10. PREVIOUS COOLING LOAD CALCULATION METHODS
Procedures described in this chapter are the most current and scientifically derived means for estimating cooling load for a defined building space, but methods in earlier editions of the ASHRAE Handbook are valid for many applications. These earlier procedures are simplifications of the heat balance principles, and their use requires experience to deal with atypical or unusual circumstances. In fact, any cooling or heating load estimate is no better than the assumptions used to define conditions and parameters such as physical makeup of the various envelope surfaces, conditions of occupancy and use, and ambient weather conditions. Experience of the practitioner can never be ignored.
The primary difference between the HB and RTS methods and the older methods is the newer methods’ direct approach, compared to the simplifications necessitated by the limited computer capability available previously.
The transfer function method (TFM), for example, required many calculation steps. It was originally designed for energy analysis with emphasis on daily, monthly, and annual energy use, and thus was more oriented to average hourly cooling loads than peak design loads.
The total equivalent temperature differential method with time averaging (TETD/TA) has been a highly reliable (if subjective) method of load estimating since its initial presentation in the 1967 Handbook of Fundamentals. Originally intended as a manual method of calculation, it proved suitable only as a computer application because of the need to calculate an extended profile of hourly heat gain values, from which radiant components had to be averaged over a time representative of the general mass of the building involved. Because perception of thermal storage characteristics of a given building is almost entirely subjective, with little specific information for the user to judge variations, the TETD/TA method’s primary usefulness has always been to the experienced engineer.
The cooling load temperature differential method with solar cooling load factors (CLTD/CLF) attempted to simplify the two-step TFM and TETD/TA methods into a single-step technique that proceeded directly from raw data to cooling load without intermediate conversion of radiant heat gain to cooling load. A series of factors were taken from cooling load calculation results (produced by more sophisticated methods) as “cooling load temperature differences” and “cooling load factors” for use in traditional conduction (q = UA Δ t) equations. The results are approximate cooling load values rather than simple heat gain values. The simplifications and assumptions used in the original work to derive those factors limit this method’s applicability to those building types and conditions for which the CLTD/CLF factors were derived; the method should not be used beyond the range of applicability.
Although the TFM, TETD/TA, and CLTD/CLF procedures are not republished in this chapter, those methods are not invalidated or discredited. Experienced engineers have successfully used them in millions of buildings around the world. The accuracy of cooling load calculations in practice depends primarily on the availability of accurate information and the design engineer’s judgment in the assumptions made in interpreting the available data. Those factors have much greater influence on a project’s success than does the choice of a particular cooling load calculation method.
The primary benefit of HB and RTS calculations is their somewhat reduced dependency on purely subjective input (e.g., determining a proper time-averaging period for TETD/TA; ascertaining appropriate safety factors to add to the rounded-off TFM results; determining whether CLTD/CLF factors are applicable to a specific unique application). However, using the most up-to-date techniques in real-world design still requires judgment on the part of the design engineer and care in choosing appropriate assumptions, just as in applying older calculation methods.
ASHRAE members can access ASHRAE Journal articles and ASHRAE research project final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.
Abushakra, B., J.S. Haberl, and D.E. Claridge. 2004. Overview of literature on diversity factors and schedules for energy and cooling load calculations (1093-RP). ASHRAE Transactions 110(1):164-176.
Armstrong, P.R., C.E. Hancock, III, and J.E. Seem. 1992a. Commercial building temperature recovery—Part I: Design procedure based on a step response model. ASHRAE Transactions 98(1):381-396.
Armstrong, P.R., C.E. Hancock, III, and J.E. Seem. 1992b. Commercial building temperature recovery—Part II: Experiments to verify the step response model. ASHRAE Transactions 98(1):397-410.
ASHRAE. 2010. Thermal environmental conditions for human occupancy. ANSI/ASHRAE Standard 55-2010.
ASHRAE. 2010. Ventilation for acceptable indoor air quality. ANSI/ASHRAE Standard 62.1-2010.
ASHRAE. 2016. Energy standard for building except low-rise residential buildings. ANSI/ASHRAE/IES Standard 90.1-2016.
