipping and grinding table ducts (sections 1 and 5, Figure 31) is 20 m/s. For ducts associated with the grinder wheels (sections 2, 3, 4, and 5), minimum duct velocity is 23 m/s. Ductwork is galvanized steel, with absolute roughness of 0.09 mm. Use sizes for which spiral duct is available (80, 100, 125, 140, 150, 160, 180, 200, 224, 250, 280, 300, 315, 355, 400, 450, 500, 560, 600, 630, 710, 800, 900, 1000, 1120, 1250, 1300, 1400, 1500, 1600, 1800, 2000, 2100, 2200, 2300, 2400, and 2500 mm).

The building is one story, and the design wind velocity is 9 m/s. For the stack, use design J shown in Figure 2 in Chapter 45 of the 2019 ASHRAE Handbook—HVAC Applications for complete rain protection; stack height, determined by calculations from Chapter 45, is 4.9 m above the roof. This height is based on minimized stack downwash; therefore, the stack discharge velocity must exceed 1.5 times the design wind velocity.

Solution: The following table summarizes initial duct sizes and transport velocities for contaminated ducts upstream of the collector. The 22.8 m/s velocity in sections 2 and 3 is acceptable because the transport velocity is not significantly lower than 23 m/s. For the next available duct size (160 mm diameter), the duct velocity is 28.8 m/s, significantly higher than 23 m/s.

Duct Section

Design Airflow, L/s

Transport Velocity, m/s

Duct Diameter, mm

Duct Velocity, m/s

1

850

20

224

21.6

2, 3

290 each

23

125

23.6

4

580

23

180

22.8

5

1430

23

180

23.2

Design calculations up through the junction after sections 1 and 4 are summarized as follows:

Design No.

D1, mm

Δp1, Pa

Δp2+4, Pa

Imbalance, Δp1− Δp2+4

1

224

411

794

−383

2

200

762

850

−88

3

180

1320

712

+609

Q1 = 850 L/s

Q2 = 290 L/s; D2 = 125 mm dia.

Q3 = 290 L/s; D3 = 125 mm dia.

Q4 = 850 L/s; D4 = 180 mm dia.


For (initial) design 1, the imbalance between section 1 and section 2 (or 3) is 383 Pa, with section 1 requiring additional resistance. Decreasing section 1 duct diameter by manufactured spiral duct sizes results in the least imbalance, 88 Pa, when the duct diameter is 200 mm (design 2). Because section 1 requires additional resistance, estimate the new airflow rate using Equation (42):

At 900 L/s flow in section 1, 130 Pa imbalance remains at the junction of sections 1 and 4. By trial-and-error solution, balance is attained when the flow in section 1 is 860 L/s. The duct between the collector and fan inlet is 355 mm round to match the fan inlet (340 mm diameter). To minimize downwash, the stack discharge velocity must exceed 13.5 m/s, 1.5 times the design wind velocity (9 m/s) as stated in the problem definition. Therefore, the stack is 355 mm round, and the stack discharge velocity is 14.5 m/s.

Table 19 summarizes the system losses by sections. The straight duct friction factor and pressure loss were calculated by Equations (18) and (19). Table 20 lists fitting loss coefficients and input parameters necessary to determine the loss coefficients. The fitting loss coefficients are from the ASHRAE Duct Fitting Database. Figure 32 shows a pressure grade line of the system. Fan total pressure, calculated by Equation (15), is 1992 Pa. To calculate the fan static pressure, use Equation (17):

where 192 Pa is the fan outlet velocity pressure. The fan airflow rate is 1440 L/s, and its outlet area is 0.081 m3 (260 by 310 mm). Therefore, the fan outlet velocity is 17.9 m/s.

System Schematic with Section Numbers for Example 9

Figure 31. System Schematic with Section Numbers for Example 9


Table 19 Total Pressure Loss Calculations by Sections for Example 9

Duct Sectiona

Duct Element

Airflow, L/s

Duct Size, mm ϕ

Velocity, m/s

Velocity Pressure, Pa

Duct Length, bm

Summary of Fitting Loss Coefficientsc

Duct Pressure Loss, Pa/md

Total Pressure Loss, Pa

Section Pressure Loss, Pa

1

Duct

860

200

27.4

—

7.32

—

40

293

 
 

Fittings

860

—

27.4

451

—

1.09

—

492

785

2, 3

Duct

290

125

23.6

—

2.7

—

54

146

 
 

Fittings

290

—

23.6

336

—

1.06

—

356

502

4

Duct

580

180

22.8

—

3.84

—

32

123

 
 

Fittings

580

—

22.8

313

—

0.51

—

160

283

5

Duct

1440

280

23.4

—

2.7

—

18.5

50

 
 

