The following guidelines, data requirements, and procedures apply to all load calculation approaches, whether heating or cooling, hand-tractable or computerized.
The initial step in the load calculation is selecting indoor and outdoor design conditions.
Indoor Conditions. Indoor conditions assumed for design purposes depend on building use, type of occupancy, and/or code requirements. Chapter 9 and ASHRAE Standard 55 define the relationship between indoor conditions and comfort.
Typical practice for cooling is to design for indoor conditions of 75°F db and a maximum of 50 to 65% rh. For heating, 68°F db and 30% rh are common design values. These conditions are the default values used throughout this chapter.
Outdoor Conditions. Outdoor design conditions for load calculations should be selected from location-specific climate data in Chapter 14, or according to local code requirements as applicable.
Cooling. The 1% design dry-bulb temperature and mean coincident wet bulb temperature from Chapter 14 climate data are generally appropriate. As previously emphasized, oversized cooling equipment results in poor system performance. Extremely hot events are necessarily of short duration (conditions always moderate each night); therefore, sacrificing comfort under typical conditions to meet occasional extremes is not recommended.
Load calculations also require the hottest-month dry-bulb temperature daily range, and wind speed. These values can also be found in Chapter 14, although wind speed is commonly assumed to be 7.5 mph.
Typical buildings in middle latitudes generally experience maximum cooling requirements in midsummer (July in the northern hemisphere and January in the southern hemisphere). For this reason, the RLF method is based on midsummer solar gains. However, this pattern does not always hold. Buildings at low latitudes or with significant south-facing glazing (north-facing in the southern hemisphere) should be analyzed at several times of the year using the RHB method. Local experience can provide guidance as to when maximum cooling is probable. For example, it is common for south-facing buildings in mild northern-hemisphere climates to have peak cooling loads in the fall because of low sun angles. Chapter 14 contains monthly temperature data to support calculations for any time of year.
Heating. General practice is to use the 99% design dry-bulb temperature from Chapter 14. Heating load calculations ignore solar and internal gains, providing a built-in safety factor. However, the designer should consider two additional factors:
-
Many locations experience protracted (several-day) cold periods during which the outdoor temperature remains below the 99% value.
-
Wind is a major determinant of infiltration. Residences with significant leakage (e.g., older houses) may have peak heating demand under conditions other than extreme cold, depending on site wind patterns.
Depending on the application and system type, the designer should consider using the 99.6% value or the mean minimum extreme as the heating design temperature. Alternatively, the heating load can be calculated at the 99% condition and a safety factor applied when equipment is selected. This additional capacity can also serve to meet pickup loads under nonextreme conditions.
Adjacent Buffer Spaces. Residential buildings often include unconditioned buffer spaces such as garages, attics, crawlspaces, basements, or enclosed porches. Accurate load calculations require the adjacent air temperature.
In many cases, a simple, conservative estimate is adequate, especially for heating calculations. For example, it is generally reasonable to assume that, under heating design conditions, adjacent uninsulated garages, porches, and attics are at outdoor temperature. Another reasonable assumption is that the temperature in an adjacent, unheated, insulated room is the mean of the indoor and outdoor temperatures.
In cases where a temperature estimate is required, a steady-state heat balance analysis yields the following:
where
| tb |
= |
buffer space temperature, °F |
| Q |
= |
buffer space infiltration/ventilation flow rate, cfm |
| to |
= |
outdoor air temperature, °F |
| Ax |
= |
area of xth buffer space surface, ft2 |
| Ux |
= |
U-factor of xth buffer space surface, Btu/h · ft2 · °F |
| tx |
= |
air temperature at outside of xth buffer space surface, °F (typically, outdoor air temperature for exterior surfaces, conditioned space temperature for surfaces between buffer space and house, or ground temperature for below-grade surfaces) |
| q |
= |
additional buffer space heat gains, Btu/h (e.g., solar gains or distribution system losses) |
Component Areas. To perform load calculations efficiently and reliably, standard methods must be used for determining building surface areas. For fenestration, the definition of component area must be consistent with associated ratings.
Gross area. It is both efficient and conservative to derive gross surface areas from outer building dimensions, ignoring wall and floor thicknesses. Thus, floor areas should be measured to the outside of adjacent exterior walls or to the centerline of adjacent partitions. When apportioning to rooms, façade area should be divided at partition centerlines. Wall height should be taken as floor-to-floor.
Using outer dimensions avoids separate accounting of floor edge and wall corner conditions. Further, it is standard practice in residential construction to define floor area in terms of outer dimensions, so outer-dimension takeoffs yield areas that can be readily checked against building plans (e.g., the sum of room areas should equal the plan floor area). Although outer-dimension procedures are recommended as expedient for load calculations, they are not consistent with rigorous definitions used in building-related standards (e.g., ASTM Standard E631). However, the inconsistencies are not significant in the load calculation context.