ASHRAE. 2012. Updating the climatic design conditions in the ASHRAE Handbook—Fundamentals (RP-1613). ASHRAE Research Project, Final Report.
ASHRAE. 2013. Underfloor air distribution (UFAD) design guide, 2nd ed.
ASTM. 2008. Practice for estimate of the heat gain or loss and the surface temperatures of insulated flat, cylindrical, and spherical systems by use of computer programs. Standard C680-08. American Society for Testing and Materials, West Conshohocken, PA.
Bach, C., and O. Sarfraz. 2017. Update to measurements of office heat gain data. ASHRAE Research Project RP-1742, Progress Report.
Bauman, F., S. Schiavon, T. Webster, and K.H. Lee. 2010. Cooling load design tool for UFAD systems. ASHRAE Journal (September):62-71. escholarship.org/uc/item/9d8430v3.
Bliss, R.J.V. 1961. Atmospheric radiation near the surface of the ground. Solar Energy 5(3):103.
CFR. Annual. Energy efficiency program for certain commercial and industrial equipment. Code of Federal Regulations 10 CFR 431. U.S. Government Publishing Office, Washington, D.C. www.ecfr.gov.
Chantrasrisalai, C., D.E. Fisher, I. Iu, and D. Eldridge. 2003. Experimental validation of design cooling load procedures: The heat balance method. ASHRAE Transactions 109(2):160-173.
Claridge, D.E., B. Abushakra, J.S. Haberl, and A. Sreshthaputra. 2004. Electricity diversity profiles for energy simulation of office buildings (RP-1093). ASHRAE Transactions 110(1):365-377.
Eldridge, D., D.E. Fisher, I. Iu, and C. Chantrasrisalai. 2003. Experimental validation of design cooling load procedures: Facility design (RP-1117). ASHRAE Transactions 109(2):151-159.
Feng, J., S. Schiavon, and F. Bauman. 2012. Comparison of zone cooling load for radiant and air conditioning systems. Proceedings of the International Conference on Building Energy and Environment. Boulder, CO. escholarship.org/uc/item/9g24f38j.
Fisher, D.R. 1998. New recommended heat gains for commercial cooking equipment. ASHRAE Transactions 104(2):953-960.
Fisher, D.E., and C. Chantrasrisalai. 2006. Lighting heat gain distribution in buildings (RP-1282). ASHRAE Research Project, Final Report.
Fisher, D.E., and C.O. Pedersen. 1997. Convective heat transfer in building energy and thermal load calculations. ASHRAE Transactions 103(2): 137-148.
Gordon, E.B., D.J. Horton, and F.A. Parvin. 1994. Development and application of a standard test method for the performance of exhaust hoods with commercial cooking appliances. ASHRAE Transactions 100(2).
Hittle, D.C. 1999. The effect of beam solar radiation on peak cooling loads. ASHRAE Transactions 105(2):510-513.
Hittle, D.C., and C.O. Pedersen. 1981. Calculating building heating loads using the frequency of multi-layered slabs. ASHRAE Transactions 87(2): 545-568.
Hosni, M.H., and B.T. Beck. 2008. Update to measurements of office equipment heat gain data (RP-1482). ASHRAE Research Project, Progress Report.
Hosni, M.H., B.W. Jones, J.M. Sipes, and Y. Xu. 1998. Total heat gain and the split between radiant and convective heat gain from office and laboratory equipment in buildings. ASHRAE Transactions 104(1A):356-365.
Hosni, M.H., B.W. Jones, and H. Xu. 1999. Experimental results for heat gain and radiant/convective split from equipment in buildings. ASHRAE Transactions 105(2):527-539.
Incropera, F.P., and D.P. DeWitt. 1990. Fundamentals of heat and mass transfer, 3rd ed. Wiley, New York.
Iu, I., and D.E. Fisher. 2004. Application of conduction transfer functions and periodic response factors in cooling load calculation procedures. ASHRAE Transactions 110(2):829-841.
Iu, I., C. Chantrasrisalai, D.S. Eldridge, and D.E. Fisher. 2003. Experimental validation of design cooling load procedures: The radiant time series method (RP-1117). ASHRAE Transactions 109(2):139-150.