Fittings

1440

—

23.4

329

—

0.23

—

76

126

—

Collector,efabric

1440

—

—

—

—

—

—

750

750

6

Duct

1440

355

14.5

—

3.0

—

6

18

 
 

Fittings

1440

—

14.5

127

—

0.03

—

4

22

7

Duct

1440

355

14.5

—

14.0

—

6

84

 
 

Fittings

1440

—

14.5

127

—

1.77

—

225

309

a See Figure 29.

b Duct lengths are to fitting centerlines.

c See Table 20.

d Duct pressure based on a 0.09 mm absolute roughness factor.

e Collector manufacturers set fabric bag cleaning mechanism to actuate at a pressure difference of 750 Pa between inlet and outlet plenums. Pressure difference across clean media is approximately 400 Pa.


Table 20 Loss Coefficient Summary by Sections for Example 9

Duct Section

Fitting Number

Type of Fitting

ASHRAE Fitting No.a

Parameters

Loss Coefficient

1

1

Hoodb

—

Hood face area: 0.9 by 1.2 m

0.25

 

2

Elbow

CD3-10

90°, 7 gore, r/D = 2.5

0.11

 

4

Capped wye (45°), with 45° elbow

ED5-6

Ab/Ac = 1

0.61 (Cb)

 

5

Wye (30°), main

ED5-1

Qs/Qc = 0.60, As/Ac = 0.510, Ab/Ac = 0.413

0.12 (Cs)

 

Summation of Section 1 loss coefficients

1.09

 

2,3

6

Hoodc

—

Type hood: For double wheels, dia. = 560 mm each, wheel width = 100 mm each; type takeoff: tapered

0.40

 

7

Elbow

CD3-12

90°, 3 gore, r/D = 1.5

0.34

 

8

Symmetrical wye (60°)

ED5-9

Qb/Qc = 0.5, Ab1/Ac = 0.482, Ab2/Ac = 0.482

0.32 (Cb)

 

Summation of Section 2 and 3 loss coefficients

1.06

 

4

9

Elbow

CD3-10

90°, 7 gore, r/D = 2.5

0.11

 

10

Elbow

CD3-13

60°, 3 gore, r/D = 1.5

0.19

 

5

Wye (30°), branch

ED5-1

Qb/Qc = 0.40, As/Ac = 0.510, Ab/Ac = 0.413

0.21 (Cb)

 

Summation of Section 4 loss coefficients

0.51

 

5

11

Exit, conical diffuser to collector

ED2-1

L = 600 mm, L/Do = 2.14, A1/Ao ≈ 21

0.23

 

Summation of Section 5 loss coefficients

0.23

 

6

12

Entry, bellmouth from collector

ER2-1

r/D1 = 0.21, r = 75 mm, Co = 4.69

0.03 (C1)

 

Summation of Section 6 loss coefficients

0.03

 

7

13

Diffuser, fan outlet d

SD4-2

Fan outlet size: 260 by 310 mm; L = 460 mm

0.16

 

14

Capped wye (45°), with 45° elbow

ED5-6

Ab/Ac = 1

0.61 (Cb)

 

15

Stackhead

SD2-6

De/D = 1

1.00

 

Summation of Section 7 loss coefficients

1.77

 

a From ASHRAE Duct Fitting Database.

b From Industrial Ventilation (ACGIH 2016, Figure VS-80-19).

c From Industrial Ventilation (ACGIH 2016, Figure VS-80-11).

d Fan specified: Industrial exhauster for granular materials: 530 mm wheel diameter, 340 mm inlet diameter, 260 by 310 mm outlet, 6 kW motor.


Total Pressure Grade Line for Example 9

Figure 32. Total Pressure Grade Line for Example 9


Hood suction for the chipping and grinding table hood is 560 Pa, calculated by Equation (5) from Chapter 32 of the 2019 ASHRAE Handbook—HVAC Applications [Ps,h = (1 + 0.25) (451) = 560 Pa, where 0.25 is hood entry loss coefficient Co, and 451 is duct velocity pressure Pv a few diameters downstream from the hood]. Similarly, hood suction for each grinder wheel is 170 Pa

where 0.4 is the hood entry loss coefficient, and 336 Pa is the duct velocity pressure.


REFERENCES

ASHRAE members can access ASHRAE Journal articles and ASHRAE research project final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.

Abushakra, B., I.S. Walker, and M.H. Sherman. 2004. Compression effects on pressure loss in flexible HVAC ducts. International Journal of HVAC&R Research (now Science and Technology for the Built Environment) 10(3):275-289.

ACCA. 2014. Manual D—Residential duct systems. Air Conditioning Contractors of America, Washington, DC.

