Mass Transfer Coefficient
Convective mass transfer is analogous to convective heat transfer where geometry and boundary conditions are similar. The analogy holds for both laminar and turbulent flows and applies to both external and internal flow problems.
Mass Transfer Coefficients for External Flows. Most external convective mass transfer problems can be solved with an appropriate formulation that relates the mass transfer flux (to or from an interfacial surface) to the concentration difference across the boundary layer illustrated in Figure 5. This formulation gives rise to the convective mass transfer coefficient, defined as
where
| hM |
= |
local external mass transfer coefficient, m/s |
|
= |
mass flux of gas B from surface, kg/(m2 · s) |
| ρBi |
= |
density of gas B at interface (saturation density), kg/m3 |
| ρB∞ |
= |
density of component B outside boundary layer, kg/m3 |
If ρBi and ρB∞ are constant over the entire interfacial surface, the mass transfer rate from the surface can be expressed as
where h̅M is the average mass transfer coefficient, defined as
Mass Transfer Coefficients for Internal Flows. Most internal convective mass transfer problems, such as those that occur in channels or in the cores of dehumidification coils, can be solved if an appropriate expression is available to relate the mass transfer flux (to or from the interfacial surface) to the difference between the concentration at the surface and the bulk concentration in the channel, as shown in Figure 6. This formulation leads to the definition of the mass transfer coefficient for internal flows:
where
| hM |
= |
internal mass transfer coefficient, m/s |
|
= |
mass flux of gas B at interfacial surface, kg/(m2 · s) |
| ρBi |
= |
density of gas B at interfacial surface, kg/m3 |
| ρBb ≡ (1/u̅BAcs) ∫Acs uB ρB dAcs) |
= |
bulk density of gas B at location x |
| u̅B ≡ (1/Acs) ∫A uB dAcs |
= |
average velocity of gas B at location x, m/s |
| Acs |
= |
cross-sectional area of channel at station x, m2 |
| uB |
= |
velocity of component B in x direction, m/s |
| ρB |
= |
density distribution of component B at station x, kg/m3 |
Often, it is easier to obtain the bulk density of gas B from
where
| ṁBo |
= |
mass flow rate of component B at station x = 0, kg/s |
| A |
= |
interfacial area of channel between station x = 0 and station x = x, m2 |
Equation (28) can be derived from the preceding definitions. The major problem is determining u̅B. If, however, analysis is restricted to cases where B is dilute and concentration gradients of B in the x direction are negligibly small, u̅B ≈ u̅. Component B is swept along in the x direction with an average velocity equal to the average velocity of the dilute mixture.
Analogy Between Convective Heat and Mass Transfer
Most expressions for the convective mass transfer coefficient hM are determined from expressions for the convective heat transfer coefficient h.
For problems in internal and external flow where mass transfer occurs at the convective surface and where component B is dilute, Bird et al. (1960) and Incropera and DeWitt (1996) found that the Nusselt and Sherwood numbers are defined as follows:
and
where f in Equations (31) and (32) indicates a functional relationship among the dimensionless groups shown. The function f is the same in both equations. Similarly, g indicates a functional relationship that is the same in Equations (33) and (34). Pr and Sc are dimensionless Prandtl and Schmidt numbers, respectively, as defined in the Symbols section. The primary restrictions on the analogy are that the surface shapes are the same and that the temperature boundary conditions are analogous to the density distribution boundary conditions for component B when cast in dimensionless form. Several primary factors prevent the analogy from being perfect. In some cases, the Nusselt number was derived for smooth surfaces. Many mass transfer problems involve wavy, droplet-like, or roughened surfaces. Many Nusselt number relations are obtained for constant-temperature surfaces. Sometimes ρBi is not constant over the entire surface because of varying saturation conditions and the possibility of surface dryout.
In all mass transfer problems, there is some blowing or suction at the surface because of condensation, evaporation, or transpiration of component B. In most cases, this blowing/suction has little effect on the Sherwood number, but the analogy should be examined closely if vi/u∞ > 0.01 or vi/u̅ > 0.01, especially if the Reynolds number is large.