Jones, B.W., M.H. Hosni, and J.M. Sipes. 1998. Measurement of radiant heat gain from office equipment using a scanning radiometer. ASHRAE Transactions 104(1B):1775-1783.
Karambakkam, B.K., B. Nigusse, and J.D. Spitler. 2005. A one-dimensional approximation for transient multi-dimensional conduction heat transfer in building envelopes. Proceedings of the 7th Symposium on Building Physics in the Nordic Countries, The Icelandic Building Research Institute, Reykjavik, vol. 1, pp. 340-347.
Kerrisk, J.F., N.M. Schnurr, J.E. Moore, and B.D. Hunn. 1981. The custom weighting-factor method for thermal load calculations in the DOE-2 computer program. ASHRAE Transactions 87(2):569-584.
Komor, P. 1997. Space cooling demands from office plug loads. ASHRAE Journal 39(12):41-44.
Kong, M., and J. Zhang. 2016. Life-cycle cost and benefit analysis of utilizing hoods for light-duty cooking appliances in commercial kitchens (RP-1631, part 2). Science and Technology for the Built Environment 22(6): 866-882.
Kong, M., J. Zhang, B. Guo, and K. Han. 2016. Measurements of grease emission and heat generation rates of electric countertop appliances (RP-1631, part 1). Science and Technology for the Built Environment 22(6): 845-865.
Kusuda, T. 1967. NBSLD, the computer program for heating and cooling loads for buildings. BSS 69 and NBSIR 74-574. National Bureau of Standards.
Latta, J.K., and G.G. Boileau. 1969. Heat losses from house basements. Canadian Building 19(10):39.
LBL. 2015. WINDOW 7.4.6: A PC program for analyzing window thermal performance for fenestration products. LBL-48255. Windows and Daylighting Group. Lawrence Berkeley Laboratory, Berkeley.
Liesen, R.J., and C.O. Pedersen. 1997. An evaluation of inside surface heat balance models for cooling load calculations. ASHRAE Transactions 103(2):485-502.
Marn, W.L. 1962. Commercial gas kitchen ventilation studies. Research Bulletin 90(March). Gas Association Laboratories, Cleveland, OH.
McClellan, T.M., and C.O. Pedersen. 1997. Investigation of outdoor heat balance models for use in a heat balance cooling load calculation procedure. ASHRAE Transactions 103(2):469-484.
McQuiston, F.C., and J.D. Spitler. 1992. Cooling and heating load calculation manual, 2nd ed. ASHRAE.
Miller, A. 1971. Meteorology, 2nd ed. Charles E. Merrill, Columbus.
Nigusse, B.A. 2007. Improvements to the radiant time series method cooling load calculation procedure. Ph.D. dissertation, Oklahoma State University.
Parker, D.S., J.E.R. McIlvaine, S.F. Barkaszi, D.J. Beal, and M.T. Anello. 2000. Laboratory testing of the reflectance properties of roofing material. FSEC-CR670-00. Florida Solar Energy Center, Cocoa.
Pedersen, C.O., D.E. Fisher, and R.J. Liesen. 1997. Development of a heat balance procedure for calculating cooling loads. ASHRAE Transactions 103(2):459-468.
Pedersen, C.O., D.E. Fisher, J.D. Spitler, and R.J. Liesen. 1998. Cooling and heating load calculation principles. ASHRAE.
PG&E. 2010-2016. Dishwashing machine performance reports: Application of ASTM F2474, standard test method for heat gain to space performance of commercial kitchen ventilation/appliance systems. PG&E Food Service Technology Center, San Ramon, CA. www.fishnick.com/publications/appliancereports/dishmachines/.
Rees, S.J., J.D. Spitler, M.G. Davies, and P. Haves. 2000. Qualitative comparison of North American and U.K. cooling load calculation methods. International Journal of Heating, Ventilating, Air-Conditioning and Refrigerating Research 6(1):75-99.
Rock, B.A. 2005. A user-friendly model and coefficients for slab-on-grade load and energy calculation. ASHRAE Transactions 111(2):122-136.
Rock, B.A., and D.J. Wolfe. 1997. A sensitivity study of floor and ceiling plenum energy model parameters. ASHRAE Transactions 103(1):16-30.