ACGIH. 2016. Industrial ventilation: A manual of recommended practice for design, 29th ed. American Conference of Governmental Industrial Hygienists, Lansing, MI.

AHRI. 2008. Procedure for estimating occupied space sound levels in the application of air terminals and air outlets. Standard 885-2008 with Addendum 1. Air-Conditioning, Heating, and Refrigeration Institute, Arlington, VA.

AMCA. 2011a. Fans and systems. AMCA Publication 201-02 (R2011). Air Movement and Control Association International, Arlington Heights, IL.

AMCA. 2011b. Field performance measurement of fan systems. AMCA Publication 203-90 (R2011). Air Movement and Control Association International, Arlington Heights, IL.

AMCA. 2016. Laboratory methods for testing fans for certified aerodynamic performance rating. ANSI/AMCA Standard 210-16. Also ANSI/ASHRAE/AMCA Standard 51-16.

AMCA. 2012. Laboratory methods of testing dampers for rating. ANSI/AMCA Standard 500-D-12. Air Movement and Control Association International, Arlington Heights, IL.

AMCA. 2015. Laboratory method of testing louvers for rating. ANSI/AMCA Standard 500-L-12 (R2015). Air Movement and Control Association International, Arlington Heights, IL.

AMCA. 2013. Certified ratings program—Product rating manual for air control. AMCA Publication 511-10 (Rev. 2013). Air Movement and Control Association International, Arlington Heights, IL.

ASHRAE. 2016. ASHRAE duct fitting database, v. 6.00.05.10.

ASHRAE. 2016. Energy standard for buildings except low-rise residential buildings. ANSI/ASHRAE/IES Standard 90.1-2016.

ASHRAE. 2007. Energy-efficient design of low-rise residential buildings. ANSI/ASHRAE Standard 90.2-2007.

ASHRAE. 2015. Energy conservation in existing buildings. ANSI/ASHRAE/IES Standard 100-2015.

ASHRAE. 2008. Measurement, testing, adjusting and balancing of building heating, ventilation and air-conditioning systems. ANSI/ASHRAE Standard 111-2008.

ASHRAE. 2016. Method of testing HVAC air ducts and fittings. ANSI/ASHRAE/SMACNA Standard 126-2016.

ASHRAE. 2016. Methods of testing air terminal units. ANSI/ASHRAE Standard 130-2016.

ASHRAE. In development. Method of test to determine leakage of operating HVAC air distribution systems. ANSI/ASHRAE Proposed Standard 215.

ASHRAE. 2014. Selecting outdoor, return, and relief dampers for air-side economizer systems. ASHRAE Guideline 16-2014.

Behls, H.F. 1971. Computerized calculation of duct friction. Building Science Series 39, p. 363. National Institute of Standards and Technology, Gaithersburg, MD.

Brown, R.B. 1973. Experimental determinations of fan system effect factors. In Fans and systems, ASHRAE Symposium Bulletin LO-73-1, Louisville, KY (June).

CEN. 1998. Ventilation for buildings—Sheet metal air ducts and fittings with rectangular cross-section—Dimensions. European Standard EN 1505-1998. European Committee for Standardization, Brussels.

CEN. 2007. Ventilation for buildings—Sheet metal air ducts and fittings with circular cross-section—Dimensions. European Standard EN 1506-2007. European Committee for Standardization, Brussels.

CEN. 2004. Ventilation for buildings—Ductwork—Measurement of ductwork surface area. European Standard EN 14239-2004. European Committee for Standardization, Brussels.

Clarke, M.S., J.T. Barnhart, F.J. Bubsey, and E. Neitzel. 1978. The effects of system connections on fan performance. ASHRAE Transactions 84(2): 227-263.

Colebrook, C.F. 1938–1939. Turbulent flow in pipes, with particular reference to the transition region between the smooth and rough pipe laws. Journal of the Institution of Civil Engineers 11:133.

Culp, C.H. 2011. HVAC flexible duct pressure loss measurements. ASHRAE Research Project RP-1333, Final Report.

Farquhar, H.F. 1973. System effect values for fans. In Fans and systems, ASHRAE Symposium Bulletin LO-73-1, Louisville, KY (June).

Griggs, E.I., and F. Khodabakhsh-Sharifabad. 1992. Flow characteristics in rectangular ducts. ASHRAE Transactions 98(1):116-127.

Griggs, E.I., W.B. Swim, and G.H. Henderson. 1987. Resistance to flow of round galvanized ducts. ASHRAE Transactions 93(1):3-16.

Heyt, J.W., and M.J. Diaz. 1975. Pressure drop in flat-oval spiral air duct. ASHRAE Transactions 81(2):221-232.