Example 5.
Air at 25°C, 100 kPa, and 60% rh flows at 10 m/s, as shown in Figure 7. Find the rate of evaporation, rate of heat transfer to the water, and water surface temperature.
Solution: Heat transfer to water from air supplies the energy required to evaporate the water.
where
| h |
= |
convective heat transfer coefficient |
| hM |
= |
convective mass transfer coefficient |
| A |
= |
0.1 × 1.5 × 2 = 0.3 m2 = surface area (both sides) |
| ṁ |
= |
evaporation rate |
| ts, ρs |
= |
temperature and vapor density at water surface |
| t∞, ρ∞ |
= |
temperature and vapor density of airstream |
This energy balance can be rearranged to give
The heat transfer coefficient h is found by first calculating the Nusselt number:
The mass transfer coefficient hM requires calculation of Sherwood number Sh, obtained using the analogy expressed in Equations (33) and (34):
With Nu and Sh known,
or
This result is valid for both laminar and turbulent flow. Using this result in the preceding energy balance gives
This equation must be solved for ρs. Then, water surface temperature ts is the saturation temperature corresponding to ρs. Air properties Sc, Pr, Dv, and k are evaluated at film temperature tf = (t∞ + ts)/2, and hfg is evaluated at ts. Because ts appears in the right side and all the air properties also vary somewhat with ts, iteration is required. Start by guessing ts = 14°C (the dew point of the airstream), giving tf = 19.5°C. At these temperatures, values on the right side are found in property tables or calculated as
| k |
= |
0.0257 W/(m · K) |
| Pr |
= |
0.709 |
| Dv |
= |
2.521 × 10−5 m2/s [from Equation (10)] |
| ρ |
= |
1.191 kg/m3 |
| μ |
= |
1.809 × 10−5 kg/(m · s) |
| Sc |
= |
μ/ρDv = 0.6025 |
| hfg |
= |
2.455 × 106 J/kg (at 14°C) |
| ρ∞ |
= |
0.01417 kg/m3 (from psychrometric chart at 25°C, 60% rh) |
| ts |
= |
14°C (initial guess) |
Solving yields ρs = 0.01896 kg/m3. The corresponding value of ts = 21.6°C. Repeat the process using ts = 21.6°C as the initial guess. The result is ρs = 0.01565 kg/m3 and ts = 18.3°C. Continue iterations until ρs converges to 0.01663 kg/m3 and ts = 19.4°C.
To solve for the rates of evaporation and heat transfer, first calculate the Reynolds number using air properties at tf = (25 + 19.4)/2 = 22.2°C.
where L = 0.1 m, the length of the plate in the direction of flow. Because ReL < 500 000, flow is laminar over the entire length of the plate; therefore,
The same value for q would be obtained by calculating the Nusselt number and heat transfer coefficient h and setting q = hA (t∞ – ts).
The kind of similarity between heat and mass transfer that results in Equations (31) to (34) can also be shown to exist between heat and momentum transfer. Chilton and Colburn (1934) used this similarity to relate Nusselt number to friction factor by the analogy
where n = 2/3, St = Nu/(Re Pr) is the Stanton number, and jH is the Chilton-Colburn j-factor for heat transfer. Substituting Sh for Nu and Sc for Pr in Equations (33) and (34) gives the Chilton-Colburn j-factor for mass transfer, jD:
where Stm = ShPAm/(Re Sc) is the Stanton number for mass transfer. Equations (35) and (36) are called the Chilton-Colburn j-factor analogy.
The power of the Chilton-Colburn j-factor analogy is represented in Figures 8 to 11. Figure 8 plots various experimental values of jD from a flat plate with flow parallel to the plate surface. The solid line, which represents the data to near perfection, is actually f/2 from Blasius’ solution of laminar flow on a flat plate (left-hand portion of the solid line) and Goldstein’s solution for a turbulent boundary layer (right-hand portion). The right-hand part also represents McAdams’ (1954) correlation of turbulent flow heat transfer coefficient for a flat plate.