Fenestration area. Fenestration includes exterior windows, skylights, and doors. Fenestration U-factor and SHGC ratings (see Table 2) are based on the entire product area, including frames. Thus, for load calculations, fenestration area is the area of the rough opening in the wall or roof, less installation clearances (projected product area Apf). Installation clearances can be neglected; it is acceptable to use the rough opening as an approximation of Apf.
Net area. Net surface area is the gross surface area less fenestration area (rough opening or Apf) contained within the surface.
Volume. Building volume is expediently calculated by multiplying floor area by floor-to-floor height. This produces a conservative estimate of enclosed air volume, because wall and floor volumes are included in the total. More precise calculations are possible but are generally not justified in this context.
Construction Characteristics.
U-factors. Except for fenestration, construction U-factors should be calculated using procedures in Chapter 27, or taken from manufacturer’s data, if available. U-factors should be evaluated under heating (winter) conditions.
Fenestration. Fenestration is characterized by U-factor and solar heat gain coefficient (SHGC), which apply to the entire assembly (including frames). If available, rated values should be used, determined according to procedures set forth by National Fenestration Rating Council (NFRC), Canadian Standards Association (CSA), or other specifying body (see Chapter 15). Ratings can be obtained from product literature, product label, or online listings (NFRC 2017). For unrated products (e.g., in existing construction), the U-factor and SHGC can be estimated using Table 2 or tables in Chapter 15. Note that fenestration U-factors are evaluated under heating (winter) design conditions but are used in this chapter for both heating and cooling calculations.
Relatively few types of glazing are encountered in residential applications. Single-glazed clear, double-glazed clear, and double-glazed low-emissivity (“low-e”) glass predominate. Single-glazed is now rare in new construction but common in older homes. Triple-glazing, reflective glass, and heat-absorbing glass are encountered occasionally. Acrylic or glass skylights are common. Multipane low-e insulated glazing is available in high- and low-solar-gain variants, as discussed in Chapter 15. Low-solar is now the more common for new construction in all parts of the United States.
Properties of windows equipped with storm windows should be estimated from data for a similar configuration with an additional pane. For example, data for clear, double-glazed should be used for a clear single-glazed window with a storm window.
Fenestration interior and exterior shading must be included in cooling load calculations, as discussed in the Cooling Load section.
Table 2 shows representative window U-factor and SHGC values for common glazing and frame combinations. Consult Chapter 15 for skylight characteristics.
Below-Grade Surfaces. For cooling calculations, heat flow into the ground is usually ignored because it is difficult to quantify. Surfaces adjacent to the ground are modeled as if well insulated on the outside, so there is no overall heat transfer, but diurnal heat storage effects are included. Heating calculations must include loss via slabs and basement walls and floors, as discussed in the Heating Load section.
Infiltration. Infiltration is generally a significant component of both cooling and heating loads. Refer to Chapter 16 for a detailed discussion of residential air leakage. The simplified residential models found in that chapter can be used to calculate infiltration rates for load calculations. Infiltration should be evaluated for the entire building, not individual rooms or zones.
Natural infiltration leakage rates are modified by mechanical pressurization caused by unbalanced ventilation or duct leakage. These effects are discussed in the section on Combined Ventilation and Infiltration Airflow.
Leakage rate. Air leakage rates are specified either as airflow rate Qi, or air exchanges per hour (ACH), related as follows:
where
| Qi |
= |
infiltration airflow rate, cfm |
| ACH |
= |
air exchange rate, changes/h |
| V |
= |
building volume, ft3 |
Infiltration airflow rate depends on two factors:
-
Building effective leakage area (envelope leaks plus other air leakage paths, notably flues) and its distribution among ceilings, walls, floors, and flues.
-
Driving pressure caused by buoyancy (stack effect) and wind.
Using the simplifying assumptions presented in Chapter 16, these factors can be evaluated separately and combined using Equation (8).
where
| AL |
= |
building effective leakage area (including flue) at reference pressure difference = 0.016 in. of water, assuming discharge coefficient CD = 1, in2 |
| IDF |
= |
infiltration driving force, cfm/in2 |
The following sections provide procedures for determining AL and IDF.
Leakage area. As discussed in Chapter 16, there are several interconvertible ways to characterize building leakage, depending on reference pressure differences and assumed discharge coefficient. This formulation uses the effective leakage area at 0.016 in. of water, assuming CD = 1, designated AL (Sherman and Grimsrud 1980).
The only accurate procedure for determining AL is by measurement using a pressurization test (commonly called a blower door test). Numerous field studies have shown that visual inspection is not adequate for obtaining even a crude estimate of leakage.
