1. BASIC CONCEPTS AND TERMINOLOGY
Outdoor air that flows through a building is often used to dilute and remove indoor air contaminants. However, the energy required to condition this outdoor air can be a significant portion of the total space-conditioning load. The magnitude of outdoor airflow into the building must be determined to size the HVAC equipment properly, and to evaluate energy consumption (if required). For buildings without mechanical cooling and dehumidification, proper ventilation and infiltration airflows are important for providing acceptable IAQ and better thermal comfort for occupants. ASHRAE Standard 55 specifies conditions under which 80% or more of the occupants in a space will find it thermally acceptable. Chapter 9 of this volume also addresses thermal comfort.
Airflow into buildings and between zones also affects fires, smoke movement, and safe occupant egress. Smoke management is addressed in Chapter 53 of the 2019 ASHRAE Handbook—HVAC Applications.
Ventilation and Infiltration
Air exchange of outdoor air with air already in a building can be divided into two broad classifications: ventilation and infiltration.
Ventilation is intentional introduction of air from the outdoors into a building; it is further subdivided into natural and mechanical ventilation. Natural ventilation is the flow of air through open windows, doors, grilles, and other planned building envelope penetrations. Mechanical (or forced) ventilation, shown in Figure 1, is the intentional movement of air into and out of a building using fans, ductwork, intake louvers, and exhaust grilles, for example.
Infiltration is the flow of outdoor air into a building through cracks and other unintentional openings and through the normal use of exterior doors for entrance and egress. Infiltration is also known as air leakage into a building. Exfiltration, depicted in Figure 1, is leakage of indoor air out of a building through similar types of openings. Like natural ventilation, infiltration and exfiltration are driven by natural and/or artificial pressure differences. These forces are discussed in detail in the section on Driving Mechanisms for Ventilation and Infiltration. Transfer air is air that moves from one interior space to another, either intentionally or not.
Ventilation and infiltration differ significantly in how they affect energy consumption, air quality, and thermal comfort, and can each vary with weather conditions, HVAC system operation, and building use. Although one mode may be expected to dominate in a particular building, both must be considered in the proper design and operation of an HVAC system. Seasonal weather and other transient factors must be considered, as well.
Ventilation air is air used to provide acceptable indoor air quality. It may be composed of mechanical or natural ventilation, infiltration, suitably treated recirculated air, transfer air, or an appropriate combination, although the allowable means of providing ventilation air varies in standards and guidelines.
Modern commercial and institutional buildings normally have mechanical ventilation and are usually intended to be pressurized somewhat to reduce or eliminate infiltration. Mechanical ventilation has the greatest potential for control of air exchange when the system is properly designed, installed, and operated; it should provide acceptable indoor air quality and thermal comfort when ASHRAE Standards 55 and 62.1’s requirements are followed, although issues (e.g., unusually strong pollutant sources) can still result in unacceptable indoor environment conditions. Mechanical ventilation equipment and systems are described in Chapters 1, 4, and 10 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment.
In commercial and institutional buildings, natural ventilation (e.g., through uncontrolled use of manually operated windows) may not be desirable from the points of view of energy conservation, comfort, security, or control of airborne pollen or other pollutants in some climates and locations. In commercial and institutional buildings with mechanical cooling and ventilation, an automatically controlled air- or water-side economizer may be preferable to operable windows for taking advantage of cool outdoor conditions when interior cooling is required. When moderate outdoor temperatures occur, an air-side economizer control scheme may not only increase the rate of ventilation but also operate the cooling equipment to optimize energy use (hybrid or mixed mode).
Infiltration may be significant in commercial and institutional buildings too, especially in tall, leaky, or partially pressurized buildings and in lobby and loading dock areas. The joint between roof decking and outer walls is often particularly leaky in commercial and other large buildings, and should be properly detailed, constructed, and inspected.
In most of the United States, residential buildings have historically relied on infiltration and natural ventilation to meet their ventilation air needs. Neither is reliable for ventilation air purposes because they depend on weather conditions, building construction, occupants, and maintenance. Natural ventilation, usually through operable windows and screened doors, is more likely to allow occupants to control indoor airborne contaminants and interior air temperature, but it can have a substantial energy cost if used while the residence’s heating or cooling equipment is operating. Opened windows and doors also may lead to security, noise, or other concerns.
In place of or in addition to operable windows, small exhaust fans should be provided for localized venting of residential spaces with high pollutant levels or moisture (e.g., kitchens, bathrooms). Not all local building codes require that such exhaust be vented to the outdoors, but it is required by ASHRAE Standard 62.2. Instead, a local code may allow the air to be treated and returned to the space or to be discharged to an attic space. Poor maintenance of these recirculating treatment devices can make nonducted vents ineffective for ventilation purposes. Warm exhaust air can hold much moisture, so condensation in attics should be avoided. If not already required by code, consider venting attached garages and other storage spaces to the outdoors, as well.
Increasingly, building codes require general mechanical ventilation in residences. Heat recovery heat exchangers are popular for reducing energy consumption, especially in cold climates. Residential buildings with low rates of infiltration and natural ventilation, including most new buildings, require mechanical ventilation at rates given in ASHRAE Standard 62.2.
Forced-Air Distribution Systems
Figure 2 shows a simple air-handling unit (AHU) or air handler that conditions air for a building. Air brought back to the air handler from the conditioned space is return air (RA). The return air either is discharged to the environment [exhaust air (EA)] or is reused [recirculated air (CA)]. Air brought in intentionally from the environment is outdoor air (OA). Because outdoor air may need treatment to be acceptable for use in a building, it should not be called “fresh air.” Outdoor and recirculated air are combined to form mixed air (MA), which is then conditioned and delivered to the spaces served as supply air (SA). Any portion of the mixed air that intentionally or unintentionally circumvents conditioning is bypass air (BA). Because of the wide variety of air-handling systems, the airflows shown in Figure 2 may not all be present in a particular system as defined here. Also, more complex systems may have additional airflows.
In HVAC design, volumetric airflow rates Q are normally reported in cubic feet per minute (cfm). The incorrect term “volume” should not be used to describe airflow rates.
The outdoor airflow introduced to a building or zone by an air-handling unit can also be described by the outdoor air fraction Xoa, which is the ratio of the volumetric flow rate Q of outdoor air brought in by the air handler to the total supply airflow rate:
When expressed as a percentage, the outdoor air fraction is called the percent outdoor air. The design outdoor airflow rate Qoa for a building’s or zone’s ventilation system is found by applying the requirements of ASHRAE Standard 62.1 or 62.2 to that specific building, occupancy, and HVAC system. The supply airflow rate Qsa is that required to meet the thermal load. The outdoor air fraction and percent outdoor air then describe the degree of recirculation, where a low value indicates a high rate of recirculation, and a high value shows little recirculation. Conventional all-air air-handling systems for commercial and institutional buildings often have approximately 10 to 40% outdoor air.
100% outdoor air means no recirculation of return air through the air-handling system. Instead, all the supply air is treated outdoor air, also known as makeup air (KA), and all return air is discharged directly to the outdoors as relief air (LA), via separate or centralized exhaust fans or relief dampers and grilles. An air-handling unit that provides exclusively 100% outdoor air to offset air that is exhausted is typically called a makeup air unit (MAU).
When outdoor air via mechanical ventilation is used to provide ventilation air, as is common in commercial and institutional buildings and increasingly in residences, this outdoor air is usually delivered to spaces as all or part of the supply air. With a variable-air-volume (VAV) system, the outdoor air fraction of the supply air may need to be increased when supply airflow is reduced to meet a particular thermal load. In some HVAC systems, such as a dedicated outdoor air system (DOAS), conditioned outdoor air may be delivered separately from the way the spaces’ loads are handled (Mumma and Shank 2001).
Air movement within spaces affects the diffusion of ventilation air and, therefore, indoor air quality and comfort. Two distinct flow patterns are commonly used to characterize air movement in rooms: displacement flow and entrainment flow. Displacement flow, shown in Figure 3, is the movement of air within a space in a piston- or plug-type motion. Ideally, no mixing of the room air occurs, which is desirable for removing pollutants generated within a space. Air mixing does occur, however, to various degrees. A laminar-flow air distribution system that is intended to sweep air across a space with reduced turbulence and mixing may produce a high degree of displacement flow and thus more effective pollutant removal. The pollutants’ buoyancy and occupants’ thermal comfort are concerns when deciding on the intended direction of airflow.
Entrainment flow, shown in Figure 4, is also known as conventional mixing. Systems with ceiling-based supply air diffusers and return air grilles are common examples of air distribution systems that produce entrainment flow. Airborne pollutants are removed by dilution by the ventilation air that is delivered as all or part of the supply air. Entrainment flow with very poor mixing in the room has been called short-circuiting flow because much of the supply air leaves the room without mixing with room air. There is little evidence that properly designed, installed, and operated air distribution systems exhibit substantial short circuiting, although poorly designed, installed, or operated systems may short circuit (especially ceiling-based systems in heating mode) to a higher degree (Offermann and Int-Hout 1989).
Theoretical perfect mixing occurs when supply air is instantly and evenly distributed throughout a space. Perfect mixing is also known as complete or uniform mixing; the air may be called well stirred or well mixed. This theoretical performance is approached by entrainment flow systems that have good mixing and by displacement flow systems that allow too much mixing (Rock et al. 1995). The outdoor air requirements given in the minimum ventilation rate in breathing zone table of ASHRAE Standard 62.1 assume delivery of ventilation air with perfect mixing within spaces. For more detailed information on space air diffusion, see Chapter 20.
Underfloor air distribution (UFAD or UAD), as shown in Figure 5, is a hybrid method of conditioning and ventilating spaces (Bauman and Daly 2003). Air is introduced through a floor plenum, with or without branch ductwork or terminal units, and delivered to a space by floor-mounted diffusers. These diffusers encourage air mixing near the floor to temper the supply air for thermal comfort. The combined air then moves vertically through the space, with reduced mixing, toward returns or exhausts placed in or near the ceiling. This vertical upward movement of the air is in the same direction as the thermal and contaminant plumes created by occupants and common equipment. The ventilating performance of UFAD systems is thus often between floor-to-ceiling displacement flow and uniform mixing.
Supply air that enters a space through a diffuser, grille, or nozzle is also known as primary air. An air jet is formed as this primary air leaves the supply air outlet. Secondary air is the room air entrained into the jet. Total air is the combination of primary and secondary air at a specific point in a jet and increases with distance from the outlet as is described further in Chapter 20. The term primary air is also used to describe supply air provided to fan-powered mixing boxes by a central air-handling unit.
