A control device is the component of a control loop used to vary the input (controlled variable). Both valves and dampers perform essentially the same function and must be properly sized and selected for the particular application. The control link to the valve or damper is called an actuator or operator, and uses electricity, compressed air, hydraulic fluid, or some other means to power the motion of the valve stem or damper linkage through its operating range. For additional information, see Chapter 36.
An automatic valve is designed to control the flow of steam, water, gas, or other fluids. It can be considered a variable orifice positioned by an actuator in response to impulses or signals from the controller. It may be equipped with a throttling plug, V-port, or rotating ball specially designed to provide a desired flow characteristic.
Types of automatic valves include the following:
A three-way mixing valve (Figure 8A) has two inlet connections and one outlet connection and a double-faced disk operating between two seats. It is used to mix two fluids entering through the two inlet connections and leaving through the common outlet, according to the position of the valve stem and disk.
A three-way diverting valve (Figure 8B) has one inlet connection and two outlet connections, and two separate disks and seats. It is used to divert flow to either of the outlets or to proportion the flow to both outlets. Three-way diverting valves are more expensive and have more complex applications, and generally are not used in typical HVAC systems.
A two-way globe valve may be either single or double seated. A single-seated valve (Figure 9A) is designed for tight shutoff. Appropriate disk materials for various pressures and media are used. A double-seated or balanced valve (Figure 9B) is designed so that the media pressure acting against the valve disk is essentially balanced, reducing the actuator force required. It is widely used where fluid pressure is too high to allow a single-seated valve to close or to modulate properly. It is not usually used where tight shutoff is required.
A butterfly valve consists of a heavy ring enclosing a disk that rotates on an axis at or near its center and is similar to a round single-blade damper. In principle, the disk seats against a ring machined within the body or a resilient liner in the body. Two butterfly valves can be used together to act like a three-way valve for mixing or diverting. In this arrangement, one valve is set up as normally open and the other is normally closed. In applications with pipe sizes 4 in. and above, butterfly valves are either two position or modulating, and they are less expensive than globe-style valves (see Chapter 47 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment for information on globe valves).
A ball valve consists of a ball with a hole drilled through it, rotating in a valve body. Ball valves are increasingly popular because of their low cost and high close-off ratings. Features that provide flow characteristics similar to or better than globe valves are available.
Pressure-independent valves are control valves with integral pressure regulators. This allows the valve to maintain a constant flow at a given shaft position because the integral pressure regulator maintains a constant differential pressure across the valve’s orifice, regardless of system pressure fluctuations.
Flow Characteristics. Valve performance is expressed in terms of its flow characteristics as it operates through its stroke, based on a constant pressure drop. Three common characteristics are shown in Figure 10 and are defined as follows:
-
Quick opening. Maximum flow is approached rapidly as the device begins to open.
-
Linear. Opening and flow are related in direct proportion.
-
Equal percentage. Each equal increment of opening increases flow by an equal percentage over the previous value.
On a pressure-dependent valve, because pressure drop across the valve’s orifice seldom remains constant as its opening changes, actual performance usually deviates from the published characteristic curve. The magnitude of deviation is determined by the overall design. For example, in a system arranged so that control valves or dampers can shut off all flow, pressure drop across a controlled device increases from a minimum at design conditions to total pressure drop at no flow. Figure 11 shows the extent of resulting deviations for a valve or damper designed with a linear characteristic, when selection is based on various percentages of total system pressure drop. To allow for adequate control by the valve, design pressure drop should be a reasonably large percentage of total system pressure drop at the valve (i.e., adequate valve authority) and the system should be designed and controlled so that pressure drop remains relatively constant. Hydronic piping circuits and valve authority are discussed in Chapters 13 and 47 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment, respectively.
Selection and Sizing. Higher pressure drops for control devices are obtained by using smaller sizes, with a possible increase in size of other equipment in the system. Sizing control valves is discussed in Chapter 47 of the 2020 ASHRAE Handbook—HVAC Systems and Equipment.
Steam Valves. Steam-to-water and steam-to-air heat exchangers are typically controlled by regulating steam flow using a two-way throttling valve. One-pipe steam systems require a line-size, two-position valve for proper condensate drainage and steam flow; two-pipe steam systems can be controlled by two-position or modulating (throttling) valves. Maximum pressure drop for steam valves is a function of operating pressure and cannot be exceeded.
Water Valves. Valves for water service may be two- or three-way and two-position or proportional. Proportional valves are used most often, but two-position valves are not unusual and are sometimes essential. Variable-flow systems are designed to keep the pressure differential constant from supply to return. For valve selection, it is safer to assume that the pressure drop across the valve increases as it modulates from fully open to fully closed.
Equal-percentage valves provide better control at part load, particularly in hot-water coils because the coil’s heat output is not linearly related to flow. As flow reduces, more heat is transferred with each unit of water, counteracting the reduction in flow. Equal-percentage valves can provide linear heat transfer from the coil with respect to the control signal.
Actuators. Valve actuators include the following general types:
-
A pneumatic valve actuator consists of a spring-opposed, flexible diaphragm or bellows attached to the valve stem. An increase in air pressure above the minimum point of the spring range compresses the spring and simultaneously moves the valve stem. Springs of various pressure ranges can sequence the operation of two or more devices, if properly selected or adjusted. For example, a chilled-water valve actuator may modulate the valve from fully closed to fully open over a spring range of 9 to 13 psig, whereas a sequenced steam valve may actuate from 3 to 8 psig.
Two-position pneumatic control is accomplished using a two-position pneumatic relay to apply either full air pressure or no pressure to the valve actuator. Pneumatic valves and valves with spring-return electric actuators can be classified as normally open or normally closed.