Huebscher, R.G. 1948. Friction equivalents for round, square and rectangular ducts. ASHVE Transactions 54:101-118.

Hutchinson, F.W. 1953. Friction losses in round aluminum ducts. ASHVE Transactions 59:127-138.

Idelchik, I.E., M.O. Steinberg, G.R. Malyavskaya, and O.G. Martynenko. 1994. Handbook of hydraulic resistance, 3rd ed. CRC Press/Begell House, Boca Raton.

Jones, C.D. 1979. Friction factor and roughness of United Sheet Metal Company spiral duct. United Sheet Metal, Division of United McGill Corp., Westerville, OH (August). Based on data in Friction loss tests, United Sheet Metal Company Spiral Duct, Ohio State University Engineering Experiment Station, File T-1011, September 1958.

Klote, J.H., J.A. Milke, P.G. Tumbull, A. Kashef, and M.J. Ferreira. 2012. Handbook of smoke control engineering. ASHRAE.

Kulkarni, D., S. Khaire, and S. Idem. 2009. Pressure loss of corrugated spiral duct. ASHRAE Transactions 115(1).

Madison, R.D., and W.R. Elliot. 1946. Friction charts for gases including correction for temperature, viscosity and pipe roughness. ASHVE Journal (October).

McGill. 1988. Round vs. rectangular duct. Engineering Report 147, United McGill Corp. (contact McGill Airflow Technical Service Department), Westerville, OH.

McGill. 1995. Flat oval vs. rectangular duct. Engineering Report 150, United McGill Corp. (contact McGill Airflow Technical Service Department), Westerville, OH.

Meyer, M.L. 1973. A new concept: The fan system effect factor. In Fans and Systems, ASHRAE Symposium Bulletin LO-73-1, Louisville, KY (June).

Moody, L.F. 1944. Friction factors for pipe flow. ASME Transactions 66: 671.

NFPA. 2008. Fire protection handbook, 20th ed. National Fire Protection Association. Quincy, MA.

NFPA. 2015. Installation of air-conditioning and ventilating systems. ANSI/NFPA Standard 90A. National Fire Protection Association, Quincy, MA.

Osborne, W.C. 1966. Fans. Pergamon, London.

Paulauskis, J.A. 2016. Understanding duct rumble. ASHRAE Journal 58(12):40-45.

Schaffer, M.E. 2011. A practical guide to noise and vibration control for HVAC systems (SI), 2nd ed. ASHRAE.

Swim, W.B. 1978. Flow losses in rectangular ducts lined with fiberglass. ASHRAE Transactions 84(2):216.

Swim, W.B. 1982. Friction factor and roughness for airflow in plastic pipe. ASHRAE Transactions 88(1):269.

Taylor. S.J., and J. Stein. 2004. Sizing VAV boxes. ASHRAE Journal 46(3): 30-35.

Tsal, R.J., and M.S. Adler. 1987. Evaluation of numerical methods for ductwork and pipeline optimization. ASHRAE Transactions 93(1):17-34.

Tsal, R.J., H.F. Behls, and R. Mangel. 1988. T-method duct design, part I: Optimization theory; Part II: Calculation procedure and economic analysis. ASHRAE Transactions 94(2):90-111.

Tsal, R.J., H.F. Behls, and R. Mangel. 1990. T-method duct design, part III: Simulation. ASHRAE Transactions 96(2).

UL. Published annually. Building materials directory. Underwriters Laboratories, Northbrook, IL.

UL. Published annually. Fire resistance directory. Underwriters Laboratories, Northbrook, IL.

UL. 2013. Fire dampers. ANSI/UL Standard 555, 7th ed. Underwriters Laboratories, Northbrook, IL.

UL. 2014. Smoke dampers. ANSI/UL Standard 555S, 5th ed. Underwriters Laboratories, Northbrook, IL.

Wright, D.K., Jr. 1945. A new friction chart for round ducts. ASHVE Transactions 51:303-316.

BIBLIOGRAPHY

Abushakra, B., I.S. Walker, and M.H. Sherman. 2002. A study of pressure losses in residential air distribution systems. Proceedings of the ACEEE Summer Study 2002, American Council for an Energy Efficient Economy, Washington, D.C. LBNL Report 49700. Lawrence Berkeley National Laboratory, CA.

Carrié, F.R., J. Andersson, and P. Wouters. 1999. Improving ductwork—A time for tighter air distribution systems. Air Infiltration and Ventilation Centre, Coventry, U.K.

Hyderman, M., S. Taylor, and J. Stein. 2009. Advanced variable air volume VAV systems design guide, 3rd edition. Pacific Gas and Electric Company.



The preparation of this chapter is assigned to TC 5.2, Duct Design.