For evaluation of indoor air quality and thermal comfort, rooms are often divided into two portions: the occupied zone and the remaining volume of the space. Often, this remaining volume is solely the space above the occupants and is referred to as the ceiling zone. The occupied zone is usually defined as the lowest 6 ft of a room, although layers near the floor and walls are sometimes deducted from it; when these deductions are made, the occupied zone is sometimes renamed the breathing zone. Ceiling and floor plenums are not normally included in the occupied or ceiling zones. Thermal zones are different from these room air zones, and are defined for HVAC subsystems and their controls.
The air change (or exchange) rate I compares airflow to the space’s volume and is
where
| Q |
= |
volumetric flow rate of air into space, cfm |
| V |
= |
interior volume of space, ft3 |
The air change rate has units of 1/time, usually h−1. When the time unit is hours, the air change rate is also called air changes per hour (ACH), with units of h−1. The air change rate may be defined for several different situations. For example, the air change rate for an entire building or thermal zone served by an air-handling unit compares the amount of outdoor air brought into the building or zone to the total interior volume. This nominal air change rate IN is
where Qoa is the outdoor airflow rate including ventilation and infiltration. IN describes the outdoor air ventilation rate entering a building or zone. It does not describe recirculation or the distribution of ventilation air to each space in a building or zone.
For a particular space, the space air exchange rate IS compares the supply airflow rate Qsa to the volume of that space:
For a particular space or zone, IS includes recirculated as well as any outdoor air in the supply air, and is used frequently in evaluating supply air outlet performance and space air mixing.
Timeconstants τ, which have units of time (usually in hours or seconds), are also used to describe ventilation and infiltration. One time constant is the time required for one air change in a building, zone, or space if ideal displacement flow existed. It is the inverse of the air change rate:
The nominal time constant compares the interior volume of a building or zone to the volumetric outdoor airflow rate:
Like the nominal air change rate, τN does not describe recirculation of air in a building or zone, or characterize the distribution of the outdoor air to individual spaces in a building or zone.
The space time constant compares the interior volume of a particular space to the total supply airflow rate to that space. The space time constant is the inverse of the space air change rate:
The space time constant includes the effect of recirculated air that is part of the supply air as well as that of outdoor air introduced to the space through the supply air. If infiltration is significant in a space, then the infiltration flow rate should be included when determining both the space air change rate and the space time constant.
Averaging Time-Varying Ventilation Rates
When assessing time-varying ventilation in terms of controlling indoor air quality, the quantity of interest is often the temporal average rather than the peak. The concept of effective ventilation (Sherman and Wilson 1986; Yuill 1986, 1991) describes the proper ventilation rate averaging process. In this concept, the average (effective) rate is the steady-state rate that yields the same average contaminant concentration over the period of interest in the occupied space as does the actual sequence of time-varying discrete ventilation rates over the same period and in the same space. This effective rate is only equal to the simple arithmetic average rate when the discrete ventilation rates are constant over the period of interest and the contaminant concentration has reached its steady-state value. Simple arithmetic averaging of instantaneous ventilation rates or concentrations cannot generally be used to determine these averages because of the nonlinear response of indoor concentrations to ventilation rate variations.
An important constraint in the effective ventilation concept is that the contaminant source strength F must be constant over the period of interest or must be uncorrelated with the ventilation rate. These conditions are satisfied in many residential and commercial buildings because the emission rates of many contaminants that are controlled by whole-building ventilation systems vary slowly. Sherman and Wilson (1986) describe how to deal with pollutants that have stepped but otherwise constant emission rates. Pollutants such as carbon monoxide, radon, and formaldehyde, whose emission rates can be affected by ventilation, cannot be properly characterized with this concept and require more complex analyses. For constant-source-strength pollutants, the relationship between effective air change rate, effective ventilation rate, volumetric flow, source strength, average concentration, and time-averaged effective turnover time is given by
The time-averaged effective turnover time τ̅e in Equation (8) represents the characteristic time for the concentration in the occupied space to approach steady state over the period of interest. It can be determined from a sequence of discrete, instantaneous ventilation air change rates Ii using the following (Sherman and Wilson 1986):
where
| Δt |
= |
length of each discrete time period |
| τ̅e |
= |
time-averaged effective turnover time |
| τ̅e, i |
= |
instantaneous turnover time in period i |
| τ̅e, i−1 |
= |
instantaneous turnover time in previous period |
ASHRAE Standard 62.2 provides a set of factors to help calculate the annual effective air exchange rate.
The age of air θage (Sandberg 1981) is the length of time t that some quantity of outdoor air has been in a building, zone, or space. The “youngest” air is at the point where outdoor air enters the building by mechanical or natural ventilation, or through infiltration (Grieve 1989). The “oldest” air may be at some location in the building or in the exhaust air. When the characteristics of the air distribution system are varied, age of air is inversely correlated with quality of outdoor air delivery. Units are of time, usually in seconds or minutes, so it is not a true efficiency or effectiveness measure. The age of air concept, however, has gained wide acceptance in Europe.
The age of air can be evaluated for existing buildings using tracer gas methods. Using either the decay (step-down) or growth (step-up) tracer gas method and assuming perfect mixing, the zone average or nominal age of air θage,N can be determined by taking concentration measurements in the exhaust air. The local age of air θage,L is evaluated through tracer gas measurements at any desired point in a space, such as at a worker’s desk. When time-dependent data of tracer gas concentration are available, the age of air can be calculated from
where Cin is the concentration of tracer gas being injected.
Because evaluation of the age of air requires integration to infinite time, an exponential tail is usually added to the known concentration data (Farrington et al. 1990).
Ventilation effectiveness is a description of an air distribution system’s ability to remove internally generated pollutants from a building, zone, or space. Air change effectiveness is a description of an air distribution system’s ability to deliver ventilation air to a building, zone, or space. The HVAC design engineer usually does not have knowledge or control of actual pollutant sources within buildings, so the minimum prescribed ventilation rates of ASHRAE Standard 62.1 define outdoor air requirements for typical, expected building uses. For most projects, therefore, air change effectiveness is of more relevance to HVAC system design than ventilation effectiveness. Various definitions for air change effectiveness have been proposed. The specific measure that meets local code requirements must be determined, if any is needed at all.
Air change effectiveness measures εI are nondimensional gages of ventilation air delivery. One common definition of air change effectiveness is the ratio of a time constant to an age of air:
The nominal air change effectiveness εI,N shows the effectiveness of outdoor air delivery to the entire building, zone, or space:
where the nominal time constant τN is usually calculated from measured airflow rates.
The local air change effectiveness εI,L shows the effectiveness of outdoor air delivery to one specific point in a space:
where τN is found either through airflow measurements or from tracer gas concentration data. An εI,L value of 1.0 indicates that the air distribution system delivers air equivalent to that of a system with perfectly mixed air in the spaces. A value less than 1.0 shows less than perfect mixing with some degree of stagnation. A value of εI,L greater than 1.0 suggests that a degree of plug or displacement flow is present at that point (Rock 1992).
An HVAC design engineer often assumes that a properly designed, installed, operated, and maintained air distribution system provides an air change effectiveness of about 1. However, the zone air distribution table of ASHRAE Standard 62.1 provides some estimates of effectiveness for operating in heating or cooling mode, and with various air distribution techniques. These values are then adjusted for commercial and institutional building design when the ventilation rate procedure (VRP) is used. If the IAQ procedure of Standard 62.1 is used, then actual pollutant sources and the air change effectiveness must be known for the successful design of HVAC systems that have fixed ventilation airflow rates.
ASHRAE Standard 129 describes a method for measuring air change effectiveness of mechanically vented spaces and buildings with limited air infiltration, exfiltration, and air leakage with surrounding indoor spaces.
3. DRIVING MECHANISMS FOR VENTILATION AND INFILTRATION
Natural ventilation and infiltration are driven by pressure differences across the building envelope caused by wind and air density differences. Mechanical air-moving systems also induce pressure differences across the envelope through operation of appliances, such as combustion devices, leaky forced-air thermal distribution systems, and mechanical ventilation systems. The indoor/outdoor pressure difference at a location depends on the magnitude of these driving mechanisms as well as on the characteristics of the openings in the building envelope.
Stack pressure is the hydrostatic pressure caused by the weight of a column of air located inside or outside a building. It can also occur within a flow element, such as a duct or chimney that has vertical separation between its inlet and outlet. The hydrostatic pressure in the air depends on density and the height of interest above a reference point.
Air density is a function of local barometric pressure, temperature, and humidity ratio, as described in Chapter 1. As a result, standard conditions should not be used to calculate the density. For example, a building site at 5000 ft has air density that is about 20% less than if the building were at sea level. An air temperature increase from −20 to 70°F causes a similar air density difference. Combined, these elevation and temperature effects can reduce air density about 45%. Moisture effects on density are generally much less but can be significant if the change in elevation is great (e.g., in a natural draft cooling tower). Saturated air at 105°F has a density about 5% less than that of dry air at the same pressure.
Assuming the air temperature and humidity ratio are constant over the height of interest, the stack pressure decreases linearly as the distance above the reference point increases. For a single column of air, the stack pressure can be calculated as
where
| ps |
= |
stack pressure, in. of water |
| pr |
= |
stack pressure at reference height, in. of water |
| g |
= |
gravitational acceleration, 32.2 ft/s2 |
| ρ |
= |
indoor or outdoor air density, lbm/ft3 |
| H |
= |
height above reference plane, ft |
| 0.00598 |
= |
unit conversion factor, in. of water · ft · s2/lbm |
For tall buildings or when significant temperature stratification occurs indoors, Equation (23) should be modified to include the density gradient over the height of the building.
Temperature, and thus air density differences between indoors and outdoors cause stack pressure differences that drive airflows across the building envelope; the stack effect is this buoyancy phenomenon. Sherman (1991) showed that any single-zone building can be treated as an equivalent box from the point of view of stack effect; if there is air leakage, follow the power law as described in the section on Residential Air Leakage. The building is then characterized by an effective stack height and neutral pressure level (NPL) or leakage distribution, as described in the section on Neutral Pressure Level. Once calculated, these parameters can be used in physical, single-zone models to estimate infiltration.
Neglecting vertical density gradients, the stack pressure difference for a horizontal leak at any vertical location is
where
| To |
= |
absolute outdoor temperature, °R |
| Ti |
= |
absolute indoor temperature, °R |
| ρo |
= |
outdoor air density, lb/ft3 |
| ρi |
= |
indoor air density, lb/ft3 |
| HNPL |
= |
height of neutral pressure level above reference plane without any other driving forces, ft |
Chastain and Colliver (1989) showed that, when there is stratification, the average of the vertical distribution of temperature differences is more appropriate to use in Equation (24) than the localized temperature difference near the opening of interest.