A normally open valve assumes an open position, providing full flow, when all actuating force is removed.
A normally closed valve assumes a closed position, stopping flow, when all actuating force is removed.
-
Double-acting or springless pneumatic valve actuators, which use two opposed diaphragms or two sides of a single diaphragm, are generally limited to special applications involving large valves or high fluid pressure.
-
An electric-hydraulic valve actuator is similar to a pneumatic one, except that it uses an incompressible fluid circulated by an internal electric pump.
-
A thermostatic valve actuator uses the volume change with temperature of a substance in a sealed chamber to move a diaphragm, which in turn moves the valve shaft. These actuators can be used as two-position or modulating. In wax thermostatic valves, the volume change is caused by phase change (the wax melts or solidifies). The heat source is usually the environment or the fluid whose temperature is being controlled, but can also be a resistive element in the chamber receiving voltage from a controller.
-
A solenoid consists of a magnetic coil operating a movable plunger. Most are for two-position operation, but modulating solenoid valves are available with a pressure equalization bellows or piston to achieve modulation. Solenoid valves are generally limited to relatively small sizes (up to 4 in.).
-
An electric actuator operates the valve stem through a gear train and linkage. Electric motor actuators are classified in the following three types:
| - Spring-return, for two-position operation (energy drives the valve to one position and a spring returns the valve to its normal position) or for modulating operation (energy drives the valve to a variable position and a spring returns the valve to an open or closed position upon a signal or power failure). With spring-return electric actuators, on loss of actuator power, the spring positions the valve to its fail-safe (normal) position (either fully open or fully closed). |
| - Electronic fail-safe, which uses a capacitor instead of a spring to drive the actuator to its fail-safe (normal) position. The fail-safe position can be set for fully open, fully closed, or anywhere in between at varying increments. |
| - Reversible, for floating and proportional operation. The motor can run in either direction and can stop in any position. It is sometimes equipped with a return spring or an electronic fail-safe. In proportional-control applications, an integral feedback potentiometer for rebalancing the control circuit is also driven by the motor. |
Automatic dampers are used in air conditioning and ventilation to control airflow. They may be used (1) in a modulating application to maintain a controlled variable, such as mixed air temperature or supply air duct static pressure; or (2) for two-position control to initiate operation, such as opening minimum outdoor air dampers when a fan is started.
Multiblade dampers are typically available in two arrangements: parallel-blade and opposed-blade (Figure 12), although combinations of the two are manufactured. They are used to control flow through large openings typical of those in air handlers. Both types are adequate for two-position control.
When dampers are applied in modulating control loops, a nonlinear relationship between flow and stroke can lead to difficulties in tuning a control loop for performance. Nonlinearity is expressed as variation in the slope of the flow versus stroke curve. Perfect linearity is not required: if slope varies throughout the range of required flow by less than a factor of 2 from the slope at the point where the loop is tuned, nonlinearity is not likely to disrupt performance.
Parallel blades are used for modulating control when the design condition pressure drop of the damper is about 25% or more of the pressure in a subsystem (Figure 13A). Opposed-blade dampers are preferable for modulating control when the damper is about 15% or less of the pressure drop in a subsystem (Figure 13B). A subsystem is defined as a portion of the duct system between two relatively constant pressure points (e.g., the return air section between the mixed air and return plenum tee). A combination may be considered between 15 and 25% damper drop. Single-blade dampers are typically used for flow control in small terminal units.
In Figure 13, A is authority, which is the ratio of pressure drop across the fully open damper at design flow to total subsystem pressure drop, including fully open control damper pressure drop. The curves here are typical for ducted applications. The Air Movement and Control Association (AMCA Standard 500) defined a number of geometric arrangements of dampers for testing pressure losses. The curves in Figure 13 are those of an AMCA 5.3 geometry, which is a fully ducted arrangement with long sections of duct before and after a damper. Other geometric applications, such as plenum or wall-mounted dampers, exhibit different response curves (Felker and Felker 2009; van Becelaere et al. 2004).
Figure 14 shows two parallel-blade (PB) applications, two opposed-blade (OB) applications, and an “anti-PB” (aPB) arrangement. The response curves are not like those of the AMCA 5.3 ducted application. These are “inherent” curves, where pressure drop across a damper is held constant as the damper rotates (so it has 100% authority). In real applications, the authority is lower (higher losses of other system components besides the damper). As system pressure losses increase, the curves move up. Note that PB dampers are significantly above linear in most cases.
Figure 15 shows three more applications with PB and OB dampers. The ducted damper has some disturbance and pressure loss ahead of it, to simulate a more realistic situation than those of AMCA 5.3. Nevertheless, the response curves are similar to AMCA 5.3. The plenum entry dampers show irregular results. Again, these are inherent curves, and lower authority causes the curves to move up toward more flow at smaller angles.
The curves shown here are typical, but do not represent every scenario. Thousands of installation variations exist, and slight variations in response always occur. For additional application examples and greater detail, see ASHRAE research project RP-1157 (van Becelaere et al. 2004).
Application. Dampers require engineering to achieve defined goals. A common application is a flow control damper, which modulates airflow. The curves in Figure 13 can be used to pick a damper with a pressure drop and authority that provides near-linear response. Another common application is economizer outdoor air, return air, and exhaust air dampers. Selection of these dampers depends on the system design, as discussed in ASHRAE Guideline 16-2014.
Damper leakage is a concern, particularly where tight shutoff is necessary to significantly reduce energy consumption. Also, outdoor air dampers in cold climates must close tightly to prevent coils and pipes from freezing. Low-leakage dampers cost more and require larger actuators because of friction of the seals in the closed position; however, the energy savings offset the extra cost.
Actuators. Either electricity or compressed air is used to actuate dampers.
