CHAPTER 22. PIPE DESIGN

 

This chapter discusses pipe systems, materials, design, installation, supports, stress calculations, pipe expansion and flexibility, bends and loops, and application of pipe systems commonly used for heating, air conditioning, refrigeration, and service water. When selecting and applying components; applicable local codes, state or provincial codes, and voluntary industry standards (some of which have been adopted by code jurisdictions) must be followed. Further details on specific piping systems can be found in application-specific chapters of the ASHRAE Handbook.

1. FUNDAMENTALS

1.1 CODES AND STANDARDS

The following organizations in the United States issue codes and standards for piping systems and components:

ASME

American Society of Mechanical Engineers

ASTM

American Society for Testing and Materials

NFPA

National Fire Protection Association

ICC

International Code Council

MSS

Manufacturers Standardization Society of the Valve and Fittings Industry, Inc.

AWWA

American Water Works Association

Parallel federal specifications also have been developed by government agencies and are used for many public works projects. Chapter IV of ASME Standard B31.9 lists applicable U.S. codes and standards for HVAC piping. In addition, it gives requirements for safe design and construction of piping systems for building heating and air conditioning. ASME Standard B31.5 gives similar requirements for refrigerant piping.

1.2 DESIGN CONSIDERATIONS

Pipes are conduits in which fluids [compressible (e.g., air, steam) and noncompressible (e.g., water)] flow in a system, in response to a pressure differential. Piping system designers should assess the following aspects:

  • Code requirements.

  • Load: the amount of energy or fluid to be moved through the pipe to where it is needed; determination of load is not covered in this chapter (see Chapters 16 to 18 for information on load calculations).

  • Working fluid and fluid properties in the pipe.

  • Pressure and temperature of the fluid.

  • External environment of the pipe: outdoor installations deal with temperature extremes, environmental contaminants, and ultraviolet radiation. Other environments could contain caustic chemicals. Soil can contain elements that can be corrosive to underground pipe systems.

  • Installation cost.

  • Pipe’s resistance to chemical attack from the fluid.

When designing a fluid flow system, two related but distinct concerns emerge: sizing the pipe and determining the flow/pressure relationship. The two are often confused because they can use the same equations and design tools. Nevertheless, they should be determined separately.

This chapter focuses on sizing the pipe during the design phase, and to this end presents design charts and tables for specific fluids in addition to the equations that describe fluid flow in pipes. Once a system has been sized, it should be analyzed with more detailed methods of calculation to determine the pump head, if applicable, required to achieve the desired flow. Computerized methods are well suited to handling the details of calculating losses around an extensive system.

Not discussed in detail in this chapter, but of potentially great importance, are physical and chemical considerations such as pipe and fitting design; materials; and joining methods appropriate for working pressures and temperatures encountered, as well as resistance to chemical attack by the fluid. For more information, see Eshbach (2009), Heald (2002), and Nayyar (1999).

For fluids not included in this chapter or for piping materials of different dimensions, manufacturers’ literature frequently supplies pressure drop charts. The Darcy-Weisbach equation, with the Moody chart or Colebrook equation, can be used as an alternative to pressure drop charts or tables.

1.3 GENERAL PIPE SYSTEMS

 Metallic Pipe Systems

Each HVAC system and, under some conditions, portions of a system require a study of the conditions of operation to determine suitable materials. For example, because the static pressure of water in a high-rise building is higher in the lower levels than in the upper levels, a heavier pipe or different materials may be required for different vertical zones.

Table 1 lists some typical systems and materials used for heating and air-conditioning metallic piping. The list is not all inclusive, because piping systems are constantly being developed. The pressure and temperature rating of each component selected must be considered; the lowest rating establishes the operating limits of the system.

Table 1 Common Applications of Pipe, Fittings, and Valves for Heating and Air Conditioning

Application

Size, in.

Material

Weight

Joint Type

Fitting Material

Class (When Applicable)

Systemg

Temperature, °F

Maximum Pressure at Temperature,a,bpsi

Chilled water

≤2

Steel Type F (CW)

Schedule 40

Thread

Cast iron

125

250

125

2.5 to 12

Steel A or B, Type E (ERW)

Schedule 40

Weld

Wrought steel

Standard

250

400

Flange

Wrought steel

150

250

250

     

Cast iron

125

250

175

       

Cast iron

250

250

400

 

Copper, hard or soft

Type K or L

Solder

Wrought or cast Cu

 

100

370 Type K soft

     

Flared (soft)

     

635 Type K hard

     

Rolled groove (2 to 8 in.)

     

250 Type L soft

     

Press-connect (0.5 to 4 in.)

     

435 Type L hard

     

Push connect (0.5 to 2 in.)

       
     

Mechanical formed

       
     

Braze

Wrought or cast Cu

 

100

250 Type L soft

     

Weld

     

370 Type K soft

 

Copper, hard

Type M

Solder

Wrought or cast Cu

 

100

395 Type M hard

     

Rolled groove (2 to 8 in.)

       
     

Press-connect (0.5 to 4 in.)

       
     

Push connect (0.5 to 2 in.)

       
     

Mechanical formed

       
     

Braze

Wrought or cast Cu

 

100

230 Type M soft

     

Weld

       

0.375 to 1.0

PEX (barrier)

SDR-9

Crimp

Bronze

 

73

145

   

Clamp

Brass

     
     

Expansion

Copper

     
     

Compression

Engineered plastic

     
     

Push fit

       
     

Proprietary

       

0.5 to 6

PE

Schedule 40,f 80, SDR

Thermal fusion, compression

PE

 

120 (140 limit for some applications)

Varies with pipe wall thickness, grade, schedule, size. Check manufacturer’s documentation for design ratings 30 to 110 at 130°F

Heating and recirculating

2 and smaller

0.25 to 12

Steel Type F (CW)

Schedule 40

Thread

Cast iron

125

250

125

Steel B Type E (ERW)

Schedule 40

Weld

Wrought steel

Standard

250

400

 

Flange

Wrought steel

150

250

250

     

Cast iron

125

250

125

     

Cast iron

250

250

400

   

Copper, hard or soft

Type K or L

Solder

Wrought or cast Cu

 

200

300 Type K soft

       

Braze

     

635 Type K hard

       

Flared (soft)

     

205 Type L soft

       

Rolled groove (2 to 8 in.)

     

435 Type L hard

       

Press-connect (0.5 to 4 in.)

       
       

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
       

Braze

Wrought or cast Cu

 

200

300 Type K soft

       

Weld

     

205 Type L soft

 

0.25 to 12

Copper, hard

Type M

Solder

Wrought or cast Cu

 

200

395 Type M hard

     

Rolled groove (2 to 8 in.)

       
       

Press-connect (0.5 to 4 in.)

       
       

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
       

Braze

Wrought or cast Cu

 

200

200 Type M soft

       

Weld

       
 

0.375 to 1.0

PEX (barrier)

SDR-9

Crimp

Bronze

 

200

79

     

Clamp

Brass

     
       

Expansion

Copper

     
       

Compression

Engineered plastic

     
       

Push fit

       
       

Proprietary

       

Steam and condensate

2 and smaller

Steel Type F (CW) or S

Schedule 40d

Thread

Cast iron

125

 

90

 

Thread

Malleable iron

150

 

90

       

Socket

Forged steel

3000

 

90

   

Steel B Type E (ERW) or S

Schedule 40d

Thread

Cast iron

125

 

100

     

Thread

Malleable iron

150

 

125

       

Socket

Forged steel

3000

 

400

   

Steel B Type E (ERW) or S

Schedule 80

Thread

Cast iron

250

 

200

     

Socket

       
       

Thread

Malleable iron

300

 

250

       

Socket

Forged steel

3000

 

400

 

2 to 12

Steel B Type E (ERW) or S

Schedule 40

Weld

Wrought steel

Standard

 

250

   

Flange

Wrought steel

150

 

200

         

Cast iron

125

 

100

   

Steel B Type E (ERW) or S

Schedule 80

Weld

Wrought steel

XS

 

700

     

Flange

Wrought steel

300

 

500

         

Cast iron

250

 

200

Ground-source heat pump

0.25 to 2

Copper, hard or soft

Type L or ACR

Flared or brazed

Wrought or cast Cu

 

200

205 Type L soft, 435 Type L hard, 240 ACR soft, 500 ACR hard

0.375 to 1.0

PEX (barrier)

SDR-9

Crimp

Bronze

 

180

100

   

Clamp

Brass

     
       

Expansion

Copper

     
       

Compression

Engineered plastic

     
       

Push fit

       
       

Proprietary

       

Refrigerant

 

Steel B Type E (ERW)

Schedule 40

Weld

   

Wrought steel

 

0.375 to 4.125

Copper, hard

Type L or ACR

Braze

Wrought or Forged Cu

 

200

435 Type L hard, 240 ACR soft

Natural gas and LP

0.25 to 12

Copper, hard or soft

Type K or L

Solder

Wrought or cast Cu

 

100

370 Type K soft

   

Rolled groove (2 to 8 in.)

     

635 Type K hard

       

Press-connect (0.5 to 4 in.)

     

250 Type L soft

       

Push connect (0.5 to 2 in.)

     

435 Type L hard

       

Mechanically formed

       
       

Braze

Wrought or cast Cu

 

100

370 Type K soft

       

Weld

     

250 Type L soft

 

0.375 to 4.125

Copper, hard

ACR

Solder

Wrought or cast Cu

 

100

500 Type ACR hard

     

Braze

Wrought or cast Cu

 

100

290 Type ACR Soft

 

0.375 to 1.0

PEX

SDR-9

Crimp

Bronze

 

73

145

     

Clamp

Brass

     
       

Expansion

Copper

     
       

Compression

Engineered plastic

     
       

Push fit

       
       

Proprietary

       
 

0.5 to 6

PE

Schedule 40, 80, SDR

Thermal fusion, compression

PE

 

120 (140limit for some applications)

Depends on pipe, grade, schedule, size. Generally 30 to 110 at 130°F

 

0.5 to 6

HDPE

SDR

Thermal fusion, compression

HDPE

 

120

Depends on pipe, grade, schedule, size. Generally 64 for SDR 11 at 120°F

Fuel oil, aboveground

2 to 12

Black Steel, B Type E (ERW) or S (seamless)

Schedule 40

Thread or weld

Black malleable iron

150

   
   

Wrought steel weld

     
   

Forged steel flanges

150

   
 

0.25 to 12

Copper, hard or soft

Type K or L

Solder

Wrought or cast Cu

 

100

300 Type K soft

   

Flared (soft)

     

635 Type K hard

       

Rolled groove (2 to 8 in.)

     

250 Type L soft

       

Press-connect (0.5 to 4 in.)

     

435 Type L hard

       

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
       

Braze or weld

Wrought or cast Cu

 

100

300 Type K soft, 250 Type L soft

   

Copper, hard

Type M

Solder

Wrought or cast Cu

 

100

395 Type M hard

       

Braze

       
       

Rolled groove (2 to 8 in.)

       
       

Press-connect (0.5 to 4 in.)

       
       

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
 

0.25 to 12

ABS

Schedule 40,f 80, SDR

Solvent weld, thread, flange

ABS

 

160 limit

Depends on pipe class: approximately 50 at 160°F

 

0.5 to 6

HDPE

SDR-9

Thermal fusion, compression

HDPE

 

120

Depends on pipe, grade, schedule, size. Generally 64 for SDR 11 at 120°F

Compressed air

≤2.5 and smaller

Black steel

Schedule 40

Thread

Black malleable iron

150

350

 

>2.5

Black steel

Schedule 40

Flange or weld

Black malleable iron

150

350

 
 

0.375 to 4.125

Copper, hard

ACR

Solder

Wrought or cast Cu

 

200

240 ACR soft

     

Flared (soft)

     

500 ACR hard

       

Mechanical formed

       
       

Braze

   

200

240 ACR hard

 

0.5 to 4

ABS

Schedule 40

Solvent weld

ABS

 

73

185

 

HDPE

Schedule 40, 80, SDR

 

HDPE

     
 

0.375 to 1.0

PEX

SDR-9

         

Potable water, inside building

0.25 to 12

Steel, galvanized

Schedule 40

Thread

Galv. cast iron

150

100

125

   

Galv. cast iron

150

100

150

 

Copper, hard or soft

Type K or L

Solderc

Wrought or cast Cu

 

100

370 Type K soft

   

Flared (soft)

     

635 Type K hard

     

Rolled groove (2 to 8 in.)

     

250 Type L soft

     

Press-connect (0.5 to 4 in.)

     

435 Type L hard

       

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
       

Braze

Wrought or cast Cu

 

100

370 Type K soft

       

Weld

     

250 Type L soft

 

0.25 to 12

Copper, hard

Type M

Solderc

Wrought or cast Cu

 

100

395 Type M hard

     

Rolled groove (2 to 8 in.)

       
       

Press-connect (0.5 to 4 in.)

       
       

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
       

Braze

Wrought or cast Cu

 

100

230 Type M soft

       

Weld

       
 

0.5 to 8

CPVC

Schedule 40,f 80

 

CPVC

 

210 Limit, 200 operating

 
 

0.375 to 1.0

PEX

SDR-9

Crimp

Bronze

 

100

145

     

Clamp

Brass

     
       

Expansion

Copper

     
       

Compression

Engineered plastic

     
       

Push fit

       
       

Proprietary

       
 

0.5 to 6

PE

Schedule 40,f 80, SDR

Thermal fusion, compression

PE

 

120 (140 limit for some applications)

Depends on pipe, grade, schedule, size generally 30 to 110 at 130°F

 

0.5 to 6

PP

Schedule 40,f 80, SDR

Thermal fusion, flange, Threade

PP

 

180

50

Water services, underground

Through 6

Ductile iron

Class 50

Mechanical joint

Cast iron

 

75

250

0.25 to 12

Copper, hard or soft

Type K or L

Solderc

Wrought or cast Cu

 

100

370 Type K soft

 

Flared (soft)

     

635 Type K hard

     

Rolled groove (2 to 8 in.)

     

250 Type L soft

     

Press-connect (0.5 to 4 in.)

     

435 Type L hard

     

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
       

Braze

Wrought or cast Cu

 

100

370 Type K soft

       

Weld

     

250 Type L soft

       

Flange

Bronze

 

100

 
 

0.25 to 12

Copper, hard

Type M

Solderc

Wrought or cast Cu

 

100

395 Type K hard

     

Rolled groove (2 to 8 in.)

       
       

Press-connect (0.5 to 4 in.)

       
       

Push connect (0.5 to 2 in.)

       
       

Mechanical formed

       
       

Braze

Wrought or cast Cu

 

100

230 Type M soft

       

Weld

       
 

0.375 to 1.0

PEX

SDR-9

Crimp

Bronze

 

73

145

     

Clamp

Brass

     
       

Expansion

Copper

     
       

Compression

Engineered plastic

     
       

Push fit

       
       

Proprietary

       
 

0.25 to 20

PVC

Schedule 40, 80, 120, SDR

Solvent weld, thread,f thermal weld

PVC

 

150 limit, 140 operating

79 to 105, depending on schedule and size

Drainage, waste, and vent (DWV)

1.25 to 8

Copper, hard

DWV

Solder

Wrought or cast Cu

 

100

250 DWV hard

1.25 to 12

ABS

Schedule DWV, 40,f 80, SDR

Solvent weld, thread, flange

ABS

 

160 limit

Depends on pipe class: approximately 50 at 160°F

1.25 to 20

PV

Schedule 40,f 80, 120, SDR

Solvent weld, thread, thermal weld

PVC

 

150 limit, 140 operating

79 to 105, depending on schedule and size

a Maximum allowable working pressures have been derated in this table. Higher system pressures can be used for lower temperatures and smaller pipe sizes. Pipe, fittings, joints, and valves must all be considered.

b Temperature and pressure relationships can vary based on pipe material composition, size, class, and schedule.

c Lead- and antimony-based solders are prohibited for potable water systems. Brazing should be used.

d Piping codes typically require thicker-walled pipe for threaded joints to maintain corrosion allowance and pressure ratings.

e All plumbing codes require both hot and cold water piping to have a 100 psi at 180°F rating.

f Threads are not recommended on Schedule 40 plastic pipe.

g Designer should confirm that all materials are suitably rated for intended operation.


Table 2 Manufacturers’ Recommendationsa,b for Plastic Materials

 

PVC

CPVC

HDPE

PEX

PP

ABS

PVDF

RTRP

Cold-water service

R

R

R

R

R

R

R

R

Hot (140°F) water

N

R

R

R

R

R

R

R

Potable-water service

R

R

R

R

R

R

R

R

Drain, waste, and vent (DWV)

R

R

R

R

Demineralized water

R

R

R

R

R

Deionized water

R

R

R

R

R

R

Salt water

R

R

R

R

R

R

R

Heating (200°F) hot water

N

N

N

N

N

N

R

Natural gas

N

N

R

R

N

N

Compressed air

N

N

R

R

N

R

Sunlight and weather resistance

N

N

R

R

R

R

R

Underground service

R

R

R

R

R

R

R

Food handling

R

R

R

R

R

R

R = Recommended

N = Not recommended

— = Insufficient information

a Before selecting material, check availability of suitable range of sizes and fittings and of satisfactory joining method. Also have manufacturer verify the best material for purpose intended.

b Consult local building codes for compliance of materials listed.


 Nonmetallic (Plastic) Pipe Systems

Nonmetallic pipe is used in HVAC and plumbing. Plastic is light, generally inexpensive, and corrosion resistant. Plastic also has a low “C” factor (i.e., its surface is very smooth), resulting in lower pumping power requirements and smaller pipe sizes. Plastic pipe’s disadvantages include rapid loss of strength at temperatures above ambient and a high coefficient of linear expansion. The modulus of elasticity of plastics is low, resulting in a short support span. Some jurisdictions do not allow certain plastics in buildings because of toxic products emitted during fires. Plenum-rated plastic and insulation may be used to achieve a plenum rating; check with the authority having jurisdiction (AHJ).

Table 2 lists nonmetallic materials used for service water and heating and air-conditioning piping. The pressure and temperature rating of each component selected must be considered; the lowest rating establishes the operating limits of the system.

 Special Systems

Some piping systems are governed by separate codes or standards. Generally, any failure of the piping in these systems is dangerous to the public, so some local areas have adopted laws enforcing the codes, such as the following:

  • Boiler piping: ASME Standard B31.1 and the ASME Boiler and Pressure Vessel Code (Section I) specify piping inside code-required stop valves on boilers that operate above 15 psig with steam, or above 160 psig or 250°F with water. These codes require fabricators and contractors to be certified for such work. The field or shop work must also be inspected while it is in progress, by inspectors commissioned by the National Board of Boiler and Pressure Vessel Inspectors.

  • Refrigeration piping: ASHRAE Standard 15 and ASME Standard B31.5.

  • Plumbing systems: Local codes.

  • Sprinkler systems: NFPA Standard 13.

  • Fuel gas: NFPA Standard 54/ANSI Standard Z223.1.

1.4 DESIGN EQUATIONS

 Darcy-Weisbach Equation

Pressure drop caused by fluid friction in fully developed flows of all well-behaved (Newtonian) fluids is described by the Darcy-Weisbach equation:

(1)

where

Δp = pressure drop, lbf/ft2
f = friction factor, dimensionless (from Moody chart, Figure 13 in Chapter 3)
L = length of pipe, ft
D = internal diameter of pipe, ft
ρ = fluid density at mean temperature, lbm/ft3
V = average velocity, fps
gc = units conversion factor, 32.2 ft · lbm/lbf · s2

Close-Coupled Test Configurations

Figure 1. Close-Coupled Test Configurations


This equation is often presented in head or specific energy form as

(2)

where

Δh = head loss, ft
g = acceleration of gravity, ft/s2

In this form, the fluid’s density does not appear explicitly (although it is in the Reynolds number that influences f).

The friction factor f is a function of pipe roughness ε, inside diameter D, and parameter Re, the Reynolds number:

(3)

where

Re = Reynolds number, dimensionless
ε = absolute roughness of pipe wall, ft
μ = dynamic viscosity of fluid, lbm/ft · s

The friction factor is frequently presented on a Moody chart (Figure 13 in Chapter 3) giving f as a function of Re with ε/D as a parameter.

A useful fit of smooth and rough pipe data for the usual turbulent flow regime is the Colebrook equation:

(4)

Table 3 K Factors: Threaded Steel Pipe Fittings

Nominal Pipe Dia., in.

90° Standard Elbow

90° Long-Radius Elbow

45° Elbow

Return Bend

Tee-Line

Tee-Branch

Globe Valve

Gate Valve

Angle Valve

Swing Check Valve

Bell Mouth Inlet

Square Inlet

Projected Inlet

3/8

2.5

0.38

2.5

0.90

2.7

20

0.40

8.0

0.05

0.5

1.0

1/2

2.1

0.37

2.1

0.90

2.4

14

0.33

5.5

0.05

0.5

1.0

3/4

1.7

0.92

0.35

1.7

0.90

2.1

10

0.28

6.1

3.7

0.05

0.5

1.0

1

1.5

0.78

0.34

1.5

0.90

1.8

9

0.24

4.6

3.0

0.05

0.5

1.0

1 1/4

1.3

0.65

0.33

1.3

0.90

1.7

8.5

0.22

3.6

2.7

0.05

0.5

1.0

1 1/2

1.2

0.54

0.32

1.2

0.90

1.6

8

0.19

2.9

2.5

0.05

0.5

1.0

2

1.0

0.42

0.31

1.0

0.90

1.4

7

0.17

2.1

2.3

0.05

0.5

1.0

2 1/2

0.85

0.35

0.30

0.85

0.90

1.3

6.5

0.16

1.6

2.2

0.05

0.5

1.0

3

0.80

0.31

0.29

0.80

0.90

1.2

6

0.14

1.3

2.1

0.05

0.5

1.0

4

0.70

0.24

0.28

0.70

0.90

1.1

5.7

0.12

1.0

2.0

0.05

0.5

1.0

Source: Engineering Data Book (Hydraulic Institute 1990).


Table 4 K Factors: Flanged Welded Steel Pipe Fittings

Nominal Pipe Dia., in.

90° Standard Elbow

90° Long-Radius Elbow

45° Long- Radius Elbow

Return Bend Standard

Return Bend Long-Radius

Tee-Line

Tee-Branch

Globe Valve

Gate Valve

Angle Valve

Swing Check Valve

1

0.43

0.41

0.22

0.43

0.43

0.26

1.0

13

4.8

2.0

1 1/4

0.41

0.37

0.22

0.41

0.38

0.25

0.95

12

3.7

2.0

1 1/2

0.40

0.35

0.21

0.40

0.35

0.23

0.90

10

3.0

2.0

2

0.38

0.30

0.20

0.38

0.30

0.20

0.84

9

0.34

2.5

2.0

2 1/2

0.35

0.28

0.19

0.35

0.27

0.18

0.79

8

0.27

2.3

2.0

3

0.34

0.25

0.18

0.34

0.25

0.17

0.76

7

0.22

2.2

2.0

4

0.31

0.22

0.18

0.31

0.22

0.15

0.70

6.5

0.16

2.1

2.0

6

0.29

0.18

0.17

0.29

0.18

0.12

0.62

6

0.10

2.1

2.0

8

0.27

0.16

0.17

0.27

0.15

0.10

0.58

5.7

0.08

2.1

2.0

10

0.25

0.14

0.16

0.25

0.14

0.09

0.53

5.7

0.06

2.1

2.0

12

0.24

0.13

0.16

0.24

0.13

0.08

0.50

5.7

0.05

2.1

2.0

Source: Engineering Data Book (Hydraulic Institute 1990).