Schiavon, S., F. Bauman, K.H. Lee, and T. Webster. 2010a. Simplified calculation method for design cooling loads in underfloor air distribution (UFAD) systems. Energy and Buildings 43(1-2):517-528. escholarship.org/uc/item/5w53c7kr.
Schiavon, S., K.H. Lee, F. Bauman, and T. Webster. 2010b. Influence of raised floor on zone design cooling load in commercial buildings. Energy and Buildings 42(5):1182-1191. escholarship.org/uc/item/2bv611dt.
Schiavon, S., F. Bauman, K.H. Lee, and T. Webster. 2010c. Development of a simplified cooling load design tool for underfloor air distribution systems. Final Report to CEC PIER Program, July. escholarship.org/uc/item/6278m12z.
Smith, V.A., R.T. Swierczyna, and C.N. Claar. 1995. Application and enhancement of the standard test method for the performance of commercial kitchen ventilation systems. ASHRAE Transactions 101(2).
Sowell, E.F. 1988a. Cross-check and modification of the DOE-2 program for calculation of zone weighting factors. ASHRAE Transactions 94(2).
Sowell, E.F. 1988b. Load calculations for 200,640 zones. ASHRAE Transactions 94(2):716-736.
Spitler, J.D., and D.E. Fisher. 1999a. Development of periodic response factors for use with the radiant time series method. ASHRAE Transactions 105(2):491-509.
Spitler, J.D., and D.E. Fisher. 1999b. On the relationship between the radiant time series and transfer function methods for design cooling load calculations. International Journal of Heating, Ventilating, Air-Conditioning and Refrigerating Research (now Science and Technology for the Built Environment) 5(2):125-138.
Spitler, J.D., D.E. Fisher, and C.O. Pedersen. 1997. The radiant time series cooling load calculation procedure. ASHRAE Transactions 103(2).
Spitler, J.D., S.J. Rees, and P. Haves. 1998. Quantitive comparison of North American and U.K. cooling load calculation procedures—Part 1: Methodology, Part II: Results. ASHRAE Transactions 104(2):36-46, 47-61.
Sun, T.-Y. 1968. Shadow area equations for window overhangs and side-fins and their application in computer calculation. ASHRAE Transactions 74(1):I-1.1 to I-1.9.
Swierczyna, R., P. Sobiski, and D. Fisher. 2008. Revised heat gain and capture and containment exhaust rates from typical commercial cooking appliances (RP-1362). ASHRAE Research Project, Final Report.
Swierczyna, R., P.A. Sobiski, and D.R. Fisher. 2009. Revised heat gain rates from typical commercial cooking appliances from RP-1362. ASHRAE Transactions 115(2):138-160.
Talbert, S.G., L.J. Canigan, and J.A. Eibling. 1973. An experimental study of ventilation requirements of commercial electric kitchens. ASHRAE Transactions 79(1):34.
Walton, G. 1983. Thermal analysis research program reference manual. National Bureau of Standards.
Webster, T., F. Bauman, F. Buhl, and A. Daly. 2008. Modeling of underfloor air distribution (UFAD) systems. SimBuild 2008, University of California, Berkeley.
Wilkins, C.K., and M.R. Cook. 1999. Cooling loads in laboratories. ASHRAE Transactions 105(1):744-749.
Wilkins, C.K., and M.H. Hosni. 2000. Heat gain from office equipment. ASHRAE Journal 42(6):33-44.
Wilkins, C.K., and M. Hosni. 2011. Plug load design factors. ASHRAE Journal 53(5):30-34.
Wilkins, C.K., and N. McGaffin. 1994. Measuring computer equipment loads in office buildings. ASHRAE Journal 36(8):21-24.
Wilkins, C.K., R. Kosonen, and T. Laine. 1991. An analysis of office equipment load factors. ASHRAE Journal 33(9):38-44.
Zhou, X., S.J. Lochhead, Z. Zhong, and C.V. Huynh. 2016. Low energy LED lighting heat distribution in buildings. ASHRAE Research Project RP-1681, Final Report.
Alereza, T., and J.P. Breen, III. 1984. Estimates of recommended heat gain due to commercial appliances and equipment. ASHRAE Transactions 90(2A):25-58.