By convention, stack pressure differences are positive when the building is pressurized relative to outdoors, which causes flow out of the building. Therefore, absent other driving forces and assuming no stack effect within the flow elements themselves, when indoor air is warmer than outdoors, the base of the building is depressurized and the top is pressurized relative to outdoors; when indoor air is cooler than outdoors, the reverse is true. At some elevation in the building, with such conditions, the pressure indoors is equal to the outdoors: this height is the neutral pressure level.
Absent other driving forces, the location of the NPL is influenced by leakage distribution over the building exterior and by interior compartmentation. As a result, the NPL is not necessarily at the mid-height of the building; with effective horizontal barriers in tall buildings, it is also possible to have more than one NPL. NPL location and leakage distribution are described in the Combining Driving Forces and Neutral Pressure Level sections.
For a penetration through the building envelope for which (1) there is vertical separation between its inlet and outlet and (2) air inside the flow element is not at the indoor or outdoor temperature (e.g., in a chimney), more complex analyses than Equation (24) are required to determine the stack effect at any location on the building envelope.
When wind impinges on and flows around and over a building, it creates a distribution of static pressures on the building’s exterior surfaces that depends on the wind direction, wind speed, air density, surface orientation, and surrounding conditions. Wind pressures are generally positive with respect to the static pressure in the undisturbed airstream on the windward side of a building and negative on the leeward sides and roof. However, these pressures depend highly on wind speed, angle, turbulence, the surroundings, and building shape. Static pressures over building surfaces are almost proportional to the velocity head of the undisturbed airstream. The wind pressure or velocity head is given by the Bernoulli equation, assuming no height change or pressure losses:
where
| pw |
= |
wind surface pressure relative to outdoor static pressure in undisturbed flow, in. of water |
| ρ |
= |
outdoor air density, lbm/ft3 (about 0.075 at or near sea level) |
| U |
= |
wind speed, mph |
| Cp |
= |
wind surface pressure coefficient, dimensionless |
| 0.0129 |
= |
unit conversion factor, in. of water · ft3/lbm · mph2 |
Cp is a function of location on the building envelope and wind direction. Chapter 24 provides additional information on values of Cp.
Most pressure coefficient data are for winds approaching perpendicularly to upwind building surfaces. Unfortunately, for a real building, this fixed wind direction rarely occurs, and when the wind is not normal to the upwind wall, these pressure coefficients do not apply. Walker and Wilson (1994) developed a harmonic trigonometric function to interpolate between the surface average pressure coefficients on a wall that were measured with the wind normal to each of the four building surfaces. This function was developed for low-rise buildings three stories or less in height. For each wall of the building, Cp is given by
where
| Cp(1) |
= |
pressure coefficient when wind is at 0° |
| Cp(2) |
= |
pressure coefficient when wind is at 180° |
| Cp(3) |
= |
pressure coefficient when wind is at 90° |
| Cp(4) |
= |
pressure coefficient when wind is at 270° |
| ϕ |
= |
wind angle measured clockwise from the normal to wall 1 |
Because the cosine term in Equation (26) can be negative, its sign must be tracked. When cos(ϕ) is negative, subtract the value of the absolute of cos(ϕ) to the 3/4 power.
The measured data used to develop the harmonic function from Akins et al. (1979) and Wiren (1985) show that typical values for the pressure coefficients are Cp(1) = 0.6, Cp(2) = –0.3, and Cp(3) = Cp(4) = –0.65. Because of geometry effects on flow around a building, application of this interpolation function is limited to low-rise buildings of rectangular plan on flat, featureless sites, with the longest wall less than three times the length of the shortest wall. For less regular buildings or sites, simple correlations are inadequate and building-specific pressure coefficients are required; computational fluid dynamic models are often used. Chapter 24 discusses wind pressures for complex building shapes and for high-rise buildings in more detail.
The wind speed most commonly available for infiltration calculations is that measured at the local weather station, typically the nearest airport. This wind speed needs to be corrected for reductions caused by the difference between the height where the wind speed is measured and the height of the building, and reductions caused by shelter effects.
The reference wind speed used to determine pressure coefficients is usually the wind speed at the eave height for a low-rise building and the building height for a high-rise building. However, meteorological wind speed measurements are made at a different height, typically 33 ft for official weather stations, and at a different location than for the buildings of interest. The difference in terrain between the measurement station and the building under study must also be addressed. Chapter 24 shows how to calculate the effective wind speed UH from the reference wind speed Umet using boundary layer theory and estimates of terrain effects.
In addition to the reduction in wind pressures caused by reduced wind speed, the effects of local shelter also act to reduce wind pressures. The shielding effects of trees, shrubbery, and other buildings within several building heights, horizontally, of a particular building produce large-scale turbulence eddies that not only reduce effective wind speed but also alter wind direction. Local geological features or gaps between neighboring large buildings can, at times, greatly increase wind velocity. Thus, meteorological wind speed data must be adjusted carefully when applied to specific buildings and their locations.
Infiltration rates measured by Wilson and Walker (1991) for a row of houses showed reductions in airflow rates of up to a factor of three when the wind changed direction from perpendicular to parallel to the row. They recommended estimating wind shelter for winds perpendicular to each side of the building and then using the interpolation function in Equation (27) to find the wind shelter for intermediate wind angles:
where
| s |
= |
shelter factor for the particular wind direction ϕ |
| s(i) |
= |
shelter factor when wind is normal to wall i (i = 1 to 4, for four sides of a building) |
Although this method gives a realistic variation of wind shelter effects with wind direction, estimates for numerical values of wind shelter factor s for each of the four cardinal directions must be provided. Table 8 in the section on Residential Calculation Examples lists typical shelter factors. The wind speed used in Equation (25) is then given by
The magnitude of pressure differences found on the surfaces of buildings varies rapidly with time because of turbulent fluctuations in the wind (Etheridge and Nolan 1979; Grimsrud et al. 1979). However, using average wind pressures to calculate pressure differences is usually sufficient to calculate average infiltration values.
Operation of mechanical equipment, such as supply or exhaust systems and vented combustion devices, affects pressure differences across the building envelope and thus air change rates. Interior static pressure adjusts such that the sum of all airflows through openings in the building envelope plus equipment-induced airflows balances to zero. To predict these changes in pressure differences and airflow rates caused by mechanical equipment, the location of each opening in the envelope and relationship between pressure difference and airflow rate for each opening must be known. The interaction between mechanical ventilation system operation and envelope airtightness has been discussed for low-rise buildings (Nylund 1980) and for office buildings (Persily and Grot 1985a; Tamura and Wilson 1966, 1967a).
Air exhausted from a building by a whole-building exhaust system must be balanced by increasing airflow into the building through other openings or the air-handling systems. As pressures vary, air leakage at some locations changes from outflow to inflow. When using makeup air and no dedicated exhaust, the situation is reversed and envelope inflows may become outflows. Thus, the effects of a mechanical system on a building must be considered. Depressurization caused by an improperly designed exhaust system can increase the rate of radon entry into a building and can interfere with proper operation of combustion device venting or other exhaust systems. Pollutant entry can be increased from garages and other attached storage spaces. Depressurization can also force moist outdoor air through the building envelope; for example, during the cooling season in hot, humid climates, moisture may condense in the building envelope and cause rust, rot, or mold. A similar phenomenon, but in reverse, can occur during the heating, and potentially humidifying, season in cold climates if the building is pressurized. Active pressure control is often recommended, as is proper use of moisture retarders, drainage, and drying of in situ building materials.
The interaction between mechanical systems and the building envelope also pertains to systems serving zones of buildings. Performance of zone-specific exhaust or pressurization systems is affected by leakage in partitions between zones as well as through exterior walls.
Mechanical systems can also create infiltration-driving forces in single-zone buildings. Specifically, some single-family houses with central forced-air duct systems have many distributed supply registers, yet only one central return grille. When insufficiently undercut internal doors are closed in these houses, large positive indoor-to-outdoor pressure differentials are created for rooms with only supply registers, whereas the room or hallway with the return grille tends to depressurize relative to the outdoors. This is caused by the resistance of the internal door undercuts, often partially blocked by carpeting, to flow from the supply register to the return; the magnitudes of the indoor/outdoor pressure differentials created average 0.012 to 0.024 in. of water (Modera et al. 1991). Balanced airflow systems with ducted air return and distributed grilles or adequately sized transfer grilles (where still allowed by fire code) reduce this effect significantly.
Building envelope airtightness and interzonal airflow resistance can also affect performance of mechanical systems. The actual airflow rate delivered by these systems, particularly ventilation systems, depends on the pressure differences they work against. This effect is the same as the interaction of a fan with its associated ductwork, which is discussed in Chapter 21 of this volume and Chapter 21 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment. The building envelope and its leakage should be considered part of the ductwork in determining the pressure drop of the system.
Duct leakage can cause similar problems. Supply leaks to the outdoors tend to depressurize the building; return leaks from the outdoors tend to pressurize it. Keeping these ducts within the conditioned buildings, and sealing all ducts well with durable materials and high-quality construction methods, significantly reduces this problem.
Pressure differences caused by wind, stack effect, and mechanical systems are considered in combination by adding them together and then determining the resulting airflow rate through each building envelope. The airflows must be determined in this manner, as opposed to adding the airflow rates caused by the separate driving forces, because the airflow rate through each opening is not linearly related to pressure difference.
For uniform indoor air temperatures, the total pressure difference across each leak can be written in terms of a reference wind parameter PU and stack effect parameter PT common to all leaks:
where T is absolute air temperature in °R.
The pressure difference across each leak, with positive pressures for flow into the building, is then given by
where ΔpI is the pressure that acts to balance inflows and outflows, including mechanical system flows. Equation (31) can then be applied to every leak for the building with appropriate values of Cp, s, and H. Thus, each leak is defined by its pressure coefficient, shelter, and height. Where indoor pressures are not uniform, more complex and often numerical analyses are required.
The neutral pressure level (NPL) varies and is that height or heights in the building envelope where, at that particular instant, there is no indoor-to-outdoor pressure difference. Internal partitions, stairwells, elevator shafts, utility ducts, chimneys, vents, operable windows, and mechanical supply and exhaust systems complicate the prediction of NPL location. An opening with a large area relative to the total building leakage causes the NPL to shift toward the opening. In particular, chimneys and openings at or above roof height raise the NPL in small buildings. Exhaust systems increase the height of the NPL; outdoor air supply systems lower it.
Figure 6 qualitatively shows the addition of driving forces for a building with uniform openings above and below mid-height and without significant internal resistance to airflow. The slopes of the pressure lines are a function of the densities of the indoor and outdoor air. In Figure 6A, with indoor air warmer than outdoor and pressure differences caused solely by thermal forces, the NPL is at mid-height, with inflow through lower openings and outflow through higher openings. For the low air velocities typical in and around buildings, the direction of flow is always from the higher to the lower-pressure region.