Pneumatic damper actuators are similar to pneumatic valve actuators, except that they have a longer stroke or the stroke is increased by a multiplying lever. Increasing air pressure produces a linear shaft motion, which, through a linkage, moves the crank arm to open or close the dampers. Releasing air pressure allows a spring to return the actuator. Double-acting actuators without springs are available also.
Electric damper actuators can be proportional or two-position. They can be spring return or nonspring. The simplest form of control is a floating three-point controller, in which contact closures drive the motor clockwise or counterclockwise. In addition, a variety of standard electronic signals from electronic controllers or DDC systems, such as 4 to 20 mA, 2 to 10 V (dc), or 0 to 10 V (dc), can be used to control proportionally actuated dampers.
Most modern actuators are electronic and use more sophisticated methods of control and operation. They are inherently positive positioning and may have communications capabilities similar to industrial-process-quality actuators.
A two-position spring-return actuator moves in one direction when power is applied to its internal windings. When no power is present, the actuator returns (via spring force) to its fail-safe (normal) position. Depending on how the actuator is connected, this action opens or closes the dampers. A proportional actuator may also have spring-return action.
Mounting. Damper actuators are mounted in different ways, depending on the size and accessibility of the damper, and the power required to move the damper. The most common method of mounting electric actuators is directly over the damper shaft (direct coupling) with no external linkage. Actuators can also be mounted in the airflow on the damper frame and be linked directly to a damper blade (though this may deform blades and make access for repairs difficult), or mounted outside the duct and connected to a crank arm attached to a shaft extension of one of the blades. Mounting methods that link the actuator to a single blade are not recommended because of the potential to bend the single drive blade or to have the blade-to-blade linkages get out of adjustment.
Large dampers may require two or more actuators, which are usually mounted at separate points on the damper. An alternative is to install the damper in two or more sections, each section being controlled by a single damper actuator. Positive positioners may be required for proper sequencing, as with a small damper controlled to maintain healthy indoor air quality, with a large damper being independently controlled for economy-cycle free cooling.
Pneumatic Positive (Pilot) Positioners
Where accurate positioning of a modulating pneumatic damper or valve is required, use positive positioners. A positive positioner provides up to full supply control air pressure to the actuator for any change in position required by the controller. A pneumatic actuatorwithout a positioner may not respond quickly or accurately enough to small changes in control pressure caused by friction in the actuator or load, or to changing load conditions such as wind acting on a damper blade. A positive positioner provides finite and repeatable positioning change and allows adjustment of the control range (spring range of the actuator) to provide a proper sequencing control of two or more control devices.
2.2 SENSORS AND TRANSMITTERS
A sensor responds to a change in the controlled variable. The response, which is a change in some physical or electrical property of the primary sensing element, is available for translation or amplification into a mechanical or electrical signal. This signal is sent to the controller.
Transmitters take the output of a sensor and convert the sensor’s signal to an industry-standard signal type (e.g., 4 to 20 mA, 0 to 10 V, network protocol).
Chapter 47 of the 2019 ASHRAE Handbook—HVAC Applications and manufacturer’s catalogs and tutorials include information on specific applications. In selecting a sensor for a specific application, consider the following:
-
Operating range of controlled variable. The sensor must be capable of providing an adequate change in its output signal over the expected input range.
-
Compatibility of controller input. Electronic and digital controllers accept various ranges and types of electronic signals. The sensor’s signal must be compatible with the controller. If the controller’s input requirements are unknown, it may be possible to use a transducer to convert the sensor signal to an industry-standard signal, such as 4 to 20 mA or 0 to 10 V (DC).
-
Accuracy, sensitivity, and repeatability. For some control applications, the controlled variable must be maintained within a narrow band around a desired set point. Both the accuracy and sensitivity of the sensor selected must reflect this requirement. Sensitivity is the ratio of a change in output magnitude to the change of input that causes it, after steady state has been reached. Repeatability is closeness of agreement among repeated measurements of the same variable under the same conditions. However, even an accurate sensor cannot maintain the set point if (1) the controller is unable to resolve the input signal, (2) the controlled device cannot be positioned accurately, (3) the controlled device exhibits excessive hysteresis, or (4) disturbances drive its system faster than the controls can regulate it. See ASHRAE Guideline 13, clause 7.9, for a discussion on end-to-end accuracy.
-
Sensor response time. Associated with a sensor/transducer arrangement is a response curve, which describes the response of the sensor output to change in the controlled variable. If the time constant of the process being controlled is short and stable and accurate control is important, then the sensor selected must have a fast response time.
-
Control agent properties and characteristics. The control agent is the medium to which the sensor is exposed, or with which it comes in contact, for measuring a controlled variable such as temperature or pressure. If the agent corrodes the sensor or otherwise degrades its performance, a different sensor should be selected, or the sensor must be isolated or protected from direct contact with the control agent.
-
Ambient environment characteristics. Even when the sensor’s components are isolated from direct contact with the control agent, the ambient environment must be considered. The temperature and humidity range of the ambient environment must not reduce the sensor’s accuracy. Likewise, the presence of certain gases, chemicals, and electromagnetic interference (EMI) can cause performance degradation. In such cases, a special sensor or transducer housing can be used to protect it. Special housings may also be required in wet, flammable, explosive, or corrosive environments.
-
Placement requirements. The sensing element must be in the correct point(s) required for proper measurement. For instance, pipe wall thickness (schedule) affects the required length of water temperature or flow probes; sensors inside air ducts (especially low-temperature switches) should be long enough to compensate for air stratification; room temperature and humidity sensors should not be installed close to heat sources, on outer walls, in direct airstreams, or in areas where air stalls (e.g., behind furniture); single measurements of return air properties, no matter how accurate, are just averages and do not detect areas with simultaneous opposite extremes.