ASHRAE. 1975. Procedure for determining heating and cooling loads for computerized energy calculations, algorithms for building heat transfer subroutines.
ASHRAE. 1979. Cooling and heating load calculation manual.
BLAST Support Office. 1991. BLAST user reference. University of Illinois, Urbana–Champaign.
Buffington, D.E. 1975. Heat gain by conduction through exterior walls and roofs—Transmission matrix method. ASHRAE Transactions 81(2):89.
Burch, D.M., B.A. Peavy, and F.J. Powell. 1974. Experimental validation of the NBS load and indoor temperature prediction model. ASHRAE Transactions 80(2):291.
Burch, D.M., J.E. Seem, G.N. Walton, and B.A. Licitra. 1992. Dynamic evaluation of thermal bridges in a typical office building. ASHRAE Transactions 98:291-304.
Butler, R. 1984. The computation of heat flows through multi-layer slabs. Building and Environment 19(3):197-206.
Ceylan, H.T., and G.E. Myers. 1985. Application of response-coefficient method to heat-conduction transients. ASHRAE Transactions 91:30-39.
Chiles, D.C., and E.F. Sowell. 1984. A counter-intuitive effect of mass on zone cooling load response. ASHRAE Transactions 91(2A):201-208.
Chorpening, B.T. 1997. The sensitivity of cooling load calculations to window solar transmission models. ASHRAE Transactions 103(1).
Clarke, J.A. 1985. Energy simulation in building design. Adam Hilger Ltd., Boston.
Davies, M.G. 1996. A time-domain estimation of wall conduction transfer function coefficients. ASHRAE Transactions 102(1):328-208.
Falconer, D.R., E.F. Sowell, J.D. Spitler, and B.B. Todorovich. 1993. Electronic tables for the ASHRAE load calculation manual. ASHRAE Transactions 99(1):193-200.
Harris, S.M., and F.C. McQuiston. 1988. A study to categorize walls and roofs on the basis of thermal response. ASHRAE Transactions 94(2):688-714.
Hittle, D.C. 1981. Calculating building heating and cooling loads using the frequency response of multilayered slabs, Ph.D. dissertation, Department of Mechanical and Industrial Engineering, University of Illinois, Urbana–Champaign.
Hittle, D.C., and R. Bishop. 1983. An improved root-finding procedure for use in calculating transient heat flow through multilayered slabs. International Journal of Heat and Mass Transfer 26:1685-1693.
Kimura and Stephenson. 1968. Theoretical study of cooling loads caused by lights. ASHRAE Transactions 74(2):189-197.
Kusuda, T. 1969. Thermal response factors for multilayer structures of various heat conduction systems. ASHRAE Transactions 75(1):246.
Mast, W.D. 1972. Comparison between measured and calculated hour heating and cooling loads for an instrumented building. ASHRAE Symposium Bulletin 72(2).
McBridge, M.F., C.D. Jones, W.D. Mast, and C.F. Sepsey. 1975. Field validation test of the hourly load program developed from the ASHRAE algorithms. ASHRAE Transactions 1(1):291.
Mitalas, G.P. 1968. Calculations of transient heat flow through walls and roofs. ASHRAE Transactions 74(2):182-188.
Mitalas, G.P. 1969. An experimental check on the weighting factor method of calculating room cooling load. ASHRAE Transactions 75(2):22.
Mitalas, G.P. 1972. Transfer function method of calculating cooling loads, heat extraction rate, and space temperature. ASHRAE Journal 14(12):52.
Mitalas, G.P. 1973. Calculating cooling load caused by lights. ASHRAE Transactions 75(6):7.
Mitalas, G.P. 1978. Comments on the Z-transfer function method for calculating heat transfer in buildings. ASHRAE Transactions 84(1):667-674.
Mitalas, G.P., and J.G. Arsenault. 1970. Fortran IV program to calculate Z-transfer functions for the calculation of transient heat transfer through walls and roofs. Use of Computers for Environmental Engineering Related to Buildings, pp. 633-668. National Bureau of Standards, Gaithersburg, MD.
Mitalas, G.P., and K. Kimura. 1971. A calorimeter to determine cooling load caused by lights. ASHRAE Transactions 77(2):65.