Figure 6B presents qualitative uniform pressure differences caused by wind alone, with opposing effects on the windward and leeward sides. When temperature difference and wind effects both exist, the pressures caused by each are added together to determine the total pressure difference across the building envelope. In Figure 6B, there is no NPL because no locations on the building envelope have zero pressure difference. Figure 6C shows the combination, where the wind force of Figure 6B has just balanced the thermal force of Figure 6A, causing no pressure difference at the top windward or bottom leeward side.
The relative importance of wind and stack pressures in a building depends on building height, internal resistance to vertical airflow, location and flow resistance characteristics of envelope openings, local terrain, and the immediate shielding of the building. The taller the building and the smaller its internal resistances to airflow, the stronger the stack effect. The stack effect can be reduced by effectively sealing the building internally between floors, typically by gasketing elevator and stairway doors, and sealing pipe, duct, and electrical penetrations; these measures, when done by code-approved means, also typically reduce undesired smoke migration during fire events. Gasketing interior doors, especially those from exterior spaces or to elevator lobbies, in tall buildings can also help restrict air leakage paths.
The effect of mechanical ventilation on envelope pressure differences is more complex and depends on both the direction of ventilation flow (exhaust or supply) and the differences in these ventilation flows among the zones of the building. If mechanically supplied outdoor air is provided uniformly to each story, the change in the exterior wall pressure difference pattern is uniform. With a nonuniform supply of outdoor air (e.g., to one story only), the extent of pressurization varies from story to story and depends on internal airflow resistance. Pressurizing all levels uniformly has little effect on pressure differences across floors and vertical shaft enclosures, but pressurizing individual stories increases the pressure drop across these internal separations. Pressurizing the ground level is often used in tall buildings in winter to reduce negative air pressures across entries; vestibules and revolving doors are also used to limit air leakage. Vestibules may also be used for elevator lobbies and stair towers to reduce air and smoke movement vertically through tall buildings.
Available data on the NPL in various kinds of buildings are limited. In tall buildings studied by Tamura and Wilson (1966, 1967b), the NPL varied from 0.3 to 0.7 of total building height. For houses, especially those with chimneys, the NPL is usually above mid-height. Operating a combustion heat source that vents to the outdoors raises the NPL further, sometimes above the ceiling (Shaw and Brown 1982).
Thermal Draft Coefficient
Compartmentation of a building also affects the NPL location. Equation (24) provides a maximum stack pressure difference, given no internal airflow resistance. The sum of pressure differences across the exterior wall at the bottom and top of the building, as calculated by these equations, equals the total theoretical draft for the building. The sum of actual top and bottom pressure differences, divided by the total theoretical draft pressure difference, equals the thermal draft coefficient. The value of the thermal draft coefficient depends on the airflow resistance of exterior walls relative to the airflow resistance between floors. For a building without internal partitions, the total theoretical draft is achieved across the exterior walls (Figure 7A), and the thermal draft coefficient equals 1. In a building with airtight separations between each floor, each story acts independently, its own stack effect being unaffected by that of any other floor (Figure 7B). The theoretical draft is minimized in this case, and each story has its own NPL.
Real multistory buildings are neither open inside, nor airtight between stories. Vertical air passages, stairwells, elevators, and other service shafts allow airflow between floors. Figure 7C represents a heated building with uniform openings in the exterior wall, through each floor, and into the vertical shaft at each story. Between floors, the slope of the line representing the indoor pressure is the same as that shown in Figure 7A, and the discontinuity at each floor (Figure 7B) represents the pressure difference across it. Some of the pressure difference maintains flow through openings in the floors and vertical shafts. As a result, the pressure difference across the exterior wall at any level is less than it would be with no internal flow resistance.
Maintaining airtightness between floors and from floors to vertical shafts is a way to control indoor/outdoor pressure differences because of the stack effect and, therefore, infiltration and exfiltration. Good separation is also conducive to proper operation of mechanical ventilation and smoke management systems. However, care is needed to avoid creating pressure differences that could prevent egress doors from opening in an emergency. Tamura and Wilson (1967a) showed that when vertical shaft leakage is at least two times envelope leakage, the thermal draft coefficient is almost one and the effect of compartmentation is negligible. Measurements of pressure differences in three tall office buildings by Tamura and Wilson (1967b) indicated that the thermal draft coefficient ranged from 0.8 to 0.9 with ventilation systems off. Modern internal sealing techniques should result in much less vertical leakage.
ASHRAE members can access ASHRAE Journal articles and ASHRAE research project final reports at technologyportal.ashrae.org. Articles and reports are also available for purchase by nonmembers in the online ASHRAE Bookstore at www.ashrae.org/bookstore.
ACGIH. 2016. Industrial ventilation: A manual of recommended practice, 29th ed. American Conference of Governmental Industrial Hygienists, Cincinnati, OH.
Ackerman, M.Y., J.D. Dale, and D.J. Wilson. 2006. Infiltration heat recovery, part 1: Field studies in an instrumented test building (RP-1169). ASHRAE Transactions 112(2):597-608. Paper QC-06-056.
AIVC. 1994. An analysis and data summary of the AIVC’s numerical database. Technical Note 44. International Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Akins, R.E., J.A. Peterka, and J.E. Cermak. 1979. Averaged pressure coefficients for rectangular buildings, vol. 1, Proceedings of the Fifth International Wind Engineering Conference, Fort Collins, pp. 369-380.
Allard, F., and M. Herrlin. 1989. Wind-induced ventilation. ASHRAE Transactions 95(2):722-728. Paper VA-89-10-2.
Anis, W. 2001. The impact of airtightness on system design. ASHRAE Journal 43(12):31-35.
Anis, W., and T. Brennan. 2014. Measuring airtightness of mid and high-rise non-residential buildings. ASHRAE Research Project RP-1478, Final Report.
Apte, M.G., W.J. Fisk, and J.M. Daisey. 2000. Associations between indoor CO2 concentrations and sick building syndrome symptoms in US office buildings: An analysis of the 1994-1996 BASE study data. Indoor Air 10(4):246-257.
ASHRAE. 2003. Risk management guidance for health, safety and environmental security under extraordinary incidents. Report, Presidential Ad Hoc Committee for Building Health and Safety Under Extraordinary Incidents.
ASHRAE. 2010a. Standard 62.2-2010 user’s manual.
ASHRAE. 2010b. Standard 62.1-2010 user’s manual.
ASHRAE. 2012. Method of testing general ventilation air-cleaning devices for removal efficiency by particle size. ANSI/ASHRAE Standard 52.2-2012.
ASHRAE. 2013. Thermal environmental conditions for human occupancy. ASHRAE Standard 55-2013.
ASHRAE. 2010. Ventilation for acceptable indoor air quality. ANSI/ASHRAE Standard 62.1-2010.
ASHRAE. 2016. Ventilation and acceptable indoor air quality in low-rise residential buildings. ANSI/ASHRAE Standard 62.2-2016.
ASHRAE. 2016. Energy standard for buildings except low-rise residential buildings. ANSI/ASHRAE Standard 90.1-2016.
ASHRAE. 2004. Air leakage performance for detached single-family residential building. ANSI/ASHRAE Standard 119-1988 (RA 2004) (withdrawn).
ASHRAE. 2002. Measuring air-change effectiveness. ANSI/ASHRAE Standard 129-97 (RA 2002).
ASHRAE. 2013. Ventilation of health care facilities. ANSI/ASHRAE/ASHE Standard 170-2013.
ASHRAE. 2014. Standard for the design of high-performance green buildings. ANSI/ASHRAE/IES/USGBC Standard 189.1-2014.
ASHRAE. 2015. Ventilation and indoor air quality in low-rise residential buildings. ASHRAE Guideline 24-2015.
Ask, A. 2003. Ventilation and air leakage. ASHRAE Journal 45(11):28-36.
ASTM. 2012. Test method for determining rate of air leakage through exterior windows, curtain walls, and doors under specified pressure differences across the specimen. Standard E283-04 (R2012). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2011. Test method for determining air change in a single zone by means of a tracer gas dilution. Standard E741-11. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2010. Test method for determining air leakage rate by fan pressurization. Standard E779-10. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2010. Test method for field measurement of air leakage through installed exterior windows and doors. Standard E783-02 (R2010). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2009. Practices for air leakage site detection in building envelopes and air barrier systems. Standard E1186-03 (R2009). American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2011. Test methods for determining airtightness of buildings using an orifice blower door. Standard E1827-11. American Society for Testing and Materials, West Conshohocken, PA.
ASTM. 2011. Guide for assessing depressurization-induced backdrafting and spillage from vented combustion appliances. Standard E1998-11. American Society for Testing and Materials, West Conshohocken, PA.
Axley, J.W. 2001a. Application of natural ventilation for U.S. commercial buildings—Climate suitability, design strategies and methods, modeling studies. GCR-01-820, National Institute of Standards and Technology, Gaithersburg, MD.
Axley, J.W. 2001b. Residential passive ventilation systems: Evaluation and design. Technical Note 54. International Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Axley, J., S. Emmerich, S. Dols, and G. Walton. 2002. An approach to the design of natural and hybrid ventilation systems for cooling buildings. Proceedings of the 9th International Conference on Indoor Air Quality and Climate, Monterey, CA. Available at www.nist.gov/manuscript-publication-search.cfm?pub_id=860870.
Bankvall, C.G. 1987. Air movements and thermal performance of the building envelope. In Thermal insulation: Materials and systems, pp. 124-131. F.J. Powell and S.L. Mathews, eds. American Society for Testing and Materials, West Conshohocken, PA.
Barley, D. 2001. Overview of residential ventilation activities in the Building America Program (phase I). NREL/TP-550-30107, National Renewable Energy Laboratory, Golden, CO.
Batterman, S., G. Hatzivasilis, and C. Jia. 2006. Concentrations and emissions of gasoline and other vapors from residential vehicle garages. Atmospheric Environment 40:1828-1844.
Bauman, F., and A. Daly. 2003. Underfloor air distribution design guide. ASHRAE.
Berg-Munch, B., G. Clausen, and P.O. Fanger. 1986. Ventilation requirements for the control of body odor in spaces occupied by women. Environmental International 12(1-4):195.
Berlad, A.L., N. Tutu, Y. Yeh, R. Jaung, R. Krajewski, R. Hoppe and F. Salzano. 1978. Air intrusion effects on the performance of permeable insulation systems. In Thermal insulation performance, STP 718, pp. 181-194. D. McElroy and R. Tye, eds. American Society for Testing and Materials, West Conshohocken, PA.
Blomsterberg, A.K., and D.T. Harrje. 1979. Approaches to evaluation of air infiltration energy losses in buildings. ASHRAE Transactions 85(1):797. Paper PH-79-10-1.