Temperature-sensing elements generally detect changes in either (1) relative dimension (caused by differences in thermal expansion), (2) the state of a vapor or liquid, or (3) some electrical property. Within each category, there are various sensing elements to measure room, duct, water, and surface temperatures. Temperature-sensing technologies commonly used in HVAC applications are as follows:
-
A bimetal element is composed of two thin strips of dissimilar metals fused together. Because the two metals have different coefficients of thermal expansion, the element bends and changes position as the temperature varies. Depending on the space available and the movement required, it may be straight, U-shaped, or wound into a spiral. This element is commonly used in room, insertion, and immersion thermostats.
-
A rod-and-tube element consists of a high-expansion metal tube containing a low-expansion rod. One end of the rod is attached to the rear of the tube. The tube changes length with changes in temperature, causing the free end of the rod to move. This element is commonly used in certain insertion and immersion thermostats.
-
A sealed bellows element is either vapor, gas, or liquid filled. Temperature changes vary the pressure and volume of the gas or liquid, resulting in a change in force or a movement.
-
A remote bulb element is a bulb or capsule connected to a sealed bellows or diaphragm by a capillary tube; the entire system is filled with vapor, gas, or liquid. Temperature changes at the bulb cause volume or pressure changes that are conveyed to the bellows or diaphragm through the capillary tube. This element is useful where the temperature-measuring point is remote from the desired thermostat location.
-
A thermistor is a semiconductor that changes electrical resistance with temperature. It has a negative temperature coefficient (i.e., resistance decreases as temperature increases). Its characteristic curve of temperature versus resistance is nonlinear over a wide range. Several techniques are used to convert its response to a linear change over a particular temperature range. With digital control, one technique is to store a computer look-up table that maps the temperature corresponding to the measured resistance. The table breaks the curve into small segments, and each segment is assumed to be linear over its range. Thermistors are used because of their relatively low cost, the large change in resistance possible for a small change in temperature, and their long-term stability.
-
A resistance temperature device (RTD) also changes resistance with temperature. Most metallic materials increase in resistance with increasing temperature; over limited ranges, this variation is linear for certain metals (e.g., platinum, copper, tungsten, nickel/iron alloys). Platinum, for example, is linear within ±0.3% from 0 to 300°F. The RTD sensing element is available in several forms for surface or immersion mounting. Flat grid windings are used for measurements of surface temperatures. For direct measurement of fluid temperatures, the windings are encased in a stainless steel bulb to protect them from corrosion.
Humidity Sensors and Transmitters
Humidity sensors, or hygrometers, measure relative humidity, dew point, or absolute humidity of ambient or moving air. Transmitters convert the signal from the humidity sensor to an industry-standard output such as 0 to 10 V or 4 to 20 mA. Some transmitters compensate for temperature variations. Two types of sensors that detect relative humidity are mechanical hygrometers and electronic hygrometers.
Electronic hygrometers can use either resistance or capacitance sensing elements. The resistance element is a conductive grid coated with a hygroscopic substance. The grid’s conductivity varies with the water retained; thus, resistance varies with relative humidity. The conductive element is arranged in an AC-excited Wheatstone bridge and responds rapidly to humidity changes.
The capacitance element is a stretched membrane of nonconductive film, coated on both sides with metal electrodes and mounted in a perforated plastic capsule. The response of the sensor’s capacity to rising relative humidity is nonlinear. The signal is linearized and temperature is compensated in the amplifier circuit to provide an output signal as relative humidity changes from 0 to 100%.
The chilled-mirror humidity sensor determines dew point rather than relative humidity. Air flows across a small mirror in the sensor. A thermoelectric cooler lowers the surface temperature of the mirror until it reaches the dew point of the air. Condensation on the surface reduces the amount of light reflected from the mirror compared to a reference light level.
Dispersive infrared (DIR) technology can be used to sense absolute humidity or dew point. It is similar to technology used to sense carbon dioxide or other gases. Infrared water vapor sensors are optical sensors that detect the amount of water vapor in air based on the infrared light absorption characteristics of water molecules. Light absorption is proportional to the number of molecules present. An infrared hygrometer typically provides a value of absolute humidity or dew point, and can operate in diffusion or flow-through sample mode. This type of humidity sensor is unique in that the sensing element (a light detector and an infrared filter) is behind a transparent window and is never exposed directly to the sample environment. As a result, this sensor has excellent long-term stability, long life, and fast response time; is not subject to saturation; and operates equally well in very high or low humidity. Previously used solely for high-end applications, infrared hygrometers are now commonly used in HVAC applications because they cost about the same as mid-range-accuracy (1 to 3%) humidity sensors.
Pressure Transmitters and Transducers
A pneumatic pressure transmitter converts a change in absolute, gage, or differential pressure to a mechanical motion using a bellows, diaphragm, or Bourdon tube mechanism. When connected through appropriate links, this mechanical motion produces a change in air pressure to a controller. In some instances, sensing and control functions are combined in a single component, a pressure controller.
An electronic pressure transducer may use mechanical actuation of a diaphragm or Bourdon tube to operate a potentiometer or differential transformer. Another type uses a strain gage bonded to a diaphragm. The strain gage detects displacement resulting from the force applied to the diaphragm. Capacitance transducers are most often used for measurements below 1 in. of water because of their high sensitivity and repeatability. Electronic circuits provide temperature compensation and amplification to produce a standard output signal.
Orifice plate, pitot-static tube, venturi, turbine, magnetic flow, thermal dispersion, vortex shedding, and ultrasonic meters are some of the technologies used to sense fluid flow. In general, pressure differential devices (orifice plates, venturi, and pitot tubes) are less expensive and simpler to use, but have limited range; thus, their accuracy depends on how they are applied and where in a system they are located.