Another form of Equation (4) appears in Chapter 21, but the two are equivalent. Equation (4) is useful in showing behavior at limiting cases: as ε/D approaches 0 (smooth limit), the 18.7/Re term dominates; at high ε/D and Re (fully rough limit), the 2ε/D term dominates.

Equation (4) is implicit in f; that is, f appears on both sides, so a value for f is usually obtained iteratively.

 Hazen-Williams Equation

A less widely used alternative to the Darcy-Weisbach formulation for calculating pressure drop is the Hazen-Williams equation, which is expressed as

(5)

or

(6)

where C = roughness factor.

Typical values of C are 150 for plastic pipe and copper tubing, 140 for new steel pipe, down to 100 and below for badly corroded or very rough pipe.

 Valve and Fitting Losses

Valves and fittings cause pressure losses greater than those caused by the pipe alone. One formulation expresses losses as

(7)

where K = geometry- and size-dependent loss coefficient (Tables 3 to 6).

 

Example 1.

Determine the pressure drop for 60°F water flowing at 4 fps through a nominal 1 in., 90° threaded elbow.

Solution: Use Equation (7). From Table 3, the K for a 1 in., 90° threaded elbow is 1.5.


The loss coefficient for valves appears in another form as Cv, a dimensional coefficient expressing the flow through a valve at a specified pressure drop.

(8)

where

Q = volumetric flow, gpm
Cv = valve coefficient, gpm at Δp = 1 psi
Δp = pressure drop, psi

See the section on Control Valve Sizing in Chapter 47 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment for more information on valve coefficients.

 

Example 2.

Determine the volumetric flow through a valve with Cv = 10 for an allowable pressure drop of 5 psi.

Solution: Use Equation (8).


Alternative formulations express fitting losses in terms of equivalent lengths of straight pipe (see Tables 8 and 27). Pressure loss data for fittings are also presented in Idelchik (1986).

Table 5 Approximate Range of Variation for K Factors of Steel Fittings

90° Elbow

Regular threaded

±20% above 2 in.

   

±40% below 2 in.

 

Long-radius threaded

±25%

 

Regular flanged

±35%

 

Long-radius flanged

±30%

45° Elbow

Regular threaded

±10%

 

Long-radius flanged

±10%

Return bend (180°)

Regular threaded

±25%

Regular flanged

±35%

Long-radius flanged

±30%

Tee

Threaded, line or branch

±25%

 

Flanged, line or branch

±35%

Globe valve

Threaded

±25%

 

Flanged

±25%

Gate valve

Threaded

±25%

 

Flanged

±50%

Angle valve

Threaded

±20%

 

Flanged

±50%

Check valve

Threaded

±50%

 

Flanged

+200%

   

−80%

Source: Engineering Data Book (Hydraulic Institute 1990).


Table 6 Summary of K Values for Steel Ells, Reducers, and Expansions

 

Pasta

ASHRAE Researchb,c

4 fps

8 fps

12 fps

2 in. S.R.e ell (R/D = 1) thread

0.60 to 1.0 (1.0)d

0.60

0.68

0.736

4 in. S.R. ell (R/D = 1) weld

0.30 to 0.34

0.37

0.34

0.33

1 in. L.R. ell (R/D = 1.5) weld

to 1.0

2 in. L.R. ell (R/D = 1.5) weld

0.50 to 0.7

4 in. L.R. ell (R/D = 1.5) weld

0.22 to 0.33 (0.22)d

0.26

0.24

0.23

6 in. L.R. ell (R/D = 1.5) weld

0.25

0.26

0.24

0.24

8 in. L.R. ell (R/D = 1.5) weld

0.20 to 0.26

0.22

0.20

0.19

10 in. L.R. ell (R/D = 1.5) weld

0.17

0.21

0.17

0.16

12 in. L.R. ell (R/D = 1.5) weld

0.16

0.17

0.17

0.17

16 in. L.R. ell (R/D = 1.5) weld

0.12

0.12

0.12

0.11

20 in. L.R. ell (R/D = 1.5) weld

0.09

0.12

0.10

0.10

24 in. L.R. ell (R/D = 1.5) weld

0.07

0.098

0.089

0.089

Reducer (2 by 1.5 in.) thread

0.53

0.28

0.20

  (4 by 3 in.) weld

0.22

0.23

0.14

0.10

  (6 by 4 in.) weld

 

0.62

0.54

0.53

  (8 by 6 in.) weld

 

0.31

0.28

0.26

  (10 by 8 in.) weld

 

0.16

0.14

0.14

  (12 by 10 in.) weld

0.14

0.14

0.14

  (16 by 12 in.) weld

0.17

0.16

0.17

  (20 by 16 in.) weld

0.16

0.13

0.13

  (24 by 20 in.) weld

0.053

0.053

0.055

Expansion (1.5 by 2 in.) thread

0.16

0.13

0.02

  (3 by 4 in.) weld

0.11

0.11

0.11

  (4 by 6 in.) weld

0.28

0.28

0.29

  (6 by 8 in.) weld

0.15

0.12

0.11

  (8 by 10 in.) weld

0.11

0.09

0.08

  (10 by 12 in.) weld

0.11

0.11

0.11

  (12 by 16 in.) weld

0.073

0.076

0.073

  (16 by 20 in.) weld

0.024

0.021

0.022

  (20 by 24 in.) weld

0.020

0.023

0.020

Source: Rahmeyer (2003a).

a Published data by Crane Co. (1988), Freeman (1941), and Hydraulic Institute (1990).

b Rahmeyer (1999a, 2002a).

c Ding et al. (2005)

d ( ) Data published in 1993 ASHRAE Handbook—Fundamentals.

e S.R.—short radius or regular ell; L.R.—long-radius ell.


Table 7 Summary of Test Data for Loss Coefficients K for Steel Pipe Tees

 

Pasta

ASHRAE Researchb,c

4 fps

8 fps

12 fps

2 in. thread tee, 100% branch

1.20 to 1.80 (1.4)d

0.93

     100% line (flow-through)

0.50 to 0.90 (0.90)d

0.19

     100% mix

1.19

 

4 in. weld tee, 100% branch

0.70 to 1.02 (0.70)d

0.57

     100% line (flow-through)

0.15 to 0.34 (0.15)d

0.06

     100% mix

0.49

6 in. weld tee, 100% branch

0.56

     100% line (flow-through)

0.12

     100% mix

0.88

8 in. weld tee, 100% branch

0.53

     100% line (flow-through)

0.08

     100% mix

0.70

10 in. weld tee, 100% branch

0.52

     100% line (flow-through)

0.06

     100% mix

0.77

12 in. weld tee, 100% branch

0.52

0.70

0.63

0.62

     100% line (flow-through)

0.09

0.062

0.091

0.096

     100% mix

0.88

0.72

0.72

16 in. weld tee, 100% branch

0.47

0.54

0.55

0.54

     100% line (flow-through)

0.07

0.032

0.028

0.028

     100% mix

0.74

0.74

0.76

a Published data by Crane Co. (1988), Freeman (1941), and Hydraulic Institute (1990).

b Rahmeyer (1999b, 2002b).

c Ding et al. (2005).

d Data published in 1993 ASHRAE Handbook—Fundamentals.


Table 8 Test Summary for Loss Coefficients K and Equivalent Loss Lengths

Schedule 80 PVC Fitting

 

K

L, ft

Injected molded elbow,

2 in.

0.91 to 1.00

8.4 to 9.2

 

4 in.

0.86 to 0.91

18.3 to 19.3

 

6 in.

0.76 to 0.91

26.2 to 31.3

 

8 in.

0.68 to 0.87

32.9 to 42.1

8 in. fabricated elbow, Type I, components

0.40 to 0.42

19.4 to 20.3

  Type II, mitered

0.073 to 0.76

35.3 to 36.8

6 by 4 in. injected molded reducer

0.12 to 0.59

4.1 to 20.3

  Bushing type

0.49 to 0.59

16.9 to 20.3

8 by 6 in. injected molded reducer

0.13 to 0.63

6.3 to 30.5

  Bushing type

0.48 to 0.68

23.2 to 32.9

  Gradual reducer type

0.21

10.2

4 by 6 in. injected molded expansion

0.069 to 1.19

1.5 to 25.3

  Bushing type

0.069 to 1.14

1.5 to 24.2

6 by 8 in. injected molded expansion

0.95 to 0.96

32.7 to 33.0

  Bushing type

0.94 to 0.95

32.4 to 32.7

  Gradual reducer type

0.99

34.1


Equation (7) and data in Tables 3 and 4 are based on the assumption that separated flow in the fitting causes the K factors to be independent of Reynolds number. In reality, the K factor for most pipe fittings varies with Reynolds number. Tests by Rahmeyer (1999a, 1999b, 2002a, 2002b) (ASHRAE research projects RP-968 and RP-1034) on 2 in. threaded and 4, 12, 16, 20, and 24 in. welded steel fittings demonstrate the variation and are shown in Tables 6 and 7. The studies also present K factors of diverting and mixing flows in tees, ranging from full through flow to full branch flow. They also examined the variation in K factors caused by variations in geometry among manufacturers and by surface defects in individual fittings.

Hegberg (1995) and Rahmeyer (1999a, 1999b) discuss the origins of some of the data shown in Tables 6 and 7. The Hydraulic Institute (1990) data appear to have come from Freeman (1941), work that was actually performed in 1895. The work of Giesecke (1926) and Giesecke and Badgett (1931, 1932a, 1932b) may not be representative of present-day fittings.

Further extending the work on determination of fitting K factors to PVC piping systems, Rahmeyer (2003a, 2003b) (ASHRAE research project RP-1193) found the data in Tables 8 and 9 giving K factors for Schedule 80 PVC 2, 4, 6, and 8 in. ells, reducers, expansions, and tees. The results of these tests are also presented in the cited papers in terms of equivalent lengths. In general, PVC fitting geometry varied much more from one manufacturer to another than steel fittings did.

 Losses in Multiple Fittings

Typical fitting loss calculations are done as if each fitting is isolated and has no interaction with any other. Rahmeyer (2002c) (ASHRAE research project RP-1035) tested 2 in. threaded ells and 4 in. ells in two and three fitting assemblies of several geometries, at varying spacing. Figure 1 shows the geometries, and Figures 2 and 3 show the ratio of coupled K values to uncoupled K values (i.e., fitting losses for the assembly compared with the sum of losses from the same number of isolated fittings).

The most important conclusion is that the interaction between fittings always reduces the loss. Also, although geometry of the assembly has a definite effect, the effects are not the same for 2 in. threaded and 4 in. welded ells. Thus, the traditional practice of adding together losses from individual fittings gives a conservative (high-limit) estimate.

Summary Plot of Effect of Close-Coupled Configurations for 2 in. Ells

Figure 2. Summary Plot of Effect of Close-Coupled Configurations for 2 in. Ells


Summary Plot of Effect of Close-Coupled Configurations for 4 in. Ells

Figure 3. Summary Plot of Effect of Close-Coupled Configurations for 4 in. Ells


Table 9 Test Summary for Loss Coefficients K of PVC Tees

Branching

Schedule 80 PVC Fitting

K1-2

K1-3

2 in. injection molded branching tee, 100% line flow

0.13 to 0.26

  50/50 flow

0 to 0.12

0.74 to 1.02

  100% branch flow

0.98 to 1.39

4 in. injection molded branching tee, 100% line flow

0.07 to 0.22

  50/50 flow

0.03 to 0.13

0.74 to 0.82

  100% branch flow

0.97 to 1.12

6 in. injection molded branching tee, 100% line flow

0.01 to 0.14

  50/50 flow

0.06 to 0.11

0.70 to 0.84

  100% branch flow

0.95 to 1.15

6 in. fabricated branching tee, 100% line flow

0.21 to 0.22

  50/50 flow

0.04 to 0.09

1.29 to 1.40

  100% branch flow

1.74 to 1.88

8 in. injection molded branching tee, 100% line flow

0.04 to 0.09

  50/50 flow

0.04 to 0.07

0.64 to 0.75

  100% branch flow

0.85 to 0.96

8 in. fabricated branching tee, 100% line flow

0.09 to 0.16

  50/50 flow

0.08 to 0.13

1.07 to 1.16

  100% branch flow

1.40 to 1.62

Mixing

PVC Fitting

K1-2

K3-2

2 in. injection molded mixing tee, 100% line flow

0.12 to 0.25

  50/50 flow

1.22 to 1.19

0.89 to 1.88

  100% mix flow

0.89 to 1.54

4 in. injection molded mixing tee, 100% line flow

0.07 to 0.18

  50/50 flow

1.19 to 1.88

0.98 to 1.88

  100% mix flow

0.88 to 1.02

6 in. injection molded mixing tee, 100% line flow

0.06 to 0.14

  50/50 flow

1.26 to 1.80

1.02 to 1.60

  100% mix flow

0.90 to 1.07

6 in. fabricated mixing tee, 100% line flow

0.19 to 0.21

  50/50 flow

2.94 to 3.32

2.57 to 3.17

  100% mix flow

1.72 to 1.98

8 in. injection molded mixing tee, 100% line flow

0.04 to 0.09

  50/50 flow

1.10 to 1.60

0.96 to 1.32

  100% mix flow

0.81 to 0.93

8 in. fabricated mixing tee, 100% line flow

0.13 to 0.70

  50/50 flow

2.36 to 10.62

2.02 to 2.67

  100% mix flow

1.34 to 1.53

Coefficients based on average velocity of 8 fps. Range of values varies with fitting manufacturers. Line or straight flow is Q2/Q1 = 100%. Branch flow is Q2/Q1 = 0%.


 Calculating Pressure Losses

The most common engineering design flow loss calculation selects a pipe size for the desired total flow rate and available or allowable pressure drop.

Because either formulation of fitting losses requires a known diameter, pipe size must be selected before calculating the detailed influence of fittings. A frequently used rule of thumb assumes that the design length of pipe is 50 to 100% longer than actual to account for fitting losses. After a pipe diameter has been selected on this basis, the influence of each fitting can be evaluated.

 Stress Calculations

Metallic Pipe. Although stress calculations are seldom required, the factors involved should be understood. The main areas of concern are (1) internal pressure stress, (2) longitudinal stress caused by pressure and weight, and (3) stress from expansion and contraction.

ASME Standard B31 standards establish a basic allowable stress S equal to one-fourth of the minimum tensile strength of the material. This value is adjusted, as discussed in this section, because of the nature of certain stresses and manufacturing processes.

Hoop stress caused by internal pressure is the major stress on pipes. Because some forming methods form a seam that may be weaker than the base material, ASME Standard B31.9 specifies a joint efficiency factor E, multiplied by the basic allowable stress to establish a maximum allowable stress value in tension SE. (Table A-1 in ASME Standard B31.9 lists values of SE for commonly used pipe materials.) The joint efficiency factor can be significant; for example, seamless pipe has a joint efficiency factor of 1, so it can be used to the full allowable stress (one-quarter of the tensile strength). In contrast, butt-welded pipe has a joint efficiency factor of 0.60, so its maximum allowable stress must be derated (SE = 0.6S).

Equation (9) determines the minimum wall thickness for a given pressure. Equation (10) determines the maximum pressure allowed for a given wall thickness.

(9)

(10)

where

SA = allowable stress range, psi
Sc = allowable cold stress at coolest temperature system will experience, psi
Sh = allowable hot stress at hottest temperature system will experience, psi

Both equations incorporate an allowance factor A to compensate for manufacturing tolerances, material removed in threading or grooving, and corrosion. For the seamless, butt-welded, and electric resistance welded (ERW) pipe most commonly used in HVAC work, the standards apply a manufacturing tolerance of 12.5%. Working pressure for steel pipe (see Table 16) has been calculated using a manufacturing tolerance of 12.5%, standard allowance for depth of thread (where applicable), and a corrosion allowance of 0.065 in. for pipes 2 1/2 in. and larger and 0.025 in. for pipes 2 in. and smaller. Where corrosion is known to be greater or smaller, pressure rating can be recalculated using Equation (10). Higher pressure ratings than shown in Table 16 can be obtained (1) by using ERW or seamless pipe in lieu of continuous-weld (CW) pipe 4 in. and less, and seamless pipe in lieu of ERW pipe 5 in. and greater (because of higher joint efficiency factors); or (2) by using heavier-wall pipe.

Longitudinal stresses caused by pressure, weight, and other sustained forces are additive, and the sum of all such stresses must not exceed the basic allowable stress S at the highest temperature at which the system will operate. Longitudinal stress caused by pressure equals approximately one-half the hoop stress caused by internal pressure; thus, at least one-half the basic allowable stress is available for weight and other sustained forces. This factor is taken into account in Table 11.

Stresses caused by expansion and contraction are cyclical, and, because creep allows some stress relaxation, the ASME Standard B31 series allows designing to an allowable stress range SA as calculated by Equation (11). Table 15 lists allowable stress ranges for commonly used piping materials.

(11)

where

SA = allowable stress range, psi
Sc = allowable cold stress at coolest temperature system will experience, psi
Sh = allowable hot stress at hottest temperature system will experience, psi

Nonmetallic. Both thermoplastics and thermosets have an allowable stress derived from a hydrostatic design basis stress (HDBS). The HDBS is determined by a statistical analysis of both static and cyclic stress rupture test data as set forth in ASTM Standard D2837 for thermoplastics and ASTM Standard D2992 for glass-fiber-reinforced thermosetting resins.

The allowable stress, called the hydrostatic design stress (HDS), is obtained by multiplying the HDBS by a service factor. HDS values recommended by some manufacturers and those allowed by ASME Standard B31 are listed in Table 18.

The pressure design thickness for plastic pipe can be calculated using the code stress values and the formula in Equation (12):

(12)

where

t = pressure design thickness, in.
p = internal design pressure, psig
D = pipe outside diameter, in.
S = hydrostatic design stress (HDS), psi

The minimum required wall thickness can be found by adding an allowance for mechanical strength, threading, grooving, erosion, and corrosion to the calculated pressure design thickness.

Another method of rating pressure rating of piping used by manufacturers is the standard dimension ratio (SDR), which is the ratio of the pipe diameter to the wall thickness:

(13)

where

D = pipe outside diameter, in.
s = pipe wall thickness, in.

An SDR of 11 means that the outside diameter D of the pipe is 11 times the thickness of the wall s. A high SDR means that the pipe’s wall is thin compared to its diameter, and a low SDR means that the pipe’s wall is thick relative to pipe diameter. SDR is inversely correlated with pressure rating: high SDR indicates a low pressure rating, whereas low-SDR pipes have higher pressure ratings.

There are many formulations of the polymers used for piping materials, and different joining methods for each, so manufacturers’ recommendations should be followed. Most catalogs give pressure ratings for pipe and fittings at various temperatures up to the maximum the material will withstand.

1.5 SIZING PROCEDURE

A procedure for sizing piping systems is as follows:

  1. Determine system type (open, closed, compressible, incompressible, pumped, gravity feed, domestic, etc.).

  2. Determine type and properties of fluid to be conveyed in the pipe.

  3. Determine temperatures used (high, low) and temperature differentials.

  4. Identify system pressures encountered in the system (working, maximum, low, fill, and relief pressures).

  5. Determine load at each device (e.g., heating or cooling requirements, fixture units for plumbing) to find flow.

  6. Sketch main, risers, and branches, and indicate equipment to be served and each device’s flow rate.

  7. Determine flow of supply pipe for each pipe segment run by summing the loads at the furthest device and running back to the source.

  8. Determine flow of each return pipe by starting at the first device returning water and summing the loads back to the source (when applicable).

  9. Determine equivalent length of pipe in the main lines, risers, branches, and returns. Because pipe sizes are not known, the exact equivalent length of various fittings cannot be determined. Add the equivalent lengths, starting at the beginning and proceeding along the mains, risers, branches, and returns (when applicable).

  10. In domestic or gravity feed: calculate the approximate design value of the average pressure drop per 100 ft of equivalent length of pipe determined in step 9. In pumped system: calculate pressure drop or head H using the flow rate and pressure drop for pipe from Equations (2) or (6), the valves and fittings using head drop from Equation (7), and head from the devices from the manufacturer’s data.

    (14)

    where

    Δp = average pressure loss per 100 ft of equivalent length of pipe, psi
    ps = pressure at the source, psig
    pf = minimum pressure required to operate device, psig
    pm = pressure drop through any meters, psi
    H = height of highest fixture above source (if open system), ft
    L = equivalent length determined in step 4, ft
  11. In domestic or gravity system: from the expected rate of flow (step 5) and Δp (step 10), select pipe sizes. In pumped system: select the pump using the flow rate and calculated H.

1.6 PIPE-SUPPORTING ELEMENTS

Pipe-supporting elements consist of (1) hangers, which support from above; (2) supports, which bear load from below; and (3) restraints, such as anchors and guides, that limit or direct movement as well as support loads. Pipe-supporting elements must withstand all static and dynamic conditions, including the following:

  • Weight of pipe, valves, fittings, insulation, and fluid contents, including test fluid if using heavier-than-normal media

  • Occasional loads such as ice, wind, and seismic forces or testing loads (e.g., hydrostatic loads on a steam pipe)

  • Forces imposed by thermal expansion and contraction of pipe bends and loops

  • Frictional, spring, and pressure thrust forces imposed by expansion joints in the system

  • Frictional forces of guides and supports

  • Other loads (e.g., water hammer, vibration, reactive force of relief valves)

  • Test load and force

In addition, pipe-supporting elements must be evaluated in terms of stress at the points of connection to the pipe and the building. Stress at the point of connection to the pipe is especially important for base elbow and trunnion supports, because this stress is usually the limiting parameter, not the strength of the structural member. Loads on anchors, cast-in-place inserts, and other attachments to concrete should not be more than one-fifth the ultimate strength of the attachment, as determined by manufacturers’ tests. All loads on the structure should be communicated to and coordinated with the structural engineer.

Table 10 Capacities of ASTM A36 Steel Threaded Rods

Rod Diameter, in.

Root Area of Coarse Thread, in2

Maximum Load,* lb

1/4

0.027

240

3/8

0.068

610

1/2

0.126

1130

5/8

0.202

1810

3/4

0.302

2710

7/8

0.419

3770

1

0.552

4960

1 1/4

0.889

8000

* Based on allowable stress of 12,000 psi reduced by 25% using root area in accordance with ASME Standard B31.1 and MSS Standard SP-58.


The ASME B31 standards establish criteria for the design of pipe-supporting elements, and the Manufacturers Standardization Society of the Valve and Fittings Industry (MSS) has established standards for the design, fabrication, selection, and installation of pipe hangers and supports based on these codes.

MSS Standard SP-69 and the catalogs of many manufacturers illustrate the various hangers and components and provide information on the types to use with different pipe systems. Table 10 lists maximum safe loads for threaded steel rods, and Tables 11 and 12 show suggested pipe support spacing for metal and PVC pipes, respectively.