Bohac, D.L., D.T. Harrje, and L.K. Norford. 1985. Constant concentration infiltration measurement technique: An analysis of its accuracy and field measurements, 176. Proceedings of the ASHRAE/DOE/BTECC Conference on the Thermal Performance of the Exterior Envelopes of Buildings III, Clearwater Beach, FL.
Bohac, D.L., D.T. Harrje, and G.S. Horner. 1987. Field study comparisons of constant concentration and PFT infiltration measurements. Proceedings of the 8th IEA Conference of the Air Infiltration and Ventilation Centre, Überlingen, Germany, pp. 47-62.
Bradley, B. 1993. Implementation of the AIM-2 infiltration model in HOT-2000. Report, for Natural Resources Canada.
Buchanan, C.R., and M.H. Sherman. 2000. A mathematical model for infiltration heat recovery. Proceedings of the 21st IEA Conference of the Air Infiltration and Ventilation Centre, The Hague, Netherlands. Report LBNL-44294. Lawrence Berkeley National Laboratory, Berkeley, CA.
Cain, W.S., B. Leaderer, R. Isseroff, L. Berglund, R. Huey, and E. Lipsitt. 1983. Ventilation requirements in buildings—I. Control of occupancy odor and tobacco smoke odor. Atmospheric Environment 17(6):1183-1197.
CGSB. 2005. Depressurization test. CAN/CGSB Standard 51.71-2005. Canadian General Standards Board, Ottawa, ON.
CGSB. 1986. Determination of the airtightness of building envelopes by the fan depressurization method. Standard 149.10-M86. Canadian General Standards Board, Ottawa, ON.
CGSB. 1996. Determination of the overall envelope airtightness of buildings by the fan pressurization method using the building’s air handling systems. Standard 149.15-96. Canadian General Standards Board, Ottawa, ON.
Charlesworth, P.S. 1988. Measurement of air exchange rates. Chapter 2 in Air exchange rate and airtightness measurement techniques—An applications guide. International Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Chastain, J.P. 1987. Pressure gradients and the location of the neutral pressure axis for low-rise structures under pure stack conditions. Unpublished M.S. thesis. University of Kentucky, Lexington.
Chastain, J.P., and D.G. Colliver. 1989. Influence of temperature stratification on pressure differences resulting from the infiltration stack effect. ASHRAE Transactions 95(1):256-268. Paper 3230.
Chastain, J.P., D.G. Colliver, and P.W. Winner, Jr. 1987. Computation of discharge coefficients for laminar flow in rectangular and circular openings. ASHRAE Transactions 93(2):2259-2283. Paper NT-87-27-1.
CHBA. 1994. HOT2000 technical manual. Canadian Home Builders Association, Ottawa, ON.
CIBSE. 2000. Testing buildings for air leakage. Standard TM-23. Chartered Institution of Building Services Engineers, London.
CIBSE. 2005. Natural ventilation in non-domestic buildings. Chartered Institution of Building Services Engineers, London.
Claridge, D.E., and S. Bhattacharyya. 1990. The measured impact of infiltration in a test cell. ASME Journal of Solar Energy Engineering 112: 123-126.
Claridge, D.E., M. Krarti, and S. Bhattacharyya. 1988. Preliminary measurements of the energy impact of infiltration in a test cell. Proceedings of the Fifth Annual Symposium on Improving Building Energy Efficiency in Hot and Humid Climates, pp. 308-317.
Cole, J.T., T.S. Zawacki, R.H. Elkins, J.W. Zimmer, and R.A. Macriss. 1980. Application of a generalized model of air infiltration to existing homes. ASHRAE Transactions 86(2):765. Paper DV-80-09-2.
Collet, P.F. 1981. Continuous measurements of air infiltration in occupied dwellings. Proceedings of the 2nd IEA Conference of the Air Infiltration Centre, Stockholm, p. 147.
CSA. 2016. Residential carbon monoxide alarming devices. CAN/CSA Standard C6.19-01 (R2016). Canadian Standards Association, Toronto.
CSA. 2014. Residential mechanical ventilation systems. CAN/CSA-F326-M91 (R2014). Canadian Standards Association, Toronto.
Cummings, J.B., and J.J. Tooley, Jr. 1989. Infiltration and pressure differences induced by forced air systems in Florida residences. ASHRAE Transactions 96(20):551-560. Paper VA-89-05-4.
Cummings, J.B., J.J. Tooley, Jr., and R. Dunsmore. 1990. Impacts of duct leakage on infiltration rates, space conditioning energy use and peak electrical demand in Florida homes. Proceedings of the ACEEE Summer Study, Pacific Grove, CA. American Council for an Energy-Efficient Economy, Washington, D.C.
Cutter. 1987. Air-to-air heat exchangers. In Energy design update. Cutter Information Corporation, Arlington, MA.
Desrochers, D., and A.G. Scott. 1985. Residential ventilation rates and indoor radon daughter levels. Transactions of the APCA Specialty Conference, Indoor Air Quality in Cold Climates: Hazards and Abatement Measures, Ottawa, p. 362.
Diamond, R.C., J.B. Dickinson, R.D. Lipschutz, B. O’Regan, and B. Shohl. 1982. The house doctor’s manual. Report PUB-3017. Lawrence Berkeley National Laboratory, Berkeley, CA.
Diamond, R.C., M.P. Modera, and H.E. Feustel. 1986. Ventilation and occupant behaviour in two apartment buildings. Proceedings of the 7th IEA Conference of the Air Infiltration and Ventilation Centre, Stratford-upon-Avon, U.K. Report LBL-21862. Lawrence Berkeley National Laboratory, Berkeley, CA.
Dickerhoff, D.J., D.T. Grimsrud, and R.D. Lipschutz. 1982. Component leakage testing in residential buildings. Proceedings of the American Council for an Energy-Efficient Economy, 1982 Summer Study, Santa Cruz, CA. Report LBL 14735. Lawrence Berkeley National Laboratory, Berkeley, CA.
Dietz, R.N., R.W. Goodrich, E.A. Cote, and R.F. Wieser. 1986. Detailed description and performance of a passive perfluorocarbon tracer system for building ventilation and air exchange measurement. In Measured air leakage of buildings, STP 904, p. 203. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Dols, W. S., L. Wang, S. J. Emmerich, and B. J. Polidoro. 2014. Development and application of an updated whole-building coupled thermal, airflow and contaminant transport simulation program (TRNSYS/CONTAM). Journal of Building Performance Simulation: 1-21.
D’Ottavio, T.W., G.I. Senum, and R.N. Dietz. 1988. Error analysis techniques for perfluorocarbon tracer derived multizone ventilation rates. Building and Environment 23(40).
Ek, C.W., S.A. Anisko, and G.O. Gregg. 1990. Air leakage tests of manufactured housing in the Northwest United States. In Air change rate and airtightness in buildings, STP 1067, pp. 152-164. M.H. Sherman, ed. American Society for Testing and Materials, West Conshohocken, PA.
Elmroth, A., and P. Levin. 1983. Air infiltration control in housing. International Energy Agency Air Infiltration Centre, Sint-Stevens-Woluwe, Belgium.
Emmerich, S.J. 2006. Simulated performance of natural and hybrid ventilation systems in an office building. HVAC&R Research (now Science and Technology for the Built Environment) 12(4):975-1004.
Emmerich, S.J., and A.K. Persily. 2005. Airtightness of commercial buildings in the U.S. Proceedings of the 26th IEA Conference of the Air Infiltration and Ventilation Centre, Brussels, pp 65-70.
Emmerich, S.J., J.E. Gorfain, and C. Howard-Reed. 2003. Air and pollutant transport from attached garages to residential living spaces—Literature review and field test. International Journal of Ventilation 2(3):265-276.
Emmerich, S.J., A.K. Persily, and L. Wang. 2013. Modeling and measuring the effects of portable gasoline powered generator exhaust on indoor carbon monoxide level. Technical Note (NIST TN) 1781. U.S. Department of Commerce, National Institute of Standards and Technology. Available at www.nist.gov/manuscript-publication-search.cfm?pub_id=912197.
Energy Resource Center. 1982. How to house doctor. University of Illinois, Chicago.
Etheridge, D.W. 1977. Crack flow equations and scale effect. Building and Environment 12:181.
Etheridge, D.W., and D.K. Alexander. 1980. The British gas multi-cell model for calculating ventilation. ASHRAE Transactions 86(2):808. Paper DV-80-09-4.
Etheridge, D.W., and J.A. Nolan. 1979. Ventilation measurements at model scale in a turbulent flow. Building and Environment 14(1):53.
Eyre, D., and D. Jennings. 1983. Air-vapour barriers—A general perspective and guidelines for installation. Energy, Mines, and Resources Canada, Ottawa, ON.
Farrington, R., D. Martin, and R. Anderson. 1990. A comparison of displacement efficiency, decay time constant, and age of air for isothermal flow in an imperfectly mixed enclosure. Proceedings of the ACEEE 1990 Summer Study on Energy Efficiency in Buildings, pp. 4.35-4.43. American Council for an Energy-Efficient Economy, Washington, D.C.
Fennell, H.C., and J. Haehnel. 2005. Setting airtightness standards. ASHRAE Journal 47(9):26-31.
Feustel, H.E., and A. Raynor-Hoosen, eds. 1990. Fundamentals of the multizone air flow model—COMIS. Technical Note 29. International Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
FGI. 2014. Guidelines for design and construction of hospital and healthcare facilities. American Institute of Architects, Facilities Guidelines Institute, and U.S. Department of Health and Human Services, Washington, D.C.
Fisk, W.J., R.K. Spencer, D.T. Grimsrud, F.J. Offermann, B. Pedersen, and R. Sextro. 1984. Indoor air quality control techniques: A critical review. Report LBL-16493. Lawrence Berkeley National Laboratory, Berkeley, CA.
Fisk, W.J., R.J. Prill, and O. Steppanen. 1989. A multi-tracer technique for studying rates of ventilation, air distribution patterns and air exchange efficiencies. Proceedings of Conference on Building Systems—Room Air and Air Contaminant Distribution, pp. 237-240. ASHRAE.
Fortmann, R.C., N.L. Nagda, and H.E. Rector. 1990. Comparison of methods for the measurement of air change rates and interzonal airflows to two test residences. In Air change rate and airtightness in buildings, STP 1067, pp. 104-118. M.H. Sherman, ed. American Society of Testing and Materials, West Conshohocken, PA.
Foster, M.P., and M.J. Down. 1987. Ventilation of livestock buildings by natural convection. Journal of Agricultural Engineering Research 37:1.
Fugler, D. 2004. Garage performance testing. CMHC Research Highlights (April). Canada Mortgage and Housing Corporation, Ottawa, ON.