More sophisticated flow devices, such as turbine, magnetic, and vortex shedding meters, usually have better range and are more accurate over a wide range. If an existing piping system is being considered for retrofit with a flow device, the expense of shutting down the system and cutting into a pipe must be considered. In this case, a noninvasive meter, such as an ultrasonic flow meter, may be cost effective.
There are two types of ultrasonic flow meters. One uses the Doppler effect, which is better for monitoring flow in slurry applications. The other type uses the transit time effect, which is more accurate at lower flows and with standard nonslurry fluids.
For air velocity metering, pitot-static tubes provide a naturally larger signal change at high velocities, with limitations on their application below 500 to 600 fpm. Vortex shedding for airflow applications has similar low-velocity limitations. Thermal dispersion sensors provide a naturally larger signal change at lower velocities without appreciable losses through velocities common in most ventilation systems, which makes them more suitable for applications below 1000 fpm.
Indoor Air Quality Sensors
Indoor air quality control can be divided into two categories: ventilation control and contamination protection. In spaces with dense populations and intermittent or highly variable occupancy, ventilation can be more efficiently applied by detecting changes in population or ventilation requirements [demand-controlled ventilation (DCV)]. This involves using time schedules and population counters, and measuring the indoor/outdoor differential levels of carbon dioxide (CO2) or other contaminants in a space. Changes in differential CO2 mirror changes in space population; thus, the amount of outdoor air introduced into the occupied space can then be controlled. Demand control helps maintain proper ventilation rates at all levels of occupancy. Control set-point levels for carbon dioxide are determined by the specific relationships between differential CO2, rate of CO2 production by occupants, the variable airflow rate required by the changing population, and a fixed amount of ventilation required to dilute building-generated contaminants unrelated to CO2 production. ASHRAE Standard 62.1 and its user’s manual (ASHRAE 2013) provide further information on ventilation for acceptable indoor air quality and DCV for single-zone systems.
Contamination protection sensors monitor levels of hazardous or toxic substances and issue warning signals and/or initiate corrective actions through the building automation system (BAS). Sensors are available for many different gases. The carbon monoxide (CO) sensor is one of the most common, and is often used in buildings wherever combustion occurs (e.g., parking garages). Refrigerant-specific sensors are used to measure, alarm, and initiate ventilation purging in enclosed spaces that house refrigeration equipment, to prevent occupant suffocation upon a refrigerant leak (see ASHRAE Standard 15 for more information). The type selected, substances monitored, and action taken in an alarm condition all depend on where these sensors are applied.
Analog lighting level transmitters packaged in various configurations allow control of ambient lighting levels using building automation strategies for energy conservation. Examples include ceiling-mounted indoor light sensors used to measure room lighting levels; outdoor ambient lighting sensors used to control parking, general exterior, security, and sign lighting; and interior skylight sensors used to monitor and control light levels in skylight wells and other atrium spaces.
Power Sensing and Transmission
Passive electronic devices that sense the magnetic field around a conductor carrying current allow low-cost instrumentation of power circuits. A wire in the sensor forms an inductive coupling that powers the internal function and senses the level of the power signal. These devices can provide an analog output signal to monitor current flow or operate a switch at a user-set level to turn on an alarm or other device.
An HVAC controller reads sensors’ signals and regulates control devices to achieve one or more objectives, which may include maintaining comfort, minimizing energy use, and ensuring safe operation and environmental conditions. Controllers can use other sources of information to determine their output, such as schedules, tables, operator commands, and weather forecasts. Controllers may also collect data about the processes and their own operation to help monitor, diagnose, and tune the processes’ operation. Digital controllers perform the control functions using a microprocessor and control algorithms. The sensors and controller can be combined in a single instrument, such as a room thermostat, or they may be separate devices.
Digital controls use microprocessors to execute software programs that are customized for use in commercial buildings. Controllers use sensors to measure values such as temperature and humidity, perform control routines in software programs, and exert control using output signals to actuators such as valves and electric or pneumatic actuators connected to dampers. The operator may enter parameters such as set points, proportional or integral gains, minimum on and off times, or high and low limits, but the control algorithms make the control decisions. The controller scans input devices, executes control algorithms, and then positions the output device(s), in a stepwise scheme. The controller calculates proper control signals digitally rather than using an analog circuit or mechanical change, as in electric/electronic and pneumatic controllers. Use of digital controls in building automation is referred to as direct digital control (DDC).
Digital controls can be used as stand-alones or can be integrated into building management systems (BMSs) through network communications. Simple controls may have a single control loop that can perform a single control function (e.g., temperature control of a unit ventilator); larger versions can control a larger number of loops or even perform complex strategies such as managing energy allocation to multiple processes and open loop controls, and balancing multiple objectives (e.g., comfort, energy consumption, equipment wear).
Advantages of digital controls include the following:
-
Sequences or equipment can be modified by changing software, which reduces the cost and diversity of hardware necessary to achieve control.
-
Features such as demand setback, reset, data logging, diagnostics, and time-clock integration can be added to the controller with small incremental cost.
-
Precise, accurate control can be implemented, limited by the resolution of sensor and analog-to-digital (A/D) and digital-to-analog (D/A) conversion processes. PID and other control algorithms can be implemented mathematically and can adjust performance based on sophisticated algorithms.
-
Controllers can communicate with each other using open or proprietary networking (e.g., Ethernet or RS-485) standards.
A single control that is fixed in functionality with flexibility to change set points and small configurations is called an application-specific controller. Many manufacturers include application-specific controls with their HVAC equipment, such as air-handling units and chillers.