A wetted-wall column is a vertical tube in which a thin liquid film adheres to the tube surface and exchanges mass by evaporation or absorption with a gas flowing through the tube. Figure 9 illustrates typical data on vaporization in wetted-wall columns, plotted as jD versus Re. The point spread with variation in μ/ρDv results from Gilliland’s finding of an exponent of 0.56, not 2/3, representing the effect of the Schmidt number. Gilliland’s equation can be written as follows:
Similarly, McAdams’ (1954) equation for heat transfer in pipes can be expressed as
This is represented by the dash-dot curve in Figure 9, which falls below the mass transfer data. The curve f/2, representing friction in smooth tubes, is the upper, solid curve.
Data for liquid evaporation from single cylinders into gas streams flowing transversely to the cylinders’ axes are shown in Figure 10. Although the dash-dot line in Figure 10 represents the data, it is actually taken from McAdams (1954) as representative of a large collection of data on heat transfer to single cylinders placed transverse to airstreams. To compare these data with friction, it is necessary to distinguish between total drag and skin friction. Because the analogies are based on skin friction, normal pressure drag must be subtracted from the measured total drag. At Re = 1000, skin friction is 12.6% of the total drag; at Re = 31 600, it is only 1.9%. Consequently, values of f/2 at a high Reynolds number, obtained by the difference, are subject to considerable error.
In Figure 11, data on evaporation of water into air for single spheres are presented. The solid line, which best represents these data, agrees with the dashed line representing McAdams’ correlation for heat transfer to spheres. These results cannot be compared with friction or momentum transfer because total drag has not been allocated to skin friction and normal pressure drag. Application of these data to air/water-contacting devices such as air washers and spray cooling towers is well substantiated.
When the temperature of the heat exchanger surface in contact with moist air is below the air’s dew-point temperature, vapor condensation occurs. Typically, air dry-bulb temperature and humidity ratio both decrease as air flows through the exchanger. Therefore, sensible and latent heat transfer occur simultaneously. This process is similar to one that occurs in a spray dehumidifier and can be analyzed using the same procedure; however, this is not generally done.
Cooling coil analysis and design are complicated by the problem of determining transport coefficients h, hM, and f. It would be convenient if heat transfer and friction data for dry heating coils could be used with the Colburn analogy to obtain the mass transfer coefficients, but this approach is not always reliable, and Guillory and McQuiston (1973) and Helmer (1974) show that the analogy is not consistently true. Figure 12 shows j-factors for a simple parallel-plate exchanger for different surface conditions with sensible heat transfer. Mass transfer j-factors and friction factors exhibit the same behavior. Dry-surface j-factors fall below those obtained under dehumidifying conditions with the surface wet. At low Reynolds numbers, the boundary layer grows quickly; the droplets are soon covered and have little effect on the flow field. As the Reynolds number increases, the boundary layer becomes thin and more of the total flow field is exposed to the droplets. Roughness caused by the droplets induces mixing and larger j-factors.
The data in Figure 12 cannot be applied to all surfaces, because the length of the flow channel is also an important variable. However, water collecting on the surface is mainly responsible for breakdown of the j-factor analogy. The j-factor analogy is approximately true when surface conditions are identical. Under some conditions, it is possible to obtain a film of condensate on the surface instead of droplets. Guillory and McQuiston (1973) and Helmer (1974) related dry sensible j- and f-factors to those for wetted dehumidifying surfaces.
The equality of jH, jD, and f/2 for certain streamlined shapes at low mass transfer rates has experimental verification. For flow past bluff objects, jH and jD are much smaller than f/2, based on total pressure drag. The heat and mass transfer, however, still relate in a useful way by equating jH and jD.
Example 6.