Loads on most pipe-supporting elements are moderate and can be selected safely in accordance with manufacturers’ catalog data and the information presented in this section; however, some loads and forces can be very high, especially in multistory buildings and for large-diameter pipe, particularly where expansion joints are used at a high operating pressure. Consequently, a qualified engineer should design or review all anchors and pipe-supporting elements, especially for the following:

  • Steam systems operating above 15 psig

  • Hydronic systems operating above 160 psig or 250°F

  • Risers over 10 stories or 100 ft

  • Systems with expansion joints, especially for pipe diameters 3 in. and greater

  • Pipe sizes over 12 in. diameter

  • Anchor loads greater than 10,000 lb (10 kips)

  • Moments on pipe or structure in excess of 1000 ft · lb

 Hanger Spacing and Pipe Wall Thickness

Table 11 suggests minimum pipe hanger spacing for use unless exceeded by the local authority having jurisdiction or engineering calculations. The primary factors determining pipe wall thickness are hoop stress caused by internal pressure, and longitudinal stresses caused by pressure, weight, and other sustained loads. Detailed stress calculations are seldom required for HVAC applications because standard pipe has ample thickness to sustain the pressure and longitudinal stress caused by weight (assuming hangers are spaced in accordance with Table 11).

Table 11 Suggested Hanger Spacing and Rod Size for Straight Horizontal Runs

NPS, in.

Hanger Spacing, ft

Rod Size, in.

Standard Steel Pipe*

Copper Tube

Water

Steam

Water

1/2

7

8

5

1/4

3/4

7

9

5

1/4

1

7

9

6

1/4

1 1/2

9

12

8

3/8

2

10

13

8

3/8

2 1/2

11

14

9

3/8

3

12

15

10

3/8

4

14

17

12

1/2

6

17

21

14

1/2

8

19

24

16

5/8

10

20

26

18

3/4

12

23

30

19

7/8

14

25

32

 

1

16

27

35

 

1

18

28

37

 

1 1/4

20

30

39

 

1 1/4

Source: Adapted from MSS Standard SP-69

* Spacing does not apply where span calculations are made or where concentrated loads are placed between supports such as flanges, valves, specialties, etc.


Support spacings for PVC and CPVC pipe systems are influenced by operating temperatures. Table 12 recommends horizontal spacing based on pipe size, schedule, material (PVC or industrial-grade CPVC), and operating temperature. Hangers and supports should not be clamped tightly because the axial movement of the pipe would be restricted. The charts are based on continuous spans and uninsulated lines carrying liquids. They are not applicable where loads between supports are concentrated (e.g., for valves, flanges) or where there is a change in direction. Hangers/supports should be located adjacent to joints, branch connections, and changes in direction. Risers should be in installed independently of adjacent horizontal hangers/supports.

For cast iron pipe, maximum spacing should be 12 ft, with at least one hanger/support for each pipe section.

1.7 PIPE EXPANSION AND FLEXIBILITY

Temperature changes cause dimensional changes in all materials. Table 13 shows the coefficients of expansion for metallic piping materials commonly used in HVAC. For systems operating at high temperatures, such as steam and hot water, the rate of expansion is high, and significant movements can occur in short runs of piping. Even though rates of expansion may be low for systems operating in the range of 40 to 100°F, such as chilled and condenser water, they can cause large movements in long runs of piping, which are common in distribution systems and high-rise buildings. Therefore, in addition to design requirements for pressure, weight, and other loads, piping systems must accommodate thermal and other movements to prevent the following:

  • Failure of pipe and supports from overstress and fatigue

  • Leakage of joints

  • Detrimental forces and stresses in connected equipment

Table 12 Suggested Maximum Spacing Between Hangers/Support for PVC and CPVC Pipe


Table 13 Thermal Expansion of Metal Pipe

Saturated Steam Pressure, psig

Temperature, °F

Linear Thermal Expansion, in/100 ft

Carbon Steel

Type 304 Stainless Steel

Copper

   

−30

−0.19

−0.30

−0.32

−20

−0.12

−0.20

−0.21

−10

−0.06

−0.10

−0.11

 

0

0.00

0.00

0.00

10

0.08

0.11

0.12

20

0.15

0.22

0.24

Vacuum

−14.6

32

0.24

0.36

0.37

−14.6

40

0.30

0.45

0.45

−14.5

50

0.38

0.56

0.57

−14.4

60

0.46

0.67

0.68

−14.3

70

0.53

0.78

0.79

−14.2

80

0.61

0.90

0.90

−14.0

90

0.68

1.01

1.02

−13.7

100

0.76

1.12

1.13

−13.0

120

0.91

1.35

1.37

−11.8

140

1.06

1.57

1.59

−10.0

160

1.22

1.79

1.80

−7.2

180

1.37

2.02

2.05

−3.2

200

1.52

2.24

2.30

 

0

212

1.62

2.38

2.43

 

2.5

220

1.69

2.48

2.52

 

10.3

240

1.85

2.71

2.76

 

20.7

260

2.02

2.94

2.99

 

34.6

280

2.18

3.17

3.22

 

52.3

300

2.35

3.40

3.46

 

75.0

320

2.53

3.64

3.70

 

103.3

340

2.70

3.88

3.94

 

138.3

360

2.88

4.11

4.18

 

181.1

380

3.05

4.35

4.42

 

232.6

400

3.23

4.59

4.87

 

666.1

500

4.15

5.80

5.91

 

1528

600

5.13

7.03

7.18

 

3079

700

6.16

8.29

8.47

   

800

7.23

9.59

9.79

   

900

8.34

10.91

11.16

   

1000

9.42

12.27

12.54


An unrestrained pipe operates at the lowest overall stress level. Anchors and restraints are needed to support pipe weight and to protect equipment connections. Anchor forces and bowing of pipe anchored at both ends are generally too large to be acceptable, so general practice is to never anchor a straight run of steel pipe at both ends. Piping must be allowed to expand or contract through thermal changes. Ample flexibility can be attained by designing pipe bends and loops or by including supplemental devices, such as expansion joints.

End reactions transmitted to rotating equipment, such as pumps or turbines, may deform the equipment case and cause bearing misalignment that may ultimately cause the component to fail. Consequently, manufacturers’ recommendations on allowable forces and movements that may be placed on their equipment should be followed.

1.8 PIPE BENDS AND LOOPS

Detailed stress analysis requires involved mathematical analysis and is generally performed by computer programs. However, such involved analysis is not typically required for most HVAC systems because the piping arrangements and temperature ranges at which they operate are usually simple to analyze. Expansion stresses discussed in this section relate only to aboveground pipe located in open air, or preinsulated pipe.

 L Bends

The guided cantilever beam method of evaluating L bends can be used to design L bends, Z bends, pipe loops, branch take-off connections, and some more complicated piping configurations. The guided cantilever equation [see Equation (17)] is generally conservative because it assumes that the pipe arrangement does not rotate. The anchor force results will be higher because of the lack of rotation, and rigorous analysis is recommended for complicated or expensive systems.

Guided Cantilever Beam

Figure 4. Guided Cantilever Beam


Equation (15) may be used to calculate the length of leg BC needed to accommodate thermal expansion or contraction of leg AB for a guided cantilever beam (Figure 4).

(15)

where

L = length of leg BC required to accommodate thermal expansion of long leg AB, ft
Δ = thermal expansion or contraction of leg AB, in.
D = actual pipe outside diameter, in.
E = modulus of elasticity, psi
SA = allowable stress range, psi

 

For the commonly used A53 Grade B seamless or ERW pipe, an allowable stress SA of 22,500 psi (see Table 15) can be used without overstressing the pipe. However, this can result in very high end reactions and anchor forces, especially with large-diameter pipe. Designing to a stress range SA of 15,000 psi and assuming E = 27.9 × 106 psi, Equation (15) reduces to Equation (16), which provides reasonably low end reactions without requiring too much extra pipe. In addition, Equation (16) may be used with A53 continuous (butt-) welded, seamless, and ERW pipe, and B88 drawn copper tubing.

(16)

The guided cantilever method of designing L bends assumes no restraints; therefore, care must be taken in supporting the pipe. For horizontal L bends, it is usually necessary to place a support near point B (see Figure 4), and any supports between points A and C must provide minimal resistance to piping movement; this is done by using slide plates or hanger rods of ample length, with hanger components selected to allow for swing no greater than 4°.

Table 14 Pipe Loop Design for A53 Grade B Carbon Steel Pipe Through 400°F

Pipe Size, in.

Anchor-to-Anchor Expansion, in.

2

4

6

8

10

12

W

H

W

H

W

H

W

H

W

H

W

H

1

2

4

3

6

3.5

7

4

8

4.5

9

5

10

2

3

6

4

8

5

10

5.5

11

6

12

7

14

3

3.5

7

5

10

6

12

6.5

13

7.5

15

8

16

4

4

8

5.5

11

6.5

13

7.5

15

8.5

17

9

18

6

5

10

6.5

13

8

16

9

18

10

20

11

22

8

5.5

11

7.5

15

9

18

10.5

21

12

24

13

26

10

6

12

8.5

17

10

20

11.5

23

13

26

14

28

12

6.5

13

9

18

11

22

12.5

25

14

28

15.5

31

14

7

14

9.5

19

11.5

23

13

26

15

30

16

32

16

7.5

15

10

20

12.5

25

14

28

16

32

17.5

35

18

8

16

11

22

13

26

15

30

17

34

18.5

37

20

8.5

17

11.5

23

14

28

16

32

18

36

19.5

39

24

9

18

12.5

25

14.5

29

17.5

35

19.5

39

21

42

Notes: 1. W and H dimensions are feet.

2. L is determined from Equation (15). W = L/5  H = 2W  2H + W = L

3. Approximate force to deflect loop = 200 lb/in. pipe diameter. For example, 8 in. pipe creates 1600 lb of force.


For L bends containing both vertical and horizontal legs, any supports on the horizontal leg must be spring hangers designed to support the full weight of pipe at normal operating temperature with a maximum load variation of 25%.

The force developed in an L bend that must be sustained by anchors or connected equipment is determined by the following equation:

(17)

where

F = force, lb
Ec = modulus of elasticity, psi
I = moment of inertia, in4
L = length of offset leg, ft
Δ = deflection of offset leg, in.
Z Bend in Pipe

Figure 5. Z Bend in Pipe


 Z Bends

Z bends, as shown in Figure 5, are very effective for accommodating pipe movements. A simple and conservative method of sizing Z bends is to design the offset leg to be 65% of the values used for an L bend in Equation (15):

(18)

where

L = length of offset leg, ft
Δ = anchor-to-anchor expansion, in.
D = pipe outside diameter, in.

The force developed in a Z bend can be calculated with acceptable accuracy as follows:

(19)

where

C1 = 4000 lb/in.
F = force, lb
D = pipe outside diameter, in.
L = length of offset leg, ft
Δ = anchor-to-anchor expansion, in.

 U Bends and Pipe Loops

Pipe loops or U bends are commonly used in long runs of piping. A simple method of designing pipe loops is to calculate the anchor-to-anchor expansion and, using Equation (15), determine the length L necessary to accommodate this movement. The pipe loop dimensions can then be determined using W = L/5 and H = 2W.

Note that guides must be spaced no closer than twice the height of the loop, and piping between guides must be supported, as described in the section on L Bends, when the length of pipe between guides exceeds the maximum allowable hanger spacing for the size pipe.

Table 14 lists pipe loop dimensions for pipe sizes 1 to 24 in. and anchor-to-anchor expansion (contraction) of 2 to 12 in.

No simple method has been developed to calculate pipe loop force; however, it is generally low. A conservative estimate is 200 lb per inch diameter (e.g., a 2 in. pipe will develop 400 lb of force and a 12 in. pipe will develop 2400 lb of force). Additional analysis should be done for pipes greater than 12 in. in diameter, because other simplified methodologies predict higher anchor forces.

 Expansion and Contraction Control of Other Materials

To design expansion and contraction loops and bends for other materials, consult the Copper Development Association (CDA 2010) for copper pipes, and Plastic Pipe and Fitting Association (PPFA 2009) for plastic pipes.

 Cold Springing of Pipe

Cold springing or cold positioning of pipe consists of offsetting or springing the pipe in a direction opposite the expected movement. Cold springing is not recommended for most HVAC piping. Furthermore, cold springing does not allow designing a pipe bend or loop for twice the calculated movement. For example, if a particular L bend can accommodate 3 in. of movement from a neutral position, cold springing does not allow the L bend to accommodate 6 in. of movement.

 Analyzing Existing Piping Configurations

Piping is best analyzed using a computer stress analysis program, which can provide all pertinent data, including stress, movements, and loads. Services can perform such analysis if programs are not available in house. However, many situations do not require such detailed analysis. A simple, satisfactory method for single and multiplane systems is to divide the system with real or imaginary anchors into a number of single-plane units, as shown in Figure 6, that can be evaluated as L and Z bends.

2. PIPE AND FITTING MATERIALS

2.1 PIPE

 Steel Pipe

Steel pipe is manufactured by several processes. Seamless pipe (Type S), made by piercing or extruding, has no longitudinal seam. Other manufacturing methods roll a strip or sheet of steel (skelp) into a cylinder and weld a longitudinal seam. A continuous-weld (Type F CW) furnace butt-welding (BW; i.e., welding pipe in a single plane) process forces and joins the edges together at high temperature. An electric current welds the seam in electric-resistance-welded (Type E ERW) pipe. ASTM standards such as A53 and A106 specify steel pipe A and B grades. The A grade has a lower tensile strength and is not widely used.

Multiplane Pipe System

Figure 6. Multiplane Pipe System


The ASME pressure piping codes require that a longitudinal joint efficiency factor E (Table 15) be applied to each type of seam when calculating the allowable stress. ASME Standard B36.10M specifies the dimensional standard for wrought steel pipe.

Steel pipe is manufactured with wall thicknesses identified by schedule or weight class. Although schedule numbers and weight class designations are related, they are not constant for all pipe sizes. Standard weight (STD) and Schedule 40 pipe have the same wall thickness through NPS 10. For 12 in. and larger standard weight pipe, the wall thickness remains constant at 0.375 in., whereas Schedule 40 wall thickness increases with each size. A similar equality exists between Extra Strong (XS) and Schedule 80 pipe through 8 in.; above 8 in., XS pipe has a 0.500 in. wall, whereas Schedule 80 increases in wall thickness. Table 16 lists properties of representative steel pipe.

Joints in steel pipe are made by welding or by using threaded, flanged, or grooved fittings or socket welding. Unreinforced welded-in branch connections weaken a main pipeline, and added reinforcement is necessary, unless the excess wall thickness of both mains and branches is sufficient to sustain the pressure.

Table 15 Allowable Stressesa for Pipe and Tube

ASTM Specification

Grade

Type

Manufacturing Process

Available Sizes, in.

Minimum Tensile Strength, psi

Basic Allowable Stress S, psi

Joint Efficiency Factor E

Allowable Stressb SE, psi

Allowable Stress RangecSA, psi

A53 steel

F

Cont. weld

1/2 to 4

45,000

11,250

0.6

6,800

16,900

A53 steel

B

S

Seamless

1/2 to 26

60,000

15,000

1.0

15,000

22,500

A53 steel

B

E

ERW

2 to 20

60,000

15,000

0.85

12,800

22,500

A106 steel

B

S

Seamless

1/2 to 26

60,000

15,000

1.0

15,000

22,500

B88 copper

Hard drawn

1/4 to 12

36,000

9,000

1.0

9,000

13,500

a Listed stresses are for temperatures to 650°F for steel pipe (to 400°F for Type F) and to 250°F for copper tubing.

b To be used for internal pressure stress calculations in Equations (10) and (11).

c To be used only for piping flexibility calculations; see Equations (12) and (13).


The ASME Standard B31 series gives formulas and guidelines for determining whether reinforcement is required. Such calculations are seldom needed in HVAC applications because (1) the fitting is designed in accordance with a standard listed in the applicable ASME B31 table and used within the pressure and temperature limits of that standard, and (2) fittings such as tees and reinforced outlet fittings provide integral reinforcement.

Type F steel pipe is not allowed for ASME Standard B31.5 refrigerant piping.

Table 16 Steel Pipe Data

Nominal Size, in.

Pipe OD, in.

Schedule Number or Weighta

Wall Thickness t, in.

Inside Diameter d, in.

Surface Area

Cross Section

Weight

Working Pressurec ASTM A53 B to 400°F

Outside, ft2/ft

Inside, ft2/ft

Metal Area, in2

Flow Area, in2

Pipe, lb/ft

Water, lb/ft

Mfr. Process

Joint Typeb

psig

1/4

0.540

40 ST

0.088

0.364

0.141

0.095

0.125

0.104

0.424

0.045

CW

T

188

   

80 XS

0.119

0.302

0.141

0.079

0.157

0.072

0.535

0.031

CW

T

871

3/8

0.675

40 ST

0.091

0.493

0.177

0.129

0.167

0.191

0.567

0.083

CW

T

203

   

80 XS

0.126

0.423

0.177

0.111

0.217

0.141

0.738

0.061

CW

T

820

1/2

0.840

40 ST

0.109

0.622

0.220

0.163

0.250

0.304

0.850

0.131

CW

T

214

   

80 XS

0.147

0.546

0.220

0.143

0.320

0.234

1.087

0.101

CW

T

753

3/4

1.050

40 ST

0.113

0.824

0.275

0.216

0.333

0.533

1.13

0.231

CW

T

217

   

80 XS

0.154

0.742

0.275

0.194

0.433

0.432

1.47

0.187

CW

T

681

1

1.315

40 ST

0.133

1.049

0.344

0.275

0.494

0.864

1.68

0.374

CW

T

226

   

80 XS

0.179

0.957

0.344

0.251

0.639

0.719

2.17

0.311

CW

T

642

1 1/4

1.660

40 ST

0.140

1.380

0.435

0.361

0.669

1.50

2.27

0.647

CW

T

229

   

80 XS

0.191

1.278

0.435

0.335

0.881

1.28

2.99

0.555

CW

T

594

1 1/2

1.900

40 ST

0.145

1.610

0.497

0.421

0.799

2.04

2.72

0.881

CW

T

231

   

80 XS

0.200

1.500

0.497

0.393

1.068

1.77

3.63

0.765

CW

T

576

2

2.375

40 ST

0.154

2.067

0.622

0.541

1.07

3.36

3.65

1.45

CW

T

230

   

80 XS

0.218

1.939

0.622

0.508

1.48

2.95

5.02

1.28

CW

T

551

2 1/2

2.875

40 ST

0.203

2.469

0.753

0.646

1.70

4.79

5.79

2.07

CW

W

533

   

80 XS

0.276

2.323

0.753

0.608

2.25

4.24

7.66

1.83

CW

W

835

3

3.500

40 ST

0.216

3.068

0.916

0.803

2.23

7.39

7.57

3.20

CW

W

482

   

80 XS

0.300

2.900

0.916

0.759

3.02

6.60

10.25

2.86

CW

W

767

4

4.500

40 ST

0.237

4.026

1.178

1.054

3.17

12.73

10.78

5.51

CW

W

430

   

80 XS

0.337

3.826

1.178

1.002

4.41

11.50

14.97

4.98

CW

W

695

6

6.625

40 ST

0.280

6.065

1.734

1.588

5.58

28.89

18.96

12.50

ERW

W

696

   

80 XS

0.432

5.761

1.734

1.508

8.40

26.07

28.55

11.28

ERW

W

1209

8

8.625

30

0.277

8.071

2.258

2.113

7.26

51.16

24.68

22.14

ERW

W

526

   

40 ST

0.322

7.981

2.258

2.089

8.40

50.03

28.53

21.65

ERW

W

643

   

80 XS

0.500

7.625

2.258

1.996

12.76

45.66

43.35

19.76

ERW

W

1106

10

10.75

30

0.307

10.136

2.814

2.654

10.07

80.69

34.21

34.92

ERW

W

485

   

40 ST

0.365

10.020

2.814

2.623

11.91

78.85

40.45

34.12

ERW

W

606

   

XS

0.500

9.750

2.814

2.552

16.10

74.66

54.69

32.31

ERW

W

887

   

80

0.593

9.564

2.814

2.504

18.92

71.84

64.28

31.09

ERW

W

1081

12

12.75

30

0.330

12.090

3.338

3.165

12.88

114.8

43.74

49.68

ERW

W

449

   

ST

0.375

12.000

3.338

3.141

14.58

113.1

49.52

48.94

ERW

W

528

   

40

0.406

11.938

3.338

3.125

15.74

111.9

53.48

48.44

ERW

W

583

   

XS

0.500

11.750

3.338

3.076

19.24

108.4

65.37

46.92

ERW

W

748

   

80

0.687

11.376

3.338

2.978

26.03

101.6

88.44

43.98

ERW

W

1076

14

14.00

30 ST

0.375

13.250

3.665

3.469

16.05

137.9

54.53

59.67

ERW

W

481

   

40

0.437

13.126

3.665

3.436

18.62

135.3

63.25

58.56

ERW

W

580

   

XS

0.500

13.000

3.665

3.403

21.21

132.7

72.04

57.44

ERW

W

681

   

80

0.750

12.500

3.665

3.272

31.22

122.7

106.05

53.11

ERW

W

1081

16

16.00

30 ST

0.375

15.250

4.189

3.992

18.41

182.6

62.53

79.04

ERW

W

421

   

40 XS

0.500

15.000

4.189

3.927

24.35

176.7

82.71

76.47

ERW

W

596

18

18.00

ST

0.375

17.250

4.712

4.516

20.76

233.7

70.54

101.13

ERW

W

374

   

30

0.437

17.126

4.712

4.483

24.11

230.3

81.91

99.68

ERW

W

451

   

XS

0.500

17.000

4.712

4.450

27.49

227.0

93.38

98.22

ERW

W

530

   

40

0.562

16.876

4.712

4.418

30.79

223.7

104.59

96.80

ERW

W

607

20

20.00

20 ST

0.375

19.250

5.236

5.039

23.12

291.0

78.54

125.94

ERW

W

337

   

30 XS

0.500

19.000

5.236

4.974

30.63

283.5

104.05

122.69

ERW

W

477

   

40

0.593

18.814

5.236

4.925

36.15

278.0

122.82

120.30

ERW

W

581

(1) 12.5% of t for mill tolerance on pipe wall thickness, plus

(2) An arbitrary corrosion allowance of 0.025 in. for pipe sizes through NPS 2 and 0.065 in. from NPS 2 1/2 through 20, plus

(3) A thread cutting allowance for sizes through NPS 2.

Because the pipe wall thickness of threaded standard pipe is so small after deducting allowance A, the mechanical strength of the pipe is impaired. It is good practice to limit standard weight threaded pipe pressure to 90 psig for steam and 125 psig for water.

a Numbers are schedule numbers per ASME Standard B36.10M; ST = Standard Weight; XS = Extra Strong.

b T = Thread; W = Weld

c Working pressures were calculated per ASME Standard B31.9 using furnace butt-weld (continuous weld, CW) pipe through 4 in. and electric resistance weld (ERW) thereafter. The allowance A has been taken as


 Copper Tube

Because of their inherent resistance to corrosion and ease of installation, copper and copper alloys are often used in heating, air-conditioning, refrigeration, and water supply installations. The two main standards for copper tube are (1) ASTM Standard B88, which includes Types K, L, M, and DWV for water and drain service; and (2) ASTM Standard B280, which specifies air-conditioning and refrigeration (ACR) tube for refrigeration service.