Firmware and Software. Preprogrammed control routines, known as firmware, are sometimes stored in permanent memory such as programmable read-only memory (PROM) or electrically programmable read-only memory (EPROM), and the application or set points are stored in changeable memory such as electrically erasable programmable read-only memory (EEPROM). The operator can modify parameters such as set points, limits, and minimum off times within the control routines, but the primary program logic cannot be changed without replacing the memory chips.
User-programmable controllers allow the algorithms to be changed by the user. The programming language provided with the controller can vary from a derivation of a standard language to custom language developed by the controller’s manufacturer, to graphically based programming. Preprogrammed routines for proportional, proportional plus integral, Boolean logic, timers, etc., are typically included in the language. Standard energy management routines may also be preprogrammed and may interact with other control loops where appropriate.
Digital controllers can have both preprogrammed firmware and user-programmed routines. These routines can automatically modify the firmware’s parameters according to user-defined conditions to accomplish the control sequence designed by the control engineer.
Operator Interface. Some digital controllers (e.g., a programmable room thermostat) are designed for dedicated purposes and are adjustable only through manual switches and potentiometers mounted on the controller. This type of controller cannot be networked with other controllers. A direct digital controller can have manually adjustable features, but it is more typically adjusted either through a built-in LED or LCD display, a hand-held device, or a terminal or computer. The direct digital controller’s digital communication allows remote connection to other controllers and to higher-level computing devices and host operating stations.
A terminal allows the user to communicate with the controller and, where applicable, to modify the program in the controller. Terminals can range from hand-held units with an LCD display and several buttons to a full-sized console with a video monitor and keyboard. The terminal can be limited in function to allow only display of sensor and parameter values, or powerful enough to allow changing or reprogramming the control strategies. In some instances, a terminal can communicate remotely with one or more controllers, thus allowing central displays, alarms, and commands. Usually, hand-held terminals are used by technicians for troubleshooting, and full-sized, fully functional terminals are used at a fixed location to monitor the entire digital control system. Standard Internet browsers can sometimes be used to access system information, complemented with online help and application libraries, plus cloud-based troubleshooting and graphic user interface design tools.
Electric/Electronic Controllers
For two-position control, the controller output may be a simple electrical contact that starts a fan or pump, or one that actuates a spring-return valve or damper actuator. Electrical contacts can be normally open (NO), normally closed (NC), or have one of each (double throw). An output that has three terminals (common, NO, and NC) is called single-pole, double-throw (SPDT). SPDTs simplify designs, because the same device can be used as NO or NC depending on the requirements of the application. In some cases, both contacts are used (e.g., to send a signal to one device or another, depending on whether the system is in cooling or heating mode). Both single-pole, single-throw (SPST) and SPDT circuits can be used for timed two-position action.
Floating control uses two NO output contacts with a neutral zone where neither contact is made. This control is used with reversible motors; it has a slow response and a wide throttling range.
Output for floating control is a SPDT switching circuit with a neutral zone where neither contact is made. This control is used with reversible motors; it has a slow response and a wide throttling range.
Pulse modulation control is an improvement over floating control. It provides closer control by varying the duration of the contact closure. As the actual condition moves closer to the set point, the pulse duration shortens for closer control. As the actual condition moves farther from the set point, the pulse duration lengthens.
Proportional control gives continuous or incremental changes in output signal to position an electrical actuator or controlled device.
Pneumatic Receiver-Controllers
Pneumatic receiver-controllers are normally combined with pneumatic elements that use a mechanical force or position reaction to the sensed variable to obtain a variable-output air pressure. Control is usually proportional, but other modes (e.g., proportional-plus-integral) can be used. These controllers are generally classified as nonrelay or relay, and as direct-acting or reverse-acting.
The nonrelay (single-pipe) pneumatic controller uses low-volume output. A relay (two-pipe) pneumatic controller actuates a relay device that amplifies the air volume available for control. The relay provides quicker response to a variable change.
Direct-acting controllers increase the output signal as the controlled variable increases. Reverse-acting controllers increase the output signal as the controlled variable decreases. For example, a reverse-acting pneumatic thermostat increases output pressure when the measured temperature drops and decreases output pressure when the measured temperature rises.
Thermostats combine sensing and control functions in a single device. Microprocessor-based thermostats have many of the following features.
-
An occupied/unoccupied or dual-temperature room thermostat controls at another set-point temperature at night. It may be indexed (changed from occupied to unoccupied) individually or in a group by a manual switch, an electronic occupancy sensor, or time switch from a remote point. Some electric units have an individual clock and switch built into the thermostat.
-
A pneumatic day/night thermostat uses a two-pressure air supply system (often 13 and 17 psig, or 15 and 20 psig). Changing pressure at a central point from one value to the other actuates switching devices in the thermostat that index it from occupied to unoccupied or vice versa.
-
A heating/cooling or summer/winter thermostat can have its action reversed and its set point changed by indexing. It is used to actuate control devices (e.g., valves, dampers) that regulate a heating source at one time and a cooling source at another.
-
A multistage thermostat operates two or more successive steps in sequence.
-
A submaster thermostat has its set point raised or lowered over a predetermined range in accordance with variations in output from a master controller. The master controller can be a thermostat, manual switch, pressure controller, or similar device.
-
A dead-band thermostat has a wide differential over which the thermostat remains neutral, requiring neither heating nor cooling. This differential may be adjustable up to 10°F. The thermostat then controls to maximum or minimum output over a small differential at the end of each dead band (Figure 16).