Giesbrecht, P., and G. Proskiw. 1986. An evaluation of the effectiveness of air leakage sealing. In Measured air leakage of buildings, STP 904, p. 312. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Grieve, P.W. 1989. Measuring ventilation using tracer-gases. Brüel and Kjær, Denmark.
Grimsrud, D.T., and K.Y. Teichman. 1989. The scientific basis of Standard 62-1989. ASHRAE Journal 31(10):51-54.
Grimsrud, D.T., M.H. Sherman, R.C. Diamond, P.E. Condon, and A.H. Rosenfeld. 1979. Infiltration-pressurization correlations: Detailed measurements in a California house. ASHRAE Transactions 85(1):851. Paper PH-79-10-5.
Grimsrud, D.T., M.H. Sherman, and R.C. Sonderegger. 1982. Calculating infiltration: Implications for a construction quality standard. Proceedings of the ASHRAE/DOE Conference on the Thermal Performance of the Exterior Envelope of Buildings II, Las Vegas, p. 422.
Grot, R.A., and R.E. Clark. 1979. Air leakage characteristics and weatherization techniques for low-income housing. Proceedings of the ASHRAE/DOE Conference on the Thermal Performance of the Exterior Envelopes of Buildings, p. 178. Orlando, FL.
Grot, R.A., and A.K. Persily. 1986. Measured air infiltration and ventilation rates in eight large office buildings. In Measured air leakage of buildings, STP 904, p. 151. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
GSA. 2010. Facilities standards for the public buildings service. PBS-P100. U.S. General Services Administration, Washington, D.C.
Hamlin, T.L. 1991. Ventilation and airtightness in new, detached Canadian housing. ASHRAE Transactions 97(2):904-910. Paper IN-91-12-3.
Hamlin, T., and W. Pushka. 1994. Predicted and measured air change rates in houses with predictions of occupant IAQ comfort. Proceedings of the 15th IEA Air Infiltration and Ventilation Centre Conference, Buxton, U.K., pp. 771-775.
Harrje, D.T., and G.J. Born. 1982. Cataloguing air leakage components in houses. Proceedings of the ACEEE 1982 Summer Study, Santa Cruz, CA. American Council for an Energy-Efficient Economy, Washington, D.C.
Harrje, D.T., and T.A. Mills, Jr. 1980. Air infiltration reduction through retrofitting. In Building air change rate and infiltration measurements. STP 719, p. 89. C.M. Hunt, J.C. King, and H.R. Trechsel, eds. American Society for Testing and Materials, West Conshohocken, PA.
Harrje, D.T., G.S. Dutt, and J. Beyea. 1979. Locating and eliminating obscure but major energy losses in residential housing. ASHRAE Transactions 85(2):521. Paper DE-79-03-1.
Harrje, D.T., R.A. Grot, and D.T. Grimsrud. 1981. Air infiltration site measurement techniques. Proceedings of the 2nd IEA Conference of the Air Infiltration Centre, p. 113. Stockholm, Sweden.
Harrje, D.T., G.S. Dutt, D.L. Bohac, and K.J. Gadsby. 1985. Documenting air movements and infiltration in multicell buildings using various tracer-gas techniques. ASHRAE Transactions 91(2):2012-2027. Paper HI-85-40-3.
Harrje, D.T., R.N. Dietz, M. Sherman, D.L. Bohac, T.W. D’Ottavio, and D.J. Dickerhoff. 1990. Tracer gas measurement systems compared in a multifamily building. In Air change rate and airtightness in buildings, STP 1067, pp. 5-12. M.H. Sherman, ed. American Society for Testing and Materials, West Conshohocken, PA.
Heiselberg, P. 2002. Principles of hybrid ventilation. Final Report, International Energy Agency Energy Conservation in Buildings and Community Systems, Annex 35. Hybrid Ventilation Centre, Aalborg University, Denmark.
Hekmat, D., H.E. Feustel, and M.P. Modera. 1986. Impacts of ventilation strategies on energy consumption and indoor air quality in single-family residences. Energy and Buildings 9(3):239.
Herrlin, M.K. 1985. MOVECOMP: A static-multicell-airflow-model. ASHRAE Transactions 91(2B):1989. Paper HI-85-40-1.
Holton, J.K., M.J. Kokayko, and T.R. Beggs. 1997. Comparative ventilation system evaluations. ASHRAE Transactions 103(2):675-692. Paper PH-97-08-1.
Honma, H. 1975. Ventilation of dwellings and its disturbances. Faibo Grafiska, Stockholm, Sweden.
Hopkins, L.P., and B. Hansford. 1974. Air flow through cracks. Building Service Engineer 42(September):123.
Hunt, C.M. 1980. Air infiltration: A review of some existing measurement techniques and data. In Building air change rate and infiltration measurements, STP 719, p. 3. C.M. Hunt, J.C. King, and H.R. Trechsel, eds. American Society for Testing and Materials, West Conshohocken, PA.
ICC. 2012a. International energy conservation code® (IECC®). International Code Council, Washington, D.C.
ICC. 2012b. International green construction code® (IgCC®). International Code Council, Washington, D.C.
ISO. 2006. Thermal performance of buildings—Determination of air permeability of buildings—Fan pressurization method. Standard 9972-2006. International Organization for Standardization, Geneva.
Iwashita, G., K. Kimura., et al. 1989. Pilot study on addition of olf units for perceived air pollution sources. Proceedings of the SHASE Annual Meeting, pp. 3221-3324. Society of Heating, Air-Conditioning and Sanitary Engineers of Japan, Tokyo.
Jacobson, D.I., G.S. Dutt, and R.H. Socolow. 1986. Pressurization testing, infiltration reduction, and energy savings. In Measured air leakage of buildings, STP 904, p. 265. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Janssen, J.E. 1989. Ventilation for acceptable indoor air quality. ASHRAE Journal 31(10):40-48.
Janu, G.J., J.D. Wegner, and C.G. Nesler. 1995. Outdoor airflow control for VAV systems. ASHRAE Journal 37(4):62-68.
Johnson, T., and T. Long. 2005. Determining the frequency of open windows in residences: A pilot study in Durham, North Carolina during varying temperature conditions. Journal of Exposure Analysis and Environmental Epidemiology 15(4):329-349.
Judkoff, R., J.D. Balcomb, C.E. Handcock, G. Barker, and K. Subbarao. 1997. Side-by-side thermal tests of modular offices: A validation study of the STEM method. Report. National Renewable Energy Laboratory, Golden, CO.
Jump, D.A., I.S. Walker, and M.P. Modera. 1996. Field measurements of efficiency and duct retrofit effectiveness in residential forced air distribution systems. Proceedings of the 1996 ACEEE Summer Study, pp. 1.147-1.156. American Council for an Energy-Efficient Economy, Washington, D.C.
Kiel, D.E., and D.J. Wilson. 1986. Gravity driven airflows through open doors, 15.1. Proceedings of the 7th IEA Conference of the Air Infiltration and Ventilation Centre, Stratford-upon-Avon, U.K.
Kim, A.K., and C.Y. Shaw. 1986. Seasonal variation in airtightness of two detached houses. In Measured air leakage of buildings, STP 904, p. 17. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Klauss, A.K., R.H. Tull, L.M. Roots, and J.R. Pfafflin. 1970. History of the changing concepts in ventilation requirements. ASHRAE Journal 12(6):51-55.
Klote, J.H., J.A. Milke, P.G. Turnbull, A. Kashef, and M.J. Ferreira. 2012. Handbook of smoke control engineering. ASHRAE.
Kohonen, R., T. Ojanen, and M. Virtanen. 1987. Thermal coupling of leakage flows and heating load of buildings. Proceedings of the 8th IEA Air Infiltration and Ventilation Centre Conference, Überlingen, Germany, pp. 10.1-10.22.
Kreith, F., and R. Eisenstadt. 1957. Pressure drop and flow characteristics of short capillary tubes at low Reynolds numbers. ASME Transactions, pp. 1070-1078.
Kronvall, J. 1980. Correlating pressurization and infiltration rate data—Tests of an heuristic model. Lund Institute of Technology, Division of Building Technology, Lund, Sweden.
Kumar, R., A.D. Ireson, and H.W. Orr. 1979. An automated air infiltration measuring system using SF6 tracer gas in constant concentration and decay methods. ASHRAE Transactions 85(2):385. Paper DE-2553.
Kvisgaard, B., and P.F. Collet. 1990. The user’s influence on air change. In Air change rate and airtightness in buildings, STP 1067, pp. 67-76. M.H. Sherman, ed. American Society for Testing and Materials, West Conshohocken, PA.
Lagus, P.L. 1989. Tracer measurement instrumentation suitable for infiltration, air leakage, and airflow pattern characterization. Proceedings of the Conference on Building Systems—Room Air and Air Contaminant Distribution, pp. 97-102. ASHRAE.
Lagus, P., and A.K. Persily. 1985. A review of tracer-gas techniques for measuring airflows in buildings. ASHRAE Transactions 91(2B):1075. Paper HI-85-2-1.
Lecompte, J.G.N. 1987. The influence of natural convection in an insulated cavity on thermal performance of a wall. In Insulation materials, testing, and applications. American Society for Testing and Materials, West Conshohocken, PA.
Li, Y., and P. Heiselberg. 2003. Analysis methods for natural and hybrid ventilation—A critical literature review and recent developments. International Journal of Ventilation 1(4):3-20.
Liddament, M.W. 1988. The calculation of wind effect on ventilation. ASHRAE Transactions 94(2):1645-1660. Paper OT-88-13-1.
Liddament, M., and C. Allen. 1983. The validation and comparison of mathematical models of air infiltration. Technical Note 11. International Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Liu, M., and D.E. Claridge. 1992a. The measured energy impact of infiltration under dynamic conditions. Proceedings of the 8th Symposium on Improving Building Systems in Hot and Humid Climates, Dallas.
Liu, M., and D.E. Claridge. 1992b. The measured energy impact of infiltration in a test cell. Proceedings of the 8th Symposium on Improving Building Systems in Hot and Humid Climates, Dallas.
Liu, M., and D.E. Claridge. 1992c. The energy impact of combined solar radiation/infiltration/conduction effects in walls and attics. Proceedings of the Thermal Performance of Exterior Envelopes of Buildings, 5th ASHRAE/DOE/BTECC Conference, Clearwater Beach, FL.
Liu, M., and D.E. Claridge. 1995. Experimental methods for identifying infiltration heat recovery in building. Proceedings of the Thermal Performance of Exterior Envelopes of Buildings, 6th ASHRAE/DOE/BTECC Conference, Clearwater Beach, FL.