Using solid cylinders of volatile solids (e.g., naphthalene, camphor, dichlorobenzene) with airflow normal to these cylinders, Bedingfield and Drew (1950) found that the ratio between the heat and mass transfer coefficients could be closely correlated by the following relation:
For completely dry air at 21°C flowing at a velocity of 9.5 m/s over a wet-bulb thermometer of diameter d = 7.5 mm, determine the heat and mass transfer coefficients from Figure 10 and compare their ratio with the Bedingfield-Drew relation.
Solution: For dry air at 21°C and standard pressure, ρ = 1.198 kg/m3, μ = 1.82 × 10−5 kg/(s · m), k = 0.02581 W/(m · K), and cp = 1.006 kJ/ (kg · K). From Equation (10), Dv = 25.13 mm2/s. Therefore,
From Figure 10 at Reda = 4700, read jH = 0.0089, and jD = 0.010. From Equations (35) and (36),
From the Bedingfield-Drew relation,
Equations (36) and (37) are called the Reynolds analogy when Pr = Sc = 1. This suggests that h/ρhM = cp = 1006 J/(kg · K). This close agreement is because the ratio Sc/Pr is 0.605/0.709 or 0.85, so that the exponent of these numbers has little effect on the ratio of the transfer coefficients.
The extensive developments for calculating heat transfer coefficients can be applied to calculate mass transfer coefficients under similar geometrical and flow conditions using the j-factor analogy. For example, Table 8 of Chapter 4 lists equations for calculating heat transfer coefficients for flow inside and normal to pipes. Each equation can be used for mass transfer coefficient calculations by equating jH and jD and imposing the same restriction to each stated in Table 8 of Chapter 4. Similarly, mass transfer experiments often replace corresponding heat transfer experiments with complex geometries where exact boundary conditions are difficult to model (Sparrow and Ohadi 1987a, 1987b).
The j-factor analogy is useful only at low mass transfer rates. As the rate increases, the movement of matter normal to the transfer surface increases the convective velocity. For example, if a gas is blown from many small holes in a flat plate placed parallel to an airstream, the boundary layer thickens, and resistance to both mass and heat transfer increases with increasing blowing rate. Heat transfer data are usually collected at zero or, at least, insignificant mass transfer rates. Therefore, if such data are to be valid for a mass transfer process, the mass transfer rate (i.e., the blowing) must be low.
The j-factor relationship jH = jD can still be valid at high mass transfer rates, but neither jH nor jD can be represented by data at zero mass transfer conditions. Chapter 24 of Bird et al. (1960) and Eckert and Drake (1972) have detailed information on high mass transfer rates.
Heat and mass transfer coefficients are satisfactorily related at the same Reynolds number by equating the Chilton-Colburn j-factors. Comparing Equations (35) and (36) gives
Inserting the definitions of St, Pr, Stm, and Sc gives
or
The quantity α/Dv is the Lewis number Le. Its magnitude expresses relative rates of propagation of energy and mass within a system. It is fairly insensitive to temperature variation. For air and water vapor mixtures, the ratio is (0.60/0.71) or 0.845, and (0.845)2/3 is 0.894. At low diffusion rates, where the heat/mass transfer analogy is valid, PAm is essentially unity. Therefore, for air and water vapor mixtures,
The ratio of the heat transfer coefficient to the mass transfer coefficient equals the specific heat per unit volume of the mixture at constant pressure. This relation [Equation (40)] is usually called the Lewis relation and is nearly true for air and water vapor at low mass transfer rates. It is generally not true for other gas mixtures because the ratio Le of thermal to vapor diffusivity can differ from unity. Agreement between wet-bulb temperature and adiabatic saturation temperature is a direct result of the nearness of the Lewis number to unity for air and water vapor.
The Lewis relation is valid in turbulent flow whether or not α/Dv equals 1 because eddy diffusion in turbulent flow involves the same mixing action for heat exchange as for mass exchange, and this action overwhelms any molecular diffusion. Deviations from the Lewis relation are, therefore, caused by a laminar boundary layer or a laminar sublayer and buffer zone where molecular transport phenomena are the controlling factors.