Types K, L, M, and DWV designate descending wall thicknesses for copper tube. All types have the same outside diameter (OD) for corresponding sizes. Table 17 lists properties of ASTM B88 copper tube. In the plumbing industry, tube of nominal size approximates the inside diameter. The heating and refrigeration trades specify copper tube by the outside diameter. ACR tubing has a different set of wall thicknesses. Types K, L, and M tube may be hard drawn or annealed (soft) temper.

Copper tubing is joined with soldered or brazed, wrought or cast copper capillary socket-end fittings. See Table 20 for lists pressure/temperature ratings of soldered and brazed joints. Small copper tube is also joined by flare or compression fittings.

Table 17 Copper Tube Data

Nominal Diameter, in.

Type

Wall Thickness t, in.

Diameter

Surface Area

Cross Section

Weight

Working Pressurea,b,c ASTM B88 to 250°F

Outside D, in.

Inside d, in.

Outside, ft2/ft

Inside, ft2/ft

Metal Area, in2

Flow Area, in2

Tube, lb/ft

Water, lb/ft

Annealed, psig

Drawn, psig

1/4

K

0.035

0.375

0.305

0.098

0.080

0.037

0.073

0.145

0.032

851

1596

 

L

0.030

0.375

0.315

0.098

0.082

0.033

0.078

0.126

0.034

730

1368

3/8

K

0.049

0.500

0.402

0.131

0.105

0.069

0.127

0.269

0.055

894

1676

 

L

0.035

0.500

0.430

0.131

0.113

0.051

0.145

0.198

0.063

638

1197

 

M

0.025

0.500

0.450

0.131

0.118

0.037

0.159

0.145

0.069

456

855

1/2

K

0.049

0.625

0.527

0.164

0.138

0.089

0.218

0.344

0.094

715

1341

 

L

0.040

0.625

0.545

0.164

0.143

0.074

0.233

0.285

0.101

584

1094

 

M

0.028

0.625

0.569

0.164

0.149

0.053

0.254

0.203

0.110

409

766

5/8

K

0.049

0.750

0.652

0.196

0.171

0.108

0.334

0.418

0.144

596

1117

 

L

0.042

0.750

0.666

0.196

0.174

0.093

0.348

0.362

0.151

511

958

3/4

K

0.065

0.875

0.745

0.229

0.195

0.165

0.436

0.641

0.189

677

1270

 

L

0.045

0.875

0.785

0.229

0.206

0.117

0.484

0.455

0.209

469

879

 

M

0.032

0.875

0.811

0.229

0.212

0.085

0.517

0.328

0.224

334

625

1

K

0.065

1.125

0.995

0.295

0.260

0.216

0.778

0.839

0.336

527

988

 

L

0.050

1.125

1.025

0.295

0.268

0.169

0.825

0.654

0.357

405

760

 

M

0.035

1.125

1.055

0.295

0.276

0.120

0.874

0.464

0.378

284

532

1 1/4

K

0.065

1.375

1.245

0.360

0.326

0.268

1.217

1.037

0.527

431

808

 

L

0.055

1.375

1.265

0.360

0.331

0.228

1.257

0.884

0.544

365

684

 

M

0.042

1.375

1.291

0.360

0.338

0.176

1.309

0.682

0.566

279

522

 

DWV

0.040

1.375

1.295

0.360

0.339

0.168

1.317

0.650

0.570

265

497

1 1/2

K

0.072

1.625

1.481

0.425

0.388

0.351

1.723

1.361

0.745

404

758

 

L

0.060

1.625

1.505

0.425

0.394

0.295

1.779

1.143

0.770

337

631

 

M

0.049

1.625

1.527

0.425

0.400

0.243

1.831

0.940

0.792

275

516

 

DWV

0.042

1.625

1.541

0.425

0.403

0.209

1.865

0.809

0.807

236

442

2

K

0.083

2.125

1.959

0.556

0.513

0.532

3.014

2.063

1.304

356

668

 

L

0.070

2.125

1.985

0.556

0.520

0.452

3.095

1.751

1.339

300

573

 

M

0.058

2.125

2.009

0.556

0.526

0.377

3.170

1.459

1.372

249

467

 

DWV

0.042

2.125

2.041

0.556

0.534

0.275

3.272

1.065

1.416

180

338

2 1/2

K

0.095

2.625

2.435

0.687

0.637

0.755

4.657

2.926

2.015

330

619

 

L

0.080

2.625

2.465

0.687

0.645

0.640

4.772

2.479

2.065

278

521

 

M

0.065

2.625

2.495

0.687

0.653

0.523

4.889

2.026

2.116

226

423

3

K

0.109

3.125

2.907

0.818

0.761

1.033

6.637

4.002

2.872

318

596

 

L

0.090

3.125

2.945

0.818

0.771

0.858

6.812

3.325

2.947

263

492

 

M

0.072

3.125

2.981

0.818

0.780

0.691

6.979

2.676

3.020

210

394

 

DWV

0.045

3.125

3.035

0.818

0.795

0.435

7.234

1.687

3.130

131

246

3 1/2

K

0.120

3.625

3.385

0.949

0.886

1.321

8.999

5.120

3.894

302

566

 

L

0.100

3.625

3.425

0.949

0.897

1.107

9.213

4.291

3.987

252

472

 

M

0.083

3.625

3.459

0.949

0.906

0.924

9.397

3.579

4.066

209

392

4

K

0.134

4.125

3.857

1.080

1.010

1.680

11.684

6.510

5.056

296

555

 

L

0.110

4.125

3.905

1.080

1.022

1.387

11.977

5.377

5.182

243

456

 

M

0.095

4.125

3.935

1.080

1.030

1.203

12.161

4.661

5.262

210

394

 

DWV

0.058

4.125

4.009

1.080

1.050

0.741

12.623

2.872

5.462

128

240

5

K

0.160

5.125

4.805

1.342

1.258

2.496

18.133

9.671

7.846

285

534

 

L

0.125

5.125

4.875

1.342

1.276

1.963

18.665

7.609

8.077

222

417

 

M

0.109

5.125

4.907

1.342

1.285

1.718

18.911

6.656

8.183

194

364

 

DWV

0.072

5.125

4.981

1.342

1.304

1.143

19.486

4.429

8.432

128

240

6

K

0.192

6.125

5.741

1.603

1.503

3.579

25.886

13.867

11.201

286

536

 

L

0.140

6.125

5.845

1.603

1.530

2.632

26.832

10.200

11.610

208

391

 

M

0.122

6.125

5.881

1.603

1.540

2.301

27.164

8.916

11.754

182

341

 

DWV

0.083

6.125

5.959

1.603

1.560

1.575

27.889

6.105

12.068

124

232

8

K

0.271

8.125

7.583

2.127

1.985

6.687

45.162

25.911

19.542

304

570

 

L

0.200

8.125

7.725

2.127

2.022

4.979

46.869

19.295

20.280

224

421

 

M

0.170

8.125

7.785

2.127

2.038

4.249

47.600

16.463

20.597

191

358

 

DWV

0.109

8.125

7.907

2.127

2.070

2.745

49.104

10.637

21.247

122

229

10

K

0.338

10.125

9.449

2.651

2.474

10.392

70.123

40.271

30.342

304

571

 

L

0.250

10.125

9.625

2.651

2.520

7.756

72.760

30.054

31.483

225

422

 

M

0.212

10.125

9.701

2.651

2.540

6.602

73.913

25.584

31.982

191

358

12

K

0.405

12.125

11.315

3.174

2.962

14.912

100.554

57.784

43.510

305

571

 

L

0.280

12.125

11.565

3.174

3.028

10.419

105.046

40.375

45.454

211

395

 

M

0.254

12.125

11.617

3.174

3.041

9.473

105.993

36.706

45.863

191

358

a When using soldered or brazed fittings, the joint determines the limiting pressure.

b Working pressures were calculated using ASME Standard B31.9 allowable stresses. A 5% mill tolerance has been used on the wall thickness. Higher tube ratings can be calculated using the allowable stress for lower temperatures.

c If soldered or brazed fittings are used on hard-drawn tubing, use the annealed ratings. Full-tube allowable pressures can be used with suitably rated flare or compression-type fittings.


Table 18 Properties of Pipe Materialsa

Material

Tensile Strength, psi (at 73°F)

Hydrostaticb Design Stress, psi (at 73°F)

Upper Temperature Limit, °F

HDSb Upper Limit, psi

Specific Gravityc

Impact Strength, ft · lb/in (at 73°F)

Modulus of Elasticity, psi (at 73°F)

Coefficient of Expansion, in/106 in · °F

Thermal Conductivity, Btu · in/h · ft2 · °F

Relative Pipe Costd

Designation

Type and Grade

Cell No.

Mfr.

ASME B31

Mfr.

ASME B31

Metals

Copper

L

Drawn – hard

36,000

 

9,000

 

400

8,200

8.90

 

17,000,000

9.4

232

2.2

Steel

A53 B

ERW

60,000

12,800

   

800

9,200

7.80

30

27,500,000

6.31

26

1.0

Stainless steel

304

Drawn or Welded

73,200

     

350

 

7.90

 

28,000,000

9.6

8

2.0

Thermoplastics

PVC 1120

T I,G1

12454-B

7,500

2,000

2,000

140

150

440

1.40

0.8

420,000

30.0

1.1

0.6

PVC 1200

T I,G2

12454-C

   

2,000

 

150

     

410,000

35.0

   

PVC 2120

T II,G1

14333-D

   

2,000

 

150

       

30.0

   

CPVC 4120

T IV,G1

23447-B

8,000

2,000

2,000

210

210

320

1.55

1.5

423,000

35.0

0.95

0.8

PE 2306

Gr. P23

     

630

 

140

     

90,000

80.0

   

PE 3306

Gr. P34

     

630

 

160

     

130,000

70.0

   

PE 3406

Gr. P33

     

630

 

180

     

150,000

60.0

   

HDPE 3408

Gr. P34

355434-C

5,000

1,600

800

140

180

800

0.96

12

110,000

120.0

2.7

1.1

PP

   

5,000

705

 

212

210

 

0.91

1.3

120,000

60.0

1.3

2.9

ABS

Acrylonitrile copolymer

6-3-3

5,500

   

176

   

1.06

8.5

240,000

56.0

1.7

3.4

ABS 1210

T I,G2

5-2-2

 

1,000

 

180

640

 

250,000

55.0

       

ABS 1316

T I,G3

3-5-5

 

1,600

 

180

1,000

 

340,000

40.0

       

ABS 2112

T II,G1

4-4-5

 

1,250

 

180

800

   

40.0

       

PVDF

   

7,000

1,275

 

280

275

306

1.78

3.8

125,000

79.0

0.8

2.6

Thermosetting

Epoxy-glass

RTRP-11AF

 

44,000

8,000

 

300

7,000

     

1,000,000

9 to 13

2.9

1.5

PEX

A,B,Ce

 

3,200

630

200

180

79

 

0.94

 

75,000

90.0

3.2

0.7

Polyester-glass

RTRP-12EF

 

44,000

9,000

200

200

5,000

     

1,000,000

9 to 11

1.3

1.5

a Properties listed are for specific materials listed; each plastic has other formulations. Consult the manufacturer of the system chosen. These values are for comparative purposes.

b Hydrostatic design stress (HDS) is equivalent to allowable design stress

c Relative to water at 62.4 lb/ft3.

d Based on cost for 2 in. pipe only, without factoring in fittings, joints, hangers, and labor.

e A, B, and C are the three manufacturing processes of PEX pipe. The classifications are not related to a ranking system.


Table 19 Applicable Standards for Fittings

Steela

ASME Std.

Pipe flanges and flanged fittings

B16.5

Factory-made wrought steel butt-welding fittings

B16.9

Forged fittings, socket-welding and threaded

B16.11

Wrought steel butt-welding short radius elbows and returns

B16.9

Cast Iron, Malleable Iron, Ductile Ironb

ASME Std.

Cast iron pipe flanges and flanged fittings

B16.1

Malleable iron threaded fittings

B16.3

Gray iron threaded fittings

B16.4

Cast iron threaded drainage fittings

B16.12

Ductile iron pipe flanges and flanged fittings, Classes 150 and 300

B16.42

Copper and Bronzec

ASME Std.

Cast bronze threaded fittings, Classes 125 and 25

B16.15

Cast copper alloy solder joint pressure fittings

B16.18

Wrought copper and copper alloy solder joint pressure fittings

B16.22

Cast copper alloy solder joint drainage fittings, DWV

B16.23

Cast copper alloy pipe flanges and flanged fittings, Classes 150, 300, 400, 600, 900, 1500, and 2500

B16.24

Cast copper alloy fittings for flared copper tubes

B16.26

Wrought copper and wrought copper alloy solder joint drainage fittings

B16.29

Nonmetallicd

ASTM Std.

Threaded PVC plastic pipe fittings, Schedule 80

D2464

Threaded PVC plastic pipe fittings, Schedule 40

D2466

Socket-Type PVC plastic pipe fittings, Schedule 80

D2467

Reinforced epoxy resin gas pressure pipe and fittings

D2517

Threaded CPVC plastic pipe fittings, Schedule 80

F437

Socket-Type CPVC plastic pipe fittings, Schedule 40

F438

Socket-Type CPVC plastic pipe fittings, Schedule 80

F439

Insert fittings for PEX tubing

F877

Plastic brass, bronze, and copper insert fittings for PEX tubing

F877

Solvent cements for PVC plastic piping systems

D2564

Solvent cements for CPVC plastic pipe and fittings

F493

a Wrought steel butt-welding fittings are made to match steel pipe wall thicknesses and are rated at the same working pressure as seamless pipe. Flanges and flanged fittings are rated by working steam pressure classes. Forged steel fittings are rated from 2000 to 6000 psi in classes and are used for high-temperature and high-pressure service for small pipe sizes.

b Class numbers refer to maximum working saturated steam gage pressure (in psi). For liquids at lower temperatures, higher pressures are allowed. Groove-end fittings of these materials are made by various manufacturers who publish their own ratings.

c Classes refer to maximum working steam gage pressure (in psi). At ambient temperatures, higher liquid pressures are allowed. Solder joint fittings are limited by the strength of the soldered or brazed joint (see Table 20).

d Ratings of plastic fittings match the pipe of corresponding schedule number.


Hard-drawn tubing has a higher allowable stress than annealed tubing, but if hard tubing is joined by soldering or brazing, the annealed allowable stress should be used.

Brass pipe and copper pipe are also made in steel pipe thicknesses for threading. High cost has eliminated these materials from the market, except for special applications.

The heating and air-conditioning industry generally uses Types L and M tubing, which have higher internal working pressure ratings than the solder joints used at fittings. Type K may be used with brazed joints for higher pressure-temperature requirements or for direct burial. Type M should be used with care where exposed to potential external damage.

Copper and brass should not be used in ammonia refrigerating systems, or in acidic drains from condensing boilers. The section on Special Systems covers other limitations on refrigerant piping.

 Ductile Iron and Cast Iron

Cast-iron soil pipe comes in XH or service weight. It is not used under pressure because the pipe is not suitable and the joints are not restrained. Cast-iron pipe and fittings typically have bell and spigot ends for lead and oakum joints or elastomer push-on joints. Cast-iron pipe and fittings are also furnished with no-hub ends for joining with no-hub clamps. Local plumbing codes specify permitted materials and joints.

Ductile iron has now replaced cast iron for pressure pipe. Ductile iron is stronger, less brittle, and similar to cast iron in corrosion resistance. It is commonly used for buried pressure water mains or in other locations where internal or external corrosion is a problem. Joints are made with flanged fittings, mechanical joint (MJ) fittings, or elastomer gaskets for bell and spigot ends. Bell and spigot and MJ joints are not self-restrained, though restrained MJ systems are available. Ductile-iron pipe is made in seven thickness classes for different service conditions. AWWA Standard C150/A21.50 covers the proper selection of pipe classes.

 Nonmetallic (Plastic)

Selecting a plastic for a specific purpose requires attention to the temperatures, pressures, chemicals, and stresses the piping will be subjected to in the specific application. All are suitable for cold water. Plastic pipe should not be used for compressed gases or compressed air if the pipe’s material is subject to brittle failure. For other liquids and chemicals, refer to charts provided by plastic pipe manufacturers and distributors. Table 18 gives properties of the various plastics discussed in this section; the last column gives the relative cost of small pipe in each category. Table 2 lists some applications pertinent to HVAC. The following are brief descriptions of common uses for the various materials.

Plastic piping materials fall into two main categories: thermoplastics and thermosets. Thermoplastics melt and are formed by extruding or molding. They are usually used without reinforcing filaments. Thermosets are cured and cannot be reformed. They are normally used with glass fiber reinforcing filaments.

For the purposes of this chapter, thermoplastic piping is made of the following materials:

PVC. Because polyvinyl chloride has the best overall range of properties at the lowest cost, it is the most widely used plastic. It is joined by solvent cementing, threading, or flanging. Gasketed push-on joints are also used for larger sizes. ASTM Standards D1784, D1785, and D2665 cover PVC pipe.

CPVC. Chlorinated polyvinyl chloride has the same properties as PVC and can withstand a higher temperature before losing strength. It is joined by the same methods as PVC. ASTM Standards D1784 and 1785 discuss CPVC.

PE. Low-density polyethylene (LDPE) is a flexible, lightweight tubing with good low-temperature properties. It is used in the food and beverage industry and for instrument tubing. Joins are mechanical, such as compression fittings or push-on connectors and clamps. See ASTM Standard D2239 for details.

HDPE. High-density polyethylene is a tough, weather-resistant material used for large pipelines in the gas industry. Fabricated fittings are available. It is joined by heat fusion for large sizes; flare, compression, or insert fittings can be used on small sizes. ASTM Standard D3350 discusses HDPE.

PP. Polypropylene is a lightweight plastic used for pressure applications and also for chemical waste lines, because it is inert to a wide range of chemicals. A broad variety of drainage fittings are available. For pressure uses, regular fittings are made. It is joined by heat fusion. See ASTM Standards F2830 and F2389 for details.

ABS. Acrylonitrile butadiene styrene is a high-strength, impact- and weather-resistant material. Some formulations can be used for beverage industry. A wide range of fittings is available. It is joined by solvent cement, threading, or flanging. ASTM Standards D2661 and D3965 cover ABS.

PVDF. Polyvinylidene fluoride is widely used for ultrapure water systems and in the pharmaceutical industry and has a wide temperature range. This material is over 20 times more expensive than PVC. It is joined by heat fusion, and fittings are made for this purpose. For smaller sizes, mechanical joints can be used. See ASTM Standard D2122 for information on PVDF.

Thermosetting piping used in HVAC is called (1) reinforced thermosetting resin (RTR) and (2) fiberglass-reinforced plastic (FRP). RTR and FRP are interchangeable and refer to pipe and fittings commonly made of (1) fiberglass-reinforced epoxy resin, (2) fiberglass-reinforced vinyl ester, and (3) fiberglass-reinforced polyester.

Pipe and fittings made from epoxy resin are generally stronger and operate at a higher temperature than those made from polyester or vinyl ester resins, so they are more likely to be used in HVAC.

PEX. Cross-linked polyethylene is made from high-density polyethylene (HDPE) and contains cross-linked bonds in the polymer structure. This changes the thermoplastic to a thermoset. It can be used up to 300°F. PEX is used in building services pipework systems, hydronic radiant heating and cooling systems, and domestic water piping. PEX comes in two types: barrier and nonbarrier. The barrier, a thin sheet of aluminum between layers of PEX material or a layer of polymer film, prevents oxygen dissolved in water from diffusing through the pipe and corroding metal components. Nonbarrier PEX is acceptable for plumbing systems. PEX can be ordered as A, B, or C (these designations refer to the manufacturing process and not the pipe’s structural or chemical properties). All PEX tubing (A, B, C) comply with the same standards: refer to ASTM Standards F876, F877, and F2023; CSA Standard B137.5; and NSF/ANSI Standards 14 and 61 for further information.

2.2 FITTINGS

Table 19 lists standards that give dimensions and pressure ratings for fittings, flanges, and flanged fittings. These data are also available from manufacturers’ catalogs.

2.3 JOINING METHODS

 Threading

Threading as per ASME Standard B1.20.1 is the most common method for joining small-diameter steel or brass pipe. Pipe with a wall thickness less than standard weight should not be threaded. ASME Standard B31.5 limits the threading for various refrigerants and pipe sizes.

 Soldering and Brazing

Copper tube is usually joined by soldering or brazing socket end fittings. Brazing materials melt above 1000°F and produce a stronger joint than solder. Table 20 lists soldered and brazed joint strengths. ASME Standard B16.22-specified wrought copper solder joint fittings and ASME Standard B16.18-specified cast copper solder joint fittings are pressure rated the same way as annealed Type L copper tube of the same size. Health concerns have caused many jurisdictions to ban solder containing lead or antimony for joining pipe in potable-water systems. Lead-based solder, in particular, must not be used for potable water.

Table 20 Internal Working Pressure for Copper Tube Joints

Alloy Used for Joints

Service Temperature, °F

Internal Working Pressure, psi

Water and Noncorrosive Liquids and Gasesa

Sat. Steam and Condensate

Nominal Tube Size (Types K, L, M), in.

 

1/4 to 1

1 1/4 to 2

2 1/2 to 4

5 to 8a

10 to 12a

1/4 to 8

50-50 tin/leadb solder (ASTM B32 Gr 50A)

100

200

175

150

130

100

150

150

125

100

90

70

200

100

90

75

70

50

250

85

75

50

45

40

15

95-5 tin/antimonyc solder (ASTM B32 Gr 50TA)

100

500

400

300

270

150

150

400

350

275

250

150

200

300

250

200

180

140

250

200

175

150

135

110

15

Brazing alloys melting at or above 1000°F

100 to 200

d

d

d

d

d

250

300

210

170

150

150

350

270

190

150

150

150

120

Source: Based on ASME Standard B31.9, Building Services Piping

(1) Flammable or toxic gases or liquids

(2) Gas, vapor, or compressed air in tubing over 4 in., unless max. pressure is limited to 20 psig.

a Solder joints are not to be used for

b Lead solders must not be used in potable-water systems.

c Tin/antimony solder is allowed for potable-water supplies in some jurisdictions.

d Rated pressure for up to 200°F applies to the tube being joined.


 Flared and Compression Joints

Flared and compression fittings can be used to join copper, steel, stainless steel, and aluminum tubing. Properly rated fittings can keep the joints as strong as the tube.

 Flanges

Flanges can be used for large pipe and all piping materials. They are commonly used to connect to equipment and valves, and wherever the joint must be opened to allow service or replacement of components. For steel pipe, flanges are available in pressure ratings to 2500 psig. High-tensile-strength bolts must be used for high-pressure flanged joints.