Lubliner, M., D.T. Stevens, and B. Davis. 1997. Mechanical ventilation in HUD-code manufactured housing in the Pacific Northwest. ASHRAE Transactions 103(1):693-705. Paper PH-97-08-2.
Marbek Resource Consultants. 1984. Air sealing homes for energy conservation. Energy, Mines and Resources Canada, Buildings Energy Technology Transfer Program, Ottawa, ON.
McDowell, T.P., S. Emmerich, J.W. Thornton, and G. Walton. 2003. Integration of airflow and energy simulation using CONTAM and TRNSYS. ASHRAE Transactions 109(2):757-770. Paper KC-03-10-2.
McWilliams, J., and M. Sherman. 2005. Review of literature related to residential ventilation requirements. Paper LBNL-57236. Lawrence Berkeley National Laboratory, Berkeley, CA.
Mendell, M.J. 1993. Non-specific symptoms in office workers: A review and summary of the epidemiologic literature. Indoor Air 3 (4):227-236.
Modera, M.P. 1989. Residential duct system leakage: Magnitude, impacts, and potential for reduction. ASHRAE Transactions 96(2):561-569. Paper VA-89-05-5.
Modera, M.P., and D.J. Wilson. 1990. The effects of wind on residential building leakage measurements. In Air change rate and airtightness in buildings, STP 1067, pp. 132-145. M.H. Sherman, ed. Lawrence Berkeley National Laboratory, Berkeley, CA. Report LBL-24195.
Modera, M.P., D. Dickerhoff, R. Jansky, and B. Smith. 1991. Improving the energy efficiency of residential air distribution systems in California. Report LBL-30866. Lawrence Berkeley National Laboratory, Berkeley, CA.
Mumma, S.A., and K.M. Shank. 2001. Achieving dry outside air in an energy efficient manner. ASHRAE Transactions 107(1):553-561. Paper AT-01-07-2.
Mumma, S.A., and Y.M. Wong. 1990. Analytical evaluation of outdoor airflow rate variation vs. supply airflow rate variation in VAV systems when the outside air damper position is fixed. ASHRAE Transactions 90(1):1197-1208.
Murphy, W.E., D.G. Colliver, and L.R. Piercy. 1991. Repeatability and reproducibility of fan pressurization devices in measuring building air leakage. ASHRAE Transactions 97(2):885-895. Paper IN-91-12-1.
Nelson, B.D., D.A. Robinson, and G.D. Nelson. 1985. Designing the envelope—Guidelines for buildings (SP-49). Proceedings of the ASHRAE/DOE/BTECC Conference—Thermal Performance of the Exterior Envelopes of Buildings III, Florida, pp. 1117-1122.
Ng, L.C., A. Musser, A.K. Persily, and S.J. Emmerich. 2012. Airflow and indoor air quality models of DOE reference commercial buildings. Technical Note 1734. National Institute of Standards and Technology, Gaithersburg, MD.
NRCC. 2010. National Building Code of Canada. National Research Council of Canada, Ottawa, ON.
Nylund, P.O. 1980. Infiltration and ventilation. Report D22:1980. Swedish Council for Building Research, Stockholm.
Offermann, F., and D. Int-Hout. 1989. Ventilation effectiveness measurements of three supply/return air configurations. Environment International 15(1-6):585-592.
Orme, M. 1999. Applicable models for air infiltration and ventilation calculations. Technical Note 51. International Energy Agency Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Ormerod, R. 1983. Nuclear shelters: A guide to design. Architectural Press, London.
Palmiter, L., and T. Bond. 1994. Modeled and measured infiltration II—A detailed case study of three homes. Report TR 102511. Electric Power Research Institute, Palo Alto, CA.
Palmiter, L., and I. Brown. 1989. The Northwest residential infiltration survey: Description and summary of results. Proceedings of the ASHRAE/DOE/BTECC/CIBSE Conference—Thermal Performance of the Exterior Envelopes of Buildings IV, Florida, pp. 445-457.
Palmiter, L., I.A. Brown, and T.C. Bond. 1991. Measured infiltration and ventilation in 472 all-electric homes. ASHRAE Transactions 97(2):979-987. Paper IN-91-15-3.
Parekh, A., K. Ruest, and M. Jacobs. 1991. Comparison of airtightness, indoor air quality and power consumption before and after air-sealing of high-rise residential buildings. Proceedings of the 12th IEA Conference of the Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Parker, G.B., M. McSorley, and J. Harris. 1990. The Northwest residential infiltration survey: A field study of ventilation in new houses in the Pacific Northwest. In Air change rate and airtightness in buildings, STP 1067, pp. 93-103. M.H. Sherman, ed. American Society for Testing and Materials, West Conshohocken, PA.
Persily, A. 1982. Repeatability and accuracy of pressurization testing. Proceedings of the ASHRAE/DOE Conference, Thermal Performance of the Exterior Envelopes of Buildings II, Las Vegas.
Persily, A.K. 1986. Measurements of air infiltration and airtightness in passive solar homes. In Measured air leakage of buildings, STP 904, p. 46. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Persily, A.K. 1988. Tracer gas techniques for studying building air exchange. Report NBSIR 88-3708. National Institute of Standards and Technology, Gaithersburg, MD.
Persily, A.K. 1991. Design guidelines for thermal envelope integrity in office buildings. Proceedings of the 12th IEA Conference of the Air Infiltration and Ventilation Centre, Ottawa, ON.
Persily, A.K. 2004. Building ventilation and pressurization as a security tool. ASHRAE Journal 46 (9):18-24.
Persily, A.K., and J. Axley. 1990. Measuring airflow rates with pulse tracer techniques. In Air change rate and airtightness in buildings, pp. 31-51. STP 1067. M.H. Sherman, ed. American Society for Testing and Materials, West Conshohocken, PA.
Persily, A.K., and R.A. Grot. 1985a. The airtightness of office building envelopes. Proceedings of the ASHRAE/DOE/BTECC Conference on the Thermal Performance of the Exterior Envelopes of Buildings III, Clearwater Beach, FL, p. 125.
Persily, A.K., and R.A. Grot. 1985b. Accuracy in pressurization data analysis. ASHRAE Transactions 91(2B):105. Paper HI-85-03-2.
Persily, A.K., and R.A. Grot. 1986. Pressurization testing of federal buildings. In Measured air leakage of buildings, STP 904, p. 184. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Persily, A.K., and G.T. Linteris. 1983. A comparison of measured and predicted infiltration rates. ASHRAE Transactions 89(2):183. Paper DC-83-04-1.
Persily, A.K., J. Gorfain, and G. Brunner. 2005. Ventilation design and performance in U.S. office buildings. ASHRAE Journal 47(4):30-35.
Persily, A.K., R.E. Chapman, S. Emmerich, W.S. Dols, H. Davis, P. Lavappa, and A. Rushing. 2007. Building retrofits for increased protection against airborne chemical and biological releases. NISTIR Report 7379. National Institute of Standards and Technology, Gaithersburg, MD.
Persily, A.K., A. Musser, and S. Emmerich. 2010. Modeled infiltration rate distributions for U.S. housing. Indoor Air 20(6):473-485.
Powell, F., M. Krarti, and A. Tuluca. 1989. Air movement influence on the effective thermal resistance of porous insulations: A literature survey. Journal of Thermal Insulation 12:239-251.
Price, P.N., and M.H. Sherman. 2006. Ventilation behavior and household characteristics in new California houses. Report LBNL-59620.
RDH. 2013. Air leakage control in multi-unit residential buildings. Canada Mortgage and Housing Corporation.
Reardon, J.T., and C.-Y. Shaw. 1997. Evaluation of five simple ventilation strategies suitable for houses without forced-air heating. ASHRAE Transactions 103(1):731-744. Paper PH-97-08-5.
Reeves, G., M.F. McBride, and C.F. Sepsy. 1979. Air infiltration model for residences. ASHRAE Transactions 85(1):667. Paper PH-79-07A-1.
Riley, M. 1990. Indoor air quality and energy conservation: The R-2000 home program experience. Proceedings of Indoor Air ’90: International Conference on Indoor Air Quality and Climate, Ottawa, vol. 5, p. 143.
Robison, P.E., and L.A. Lambert. 1989. Field investigation of residential infiltration and heating duct leakage. ASHRAE Transactions 95(2):542-550. Paper VA-89-05-3.
Rock, B.A. 1992. Characterization of transient pollutant transport, dilution, and removal for the study of indoor air quality. Ph.D. dissertation, University of Colorado at Boulder. University Microfilms International.
Rock, B.A. 2005. A user-friendly model and coefficients for slab-on-grade load and energy calculations. ASHRAE Transactions 111(2):122-136. Paper 4795.
Rock, B.A. 2006. Ventilation for environmental tobacco smoke. Elsevier Science, New York, and ASHRAE.
Rock, B.A., and D. Zhu. 2002. Designer’s guide to ceiling-based air diffusion. ASHRAE.
Rock, B.A., M.J. Brandemuehl, and R. Anderson. 1995. Toward a simplified design method for determining the air change effectiveness. ASHRAE Transactions 101(1):217-227. Paper 3852.
Rudd, A.F. 1998. Design/sizing methodology and economic evaluation of central-fan-integrated supply ventilation systems. ACEEE 1998 Summer Study on Energy Efficiency in Buildings. 23-28 August, Pacific Grove, CA. American Council for an Energy Efficient Economy, Washington, D.C.
Russell, M., M. Sherman, and A. Rudd. 2005. Review of residential ventilation technologies. Paper LBNL-576. Lawrence Berkeley National Laboratory, Berkeley, CA.
Sandberg, M.H. 1981. What is ventilation efficiency? Building and Environment 16:123-135.
Seppanen, O.A., W.J. Fisk and M.J. Mendell. 1999. Association of ventilation rates and CO2 concentrations with health and other responses in commercial and institutional buildings. Indoor Air 9(4):226-252.
Shaw, C.Y. 1981. A correlation between air infiltration and air tightness for a house in a developed residential area. ASHRAE Transactions 87(2):333. Paper CI-2655.
Shaw, C.Y., and W.C. Brown. 1982. Effect of a gas furnace chimney on the air leakage characteristic of a two-story detached house. Proceedings of the 3rd IEA Conference of the Air Infiltration Centre, London.
Sherman, M.H. 1986. Infiltration degree-days: A statistic for quantifying infiltration-related climate. ASHRAE Transactions 92(2):161-181. Paper 2986.
Sherman, M.H. 1987. Estimation of infiltration from leakage and climate indications. Energy and Buildings 10(1):81.
Sherman, M.H. 1989a. Uncertainty in airflow calculations using tracer gas measurements. Building and Environment 24(4):347-354.
Sherman, M.H. 1989b. On the estimation of multizone ventilation rates from tracer gas measurements. Building and Environment 24(4):355-362.