2.4 AUXILIARY CONTROL DEVICES
Auxiliary control devices for electric systems include the following:
Relays provide a means for one electrical source to switch to a different electrical circuit. The switched voltage may be the same or different. Relay configurations include several variations:
-
Shape and number of electrical connections
-
Optional override button and/or LED indication
-
Base or panel mount
-
Electromechanical or solid state
-
Normally open or normally closed (or both)
-
Latching or nonlatching
Electric relays can be used to start and stop electric heaters, burners, compressors, fans, pumps, or other apparatus for which the electrical load is too large to be handled directly by the controller. Other uses include time-delay and circuit-interlocking safety applications. Form letters are part of an industry consensus that defines the arrangement of contacts for relays and switches. The three most common types in HVAC are forms A, B, and C. Form A relays are single pole, single throw, normally open (SPST-NO). Form B relays are single pole, single throw, normally closed (SPST-NC). Form C relays are single pole, double throw (SPDT) and can be either normally open or normally closed, so control panels can be built using all form C (SPDT) relays. In small sizes, the added cost of the second contact is insignificant. As current ratings go up, forms A and B become more cost effective.
Time-delay relays, similar to control relays, include an adjustable time delay that is set using dipswitches and/or a knob. The device is either a delay-on-make (on delay) or delay-on-break (off delay). The time delay is either in seconds to minutes or minutes to hours. Uses include preventing multiple pieces of equipment from starting simultaneously and overloading the electrical supply, ensuring equipment completes its warm-up cycle, preventing triggering of nuisance alarms during short transitions (e.g., before equipment has reached enough speed for its status sensors to activate), and temporarily changing the mode of operation (e.g., thermostat override timer during unoccupied hours).
Power relays handle high-power switching of electrical loads in motor control centers and lighting control applications. They may be of open-frame construction or enclosed, single or multiple pole, panel mounted or field mounted, with or without auxiliary contacts.
Solid-state relays are optically isolated relays used to switch voltages up to 600 V with high amperage loads using a form A contact. They have a high surge dielectric strength, and reverse voltage protection. They operate using an input voltage of 4 to 32 V DC. These devices are easily affected by high temperatures and induced currents, but their life expectancy, measured in number of operations, is much greater than that of electromechanical switches, so they are used wherever switching every few minutes or seconds is required, as in pulse-width modulation (PWM) controls.
Control relay sockets are used with control relays to terminate all the wires that need to be connected to the relay. They may have either blade- or pin-type terminals. Sockets make wiring easier (without the relay getting in the way), provide a way to ensure equipment is not started until the system is commissioned, and allow relay replacement without redoing the wiring terminations.
Auxiliary contacts are sometimes used to determine equipment status. The auxiliary contacts close when the starter’s contactor closes, so they do not account for broken belts, couplings, or wires; locked rotors; flow obstructions; or missing power.
Differential pressure switches are used for status indication for air filters, fans, and pumps. Additionally, they can be used to provide flow and level status and in safety circuits to protect system components.
Current switches are current-sensing relays used to monitor the status of electrical devices. Typically, they have one or more adjustable current set points. They should be adjusted at start-up so that if the fan or pump motor coupling breaks, the current switch does not indicate on status.
Paddle switches indicate flow of water or air and are used to sense the status of pumps and fans.
Equipment with embedded controls such as boilers, chillers, terminal units, and variable-speed pumps and fans usually provide their status through contacts and over serial communication.
Limit switches convert mechanical motion into a switching action. Common applications include valve and damper position and proximity feedback.
Manual switches, either two-position or multiple-position with single or multiple poles, are used to switch equipment from one state to another.
Auxiliary switches on electric or electronic equipment, such as valve and damper actuators, sensors, and variable-speed controls are used to select a sequence or mode of operation.
Moisture switches are used to detect moisture in drain pains, under raised floors, and in containment areas to shut down equipment and/or alert operators before flooding or damage occurs.
Level switches (float, conductive probe, or ultrasonic) are used to start/stop equipment, either in normal operation, such as supply or drain pumps, or in protection circuits, as in boilers or chillers.
Time switches (mechanical or electronic) turn electrical loads on and off, based on a 24 h/7 day or 24 h/365 day schedule.
Analog time switches are set manually to control an electrical load. They have either normally open or normally closed contacts. Timing is either in minutes or hours, and may have an override hold feature to keep the load on or off continuously.
Digital time switches are set manually to control an electrical load and have either normally open or normally closed contacts. The timing function is either in minutes or hours, and sometimes combines a regular weekly calendar with a yearly exceptions calendar used for holidays and other special events. They may have an override hold feature to keep the load on or off continuously, and a flash or beeper option to notify the operator that the load will be turning off shortly.
Transducers are devices that convert one signal (sensor reading or command) into a signal of another type that conveys some or all of the original information. Examples include pressure into voltage, voltage into current, voltage into contact closure, and rotational speed into pulse frequency. Transducers may convert proportional input to either proportional or two-position output.
The electronic-to-pneumatic transducer (EPT is used in many applications. It converts a proportional electronic output signal into a proportional pneumatic signal and can be used to combine electronic and pneumatic control components to form a control loop (Figure 17). Electronic components are used for sensing and signal conditioning, whereas pneumatic components are used for actuation. The electronic controller can be either analog or digital.
The EPT presents a special option for retrofit applications. An existing HVAC system with pneumatic controls can be retrofitted with electronic sensors and controllers while retaining the existing pneumatic actuators (Figure 18).
Signal transducers to change one standard signal into another. Variables usually transformed include voltage [0 to 10, 0 to 5, 2 to 10 V (DC)], current (4 to 20 mA), resistance (0 to 135 Ω), pressure (3 to 15, 0 to 20 psig), phase cut voltage [0 to 20 V (DC)], pulse-width modulation, and time duration pulse. Signal transducers allow use of an existing control device in a retrofit application.