For welded pipe, weld neck, slip-on, or socket weld flanges are available. Thread-on flanges are available for threaded pipe.

Flanges are generally flat faced or raised face. Flat-faced flanges with full-faced gaskets are most often used with cast iron and materials that cannot take high bending loads. Raised-face flanges with ring gaskets are preferred with steel pipe because they facilitate increasing the sealing pressure on the gasket to help prevent leaks. Other facings, such as O ring and ring joint, are available for special applications.

All flat-faced, raised-face, and lap-joint flanges require a gasket between the mating flange surfaces. Gaskets are made from rubber, synthetic elastomers, cork, fiber, plastic, polytetrafluoroethylene (PTFE), metal, and combinations of these materials. The gasket must be compatible with the flowing media and the temperatures at which the system operates.

 Welding

Welded-steel pipe joints offer the following advantages:

  • Do not age, dry out, or deteriorate as gasketed joints do

  • Can accommodate greater vibration and water hammer and higher temperatures and pressures than other joints

  • For critical service, can be tested by several nondestructive examination (NDE) methods, such as radiography or ultrasound

  • Provide maximum long-term reliability

The applicable sections of the ASME Standard B31 series and the ASME Boiler and Pressure Vessel Code give rules for welding. ASTM Standard B31 requires that all welders and welding procedure specifications (WPS) be qualified. Separate WPS are needed for different welding methods and materials. The qualifying tests and the variables requiring separate procedure specifications are set forth in the ASME Boiler and Pressure Vessel Code, Section IX. The manufacturer, fabricator, or contractor is responsible for the welding procedure and welders. ASME Standard B31.9 requires visual examination of welds and outlines limits of acceptability.

The following welding processes are often used in the HVAC industry:

  • Shielded metal arc welding (SMAW), also called stick welding): the molten weld metal is shielded by vaporization of the electrode coating.

  • Gas metal arc welding (GMAW), also called metal inert gas (MIG) welding: the electrode is a continuously fed wire shielded by argon or carbon dioxide gas from the welding gun nozzle.

  • Gas tungsten arc welding (GTAW), also called tungsten insert gas (TIG) welding: this process uses a nonconsumable tungsten electrode surrounded by a shielding gas. The weld material may be provided from a separate noncoated rod.

 Integrally Reinforced Outlet Fittings

Integrally reinforced outlet fittings are used to make branch and take-off connections and are designed to allow welding directly to pipe without supplemental reinforcing. Fittings are available with threaded, socket welded, or butt-weld outlets.

 Solvent Cement

Solvent cement welds nonmetallic pipe together by softening surface of the materials being joined. It is different from gluing, which hardens and holds the material together. Sometimes this join is called a solvent-welded joint.

 Rolled-Groove Joints

Grooved joints require special grooved fittings and a shallow groove cut or rolled into the pipe end. These joints can be used with steel, cast iron, ductile iron, copper, and plastic pipes. A segmented clamp engages the grooves and a special gasket uses internal pressure to tighten the seal. Some clamps are designed with clearance between tongue and groove to accommodate misalignment and thermal movements, and others are designed to limit movement and provide a rigid system. Manufacturers’ data give temperature and pressure limitations.

 Bell-and-Spigot Joints

A bell-and-spigot joint is mechanical joint consists of a sleeve slightly larger than the outside diameter of the pipe. The pipe ends are inserted into the sleeve, and gaskets are packed into the annular space between the pipe and coupling and held in place by retainer rings. This type of joint can accept some axial misalignment, but it must be anchored or otherwise restrained to prevent axial pullout or lateral movement. Manufacturers provide pressure/temperature data.

 Press-Connect (Press Fit) Joints

These joints rely on an elastomeric gasket or seal and an approved pressing tool and jaws to seal the joint.

 Push-Connect Joints

Push-connect joining use and integral elastomeric seal or gasket and stainless steel ring to make a leak-free joint. There are two common types, both of which form strong, permanent joints: one type is removable for servicing, and the other type is not easily removed after installation.

 Unions

Unions allow disassembly of threaded pipe systems. Unions are three-part fittings with a mating machined seat on the two parts that thread onto the pipe ends. A threaded locking ring holds the two ends tightly together. A union also allows threaded pipe to be turned at the last joint connecting two pieces of equipment. Companion flanges (a pair) for small pipe serve the same purpose.

2.4 EXPANSION JOINTS AND EXPANSION COMPENSATING DEVICES

Although the inherent flexibility of the piping should be used to the maximum extent possible, expansion joints must be used where movements are too large to accommodate with pipe bends or loops or where insufficient room exists to construct a loop of adequate size. Typical situations are tunnel piping and risers in high-rise buildings, especially for steam and hot-water pipes where large thermal movements are involved.

Packed and packless expansion joints and expansion compensating devices are used to accommodate movement, either axially or laterally.

In the axial method of accommodating movement, the expansion joint is installed between anchors in a straight-line segment and accommodates axial motion only. This method has high anchor loads, primarily because of pressure thrust. It requires careful guiding, but expansion joints can be spaced conveniently to limit movement of branch connections. The axial method finds widest application for long runs without natural offsets, such as tunnel and underground piping and risers in tall buildings.

The lateral or offset method requires the device to be installed in a leg perpendicular to the expected movement and accommodates lateral movement only. This method generally has low anchor forces and minimal guide requirements. It finds widest application in lines with natural offsets, especially where there are few or no branch connections.

Packed expansion joints depend on slipping or sliding surfaces to accommodate the movement and require some type of seals or packing to seal the surfaces. Most such devices require some maintenance but are not subject to catastrophic failure. Further, with most packed expansion joint devices, any leaks that develop can be repacked under full line pressure without shutting down the system.

Packless expansion joints depend on the flexing or distortion of the sealing element to accommodate movement. They generally do not require any maintenance, but maintenance or repair is not usually possible. If a leak occurs, the system must be shut off and drained, and the entire device must be replaced. Further, catastrophic failure of the sealing element can occur and, although likelihood of such failure is remote, it must be considered in certain design situations.

Packed expansion joints are preferred where long-term system reliability is of prime importance (using types that can be repacked under full line pressure) and where major leaks can be life threatening or extremely costly. Typical applications are risers, tunnels, underground pipe, and distribution piping systems. Packless expansion joints are generally used where even small leaks cannot be tolerated (e.g., for gas and toxic chemicals), where temperature limitations preclude the use of packed expansion joints, and for very-large-diameter pipe where packed expansion joints cannot be constructed or the cost would be excessive.

In all cases, expansion joints should be installed, anchored, and guided in accordance with expansion joint manufacturers’ recommendations.

 Packed Expansion Joints

There are two types of packed expansion joints: packed slip expansion joints and flexible ball joints.

Packed Slip Expansion Joints. These are telescoping devices designed to accommodate axial movement only. Packing seals the sliding surfaces. The original packed slip expansion joint used multiple layers of braided compression packing, similar to the stuffing box commonly used with valves and pumps; this arrangement requires shutting and draining the system for maintenance and repair. Advances in design and packing technology have eliminated these problems, and most current packed slip joints use self-lubricating semiplastic packing, that can be injected under full line pressure without shutting off the system (Figure 7). (Many manufacturers use asbestos-based packings, unless requested otherwise. Asbestos-free packings, such as flake graphite, are available and, although more expensive, should be specified in lieu of products containing asbestos.)

Packed Slip Expansion Joint

Figure 7. Packed Slip Expansion Joint


Standard packed slip expansion joints are constructed of carbon steel with weld or flange ends in sizes 1.5 to 36 in. for pressures up to 300 psig and temperatures up to 800°F. Larger, higher-temperature, and higher-pressure designs are available. Standard single joints are generally designed for 4, 8, or 12 in. axial traverse; double joints with an intermediate anchor base can accommodate twice these movements. Special designs for greater movements are available.

Flexible Ball Joints. These joints are used in pairs to accommodate lateral or offset movement and must be installed in a leg perpendicular to the expected movement. The original flexible ball joint design incorporated only inner and outer containment seals that could not be serviced or replaced without removing the ball joint from the system. The packing technology of the packed slip expansion joint, explained previously, has been incorporated into the flexible ball joint design; now, packed flexible ball joints have self-lubricating semiplastic packing that can be injected under full line pressure without shutting off the system (Figure 8).

Flexible Ball Joint

Figure 8. Flexible Ball Joint


Standard flexible ball joints are available in sizes 1 1/4 to 30 in. with threaded (1 1/4 to 2 in.), weld, and flange ends for pressures to 300 psig and temperatures to 750°F. Flexible ball joints are available in larger sizes and for higher temperature and pressure ranges.

 Packless Expansion Joints

Types include metal bellows expansion joints, rubber expansion joints, and flexible hose or pipe connectors.

Metal Bellows Expansion Joints. These expansion joints have a thin-walled convoluted section that accommodates movement by bending or flexing. The bellows material is generally Type 304, 316, or 321 stainless steel, but other materials are commonly used to satisfy service conditions. Small-diameter expansion joints 3/4 to 3 in. are generally called expansion compensators and are available in all-bronze or steel construction. Metal bellows expansion joints can generally be designed for the pressures and temperatures commonly encountered in HVAC systems and can also be furnished in rectangular configurations for ducts and chimney connectors.

Overpressurization, improper guiding, and other forces can distort the bellows element. For low-pressure applications, such distortion can be controlled by the geometry of the convolution or the thickness of the bellows material. For higher pressure, internally pressurized joints require reinforcing. Externally pressurized designs are not subject to such distortion and are not generally furnished without supplemental bellows reinforcing.

Single- and double-bellows expansion joints primarily accommodate axial movement only, similar to packed slip expansion joints. Although bellows expansion joints can accommodate some lateral movement, the universal tied bellows expansion joint better accommodates large lateral movement. This device operates much like a pair of flexible ball joints, except that bellows elements are used instead of flexible ball elements. The tie rods on this joint contain the pressure thrust, so anchor loads are much lower than with axial-type expansion joints.

Rubber Expansion Joints. Similar to single-metal bellows expansion joints, rubber expansion joints incorporate a nonmetallic elastomeric bellows sealing element and generally have more stringent temperature and pressure limitations. Although rubber expansion joints can be used to accommodate expansion and contraction of the piping, they are primarily used as flexible connectors at equipment to isolate sound and vibration and eliminate stress at equipment nozzles.

Table 21 Piping System Design Maximum Flow Rate for Energy Conservationa,b

Operating Hours/year

≤2000

>2000 and ≤4400

>4400

Pipe Size, in.

Other

Variable Flow/Variable Speed

Other

Variable Flow/Variable Speed

Other

Variable Flow/Variable Speed

Nominal

IPS Sched. 40 Std. ID

gpm

fps

gpm

fps

gpm

fps

gpm

fps

gpm

fps

gpm

fps

2.5

2.469

120

8.04

180

12.06

85

5.7

130

8.71

68

4.56

110

7.37

3

3.068

180

7.81

270

11.72

140

6.08

210

9.12

110

4.77

170

7.38

4

4.026

350

8.82

530

13.36

260

6.55

400

10.08

210

5.29

320

8.07

5

5.047

410

6.58

620

9.94

310

4.97

470

7.54

250

4.01

370

5.93

6

6.056

750

8.35

1100

12.25

570

6.35

860

9.58

440

4.90

680

7.58

8

7.981

1200

7.70

1800

11.55

900

5.77

1400

8.98

700

4.49

1100

7.06

10

10.02

1800

7.32

2700

10.99

1300

5.29

2000

8.14

1000

4.07

1600

6.51

12

11.938

2500

7.17

3800

10.89

1900

5.45

2900

8.13

1500

4.30

2300

6.59

>12

 

NA

8.5

NA

13.0

NA

6.5

NA

9.5

NA

5

NA

7.5

a Source: Based on ASHRAE Standard 90.1-2013 Table 6.5.4.5 with the addition of IPS and calculation for velocity in feet per second (fps).

b This table does not apply to district energy systems, and velocities in larger-bore piping can exceed these values per an interpretation of the ASHRAE 90.1 committee.


Flexible Hose. This type of hose can be constructed of elastomeric material or corrugated metal with an outer braid for reinforcing and end restraint. Flexible hose is primarily used as a flexible connector at equipment to isolate sound and vibration and eliminate stress at equipment nozzles; however, flexible metal hose is well suited for use as an offset-type expansion joint, especially for copper tubing and branch connections off risers.

Table 22 Water Velocities Based on Type of Service

Type of Service

Velocity, fps

Reference

General service

4 to 10

a, b, c

City water

3 to 7

a, b

 

2 to 5

c

Boiler feed

6 to 15

a, c

Pump suction and drain lines

4 to 7

a, b

a Crane Co. (1976).

b Carrier (1960).

c Grinnell Company (1951).


3. APPLICATIONS

3.1 WATER PIPING

 Flow Rate Limitations

Stewart and Dona (1987) surveyed the literature relating to water flow rate limitations. Noise, erosion, and installation and operating costs all limit the maximum and minimum velocities in piping systems. If piping sizes are too small, noise levels, erosion levels, and pumping costs can be unfavorable. If piping sizes are too large, installation costs are excessive. Therefore, pipe sizes are chosen to minimize initial cost while avoiding the undesirable effects of high velocities. ASHRAE Standard 90.1 has been accepted by authorities having jurisdiction (AHJs) as a code and, as such, limits the flow for energy conservation. The table (Table 21) is reproduced with modification showing velocity limitations.

Various upper limits of water velocity and/or pressure drop in piping and piping systems are used. One recommendation places a velocity limit of 4 fps for 2 in. pipe and smaller, and a pressure drop limit of 4 ft of water/100 ft for piping over 2 in. Other guidelines are based on the type of service (Table 22) or annual operating hours (Table 23). These limitations are imposed either to control the levels of pipe and valve noise, erosion, and water hammer pressure or for economic reasons. Carrier (1960) recommends that the velocity not exceed 15 fps in any case.

 Noise Generation

Velocity-dependent noise in piping and piping systems results from any or all of four sources: turbulence, cavitation, release of entrained air, and water hammer. In investigations of flow-related noise, Ball and Webster (1976), Marseille (1965), and Rogers (1953, 1954, 1956) reported that velocities on the order of 10 to 17 fps lie within the range of allowable noise levels for residential and commercial buildings. The experiments showed considerable variation in noise levels obtained for a specified velocity. Generally, systems with longer pipe and with more numerous fittings and valves were noisier. In addition, sound measurements were taken under widely differing conditions; for example, some tests used plastic-covered pipe, whereas others did not. Thus, no detailed correlations relating sound level to flow velocity in generalized systems are available.

Table 23 Maximum Water Velocity to Minimize Erosion

Normal Operation, h/yr

Water Velocity, fps

1500

15

2000

14

3000

13

4000

12

6000

10

Source: Carrier (1960).


Noise generated by fluid flow in a pipe increases sharply if cavitation or release of entrained air occurs. Usually, the combination of high water velocity with a change in flow direction or a decrease in pipe cross section, causing a sudden pressure drop, is necessary to cause cavitation. Ball and Webster (1976) found that at their maximum velocity of 42 fps, cavitation did not occur in straight 3/8 and 1/2 in. pipe; using the apparatus with two elbows, cold-water velocities up to 21 fps caused no cavitation. Cavitation did occur in orifices of 1:8 area ratio (orifice flow area is one-eighth of pipe flow area) at 5 fps and in 1:4 area ratio orifices at 10 fps (Rogers 1954).

Some data are available for predicting hydrodynamic (liquid) noise generated by control valves. The International Society of Automation compiled prediction correlations in an effort to develop control valves for reduced noise levels (ISA 2007). The correlation to predict hydrodynamic noise from control valves is

(20)

where

SL = sound level, dB
Cv = valve coefficient, gpm/(psi)0.5
Q = flow rate, gpm
Δp = pressure drop across valve, psi
t = downstream pipe wall thickness, in.

Air entrained in water usually has a higher partial pressure than the water. Even when flow rates are small enough to avoid cavitation, the release of entrained air may create noise. Every effort should be made to vent the piping system or otherwise remove entrained air.

 Erosion

Erosion in piping systems is caused by water bubbles, sand, or other solid matter impinging on the inner surface of the pipe. Generally, at velocities lower than 10 fps, erosion is not significant as long as there is no cavitation. When solid matter is entrained in the fluid at high velocities, erosion occurs rapidly, especially in bends. Thus, high velocities should not be used in systems where sand or other solids are present or where slurries are transported.

 Allowances for Aging

With age, the internal surfaces of pipes become increasingly rough. This reduces the available flow with a fixed pressure supply. However, designing with excessive age allowances may result in oversized piping. Age-related decreases in capacity depend on type of water, type of pipe material, temperature of water, and type of system (open or closed) and include

  • Sliming (biological growth or deposited soil on the pipe walls): occurs mainly in unchlorinated, raw water systems.

  • Caking of calcareous salts: occurs in hard water (i.e., water bearing calcium salts) and increases with water temperature.

  • Corrosion (incrustations of ferrous and ferric hydroxide on the pipe walls): occurs in metal pipe in soft water. Because oxygen is necessary for corrosion to take place, significantly more corrosion takes place in open systems.

Allowances for expected decreases in capacity are sometimes treated as a specific amount (percentage). Dawson and Bowman (1933) added an allowance of 15% friction loss to new pipe (equivalent to an 8% decrease in capacity). The HDR Design Guide (1981) increased the friction loss by 15 to 20% for closed piping systems and 75 to 90% for open systems. Carrier (1960) indicates a factor of approximately 1.75 between friction factors for closed and open systems.

Obrecht and Pourbaix (1967) differentiated between the corrosive potential of different metals in potable water systems and concluded that iron is the most severely attacked, then galvanized steel, lead, copper, and finally copper alloys (e.g., brass). Freeman (1941) and Hunter (1941) showed the same trend. After four years of cold- and hot-water use, copper pipe had a capacity loss of 25 to 65%. Aged ferrous pipe has a capacity loss of 40 to 80%. Smith (1983) recommended increasing the design discharge by 1.55 for uncoated cast iron, 1.08 for iron and steel, and 1.06 for cement or concrete.

The Plastic Pipe Institute (1971) found that corrosion is not a problem in plastic pipe; the capacity of plastic pipe in Europe and the United States remains essentially the same after 30 years in use.

Extensive age-related flow data are available for use with the Hazen-Williams empirical equation. Difficulties arise in its application, however, because the original Hazen-Williams roughness coefficients are valid only for the specific pipe diameters, water velocities, and water viscosities used in the original experiments. Thus, when the Cs are extended to different diameters, velocities, and/or water viscosities, errors of up to about 50% in pipe capacity can occur (Sanks 1978; Williams and Hazen 1933).

 Water Hammer

When any moving fluid (not just water) is abruptly stopped, as when a valve closes suddenly, large pressures can develop. Although detailed analysis requires knowledge of the elastic properties of the pipe and the flow-time history, the limiting case of rigid pipe and instantaneous closure is simple to calculate. Under these conditions,

(21)

where

Δph = pressure rise caused by water hammer, lbf/ft2
ρ = fluid density, lbm/ft3
cs = velocity of sound in fluid, fps
V = fluid flow velocity, fps

The cs for water is 4720 fps, although the pipe’s elasticity reduces the effective value.

Example 3.

What is the maximum pressure rise if water flowing at 10 fps is stopped instantaneously?

Solution: Δph = 62.4 × 4720 × 10/32.2 = 91,468 lb/ft2 = 635 psi


3.2 SERVICE WATER PIPING

Sizing service water piping differs from sizing process lines in that design flows in service water piping are determined by the probability of simultaneous operation of multiple individual loads such as water closets, urinals, lavatories, sinks, and showers. The full-flow characteristics of each load device are readily obtained from manufacturers; however, service water piping sized to handle all load devices simultaneously would be seriously oversized. Thus, a major issue in sizing service water piping is to determine the diversity of the loads.

The procedure shown in this chapter uses the work of R.B. Hunter for estimating diversity (Hunter 1940, 1941). The present-day plumbing designer is usually constrained by building or plumbing codes, which specify the individual and collective loads to be used for pipe sizing. Frequently used codes (including the ICC International Plumbing Code and the PHCC National Standard Plumbing Code) contain procedures quite similar to those shown here. The designer must be aware of the applicable code for the location being considered.

Federal mandates are forcing plumbing fixture manufacturers to reduce design flows to many types of fixtures, but these may not yet be included in locally adopted codes. Also, the designer must be aware of special considerations; for example, toilet usage at sports arenas will probably have much less diversity than codes allow and thus may require larger supply piping than the minimum specified by codes.

Table 24 gives the rate of flow desirable for many common fixtures and the average pressure necessary to give this rate of flow. Pressure varies with fixture design.

In estimating load, the rate of flow is frequently computed in fixture units that are relative indicators of flow. Table 25 gives the demand weights in terms of fixture units for different plumbing fixtures under several conditions of service, and Figure 9 gives the estimated demand corresponding to any total number of fixture units. Figures 10 and 11 provide more accurate estimates at the lower end of the scale.

The estimated demand load for fixtures used intermittently on any supply pipe can be obtained by multiplying the number of each kind of fixture supplied through that pipe by its weight from Table 25, adding the products, and then referring to the appropriate curve of Figure 9, 10, or 11 to find the demand corresponding to the total fixture units. In using this method, note that the demand for fixture or supply outlets other than those listed in the table of fixture units is not yet included in the estimate. The demands for outlets (e.g., hose connections and air-conditioning apparatus) that are likely to impose continuous demand during heavy use of the weighted fixtures should be estimated separately and added to demand for fixtures used intermittently to estimate total demand.

Demand Versus Fixture Units, Mixed System, High Part of Curve (Adapted from Hunter 1941)

Figure 9. Demand Versus Fixture Units, Mixed System, High Part of Curve (Adapted from Hunter 1941)


Estimate Curves for Demand Load (Adapted from Hunter 1941)

Figure 10. Estimate Curves for Demand Load (Adapted from Hunter 1941)


Section of Figure 10 on Enlarged Scale

Figure 11. Section of Figure 10 on Enlarged Scale


Table 24 Proper Flow and Pressure Required During Flow for Different Fixtures

Fixture

Flow Pressure, psiga

Flow, gpm

Ordinary basin faucet

8

3.0

Self-closing basin faucet

12

2.5

Sink faucet, 3/8 in.

10

4.5

Sink faucet, 1/2 in.

5

4.5

Dishwasher

15 to 25

b

Bathtub faucet

5

6.0

Laundry tube cock, 1/4 in.

5

5.0

Shower

12

3 to 10

Ball cock for closet

15

3.0

Flush valve for closet

10 to 20

15 to 40c

Flush valve for urinal

15

15.0

Garden hose, 50 ft, and sill cock

30

5.0

a Flow pressure is that in pipe at entrance to fixture.

b Varies; see manufacturers’ data.

c Wide range because of variation in design and type of flush valve closets.


Table 25 Demand Weights of Fixtures in Fixture Unitsa

Fixture or Groupb

Occupancy

Type of Supply Control

Weight in Fixture Unitsc

Water closet

Public

Flush valve

10

   

Flush tank

5

Pedestal urinal

Public

Flush valve

10

Stall or wall urinal

Public

Flush valve

5

   

Flush tank

3

Lavatory

Public

Faucet

2

Bathtub

Public

Faucet

4

Shower head

Public

Mixing valve

4

Service sink

Office, etc.