For buildings in design, a pressurization test is not possible and leakage area must be assumed for design purposes. Leakage can be estimated using tabulated component leakage areas found in Chapter 16. A simpler approach is based on an assumed average leakage per unit of building surface area:
where
| Aes |
= |
building exposed surface area, ft2 |
| Aul |
= |
unit leakage area, in2/ft2 (from Table 3) |
Aul is the leakage area per unit surface area; suitable design values are found in Table 3. Field experience indicates that the level of care applied to reducing leakage often depends on winter conditions, because cold-air leakage is readily detected. Thus, lower Aul values are expected in colder climates. Note that the Aul value doubles at each reduced construction quality step in Table 3; very high infiltration loads are typical in older houses.
In Equation (9), Aes is the total building surface area at the envelope pressure boundary, defined as all above-grade surface area that separates the outdoors from conditioned or semiconditioned space. Table 4 provides guidance for evaluating Aes.
IDF. To determine IDF, use the Chapter 16 methods cited previously. As a further simplification, Barnaby and Spitler (2005) derived the following relationship that yields results approximately equal to the AIM-2 model (Walker and Wilson 1990, 1998; Chapter 16’s enhanced model) at design conditions:
where
| I0, I1, I2 |
= |
coefficients, as follows: |
| H |
= |
building average stack height, ft (typically 8 to 10 ft per story) |
| Δt |
= |
difference between indoor and outdoor temperatures, °F |
| AL, flue |
= |
flue effective leakage area at reference pressure difference = 0.016 in. of water, assuming CD = 1, in2 (total for flues serving furnaces, domestic water heaters, fireplaces, or other vented equipment, evaluated assuming associated equipment is not operating and with dampers in closed position; see Chapter 16)
|
Building stack height H is the average height difference between the ceiling and floor (or grade, if the floor is below grade). Thus, for buildings with vented crawlspaces, the crawlspace height is not included. For basement or slab-on-grade construction, H is the average height of the ceiling above grade. Generally, there is significant leakage between basements and spaces above, so above-grade basement height should be included whether or not the basement is fully conditioned. With suitable adjustments for grade level, H can also be estimated as V/Acf (conditioned floor area).
Equation (10) is valid for typical suburban residential wind sheltering, AL, flue < AL/2, and at any elevation. Table 5 shows IDF values derived with Equation (10), assuming AL, flue = 0.
Verification of leakage. A postconstruction pressurization test is strongly recommended to verify that design leakage assumptions are actually achieved. Excess leaks should be located and repaired.
Allocation of infiltration to rooms. Total building infiltration should typically be allocated to rooms according to room volume; that is, it should be assumed that each room has the same air exchange rate as the whole building. In reality, leakage varies by room and over time, depending on outdoor temperature and wind conditions. These effects can either increase or decrease room leakage. In addition, system air mixing tends to redistribute localized leakage to all rooms. Thus, in most cases, there is no reasonable way to assign more or less leakage to specific rooms.
An exception is leaky, multistory houses. The preferable and cost-effective response is mitigation of the leakage. If repair is not possible, then for heating load calculation purposes, some leakage can be differentially assigned to lower story and/or windward rooms in proportion to exposed surface area (i.e., adjustment using an “exposure factor”).
Multifamily buildings. Usually, the simplified methods in Chapter 16 and this section do not apply to multifamily residences. However, they can be used for row houses that are full building height and have more than one exposed façade. For apartment units subdivided within a former detached residence, the entire building should be analyzed and the resulting exchange rate applied to the apartment volume. In other multifamily structures, infiltration is determined by many factors, including overall building height and degree of sealing between apartments. For low-rise construction, an upper bound for the infiltration rate can be found by evaluating the entire building. As building height increases, leakage problems can be magnified, as discussed in Chapter 16. Estimating leakage rates may require advice from a high-rise infiltration specialist.
Ventilation.
Whole-building ventilation. Because of energy efficiency concerns, residential construction has become significantly tighter over the last several decades. Natural leakage rates are often insufficient to maintain acceptable indoor air quality. ASHRAE Standard 62.2 specifies the required minimum whole-building ventilation rate as
where
| Qv |
= |
required ventilation flow rate, cfm |
| Ac f |
= |
building conditioned floor area, ft2 |
| Nb r |
= |
number of bedrooms (not less than 1) |
Certain mild climates are exempted from this standard; local building authorities ultimately dictate actual requirements. In addition, Standard 62.2 specifies alternative methods for determining ventilation requirements that may result in smaller Qv values. Whole-building ventilation is expected to become more common because of a combination of regulation and consumer demand. The load effect of Qv must be included in both cooling and heating calculations.
Heat recovery. Heat recovery devices should be considered part of mechanical ventilation systems. These appliances are variously called heat recovery ventilators (HRVs) or energy recovery ventilators (ERVs) and integrate with residential distribution systems, as described in Chapter 26 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment. Either sensible heat or total heat (enthalpy) can be exchanged between the exhaust and intake airstreams. ERV/HRV units are characterized by their sensible and total effectiveness.