Mitalas, G.P., and D.G. Stephenson. 1967. Room thermal response factors. ASHRAE Transactions 73(2):III.2.1.
Nevins, R.G., H.E. Straub, and H.D. Ball. 1971. Thermal analysis of heat removal troffers. ASHRAE Transactions 77(2):58-72.
NFPA. 2012. Health care facilities code. Standard 99-2012. National Fire Protection Association, Quincy, MA.
Ouyang, K., and F. Haghighat. 1991. A procedure for calculating thermal response factors of multi-layer walls—State space method. Building and Environment 26(2):173-177.
Peavy, B.A. 1978. A note on response factors and conduction transfer functions. ASHRAE Transactions 84(1):688-690.
Peavy, B.A., F.J. Powell, and D.M. Burch. 1975. Dynamic thermal performance of an experimental masonry building. NBS Building Science Series 45 (July).
Romine, T.B., Jr. 1992. Cooling load calculation: Art or science? ASHRAE Journal, 34(1):14.
Rudoy, W. 1979. Don’t turn the tables. ASHRAE Journal 21(7):62.
Rudoy, W., and F. Duran. 1975. Development of an improved cooling load calculation method. ASHRAE Transactions 81(2):19-69.
Seem, J.E., S.A. Klein, W.A. Beckman, and J.W. Mitchell. 1989. Transfer functions for efficient calculation of multidimensional transient heat transfer. Journal of Heat Transfer 111:5-12.
Sowell, E.F., and D.C. Chiles. 1984a. Characterization of zone dynamic response for CLF/CLTD tables. ASHRAE Transactions 91(2A):162-178.
Sowell, E.F., and D.C. Chiles. 1984b. Zone descriptions and response characterization for CLF/CLTD calculations. ASHRAE Transactions 91(2A): 179-200.
Spitler, J.D. 1996. Annotated guide to load calculation models and algorithms. ASHRAE.
Spitler, J.D., F.C. McQuiston, and K.L. Lindsey. 1993. The CLTD/SCL/CLF cooling load calculation method. ASHRAE Transactions 99(1): 183-192.
Spitler, J.D., and F.C. McQuiston. 1993. Development of a revised cooling and heating calculation manual. ASHRAE Transactions 99(1):175-182.
Stephenson, D.G. 1962. Method of determining non-steady-state heat flow through walls and roofs at buildings. Journal of the Institution of Heating and Ventilating Engineers 30:5.
Stephenson, D.G., and G.P. Mitalas. 1967. Cooling load calculation by thermal response factor method. ASHRAE Transactions 73(2):III.1.1.
Stephenson, D.G., and G.P. Mitalas. 1971. Calculation of heat transfer functions for multi-layer slabs. ASHRAE Transactions 77(2):117-126.
Sun, T.-Y. 1968. Computer evaluation of the shadow area on a window cast by the adjacent building. ASHRAE Journal (September).
Todorovic, B. 1982. Cooling load from solar radiation through partially shaded windows, taking heat storage effect into account. ASHRAE Transactions 88(2):924-937.
Todorovic, B. 1984. Distribution of solar energy following its transmittal through window panes. ASHRAE Transactions 90(1B):806-815.
Todorovic, B. 1987. The effect of the changing shade line on the cooling load calculations. In ASHRAE videotape, Practical applications for cooling load calculations.
Todorovic, B. 1989. Heat storage in building structure and its effect on cooling load; Heat and mass transfer in building materials and structure. Hemisphere Publishing, New York.
Todorovic, B., and D. Curcija. 1984. Calculative procedure for estimating cooling loads influenced by window shading, using negative cooling load method. ASHRAE Transactions 2:662.
Todorovic, B., L. Marjanovic, and D. Kovacevic. 1993. Comparison of different calculation procedures for cooling load from solar radiation through a window. ASHRAE Transactions 99(2):559-564.
Wilkins, C.K. 1998. Electronic equipment heat gains in buildings. ASHRAE Transactions 104(1B):1784-1789.
York, D.A., and C.C. Cappiello. 1981. DOE-2 engineers manual (Version 2.1A). Lawrence Berkeley Laboratory and Los Alamos National Laboratory.