Faucet

3

Kitchen sink

Hotel or restaurant

Faucet

4

Water closet

Private

Flush valve

6

   

Flush tank

3

Lavatory

Private

Faucet

1

Bathtub

Private

Faucet

2

Shower head

Private

Mixing valve

2

Bathroom group

Private

Flush valve for closet

8

   

Flush tank for closet

6

Separate shower

Private

Mixing valve

2

Kitchen sink

Private

Faucet

2

Laundry trays (1 to 3)

Private

Faucet

3

Combination fixture

Private

Faucet

3

Source: Hunter (1941).

a For supply outlets likely to impose continuous demands, estimate continuous supply separately, and add to total demand for fixtures.

b For fixtures not listed, weights may be assumed by comparing fixture to listed one using water in similar quantities and at similar rates.

c Given weights are for total demand. For fixtures with both hot- and cold-water supplies, weights for maximum separate demands can be assumed to be 75% of listed demand for the supply.


The Hunter curves in Figures 9, 10, and 11 are based on use patterns in residential buildings and can be erroneous for other usages such as sports arenas. Williams (1976) discusses the Hunter assumptions and presents an analysis using alternative assumptions.

So far, the information presented shows the design rate of flow to be determined in any particular section of piping. The next step is to determine the size of piping. As water flows through a pipe, the pressure continually decreases along the pipe because of loss of energy from friction. The problem is then to ascertain the minimum pressure in the street main and the minimum pressure required to operate the topmost fixture. (A pressure of 15 psig may be ample for most flush valves, but manufacturers’ requirements should be consulted. Some fixtures require a pressure up to 25 psig. A minimum of 8 psig should be allowed for other fixtures.) The pressure differential overcomes pressure losses in the distributing system and the difference in elevation between the water main and the highest fixture.

The pressure loss (in psi) resulting from the difference in elevation between the street main and the highest fixture can be obtained by multiplying the difference in elevation in feet by the conversion factor 0.434.

Pressure losses in the distributing system consist of pressure losses in the piping itself, plus the pressure losses in the pipe fittings, valves, and the water meter, if any. Approximate design pressure losses and flow limits for disk-type meters for various rates of flow are given in Figure 12. Water authorities in many localities require compound meters for greater accuracy with varying flow; consult the local utility. Design data for compound meters differ from the data in Figure 12. Manufacturers give data on exact pressure losses and capacities.

Figure 13 shows the variation of pressure loss with rate of flow for various faucets and cocks. The water demand for hose bibbs or other large-demand fixtures taken off the building main frequently results in inadequate water supply to the upper floor of a building. This condition can be prevented by sizing the distribution system so that pressure drops from the street main to all fixtures are the same. An ample building main (not less than 1 in. where possible) should be maintained until all branches to hose bibbs have been connected. Where street main pressure is excessive and a pressure-reducing valve is used to prevent water hammer or excessive pressure at fixtures, hose bibbs should be connected ahead of the reducing valve.

The principles involved in sizing upfeed and downfeed systems are the same. In the downfeed system, however, the difference in elevation between the overhead supply mains and the fixtures provides the pressure required to overcome pipe friction. Because friction pressure loss and height pressure loss are not additive, as in an upfeed system, smaller pipes may be used with a downfeed system.

Pressure Losses in Disk-Type Water Meters

Figure 12. Pressure Losses in Disk-Type Water Meters


Variation of Pressure Loss with Flow Rate for Various Faucets and Cocks

Figure 13. Variation of Pressure Loss with Flow Rate for Various Faucets and Cocks


 Plastic Pipe

The maximum safe water velocity in a thermoplastic piping system under most operating conditions is typically 5 fps; however, higher velocities can be used in cases where the operating characteristics of valves and pumps are known so that sudden changes in flow velocity can be controlled. The total pressure in the system at any time (operating pressure plus surge of water hammer) should not exceed 150% of the pressure rating of the system.

 Procedure for Sizing Cold-Water Systems

The recommended procedure for sizing piping systems is as follows:

  1. Sketch the main lines, risers, and branches, and indicate the fixtures to be served. Indicate the rate of flow of each fixture.

  2. Using Table 25, compute the demand weights of the fixtures in fixture units.

  3. Determine the total demand in fixture units and, using Figure 9, 10, or 11, find the expected demand.

  4. Determine the equivalent length of pipe in the main lines, risers, and branches. Because the sizes of the pipes are not known, the exact equivalent length of various fittings cannot be determined. Add the equivalent lengths, starting at the street main and proceeding along the service line, main line of the building, and up the riser to the top fixture of the group served.

  5. Determine the average minimum pressure in the street main and the minimum pressure required for operation of the topmost fixture, which should be 8 to 25 psi.

  6. Calculate the approximate design value of the average pressure drop per 100 ft of equivalent length of pipe determined in step 4 and using Equation (1).

    where

    Δp = average pressure loss per 100 ft of equivalent length of pipe, psi
    ps = pressure in street main, psig
    pf = minimum pressure required to operate topmost fixture, psig
    pm = pressure drop through water meter, psi
    H = height of highest fixture above street main, ft
    L = equivalent length determined in step 4, ft
  7. If the system is downfeed supply from a gravity tank, height of water in the tank, converted to psi by multiplying by 0.434, replaces the street main pressure, and the term 0.434H is added instead of subtracted in calculating Δp. In this case, H is the vertical distance of the fixture below the bottom of the tank. The pressure conversion factor 0.434 is determined by the weight of water occupying a 1 ft3 volume, or 62.4/144 = 0.434 psi per foot of water.

  8. From the expected rate of flow determined in step 3 and the value of Δp calculated in step 6, choose the sizes of pipe from Figure 14, 15, or 16.

Example 4.

Assume a minimum street main pressure of 55 psig; a height of topmost fixture (a urinal with flush valve) above street main of 50 ft; an equivalent pipe length from water main to highest fixture of 100 ft; a total load on the system of 50 fixture units; and that the water closets are flush valve operated. Find the required size of supply main.

Solution: Use Equation (1):

ps = Street main pressure (given) = 55 psig
H = 50 ft (given)
Pf = 15 psig from Table 24
Flow = 51 gpm from Figure 11

For a trial run, use 1 1/2 in.; then Pm= 6.5 psig from Figure 12 at 51 gpm. The pressure drop available for overcoming friction in pipes and fittings is 55 – 0.434 × 50 – 15 – 6.5 = 12 psi.

At this point, estimate the equivalent pipe length of the fittings on the direct line from the street main to the highest fixture. The exact equivalent length of the various fittings cannot be determined because the pipe sizes of the building main, riser, and branch leading to the highest fixture are not yet known, but a first approximation is necessary to tentatively select pipe sizes. If the computed pipe sizes differ from those used in determining the equivalent length of pipe fittings, a recalculation using the computed pipe sizes for the fittings will be necessary. It is common practice for the first trial to assume that the total equivalent length of the pipe fittings is 50% of the total length of pipe. In this example, 100 ft × 50% = 50 ft.

The permissible pressure loss per 100 ft of equivalent pipe is 12 × 100/(100 + 50) = 8 psi or 18 ft/100 ft. A 1  1/2 in. building main is adequate.

The sizing of the branches of the building main, the risers, and the fixture branches follows these principles. For example, assume that one of the branches of the building main carries the cold-water supply for three water closets, two bathtubs, and three lavatories. Using the permissible pressure loss of 8 psi per 100 ft, the size of branch (determined from Table 25 and Figures 14 and 11) is found to be 1 1/2 in. Items included in the computation of pipe size are as follows:

Fixtures, No. and Type

Fixture Units (Table 25 and Note c)

Demand (Figure 11)

Pipe Size (Figure 14)

3 flush valves

3 × 6 = 18

   

2 bathtubs

0.75 × 2 × 2 = 3

   

3 lavatories

0.75 × 3 × 1 = 2.25

   

Total

= 23.25

38 gpm

1 1/2 in.


Table 26 is a guide to minimum pipe sizing where flush valves are used.

Velocities exceeding 10 fps cause undesirable noise in the piping system. This usually governs the size of larger pipes in the system, whereas in small pipe sizes, the friction loss usually governs the selection because the velocity is low compared to friction loss. Velocity is the governing factor in downfeed systems, where friction loss is usually neglected. Velocity in branches leading to pump suctions should not exceed 5 fps.

If the street pressure is too low to adequately supply upper-floor fixtures, the pressure must be increased. Constant- or variable-speed booster pumps, alone or in conjunction with gravity supply tanks, or hydropneumatic systems may be used.

Flow control valves for individual fixtures under varying pressure conditions automatically adjust flow at the fixture to a predetermined quantity. These valves allow the designer to (1) limit flow at the individual outlet to the minimum suitable for the purpose, (2) hold total demand for the system more closely to the required minimum, and (3) design the piping system as accurately as is practicable for the requirements.

Table 26 Allowable Number of 1 in. Flush Valves Served by Various Sizes of Water Pipe*

Pipe Size, in.

No. of 1 in. Flush Valves

1 1/4

1

1 1/2

2 to 4

2

5 to 12

2 1/2

13 to 25

3

26 to 40

4

41 to 100

* Two 3/4 in. flush valves are assumed equal to one 1 in. flush valve but can be served by a 1 in. pipe. Water pipe sizing must consider demand factor, available pressure, and length of run.


 Hydronic System Piping

The Darcy-Weisbach equation with friction factors from the Moody chart or Colebrook equation (or, alternatively, the Hazen-Williams equation) is fundamental to calculating pressure drop in hot- and chilled-water piping; however, charts calculated from these equations (such as Figures 14, 15, and 16) provide easy determination of pressure drops for specific fluids and pipe standards. In addition, tables of pressure drops can be found in Crane Co. (1976) and Hydraulic Institute (1990).

The Reynolds numbers represented on the charts in Figures 14, 15, and 16 are all in the turbulent flow regime. For smaller pipes and/or lower velocities, the Reynolds number may fall into the laminar regime, in which the Colebrook friction factors are no longer valid.

Most tables and charts for water are calculated for properties at 60°F. Using these for hot water introduces some error, although the answers are conservative (i.e., cold-water calculations overstate the pressure drop for hot water). Using 60°F water charts for 200°F water should not result in errors in Δp exceeding 20%.

 Range of Usage of Pressure Drop Charts

General Design Range. The general range of pipe friction loss used for design of hydronic systems is between 1 and 4 ft of water per 100 ft of pipe. A value of 2.5 ft/100 ft represents the mean to which most systems are designed. Wider ranges may be used in specific designs if certain precautions are taken.

Friction Valvesfriction lossesValvesRegulators Loss for Water in Commercial Steel Pipe (Schedule 40)

Figure 14. Friction Loss for Water in Commercial Steel Pipe (Schedule 40)


Friction Loss for Water in Copper Tubing (Types K, L, M)

Figure 15. Friction Loss for Water in Copper Tubing (Types K, L, M)


Friction Loss for Water in Plastic Pipe (Schedule 80)

Figure 16. Friction Loss for Water in Plastic Pipe (Schedule 80)


Table 27 Equivalent Length in Feet of Pipe for 90° Elbows

Velocity, fps

Pipe Size

1/2

3/4

1

1 1/4

1 1/2

2

2 1/2

3

3 1/2

4

5

6

8

10

12

1

1.2

1.7

2.2

3.0

3.5

4.5

5.4

6.7

7.7

8.6

10.5

12.2

15.4

18.7

22.2

2

1.4

1.9

2.5

3.3

3.9

5.1

6.0

7.5

8.6

9.5

11.7

13.7

17.3

20.8

24.8

3

1.5

2.0

2.7

3.6

4.2

5.4

6.4

8.0

9.2

10.2

12.5

14.6

18.4

22.3

26.5

4

1.5

2.1

2.8

3.7

4.4

5.6

6.7

8.3

9.6

10.6

13.1

15.2

19.2

23.2

27.6

5

1.6

2.2

2.9

3.9

4.5

5.9

7.0

8.7

10.0

11.1

13.6

15.8

19.8

24.2

28.8

6

1.7

2.3

3.0

4.0

4.7

6.0

7.2

8.9

10.3

11.4

14.0

16.3

20.5

24.9

29.6

7

1.7

2.3

3.0

4.1

4.8

6.2

7.4

9.1

10.5

11.7

14.3

16.7

21.0

25.5

30.3

8

1.7

2.4

3.1

4.2

4.9

6.3

7.5

9.3

10.8

11.9

14.6

17.1

21.5

26.1

31.0

9

1.8

2.4

3.2

4.3

5.0

6.4

7.7

9.5

11.0

12.2

14.9

17.4

21.9

26.6

31.6

10

1.8

2.5

3.2

4.3

5.1

6.5

7.8

9.7

11.2

12.4

15.2

17.7

22.2

27.0

32.0


Piping Noise. Closed-loop hydronic system piping is generally sized below certain arbitrary upper limits, such as a velocity limit of 4 fps for 2 in. pipe and under, and a pressure drop limit of 4 ft per 100 ft for piping over 2 in. in diameter. Velocities in excess of 4 fps can be used in piping of larger size. This limitation is generally accepted, although it is based on relatively inconclusive experience with noise in piping. Water velocity noise is not caused by water but by free air, sharp pressure drops, turbulence, or a combination of these, that cause cavitation or flashing of water into steam. Therefore, higher velocities may be used if proper precautions are taken to eliminate air and turbulence.

 Air Separation

Air in hydronic systems is usually undesirable because it causes flow noise, allows oxygen to react with piping materials, and sometimes even prevents flow in parts of a system. Air may enter a system at an air/water interface in an open system or in an expansion tank in a closed system, or it may be brought in dissolved in makeup water. Most hydronic systems use air separation devices to remove air. The solubility of air in water increases with pressure and decreases with temperature; thus, separation of air from water is best achieved at the point of lowest pressure and/or highest temperature in a system. For more information, see Chapter 13 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment.

In the absence of venting, air can be entrained in the water and carried to separation units at flow velocities of 1.5 to 2 fps or more in pipe 2 in. and under. Minimum velocities of 2 fps are therefore recommended. For pipe sizes 2 in. and over, minimum velocities corresponding to a head loss of 0.75 ft/100 ft are normally used. Maintaining minimum velocities is particularly important in the upper floors of high-rise buildings where the air tends to come out of solution because of reduced pressures. Higher velocities should be used in downcomer return mains feeding into air separation units located in the basement.

Table 28 Iron and Copper Elbow Equivalents*

Fitting

Iron Pipe

Copper Tubing

Elbow, 90°

1.0

1.0

     45°

0.7

0.7

     90° long-radius

0.5

0.5

     90° welded

0.5

0.5

Reduced coupling

0.4

0.4

Open return bend

1.0

1.0

Angle radiator valve

2.0

3.0

Radiator or convector

3.0

4.0

Boiler or heater

3.0

4.0

Open gate valve

0.5

0.7

Open globe valve

12.0

17.0

Sources: Giesecke (1926) and Giesecke and Badgett (1931, 1932a).

* See Table 10 for equivalent length of one elbow.


Example 5.

Determine the iron pipe size for a circuit requiring 20 gpm flow.

Solution: Enter Figure 4 at 20 gpm, read up to pipe size within normal design range (1 to 4 ft/100 ft), and select 1 1/2 in. Velocity is 3.1 fps, which is between 2 and 4. Pressure loss is 2.9 ft/100 ft.


 Valve and Fitting Pressure Drop

Valves and fittings can be listed in elbow equivalents, with an elbow being equivalent to a length of straight pipe. Table 27 lists equivalent lengths of 90° elbows; Table 28 lists elbow equivalents for valves and fittings for iron and copper.

Example 6.

Determine equivalent feet length of pipe for a 4 in. open gate valve at a flow velocity of approximately 4 fps.

Solution: From Table 27, at 4 fps, each elbow is equivalent to 10.6 ft of 4 in. pipe. From Table 28, the gate valve is equivalent to 0.5 elbows. The actual equivalent pipe length (added to measured circuit length for pressure drop determination) will be 10.6 × 0.5, or 5.3 equivalent feet of 4 in. pipe.


Tee Fitting Pressure Drop. Pressure drop through pipe tees varies with flow through the branch. Figure 17 shows pressure drops for nominal 1 in. tees of equal inlet and outlet sizes and for the flow patterns shown. Idelchik (1986) also presents data for threaded tees.

Elbow Equivalents of Tees at Various Flow Conditions (Giesecke and Badgett 1931, 1932b)

Figure 17. Elbow Equivalents of Tees at Various Flow Conditions (Giesecke and Badgett 1931, 1932b)


Different investigators present tee loss data in different forms, and it is sometimes difficult to reconcile results from several sources. As an estimate of the upper limit to tee losses, a pressure or head loss coefficient of 1.0 may be assumed for entering and leaving flows (i.e., ).

Example 7.

Determine the pressure or head losses for a 1 in. (all openings) threaded pipe tee flowing 25% to the side branch, 75% through. The entering flow is 10 gpm (3.71 fps).

Solution: From Figure 17, bottom curve, the number of equivalent elbows for the through-flow is 0.15 elbows; the through-flow is 7.5 gpm (2.78 fps); and the head loss or pressure drop is based on the exit flow rate. Table 27 gives the equivalent length of a 1 in. elbow at 3 fps as 2.7 ft. Using Figure 14, the head loss is 4 ft/100 ft for 1 in. pipe and 7.5 gpm flow.

From Figure 17, top curve, the number of equivalent elbows for the branch flow of 25% is 13 elbows; the branch flow is 2.5 gpm (0.93 fps); and the head loss or pressure drop is based on the exit flow rate. Table 27 gives the equivalent of a 1 in. elbow at 1 fps as 2.2 ft. Using Figure 14, the head loss is 0.55 ft/100 ft for 1 in. pipe and 2.5 gpm flow.


3.3 STEAM PIPING

Pressure losses in steam piping for flows of dry or nearly dry steam are governed by Equations (2) to (8) in the section on Design Equations. This section incorporates these principles with other information specific to steam systems.

 Pipe Sizes

Required pipe sizes for a given load in steam heating depend on the following factors:

  • The initial pressure and the total pressure drop that can be allowed between the source of supply and the end of the return system

  • The maximum velocity of steam allowable for quiet and dependable operation of the system, taking into consideration the direction of condensate flow

  • The equivalent length of the run from the boiler or source of steam supply to the farthest heating unit

Initial Pressure and Pressure Drop. Table 29 lists pressure drops commonly used with corresponding initial steam pressures for sizing steam piping.

Several factors, such as initial pressure and pressure required at the end of the line, should be considered, but it is most important that (1) the total pressure drop does not exceed the initial gage pressure of the system (in practice, it should never exceed one-half the initial gage pressure); (2) pressure drop is not great enough to cause excessive velocities; (3) a constant initial pressure is maintained, except on systems specially designed for varying initial pressures (e.g., subatmospheric pressure), that normally operate under controlled partial vacuums; and (4) for gravity return systems, pressure drop to heating units does not exceed the water column available for removing condensate (i.e., height above the boiler water line of the lowest point on the steam main, on the heating units, or on the dry return).

Maximum Velocity. For quiet operation, steam velocity should be 8000 to 12,000 fpm, with a maximum of 15,000 fpm. The lower the velocity, the quieter the system. When condensate must flow against the steam, even in limited quantity, the steam’s velocity must not exceed limits above which the disturbance between the steam and the counterflowing water may (1) produce objectionable sound, such as water hammer, or (2) result in the retention of water in certain parts of the system until the steam flow is reduced sufficiently to allow water to pass. These limits are a function of (1) pipe size; (2) pitch of the pipe if it runs horizontally; (3) quantity of condensate flowing against the steam; and (4) freedom of the piping from water pockets that, under certain conditions, act as a restriction in pipe size. Table 30 lists maximum capacities for various size steam lines.

Table 29 Pressure Drops Used for Sizing Steam Pipe*

Initial Steam Pressure, psig

Pressure Drop per 100 ft

Total Pressure Drop in Steam Supply Piping

Vacuum return

2 to 4 oz/in2

1 to 2 psi

0

0.5 oz/in2

1 oz/in2

1

2 oz/in2

1 to 4 oz/in2

2

2 oz/in2

8 oz/in2

5

4 oz/in2

1.5 psi

10

8 oz/in2

3 psi

15

1 psi

4 psi

30

2 psi

5 to 10 psi

50

2 to 5 psi

10 to 15 psi

100

2 to 5 psi

15 to 25 psi

150

2 to 10 psi

25 to 30 psi

* Equipment, control valves, and so forth must be selected based on delivered pressures.


Equivalent Length of Run. All tables for the flow of steam in pipes based on pressure drop must allow for pipe friction, as well as for the resistance of fittings and valves. These resistances are generally stated in terms of straight pipe; that is, a certain fitting produces a drop in pressure equivalent to the stated length of straight run of the same size of pipe. Table 31 gives the length of straight pipe usually allowed for the more common types of fittings and valves. In all pipe sizing tables in this chapter, length of run refers to the equivalent length of run as distinguished from the actual length of pipe. A common sizing method is to assume the length of run and to check this assumption after pipes are sized. For this purpose, length of run is usually assumed to be double the actual length of pipe.

Table 30 Comparative Capacity of Steam Lines at Various Pitches for Steam and Condensate Flowing in Opposite Directions

Pitch of Pipe, in/10 ft

Nominal Pipe Diameter, in.

3/4

1

1 1/4

1 1/2

2

Capacity

Maximum Velocity

Capacity

Maximum Velocity

Capacity

Maximum Velocity

Capacity

Maximum Velocity

Capacity

Velocity

1/4

3.2

8

6.8

9

11.8

11

19.8

12

42.9

15

1/2

4.1

11

9.0

12

15.9

14

25.9

16

54.0

18

1

5.7

13

11.7

15

19.9

17

33.0

19

68.8

24

1 1/2

6.4

14

12.8

17

24.6

20

37.4

22

83.3

27

2

7.1

16

14.8

19

27.0

22

42.0

24

92.9

30

3

8.3

17

17.3

22

31.3

25

46.8

26

99.6

32

4

9.9

22

19.2

24

33.4

26

50.8

28

102.4

32

5

10.5

22

20.5

25

38.5

31

59.2

33

115.0

33

Source: Laschober et al. (1966).

Velocity in fps; capacity in lb/h.


Example 8.

Using Table 31, determine the equivalent length in feet of pipe for the run shown.


 Sizing Charts

Figure 18 is the basic chart for determining the flow rate and velocity of steam in Schedule 40 pipe for various values of pressure drop per 100 ft, based on 0 psig saturated steam. Figures 19A through 19D present charts for sizing steam piping for systems of 30, 50, 100, and 150 psig at various pressure drops. These charts are based on the Moody friction factor, which considers the Reynolds number and the roughness of the internal pipe surfaces; they contain the same information as the basic chart (Figure 18) but in a more convenient form.

Using the multiplier chart (Figure 20), Figure 18 can be used at all saturation pressures between 0 and 200 psig (see Example 10).