Sherman, M.H. 1990. Tracer gas techniques for measuring ventilation in a single zone. Building and Environment 25(4):365-374.
Sherman, M.H. 1991. Single-zone stack-dominated infiltration modeling. Proceedings of the 12th IEA Conference of the Air Infiltration and Ventilation Centre, Ottawa, ON, pp. 297-314.
Sherman, M.H. 1992a. A power law formulation of laminar flow in short pipes. Journal of Fluids Engineering 114:601-605. Report LBL-29414, Lawrence Berkeley National Laboratory, Berkeley, CA.
Sherman, M.H. 1992b. Superposition in infiltration modeling. Indoor Air 2:101-114.
Sherman, M.H., and D. Dickerhoff. 1989. Description of the LBL multitracer measurement system. Proceedings of the ASHRAE/DOE/BTECC/CIBSE Conference—Thermal Performance of the Exterior Envelopes of Buildings IV, pp. 417-432.
Sherman, M.H., and D.J. Dickerhoff. 1998. Airtightness of U.S. dwellings. ASHRAE Transactions 104(2):1359-1367. Paper TO-98-25-1.
Sherman, M.H., and D.T. Grimsrud. 1980. Infiltration-pressurization correlation: Simplified physical modeling. ASHRAE Transactions 86(2):778. Paper DV-80-09-3.
Sherman, M.H., and N. Matson. 1997. Residential ventilation and energy characteristics. ASHRAE Transactions 103(1):717-730. Paper PH-97-08-4.
Sherman, M.H., and M.P. Modera. 1986. Comparison of measured and predicted infiltration using the LBL infiltration model. In Measured air leakage of buildings, STP 904, p. 325. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Sherman, M.H., and D.J. Wilson. 1986. Relating actual and effective ventilation in determining indoor air quality. Building and Environment 21(3/4):135.
Sherman, M.H., D.T. Grimsrud, P.E. Condon, and B.V. Smith. 1980. Air infiltration measurement techniques. Proceedings of the 1st IEA Conference of the Air Infiltration Centre, London. Report LBL-10705. Lawrence Berkeley National Laboratory, Berkeley, CA.
Sibbitt, B.E., and T. Hamlin. 1991. Meeting Canadian residential ventilation standard requirements with low-cost systems. Canada Mortgage and Housing Corporation, Ottawa, ON.
Sinden, F.W. 1978a. Wind, temperature and natural ventilation—Theoretical considerations. Energy and Buildings 1(3):275.
Sinden, F.W. 1978b. Multi-chamber theory of air infiltration. Building and Environment 13:21-28.
Sorensen, J.H., and B.M. Vogt. 2001. Will duct tape and plastic really work? Issues related to expedient sheltering-in-place. Report ORNL/TM-2001/154. Oak Ridge National Laboratory, Oak Ridge, TN.
Sundell, J., H. Levin, W.W. Nazaroff, W.S. Cain, W.J. Fisk, D.T. Grimsrud, and F. Gyntelberg. 2011. Ventilation rates and health: Multidisciplinary review of the scientific literature. Indoor Air 21(3):191-204.
Tamura, G.T., and C.Y. Shaw. 1976a. Studies on exterior wall air tightness and air infiltration of tall buildings. ASHRAE Transactions 82(1):122. Paper DA-2388.
Tamura, G.T., and C.Y. Shaw. 1976b. Air leakage data for the design of elevator and stair shaft pressurization system. ASHRAE Transactions 82(2):179. Paper SE-2413.
Tamura, G.T., and A.G. Wilson. 1966. Pressure differences for a nine-story building as a result of chimney effect and ventilation system operation. ASHRAE Transactions 72(1):180.
Tamura, G.T., and A.G. Wilson. 1967a. Pressure differences caused by chimney effect in three high buildings. ASHRAE Transactions 73(2):II.1.1.
Tamura, G.T., and A.G. Wilson. 1967b. Building pressures caused by chimney action and mechanical ventilation. ASHRAE Transactions 73(2):II.2.1.
Timusk, J., A.L. Seskus, and K. Linger. 1992. A systems approach to extend the limit of envelope performance. Proceedings of the 6th ASHRAE/DOE/BTECC Conference—Thermal Performance of Exterior Envelopes of Buildings, Clearwater Beach, FL.
Turk, B.T., D.T. Grimsrud, J.T. Brown, K.L. Geisling-Sobotka, J. Harrison, and R.J. Prill. 1989. Commercial building ventilation rates and particle concentrations. ASHRAE Transactions 95(1):422-433. Paper 3248.
USACE. 2009. U.S. Army Corps of Engineers air leakage test protocol for building envelopes. Air Barrier Association of America, Walpole, MA, and U.S. Army Corps of Engineers.
Verschoor, J.D., and J.O. Collins. 1986. Demonstration of air leakage reduction program in navy family housing. In Measured air leakage of buildings, STP 904, p. 294. H.R. Trechsel and P.L. Lagus, eds. American Society for Testing and Materials, West Conshohocken, PA.
Walker, I.S. 1999. Distribution system leakage impacts on apartment building ventilation rates. ASHRAE Transactions 105(1):943-950. Paper CH-99-14-2.
Walker, I.S., and T.W. Forest. 1995. Field measurements of ventilation rates in attics. Building and Environment 30(3):333-347.
Walker, I.S., and D.J. Wilson. 1993. Evaluating models for superposition of wind and stack effects in air infiltration. Building and Environment 28(2):201-210.
Walker, I.S., and D.J. Wilson. 1994. Practical methods for improving estimates of natural ventilation rates. Proceedings of the 15th IEA Conference of the Air Infiltration and Ventilation Centre, Buxton, U.K., pp. 517-526.
Walker, I.S., and D.J. Wilson. 1998. Field validation of algebraic equations for stack and wind driven air infiltration calculations. International Journal of HVAC&R Research (now Science and Technology for the Built Environment) 4(2):119-140.
Walker, I.S., D.J. Wilson., and M.H. Sherman. 1997. A comparison of the power law to quadratic formulations for air infiltration calculations. Energy and Buildings 27(3).
Walker, I., M. Sherman, J. Siegel, D. Wang, C. Buchanan, and M. Modera. 1999. Leakage diagnostics, sealant longevity, sizing and technology transfer in residential thermal distribution systems: Part II. Report LBNL-42691.
Walton, G.N. 1984. A computer algorithm for predicting infiltration and interroom airflows. ASHRAE Transactions 90(1B):601. Paper AT-84-11-3.
Walton, G.N. 1989. Airflow network models for element-based building airflow modeling. ASHRAE Transactions 95(2):611-620. Paper VA-89-06-5.
Walton, G., and W.S. Dols. 2003. CONTAM 2.1 supplemental user guide and program documentation. NISTIR Report 7049, National Institute of Standards and Technology, Gaithersburg, MD.
Warden, D. 1995. Outdoor air: Calculation and delivery. ASHRAE Journal 37(6):54-63.
Warren, P.R., and B.C. Webb. 1980. The relationship between tracer gas and pressurization techniques in dwellings. Proceedings of the 1st IEA Conference of the Air Infiltration Centre, London.
Warren, P.R., and B.C. Webb. 1986. Ventilation measurements in housing. CIBSE Symposium, Natural Ventilation by Design. Chartered Institution of Building Services Engineers, London.
Weidt, J.L., J. Weidt, and S. Selkowitz. 1979. Field air leakage of newly installed residential windows. Proceedings of the ASHRAE/DOE Conference—Thermal Performance of the Exterior Envelopes of Buildings Orlando, FL, p. 149.
Weschler, C.J. 2000. Ozone in indoor environments: Concentration and chemistry. Indoor Air 10:269-288.
Wilson, D.J., and I.S. Walker. 1991. Wind shelter effects on air infiltration for a row of houses. Proceedings of the 12th IEA Conference of the Air Infiltration and Ventilation Centre, Ottawa, ON, pp. 335-346.
Wilson, D.J., and I.S. Walker. 1992. Feasibility of passive ventilation by constant area vents to maintain indoor air quality in houses. Proceedings of Indoor Air Quality ’92, ASHRAE/ACGIH/AIHA Conference, San Francisco.
Wilson, D.J., and I.S. Walker. 1993. Infiltration data from the Alberta Home Heating Research Facility. Technical Note 41. Air Infiltration and Ventilation Centre, Sint-Stevens-Woluwe, Belgium.
Wiren, B.G. 1984. Wind pressure distributions and ventilation losses for a single-family house as influenced by surrounding buildings—A wind tunnel study. Proceedings of the Air Infiltration Centre Wind Pressure Workshop, Brussels, pp. 75-101.
Wolf, S. 1966. A theory of the effects of convective air flow through fibrous thermal insulation. ASHRAE Transactions 72(1):III 2.1-III 2.9.
Yaglou, C.P., and W.N. Witheridge. 1937. Ventilation requirements. ASHVE Transactions 43:423.
Yaglou, C.P., E.C. Riley, and D.I. Coggins. 1936. Ventilation requirements. ASHVE Transactions 42:133.
Yuill, G.K. 1986. The variation of the effective natural ventilation rate with weather conditions. Proceedings of the Solar Energy Society of Canada Renewable Energy Conference ’86, pp. 70-75.
Yuill, G.K. 1991. The development of a method of determining air change rates in detached dwellings for assessing indoor air quality. ASHRAE Transactions 97(2):896-903. Paper IN-91-12-2.
Yuill, G.K. 1996. Impact of high use automatic doors on infiltration. ASHRAE Research Project RP-763, Final Report.
Yuill, G.K., and G.M. Comeau. 1989. Investigation of the indoor air quality, air tightness and air infiltration rates of a random sample of 78 houses in Winnipeg. Proceedings of IAQ ’89, The Human Equation—Health and Comfort, pp. 122-127. ASHRAE.
Yuill, G.K., M.R. Jeanson, and C.P. Wray. 1991. Simulated performance of demand-controlled ventilation systems using carbon dioxide as an occupancy indicator. ASHRAE Transactions 97(2):963-968. Paper IN-91-15-1.
Yuill, D.P., G.K. Yuill, and A.H. Coward. 2008. Measurement and analysis of vitiation of secondary air in air distribution systems (RP-1276). HVAC&R Research (now Science and Technology for the Built Environment) 14(3):345-357.
Yuill, D.P., G.K. Yuill, and A.H. Coward. 2012. Experimental validation of the multiple-zone system ventilation efficiency equation of ANSI/ASHRAE Standard 62.1 (RP-1276). HVAC&R Research (now Science and Technology for the Built Environment) 18(3).
Zhivov, A. 2013. Air tightness in new and retrofitted US army buildings. Air Barrier Association of America, Walpole, MA.