Local mechanical exhaust. Kitchen and bathroom exhaust fans are required by Standard 62.2 and are typically present. Exhaust fans that operate intermittently by manual control are generally not included in load calculations. Continuously operating ventilation should be included. Note that exhaust fans induce load only through enhanced infiltration because of building depressurization (see the section on Combined Ventilation and Infiltration Airflow for further discussion).
Combustion Air. Fuel-fired boilers, furnaces, and domestic water heaters require combustion air. If the combustion air source is within the building envelope (including in semiconditioned basements), additional infiltration and heating load are induced. Locating the equipment outside of conditioned space (e.g., in a garage or vented mechanical closet) or using sealed-combustion equipment eliminates this load.
Combustion air requirements for new forced-draft equipment can be estimated at 0.25 cfm per 1000 Btu/h or about 25 cfm for a 100,000 Btu/h heating appliance. The requirements for existing natural draft equipment should be estimated at twice that amount. In many cases, these quantities are relatively small and can be neglected.
For cooling load calculations, heating equipment is assumed to be not operating, leaving only any domestic water heaters, for which the combustion air requirements are generally neglected.
Combined Ventilation and Infiltration Airflow. Mechanical pressurization modifies the infiltration leakage rate. To assess this effect, overall supply and exhaust flow rates must be determined and then divided into “balanced” and “unbalanced” components.
where
| Qbal |
= |
balanced airflow rate, cfm |
| Qsup |
= |
total ventilation supply airflow rate, cfm |
| Qexh |
= |
total ventilation exhaust airflow rate (including any combustion air requirements), cfm |
| Qunbal |
= |
unbalanced airflow rate, cfm |
Note that unbalanced duct leakage can produce additional pressurization or depressurization. This effect is discussed in the section on Distribution Losses.
Airflow components can be combined with infiltration leakage as follows (Palmiter and Bond 1991; Sherman 1992):
where
| Qvi |
= |
combined infiltration/ventilation flow rate (not including balanced component), cfm |
| Qi |
= |
infiltration leakage rate assuming no mechanical pressurization, cfm |
Ventilation/infiltration load. The cooling or heating load from ventilation and infiltration is calculated as follows:
where
| qvi, s |
= |
sensible ventilation/infiltration load, Btu/h |
| εs |
= |
HRV/ERV sensible effectiveness |
| Qbal, hr |
= |
balanced ventilation flow rate via HRV/ERV equipment, cfm |
| Qbal, oth |
= |
other balanced ventilation supply airflow rate, cfm |
| Δt |
= |
indoor/outdoor temperature difference, °F |
| ΔW |
= |
indoor/outdoor humidity ratio difference |
| qvi,t |
= |
total ventilation/infiltration load, Btu/h |
| εt |
= |
HRV/ERV total effectiveness |
| Δh |
= |
indoor/outdoor enthalpy difference, Btu/lb |
| qvi,l |
= |
latent ventilation/infiltration load, Btu/h |
Distribution Losses. Air leakage and heat losses from duct systems frequently impose substantial equipment loads in excess of building requirements. The magnitude of losses depends on the location of duct runs, their surface areas, surrounding temperatures, duct wall insulation, and duct airtightness. These values are usually difficult to accurately determine at the time of preconstruction load calculations, and must be estimated using assumed values, so that selected equipment capacity is sufficient.
Good design and workmanship both reduce duct losses. In particular, locating duct runs within the conditioned envelope (above dropped hallway ceilings, for example) substantially eliminates duct losses. Specific recommendations are found in Chapter 10 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment. Good workmanship and correct materials are essential to achieve low leakage. Many common sealing techniques, notably duct tape, have been shown to fail in a few years. Well-constructed duct systems show leakage rates of 5% of fan flow from supply and return runs, whereas 11% or more on each side is more typical. Because of the potentially large load impact of duct leakage, postconstruction verification of airtightness is strongly recommended.
Duct losses can be estimated using models specified in ASHRAE Standard 152, Francisco and Palmiter (1999), and Palmiter and Francisco (1997). The allowance for distribution losses is calculated as follows:
where
| qd |
= |
distribution loss, Btu/h |
| Fdl |
= |
duct loss/gain factor, from Table 6 or ASHRAE Standard 152 design efficiencies or a detailed model |
| qbl |
= |
total building load, Btu/h |
Table 6 shows typical duct loss/gain factors calculated for the conditions indicated. These values can provide guidance for hand estimates, and illustrate the need for achieving low duct leakage. To the extent conditions differ from those shown, specific calculations should be made using a method cited previously. Note also that Table 6 cooling factors represent sensible gain only. Duct leakage may also introduce significant latent gain; see ASHRAE Standard 152.