3.4 LOW-PRESSURE STEAM PIPING

Values in Table 32 (taken from Figure 18) provide a more rapid means of selecting pipe sizes for the various pressure drops listed and for systems operated at 3.5 and 12 psig. The flow rates shown for 3.5 psig can be used for saturated pressures from 1 to 6 psig, and those shown for 12 psig can be used for saturated pressures from 8 to 16 psig with an error not exceeding 8%.

Table 31 Equivalent Length of Fittings to Be Added to Pipe Run

Nominal Pipe Diameter, in.

Length to Be Added to Run, ft

Standard Elbow

Side Outlet Teeb

Gate Valvea

Globe Valvea

Angle Valvea

1/2

1.3

3

0.3

14

7

3/4

1.8

4

0.4

18

10

1

2.2

5

0.5

23

12

1 1/4

3.0

6

0.6

29

15

1 1/2

3.5

7

0.8

34

18

2

4.3

8

1.0

46

22

2 1/2

5.0

11

1.1

54

27

3

6.5

13

1.4

66

34

3 1/2

8

15

1.6

80

40

4

9

18

1.9

92

45

5

11

22

2.2

112

56

6

13

27

2.8

136

67

8

17

35

3.7

180

92

10

21

45

4.6

230

112

12

27

53

5.5

270

132

14

30

63

6.4

310

152

a Valve in full-open position.

b Values apply only to a tee used to divert the flow in the main to the last riser.


Both Figure 18 and Table 32 can be used where the flow of condensate does not inhibit the flow of steam. Columns B and C of Table 33 are used in cases where steam and condensate flow in opposite directions, as in risers or runouts that are not dripped. Columns D, E, and F are for one-pipe systems and include risers, radiator valves and vertical connections, and radiator and riser runout sizes, all of which are based on the critical velocity of the steam to allow counterflow of condensate without noise.

Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 0 psig

Figure 18. Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 0 psig


Return piping can be sized by Table 34, using pipe capacities for wet, dry, and vacuum return lines for several values of pressure drop per 100 ft of equivalent length.

Example 9.

What pressure drop should be used for the steam piping of a system if the measured length of the longest run is 500 ft, and the initial pressure must not exceed 2 psig?

Solution: It is assumed, if the measured length of the longest run is 500 ft, that when the allowance for fittings is added, the equivalent length of run does not exceed 1000 ft. Then, with the pressure drop not over one-half of the initial pressure, the drop could be 1 psi or less. With a pressure drop of 1 psi and a length of run of 1000 ft, the drop per 100 ft would be 0.1 psi; if the total drop were 0.5 psi, the drop per 100 ft would be 0.05 psi. In both cases, the pipe could be sized for a desired capacity according to Figure 18.

On completion of the sizing, the drop could be checked by taking the longest line and actually calculating the equivalent length of run from the pipe sizes determined. If the calculated drop is less than that assumed, the pipe size is adequate; if it is more, an unusual number of fittings is probably involved, and either the lines must be straightened, or the next larger pipe size must be tried.


 High-Pressure Steam Piping

Many heating systems for large industrial buildings use high-pressure steam (15 to 150 psig). These systems usually have unit heaters or large built-up fan units with blast heating coils. Temperatures are controlled by a modulating or throttling thermostatic valve or by face or bypass dampers controlled by the room air temperature, fan inlet, or fan outlet.

Table 32 Flow Rate of Steam in Schedule 40 Pipe

Nominal Pipe Size, in.

Pressure Drop per 100 ft of Length

1/16 psi (1 oz/in2)

1/8 psi (2 oz/in2)

1/4 psi (4 oz/in2)

1/2 psi (8 oz/in2)

3/4 psi (12 oz/in2)

1 psi

2 psi

Sat. Press., psig

Sat. Press., psig

Sat. Press., psig

Sat. Press., psig

Sat. Press., psig

Sat. Press., psig

Sat. Press., psig

3.5

12

3.5

12

3.5

12

3.5

12

3.5

12

3.5

12

3.5

12

3/4

9

11

14

16

20

24

29

35

36

43

42

50

60

73

1

17

21

26

31

37

46

54

66

68

82

81

95

114

137

1 1/4

36

45

53

66

78

96

111

138

140

170

162

200

232

280

1 1/2

56

70

84

100

120

147

174

210

218

260

246

304

360

430

2

108

134

162

194

234

285

336

410

420

510

480

590

710

850

2 1/2

174

215

258

310

378

460

540

660

680

820

780

950

1,150

1,370

3

318

380

465

550

660

810

960

1,160

1,190

1,430

1,380

1,670

1,950

2,400

3 1/2

462

550

670

800

990

1,218

1,410

1,700

1,740

2,100

2,000

2,420

2,950

3,450

4

640

800

950

1,160

1,410

1,690

1,980

2,400

2,450

3,000

2,880

3,460

4,200

4,900

5

1,200

1,430

1,680

2,100

2,440

3,000

3,570

4,250

4,380

5,250

5,100

6,100

7,500

8,600

6

1,920

2,300

2,820

3,350

3,960

4,850

5,700

6,800

7,000

8,600

8,400

10,000

11,900

14,200

8

3,900

4,800

5,570

7,000

8,100

10,000

11,400

14,300

14,500

17,700

16,500

20,500

24,000

29,500

10

7,200

8,800

10,200

12,600

15,000

18,200

21,000

26,000

26,200

32,000

30,000

37,000

42,700

52,000

12

11,400

13,700

16,500

19,500

23,400

28,400

33,000

40,000

41,000

49,500

48,000

57,500

67,800

81,000

Notes:

1. Flow rate is in lb/h at initial saturation pressures of 3.5 and 12 psig. Flow is based on Moody friction factor, where the flow of condensate does not inhibit the flow of steam.

2. The flow rates at 3.5 psig cover saturated pressure from 1 to 6 psig, and the rates at 12 psig cover saturated pressure from 8 to 16 psig with an error not exceeding 8%.

3. The steam velocities corresponding to the flow rates given in this table can be found from Figures 18 and 20.


Table 33 Steam Pipe Capacities for Low-Pressure Systems

Nominal Pipe Size, in.

Capacity, lb/h

Two-Pipe System

One-Pipe Systems

Condensate Flowing Against Steam

Supply Risers Upfeed

Radiator Valves and Vertical Connections

Radiator and Riser Runouts

Vertical

Horizontal

A

Ba

Cb

Dc

E

Fb

3/4

8

7

6

7

1

14

14

11

7

7

1 1/4

31

27

20

16

16

1 1/2

48

42

38

23

16

2

97

93

72

42

23

2 1/2

159

132

116

42

3

282

200

200

65

3 1/2

387

288

286

119

4

511

425

380

186

5

1,050

788

278

6

1,800

1,400

545

8

3,750

3,000

10

7,000

5,700

12

11,500

9,500

16

22,000

19,000

Notes:

1. For one- or two-pipe systems in which condensate flows against steam flow.

2. Steam at average pressure of 1 psig used as basis of calculating capacities.

a Do not use column B for pressure drops of less than 1/16 psi per 100 ft of equivalent run. Use Figure 18 or Table 31 instead.

b Pitch of horizontal runouts to risers and radiators should be not less than 0.5 in/ft. Where this pitch cannot be obtained, runouts over 8 ft in length should be one pipe size larger than that called for in this table.

c Do not use column D for pressure drops of less than 1/24 psi per 100 ft of equivalent run except on sizes 3 in. and over. Use Figure 18 or Table 31 instead.


 Use of Basic and Velocity Multiplier Charts

Example 10.

Given a flow rate of 6700 lb/h, an initial steam pressure of 100 psig, and a pressure drop of 11 psi/100 ft, find the size of Schedule 40 pipe required and the velocity of steam in the pipe.

Solution: The following steps are shown by the broken line on Figures 18 and 20.

1. Enter Figure 18 at a flow rate of 6700 lb/h, and move vertically to the horizontal line at 100 psig

2. Follow along inclined multiplier line (upward and to the left) to horizontal 0 psig line. The equivalent mass flow at 0 psig is about 2500 lb/h.

3. Follow the 2500 lb/h line vertically until it intersects the horizontal line at 11 psi per 100 ft pressure drop. Nominal pipe size is 2 1/2 in. The equivalent steam velocity at 0 psig is about 32,700 fpm.

4. To find the steam velocity at 100 psig, locate the value of 32,700 fpm on the ordinate of the velocity multiplier chart (Figure 20) at 0 psig.

5. Move along the inclined multiplier line (downward and to the right) until it intersects the vertical 100 psig pressure line. The velocity as read from the right (or left) scale is about 13,000 fpm.

Note: Steps 1 through 5 would be rearranged or reversed if different data were given.


3.5 STEAM CONDENSATE SYSTEMS

The majority of steam systems used in heating applications are two-pipe systems (steam pipe and condensate pipe). This discussion is limited to sizing the condensate lines in two-pipe systems.

 Two-Pipe Systems

When steam is used for heating a liquid to 215°F or less (e.g., in domestic water heat exchangers, domestic heating water converters, or air-heating coils), the devices are usually provided with a steam control valve. As the control valve throttles, the absolute pressure in the load device decreases, removing all pressure motivation for flow in the condensate return system. To ensure the flow of steam condensate from the load device through the trap and into the return system, it is necessary to provide a vacuum breaker on the device ahead of the trap. This ensures a minimum pressure at the trap inlet of atmospheric pressure plus whatever liquid leg the designer has provided. Then, to ensure flow through the trap, it is necessary to design the condensate system so that it will never have a pressure above atmospheric in the condensate return line.

Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 30 psig

Figure 19A. Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 30 psig


Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 50 psig

Figure 19B. Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 50 psig


Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 100 psig

Figure 19C. Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 100 psig


Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 150 psig

Figure 19D. Flow Rate and Velocity of Steam in Schedule 40 Pipe at Saturation Pressure of 150 psig


Table 34 Return Main and Riser Capacities for Low-Pressure Systems, lb/h

 

Pipe Size, in.

1/32 psi (1/2 oz/in2) Drop per 100 ft

1/24 psi (2/3 oz/in2) Drop per 100 ft

1/16 psi (1 oz/in2) Drop per 100 ft

1/8 psi (2 oz/in2) Drop per 100 ft

1/4 psi (4 oz/in2) Drop per 100 ft

1/2 psi (8 oz/in2) Drop per 100 ft

Wet

Dry

Vac.

Wet

Dry

Vac.

Wet

Dry

Vac.

Wet

Dry

Vac.

Wet

Dry

Vac.

Wet

Dry

Vac.

 

G

H

I

J

K

L

M

N

O

P

Q

R

S

T

U

V

W

X

Y

Return Main

3/4

42

100

142

200

283

1

125

62

145

71

143

175

80

175

250

103

249

350

115

350

494

1 1/4

213

130

248

149

244

300

168

300

425

217

426

600

241

600

848

1 1/2

338

206

393

236

388

475

265

475

675

340

674

950

378

950

1,340

2

700

470

810

535

815

1,000

575

1,000

1,400

740

1,420

2,000

825

2,000

2,830

2 1/2

1,180

760

1,580

868

1,360

1,680

950

1,680

2,350

1,230

2,380

3,350

1,360

3,350

4,730

3

1,880

1,460

2,130

1,560

2,180

2,680

1,750

2,680

3,750

2,250

3,800

5,350

2,500

5,350

7,560

3 1/2

2,750

1,970

3,300

2,200

3,250

4,000

2,500

4,000

5,500

3,230

5,680

8,000

3,580

8,000

11,300

4

3,880

2,930

4,580

3,350

4,500

5,500

3,750

5,500

7,750

4,830

7,810

11,000

5,380

11,000

15,500

5

7,880

9680

13,700

19,400

27,300

6

12,600

15,500

22,000

31,000

43,800

Riser

3/4

48

48

143

48

175

48

249

48

350

494

1

113

113

244

113

300

113

426

113

600

848

1 1/4

248

248

388

248

475

248

674

248

950

1,340

1 1/2

375

375

815

375

1,000

375

1,420

375

2,000

2,830

2

750

750

1,360

750

1,680

750

2,380

750

3,350

4,730

2 1/2

2,180

2,680

3,800

5,350

7,560

3

3,250

4,000

5,680

8,000

11,300

3 1/2

4,480

5,500

7,810

11,000

15,500

4

7,880

9680

13,700

19,400

27,300

5

12,600

15,500

22,000

31,000

43,800


Table 35 Vented Dry Condensate Return for Gravity Flow Based on Manning Equation

Nominal Diameter, in. IPS

Condensate Flow, lb/ha,b

Condensate Line Slope, in/ft

1/16

1/8

1/4

1/2

1/2

38

54

76

107

3/4

80

114

161

227

1

153

216

306

432

1-1/4

318

449

635

898

1-1/2

479

677

958

1,360

2

932

1,320

1,860

2,640

2-1/2

1,500

2,120

3,000

4,240

3

2,670

3,780

5,350

7,560

4

5,520

7,800

11,000

15,600

5

10,100

14,300

20,200

28,500

6

16,500

23,300

32,900

46,500

a Flow is in lb/h of 180°F water for Schedule 40 steel pipes.

b Flow was calculated from Equation (22) and rounded.


Vented (Open) Return Systems. To achieve this pressure requirement, the condensate return line is usually vented to the atmosphere (1) near the point of entrance of the flow streams from the load traps, (2) in proximity to all connections from drip traps, and (3) at transfer pumps or feedwater receivers.

The dry return lines in a vented return system have flowing liquid in the bottom of the line and gas or vapor in the top (Figure 21A). The liquid is the condensate, and the gas may be steam, air, or a mixture of the two. The flow phenomenon for these dry return systems is open channel flow, which is best described by the Manning equation:

(22)

where

Q = volumetric flow rate, cfs
A = cross-sectional area of conduit, ft2
r = hydraulic radius of conduit, ft
n = coefficient of roughness (usually 0.012)
S = slope of conduit, ft/ft

Table 35 is a solution to Equation (22) that shows pipe size capacities for steel pipes with various pitches. Recommended practice is to size vertical lines by the maximum pitch shown, although they would actually have a capacity far in excess of that shown. As pitch increases, hydraulic jump that could fill the pipe and other transient effects that could cause water hammer should be avoided. Flow values in Table 35 are calculated for Schedule 40 steel pipe, with a factor of safety of 3.0, and can be used for copper pipes of the same nominal pipe size.

The flow characteristics of wet return lines (Figure 21B) are best described by the Darcy-Weisbach equation [Equation (1)]. The motivation for flow is the fluid head difference between the entering section of the flooded line and the leaving section. It is common practice, in addition to providing for the fluid head differential, to slope the return in the direction of flow to a collection point such as a dirt leg to clear the line of sediment or solids. Table 36 is a solution to Equation (1) that shows pipe size capacity for steel pipes with various available fluid heads. Table 36 can also be used for copper tubing of equal nominal pipe size.

Nonvented (Closed) Return Systems. For systems with a continual steam pressure difference between the point where the condensate enters the line and the point where it leaves (Figure 21C), Table 34 or Table 35, as applicable, can be used for sizing the condensate lines. Although these tables express condensate capacity without slope, common practice is to slope the lines in the direction of flow to a collection point (similar to wet returns) to clear the lines of sediment or solids.

When saturated condensate at pressures above the return system pressure enters the return (condensate) mains, some of the liquid flashes to steam. This occurs typically at drip traps into a vented return system or at load traps leaving process load devices that are not valve controlled and typically have no subcooling. If the return main is vented, the vent lines relieve any excessive pressure and prevent a backpressure phenomenon that could restrict flow through traps from valved loads; the pipe sizing would be as described for vented dry returns. If the return line is not vented, flash steam causes a pressure rise at that point and the piping could be sized as described for closed returns, and in accordance with Table 34 or Table 37, as applicable.

Table 36 Vented Wet Condensate Return for Gravity Flow Based on Darcy-Weisbach Equation

Nominal Diameter, in. IPS

Condensate Flow, lb/ha,b

Condensate Head, ft per 100 ft

0.5

1

1.5

2

2.5

3

3.5

4

1/2

105

154

192

224

252

278

302

324

3/4

225

328

408

476

536

590

640

687

1

432

628

779

908

1,020

1,120

1,220

1,310

1 1/4

901

1,310

1,620

1,890

2,120

2,330

2,530

2,710

1 1/2

1,360

1,970

2,440

2,840

3,190

3,510

3,800

4,080

2

2,650

3,830

4,740

5,510

6,180

6,800

7,360

7,890

2 1/2

4,260

6,140

7,580

8,810

9,890

10,900

11,800

12,600

3

7,570

10,900

13,500

15,600

17,500

19,300

20,900

22,300

4

15,500

22,300

27,600

32,000

35,900

39,400

42,600

45,600

5

28,200

40,500

49,900

57,900

64,900

71,300

77,100

82,600

6

45,800

65,600

80,900

93,800

105,000

115,000

125,000

134,000

a Flow is in lb/h of 180°F water for Schedule 40 steel pipes.

b Flow calculated from Equation (1) and rounded.


Velocity Multiplier Chart for Figure 18

Figure 20. Velocity Multiplier Chart for Figure 18


Types of Condensate Return Systems

Figure 21. Types of Condensate Return Systems


Passage of fluid through the steam trap is a throttling or constant-enthalpy process. The resulting fluid on the downstream side of the trap can be a mixture of saturated liquid and vapor. Thus, in nonvented returns, it is important to understand the fluid’s condition when it enters the return line from the trap.

The condition of the condensate downstream of the trap can be expressed by the quality x, defined as

(23)

where

mv = mass of saturated vapor in condensate
ml = mass of saturated liquid in condensate

Likewise, the volume fraction Vc of the vapor in the condensate is expressed as

(24)

where

Vv = volume of saturated vapor in condensate
Vl = volume of saturated liquid in condensate

The quality and the volume fraction of the condensate downstream of the trap can also be estimated from Equations (25) and (26), respectively.

(25)

(26)

where

h1 = enthalpy of liquid condensate entering trap evaluated at supply pressure for saturated condensate or at saturation pressure corresponding to temperature of subcooled liquid condensate
hf2 = enthalpy of saturated liquid at return or downstream pressure of trap
hg2 = enthalpy of saturated vapor at return or downstream pressure of trap
vf2 = specific volume of saturated liquid at return or downstream pressure of trap
vg2 = specific volume of saturated vapor at return or downstream pressure of trap.

Table 37 Flow Rate for Dry-Closed Returns

Pipe Dia. D, in.

Supply Pressure = 5 psig

Return Pressure = 0 psig

Supply Pressure = 15 psig

Return Pressure = 0 psig

Supply Pressure = 30 psig

Return Pressure = 0 psig

Supply Pressure = 50 psig

Return Pressure = 0 psig

Δ p/L, psi/100 ft

1/16

1/4

1

1/16

1/4

1

1/16

1/4

1

1/16

1/4

1

Flow Rate, lb/h

1/2

240

520

1,100

95

210

450

60

130

274

42

92

200

3/4

510

1,120

2,400

210

450

950

130

280

590

91

200

420

1

1,000

2,150

4,540

400

860

1,820

250

530

1,120

180

380

800

1 1/4

2,100

4,500

9,500

840

1,800

3,800

520

1,110

2,340

370

800

1,680

1 1/2

3,170

6,780

14,200

1,270

2,720

5,700

780

1,670

3,510

560

1,200

2,520

2

6,240

13,300

*

2,500

5,320

*

1,540

3,270

*

1,110

2,350

*

2 1/2

10,000

21,300

*

4,030

8,520

*

2,480

5,250

*

1,780

3,780

*

3

18,000

38,000

*

7,200

15,200

*

4,440

9,360

*

3,190

6,730

*

4

37,200

78,000

*

14,900

31,300

*

9,180

19,200

*

6,660

13,800

*

6

110,500

*

*

44,300

*

*

27,300

*

*

19,600

*

*

8

228,600

*

*

91,700

*

*

56,400

*

*

40,500

*

*

Pipe Dia. D, in.

Supply Pressure = 100 psig

Return Pressure = 0 psig

Supply Pressure = 150 psig

Return Pressure = 0 psig

Supply Pressure = 100 psig

Return Pressure = 15 psig

Supply Pressure = 150 psig

Return Pressure = 15 psig

Δp/L, psi/100 ft

1/16

1/4

1

1/16

1/4

1

1/16

1/4

1

1/16

1/4

1

Flow Rate, lb/h

1/2

28

62

133

23

51

109

56

120

260

43

93

200

3/4

62

134

290

50

110

230

120

260

560

93

200

420

1

120

260

544

100

210

450

240

500

1,060

180

390

800

1 1/4

250

540

1,130

200

440

930

500

1,060

2,200

380

800

1,680

1 1/2

380

810

1,700

310

660

1,400

750

1,600

3,320

570

1,210

2,500

2

750

1,590

*

610

1,300

*

1,470

3,100

6,450

1,120

2,350

4,900

2 1/2

1,200

2,550

*

980

2,100

*

2,370

5,000

10,300

1,800

3,780

7,800

3

2,160

4,550

*

1,760

3,710

*

4,230

8,860

*

3,200

6,710

*

4

4,460

9,340

*

3,640

7,630

*

8,730

18,200

*

6,620

13,800

*

6

13,200

*

*

10,800

*

*

25,900

53,600

*

19,600

40,600

*

8

27,400

*

*

22,400

*

*

53,400

110,300

*

40,500

83,600

*

* For these sizes and pressure losses, velocity is above 7000 fpm. Select another combination of size and pressure loss.


Table 38 Flash Steam from Steam Trap on Pressure Drop

Supply Pressure, psig

Return Pressure, psig

x, Fraction Vapor, Mass Basis

Vc, Fraction Vapor, Volume Basis

5

0

0.016

0.962

15

0

0.040

0.985

30

0

0.065

0.991

50

0

0.090

0.994

100

0

0.133

0.996

150

0

0.164

0.997

100

15

0.096

0.989

150

15

0.128

0.992


Table 39 Estimated Return Line Pressures

Pressure Drop, psi/100 ft

Pressure in Return Line, psig

30 psig Supply

150 psig Supply

1/8

0.5

1.25

1/4

1

2.5

1/2

2

5

3/4

3

7.5

1

4

10

2

20


Table 38 presents some values for quality and volume fraction for typical supply and return pressures in heating and ventilating systems. Note that the percent of vapor on a mass basis x is small, although the percent of vapor on a volume basis Vc is very large. This indicates that the return pipe cross section is predominantly occupied by vapor. Figure 22 is a working chart to determine the quality of condensate entering the return line from the trap for various combinations of supply and return pressures. If the liquid is subcooled entering the trap, the saturation pressure corresponding to the liquid temperature should be used for the supply or upstream pressure. Typical pressures in the return line are given in Table 39.

 One-Pipe Systems

Gravity one-pipe air vent systems in which steam and condensate flow in the same pipe, frequently in opposite directions, are considered obsolete and are no longer being installed. Chapter 33 of the 1993 ASHRAE Handbook—Fundamentals or earlier ASHRAE Handbook volumes include descriptions of and design information for one-pipe systems.

3.6 GAS PIPING

Piping for gas appliances should be of adequate size and installed so that it provides a supply of gas sufficient to meet the maximum demand without undue loss of pressure between the point of supply (the meter) and the appliance. The size of gas pipe required depends on (1) maximum gas consumption to be provided, (2) length of pipe and number of fittings, (3) allowable pressure loss from the outlet of the meter to the appliance, and (4) specific gravity of the gas.