Other Auxiliary Control Devices
Variable-frequency drives (VFDs) control AC motors’ speed by using electronics to vary the frequency and voltage amplitude of the electrical input power. VFDs are commonly applied to fans, heat recovery wheels, pumps, and compressors.
Occupancy sensors are used to automatically adjust controlled variables (e.g., lighting, ventilation rate, temperature) based on occupancy.
Potentiometers are used for manual positioning of proportional control devices, for remote set-point adjustment of electronic controllers, and for position feedback.
Smoke detectors sense smoke and other combustion products in air moving through HVAC ducts. Through sampling tubes, selected based on duct size, they test air moving in the duct. For duct applications, using only photoelectric sensor heads is recommended. The device typically has two alarm contacts, used to shut down the associated equipment and provide remote indication, and a trouble contact, which monitors incoming power and removal of the detector head. Where a fire alarm system is installed, the smoke detectors must be listed for use with the fire alarm system. Addressable fire alarm systems may use a separate programmable relay for fan shutdown rather than a hard-wired connection to the detector.
Transient voltage surge suppressors (TVSSs), formerly called lightning arrestors, protect communication lines and critical power lines between buildings or at building entrance vaults against high-voltage transients caused by VFDs, motors, transmitters, and lightning. To be effective, they must be grounded to a grounding rod in compliance with the National Electrical Code® (NFPA Standard 70) or local equivalent, and the manufacturer’s recommendations.
Transformers provide current at the required voltage.
Regulated DC power supply devices convert AC voltage into a DC voltage, kept constant independently of the current draw, and usually between 12 and 24 V DC. They may be used to power temperature, pressure, and humidity transmitters.
Fuses are safety devices with a specific amp rating, used with power supplies, circuit boards, control transformers, and transducers. They may be rated for either high or low inrush currents, and are available in slow-blow or fast-acting models.
Step controllers operate several switches in sequence using a proportional electric or pneumatic input signal. They are commonly used to control several steps of heating or refrigeration capacity. They may be arranged to prevent simultaneous starting of compressors and to alternate the sequence to equalize wear.
Power controllers control electric power input to resistance heating elements. They are available with various ratings for single- or three-phase heater loads and are usually arranged to regulate power input to the heater in response to the demands of the proportional electronic or pneumatic controllers. Silicon controlled rectifiers (SCRs) are the most common form of power controller used for electric heat. Solid-state controllers in fast-switching two-position control modes are used because they are without mechanical contacts, which wear out too quickly to be of practical use for this application, and can arc when power is applied or removed.
High-temperature limits are safety devices that shut down equipment when the temperature exceeds the high limit set point. They are typically set at 125 to 150°F for heating air applications and 195 to 205°F for hot-water applications. A manual or automatic reset reactivates the device once the condition has cleared.
Low-temperature limits for ducts are used to protect chilled-water and preheat coils from freezing. They typically have a 20 ft long vapor-charged sensing element, set at 35°F, that shuts down equipment when the temperature in any 12 or 18 in. section falls below its set point. They may be manually or automatically reset. The device must be mounted parallel to the coil tubes with capillary mounting clips for proper measurement. Limits may be either SPST or double-pole, double-throw (DPDT), with the second contact used to alert operators that the device has tripped.
Three- and five-valve manifolds protect water differential pressure sensors from overpressurization during installation, start-up, shutdown, system testing, and maintenance. Three-valve manifolds are comprised of two isolation valves and a bypass valve. A five-valve manifold includes two additional valves to allow online calibration. Depending on the application, snubbers may be required, as well.
Snubbers, made of brass or stainless steel, stop shocks and pulsations caused by fluid hammering and system surges. Two types of pressure snubbers are used in HVAC applications: porous and piston. A porous snubber has no moving parts and uses a porous material to stop device damage. A piston snubber uses a moving piston inside a tube that moves up and down to stop device damage and push away any sediment or scale that may clog the system’s monitoring devices. Depending on the application, the type of piston to be used may need to be specified.
Steam pigtail siphons protect pressure transmitters from the high temperature of steam. They are typically made from steel or stainless steel of a specific length with a loop. The temperature of the medium being monitored determines the length and material. Most pressure devices have an operating temperature range of 0 to 200°F.
Thermostat guards are plastic or metal covers that protect switches, thermostat controllers, and sensors from damage, tampering, and unauthorized adjustment.
Enclosures/control panels may be used indoors or outdoors to protect equipment and people. In North America, enclosures are rated by the National Electrical Manufacturers Association (NEMA Standard 250) and Electrical and Electronic Manufacturer Association of Canada (EEMAC); elsewhere, they receive an ingress protection (IP) rating, which describes their degree of resistance to ingress of objects, dust, and water (IEC Standard 60529).
Pilot lights are replaceable incandescent or light-emitting diode (LED) lights that indicate the status or mode of operation of mechanical and electrical equipment. They are panel-mounted, and may be round or flat, of various colors, and powered using either AC or DC power. They are typically installed in an enclosure rated for the application under NEMA Standard 250, or with an appropriate IP rating.
Strobes use a high-intensity xenon flash tube to generate a high-intensity light that is visible in all directions. If this device is used in a safety application (e.g., refrigeration monitoring), in the United States, it must comply with UL Standard 1971 and the Americans with Disabilities Act (ADA), Title III; in Canada, with ULC Standard S526; elsewhere, it must meet requirements of British Standards Institution (BSI) Standard BS EN 54–23.
Horns provide an audible tone with a specified loudness rated in decibels (dB), and are mounted in a panel or junction box. The tone may be continuous, warbled, short beeps, or long beeps. The tone should be at least 10 dB above the ambient noise level in the area that the device is mounted. The operating voltage may be either DC or AC. When used in a life safety application, it must comply with NFPA Standard 72 or BSI Standard BS EN 54-3.