Gas consumption in ft3/h is obtained by dividing the Btu input rate at which the appliance is operated by the average heating value of the gas in Btu/ft3. Insufficient gas flow from excessive pressure losses in gas supply lines can cause inefficient operation of gas-fired appliances and sometimes create hazardous operations. Gas-fired appliances are normally equipped with a data plate giving information on maximum gas flow requirements or Btu input as well as inlet gas pressure requirements. The local gas utility can give the gas pressure available at the utility’s gas meter. Using this information, the required size of gas piping can be calculated for satisfactory operation of the appliance(s).

Working Chart for Determining Percentage of Flash Steam (Quality)

Figure 22. Working Chart for Determining Percentage of Flash Steam (Quality)


Typical Oil Circulating Loop

Figure 23. Typical Oil Circulating Loop


Table 40 gives pipe capacities for gas flow for up to 200 ft of pipe based on a specific gravity of 0.60. Capacities for pressures less than 1.5 psig may also be determined by the following equation from NFPA/IAS National Fuel Gas Code (NFPA Standard 54/ANSI Standard Z223.1):

(27)

where

Q = flow rate at 60°F and 30 in. Hg, cfh
d = inside diameter of pipe, in.
Δp = pressure drop, in. of water
C = factor for viscosity, density, and temperature
= 0.00354(t + 460)s0.848μ0.152
t = temperature, °F
s = ratio of density of gas to density of air at 60°F and 30 in. Hg
μ = viscosity of gas, centipoise (0.012 for natural gas, 0.008 for propane)
L = pipe length, ft

Gas service in buildings is generally delivered in the low-pressure range of 7 in. of water. The maximum pressure drop allowable in piping systems at this pressure is generally 0.5 in. of water but is subject to regulation by local building, plumbing, and gas appliance codes [see also the NFPA/IAS National Fuel Gas Code (NFPA Standard 54/ANSI Standard Z223.1)].

Where large quantities of gas are required or where long lengths of pipe are used (e.g., in industrial buildings), low-pressure limitations result in large pipe sizes. Local codes may allow (and local gas companies may deliver) gas at higher pressures (e.g., 2, 5, or 10 psig). Under these conditions, an allowable pressure drop of 10% of the initial pressure is used, and pipe sizes can be reduced significantly. Gas pressure regulators at the appliance must be specified to accommodate higher inlet pressures. NFPA/IAS (2012) provides information on pipe sizing for various inlet pressures and pressure drops at higher pressures. More complete information on gas piping can be found in the Gas Engineers’ Handbook (1970).

Table 40 Maximum Capacity of Gas Pipe in Cubic Feet per Hour

Nominal Iron Pipe Size, in.

Internal Diameter, in.

Length of Pipe, ft

10

20

30

40

50

60

70

80

90

100

125

150

175

200

1/4

0.364

32

22

18

15

14

12

11

11

10

9

8

8

7

6

3/8

0.493

72

49

40

34

30

27

25

23

22

21

18

17

15

14

1/2

0.622

132

92

73

63

56

50

46

43

40

38

34

31

28

26

3/4

0.824

278

190

152

130

115

105

96

90

84

79

72

64

59

55

1

1.049

520

350

285

245

215

195

180

170

160

150

130

120

110

100

1 1/4

1.380

1,050

730

590

500

440

400

370

350

320

305

275

250

225

210

1 1/2

1.610

1,600

1,100

890

760

670

610

560

530

490

460

410

380

350

320

2

2.067

3,050

2,100

1,650

1,450

1,270

1,150

1,050

990

930

870

780

710

650

610

2 1/2

2.469

4,800

3,300

2,700

2,300

2,000

1,850

1,700

1,600

1,500

1,400

1,250

1,130

1,050

980

3

3.068

8,500

5,900

4,700

4,100

3,600

3,250

3,000

2,800

2,600

2,500

2,200

2,000

1,850

1,700

4

4.026

17,500

12,000

9,700

8,300

7,400

6,800

6,200

5,800

5,400

5,100

4,500

4,100

3,800

3,500

Note: Capacity is in cubic feet per hour at gas pressures of 0.5 psig or less and pressure drop of 0.3 in. of water; specific gravity = 0.60.

Copyright by American Gas Association and National Fire Protection Association. Used by permission of copyright holders.


3.7 FUEL OIL PIPING

The pipe used to convey fuel oil to oil-fired appliances must be large enough to maintain low pump suction pressure and, in the case of circulating loop systems, to prevent overpressure at the burner oil pump inlet. Pipe materials must be compatible with the fuel and must be carefully assembled to eliminate all leaks. Leaks in suction lines can cause pumping problems that result in unreliable burner operation. Leaks in pressurized lines create fire hazards. Cast-iron or aluminum fittings and pipe are unacceptable. Pipe joint compounds must be selected carefully.

Oil pump suction lines should be sized so that at maximum suction line flow conditions, the maximum vacuum will not exceed 10 in. Hg for distillate grade fuels and 15 in. Hg for residual oils. Oil supply lines to burner oil pumps should not be pressurized by circulating loop systems or aboveground oil storage tanks to more than 5 psi, or pump shaft seals may fail. A typical oil circulating loop system is shown in Figure 23.

In assembling long fuel pipe lines, be careful to avoid air pockets. On overhead circulating loops, the line should vent air at all high points. Oil supply loops for one or more burners should be the continuous circulation type, with excess fuel returned to the storage tank. Dead-ended pressurized loops can be used, but air or vapor venting is more problematic.

Where valves are used, select ball or gate valves. Globe valves are not recommended because of their high pressure drop characteristics.

Oil lines should be tested after installation, particularly if they are buried, enclosed, or otherwise inaccessible. Failure to perform this test is a frequent cause of later operating difficulties. A suction line can be hydrostatically tested at 1.5 times its maximum operating pressure or at a vacuum of not less than 20 in. Hg. Pressure or vacuum tests should continue for at least 60 min. If there is no noticeable drop in the initial test pressure, the lines can be considered tight.

Table 41 Recommended Nominal Size for Fuel Oil Suction Lines from Tank to Pump (Residual Grades No. 5 and No. 6)

Pumping Rate, gph

Length of Run in Feet at Maximum Suction Lift of 15 ft

25

50

75

100

125

150

175

200

250

300

10

1 1/2

1 1/2

1 1/2

1 1/2

1 1/2

1 1/2

2

2

2 1/2

2 1/2

40

1 1/2

1 1/2

1 1/2

2

2

2 1/2

2 1/2

2 1/2

2 1/2

3

70

1 1/2

2

2

2

2

2 1/2

2 1/2

2 1/2

3

3

100

2

2

2

2 1/2

2 1/2

3

3

3

3

3

130

2

2

2 1/2

2 1/2

2 1/2

3

3

3

3

4

160

2

2

2 1/2

2 1/2

2 1/2

3

3

3

4

4

190

2

2 1/2

2 1/2

2 1/2

3

3

3

4

4

4

220

2 1/2

2 1/2

2 1/2

3

3

3

4

4

4

4

Notes:

1. Pipe sizes smaller than 1 in. IPS are not recommended for use with residual grade fuel oils.

2. Lines conveying fuel oil from pump discharge port to burners and tank return may be reduced by one or two sizes, depending on piping length and pressure losses.


 Pipe Sizes for Heavy Oil

Tables 41 and 42 give recommended pipe sizes for handling No. 5 and No. 6 oils (residual grades) and No. 1 and No. 2 oils (distillate grades), respectively. Storage tanks and piping and pumping facilities for delivering the oil from the tank to the burner are important considerations in the design of an industrial oil-burning system. The construction and location of the tank and oil piping are usually subject to local regulations and National Fire Protection Association (NFPA) Standards 30 and 31.

Table 42 Recommended Nominal Size for Fuel Oil Suction Lines from Tank to Pump (Distillate Grades No. 1 and No. 2)

Pumping Rate, gph

Length of Run in Feet at Maximum Suction Lift of 10 ft

25

50

75

100

125

150

175

200

250

300

10

1/2

1/2

1/2

1/2

1/2

1/2

1/2

3/4

3/4

1

40

1/2

1/2

1/2

1/2

1/2

3/4

3/4

3/4

3/4

1

70

1/2

1/2

3/4

3/4

3/4

3/4

3/4

1

1

1

100

1/2

3/4

3/4

3/4

3/4

1

1

1

1

1 1/4

130

1/2

3/4

3/4

1

1

1

1

1

1 1/4

1 1/4

160

3/4

3/4

3/4

1

1

1

1

1 1/4

1 1/4

1 1/4

190

3/4

3/4

1

1

1

1

1 1/4

1 1/4

1 1/4

2

220

3/4

1

1

1

1

1 1/4

1 1/4

1 1/4

1 1/4

2


REFERENCES

ASHRAE members can access ASHRAE Journal articles and ASHRAE research project final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.

ASHRAE. 2013. Safety standard for refrigeration systems. ANSI/ASHRAE Standard 15-2013.

ASHRAE. 2013. Energy standard for buildings except low-ride residential buildings. ANSI/ASHRAE/IES Standard 90.1-2013.

ASME. 2013. Pipe threads, general purpose, inch. Standard B1.20.1-2013. American Society of Mechanical Engineers, New York.

ASME. 2006. Pipe threads, 60 deg. general purpose (metric). Standard B1.20.2M-2006. American Society of Mechanical Engineers, New York.

ASME. 2015. Gray iron pipe flanges and flanged fittings: Classes 25, 125, and 250. Standard B16.1-2015. American Society of Mechanical Engineers, New York.

ASME. 2011. Malleable iron threaded fittings: Classes 150 and 300. Standard B16.3-2011. American Society of Mechanical Engineers, New York.

ASME. 2011. Gray iron threaded fittings: Classes 125 and 250. Standard B16.4-2011. American Society of Mechanical Engineers, New York.

ASME. 2009. Pipe flanges and flanged fittings: NPS 1/2 through NPS 24 metric/inch standard. Standard B16.5-2009. American Society of Mechanical Engineers, New York.

ASME. 2012. Factory made wrought buttwelding fittings. Standard B16.9-2012. American Society of Mechanical Engineers, New York.

ASME. 2009. Forged fittings, socket-welding and threaded. Standard B16.11-2009. American Society of Mechanical Engineers, New York.

ASME. 2009. Cast iron threaded drainage fittings. Standard B16.12-2009. American Society of Mechanical Engineers, New York.

ASME. 2013. Cast copper alloy threaded fittings: Classes 125 and 250. Standard B16.15-2013. American Society of Mechanical Engineers, New York.

ASME. 2012. Cast copper alloy solder joint pressure fittings. Standard B16.18-2012. American Society of Mechanical Engineers, New York.

ASME. 2013. Wrought copper and copper alloy solder-joint pressure fittings. Standard B16.22-2013. American Society of Mechanical Engineers, New York.

ASME. 2011. Cast copper alloy solder joint drainage fittings: DWV. Standard B16.23-2011. American Society of Mechanical Engineers, New York.

ASME. 2011. Cast copper alloy pipe flanges and flanged fittings: Classes 150, 300, 600, 900, 1500, and 2500. Standard B16.24-2011. American Society of Mechanical Engineers, New York.

ASME. 2011. Cast copper alloy fittings for flared copper tubes. Standard B16.26-2011. American Society of Mechanical Engineers, New York.

ASME. 2012. Wrought copper and wrought copper alloy solder-joint drainage fittings—DWV. Standard B16.29-2012. American Society of Mechanical Engineers, New York.

ASME. 2011. Ductile iron pipe flanges and flanged fittings: Classes 150 and 300. Standard B16.42-2011. American Society of Mechanical Engineers, New York.

ASME. 2016. Power piping. Standard B31.1-2016. American Society of Mechanical Engineers, New York.

ASME. 2016. Refrigeration piping and heat transfer components. Standard B31.5-2016. American Society of Mechanical Engineers, New York.

ASME. 2014. Building services piping. Standard B31.9-2014. American Society of Mechanical Engineers, New York.

ASME. 2015. Welded and seamless wrought steel pipe. Standard B36.10M-2015. American Society of Mechanical Engineers, New York.

ASME. 2015. Qualification standard for welding and brazing procedures, welders, brazers, and welding and brazing operators. Boiler and Pressure Vessel Code, Section IX. American Society of Mechanical Engineers, New York.

ASTM. 2012. Standard specification for pipe, steel, black and hot-dipped, zinc-coated, welded, and seamless. Standard A53. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for seamless carbon steel pipe for high-temperature service. Standard A106. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2014. Standard specification for seamless copper water tube. Standard B88. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2016. Standard specification for seamless copper tube for air conditioning and refrigeration field service. Standard B280. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2011. Standard specification for rigid poly(vinyl chloride) (PVC) compounds and chlorinated poly(vinyl chloride) (CPVC) compounds. Standard D1784. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for poly(vinyl chloride) (PVC) plastic pipe, schedules 40, 80, and 120. Standard D1785. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard test method for determining dimensions of thermoplastic pipe and fittings. Standard D2122. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2012. Standard specification for polyethylene (PE) plastic pipe (SIDR-PR) based on controlled inside diameter. Standard D2239. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for threaded poly(vinyl chloride) (PVC) plastic pipe fittings, schedule 80. Standard D2464. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for poly(vinyl chloride) (PVC) plastic pipe fittings, schedule 40. Standard D2466. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for poly(vinyl chloride) (PVC) plastic pipe fittings, schedule 80. Standard D2467. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2012. Standard specification for solvent cements for poly(vinyl chloride) (PVC) plastic piping systems. Standard D2564. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2014. Standard specification for acrylonitrile-butadiene-styrene (ABS) schedule 40 plastic drain, waste, and vent pipe and fittings. Standard D2661. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2014. Standard specification for poly(vinyl chloride) (PVC) plastic drain, waste, and vent pipe and fittings. Standard D2665. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2013. Standard test method for obtaining hydrostatic design basis for thermoplastic pipe materials or pressure design basis for thermoplastic pipe products. Standard D2837-13e1. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2012. Standard practice for obtaining hydrostatic or pressure design basis for “fiberglass” (glass-fiber-reinforced thermosetting-resin) pipe and fittings. Standard D2992. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2014. Standard specification for polyethylene plastics pipe and fittings materials. Standard D3350. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2016. Standard classification system and basis for specifications for rigid acrylonitrile-butadiene-styrene (ABS) materials for pipe and fittings. Standard D3965. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for threaded chlorinated poly(vinyl chloride) (CPVC) plastic pipe fittings, schedule 80. Standard F437. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for socket-type chlorinated poly(vinyl chloride) (CPVC) plastic pipe fittings, schedule 40. Standard F438. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2013. Standard specification for chlorinated poly(vinyl chloride) (CPVC) plastic pipe fittings, schedule 80. Standard F439. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for crosslinked polyethylene (PEX) tubing. Standard F876. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2011. Standard specification for crosslinked polyethylene (PEX) hot- and cold-water distribution systems. Standard F877. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2014. Standard specification for solvent cements for chlorinated poly(vinyl chloride) (CPVC) plastic pipe and fittings. Standard F493. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard test method for evaluating the oxidative resistance of crosslinked polyethylene (PEX) pipe, tubing and systems to hot chlorinated water. Standard F2023. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2015. Standard specification for pressure-rated polypropylene (PP) piping systems. Standard F2389. American Society for Testing and Materials, West Conshohocken, PA.

ASTM. 2011. Standard specification for manufacture and joining of polyethylene (PE) gas pressure pipe with a peelable polypropylene (PP) outer layer. Standard F2830. American Society for Testing and Materials, West Conshohocken, PA.

AWWA. 2014. Thickness design of ductile-iron pipe. Standard C150/A21.50. American Water Works Association, Denver.

Ball, E.F., and C.J.D. Webster. 1976. Some measurements of water-flow noise in copper and ABS pipes with various flow velocities. The Building Services Engineer 44(2):33.

Carrier. 1960. Piping design. In System design manual. Carrier Air Conditioning Company, Syracuse, NY.

CDA. 2010. The copper tube handbook. Copper Development Association, New York.

Crane Co. 1976. Flow of fluids through valves, fittings and pipe. Technical Paper 410. Crane Company, New York.

Crane Co. 1988. Flow of fluids through valves, fittings and pipe. Technical Paper 410. Crane Company, New York.

Dawson, F.M., and J.S. Bowman. 1933. Interior water supply piping for residential buildings. University of Wisconsin Experiment Station Bulletin 77.

Ding, C., L. Carlson, C. Ellis, and O. Mohseni. 2005. Pressure loss coefficients in 6, 8, and 10 inch steel pipe fittings. ASHRAE Research Project TRP-1116, Final Report. University of Minnesota, Saint Anthony Falls Laboratory.

Eshbach, O.W. 2009. Eshbach’s handbook of engineering fundamentals, 5th ed. M. Kutz, ed. John Wiley & Sons, New York.

Freeman, J.R. 1941. Experiments upon the flow of water in pipes. American Society of Mechanical Engineers, New York.

Gas Engineers’ Handbook. 1970. Industrial Press, New York.

Giesecke, F.E. 1926. Friction of water elbows. ASHVE Transactions 32:303.

Giesecke, F.E., and W.H. Badgett. 1931. Friction heads in one-inch standard cast-iron tees. ASHVE Transactions 37:395.

Giesecke, F.E., and W.H. Badgett. 1932a. Loss of head in copper pipe and fittings. ASHVE Transactions 38:529.

Giesecke, F.E., and W.H. Badgett. 1932b. Supplementary friction heads in one-inch cast-iron tees. ASHVE Transactions 38:111.

Grinnell Company. 1951. Piping design and engineering. Grinnell Company, Cranston, RI.

HDR design guide. 1981. Hennington, Durham and Richardson, Omaha, NE.

Heald, C.C. 2002. Cameron hydraulic data, 19th ed. Flowserve Corporation, Irving, TX.

Hegberg, R.A. 1995. Where did the k-factors for pressure loss in fittings come from? ASHRAE Transactions 101(1):1264-78. Paper CH-95-20-3.

Hunter, R.B. 1940. Methods of estimating loads in plumbing systems. NBS Report BMS 65. National Institute of Standards and Technology, Gaithersburg, MD.

Hunter, R.B. 1941. Water distributing systems for buildings. NBS Report BMS 79. National Institute of Standards and Technology, Gaithersburg, MD.

Hydraulic Institute. 1990. Engineering data book. Hydraulic Institute, Parsippany, NJ.

ICC. 2012. International plumbing code®. International Code Council, Washington, D.C.

Idelchik, I.E. 1986. Handbook of hydraulic resistance. Hemisphere Publishing, New York.

ISA. 2007. Flow equations for sizing control valves. Standard 75.01.01-07. International Society of Automation, Research Triangle Park, NC.

Laschober, R.R., G.Y. Anderson, and D.G. Barbee. 1966. Counterflow of steam and condensate in slightly pitched pipes. ASHRAE Transactions 72(1):157.

Marseille, B. 1965. Noise transmission in piping. Heating and Ventilating Engineering (June):674.

MSS. 2009. Pipe hangers and supports—Materials, design, manufacture, selection, application, and installation. ANSI/MSS Standard SP-58. Manufacturers Standardization Society of the Valve and Fittings Industry, Vienna, VA.

MSS. 2003. Pipe hangers and supports—Selection and application. Standard SP-69. Manufacturers Standardization Society of the Valve and Fittings Industry, Vienna, VA.

Nayyar, M. 1999. Piping handbook. McGraw-Hill, New York.

NFPA. 2010. Installation of sprinkler systems. Standard 13. National Fire Protection Association, Quincy, MA.

NFPA/AGA. 2012. National fuel gas code. ANSI/NFPA Standard 54. National Fire Protection Association, Quincy, MA. ANSI/AGA Standard Z223.1-2002. American Gas Association, Arlington, VA.

NSF/ANSI. 2016. Plastics piping system components and related materials. ANSI/NSF Standard 14-2016. NSF International, Ann Arbor, MI.

NSF/ANSI. 2016. Drinking water system components—Health effects. ANSI/NSF Standard 61. NSF International, Ann Arbor, MI.

Obrecht, M.F., and M. Pourbaix. 1967. Corrosion of metals in potable water systems. AWWA 59:977. American Water Works Association, Denver, CO.

PHCC. 2012. National standard plumbing code. Plumbing-Heating-Cooling Contractors Association, Falls Church, VA.

Plastic Pipe Institute. 1971. Water flow characteristics of thermoplastic pipe. Plastic Pipe Institute, New York.

PPFA. 2009. PVC piping systems for commercial and industrial applications design guide. Plastic Pipe and Fitting Association, Glenn Ellyn, IL

Rahmeyer, W.J. 1999a. Pressure loss coefficients of threaded and forged weld pipe fittings for ells, reducing ells, and pipe reducers (RP-968). ASHRAE Transactions 105(2):334-354. Paper 4308.

Rahmeyer, W.J. 1999b. Pressure loss coefficients of pipe fittings for threaded and forged weld pipe tees (RP-968). ASHRAE Transactions 105(2):355-385. Paper 4309.

Rahmeyer, W.J. 2002a. Pressure loss data for large pipe ells, reducers, and expansions. ASHRAE Transactions 108(1):360-375. Paper 4533.

Rahmeyer, W.J. 2002b. Pressure loss data for large pipe tees. ASHRAE Transactions 108(1):376-389. Paper 4534.

Rahmeyer, W.J. 2002c. Pressure loss coefficients for close-coupled pipe ells. ASHRAE Transactions 108(1):390-406. Paper 4535.

Rahmeyer, W.J. 2003a. Pressure loss data for PVC pipe elbows, reducers, and expansions (RP-1193). ASHRAE Transactions 109(2):230-251. Paper 4653.

Rahmeyer, W.J. 2003b. Pressure loss data for PVC pipe tees (RP-1193). ASHRAE Transactions 109(2):252-271. Paper 4654.

Rogers, W.L. 1953. Experimental approaches to the study of noise and noise transmission in piping systems. ASHVE Transactions 59:347-360.

Rogers, W.L. 1954. Sound-pressure levels and frequencies produced by flow of water through pipe and fittings. ASHRAE Transactions 60:411-430.

Rogers, W.L. 1956. Noise production and damping in water piping. ASHAE Transactions 62:39.

Sanks, R.L. 1978. Water treatment plant design for the practicing engineer. Ann Arbor Science, Ann Arbor, MI.

Smith, T. 1983. Reducing corrosion in heating plants with special reference to design considerations. Anti-Corrosion Methods and Materials 30 (October):4.

Stewart, W.E., and C.L. Dona. 1987. Water flow rate limitations (RP-450). ASHRAE Transactions 93(2):811-825. Paper 3106.

Williams, G.J. 1976. The Hunter curves revisited. Heating/Piping/Air Conditioning (November):67.

Williams, G.S., and A. Hazen. 1933. Hydraulic tables. John Wiley & Sons, New York.

BIBLIOGRAPHY

ASTM. 2009. Standard specification for chlorinated poly(vinyl chloride) (CPVC) plastic pipe, Schedules 40 and 80. Standard F441/F441M. American Society for Testing and Materials, West Conshohocken, PA.



The preparation of this chapter is assigned to TC 6.1, Hydronic and Steam Equipment and Systems.